Warnings are intended to warn people of possible injuries and to avoid personal injury and damage to the product. They relate to individual actions with and on the product.
Indicates an immediately dangerous situation.
Serious injury or death will result if the danger is not avoided.
Action step to escape the situation.
Serious injury or death may result if the danger is not avoided.
Minor or moderate injury may result if the danger is not avoided.
Indicates a situation that may result in property damage.
If the situation is not avoided, impaired work results, material damage to the product or other property are the possible consequences.
Action step to avoid the situation.
Safety instructions are designed to ensure safe product use. They are preventive and help to inform users about the fundamental risks involved when dealing with the product. They do not refer specifically to individual actions with and on the product.
Incorrect operation or misuse
IMPORTANT!
Tampered-with and non-functioning protection devices
The device may be damaged
When installing devices with ventilation slots, ensure that the ambient air can enter and exit unhindered through the vents. When selecting the installation site, observe the protection class (IP).
Operation or storage of the machine outside the stipulated area will be deemed as not in accordance with the intended purpose.
For exact information on permitted environmental conditions, please refer to the technical data.
During operation, due to the high electrical voltages and currents, local electromagnetic fields (EMF) are generated. These occur in the immediate vicinity of the inverter and the Fronius system components. Electromagnetic fields are also present in the area of the PV modules and their supply lines.
As long as the intended use and a minimum distance of 20 cm are observed, all limit values for human exposure are observed.
If the limit values are complied with, according to current scientific knowledge, no negative health effects from EMF exposure are to be expected. For persons with prostheses1) or active physical aids2), there is a possible health risk in the vicinity of photovoltaic system components. To avoid possible health risks, consult with the responsible doctor.
1) e.g., implants or metal parts
2) e.g., pacemaker, insulin pump, hearing aid, etc.
Connection of a point in the device, system or installation to earth to protect against electric shock in the event of a fault. When installing the Tauro inverter, the PE connection is mandatory as it is a protection class 1 device. When connecting the PE conductor, ensure that it is secured against accidental disconnection. All points listed under "Connecting the inverter to the public grid (AC side)" must be observed, including the use of washers, screw locks, and nuts with the defined torque.
It must be ensured that when using the strain-relief devices, the ground conductor is the last to be disconnected in the event of a possible failure. When connecting the ground conductor, the minimum cross-section requirements specified by the respective national regulations must be observed. In addition, the minimum cross-section of the PE conductor must be at least half of the phase cross-sections according to the product standard IEC 62109-1, as a cross-section of at least 35 mm² (50 kW) or 70 mm² (99.99 / 100 kW) must be used for the phases (L1 / L2 / L3).
In principle, Tauro inverters are maintenance-free. If maintenance work is nevertheless carried out on the inverter, such as cleaning or replacing components, this must be done in consultation with a Fronius-trained service technician. The manufacturer accepts no liability for damage caused by improper use.
All the work and functions described in this document must only be carried out by trained and qualified personnel.
Read and understand this document.
Read and understand all the Operating Instructions for the system components, especially the safety rules.
Danger from electromagnetic fields. Electromagnetic fields are generated during operation.
Effects on the health of persons (e.g., those wearing a pacemaker) can result.
Do not remain closer than 20 cm from the inverter for a prolonged period of time.
The inverter offers the option to use the integrated AC relays as section switches in conjunction with a central grid and system protection unit (in accordance with VDE-AR-N 4105:2018:11 § 6.4.1). For this purpose, integrate the central trigger device (switch) into the WSD chain as described in chapter (→) on page WSD (wired shutdown).
Grid and system protection for systems with multiple invertersThe wired shutdown (WSD) interrupts the inverter's grid power feed if the trigger device (switch, e.g., Emergency Stop or fire alarm contact) has been activated.
If an inverter (slave) fails, it is bypassed and the other inverters continue operating. If a second inverter (slave) or the inverter (master) fails, the operation of the entire WSD chain is interrupted.
For installation, see Installing the WSD (wired shutdown) on page (→).
The inverter is equipped with an RCMU (RCMU = residual current monitoring unit) according to IEC 62109-2 and IEC63112.
It monitors residual currents from the PV module up to the AC output and disconnects the inverter from the grid when an improper residual current is detected.
| The surge protection device (SPD) protects against temporary overvoltages and diverts surge currents (e.g., lightning strike). Based on an overall lightning protection concept, the SPD contributes to the protection of the photovoltaic system components. | |
| If the surge protection device is triggered, the color of the indicator changes from green to red (mechanical display). A triggered SPD must be replaced with a fully functional SPD immediately by an authorized specialist company in order to maintain the full protective function of the device. | |
| It is possible to enable the option of digitally displaying the triggering of an SPD. If you wish to set this function, refer to the PDF "SPD Triggering / Temporary SPD Triggering" in the Service & Support area at www.fronius.com |
IMPORTANT!
After setting the function described above, the inverter also responds if the 2-pole signal cable of the surge protection device is damaged or is subject to an interruption.
Note: Replacing a device does not automatically result in replacement of the existing SPDs.
There is a device variant with arc detection AFCI (ArcFault Circuit Interrupter).
An AFCI protects against arc faults and is a protection device in the event of contact faults. The AFCI evaluates faults that occur in the current and voltage flow using an electronic circuit and shuts down the circuit if a contact fault is detected. This prevents overheating and possible fires at poor contact points.
IMPORTANT! Active PV module electronics (e.g., power optimizers) can impair the function of the Arc Fault Circuit Interrupter. We cannot guarantee that the Arc Fault Circuit Interrupter will work correctly in combination with active PV module electronics.
Arc faults due to faulty or incorrect DC installation
Risk of fire as well as serious injuries and damage to the inverter and PV system.
Connection work must be carried out in accordance with the technical specifications.
Check the plug connections to ensure that they are in proper condition.
Professionally repair faulty insulation.
IMPORTANT! Despite the integrated Arc Fault Circuit Interrupter and arc interruption, damage to the device as well as to other system components may occur (e.g., due to a parallel arc).
Reconnection behavior
The inverter interrupts grid power feed operation and stops PV power generation after an arc has been detected. The configuration in the Country Setup > Safety > DC Arc Fault Protection menu item determines whether or not the inverter automatically resumes PV power generation and grid power feed operation. If more arcs have been detected within 24 hours than are set in Automatic Reconnects, a manual reconnection needs to be performed.
If one of the following safety devices trips, the inverter will change to a safe state:
In the safe state, the inverter no longer feeds into the grid and is disconnected from the grid by opening the AC relays.
Technical data, warning notices, labels, and safety symbols are located on and in the inverter. This information must be kept in a legible condition and must not be removed, covered, pasted over, or painted over. The notices and symbols warn against incorrect operation that may result in serious injury and damage.
Symbols on the rating plate: | |
CE label – confirms compliance with applicable EU directives and regulations. | |
UKCA marking – confirms compliance with applicable UK directives and regulations. | |
WEEE marking – waste electrical and electronic equipment must be collected separately and recycled in an environmentally sound manner in accordance with the European Directive and national law. | |
RCM marking – tested according to the requirements of Australia and New Zealand. | |
ICASA marking – tested according to the requirements of the Independent Communications Authority of South Africa. | |
CMIM marking – tested according to IMANOR requirements for import regulations and compliance with Moroccan standards. | |
Safety symbols: | |
Risk of serious injury and property damage due to incorrect operation. | |
Dangerous electrical voltage. | |
Wait until the capacitors have discharged before opening the device. | |
Warning notice text:
WARNING!
An electric shock can be fatal. Before opening the device, ensure that the input and output sides are de-energized and isolated.
Safety symbols: | |
WARNING!
Application notes
Software
Example: Click Save.
Instructions for action
This document provides detailed information and instructions to ensure that people can use the machine safely and efficiently.
The information is intended for the following groups of people:Regardless of any qualifications, only perform the activities listed in this document.
The definition of professional qualifications and their applicability are subject to national law.
When you connect your device (and any associated devices) to the internet, the following device and operating data (device ID/identifier, device IP address, device time, configuration settings, hardware and software information, device status log files, serial number) is sent automatically to
Fronius International GmbH, Froniusstraße 1, 4643 Pettenbach, Austria, telephone +43(0) 7242241-0, email: contact@fronius.com (controller)
and stored.
The processing of this device and operating data is carried out for the purpose of ensuring the operational safety of the device (time synchronization, provision of updates). This processing is therefore necessary for the functionality of the device and thus for the fulfillment of the contract (Art. 6 (1) (b) GDPR).
If you do not wish to have such data processed, you must manually disable the device's internet connection.
In addition, the device and operating data is also processed for the purpose of providing services as part of a supplementary digital service for your device (such as solar.web or similar) as soon as you have registered your device with such a digital service (identification). This data is processed to provide the requested digital services and is therefore necessary for the fulfillment of the contract (Art. 6 (1) (b) GDPR).
Furthermore, this data processing is also carried out for maintenance and support purposes and for handling customer concerns as well as in warranty and guarantee cases (only in individual cases and given connection between device and internet). In this context, the device and operating data may also be passed on to our cooperation partners (third-party providers and suppliers). The processing of this data is necessary for maintenance and support purposes or for processing warranty and guarantee cases and thus for the fulfillment of the contract (Art. 6 (1) (b) GDPR).
Device and operating data are also processed for analysis and diagnostic purposes in order to gain insights into the functionality of the devices and improve them accordingly. This data processing is based on our legitimate interest (Art. 6 (1) (f) GDPR).
We store this data for as long as it is necessary to fulfill the existing contract with you. Any storage beyond this is carried out for legal reasons or if we have a legitimate interest in doing so. For more information on data processing for the solar.web-digital service, as well as our general privacy policy and your rights as a data subject, please visit https://www.fronius.com.
The inverter transforms the direct current generated by the PV modules into alternating current. This alternating current is fed into the public grid and synchronized with the mains voltage in use.
The inverter has been designed exclusively for use in grid-connected photovoltaic systems. It cannot generate electric power independently of the grid.
The inverter also has a design and functions that ensure it can offer maximum safety during installation and during operation.
With the "AC Daisy Chain" inverter version, the AC lead can be fed directly from the inverter to another inverter. Several Tauro inverters, up to an output power of max. 200 kW, can be thereby be quickly connected to one another.
The minimum cable cross-section is defined by the fuse at the mains connection point. A larger cable cross-section can be selected at any time. The applicable national standards must be taken into account and applied.
Only applies to device types Fronius Tauro 50-3-D / Eco 50-3-D / Eco 99-3-D / Eco 100-3-D (direct):
String fuses are used in the Fronius Tauro to provide additional protection for the solar modules.
The maximum short circuit current Isc, the maximum module return current IR or the maximum string fuse rating specified in the module data sheet of the respective solar module is crucial in affording the solar modules the correct fuse protection.
The national regulations regarding fuse protection must be observed. The electrical engineer carrying out the installation is responsible for the correct choice of string fuses.
To replace the string fuses, see chapter Replacing the string fuses on page (→).
System owners and installers can easily monitor and analyze the PV system using Fronius Solar.web or Fronius Solar.web Premium. With the appropriate configuration, the inverter transmits data such as power, yield, load, and energy balance to Fronius Solar.web. More detailed information can be found at Solar.web - Monitoring & analysis.
Configuration is carried out via the Setup wizard, see chapter Installation with the app or Installation with the browser.
Requirements for configuration:| * | These specifications do not provide an absolute guarantee of flawless operation. High error rates in the transmission, fluctuating receptions or misfires can have an adverse effect on data transfer. Fronius recommends on-site testing to ensure that the connections meet the minimum requirements. |
The inverter can be found via the Multicast DNS (mDNS) protocol. We recommend searching for the inverter using the assigned host name.
The following data can be called up via mDNS:The inverter is designed exclusively to convert direct current from PV modules into alternating current and feed this power into the public grid.
Intended use also includes following all information from the operating instructions.
The inverter is designed exclusively to be connected and used with PV modules.
Use with other DC generators (e.g., wind generators) is not permitted.
When configuring the photovoltaic system, make sure that all photovoltaic system components are operating exclusively within their permitted operating range.
All measures recommended by the PV module manufacturer for maintaining the PV module properties must be followed.
The inverter is fully automatic. Starting at sunrise, as soon as the PV modules are generating enough energy, the inverter starts checking the PV system (insulation measurement) and the grid (mains voltage and mains frequency). If all values are within the normative framework, the system is automatically connected to the grid and grid power feed operation begins.
The control system of the inverter ensures that the maximum possible power output is drawn from the PV modules at all times. This function is called MPPT (Maximum Power Point Tracking). In the event of shady conditions affecting the PV modules, a large part of the local maximum power point (LMPP) of the PV system can still be obtained via the "Dynamic Peak Manager" function.
As dusk starts and there is no longer sufficient energy available to feed energy into the grid, the inverter shuts down the connection of the power electronics to the grid completely and stops operating. All settings and recorded data are saved.
Cooling of the inverter is performed by a forced-air ventilation system via temperature-controlled fans. Air is sucked in from the front and fed, via a sealed duct, through the AC and DC heat sink, before passing directly over the inductors and dissipating.
The sealed air duct prevents the electronics compartment from coming into contact with the ambient air. This approach largely prevents any contamination of the electronics compartment.
The fan speed and temperature of the inverter are monitored.
The variable-speed, ball-bearing mounted fans in the inverter permit the following:
When the device temperature gets too high, the inverter automatically reduces the current output power in order to protect itself. Reasons for an excessively high device temperature can be a high ambient temperature or insufficient heat dissipation (for example, when installed in containers without sufficient heat dissipation).
The output of the inverter is reduced such that the temperature will not exceed the permissible limit.
If a maximum temperature is exceeded, the inverter switches off in a safe state and resumes grid power feed operation only after the device has cooled down.
| (1) | DC disconnector Disconnects the electrical connection from the solar modules to the inverter. Depending on the device type, 2 or 3 DC disconnectors are installed. The DC disconnectors can be secured against switching on with a padlock. |
| (2) | AC disconnector option The optional AC disconnector breaks the connection from the inverter to the grid |
| (3) | Button function For further information about the button function, see Button functions and LED status indicator |
| (4) | LED status indicator For further information about the LED status indicator, see Button functions and LED status indicator |
The currents of the individual strings are visible in Solar.web under History - Devices - Channels.
Solar.web | 20 A option | 30 A option | ||||
50-3-D | ECO 50-3-D | ECO 99-3-D / | 50-3-D | ECO 50-3-D | ECO 99-3-D / | |
1 | PV1.1 | PV1.1 | PV1.1 | PV1.1 | PV1.1 | PV1.1 |
2 | PV1.2 | PV1.2 | PV1.2 | PV1.2 | PV1.2 | PV1.2 |
3 | PV1.3 | PV1.3 | PV1.3 | PV1.3 | PV1.3 | PV1.3 |
4 | PV1.4 | PV1.4 | PV1.4 | PV1.4 | PV1.4 | PV1.4 |
5 | PV2.1 | PV1.5 | PV1.5 | PV2.1 | PV2.1 | PV2.1 |
6 | PV2.2 | PV1.6 | PV1.6 | PV2.2 | PV2.2 | PV2.2 |
7 | PV2.3 | PV1.7 | PV1.7 | PV2.3 | PV2.3 | PV2.3 |
8 | PV3.1 | PV2.1 | PV2.1 | PV2.4 | PV2.4 | PV2.4 |
9 | PV3.2 | PV2.2 | PV2.2 | PV2.5 | PV2.5 | PV2.5 |
10 | PV3.3 | PV2.3 | PV2.3 | PV3.1 | PV3.1 | |
11 | PV3.4 | PV2.4 | PV2.4 | PV3.2 | PV3.2 | |
12 | PV3.5 | PV2.5 | PV2.5 | PV3.3 | PV3.3 | |
13 | PV3.6 | PV2.6 | PV2.6 | PV3.4 | PV3.4 | |
14 | PV3.7 | PV2.7 | PV2.7 | PV3.5 | PV3.5 | |
15 |
| PV3.1 |
16 |
| PV3.2 |
17 |
| PV3.3 |
18 |
| PV3.4 |
19 |
| PV3.5 |
20 |
| PV3.6 |
21 |
| PV3.7 |
22 |
| PV3.8 |
Tauro Eco 50-3-P / 99-3-P / 100-3-P |
| Tauro 50-3-P |
Above the DC connection area there is space for mounting third-party components. Components up to a maximum width of 14.5 cm (8 DU) can be mounted on the DIN rail. The components must have a temperature resistance of ‑40 °C to +85 °C.
The data communication area (Pilot PC board) is located above the DC connections in the inverter.
| Indicates the inverter operating status. |
WSD (wired shutdown) switch | Defines the inverter as the WSD master or WSD slave. |
Modbus 0 (MB0) switch | Switches the terminating resistor for Modbus 0 (MB0) on/off. |
Modbus 1 (MB1) switch | Switches the terminating resistor for Modbus 1 (MB1) on/off. |
| For operating the inverter. See chapter Button functions and LED status indicator on page (→). |
| Indicates the inverter connection status. |
LAN 1 | Ethernet connection for data communication (e.g., WiFi router, home network or, for commissioning with a laptop, see chapter Installation with the browser on page (→)). |
LAN 2 | Reserved for future functions. To avoid malfunctions, only use LAN 1. |
I/O terminal | Push-in terminal for digital inputs/outputs. See chapter Permitted cables for the data communication area on page (→). |
WSD terminal | Push-in terminal for the WSD installation. See chapter WSD (wired shutdown) on page (→). |
Modbus terminal | Push-in terminal for the installation of Modbus 0, Modbus 1, 12 V, and GND (ground). |
The V+/ GND pin provides the possibility of feeding in a voltage in the range of 12.5 to 24 V (+ max. 20%) using an external power supply unit. Outputs IO 0 - 5 can then be operated using the external voltage that has been fed in. A maximum of 1 A may be drawn per output, whereby a total of max. 3 A is permitted. The fuse protection must take place externally.
Danger from polarity reversal at the terminals due to improper connection of external power supply units.
This may result in severe damage to the inverter.
Check the polarity of the external power supply unit with a suitable measuring device before connecting it.
Connect the cables to the V+/GND outputs while ensuring the correct polarity.
IMPORTANT!
If the total output (6 W) is exceeded, the inverter switches off the entire external power supply.
| (1) | Current limitation |
The operating status LED displays the status of the inverter. In case of faults, follow the individual steps in the Fronius Solar.web live app. | |
The optical sensor is actuated by touching it with a finger. | |
The communications LED displays the connection status. To establish a connection, follow the individual steps in the Fronius Solar.web live app. |
Sensor functions | ||
| 1x | |
| 2x | |
3 seconds | ||
LED status indicator | ||
| The inverter is operating correctly. | |
| The inverter is starting. | |
| The inverter is on standby, is not operating (e.g., no energy fed into the grid at night), or is not configured. | |
| The inverter displays a non-critical status. | |
| The inverter displays a critical status and no energy is fed into the grid. | |
| The network connection is being established via WPS. | |
| The network connection is being established via WLAN AP. | |
| The network connection is not configured. | |
| A network error is displayed, the inverter is operating correctly. | |
| The inverter is performing an update. | |
There is a service message. | ||
All installed components in the PV system must be compatible with each other and have the necessary configuration options. The installed components must not restrict or negatively affect the functioning of the PV system.
Risk due to components in the PV system that are not and/or only partially compatible.
Incompatible components can restrict and/or negatively affect the operation and/or functioning of the PV system.
Only install components recommended by the manufacturer in the PV system.
Before installation, check the compatibility of components that have not been expressly recommended with the manufacturer.
Please observe the following criteria when choosing a location for the inverter:
Only install on a solid, non-flammable surface
Max. ambient temperatures: -40 °C / +65 °C
* with built-in optional AC disconnector: -30 °C / +65 °C
Relative humidity: 0 - 100%
When installing the inverter in a switch cabinet or similar closed environment, ensure adequate heat dissipation by forced-air ventilation.
When installing the inverter on the outer walls of cattle sheds, it is important to maintain a minimum clearance of 2 m between all sides of the inverter and the ventilation and building openings.
The following surfaces are permitted for installation:The DC disconnectors must always be freely accessible after installation of the inverter.
| The inverter is suitable for indoor installation. | |
| The inverter is suitable for outdoor installation. Because of its IP 65 protection class, the inverter is not susceptible to hose water on any side and can also be operated in moist environments. | |
| The inverter is suitable for outdoor installation. In order to keep inverter heating as low as possible, it is recommended that the inverter is not exposed to direct sunlight. The inverter should be installed in a protected location, for example, near the solar modules or under an overhanging roof. | |
| IMPORTANT! The inverter must not be installed or operated at more than 4000 m above sea level. | |
| Do not install the inverter:
| During certain operating phases the inverter may produce a noise. For this reason it should not be installed in an occupied living area. | |
| Do not install the inverter in:
| The inverter is designed to be dust-proof (IP 65). However, in areas of high dust accumulation, the cooling surfaces can become dusty, which can impair the thermal performance. In this case, the dust must be removed regularly. We therefore recommend not installing the inverter in areas and environments with high dust accumulation. |
| The inverter is designed to be installed vertically on a vertical wall. The optional floor racks must not be used for vertical mounting. | |
| The inverter should have a minimum inclination of 3° in a horizontal installation position so that water can run off. Mounting of the optional floor racks is recommended. The floor racks may only be used on an installation position of 0 - 45°. | |
| The inverter is suitable for installation on a sloping surface. | |
| Do not install the inverter on a sloping surface with its connection sockets at the top. | |
| Do not install the inverter at an angle on a vertical wall or column. | |
| Do not install the inverter horizontally on a vertical wall or pillar. | |
| Do not install the inverter on a vertical wall or pillar with its connection sockets facing upwards. | |
| Do not install the inverter overhanging with the connection sockets at the top. | |
| Do not install the inverter overhanging with the connection sockets at the bottom. | |
| Do not install the inverter on the ceiling. |
Danger of serious injury and damage from articles being dropped or falling over.
When transporting by crane:
Hook chains and ropes onto the suspension points only
Always hook chains and ropes onto both suspension points
Falling or toppling devices can be deadly.
When transporting the inverter by forklift or lift truck secure the inverter from falling.
Do not turn, brake, or accelerate in a sudden, jerking manner
Use the corresponding fixing materials depending on the subsurface and observe the screw dimension recommendations for the mounting bracket.
The installer is responsible for selecting the right type of fixing.
Dimensions of the mounting bracket—all dimensions in mm.
To attach the inverter to the mounting bracket, use only the screws included in the scope of delivery.
The floor racks can be ordered as an optional accessory.
Mounting the inverter on a horizontal mounting surface is not mandatory, but recommended.
Depending on the surface, different wall plugs and screws are required for floor mounting the floor racks. Wall plugs and screws are therefore not included in the scope of supply of the inverter. The installer is responsible for selecting the correct wall plugs and screws.
Do not climb onto the device!
IMPORTANT! To provide the best possible grid monitoring, the resistance in the leads to the mains connections should be as low as possible.
IMPORTANT! Only the following cables may be connected to V-type terminals:
Fine-core cables without ferrules may only be connected to the M12 threaded bolts of the grid connections using a suitable M12 cable lug;
torque = 32 Nm
Cable gland "Multicore" version
The following cable outer diameters are compatible with the larger bushing:
16 - 27.8 - 36.2 - 44.6 - 53 - 61.4 mm
For the small bushing (M32 PG gland), earth cables of 10 - 25 mm can be fed through.
Cable gland "Singlecore" version
5 M40 bushings
Cable gland "AC Daisy Chain" version
10 M32 bushings
Aluminum cables can also be connected to the AC connections.
When using aluminum cables:
Follow all national and international guidelines regarding the connection of aluminum cables.
Grease aluminum wires with appropriate grease to protect them from oxidation.
Follow the instructions of the cable manufacturer.
The temperature resistance of the AC cables must be at least 90 °C.
If cables are used that do not withstand this temperature requirement, fit the protective hose (item number: 4.251.050) over the phases (L1 / L2 / L3) and neutral conductor (N)! The grounding PE does not need to be protected with a protective hose.
With the AC daisy chain option, all phases and neutral conductors must be protected with the protective hose. This means that the AC daisy chain option requires two protective hose sets.
AC connections
Select a sufficiently large cable cross-section based on the power category and connection variant!
Power category | Connection variant | Cable cross-section |
Tauro 50-3 | Single core / multi-core | 35 - 240 mm2 * |
Optional AC disconnector | 35 - 240 mm2 * | |
Daisy chain (without AC disconnector) | 35 - 240 mm2 * | |
Tauro ECO 99-3 | Single core / multi-core | 70 - 240 mm2 * |
Optional AC disconnector | 70 - 240 mm2 * | |
Daisy chain (without AC disconnector) | 70 - 240 mm2 * |
* The cable cross-section of the neutral conductor can be reduced to 25 mm² if no local guidelines or standards require otherwise.
There is no general requirement to use a residual current circuit breaker.
Nonetheless, if a residual current circuit breaker (RCD) is used then it must be a type B with a release current of at least 1000 mA.
The inverter may be used with a maximum C355 A automatic circuit breaker.
| 50-3-D / 50-3-P | Eco 50-3-D / 50-3-P | Eco 99-3-P | Eco 99-3-D | Eco 100-3-P | Eco 100-3-D |
Recommended output overcurrent protection [A] | 80 | 80 | - | - | - | - |
Recommended output overcurrent protection [A] | 160 | 160 | 160 | 160 | 160 | 160 |
Recommended output overcurrent protection [A] | 250 | 250 | 250 | 250 | 250 | 250 |
Recommended output overcurrent protection [A] | 355 | 355 | 355 | 355 | 355 | 355 |
The clamping range of the V-type terminal is 35 - 150 mm² when delivered. The clamping range can be changed to 185 - 240 mm² by a simple modification of the V-type terminal.
An optional hole can be made on the right side of the housing at the bottom for an additional PE introduction.
Danger from faulty or incorrect holes.
This may lead to injuries to the eyes and hands as a result of flying debris and sharp edges, as well as damage to the inverter.
When drilling, wear suitable protective goggles.
Only use a step drill when drilling.
Ensure that nothing is damaged inside the device (for example connection block).
Adapt the diameter of the hole to match the corresponding connection.
Deburr the holes using a suitable tool.
Remove the drilling residues from the inverter.
Insert the screw connection in the hole and secure to the torque specified by the manufacturer.
The opening must be sealed in accordance with the protection class of the inverter!
Danger from mains voltage and DC voltage from PV modules.
Prior to any connection work, ensure that the inverter is de-energized on the AC side and the DC side.
Only an authorized electrical engineer is permitted to connect this equipment to the public grid.
Danger of damaging the inverter due to improperly connected wires.
Improperly connected wires can cause thermal damage to the inverter and may cause a fire.
When connecting AC and DC wires, make sure that all cables are secured to the inverter connections using the correct torque.
IMPORTANT! For the PE connection, the requirements defined under "Safety rules" for safe connection of the PE conductor must also be observed.
Ensure that the phases are connected in the right order: PE, N, L1, L2 and L3.
Ensure that the phases are connected in the right order: PE, PEN, L1, L2 and L3.
The PEN conductor must be produced with ends that are permanently marked blue, according to the national provisions.
When connecting, ensure that the phases are in the correct order: PE, N, L1, L2 and L3.
Alternatively, a cable with a cable lug can be connected to the M12 threaded bolts on the grid connections in order to connect the cables to the V-type terminals.
Danger due to grid voltage and DC voltage from solar modules that are exposed to light.
Prior to any connection work, disconnect the inverter on the AC side and the DC side.
Only an authorized electrical technician is permitted to connect this equipment to the public grid.
Danger of electric shock due to incorrectly connected terminals / PV plug connectors.
When connecting version D ("direct string"), ensure that every pole of a string is fed across the same PV input, e.g.:
"+ pole string 1" at input PV 1.1+ and "- pole string 1" at input PV 1.1-
Danger from DC voltage. Even when the DC disconnectors are switched off, the fuse boards (100-3-D / 99-3-D) / fuse board (50-3-D) and everything before the DC disconnectors are live.
Risk of damage to the inverter as the result of incorrectly tightened terminals.
Incorrectly tightened terminals can cause heat damage to the inverter that may result in a fire.
When connecting AC and DC cables, ensure that all the terminals are tightened to the specified torque.
Risk of damage to the inverter due to PV modules that are not connected with the correct polarity.
PV modules that are not connected with the correct polarity can cause thermal damage to the inverter.
Measure the DC cables from the PV modules and connect them to the inverter with the correct polarity.
Risk of damage to the inverter by exceeding the maximum input current per string.
Exceeding the maximum input current per string can cause damage to the inverter.
Observe the maximum input current per string for the inverter according to the technical data.
The maximum input current must not be exceeded even when using Y or T connectors.
To enable suitable PV modules to be chosen and to use the inverter as efficiently as possible, it is important to bear the following points in mind:
IMPORTANT!
Before connecting up the PV modules, check that the voltage for the PV modules specified by the manufacturer corresponds to the actual measured voltage.
IMPORTANT!
The PV modules connected to the inverter must comply with the IEC 61730 Class A standard.
IMPORTANT!
Solar module strings must not be grounded.
DC connections
Select a sufficiently large cable cross-section based on the device type! The temperature resistance of the DC cables must be at least 90 °C.
Power category | Device type | Cable cross-section |
Tauro 50-3 / Eco 50-3 / | pre-combined | 25 - 95 mm2 |
direct | 2.5 - 10 mm² (see data sheet of the plug) |
Risk of damage to the inverter as the result of incorrectly fused PV lines.
PV lines for the "pre-combined" model that are not fused can cause damage to the inverter.
PV lines must be fused in a combiner box before the inverter ("pre-combined" version).
Distribute the existing solar module strings evenly between the PV inputs (PV1 / PV2 / PV3) of the inverter.
Start with the odd inputs first and then fill the even inputs to distribute the power as evenly as possible and increase the service life of the fuses, for example: (1.1, 2.1, 3.1, 1.3, 2.3etc.).
Connect the PV cables from the solar modules to the MC4 connectors as labeled
Unused MC4 connectors on the inverter must be covered with the cover plates supplied with the inverter.
To protect the MC4 connectors, a cover plate can be mounted on the inverter. The cover plate can be ordered as an optional accessory together with the floor racks.
Solar module strings that are combined in a DC combiner box, must, according to the applicable national regulations, be fused per string in the DC combiner box!
| Before working in the connection area of the inverter, the DC voltage must be switched off. This can also be done in the DC combiner box. |
Danger due to faulty fuses.
This can lead to fires.
Only replace faulty fuses with new ones of the same rating.
Do not replace faulty fuses with bolts.
Danger due to incorrectly dimensioned string fuses
Incorrectly dimensioned string fuses can cause damage to the inverter for these connected components.
The following string fuses should be used for the -D (direct) version of the Fronius Tauro:
Max. 10 A per string → use of 15 A gPV fuse 1000 V possible (Fronius item number: 41,0007,0230 - fuse 15 1000 F PV 15A)
Max. 14.5 A per string → use of 20 A gPV fuse 1000V required (Fronius item number: 41,0007,0233 - fuse-HL 20 A 1KV fast)
Max. 22 A per string → use of 30 A gPV fuse 1000V required (Fronius item number: 41,0007,0241 - fuse-HL 30 A 1KV fast)
Danger due to DC disconnectors that are not switched on properly
Turn all existing DC disconnectors to the ON position before turning on the AC connection.
The DC disconnectors may only ever be actuated simultaneously (one immediately after the other).
The WLAN access point can be opened with the optical sensor, see chapter Button functions and LED status indicator on page (→)
The inputs M0 and M1 can be freely selected. A maximum of 4 Modbus participants can be connected to the Modbus terminal on inputs M0 and M1.
IMPORTANT!
If the function “Inverter control via Modbus” is activated in the menu area “Communication” → “Modbus”, no Modbus participants are possible. It is not possible to send and receive data at the same time.
IMPORTANT!
Cables with the following design can be connected to the terminals of the inverter:
WSD connections with push-in terminal | ||||||||||||||
Distance | Stripping length | Solid | Fine-stranded | Fine-stranded with ferrules with collar | Fine-stranded with ferrules without collar | Cable recommendation | ||||||||
100 m | 10 mm | 0.14 - 1.5 mm2 | 0.14 - 1.5 mm2 | 0.14 - 1 mm2 | 0.14 - 1.5 mm2 | min. CAT 5 UTP | ||||||||
Modbus connections with push-in terminal | ||||||||||||||
300 m | 10 mm | 0.14 - 1.5 mm2 | 0.14 - 1.5 mm2 | 0.14 - 1 mm2 | 0.14 - 1.5 mm2 | min. CAT 5 STP | ||||||||
IO connections with push-in terminal | ||||||||||||||
30 m | 10 mm | 0.14 - 1.5 mm2 | 0.14 - 1.5 mm2 | 0.14 - 1 mm2 | 0.14 - 1.5 mm2 | Single conductors possible | ||||||||
LAN connections | ||||||||||||||
Fronius recommends using at least CAT 5 STP (shielded twisted pair) cables and a maximum distance of 100 m. |
The network cabling of the inverters must be in a star arrangement. Observe the maximum lengths and requirements for the cable!
In order to be able to use the connection to Fronius Solar.web or Modbus TCP, each Tauro must be connected directly to the network via LAN.
IMPORTANT! If data communication cables are wired into the inverter, observe the following points:
Note! Ingress protection rating IP65 cannot be ensured if blanking plugs are missing or incorrectly inserted.
Remove the cap nut on the strain-relief device and press the sealing ring out from the inside of the device using the blanking plugs.
Open up the sealing ring at the location where the blanking plugs are to be removed.
* Remove the blanking plugs with a sideways motion.
First, guide the data cables through the cap nut of the strain-relief device and then through the housing opening.
Insert the sealing ring between the cap nut and the housing opening. Press the data cables into the seal's cable guide. Then press in the seal until it reaches the underside of the strain-relief device.
Connect the data cables to the data communication area using a movement loop, and fasten the cap nut with min. 2.5–max. 4 Nm.
IMPORTANT!
The push-in WSD terminal in the inverter's connection area is delivered with a bypass ex works as standard. The bypass must be removed when installing a trigger device or a WSD chain.
The WSD switch of the first inverter with connected trigger device in the WSD chain must be in position 1 (master). The WSD switch of all other inverters should be in position 0 (secondary device).
Max. distance between 2 devices: 100 m
Max. Number of devices: 28
* Floating contact of the trigger device (e.g., central grid and system protection). If several floating contacts are used in a WSD chain, these must be connected in series.
When starting the inverter for the first time, various setup settings must be configured.
If the setup is canceled before completion, the input data is not saved and the start screen with the installation wizard is shown once again. The data is saved in the event of an interruption, e.g., a power failure. Commissioning is continued at the point at which the interruption occurred after the power supply is restored. If the setup was interrupted, the inverter feeds energy into the grid at maximum 500 W and the operating status LED flashes yellow.
The country setup can only be set when starting the inverter for the first time. If the country setup needs to be changed at a later date, contact your installer/technical support.
To simplify the display, the vertical installation position of the Pilot PC board (LED display) is shown horizontally below.
The Fronius Solar.start app is required for installation. Depending on the mobile device used to perform the installation, the app is available on the relevant platform.
WiFi:
Ethernet:
IMPORTANT!
Wait for the capacitors of the inverter to discharge!
IMPORTANT!
IMPORTANT!
Depending on the authorization of the user, settings can be made in the individual menu areas.
IMPORTANT!
IMPORTANT!
All available components of the system can be added via "Add component+".
PV Generator
Activate the respective PV generator and enter the connected PV output in the relevant field.
Primary meter
For problem-free operation with further energy generators, it is important to install the Fronius Smart Meter at the feed-in point. The inverter and further generators must be connected to the public grid via the Fronius Smart Meter. This setting also has an effect on the behavior of the inverter during the night. If the function is deactivated, the inverter switches to standby mode as soon as there is no more PV power available. The message "Power low" appears. The inverter starts up again as soon as sufficient PV power is available.
After connecting the meter, select one of the following device types:
For communication via MQTT, the inverter and Smart Meter must be in the same sub-network.
The following parameters must also be defined for the Smart Meter:
Several Fronius Smart Meters can be installed in the system. The Watt value in the "Production meter" field is the sum of all the production meters. The Watt value in the "Consumption meter" field is the sum of all the secondary meters.
Ohmpilot
All the Ohmpilots available in the system are displayed. Select the desired Ohmpilot and add to the system via "Add".
PV Generator
Primary meter
Ohmpilot
Load Management
Select up to four pins for the load management. Further settings for the load management are available in the Load Management menu item.
Australia - Demand Response Modes (DRM)
Activate the slider if DRM is required. Configure the pins for control via DRM as follows:
Mode | Description | Information | Default pin |
DRM0 | Inverter disconnects from the grid | Grid relays open | |
REF GEN |
| RG0 | |
COM LOAD |
| CL0 | |
DRM0 occurs in the event of an interruption or short circuit on the REF GEN or COM LOAD lines. Or in the event of an invalid combination of DRM1—DRM8. |
IMPORTANT! If the Australia - Demand Response Modes (DRM) function is activated and no DRM control is connected, the inverter switches to standby mode.
Here, for the Australian country setup, a value for the apparent power consumption and the apparent power output can be entered.
"Force standby"
When this function is activated, the power feed from the inverter into the grid is interrupted. This makes it possible to shut down the inverter without power and protect its components. The standby function is automatically deactivated when the inverter is restarted.
"PV 1" and "PV 2"
Parameter | Value range | Description |
"Mode" | Off | The MPP tracker is deactivated. |
Auto | The inverter uses the voltage at which the maximum possible output of the MPP tracker is possible. | |
Fixed | The MPP tracker uses the voltage defined in "UDC fixed". | |
"UDC fixed" | 80 ‑ 530 V | The inverter uses the fixed voltage that is used on the MPP tracker. |
"Dynamic Peak Manager" | Off | Function is deactivated. |
On | The entire solar module string is checked for optimization potential and the best possible voltage for the supply of energy from the inverter into the grid is determined. |
"Ripple control signal"
Ripple control signals are signals that are sent by the energy company in order to switch controllable loads on and off. Depending on the installation situation, ripple control signals can be dampened or amplified by the inverter. This can be counteracted if necessary by applying the following settings.
"Reduction of influence" | Off | Function is deactivated. |
On | Function is activated. | |
"Frequency of the ripple control signal" | 100 ‑ 3000 Hz | The frequency specified by the energy company must be entered here. |
"Grid inductance" | 0.00001 ‑ 0.005 H | The value measured at the feed-in point must be entered here. |
"Measure against RCD false triggers"
(when using a 30 mA residual current circuit breaker)
A residual current circuit breaker for the AC connecting cable may be required depending on national regulations, the grid operator, and other conditions.
A type A residual current circuit breaker is generally sufficient in this case. Nevertheless, false alarms can be triggered for the type A residual current circuit breaker in individual cases and depending on local conditions. For this reason, Fronius recommends using a residual current circuit breaker suitable for frequency inverters with a release current of least 100 mA, taking into account national provisions.
Leakage current factor to reduce RCMU/FI false tripping | 0 ‑ 0.25 | By reducing the setting value, the leakage current is reduced and the intermediate circuit voltage is increased, which slightly lowers the efficiency.
Shutdown before 30 mA RCD triggers | Off | The function for reducing false tripping of the residual current circuit breaker is deactivated. |
On | The function for reducing false tripping of the residual current circuit breaker is activated. | |
Rated non-tripping fault current limit value | 0.015 ‑ 0.3 | Value of the non-tripping residual current specified by the manufacturer for the residual current circuit breaker at which the residual current circuit breaker does not switch off under specified conditions. |
"Insulation warning"
"Insulation warning" | Off | The insulation warning is deactivated. |
On | The insulation warning is activated. | |
"Insulation measurement mode"
| Exact | Insulation monitoring takes place with the highest degree of accuracy and the measured insulation resistance is displayed on the user interface of the inverter. |
Fast | Insulation monitoring takes place with a lesser degree of accuracy, whereby the time to take the insulation measurement is shortened and the insulation value is not displayed on the user interface of the inverter. | |
"Threshold for the insulation warning" | 10 ‑ | If the value drops below the threshold, status code 1083 is displayed on the user interface of the inverter. |
All available updates for inverters and other Fronius devices are provided on the product pages and in the "Fronius Download Search" area at www.fronius.com .
The guided setup wizard can be accessed here.
All settings
Resets all configuration data, apart from the country setup. Changes to the country setup may only be made by authorized personnel.
All settings without network
Resets all configuration data, apart from the country setup and the network settings. Changes to the country setup may only be made by authorized personnel.
Current messagesAll current events of the linked system components are displayed here.
IMPORTANT!
Depending on the type of event, this must be confirmed via the "tick" button so that it can be further processed.
History
All events of the linked system components that are no longer present are displayed here.
All the information regarding the system and the current settings is displayed and provided for download in this menu area.
The power data and functional scope of the inverter are stored in the license file.
If the inverter, power stage set control PCB, or the data communication area is replaced, the license file must also be replaced.
IMPORTANT!
The support user exclusively enables Fronius Technical Support to configure settings on the inverter via a secure connection. Access is deactivated by clicking the Terminate Support User Session button.
IMPORTANT!
The remote access exclusively enables Fronius Technical Support to access the inverter via a secure connection. In this case, diagnostics data are transmitted, which are used for troubleshooting. The remote access can be activated only upon request by Fronius Support.
Server addresses for data transfer
If a firewall is used for outgoing connections, allow the below protocols, server addresses, and ports for successful data transfer, see:
When using FRITZ!Box products, configure Internet access without any restrictions or limitations. Do not set the DHCP Lease Time (validity) to 0 (=infinite).
LAN:
After establishing the connection, check the connection status.
WiFi:
Activate the access point of the inverter. This is opened by touching the sensor > Communications LED flashes blue
After connecting, the status of the connection should be checked.
Access point:
The inverter serves as the access point. A PC or mobile device connects directly to the inverter. Connecting to the Internet is not possible. Assign a Network Name (SSID) and Network Key (PSK) to establish a connection. Assign a Network Key (PSK) with at least 20 characters, consisting of upper and lower case letters, special characters, and numbers, to protect the device from unauthorized access.
It is possible to operate a connection via WiFi and via the access point at the same time.
LAN:
WiFi:
Access point:
To use the Modbus TCP or the connection to Fronius Solar.web, each Tauro must be connected directly to the network via LAN.
Modbus RTU interface 0 / 1
If one of the two Modbus RTU interfaces is set to Slave, the following input fields are available:
| Baud rate |
| Parity |
| SunSpec Model Type |
| Meter address |
| Meter address |
Slave as Modbus TCP
This setting is necessary to enable inverter control via Modbus. If the function Slave as Modbus TCP is activated, the following input fields are available:
| Modbus port |
| Meter address |
| Inverter address |
| Inverter control via Modbus If this option is activated, the inverter is controlled via Modbus. Inverter control includes the following functions:
| Restrict Control |
The utility/energy supplier can influence the output power of the inverter with Cloud control. This requires the inverter to have an active Internet connection.
Parameter | Display | Description |
Cloud control | Off | Cloud control of the inverter is deactivated. |
On | Cloud control of the inverter is activated. |
Profile | Value range | Description |
Allow cloud control for regulatory purposes (Technician) | Deactivated/Activated | The function may be mandatory for proper operation of the system.* |
Allow cloud control for Virtual Power Plants (Customer) | Deactivated/Activated | If the Allow remote control for regulatory purposes (technician) function is activated (technician access required), the Allow remote control for virtual power plants function is automatically activated and cannot be deactivated.* |
* Cloud control
A virtual power plant is an interconnection of multiple generators. This virtual power plant can be controlled by means of the cloud control via the Internet. An active inverter Internet connection is a prerequisite for this. System data are transferred.
The Solar API is an IP-based, open JSON interface. If enabled, IOT devices in the local network may access inverter information without authentication. For security reasons, the interface is disabled in the factory. Activate the interface manually if it is required for a third-party application (e.g., EV charger, smart home solutions, etc.). If there is a Fronius Wattpilot in the network, the inverter automatically activates the Solar API.
Fronius recommends using Fronius Solar.web for monitoring and analyzing the inverter and connected system components.
In the event of a firmware update to version 1.14.x, the Solar API setting is applied. In systems with a version below 1.14.x, the Solar API is activated; with higher versions, it is deactivated but can be switched on and off via the menu.
Manually activating the Fronius Solar API
On the user interface of the inverter in the Communication > Solar API menu area, activate the function Activate communication via Solar API.
In this menu, you can agree to the technically necessary data processing or reject it.
In addition, the transfer of analysis data and remote configuration via Fronius Solar.web can be enabled or disabled.
Danger from unauthorized fault analyses and repair work.
Fault analyses and repair work on the PV system may only be carried out by installers/service technicians from authorized specialist companies in accordance with national standards and regulations.
Risk due to unauthorized access.
Incorrectly set parameters can have a negative effect on the public grid and/or the grid power feed operation of the inverter and result in the loss of standard conformity.
Parameters may only be adjusted by installers/service technicians from authorized specialist companies.
Do not give the access code to third parties and/or unauthorized persons.
Risk due to incorrectly set parameters.
Incorrectly set parameters can have a negative effect on the public grid and/or cause inverter malfunctions and failures and result in the loss of standard conformity.
Parameters may only be adjusted if this has been approved or requested by the utility.
Any parameter adjustments must be made in compliance with nationally applicable standards and/or directives as well as the specifications of the utility.
The Country Setup menu area is intended exclusively for installers/service technicians from authorized specialist companies. To apply for the access code required for this menu area, see chapter Requesting inverter codes in Solar.SOS.
The selected country setup for the country in question contains preset parameters in accordance with nationally applicable standards and requirements. Changes may need to be made to the selected country setup depending on local grid conditions and the specifications of the utility.
The Country Setup menu area is intended exclusively for installers/service technicians from authorized specialist companies. The inverter access code required for this menu area can be requested in the Fronius Solar.SOS portal.
Activating this function limits the output power of the inverter to the specified value in watts.
Energy companies or grid operators can prescribe import limitations for inverters. The amperage is limited to the set value.
Due to hardware limitations, the Fronius Tauro cannot reduce the power to 0%, but only to 0.5 to 1%.
Grid operators or utilities can prescribe feed-in limits for an inverter (e.g., max. 70% of the kWp or max. 5 kW).
The feed-in limit takes account of self-consumption before the power of an inverter is reduced:
The following formulas provide guidance on which solution can be used:
PWRn ... Power of inverter n
0% PWR1 + 100% PWR2 + 100% PWR3... ≤ feed-in limit → solution a)
0% PWR1 + 100% PWR2 + 100% PWR3... > feed-in limit → solution b)
Solution a) – Power reduction of a single inverter
The specifications can be met if the prescribed feed-in limit is reached by reducing the power of a single inverter to ≥ 0%.
Example:
There are 3 inverters in a system: 1x Fronius Tauro 100 kW, 2x Fronius Tauro 50 kW. The specified feed-in limit at the transfer point must not exceed 100 kW.
Solution:
The Fronius Tauro can be regulated to 0% output power to meet the feed-in limit. The power of the other two inverters is not reduced and can be fed in at any time without restriction.
If the power reduction of an inverter to 0% is not sufficient, solution b) must be used.
Solution b) – Integration of a plant controller
This solution is used if the requirements of the utility cannot be met by limiting a single inverter or if permanent access (e.g., remote shutdown) is required. In this case, the integration of a PLANT CONTROLLER is recommended.
A detailed technical overview of this solution can be found at www.fronius.com using the keyword "feed-in management".
In order to benefit from the advantages of Fronius Solar.web in addition to the monitoring function of the PLANT CONTROLLER system, a Fronius Smart Meter can also be installed. The integration of a Fronius Smart Meter ensures that the consumption and feed-in data of the PV system are visualized in Fronius Solar.web and are available for analysis.
Total DC power of the system
Input field for the total DC power of the entire system in Wp. Always enter this value if the Maximum grid feed-in power is specified in %.
Power Control deactivated
The inverter converts all available PV energy.
Power Control activated
Feeding in limited with the following selection options:
Export Limit Control (Soft Limit)
If this value is exceeded, the inverter readjusts down to the set value. The adjustment of the value takes place within the time required by the national standards and regulations.
Input field for the Maximum grid feed-in power in W or % (setting range: -10 to 100%).
If there is no meter in the system or if the primary meter has failed, the inverter limits its output power to the set value.
Export Limit Protection (PAV,E protection)
This function monitors compliance with the feed-in limit. If Dynamic feed-in limit (Soft Limit) is activated, the inverter controls the power of feeding in in such a way that this function is usually not activated. If the specified limit values and the switch-off times are exceeded, this protection function disconnects the inverter from the grid.
The Maximum grid feed-in power (PAV,E) in the case of an asymmetric feed-in (Limit per phase – weakest phase) can be combined with the export limit protection (PAV,E protection) function. The Maximum grid feed-in power is calculated as follows: Maximum grid feed-in power per phase (PAV,E) x 3.
The export limit protection (PAV,E protection) function is only possible if a Smart Meter IP configured with MQTT is installed at the feed-in point.
IMPORTANT! To view and change settings in this menu item, select the Technician user. Enter and confirm the password for the Technician user. Settings in this menu area may only be made by technical specialists.
The inverter can be used as a primary device to control dynamic feed-in limits for additional Fronius inverters (secondary devices) so that feed-in limits prescribed by energy companies or utilities can be centrally managed. This control refers to the Soft Limit feed-in limit, see Feed-in limit. To do so, the following requirements must be met:
IMPORTANT! Only one primary meter is required for the primary device.
IMPORTANT! If an inverter with a battery is connected, use this inverter as the primary device for Multiple Inverter Control.
External grid and system protection
Regional standards and guidelines may require the installation of external grid and system protection for systems >30 kVA (see Central grid and system protection).
Multiple Inverter Control is available for the following device combinations:
Primary devices | Secondary devices |
GEN24, Verto, Tauro |
Primary meter
One Fronius Smart Meter acts as the only primary meter and is connected directly to the primary device. This Smart Meter measures the total output power of all inverters into the grid and passes this information to the primary device.
Primary device
Configure the feed-in limit on the user interface of the inverter:
To perform the search again, press the Refresh button.
If Use Modbus TCP is enabled, it is also possible to select Fronius SnapINverters with Datamanager 2.0 and Fronius Argeno with Use Inverter.
For more information on configuring the Fronius Argeno or Fronius Datamanager 2.0 as a secondary device, refer to the respective operating instructions.
Secondary device
Each secondary device takes over the settings for the feed-in limit from the primary device. A secondary device does not transmit any data for the feed-in limit to the primary device. To do so, the following requirements must be met:
Set the following configurations for the feed-in limit on the secondary device:
Only carry out work steps 2 and 3 if Use Modbus TCP is enabled on the primary device.
General
Settings relevant to the grid operator are defined as rules under this menu item. This relates to an effective power limit in % or watts and/or a power factor specification. To view and change settings, select the Technician user, and enter and confirm the password. Only technical specialists may make settings in this menu area.
Under Rules, expand a menu area (e.g., Rule 1). Configure the following settings:
Limitation
IMPORTANT!
A dynamic feed-in limit for several inverters can be configured under Feed-in limit. I/O power management rules are transferred from the inverter (primary device) to connected inverters in the system (secondary devices).
Select the following rules for power management:
IMPORTANT!
The rules for shutdown apply to this device and cannot be applied to other inverters in the system.
Input pattern (assignment of individual I/Os)
1 click = white, contact open
2 clicks = blue, contact closed
3 clicks = gray, not used
Power Factor (cos φ) (define value)
Impedance response
DNO Feedback
If the rule is activated, always configure the DNO Feedback output, e.g., for operating a signal device.
The Import and Export of defined rules can be carried out in the data format *.fpc. The rules and pin assignments in the following connection examples are not the only possible configurations. For pin assignment, take into account the available connections at the Data communication area and settings of the device configuration.
If there is an active rule for the control of the inverter, the device indicates this in the overview of the user interface under Device State.
Controlling Priorities
Used to set controlling priorities for I/O Power Management (DRM or ripple control receiver), the feed-in limit, and control via Modbus.
1 = highest priority, 3 = lowest priority
Local priorities of the I/O power management, the feed-in limit, and the Modbus interface are deactivated by cloud control commands (regulatory purposes and virtual power plants) – see Cloud control – and by backup power.
In terms of controlling priorities, the device differentiates between power control and inverter shutdown. Inverter shutdown always takes precedence over power control. An inverter shutdown command is always executed and does not need to be prioritized.
Power controlConnect the ripple control signal receiver and the I/O terminals of the inverter to one another as shown in the connection diagram.
For distances greater than 10 m between the inverter and the ripple control signal receiver, use a shielded data communication cable (CAT 5 or higher) with twisted cable pairs. Connect the shielding on one side to the terminal of the data communication area (SHIELD).
| (1) | Ripple control signal receiver with 4 relays for effective power limitation. |
| (2) | I/O connection terminals of the data communication area. |
| (1) | Ripple control signal receiver with 3 relays for effective power limitation. |
| (1) | Ripple control signal receiver with 2 relays for effective power limitation. |
| (1) | Ripple control signal receiver with 1 relay for effective power limitation. |
The grid operator may request the connection of one or more inverters to a ripple control receiver in order to limit the active power and/or the power factor of the photovoltaic system.
On the user interface of each inverter connected to the ripple control receiver, set the same parameters for I/O power management.
| Cause: | An arc was detected at a specific point on the PV system. |
| Remedy: | No action required. Feed-in mode is restarted again automatically after 5 minutes. |
| Cause: | A device that is connected in the WSD chain has interrupted the signal line (e.g., surge protection device) or the bypass installed ex works as standard has been removed and no trigger device has been installed. |
| Remedy: | If the SPD surge protection device has tripped, the inverter must be repaired by an authorized specialist. |
| OR: | Install the bypass installed ex works as standard or a trigger device. |
| OR: | Turn the WSD (wired shutdown) switch to position 1 (WSD primary device). |
WARNING!Danger from work that is not carried out properly. This can result in serious injury and damage to property. The installation and connection of an SPD surge protection device may only be carried out by Fronius-trained service personnel in accordance with the technical specifications. Observe safety rules. | |
| Cause: | An electric arc has been identified on the PV system, and the maximum number of automatic connections within 24 hours has been reached. |
| Remedy: | Keep the sensor pressed on the inverter for 3 seconds |
| OR: | On the user interface of the inverter, in the System > Event Log menu area, confirm the status 1173 - ArcContinuousFault. |
| OR: | On the user interface of the inverter, in the Notifications user menu, confirm the status 1173 - ArcContinuousFault. |
CAUTION!Danger from damaged components of the PV system Serious personal injury/damage to property may result. Before the status 1173 - ArcContinuousFault is confirmed, the entire photovoltaic system affected must be checked for any possible damage. Damaged components must be repaired by qualified specialists. | |
Input data | |
Maximum input voltage | 1000 VDC |
Start-up input voltage | 200 VDC |
MPP voltage range | 400 - 870 VDC |
Number MPP-controller | 3 |
Maximum input current (IDC max) Total | 134 A |
Max. short circuit current 8) Total | 240 A |
Maximum PV field power (PPV max) Total | 75 kWp |
DC overvoltage category | 2 |
Max. inverter backfeed current to the array 3) |
Max. capacity of the PV generator against earth | 10,000 nF |
Limit value of the insulation resistance test between PV generator and ground (on delivery) 7) | 34 kΩ |
Adjustable range of insulation resistance test between PV generator and ground 6) | 10 - 10,000 kΩ |
Limit value and trip time of sudden residual fault current monitoring (on delivery) | 30 / 300 mA / ms |
Limit value and trip time of continuous residual fault current monitoring (on delivery) | 450 / 300 mA / ms |
Adjustable range of continuous residual current monitoring 6) | 30 - 1000 mA |
Cyclic repetition of the insulation resistance test (on delivery) | 24 h |
Adjustable range for cyclic repetition of the insulation resistance test | - |
Output data | |
Grid voltage range | 180 - 270 VAC |
Rated grid voltage | 220 VAC | 230 VAC 1) |
Rated power | 50 kW |
Rated apparent power | 50 kVA |
Rated frequency | 50/60 Hz 1) |
Maximum output current / phase | 76 A |
Initial symmetrical short-circuit current / phase IK" | 76 A |
Power factor (cos phi) | 0 - 1 ind./cap.2) |
Grid connection | 3~ (N)PE 380 / 220 VAC |
Earthing systems | TT (allowed if UN_PE < 30V) |
Maximum output power | 50 kW |
Nominal output power | 50 kW |
Rated output current / phase | 75.8 A / 72.5 A |
Total harmonic distortion | < 3% |
AC overvoltage category | 3 |
Current (inrush) 5) | 228 A peak / |
Max. output fault current / duration | 44.7 A / 16.24 ms |
General data | |
Night-time power loss = standby consumption | 15 W |
European Efficiency (400 / 600 / 800 / 870 VDC) | 97.8 / 98.3 / 97.9 / 97.7% |
Maximum efficiency | 98.5% |
Safety class | 1 |
EMC emission class | B |
Pollution degree | 3 |
Permitted ambient temperature | - 40 °C - +65 °C |
Permitted storage temperature | - 40 °C - +70 °C |
Relative humidity | 0 - 100% |
Sound pressure level (600 VDC) | 68.4 dB(A) (ref. 20 µPA) |
Protection class | IP65 |
Dimensions (height x width x depth) | 755 x 1109 x 346 mm |
Weight | 98 kg |
Inverter topology | Non-insulated, no transformer |
Protection devices | |
DC disconnector | Integrated |
Cooling principle | Controlled forced-air ventilation |
RCMU 9) | Integrated |
DC isolation measurement 9) | integrated 2) |
Overload performance | Operating point shift, |
Active anti-islanding method | Frequency shift method |
AFCI (only for D variant with 15/20 A fuse) | Optional |
AFPE (AFCI) classification (according to IEC 63027) 9) | = F-I-AFPE-1-4/3/7-3 |
Input data | |
Output data | |
General data | |
Safety class | 1 |
Weight | 98 kg |
Input data | |
Start-up input voltage | 650 VDC |
MPP voltage range | 580 - 930 VDC |
Number MPP-controller | 1 |
Maximum input current (IDC max) Total | 87.5 A |
Max. short circuit current 8) Total | 178 A |
Max. inverter backfeed current to the array 3) | 125 A4) |
Limit value of the insulation resistance test between PV Generator and ground (on delivery) 7) | 34 kΩ |
Output data | |
Current (inrush) 5) | 209 A peak / |
Max. output fault current / duration | 37.2 A / 19.4 ms |
General data | |
European Efficiency (580 / 800 / 930 VDC) | 98.2 / 97.7 / 97.3% |
Safety class | 1 |
Sound pressure level (580 VDC) | 68.5 dB(A) (ref. 20 µPA) |
Weight | 74 kg |
AFPE (AFCI) classification (according to IEC 63027) 9) | = F-I-AFPE-1-7/7-2 |
Input data | |
Maximum input current (IDC max) Total | 175 A |
Max. short circuit current 8) |
Maximum PV field power (PPV max) Total | 150 kWp |
Max. capacity of the PV generator against earth | 19,998 nF |
Limit value and trip time of continuous residual fault current monitoring (on delivery) | 900 / 300 mA / ms |
Output data | |
Rated power | 99.99 kW |
Rated apparent power | 99.99 kVA |
Maximum output current / phase | 152 A |
Initial symmetrical short-circuit current / phase IK" | 152 A |
Maximum output power | 99.99 kW |
Nominal output power | 99.99 kW |
Rated output current / phase | 151.5 A / 144.9 A |
Current (inrush) 5) | 244 A peak / |
Max. output fault current / duration | 93.9 A / 22 ms |
General data | |
Safety class | 1 |
Sound pressure level (580 VDC / 930 VDC) | 74.4 / 79.3 dB(A) (ref. 20 µPA) |
Weight | 103 kg |
AFPE (AFCI) classification (according to IEC 63027) 9) | = F-I-AFPE-1-7/7/8-3 |
Input data | |
Output data | |
Rated power | 100 kW |
Rated apparent power | 100 kVA |
Maximum output power | 100 kW |
Nominal output power | 100 kW |
General data | |
Safety class | 1 |
Weight | 103 kg |
Frequency range | 2412 - 2462 MHz |
Channels / power used | Channel: 1-11 b,g,n HT20 |
Modulation | 802.11b: DSSS (1Mbps DBPSK, 2Mbps DQPSK, 5.5/11Mbps CCK) |
| 1) | The values stated are defaults; the inverter is configured specifically to suit the requirements of the relevant country. |
| 2) | Depending on the country setup or device-specific settings (ind. = inductive; cap. = capacitive). |
| 3) | Maximum current from a defective PV module to all other PV modules. From the inverter itself to the PV side of the inverter, it is 0 A. |
| 4) | Guaranteed by the electrical configuration of the inverter. |
| 5) | Current peak when switching on the inverter. |
| 6) | Specified values are standard values; depending on the requirement and PV power, these values must be adjusted accordingly. |
| 7) | Specified value is a max. value; exceeding the max. value may negatively affect the function. |
| 8) | ISC PV = ICP PV ≥ ISC max = I SC (STC) x 1.25 according to e.g., IEC 60364-7-712, NEC 2020, AS/NZS 5033:2021 |
| 9) | Software class B (single channel with periodic self-test) control function according to IEC60730-1 Annex H. |
General data | |
Product name | EATON PV-DIS-10-125/2-REFOHA |
Rated insulation voltage | 1000 VDC |
Rated impulse withstand voltage | 6 kV |
Suitability for insulation | Yes, DC only |
Rated operating current | Rated operating current Ie ≤ 100 A: DC-PV2 utilization category (according to IEC/EN 60947-3) |
Rated operating current Ie ≤ 125 A: DC-PV1 utilization category (according to IEC/EN 60947-3) | |
Utilization category and/or PV utilization category | according to IEC/EN 60947-3 utilization category DC-PV2 |
Rated short-time withstand current (Icw) | 12 x le |
Rated short-circuit capacity (Icm) | 1 000 A |
Rated operating current and rated breaking capacity | ||||
Rated operating voltage (Ue) | Rated operating current (Ie) DC-PV1 | I(make) / I(break) DC-PV1 | Rated operating current (Ie) DC-PV2 | I(make) / I(break) DC-PV2 |
≤ 500 VDC | 125 A | 187.5 A | 125 A | 500 A |
600 VDC | 125 A | 187.5 A | 125 A | 500 A |
800 VDC | 125 A | 187.5 A | 125 A | 500 A |
900 VDC | 125 A | 187.5 A | 110 A | 440 A |
1 000 VDC | 125 A | 187.5 A | 100 A | 400 A |
The equipment complies with all the requisite and relevant standards and directives that form part of the relevant EU directive, and therefore is permitted to display the CE mark.
Compliance with 2014/53/EU Radio Equipment Directive (RED)
The above table of technical data lists the frequency ranges and maximum HF transmission power used by Fronius wireless products available for sale in the EU in accordance with Article 10.8 (a) and 10.8 (b) of the RED.
Fronius products must be installed and operated such that the product is always 20 cm or more away from the body.
The standard measurement and safety procedures integrated into the inverter ensure that the power feed is immediately interrupted in the event of a grid failure (for example shut-off by the grid operator or damage to lines).
Under sos.fronius.com you can retrieve warranty and device information at any time, start troubleshooting independently, and request replacement components.
For more information on spare parts, contact your installer or point of contact for the PV system.
Detailed warranty conditions specific to your country can be found at https://www.fronius.com/en/download-center?searchword=Warranty+conditions .
If there is a warranty for the relevant product, register the product at https://warranty.fronius.com/ and activate or extend the warranty.
Used equipment and batteries must be returned to the distributor or an authorized local collection system. Do not dispose of batteries with domestic waste. Protect batteries from high temperatures, direct sunlight, moisture and corrosive environments.
Arrange for the safe collection and proper disposal of damaged, leaking or used batteries by a battery recycling company or the Fronius Service Partner.
In addition, it should be noted that batteries contain substances that, if disposed of improperly, can have a significant negative impact on the environment as well as on human health and the safety of persons, in particular due to the leakage of hazardous substances such as heavy metals or electrolytes, which can contaminate soil, water and air.
This ensures environmental protection and the sustainable use of natural resources.Packaging materials