en
      Operating instructionsGEN24, Tauro and Verto Country Setup Menu
    • General
      • How information is presented in the document
      • Country setup
      • Territorial Limitations
      • Requesting inverter codes in Solar.SOS
      • Adjusting parameters with the Fronius Solar.start app
      • Adjusting parameters with the browser
    • Country setup
      • Country setup selection
      • General
        • Startup and Reconnection
        • Ramp rates
      • Safety
        • Unintentional islanding detection
        • Insulation monitoring
        • DC arc fault protection
        • RCMU
        • DC shutdown communication
      • Interface protection
        • Voltage
        • Frequency
        • Export limit protection
        • DC injection
      • Grid support functions
        • Voltage fault ride-through (VFRT)
        • Active power
        • Reactive power
    • 018-16112026
    download
    Access code
    Grid backup functions
    ContactImprintTerms of usePrivacy statementCookie policy
    018-16112026
    General
    link_horizontalLink copied
    Application notes
    Software
    Example: Click Save.
    Instructions for action
    1Action steps are displayed with consecutive numbering.
    ✓This symbol indicates the result of the action step or the entire instruction.
    1. General
    Application notes
    Software
    1. General
    Country setup
    WARNING
    Danger from unauthorized fault analyses and repair work.
    Fault analyses and repair work on the PV system may only be carried out by installers/service technicians from authorized specialist companies in accordance with national standards and regulations.
    NOTE
    Risk due to unauthorized access.
    Incorrectly set parameters can have a negative effect on the public grid and/or the grid power feed operation of the inverter and result in the loss of standard conformity.
    Parameters may only be adjusted by installers/service technicians from authorized specialist companies.
    Do not give the access code to third parties and/or unauthorized persons.
    NOTE
    Risk due to incorrectly set parameters.
    Incorrectly set parameters can have a negative effect on the public grid and/or cause inverter malfunctions and failures and result in the loss of standard conformity.
    Parameters may only be adjusted if this has been approved or requested by the utility.
    Any parameter adjustments must be made in compliance with nationally applicable standards and/or directives as well as the specifications of the utility.
    The Country Setup menu area is intended exclusively for installers/service technicians from authorized specialist companies. To apply for the access code required for this menu area, see chapter Requesting inverter codes in Solar.SOS.
    The selected country setup for the country in question contains preset parameters in accordance with nationally applicable standards and requirements. Changes may need to be made to the selected country setup depending on local grid conditions and the specifications of the utility.
    1. General
    This product is intended for use and sale outside the Province of Québec. It does not meet the French language documentation and labeling requirements of Québec's Charter of the French Language. Accordingly, Fronius International GmbH does not offer this product for sale to, or for delivery to, any address within the Province of Québec.
    By placing an order, the customer represents and warrants that they are not purchasing the product for use or resale within Québec. Fronius International GmbH disclaims all liability and warranty obligations for any products operated in Québec in violation of these restrictions.
    1. General
    The Country Setup menu area is intended exclusively for installers/service technicians from authorized specialist companies. The inverter access code required for this menu area can be requested in the Fronius Solar.SOS portal.
    Requesting inverter codes in Fronius Solar.SOS:
    1.
    Open solar-sos.fronius.com in the browser
    2.
    Log in with your Fronius account
    3.
    At the top right, click on the drop-down menu
    4.
    Select the Show inverter codes menu item
    5.
    A contract page appears on which the request for the access code to change the grid parameters for Fronius inverters is located
    6.
    Accept the terms and conditions of use by checking Yes, I have read and agree to the terms of use and click Confirm & Save
    7.
    After that, the codes can be retrieved in the drop-down menu at the top right under Show inverter codes
    1Open solar-sos.fronius.com in the browser
    2Log in with your Fronius account
    3At the top right, click on the drop-down menu
    4Select the Show inverter codes menu item
    ✓A contract page appears on which the request for the access code to change the grid parameters for Fronius inverters is located
    5Accept the terms and conditions of use by checking Yes, I have read and agree to the terms of use and click Confirm & Save
    6After that, the codes can be retrieved in the drop-down menu at the top right under Show inverter codes
    CAUTION
    1. General
    The "Fronius Solar.start" app is needed for registration. Depending on the end device, the app is available on the respective platform.
    1Start the installation in the app.
    2Select the product to which the connection should be established.
    3Open the access point by touching the sensor once   .
    ✓Communication LED: flashes blue.
    4Select the Technician user in the User menu and enter and confirm the password for the Technician user.
    5Call up the Safety and grid regulations → Country setup menu area.
    6Enter the requested access code (see chapter Requesting inverter codes in Solar.SOS on page (→)) in the input field Access code country setup and click the button Activate.
    7Adjust the parameters in the individual menu areas taking into account the nationally applicable standards and/or the specifications of the utility.
    1. General
    WLAN:
    1Open the access point by touching the sensor once   .
    2Establish the connection to the inverter in the network settings.
    ✓The inverter is displayed with the name "FRONIUS_PILOT" and the serial number of the device
    3Password: enter 12345678 and confirm.
    IMPORTANT!
    To enter the password on a Windows 10 operating system, the link "Connect using a security key instead" must first be activated to establish a connection with the password: 12345678.
    4In the browser address bar, enter and confirm the IP address 192.168.250.181.
    5Select the Technician user in the User menu and enter and confirm the password for the Technician user.
    6Call up the Safety and grid regulations → Country setup menu area.
    7Enter the requested access code (see chapter Requesting inverter codes in Solar.SOS on page (→)) in the input field Access code country setup and click the button Activate.
    8Adjust the parameters in the individual menu areas taking into account the nationally applicable standards and/or the specifications of the utility.
    Ethernet:
    1Establish a connection to the inverter (LAN1) with a network cable (CAT5 STP or higher).
    2Open the access point by touching the sensor once   .
    3In the browser address bar, enter and confirm IP address 169.254.0.180.
    Country setup
    Predefined setups can be selected in the Country setup selection menu. The selected country setup for the respective country contains preset parameters according to the nationally applicable standards and requirements. Depending on local grid conditions and the specifications of the utility, adjustments to the selected country setup may be necessary.
    Parameter
    Description
    Country / Region
    Selecting the respective country or region limits/displays the available country setups for the inverter.
    Country setup
    Displays the available setups per country/region.
    A setup is a device configuration predefined by Fronius. The selection of the country setup must be made in consideration of the applicable standards or in coordination with the grid operator.
    Rated Frequency (Hz)
    The rated frequency is predetermined by the country setup selection. Changing this parameter affects the stable operation of the inverter and is therefore only permitted in consultation with Fronius.
    Rated Voltage (V)
    The rated voltage is predetermined by the choice of the country setup. Changing this parameter affects the stable operation of the inverter and is therefore only permitted in consultation with Fronius.
    1. Country setup
    Parameter
    Description
    Country / Region
    Country setup
    Rated Voltage (V)
    1. Country setup
    2. Country setup selection
    Parameter
    Description
    Country / Region
    Country setup
    Rated Voltage (V)
    1. Country setup
    General
    These parameters can be used to set the grid monitoring times before the inverter is switched on.
    For the set time, both the mains voltage and the mains frequency must be within the permissible range before connection is allowed.
    • The permissible range for the mains voltage is defined in the menu area Grid and system protection → Voltage → Startup and reconnection (see chapter Voltage).
    • The permissible range for the mains frequency is defined in the menu area Grid and system protection → Frequency → Startup and reconnection (see chapter Frequency).
    Parameter
    Range of values
    Description
    Grid Monitoring Time Startup
    1 - 900 [s]
    Grid monitoring time before the inverter is switched on during a normal start-up process in seconds (e.g., at sunrise).
    Parameter
    Range of values
    Description
    Grid Monitoring Time Reconnection
    1 - 900 [s]
    Grid monitoring time before the inverter is switched back on after a grid fault (see table Grid faults) in seconds (e.g., if a fault occurs in the AC grid during the day which causes the inverter to shut down).
    The following errors are defined by the inverter as grid errors for this functionality:
    Name
    Description
    StateCode name
    StateCode number
    Overvoltage
    Mains voltage exceeds an overvoltage limit (Inner, Middle, or Outer Limit Overvoltage).
    AC voltage too high
    1114
    Undervoltage
    Mains voltage falls below an undervoltage limit (Inner, Middle or Outer Limit Undervoltage).
    AC voltage too low
    1119
    Overfrequency
    Mains frequency exceeds an overfrequency limit (Inner, Outer or Alternative Limit Overfrequency).
    AC frequency too high
    1035
    Underfrequency
    Mains frequency falls below an underfrequency limit (Inner, Outer or Alternative Limit Underfrequency).
    AC frequency too low
    1037
    Fast Overvoltage Disconnect
    Triggering of the fast surge protection (> 135%).
    Grid voltage too high (fast overvoltage cut-out)
    1115, 1116
    Long Time Average Overvoltage Limit
    Mains voltage exceeds the long-term overvoltage limit (Long Time Average Limit).
    Long-term mains voltage limit exceeded
    1117
    Unintentional Islanding Detection.
    Unintentional islanding was detected.
    Islanding detected
    1004
    1. Country setup
    2. General
    Parameter
    Range of values
    Description
    1 - 900 [s]
    Parameter
    Range of values
    Description
    1 - 900 [s]
    Name
    Description
    StateCode name
    StateCode number
    Overvoltage
    AC voltage too high
    1114
    Undervoltage
    AC voltage too low
    1119
    Overfrequency
    1035
    Underfrequency
    1037
    1115, 1116
    1117
    Islanding detected
    1004
    1. Country setup
    2. General
    Ramp rates
    Ramp rates limit the maximum rate of change of active power in specific situations. Rising ramps (ramp-up) limit the increase in active power at the inverter’s AC output. Falling ramps (ramp-down) limit the decrease in active power at the inverter’s AC output.
    Note that if there are multiple specifications for the rate of change, the lowest rate of change is applied. For example, an irradiation ramp can, thus, be rendered ineffective by a lower startup ramp or another function that affects the rate of change (e.g., P(U) or P(F)).
    Ramp-up at startup and reconnection
    When the inverter is switched on, the maximum rate of change of active power can be limited by a rising ramp with a defined slope. As soon as the increase in active power is influenced by the available photovoltaic power or another control mechanism, the ramp is terminated.
    Parameter
    Value range
    Description
    On
    On startup or reconnection, active power is limited by the ramp-up at startup and reconnection rate with a rate of change.
    Off
    Function is deactivated.
    On at reconnection after tripping
    The function is reactivated after the inverter is shut down.
    Ramp-up at startup and reconnection rate
    0.001 ‑ 100 [%/s]
    Permissible rate of change of active power during startup or reconnection.
    Ramp-up/down irradiation
    The irradiation ramp is a permanent limit on the rate of change of active power. If the photovoltaic power changes rapidly due to passing clouds, the rate of change of the inverter’s output power is limited by the ramp-up irradiation rate or the ramp-down irradiation rate.
    Parameter
    Value range
    Description
    Ramp-up irradiation
    On
    The increase in active power is limited by the ramp-up irradiation rate with a rate of change.
    Off
    Ramp-up irradiation rate
    0 - 200 [%/s]
    Permissible rate of change during a power increase.
    Ramp-down irradiation
    Note: This feature affects only inverters that have storage.
    On
    The reduction in active power is limited by the ramp-down irradiation rate with a rate of change.
    Off
    Ramp-down irradiation rate
    0 - 200 [%/s]
    Permissible rate of change of active power.
    Example: Active power limitation due to irradiation ramp-up/ramp-down caused by a change in available photovoltaic power.
    Ramp-up/down communication
    This refers to a limit on the rate of change of active power when external active power specifications are modified. These can include, for example, power limits via I/Os or Modbus commands. If lower rates of change are specified via a Modbus command, those rates are applied. Higher rates of change are limited by the ramp-up communication rate and ramp-down communication rate values.
    Parameter
    Value range
    Description
    Ramp-up communication
    On
    The limit on the rate of change (corresponding to the ramp-up communication rate) when active power increases due to an external specification is enabled.
    Off
    Ramp-up communication rate
    0 ‑ 100 [%/s]
    Ramp-down communication
    On
    The limit on the rate of change (corresponding to the ramp-down communication rate) during active power reduction due to an external specification is enabled.
    Off
    Ramp-down communication rate
    0 ‑ 100 [%/s]
    Permissible rate of change during power reduction.
    1. Country setup
    Safety
    Unintentional formation of islanding
    In the event of a power outage or the disconnection of a small portion of the grid from the greater power grid, under certain conditions, local loads and inverters may form an unintentional island grid. If generation and load (of both active and reactive power) are balanced, the AC voltage and frequency can remain within permissible limits. In this case, the inverter (without additional islanding detection) will maintain grid-feeding operation, will not automatically shut down, and will supply power to local loads. This is an unintentional condition. To prevent these situations, you can employ active or passive methods for islanding detection.
    Active anti-islanding method
    The inverter’s active anti-islanding method identifies unintentional stand-alone operation; the inverter terminates grid-feeding operation and disconnects from the AC grid on all poles.
    The detection process uses an active frequency drift method: In the event of brief changes in grid frequency, the inverter feeds alternating current into the grid at a different frequency (frequency drift). In the event of a disconnection from the grid, the AC voltage will also change its frequency. This results in a feedback effect: The frequency shifts to such an extent that it exceeds or falls below the permissible limits. As a result, the inverter terminates grid-feeding operation.
    In the case of three-phase inverters, the method is also capable of detecting islanding on any individual phase. This function is an active anti-islanding method because the inverter deliberately modifies its feed-in behavior during the detection process.
    The following islanding detection parameters are preselected based on the respective country setup and cannot be changed.
    Parameter
    Description
    Active islanding detection is enabled or disabled depending on the selected country settings.
    Quality factor
    The higher this value, the stronger/more aggressive the frequency shift in islanding detection.
    Higher values, therefore, result in shorter islanding detection times. However, values that are too high can also negatively affect voltage quality.
    Maximum disconnect time
    Maximum allowable shutdown time for islanding detection
    In contrast, there are passive methods that detect the formation of an island grid solely based on measurements of AC grid parameters. This group includes, e.g., the rate of change of frequency (RoCoF) protection.
    1. Country setup
    2. Safety
    Parameter
    Description
    Quality factor
    1. Country setup
    2. Safety
    Before each startup (at least once a day), the inverter performs a DC isolation measurement on the DC terminals of the PV array. Insulation monitoring must be enabled for both the insulation warning and the insulation fault.
    Insulation warning
    The insulation monitoring measurement value is used to trigger an insulation warning. If the value falls below a limit value setting, status code 1083 is displayed.
    Insulation error
    The insulation monitoring measurement value is also used for insulation error monitoring. If the insulation measurement value falls below the limit value for insulation error threshold, power feed-in to the public grid is prevented, and status code 1082 is displayed.
    1Configure the parameters for insulation measurement using the following settings under menu item Safety and grid requirements > Country setup > Safety > Insulation monitoring:
    Parameter
    Value range
    Description
    Insulation monitoring mode
    Default
    This feature is enabled or disabled depending on the country settings.
    Insulation error threshold
    100 ‑ 1,000 kOhm
    If the insulation measurement value is lower than this value, the inverter prevents grid-feeding operation (when insulation monitoring is enabled). Status code 1182 is displayed on the user interface of the inverter.
    2Configure the parameters for the insulation warning using the following settings under menu item Device configuration > Inverter > Insulation warning:
    Parameter
    Value range
    Description
    Insulation warning
    On
    The insulation warning is enabled.
    If the value falls below the threshold for the insulation warning, a warning is triggered, but the system does not shut down.
    Off
    Insulation measurement mode
    Exact
    Insulation monitoring takes place with the highest degree of accuracy and the measured insulation resistance is displayed on the user interface of the inverter.
    Fast
    Insulation monitoring is performed with lower accuracy, which shortens the duration of the insulation measurement, and the insulation value is not displayed.
    Threshold for the insulation warning
    100 ‑ 1,000 kOhm
    If the value drops below the threshold, status code 1183 is displayed on the user interface of the inverter.
    1. Country setup
    2. Safety
    These parameters are used to configure the arc detection behavior at the inverter’s DC terminals. The DC arc fault protection function protects against arc faults and ground faults. Any faults in the current and voltage waveforms are continuously monitored, and the circuit is shut down if a ground fault is detected. This prevents overheating at faulty connection points and may help prevent fires.
    Parameter
    Value range
    Description
    Arc fault detection (AFD)
    For enabling and disabling arc fault detection. The Arc logging and Automatic reconnects parameters are taken into account only when Arc fault detection (AFD) is enabled.
    Off
    Arcs are not detected.
    Off (with warning)
    Arc faults are not detected, and status code 1184 is displayed continuously on the user interface of the inverter.
    On
    Arc fault detection (AFD) is enabled for diagnostic purposes. No status codes are displayed.
    Arc fault circuit interrupter (CI)
    Describes the behavior when an arc is detected and simultaneously enables/disables the integrated self-test.
    Off
    Detection of an arc does not cause the inverter to shut down and is not displayed on the user interface of the inverter.
    Off (with warning)
    Detection of an arc does not cause the inverter to shut down. Status code 1185 is displayed continuously on the user interface of the inverter.
    On
    If an arc is detected, the inverter interrupts photovoltaic power generation and grid-feeding operation.
    Depending on the configuration of the Automatic reconnects parameter, the inverter will attempt to restart PV power generation and grid-feeding operation. An integrated self-test is active and runs at regular intervals.
    Automatic reconnections
    The Automatic Reconnects setting determines whether the inverter resumes PV power generation and grid-feeding operation after detecting an arc fault.
    Unlimited
    The 24-hour counter is disabled. After each detected arc, the inverter resumes generating PV power and grid-feeding operation.
    0 - No reconnection
    Once an arc is detected, the system will not reconnect. Status code 1173 appears on the user interface of the inverter and must be acknowledged manually.
    1 - 4
    If more arcs than the number set in Automatic reconnects are detected within 24 hours, manual reconnection is required. Status code 1173 is displayed on the user interface of the inverter and must be acknowledged manually.
    Arc logging
    Enables or disables the recording of arc signatures. The data are uploaded to the cloud and used to continuously improve the arc detection system’s immunity to interference and fault tolerance.
    Off
    Arc signatures are not recorded.
    On
    Arc signatures are recorded, uploaded to the cloud, and used to continuously improve the arc detection system’s immunity to interference and fault tolerance.
    1. Country setup
    2. Safety
    RCMU
    The inverter is equipped with an all-current-sensitive residual current monitoring unit (RCMU) in accordance with IEC 62109-2, which monitors residual currents from the PV module to the inverter’s AC output and disconnects the inverter from the public grid in the event of an impermissible residual current.
    The following parameters are preset after the country setup is selected, and they cannot be changed.
    Parameter
    Value range
    Description
    RCMU
    Off
    The protection feature is disabled.
    Off (with warning)
    The protection feature is disabled. Status code 1188 is displayed continuously on the user interface of the inverter.
    On
    The protection feature is enabled.
    If more residual currents than the number set in Automatic reconnects are detected within 24 hours, the inverter will not make any further attempts to start grid-feeding operation. Status code 1076 is displayed on the user interface of the inverter and must be acknowledged manually.
    0
    Residual current exceeding 300 mA is not permitted. After any residual current is detected, grid-feeding operation is interrupted, and the status code must be acknowledged manually on the user interface of the inverter.
    1 - 4
    After a shutdown caused by a residual current exceeding 300 mA, 1, 2, 3, or 4 attempts are made within 24 hours to restart grid-feeding operation. After this number of attempts, no further attempts will be made to restart grid-feeding operation, and the status code must be acknowledged manually on the user interface of the inverter.
    Unlimited
    The 24-hour counter is disabled. The inverter resumes grid-feeding operation after every detected residual current exceeding 300 mA.
    1. Country setup
    2. Safety
    Devices for shutting down within the DC generator (e.g., in or on the module, or within a string) can be controlled by the inverter. This requires compatibility specifically with the inverter’s communication system.
    Parameter
    Value range
    Description
    Powerline communication
    Enables and disables DC powerline communication (PLC) on the inverter.
    Off
    DC powerline communication is disabled on the inverter. No shutdown devices are installed in the photovoltaic system, or, if shutdown devices are installed in the photovoltaic system that are waiting for an enable signal, this signal must come from another device (transmitter) (otherwise, the system will not function).
    SunSpec PLC
    The inverter communicates via DC powerline communication in accordance with the SunSpec rapid shutdown standard. Compatible shutdown devices must be used to ensure the proper operation of the photovoltaic system.
    1. Country setup
    2. Safety
    Parameter
    Value range
    Description
    Off
    SunSpec PLC
    1. Country setup
    Voltage
    This section describes the protection settings for overvoltage and undervoltage. Voltage limit values are defined for this purpose. The default values depend on the selected country setup but can be adjusted as needed.
    Each voltage limit value consists of:
    • an undervoltage or overvoltage value and
    • a corresponding protection time.
    The protection time is the duration during which the voltage may remain outside the respective voltage limit value. After this time, the inverter shuts down and displays an error message. Up to three limit values can be defined for both overvoltage (U>/U>>) and undervoltage (U</U<<):
    • Inner limits – The limit value closest to the nominal voltage.
    • Middle limits – A limit value at the middle point from the nominal voltage.
    • Outer limits – The limit value furthest from the nominal voltage.
    To use the limits effectively, set a longer protection time for inner limits than for outer limits. If you also use middle limits, set their protection time to fall between the protection times of the inner limits and outer limits. See the example in the diagram.
    Diagram explaining the limits
    IL
    Inner limits - inner limit value
    ML
    Middle limits - middle limit value
    OL
    Outer limits - outer limit value
    (1)
    Trigger range
    OV
    Overvoltage
    UV
    Undervoltage
    tx
    Protection time
    These voltage limit values are not active during backup power mode. Under Device configuration > Inverter > Backup power, you can configure the voltage limit values that apply during backup power mode.
    Inner limits
    Parameter
    Description
    Undervoltage U<
    Setting value for undervoltage protection < in [V]
    Undervoltage time U<
    Time setting value for undervoltage protection U< in [s]
    Overvoltage U>
    Setting value for surge protection U> in [V]
    Overvoltage time U>
    Time setting value for surge protection U> in [s]
    Middle limits
    Parameter
    Description
    Middle limits for voltage
    Enable/disable the middle voltage limit values On/Off
    Undervoltage U<
    Overvoltage U>
    Overvoltage time U>
    Outer limits
    Parameter
    Description
    Outer limits for voltage
    Enable/disable outer voltage limit values On/Off
    Undervoltage U<<
    Setting value for undervoltage Protection U<< in [V]
    “Undervoltage time U<<”
    Time setting value for undervoltage protection U<< in [s]
    Overvoltage U>>
    Setting value for surge protection U>> in [V]
    Overvoltage time U>>
    Time setting value for surge protection U>> in [s]
    Long time average limit
    This function calculates a moving average of the voltage over the set time period and compares it to the set values for the surge protection. If the value exceeds the surge protection threshold, the system shuts down.
    Parameter
    Description
    Enable/disable the voltage average limit value On/Off/On at Smart Meter (On at Smart Meter corresponds to software-based NA protection with remote voltage measurement in accordance with VDE-AR-N 4105:2024.)
    Overvoltage U>
    Setting value of surge protection with averaging U> in [V] (measured at the feed-in point)
    Internal overvoltage U> during “On at Smart Meter” mode
    Setting value for surge protection with averaging U> in [V] (measured at the Fronius Smart Meter). This corresponds to the software-based NA protection device with remote voltage measurement in accordance with VDE-AR-N 4105:2024.
    Overvoltage averaging time U>
    The time period over which the average value is calculated in [s]. If 0 s is set, the check is not active.
    Fast overvoltage disconnect
    Fast overvoltage shutdown capable of responding to voltage spikes within a cycle.
    Parameter
    Description
    Fast overvoltage disconnect threshold
    Threshold value for rapid RMS overvoltage shutdown (setting value: 0 - 200% V)
    Fast overvoltage disconnect time
    Setting value for the fast surge protection (exceeding the peak value by 35%) in [s]. This shutdown can be configured in the microsecond range.
    Instant backup limits
    Before the inverter switches to backup power mode in fast-switching mode, the voltage connection conditions must be met.
    Parameter
    Description
    Undervoltage U<
    Overvoltage U>
    Before the inverter is allowed to connect to the grid, the connection conditions for voltage and frequency must be met for a specified period of time.
    A distinction is made between:
    • Startup: connecting the inverter during a normal startup procedure (e.g., at sunrise) and
    • Reconnection: reconnecting the inverter to the grid after a grid fault (see the Grid faults table). For example, if a fault occurs in the AC grid during the day, causing the inverter to shut down.
    The limit values used for checking the connection conditions depend on whether a grid fault has occurred and which mode is defined. The mode affects only the limit values and not the monitoring time. The monitoring time is determined by the parameters under General settings > Startup and reconnection. The monitoring time used depends on whether the connection is a startup or reconnection and applies equally to frequency and voltage limit values. Once the grid monitoring period has elapsed, the previously mentioned interface protection values become active. In backup power mode, these startup and reconnection parameters are not active.
    Parameter
    Description
    Mode
    The following modes are available:
    • Startup values are used for startup/reconnection values are used for reconnection: During a normal startup, the startup values are used as the connection conditions. During reconnection following a power failure, the reconnection values are used as the connection conditions.
    • Startup values are used for startup and reconnection: Regardless of the type of connection, the startup values are always used as the connection conditions.
    Startup minimum voltage
    Lower voltage value for normal startup in [V]
    Startup maximum voltage
    Upper voltage value for normal startup in [V]
    Minimum reconnection voltage
    Lower voltage value for reconnection in [V]
    Maximum reconnection voltage
    Upper voltage value for reconnection in [V]
    Reset time for voltage limit violation
    Reset time if the voltage limit value is violated, in [s]
    The following faults are defined as grid errors by the inverter for this functionality:
    Designation
    Description
    StateCode name
    StateCode number
    Overvoltage
    Grid voltage exceeds an overvoltage limit (inner, middle, or outer limit overvoltage).
    AC voltage too high
    1114
    Undervoltage
    Grid voltage falls below an undervoltage limit (inner, middle, or outer limit undervoltage).
    AC voltage too low
    1119
    Overfrequency
    Grid frequency exceeds an overfrequency limit (inner, outer, or alternative limit overfrequency).
    1035
    Underfrequency
    Grid frequency falls below an underfrequency limit (inner, outer, or alternative limit underfrequency).
    1037
    Triggering of the fast surge protection device (> 135%).
    1115, 1116
    Long time average overvoltage limit
    The grid voltage exceeds the long time overvoltage limit (Long time average limit).
    Long-term grid voltage limit exceeded
    1117
    Unintentional islanding has been detected.
    Islanding detected
    1004
    1. Country setup
    2. Interface protection
    Voltage
    IL
    ML
    OL
    (1)
    Trigger range
    OV
    Overvoltage
    UV
    Undervoltage
    tx
    Protection time
    Inner limits
    Parameter
    Description
    Undervoltage U<
    Overvoltage U>
    Overvoltage time U>
    Middle limits
    Parameter
    Description
    Undervoltage U<
    Overvoltage U>
    Overvoltage time U>
    Outer limits
    Parameter
    Description
    Undervoltage U<<
    Overvoltage U>>
    Parameter
    Description
    Overvoltage U>
    Parameter
    Description
    Parameter
    Description
    Undervoltage U<
    Overvoltage U>
    Parameter
    Description
    Mode
    Designation
    Description
    StateCode name
    StateCode number
    Overvoltage
    AC voltage too high
    1114
    Undervoltage
    AC voltage too low
    1119
    Overfrequency
    1035
    Underfrequency
    1037
    1115, 1116
    1117
    Islanding detected
    1004
    1. Country setup
    Frequency
    This chapter covers the protection settings for overfrequency and underfrequency. To this end, grid-frequency limit values are defined. They depend on the country-specific setup and can be adjusted as described below.
    Each frequency limit value is defined by:
    • an underfrequency with corresponding protection time, or
    • an overfrequency with corresponding protection time.
    The protection time describes the duration during which the frequency may remain outside the respective frequency limit value before the inverter shuts down with an error message. Two overfrequency and two underfrequency limit values can be used. The inner limits (f< for underfrequency; f> for overfrequency) refer to the limit values that are closer to the rated frequency than the outer limits (f<< for underfrequency; f>> for overfrequency). To make effective use of both ranges, set the inner limit values for a longer time period than the outer limit values.
    IL
    Inner limit - Inner limit value
    OL
    Outer limit - Outer limit value
    (1)
    Trigger range
    OF
    Overfrequency
    UF
    Underfrequency
    In backup power mode, the inverter itself determines the frequency, and the frequency limit values are therefore not active.
    Inner limits
    Parameter
    Description
    Underfrequency f<
    Setting value for underfrequency protection f< in [Hz]
    Underfrequency time f<
    Time setting value for underfrequency protection f< in [s]
    Overfrequency f>
    Setting value for overfrequency protection f> in [Hz]
    Overfrequency time f>
    Time setting value for overfrequency protection f> in [s]
    Outer limits
    Parameter
    Description
    Frequency outer limits
    Activation/deactivation of the outer frequency limit values On/Off
    Underfrequency f<<
    Setting value for underfrequency protection f<< in [Hz]
    Underfrequency time f<<
    Time setting value for underfrequency protection f<< in [s]
    Overfrequency f>>
    Setting value for overfrequency protection f>> in [Hz]
    Overfrequency time f>>
    Time setting value for overfrequency protection f>> in [s]
    Alternative limits
    There is also a second set of parameters for the internal frequencies limit values that apply only to Italy. To enable the second set of parameters, you need to set the alternative frequency limit value to On on the user interface of the inverter and enable/disable it via an external signal as follows:
    • Activation: http://<IP>/status/SetSignaleEsterno
    • Deactivation: http://<IP>/status/ClearSignaleEsterno
    Each time the inverter is restarted, the Frequency alternative limit does not need to be set to On again, but the external signal to activate it must be sent again. If it is not sent, the inner frequency limit value is used.
    Parameter
    Description
    Frequency alternative limits
    Activation/deactivation of alternative frequency limit values On/Off
    Underfrequency f<
    Setting value for alternative underfrequency protection f< in [Hz]
    Time setting value for alternative underfrequency protection f< in [s]
    Overfrequency f>
    Setting value for alternative surge protection f> in [Hz]
    Time setting value for alternative surge protection f> in [s]
    Before the inverter switches to backup power mode in fast-switching mode, the frequency connection conditions must be met.
    Parameter
    Description
    Underfrequency f<
    Overfrequency f>
    • Reconnection: reconnecting the inverter to the grid after a grid fault (see the Grid faults table) (e.g., if a fault occurs in the AC grid during the day, causing the inverter to shut down).
    The limit values used for checking the connection conditions depend on whether a grid fault has occurred and which mode is defined. The mode affects only the limit values and not the monitoring time. The monitoring time is determined by the parameters described in General settings / Startup and reconnection. The monitoring time used depends on whether the process is a startup or reconnection and applies equally to frequency and voltage limit values. Once the grid monitoring period has elapsed, the previously mentioned “Interface protection” values become active. In backup power mode, these “Startup and reconnection” parameters are not active.
    Parameter
    Description
    “Mode”
    • Startup values are used for reconnection: When the inverter reconnects after a grid fault, the startup values are used as connection criteria. During a normal startup, the frequency inner limits f< and f> are used as connection criteria.
    Startup minimum frequency
    Lower value of the grid frequency for the normal startup process in [Hz]
    Startup maximum frequency
    Upper value of the grid frequency for the normal startup process in [Hz]
    Reconnection minimum frequency
    Lower value of the grid frequency for reconnection in [Hz]
    Reconnection maximum frequency
    Upper value of the grid frequency for reconnection in [Hz]
    Tripping time for frequency limit violation
    Tripping time when the frequency limit value is exceeded in [s]
    Designation
    Description
    StateCode name
    StateCode number
    Overvoltage
    AC voltage too high
    1114
    Undervoltage
    AC voltage too low
    1119
    Overfrequency
    1035
    Underfrequency
    1037
    1115, 1116
    Grid voltage exceeds the long time overvoltage limit (Long time average limit).
    1117
    Islanding detected
    1004
    Rate of change of frequency (RoCoF) protection
    This function allows you to enable and configure RoCoF (rate of change of frequency) ‑detection and shutdown ‑. If frequency changes exceed a set value and last longer than the set time, the inverter will shut down. RoCoF detection is a passive islanding detection method.
    IMPORTANT!
    RoCoF detection is a protective function that specifically detects critical frequency changes and shuts down the inverter if necessary. It is not a function designed to allow rapid frequency changes without shutting down the inverter (RoCoF robustness). RoCoF robustness is an intrinsic capability of an inverter and cannot be enabled or disabled.
    Parameter
    Value range
    Default value
    Description
    On/Off
    Off
    Activation and deactivation of the RoCoF protection.
    RoCoF limit
    0.05 - 99 Hz/s
    2.5 Hz/s
    Limit value for the frequency change that causes a shutdown when RoCoF detection is activated.
    RoCoF detection measurement window time
    0.04 - 10 s
    0.5 s
    Measurement window length for calculating the RoCoF value
    RoCoF trip time
    0.05 - 16 s
    0.3 s
    Setting value for the RoCoF protection shutdown time.
    1. Country setup
    Export limit protection (PAV,E) monitors compliance with the feed-in limit agreed upon with the utility. If the limit values are exceeded or the control response is too slow, all inverters in the system are shut down.
    Pmom, grid
    Measured, current power of feeding in
    Pinst
    Total AC power installed (Pinst) – installed active power of all operated producers in the system
    PAV,E
    Maximum grid feed-in power (PAV,E) – agreed feed-in limit
    PAV,E protection setting values
    Parameter
    Explanation
    Switch-off value*
    Factor P>>>
    y-coordinate point 1
    90% (0.9)
    Time P>>>
    x-coordinate point 1
    1.6 s
    Factor P>>
    y-coordinate point 2
    15% (0.5)
    Time P>>
    x-coordinate point 2
    4 s
    Factor P>
    y-coordinate point 3
    5% (0.05)
    Time P>
    x-coordinate point 3
    11 s
    *The above example values apply to Germany.
    1. Country setup
    DC injection
    DC injection refers to the feeding of an AC current into the public grid that unintentionally contains a DC component. This DC component causes a shift in the pure AC current along the y axis (offset).
    Due to the way the inverter operates, DC injection does not occur during normal operation. However, for protection against malfunctions or inaccuracies, many connection regulations require monitoring of DC injection and a shutdown if limit values are exceeded.
    Inner and outer limits can be defined for the limit values. By default, inner limits have tighter limit values and longer protection times, while outer limits have wider limit values and shorter protection times, so that shutdown occurs more quickly when DC components are higher. For both limit values, there is a protection time that defines the maximum duration of the exceedance.
    Inner limit
    Parameter
    Value range
    Description
    Mode
    Off
    Inner limit monitoring is disabled.
    Absolute
    DC component monitoring with an absolute current limit in [A].
    Relative
    DC component monitoring with a relative current limit in [%] based on the inverter’s nominal current.
    DC current absolute value
    0.0 A ‑ 10.0 A
    Absolute DC current limit in [A] - If the DC component of the injected AC current exceeds this limit for the duration defined by the DC injection time, grid-feeding operation is interrupted with status code 1052.
    This limit applies only in Absolute mode.
    DC current relative value
    0.0 % ‑ 10.0 %
    Relative DC limit in [%] based on the inverter’s nominal current - If the relative DC component of the injected AC current exceeds this limit for the duration defined by the DC injection time, grid-feeding operation is interrupted with status code 1052.
    This limit applies only in Relative mode.
    DC injection time
    0.0 s ‑ 10.0 s
    Protection time for the inner limit - The system shuts down after the respective limit value for this time has been exceeded.
    Outer limit
    Parameter
    Value range
    Description
    Mode
    Off
    Monitoring of the outer limit is disabled.
    Absolute
    Relative
    0.0 A ‑ 10.0 A
    0.0 % ‑ 10.0 %
    DC injection time
    0.0 s ‑ 10.0 s
    Protection time for the upper limit - The system shuts down after the respective limit value for this time has been exceeded.
    1. Country setup
    In the event of disturbances in the grid, there is a risk of an unintentional shutdown of a large number of power plants and, consequently, a risk of grid failures. Grid voltage faults (voltage faults, grid voltage disturbances) are short-term voltage dips or surges in the grid. These voltage changes exceed the normal operating voltage range (e.g., nominal voltage ± 10%). However, the duration of these voltage changes is brief, so that the normal operating voltage is restored before the system shuts down (due to interface protection). Voltage fault ride-through means that the inverter can withstand such a grid voltage disturbance without shutting down prematurely. If the shutdown conditions of the protection settings (grid and system protection or interface protection) are met (time and value), the inverter always shuts down, thereby ending VFRT operation. The requirements for the exact behavior of the inverters during the fault depend on the respective grid connection rules. The parameters described below determine this behavior.
    Division into regions
    The inverter’s voltage disturbance detection system identifies severe or rapid changes in grid voltage and classifies them into so-called regions based on the magnitude of the fault voltage (voltage level during the disturbance). Each region is assigned a specific range of grid voltage values. You can configure 3 individual regions: R1, R2, and R3. Each region has an adjustable detection threshold and several parameters that determine the inverter’s behavior within that region. The detection threshold is a relative voltage value and is specified as a percentage of the nominal AC voltage. A value greater than 100% indicates that the corresponding region describes an overvoltage disturbance (high-voltage ride-through, HVRT). A value less than 100% means that the corresponding region describes an undervoltage disturbance (low-voltage ride-through, LVRT). Figure  1 shows an example of a typical arrangement of the 3 regions (shown here as horizontal bars) achieved through the deliberate selection of detection thresholds: R1 threshold 110%, R2 threshold 90%, R3 threshold 40%. The voltage range between the limits of Region 1 and Region 2 (white bar) covers the voltage range for normal operation (here: 90 - 110% of the nominal voltage). Region 1 handles overvoltage disturbances. Region 2 handles mild undervoltage disturbances (from 90 - 40%). Region 3 handles severe undervoltage disturbances (below 40%).
    Division of the grid voltage range into 3 fault regions through the selection of detection thresholds.
    IMPORTANT!
    The length of the bars represents trip times for overvoltage and undervoltage detection in the “Interface protection” function group. This has no bearing on the VFRT functionality.
    Regions R1 through R3 must have decreasing detection threshold values:
    • The R1 threshold must be higher than the R2 threshold, and so on.
    • Using identical thresholds for multiple regions is prohibited.
    • The use of the threshold value 0% is permitted.
    To disable a specific region, you can use its threshold value:
    Disable an HV region (R1) by setting the threshold to 200%. Disable an unused LV region (usually R3) by setting the threshold to 0%.
    General VFRT settings
    The following settings apply equally to all regions.
    Parameter
    Value range
    Default value
    Description
    Mode
    On
    The VFRT function is active according to the set parameter values.
    Off
    Off
    Unless specific behavior is required during grid disturbances, this setting tells the inverter to operate according to the default values in this table. Any parameter settings that have been configured are ignored.
    Region 1
    These settings define how the inverter operates within Region 1. The setting selected has no effect on Regions 2 or 3.
    Parameter
    Value range
    Default value
    Description
    Static threshold
    0 ‑ 200
    [% UacNominal
    125%
    Static voltage threshold (as % of the nominal voltage) that the value must exceed or fall below to activate VFRT Region 1 and its associated current injection mode.
    • > 100% - Region 1 is used as the HVRT region.
    • < 100% - Region 1 is used as the LVRT region.
    Setting condition:
    Threshold R1 > Threshold R2 > Threshold R3
    The default value of 125% means that the inverter operates in normal power feed-in mode up to 125% of the nominal voltage. Above 125%, VFRT becomes active with the selected power feed-in mode (default mode for Region 1: “Zero current”).
    Static detection mode
    Voltage system used for static threshold detection in VFRT Region 1.
    For three-phase devices, the minimum value (for LVRT regions) or the maximum value (for HVRT regions) is used from the individual voltages.
    L-N voltage
    L-N voltage
    The phase-neutral voltage system (line-neutral) is used for static threshold detection in VFRT Region 1.
    L-L voltage
    The phase-to-phase voltage system (line-to-line) is used for static threshold detection in VFRT Region 1.
    L-L and L-N voltage
    Both voltage systems (line-neutral and line-line) are used for static threshold detection in VFRT Region 1.
    Current calculation mode
    Power feed-in mode for Region 1.
    This parameter defines the type of power injection during a region 1 voltage disturbance.
    Passive
    The pre-fault behavior is maintained as much as possible during the fault.
    Zero current
    Zero current
    The alternating current is regulated to zero. During the fault, no active or reactive power is fed into the grid.
    Active symmetric current
    Symmetric reactive current (positive-sequence system reactive current) is fed into the grid. The amount of the additional reactive current is calculated by multiplying the k-factor positive sequence by the amount of the voltage dip. No active current is fed into the grid.
    Active asymmetric current
    Additional reactive current is fed into the grid. At the same time, active current is fed in (with reactive current taking priority). The amount of the additional reactive current is determined by the k-factors multiplied by the amount of the voltage dip. If the k-factor negative sequence is set to 0, the injection is symmetric. Otherwise, the system responds to asymmetric faults with an asymmetric current injection.
    0 ‑ 10
    2.0
    Multiplication factor (k-factor) for the positive-sequence system reactive current in Region 1.
    Applies only to the “Active symmetric current” and “Active asymmetric current” power feed-in modes.
    0 ‑ 10
    2.0
    Multiplication factor (k-factor) for the negative-sequence system reactive current in Region 1.
    Applies only to the “Active asymmetric current” power feed-in mode. When asymmetric power injection is required, this setting is typically configured to match the “k-factor positive sequence” setting. When symmetric power injection is required, this setting is set to 0.
    Region 2
    These settings define how the inverter operates within Region 2. The setting selected has no effect on Regions 1 or 3.
    Parameter
    Value range
    Default value
    Description
    Static threshold
    0 ‑ 200
    [% UacNominal]
    40%
    Static voltage threshold (as % of the nominal voltage) that the value must exceed or fall below to activate VFRT Region 2 and its associated current injection mode.
    • > 100% - Region 2 is used as the HVRT region.
    • < 100% - Region 2 is used as the LVRT region.
    Setting condition:
    The default value 40% means that the inverter operates in normal current feed-in mode up to 40% of the nominal voltage. Above 40%, VFRT becomes active with the selected current feed-in mode (default mode for Region 2: Zero current).
    Voltage system used for static threshold detection in VFRT Region 2.
    L-N voltage
    L-N voltage
    The phase-neutral voltage system (line-neutral) is used for static threshold detection in VFRT Region 2.
    L-L voltage
    The phase-to-phase voltage system (line-to-line) is used for static threshold detection in VFRT Region 2.
    L-L and L-N voltage
    Both voltage systems (line-neutral and line-line) are used for static threshold detection in VFRT Region 2.
    Power feed-in mode for Region 2.
    This parameter defines the type of power injection during a Region 2 voltage disturbance.
    Passive
    The pre-fault active and reactive current are maintained as long as the fault persists.
    Zero current
    Zero current
    0 ‑ 10
    2.0
    Multiplication factor (k-factor) for the positive-sequence system reactive current in Region 2.
    Applies only to the Active symmetric current and Active asymmetric current power feed-in modes.
    0 ‑ 10
    2.0
    Multiplication factor (k-factor) for the negative-sequence system reactive current in Region 2.
    Applies only to the Active asymmetric current power feed-in mode. When asymmetric power injection is required, this setting is typically set to the same value as the k-factor positive sequence. When symmetric power injection is required, this setting is set to 0.
    Region 3
    These settings define how the inverter operates within Region 3. The setting selected has no effect on Regions 1 or 2.
    Parameter
    Value range
    Default value
    Description
    Static threshold
    0 ‑ 200
    [% UacNominal]
    0%
    Static voltage threshold (as % of the nominal voltage) that the value must exceed or fall below to activate VFRT Region 3 and its associated current injection mode.
    • > 100% - Region 3 is used as the HVRT region.
    • < 100% - Region 3 is used as the LVRT region.
    Setting condition:
    The default value of 0% means that Region 3 is disabled/inactive.
    Voltage system used for static threshold detection in VFRT Region 3.
    L-N voltage
    L-N voltage
    The phase-neutral voltage system (line-neutral) is used for static threshold detection in VFRT Region 3.
    L-L voltage
    The phase-to-phase voltage system (line-to-line) is used for static threshold detection in VFRT Region 3.
    L-L and L-N voltage
    Both voltage systems (line-neutral and line-line) are used for static threshold detection in VFRT Region 3.
    Power feed-in mode for Region 3.
    This parameter defines the type of power injection during a Region 3 voltage disturbance.
    Passive
    Zero current
    Zero current
    0 ‑ 10
    2.0
    Multiplication factor (k-factor) for the positive-sequence system reactive current in Region 3.
    0 ‑ 10
    2.0
    Multiplication factor (k-factor) for the negative-sequence system reactive current in Region 3.
    General setting - Voltage fault ride-through
    Parameter
    Value range
    Default value
    Description
    Reactive current limit for overexcited operation
    0 ‑ 110
    [% IacNominal]
    100%
    Limitation of reactive current during a line voltage disturbance and overexcitation, expressed as a percentage [%] of the nominal current IN.
    This parameter is effective only for the “Active asymmetric current” power feed-in mode.
    Reactive current limit for underexcited operation
    0 ‑ 110
    [% IacNominal]
    100%
    Limitation of reactive current during a line voltage disturbance and underexcited operation, expressed as a percentage [%] of the nominal current IN.
    Follow-up time
    0 - 1
    0.02
    Sudden voltage change detection (SVCD)
    On
    The detection of sudden voltage changes within the normal voltage range is enabled.
    So-called sudden voltage changes do not typically exceed static voltage limits, but they are indicators of power grid disturbances.
    Off
    Off
    No detection of sudden voltage changes within the normal voltage range.
    Insensitivity range (SVCD)
    0 ‑ 100
    [% Uac 1s‑Avg]
    5%
    The limit value that a sudden voltage change (a change in the positive-sequence or negative-sequence system voltage) must exceed in order for a grid voltage disturbance to be detected. The reference value used to calculate this limit value is the moving average of the grid voltage over 1 second (1s‑Avg).
    Deactivation time (SVCD)
    0 ‑ 100 [s]
    5 s
    Time duration of the grid disturbance handling for sudden voltage changes. Once this time has elapsed, the grid disturbance handling is automatically terminated if no static voltage limits were violated (see the Threshold static parameter under Regions 1, 2, and 3).
    Operating range check
    On/Off
    On
    VFRT deactivation if the voltage remains below the Operation range undervoltage limit for the duration of the Operation range undervoltage timeout.
    Operating range undervoltage limit
    0 - 100%
    10
    Undervoltage limit for the Operation range check
    0 - 100 s
    1.2
    Time for Operation range check
    1. Country setup
    2. Grid support functions
    IMPORTANT!
    Parameter
    Value range
    Default value
    Description
    Mode
    On
    Off
    Off
    Region 1
    Parameter
    Value range
    Default value
    Description
    Static threshold
    0 ‑ 200
    [% UacNominal
    125%
    Setting condition:
    L-N voltage
    L-N voltage
    L-L voltage
    L-L and L-N voltage
    Passive
    Zero current
    Zero current
    0 ‑ 10
    2.0
    0 ‑ 10
    2.0
    Region 2
    Parameter
    Value range
    Default value
    Description
    Static threshold
    0 ‑ 200
    [% UacNominal]
    40%
    Setting condition:
    L-N voltage
    L-N voltage
    L-L voltage
    L-L and L-N voltage
    Passive
    Zero current
    Zero current
    0 ‑ 10
    2.0
    0 ‑ 10
    2.0
    Region 3
    Parameter
    Value range
    Default value
    Description
    Static threshold
    0 ‑ 200
    [% UacNominal]
    0%
    Setting condition:
    L-N voltage
    L-N voltage
    L-L voltage
    L-L and L-N voltage
    Passive
    Zero current
    Zero current
    0 ‑ 10
    2.0
    0 ‑ 10
    2.0
    Parameter
    Value range
    Default value
    Description
    0 ‑ 110
    [% IacNominal]
    100%
    0 ‑ 110
    [% IacNominal]
    100%
    Follow-up time
    0 - 1
    0.02
    On
    Off
    Off
    0 ‑ 100
    [% Uac 1s‑Avg]
    5%
    0 ‑ 100 [s]
    5 s
    On/Off
    On
    0 - 100%
    10
    0 - 100 s
    1.2
    1. Country setup
    Active power
    Voltage-dependent power control
    Also known as the volt/watt function or P(U) function, it causes a change in active power depending on the grid voltage. Reducing active power when the grid voltage is high (or increasing active power when the grid voltage is low) prevents the inverter from shutting down unintentionally due to overvoltage or undervoltage limits. The resulting loss of output is less than the loss that would occur if the inverter were to shut down.
    When this function is enabled, the active power behaves as follows if a defined grid voltage limit value is exceeded:
    • Reduces when the grid voltage is too high, according to a defined gradient (see the System without storage example, red characteristic line)
    • Increases when the grid voltage is too low, according to a defined gradient (possible only with hybrid inverters; see the System with storage example, green characteristic line).
    With a hybrid inverter that has Active grid support enabled, additional scenarios arise:
    • If the output power has already been reduced to 0 W due to excessively high voltage and the voltage continues to rise, additional energy can be drawn from the public grid (this charges the battery; see System with storage and active grid support enabled, blue characteristic line in the lower power input area).
    • If the charging power (drawn from the public grid) is reduced to 0 W when the voltage is too low and the voltage continues to drop, additional energy can be drawn from the battery to increase the output power (see the System with storage and active grid support enabled example, blue characteristic line in the upper power output area).
    Examples of active grid support:
    (Graph - red characteristic line)
    Parameter description
    • Mode: On (without hysteresis)
    • No battery is present in the system
    • Active grid support: Off
    • Calculation mode: Pmax = Pm‑Pn(k*df)
    (1)
    Instantaneous active power when the activation threshold overvoltage is reached: 50% of Pn (device nominal output)
    (2)
    Activation threshold overvoltage: 250 V
    (3)
    Gradient overvoltage: 7.5%/V
    System with storage and active grid support disabled
    (Graph - green characteristic line)
    • Battery is active
    (1) (4)
    Instantaneous active power when the value reaches the respective activation threshold: 50% of Pn (device nominal output)
    (2)
    (3)
    (5)
    Activation threshold undervoltage: 210 V
    (6)
    Gradient undervoltage: 7.5%/V
    (Graph - blue characteristic line)
    • Battery is active
    • Active grid support: On
    (1) (4)
    (2)
    (3)
    (5)
    (6)
    General power curve as a function of grid voltage.
    SOC (state of charge) limits can be set for active grid support with battery. If a limit is reached, the battery is no longer used for active grid support. These limits can be found under Battery SoC limitation for grid support:
    • Battery SoC lower limit - The battery will not discharge any further once the lower limit is reached.
    • Battery SoC upper limit - The battery will stop charging once the upper limit is reached.
    Parameter
    Value range
    Description
    Availability
    Mode
    Off
    Function is activated.
    Voltage reference
    Common mode voltage
    The reference voltage is the average system voltage.
    Average
    The reference voltage is the average of the P-N voltages.
    Maximum voltage
    The reference voltage is the highest of the 3 P-N voltages.
    Minimum voltage
    The reference voltage is the lowest of the 3 P-N voltages.
    208 ‑ 311 [V]
    Grid voltage limit value at which power reduction begins.
    0.01 ‑ 100 [%/V]
    The rate at which active power is reduced.
    Example - Conversion from static to gradient:
    Static s = 4% → Gradient k = 1/(0.04 × 230 V) = 10.9%/V
    Calculation mode
    Pmax =
    Pm-Pm(k*dV)
    Pmax =
    Pn-Pn(k*dV)
    Pmax =
    Pm-Pn(k*dV)
    Specifies the reference power used to calculate the power limit in the event of overvoltage or undervoltage.
    Reference power:
    • Pm → Instantaneous power when the power exceeds grid voltage limit value.
    • Pn → Rated power of the device.
    Active grid support
    Off
    Disables advanced, active grid support for devices with batteries.
    Has no effect in the following setups:
    • OFF
      Region A 2020
    • OFF
      Region B 2020
    • OFF
      Region C 2020
    • NZS 2020
    On
    Enables advanced, active grid support for devices with batteries.
    0 ‑ 311 [V]
    Grid voltage limit value at which the power output increases.
    0 ‑ 100 [%/V]
    The rate at which active power increases.
    Time constant (τ)
    0 ‑ 600 [s]
    Time constant (1 tau) in seconds [s]. Whenever the set value changes, the new set value is not reached abruptly but is adjusted gradually according to PT1 behavior. The time constant describes how quickly the new set value is reached. (After 3 time constants, 95% of the final value is reached.)
    Stop voltage at overvoltage
    0 ‑ 311 [V]
    Grid voltage limit value at which power reduction occurs. The gradient is calculated automatically based on the Activation threshold overvoltage and Power at stop voltage at overvoltage parameters. The Gradient overvoltage and Calculation code parameters have no function.
    Used exclusively in the following setups:
    • OFF
      Region A 2020
    • OFF
      Region B 2020
    • OFF
      Region C 2020
    • NZS 2020
    Power at stop voltage - overvoltage
    0 ‑ 100 [%]
    Power consumption when the set grid voltage limit value is reached.
    Activation delay
    0 ‑ 60 s
    Wait time before the P(U) function is activated
    Reset delay
    0 ‑ 60 s
    Waiting period for a power increase following a P(U) event
    Example: Setups OFF/NSZ 2020
    (1)
    (2)
    Stop at voltage at overvoltage: 260 V
    (3)
    Power at stop voltage - overvoltage: 20%
    Power curve when the power exceeds the Activation threshold overvoltage
    Parameter
    Value range
    Description
    Availability
    Stop voltage at undervoltage
    200 ‑ 311 [V]
    Grid voltage limit value at which the battery charging power is reduced. The gradient is calculated automatically based on the Activation threshold undervoltage and Power at stop voltage at undervoltage parameters. The Gradient undervoltage and Calculation mode parameters have no function.
    • OFF
      Region A 2020
    • OFF
      Region B 2020
    • OFF
      Region C 2020
    • NZS 2020
    Power at stop voltage - undervoltage
    0 ‑ 100 [%]
    Power consumption when the set grid voltage limit value is reached. Applies only to devices with a battery in charging mode.
    (1)
    (2)
    Stop at voltage at undervoltage: 200 V
    (3)
    Power at stop voltage - undervoltage: 20%
    Charging power limit when power exceeds the Activation threshold undervoltage.
    Frequency-dependent power control
    Also known as the frequency/watt function or P(f) function, it causes a change in active power depending on the grid frequency.
    • Overfrequency
    • Underfrequency
    When this function is enabled, the active power behaves as follows if a defined grid frequency limit value is exceeded:
    • Reduces in the event of overfrequency according to a defined gradient (For an inverter with a storage system, discharging from the storage system is stopped before the PV array’s output is reduced.)
    • Increases in the event of underfrequency according to a defined gradient (For an inverter without storage or with active grid support disabled, this behavior occurs only in conjunction with a manual power reduction and the corresponding priority.)
    The gradients depend on the Configuration method parameter:
    • Gradient: The gradient is specified as a percentage per hertz (%/Hz) relative to the device’s nominal output or the instantaneous power at the time the function is activated (see Example 1).
    • Stop frequency: With this method, the gradient is always calculated based on the current power at the time the function is activated for the stop frequency set in the setup and power at stop frequency (see Example 2).
    For an inverter with storage and active grid support enabled, additional scenarios arise:
    • If the output power has already been reduced to 0 W due to overfrequency and the frequency continues to rise, additional energy can be drawn from the grid (which charges the battery).
    • If the charging power (drawn from the grid) is reduced to 0 W during underfrequency and the frequency continues to drop, additional energy can be drawn from the battery to increase the output power.
    SOC (state of charge) limits can be set for active grid support with a battery. These can be found under Battery SoC limitation for grid support:
    If, after power has been reduced, the grid frequency returns to within an acceptable frequency range, the system can resume operating at full available power as follows, depending on the country-specific setup:
      The inverter increases the power from its currently reduced level to its original level, following the same gradient as that used for the power reduction.
    • Mode: On (with hysteresis)
      The inverter does not increase the power to its original level until the frequency has been within the target range for a certain period of time.
    Example 1
    • P(f) mode: On (without hysteresis)
    • Configuration method: Gradient
    • Calculation mode underfrequency: Pmax = Pm-Pn(k*df)
    • Calculation mode overfrequency: Pmax = Pm-Pn(k*df)
    (1)
    Instantaneous active power when the respective activation threshold is reached: 60% of Pn (nominal output).
    (2)
    Gradient underfrequency: 80%/Hz - Increasing the output power without a battery is possible only if sufficient power is available from the PV array and manual power limitation is active. The Priority at underfrequency parameter must be set to Priority on frequency-dependent power limitation for this to work.
    (3)
    Activation threshold underfrequency: 49.7 Hz
    (4)
    Gradient overfrequency: 60%/Hz
    (5)
    Activation threshold overfrequency: 50.3 Hz
    General performance curve for overfrequency and underfrequency without hysteresis, with gradients.
    Example 2
    • Configuration method: Stop frequency
    (1)
    (2)
    (3)
    Stop frequency - underfrequency: 49.0 Hz
    (4)
    Power at stop frequency - underfrequency: 85%
    (5)
    (6)
    Stop frequency - overfrequency: 51.3 Hz
    (7)
    Power at stop frequency - overfrequency: 20%
    General performance curve for overfrequency and underfrequency without hysteresis, with stop frequency.
    Example 3
    • P(f) mode: On (with hysteresis)
    (1)
    (2)
    (3)
    “Activation threshold underfrequency”: 49.7 Hz
    (4)
    Lower deactivation threshold underfrequency: 49.9 Hz
    (5)
    Upper deactivation threshold underfrequency: 50.1 Hz
    (6)
    (7)
    (8)
    Lower deactivation threshold overfrequency: 49.9 Hz
    (9)
    Upper deactivation threshold overfrequency: 50.1 Hz
    (10)
    Deactivation time: 30 s
    General performance curve for overfrequency and underfrequency with hysteresis, with gradients.
    Parameter
    Value range
    Description
    Availability
    Mode
    Off
    The function is enabled with hysteresis.
    The function is enabled without hysteresis.
    In the following setups, On (without hysteresis) is not possible:
    • OFF
      Region A 2020
    • OFF
      Region B 2020
    • OFF
      Region C 2020
    • NZS 2020
    Gradient
    For calculating the power limitation based on the Gradient overfrequency or Gradient underfrequency parameters.
    Stop - frequency
    The gradient is calculated automatically using the Stop frequency - overfrequency and Power at stop frequency - overfrequency parameters, as well as the Stop frequency - underfrequency and Power at stop frequency - underfrequency parameters.
    Transition frequency at overfrequency
    45 ‑ 66 [Hz]
    The frequency at which the device, with the battery active, achieves an output power of 0 W. If the grid frequency continues to rise, power is drawn from the public grid, which charges the battery. If there is no battery in the system or it is inactive, this parameter has no function (behavior as in Example 3 - overfrequency).
    • OFF
      Region A 2020
    • OFF
      Region B 2020
    • OFF
      Region C 2020
    • NZS 2020
    Transition frequency at underfrequency
    45 ‑ 66 [Hz]
    Frequency at which the device, with the battery active, achieves an output power of 0 W (charging power is reduced). If the grid frequency drops further, additional energy is fed into the grid. This energy can come from the PV array or from the battery. If there is no battery in the system or it is inactive, this parameter has no function (behavior as in Example 3 - underfrequency).
    • OFF
      Region A 2020
    • OFF
      Region B 2020
    • OFF
      Region C 2020
    • NZS 2020
    Overfrequency
    Parameter
    Value range
    Description
    Availability
    Pmax =
    Pm-Pm(k*df)
    Specifies the reference power for calculating the power limit in the event of an overfrequency condition.
    Reference power
    • Pm → Instantaneous power when the power exceeds the frequency limit value.
    • Pn → Nominal output of the device.
    Pmax =
    Pn-Pn(k*df)
    Pmax =
    Pm-Pn(k*df)
    45 ‑ 66 [Hz]
    Frequency limit value at which power reduction begins.
    0.01 ‑ 300 [%/Hz]
    Static s = 5% → Gradient k = 1/(0.05 × 50 Hz) = 40%/Hz
    45 ‑ 66 [Hz]
    The frequency value at which the power reduction ends.
    -100 ‑ 0 [%]
    Power output when the set frequency limit value Stop frequency - overfrequency is reached. Can be configured between 0% and full charging power (-100%).
    45 ‑ 66 [Hz]
    Used when Mode - On (with hysteresis) is selected.
    If the grid frequency falls below this value, the frequency-dependent power reduction is terminated, taking into account the settings under Frequency-dependent power control - general settings.
    45 ‑ 66 [Hz]
    If this value is less than the Upper deactivation threshold overfrequency, a frequency window is defined within which the grid frequency must fall for the function to be terminated. If this value is greater than or equal to the Upper deactivation threshold overfrequency, it is not applied.
    Example 4: Setups OFF/NSZ 2020
    • Battery is active
    (1)
    (2)
    The gradient for power reduction during generator-powered operation at overfrequency is automatically determined by the two set parameters, Activation threshold overfrequency and Transition frequency at overfrequency.
    (3)
    Activation threshold overfrequency: 50.25 Hz
    (4)
    Transition frequency at overfrequency: 50.75 Hz
    (5)
    The gradient for increasing the charging power at overfrequency is automatically determined by the two set parameters, Transition frequency at overfrequency and Stop frequency - overfrequency. Depending on the selected country setup, the power at the stop frequency refers to 100% of the power drawn from the public grid. The Power at stop frequency – overfrequency parameter has no function in these countries.
    (6)
    Stop frequency - overfrequency: 52.0 Hz
    (7)
    Upper deactivation threshold overfrequency: 50.0 Hz - When the grid frequency returns to or falls below the set limit value, the active power may be increased again.
    (8)
    Deactivation time: 20  - The frequency must remain within the valid range for at least this amount of time before the function ends.
    (9)
    Return gradient 1: Return to the power level prior to entering P(f), expressed in percent per second.
    Power curve for overfrequency with hysteresis.
    Underfrequency
    Parameter
    Value range
    Description
    Availability
    Active grid support
    Off
    • OFF
      Region A 2020
    • OFF
      Region B 2020
    • OFF
      Region C 2020
    • NZS 2020
    On
    Pmax =
    Pm-Pm(k*df)
    Specifies the reference power used to calculate the power limit in the event of underfrequency.
    Reference power
    Pmax =
    Pn-Pn(k*df)
    Pmax =
    Pm-Pn(k*df)
    45 ‑ 66 [Hz]
    Frequency limit value at which the power increase begins.
    0 ‑ 100 [%/Hz]
    45 ‑ 66 [Hz]
    Frequency at which the increase in power ceases.
    0 ‑ 100 [%]
    Power output when the set frequency limit value Stop frequency - underfrequency is reached. Can be configured between 0% and full power of feeding in (100%).
    45 ‑ 66 [Hz]
    If this value is greater than the Lower deactivation threshold for underfrequency, a frequency window is defined within which the grid frequency must fall for the function to be deactivated. If this value is less than or equal to the Lower deactivation threshold for underfrequency, it is not applied.
    45 ‑ 66 [Hz]
    In use when set to Mode - On (with hysteresis).
    If the grid frequency exceeds this value, the function is terminated in accordance with the settings under Frequency-dependent power control - General settings.
    Example 5: Setups OFF/NSZ 2020
    • Battery is active
    (1)
    Current draw (battery discharge rate) when the respective Activation threshold is reached (3): 80% of Pn (nominal output)
    (2)
    The gradient for reducing the charging power during underfrequency is automatically determined by the two set parameters, Activation threshold underfrequency (3) and Transition frequency at underfrequency (4).
    (3)
    Activation threshold underfrequency: 49.75 Hz
    (4)
    Transition frequency at underfrequency: 49.0 Hz
    (5)
    The gradient for increasing the output power during underfrequency is automatically determined by the two set parameters, Transition frequency at underfrequency (4) and Stop frequency - underfrequency (6). Depending on the selected country setup, the power at the stop frequency refers to 100% of the output power (nominal output of the inverter). The Power at stop frequency - underfrequency parameter has no function in these countries.
    (6)
    Stop frequency - underfrequency: 48.0 Hz
    (7)
    Lower deactivation threshold underfrequency: 50.0 Hz - When the grid frequency returns to or exceeds the set limit value, the active power may return to the value it had before the function was triggered.
    (8)
    Deactivation time: 20 s - The frequency must remain within the valid range for at least this amount of time before the function ends.
    (9)
    Power curve at underfrequency with hysteresis.
    General setting - Frequency-dependent power control
    Parameter
    Value range
    Description
    Availability
    Return gradient 1
    0.01 ‑ 100 [%/s]
    Rate of change at which the inverter increases the active power after limiting has ended.
    Return gradient 1 alternative
    0.01 ‑ 100 [%/s]
    Rate of change at which the inverter increases active power after limiting has ended. This is activated when the difference between the rated power and the currently reduced power is greater than the Return Gradient 1 alternative threshold value.
    Return gradient 1 alternative threshold
    0 ‑ 100 [W%]
    Threshold value at which Return gradient 1 or Return gradient 1 alternative is applied.
    Example:
    If the difference between the rated power and the currently reduced power is less than or equal to the threshold value, Return gradient 1 is applied. If the difference between the rated power and the currently reduced power is greater than the threshold value, Return gradient 1 alternative is applied. 0.01 - 100%. 100% means that Return gradient 1 is always applied.
    Example 6
    Pm
    Instantaneous power at the moment the power exceeds the limit value
    Pred
    Reduced performance
    (1)
    (2)
    Deactivation time
    (3)
    Return gradient 1
    (4)
    (5)
    Return gradient 1 alternative threshold: Pm - Pred ≤ 25%
    (6)
    Return gradient 1 alternative threshold: Pm - Pred > 25%
    (7)
    Intentional delay
    The grid frequency returns to the permissible range at Pred.
    After the wait time (2) has elapsed, the power is increased to the initial value Pm using one of the following gradients:
    Route 1 - red
    The difference between the current power Pm and the reduced power Pred is ≤ the Return gradient 1 alternative threshold of 25% (5). Thus, the power is increased to the initial value Pm using Return gradient 1 (3).
    Route 2 - gray
    The difference between the current power Pm and the reduced power Pred is greater than the Return gradient 1 alternative threshold of 25% (5). Consequently, the power is increased to the initial value Pm using Return gradient 1 alternative (4).
    Application example of Return gradient 1 alternative and Return gradient 1 alternative threshold.
    Parameter
    Value range
    Description
    Availability
    Return gradient 2 mode
    Off
    Disables the use of Return gradient 2. Return gradient 1 controls the increase in active power from the reduced value to the device’s rated power.
    On
    Enables a different rate of change at which the inverter increases the active power from its initial value to the device’s rated power. Return gradient 2 controls the increase in active power from its initial value to the device’s rated power.
    Return gradient 2
    0.01 ‑ 100 [%/s]
    Rate of change at which the inverter increases the active power from its initial value to the device’s rated power.
    Example 7
    • Return gradient 2 mode = On
    Pm
    Pred
    Reduced performance
    (1)
    (2)
    Deactivation time
    (3)
    Return gradient 1
    (4)
    Return gradient 2
    (5)
    Intentional delay
    The grid frequency returns to the permissible range at Pred. After the wait time (2) has elapsed, the power is increased to the initial value Pm using Return gradient 1. The power is then increased to the device’s rated power Pn using Return gradient 2 (4).
    Application example of Return gradient 2 mode.
    Parameter
    Value range
    Description
    Availability
    Deactivation time
    0 ‑ 600 [s]
    Delay period after which the inverter increases its output again (once the grid frequency has returned to within the permitted frequency range between the Upper deactivation threshold and the Lower deactivation threshold).
    Intentional delay
    0.5 ‑ 60 [s]
    Delays the onset of frequency-dependent power control after the power exceeds the respective Activation threshold.
    Time constant (τ)
    0 ‑ 60 [s]
    Parameter
    Value range
    Description
    Availability
    Mode
    Off
    SoC limitation disabled
    On
    SoC limitation enabled
    0 ‑ 100%
    The battery will not discharge any further once it reaches the lower limit.
    0 ‑ 100%
    The battery stops charging once it reaches the upper limit.
    General setting - active power
    Parameter
    Value range
    Description
    Availability
    Priority on manual power limitation
    When Priority on manual power limitation is enabled, power will not be increased beyond the set limit in the event of underfrequency.
    When Priority on frequency-dependent power limitation is enabled, underfrequency will cause the manual power limit to be ignored and the output power to be increased based on the frequency. This requires that sufficient energy is available from the PV array or the battery.
    1. Country setup
    Reactive power
    link_horizontalLink copied
    The voltage in the public grid can be influenced by the controlled use of reactive power by the inverter. When reactive power control is used, the active power generated at the same time is not affected, or is affected only to a small extent.
    IMPORTANT!
    The exchange of reactive power (in addition to the injection of active power) increases the current by a factor of 1/cos φ.
    Largely independent of active power, and thus independent of energy yield, reactive power exchange can both increase and decrease the voltage:
    • In overexcited or capacitive operation, reactive power is fed into the public grid. This causes the grid voltage to increase.
    • In underexcited or inductive operation, the inverter draws reactive power. This causes the grid voltage to drop.
    Potential operating range
    Reactive power operation is limited by the maximum apparent power Sn (and the maximum output current) as well as by the inverter’s operative reactive power limit:
    • Primo GEN24: Qmax = 60% of Sn (or cos φ = 0.80 at Sn)
    • Symo GEN24: Qmax = 71% of Sn (or cos φ = 0.70 at Sn)
    • Tauro: Qmax = 100% of Sn (or cos φ = 0.00)
    • Verto: Qmax = 100% of Sn (or cos φ = 0.00)
    Depending on the selected country-specific settings, the value range specified for the following parameters may be further restricted.
    The following figure shows the inverter’s possible operating range. All valid operating points defined by active power P and reactive power Q are within the gray area.
    Example: Primo GEN24
    General settings
    Parameter
    Value range
    Description
    Mode
    Reactive power mode selection option. The following modes are described in the subsections.
    Off
    No reactive power is fed into the grid.
    Cos φ - Constant power factor
    Constant cos φ.
    Q absolute - Constant reactive power
    Constant reactive power in [Var].
    Q relative - Constant reactive power
    Constant reactive power as a percentage [%] of Sn.
    Cos φ(P) - Power-dependent power factor characteristic
    Active power-dependent cos φ control.
    Q(P) - Power-dependent reactive power characteristic
    Active power-based reactive power control.
    Q(U) - Voltage-dependent reactive power characteristic
    Grid voltage-dependent reactive power control.
    P/Q priority
    Q priority
    When the maximum apparent power is reached, the Q priority setting reduces active power in order to meet the reactive power target.
    P priority
    When the maximum apparent power is reached, the P priority setting reduces reactive power in order to maximize the available active power.
    Cos φ minimum
    0 ‑ 1
    Minimum cos φ, which, together with the maximum apparent power, imposes an additional limitation on reactive power when active power is low.
    Depending on the selected mode, only the settings in the respective subsection and these general settings will take effect.
    Constant cos φ
    Reactive power specification defined by a constant cos φ. The function is limited by the maximum apparent power and the minimum cos φ; the P/Q priority has no effect.
    Parameter
    Value range
    Description
    cos φ - Power factor
    0 ‑ 1
    Setting value cos φ (set value)
    Direction/excitation
    The direction of current flow corresponds to the production meter arrow system.
    Injection/overexcited/capacitive
    Overexcited operation = capacitive operation = reactive power is supplied = reactive current is fed into the system lagging behind the active current.
    Absorption/underexcited/inductive
    Underexcited operation = inductive operation = reactive power is drawn = reactive current is fed into the circuit leading the active current.
    Time constant (τ)
    0.01 s ‑ 60 s
    Time constant (1 tau) in seconds [s]. Whenever the set value changes, the new set value is not reached abruptly but gradually, according to PT1 behavior. The time constant describes how quickly the new set value is reached. (After 3 time constants, 95% of the final value is reached.)
    Reactive power specification defined by a constant value [Var]. The function is limited by the maximum apparent power and by “cos φ minimum.”
    Parameter
    Value range
    Description
    Q - Reactive power (Var)
    -200,000 Var to 200,000 Var
    Reactive power setting in [Var] (set value)
    Time constant (τ)
    0.01 s ‑ 60 s
    Reactive power specification defined by a constant value in percent [%], relative to the inverter’s rated apparent power (Sn). The function is limited by the maximum apparent power and by “cos φ minimum.”
    Parameter
    Value range
    Description
    Q - Reactive power (% of power reference)
    -100% - 100%
    Reactive power setting value in percent [%] relative to the rated apparent power (set value)
    Time constant (τ)
    0.01 s ‑ 60 s
    Power reference (RefType)
    Apparent power
    The RefType specifies the basis on which the SetValue for the reactive power specification is calculated. Here, the calculation is based on the inverter’s rated apparent power.
    Reactive power
    Maximum reactive power capacity of the inverter.
    Active power
    Rated active power of the inverter.
    Reactive power available
    This option is hidden by default and is visible only if a specific configuration is set on the inverter.
    This function controls the cos φ as a function of the instantaneous active power according to a characteristic line. The characteristic line is defined by 4 data points (1‑2‑3‑4) for grid feeding operation and 4 points (5-6-7-8) for consumption (battery charging). If fewer data points are required, the same parameters can be set using just 2 points. The function is limited by the maximum apparent power and by cos φ minimum. For the characteristic lines, the data points must be entered on the x‑axis (active power) and on the y‑axis (cos φ).
    Point
    Parameter
    Value range
    Description
    Active power (% of nominal apparent power)
    0% ‑ 100%
    Active power as a percentage [%] of the rated apparent power Sn.
    0 ‑ 1
    Cos φ setting value (set value).
    0% ‑ 100%
    Active power as a percentage [%] of the rated apparent power SN.
    0 ‑ 1
    0% ‑ 100%
    0 ‑ 1
    0% ‑ 100%
    0 ‑ 1
    Active power (% of power reference)
    0% ‑ 100%
    0 ‑ 1
    5
    0% ‑ 100%
    0 ‑ 1
    6
    0% ‑ 100%
    0 ‑ 1
    7
    0% ‑ 100%
    0 ‑ 1
    8
    0% ‑ 100%
    0 ‑ 1
    Example: A curve defined by 4 data points.
    P = 15%, cos , φ = 0.85 - overexcited
    P = 25%, cos , φ = 1 - overexcited
    P = 45%, cos , φ = 1 - overexcited
    P = 90%, cos , φ = 0.9 - underexcited
    General information
    In addition to the 4 points, the following parameters also come into play:
    Parameter
    Value range
    Description
    Additional description
    Lock-in voltage-dependent (% of nominal voltage)
    0% ‑ 120%
    AC voltage as a percentage [%] of the nominal voltage. If this value is exceeded, the cos φ(P) characteristic line is activated.
    The voltage-dependent lock-in/lock-out values can be used to configure the system so that the cos φ(P) control is deactivated at low voltages.
    The different values for activation (lock-in) and deactivation (lock-out) allow for hysteresis to prevent the function from turning on and off frequently by accident. The lock-in value must be greater than the lock-out value for this function to work.
    Lock-out voltage-dependent (% of nominal voltage)
    0% ‑ 120%
    AC voltage as a percentage [%] of the nominal voltage. If the voltage falls below this value, the cos φ(P) characteristic line is deactivated. The lock-out limit takes precedence over the lock-in limit.
    Time constant (τ)
    0.01 s ‑ 60 s
    This function controls the reactive power based on the current active power according to a characteristic line. The characteristic line is defined by 4 data points (1‑2‑3‑4) for grid feeding operation and 4 points (5-6-7-8) for consumption (battery charging). If fewer data points are required, the same parameters can be set using just 2 points. The function is limited by the maximum apparent power and by “cos φ minimum.” For the characteristic lines, the data points must be entered on the x‑axis (active power) and on the y‑axis (reactive power).
    Point
    Parameter
    Value range
    Description
    0% ‑ 100%
    Active power as a percentage [%] relative to the rated apparent power Sn (x‑axis).
    Reactive power (% of nominal apparent power)
    -100% ‑ 100%
    Reactive power as a percentage [%] relative to the rated apparent power Sn (y‑axis).
    0% ‑ 100%
    -100% ‑ 100%
    0% ‑ 100%
    -100% ‑ 100%
    0% ‑ 100%
    -100% ‑ 100%
    5
    0% ‑ 100%
    -100% ‑ 100%
    6
    0% ‑ 100%
    -100% ‑ 100%
    7
    0% ‑ 100%
    -100% ‑ 100%
    8
    0% ‑ 100%
    -100% ‑ 100%
    P = 0%, Q = 0%
    P = 25%, Q = 0%
    P = 50%, Q = 0%
    P = 95%, Q = -32%
    Parameter
    Value range
    Description
    0% ‑ 120%
    AC voltage as a percentage [%] of the nominal voltage. If this value is exceeded, the Q(P) characteristic line is activated.
    The voltage-dependent lock-in/lock-out values can be used to configure the system so that the Q(P) control is deactivated at low voltages.
    0% ‑ 120%
    AC voltage as a percentage [%] of the nominal voltage. If the voltage falls below this value, the Q(P) characteristic line is deactivated. The lock-out limit takes precedence over the lock-in limit.
    Lock-out P-dependent (% of nominal apparent power)
    0% ‑ 100%
    Active power as a percentage [%] of the rated apparent power SN. If this value is not met, the Q(P) characteristic line is deactivated.
    The active power-dependent lock-out values can be used to configure the system so that the Q(P) control is deactivated at low active power levels.
    For characteristic lines with reactive power not equal to 0% at data point 1, reactive power of 0% is resumed when the active power falls below this value. Otherwise, for active power values that are smaller than those defined at data point 1, the reactive power associated with data point 1 remains active.
    Time constant (τ)
    0.01 s ‑ 60 s
    Power reference (Y-RefType)
    Apparent power
    The RefType specifies the basis on which the SetValue for Q(P) - Power-dependent reactive power characteristic is calculated.
    Rated apparent power of the inverter.
    Reactive power
    Active power
    This function controls reactive power based on the instantaneous grid voltage according to a characteristic line. The characteristic line is defined by 4 data points (1‑2‑3‑4). If fewer data points are required, the same parameters can be set for 2 points. The function is limited by the maximum apparent power and by “cos φ minimum.” For the characteristic lines, the data points must be entered on the x‑axis (voltage) and on the y‑axis (reactive power).
    Point
    Parameter
    Value range
    Description
    Voltage (% of nominal voltage)
    50% ‑ 150%
    AC voltage as a percentage [%] of the nominal voltage (x‑axis).
    -100% ‑ 100%
    50% ‑ 150%
    -100% ‑ 100%
    50% ‑ 150%
    -100% ‑ 100%
    50% ‑ 150%
    -100% ‑ 100%
    General information
    Parameter
    Value range
    Description
    Offset factor
    -1 - 1
    Shift of the Q(U) characteristic line along the y‑axis (Q‑axis) by an offset factor. The offset factor is based on the reactive power set in point 1 or point 4, which continues to limit the characteristic line.
    Initial delay time
    0 s ‑ 60 s
    Start-up delay in seconds [s] - Delays the start of Q(U) control when the voltage leaves the range between data point 2 and data point 3.
    Lock-in P-dependent (% of nominal apparent power)
    0% ‑ 120%
    Active power as a percentage [%] of the rated apparent power Sn. If this value is exceeded, the Q(P) characteristic line is activated.
    The power-dependent lock-in/lock-out values can be used to configure the system so that the Q(U) control is deactivated at low power levels.
    0% ‑ 100%
    Active power as a percentage [%] of the rated apparent power SN. If this value is not met, the Q(P) characteristic line is deactivated. The lock-out limit takes precedence over the lock-in limit.
    Time constant (τ)
    0.01 s ‑ 60 s
    Voltage reference
    Common mode voltage
    Average
    Maximum voltage
    Minimum voltage
    Auto-adjusting reference voltage mode
    Off/On
    If this option is enabled, the reactive power characteristic line is centered on the nominal AC voltage; otherwise, it is centered on the reference voltage (Uref).
    Reference voltage Uref
    95 - 105%
    Reference voltage setting value in %
    Auto-adjusting reference voltage time constant (tref)
    300 - 5,000 s
    Specifies the time constant used to center the reactive power characteristic line Q(U) on the nominal voltage when Auto-adjusting reference voltage mode is enabled.
    Apparent power
    The RefType specifies the basis on which the SetValue for Q(U) - Voltage-dependent reactive power characteristic is calculated.
    Reactive power
    Active power
    Shift of the Q(U) characteristic line on the y axis (Q axis) by an offset factor.
    U = 95%, Q = 32%
    U = 97%, Q = 0%
    U = 104%, Q = 0%
    U = 105%, Q = -32%
    (1)
    Lock-out P-dependent (% of nominal apparent power) = 5%
    (2)
    Lock-in P-dependent (% of nominal apparent power) = 30%
    (3)
    Cos φ minimum = 0.9