LogoFronius Backup Controller 3P-35A
  • en
    • Contact
    • Imprint
    • Terms and Conditions
    • Data privacy statement
    • 001-04062024
    • Safety rules
      • Safety rules
        • Explanation of safety notices
        • General
        • Environmental conditions
        • Qualified personnel
        • EMC measures
        • Data security
        • Copyright
    • General information
      • Intended use
      • Information on the device
      • Scope of supply
      • Explanation of symbols
      • Positioning
      • Recommended Fronius Smart Meter
    • Control elements and connections
      • Connection area
      • Description of digital inputs/outputs (I/Os)
      • LED status indicator
    • Installation
      • Prerequisites for connecting the Backup Controller
        • Different cable types
        • Permissible cables for the electrical connection
        • Permitted cables for digital inputs/outputs (I/Os)
        • Requirements
      • Installation
        • Safety
        • De-energising all sides of the PV system
        • Installation
        • Connecting the Backup Controller to the public grid
        • Connecting loads in the backup power circuit to the Backup Controller
        • Connecting generators in the backup power circuit to the Backup Controller
        • Connecting the neutral conductor for the Fronius Smart Meter to the Backup Controller (optional)
        • Connecting the data communication cable to the Backup Controller
    • Start-up
      • Putting the PV system into operation
      • General
      • Backup power - Configuring Full Backup
      • Testing backup power mode
    • Appendix
      • Cleaning
      • Maintenance
      • Disposal
      • Fronius manufacturer's warranty
      • Technical data
    • Circuit diagram
      • Fronius Backup Controller 3-pin separation, e.g. Austria
        • Circuit diagram
    • Dimensions
      • Dimensions - Fronius Backup Controller 3P-35A
        • Fronius Backup Controller 3P‑35A
    Fronius Backup Controller 3P-35A Operating Instructions
    Controls and connections
    Installation
    Commissioning
    Technical data
    Safety rules
    Safety rules
    DANGER!
    Indicates immediate danger.
    If not avoided, death or serious injury will result.
    WARNING!
    Indicates a potentially hazardous situation.
    If not avoided, death or serious injury may result.
    CAUTION!
    Indicates a situation where damage or injury could occur.
    If not avoided, minor injury and/or damage to property may result.
    NOTE!
    Indicates a risk of flawed results and possible damage to the equipment.
    1. Safety rules
    Safety rules
    DANGER!
    WARNING!
    CAUTION!
    NOTE!
    1. Safety rules
    2. Safety rules
    DANGER!
    WARNING!
    CAUTION!
    NOTE!
    1. Safety rules
    2. Safety rules
    General
    The device has been manufactured in line with the state of the art and according to recognized safety standards. If used incorrectly or misused, however, it can cause:
    • Injury or death to the operator or a third party
    • Damage to the device and other material assets belonging to the operating company.
    All personnel involved in commissioning, maintenance, and servicing of the device must:
    • Be suitably qualified
    • Have knowledge of and experience in dealing with electrical installations and
    • Have fully read and precisely followed these Operating Instructions
    The Operating Instructions must always be at hand wherever the device is being used. In addition to the Operating Instructions, attention must also be paid to any generally applicable and local regulations regarding accident prevention and environmental protection.
    All safety and danger notices on the device:
    • Must be kept in a legible state
    • Must not be damaged
    • Must not be removed
    • Must not be covered, pasted or painted over
    The terminals can reach high temperatures.
    Only operate the device when all protection devices are fully functional. If the protection devices are not fully functional, there is a danger of:
    Any safety devices that are not fully functional must be repaired by an authorised specialist before the device is switched on.
    Never bypass or disable protection devices.
    For the location of the safety and danger notices on the device, refer to the section headed "General remarks" in the Operating Instructions for the device.
    Any equipment malfunctions which might impair safety must be remedied before the device is turned on.
    This is for your personal safety!
    1. Safety rules
    2. Safety rules
    Operation or storage of the device outside the stipulated area will be deemed as not in accordance with the intended purpose. The manufacturer accepts no liability for any damage resulting from improper use.
    1. Safety rules
    2. Safety rules
    Qualified personnel
    The servicing information contained in these operating instructions is intended only for the use of qualified service engineers. An electric shock can be fatal. Do not carry out any actions other than those described in the documentation. This also applies to qualified personnel.
    All cables and leads must be secured, undamaged, insulated and adequately dimensioned. Loose connections, scorched, damaged or inadequately dimensioned cables and leads must be immediately repaired by authorised personnel.
    Maintenance and repair work must only be carried out by an authorised specialist.
    It is impossible to guarantee that bought-in parts are designed and manufactured to meet the demands made on them, or that they satisfy safety requirements. Use only original spare parts (also applies to standard parts).
    Do not carry out any alterations, installations, or modifications to the device without first obtaining the manufacturer's permission.
    Components that are not in perfect condition must be changed immediately.
    1. Safety rules
    2. Safety rules
    EMC measures
    In certain cases, even though a device complies with the standard limit values for emissions, it may affect the application area for which it was designed (e.g., when there is equipment that is susceptible to interference at the same location, or if the site where the device is installed is close to either radio or television receivers). If this is the case, then the operator is obliged to take action to rectify the situation.
    1. Safety rules
    2. Safety rules
    Data security
    With regard to data security, the user is responsible for:
    • backing up any changes made to the factory settings
    • saving and retaining personal settings
    1. Safety rules
    2. Safety rules
    Copyright
    Copyright of these operating instructions remains with the manufacturer.
    Text and illustrations were accurate at the time of printing, subject to change.
    We are grateful for suggestions for improvement and information regarding any discrepancies in the operating instructions.
    General information
    Intended use
    The Fronius Backup Controller is a fixed piece of equipment designed for use in public grids with TN-C-S/TN-S systems. Its main function is to automatically and securely disconnect all connected loads and generators from the public grid in the event of a grid failure or grid malfunction in accordance with the specifications of the grid operator. As soon as grid stability has been restored, the loads and generators are automatically reconnected to the public grid.
    1. Application: The Fronius Backup Controller is required for systems with storage batteries to enable automatic backup power switching.
    2. Installation: The Fronius Backup Controller is installed either on an indoor DIN rail or in special enclosures with corresponding IP protection, depending on the environmental conditions.
    3. Safety precautions: In conjunction with a Fronius Smart Meter, corresponding back-up fuses must be selected to suit the cable cross-sections of the copper conductors and the maximum current of the Fronius Backup Controller.
    4. Intended use: The Fronius Backup Controller must only be operated in accordance with the specifications in the enclosed documentation and in accordance with local laws, regulations, provisions, standards and within the limits of technical possibilities. Any use of the product other than as described under intended use shall be deemed to be not in accordance with intended use.
    5. Documentation: The available documentation forms part of the product and must be read, observed and kept in good condition. It must also be accessible at all times at the place of installation. The available documents do not replace regional, state, provincial or national laws, or regulations or standards that apply to the installation, electrical safety and use of the product. Fronius International GmbH assumes no responsibility for compliance with or non-compliance with these laws or regulations in connection with the installation of the product.
    6. Interventions and modifications: Interventions in the Fronius Backup Controller, e.g. modifications and alterations, are not permitted. Unauthorised interventions will void the warranty and warranty claims and, as a rule, void the user's authority to operate the equipment. The manufacturer shall not be liable for any damage resulting from such use.
    7. Reasonably foreseeable misuse: The Fronius Backup Controller is not suitable for supplying power to life-sustaining medical equipment.
    1. General information
    Intended use
    Technical data and markings are located on the Fronius Backup Controller. These must NOT be removed or painted over.
    The information is located on the right side of the Backup Controller.
    Markings:
    CE mark – confirms compliance with applicable EU directives and regulations.
    WEEE mark – waste electrical and electronic equipment must be collected separately and recycled in an environmentally sound manner in accordance with the European Directive and national law.
    RCM mark – tested in accordance with the requirements of Australia and New Zealand.
    Scope of supply
    Package contents
    (1)
    (2)
    Quick Start Guide
    (3)
    Backup power warning notice
    PV module
    generates direct current
    Fronius GEN24 inverter
    converts direct current into alternating current and charges the battery (battery charging is only possible with Fronius GEN24 Plus inverters). The integrated system monitoring enables the inverter to be integrated into a network by means of WLAN.
    automatically and securely disconnects all connected loads and generators from the public grid in the event of a grid failure or grid malfunction in accordance with the specifications of the grid operator. As soon as grid stability has been restored, the loads and generators are automatically reconnected to the public grid.
    Inverter in the system
    e. g. Fronius Primo, Fronius Symo, etc.
    Primary meter
    records the system's load curve and provides measurement data for energy profiling in Fronius Solar.web. The primary meter also controls the dynamic power of feeding in.
    Utility meter
    measures the measurement data relevant for billing amounts of energy (in particular kilowatt hours of energy sourced from the grid and energy fed into the grid). Based on the relevant billing data, the electricity retailer will invoice the energy sourced from the grid and the purchaser of the surplus energy will reimburse the energy fed into the grid.
    Grid
    supplies the loads in the system if insufficient power is being generated by the PV modules or supplied by the battery.
    Battery
    is coupled to the inverter on the direct current side, and stores electrical energy.
    Loads in the system
    e. g. washing machine, lamps, TV, etc.
    Positioning
    The Fronius Backup Controller must be installed in the following position in the system.
    The Backup Controller is installed in the backup power circuit.
    Device name
    Item number
    Fronius Smart Meter IP
    42,0411,0347
    Fronius Smart Meter 63A-3
    43,0001,1473
    Fronius Smart Meter TS 65A-3
    43,0001,0044
    Connection area
    Overview of the connection area.
    (1)
    1-pin push-in terminal for the neutral conductor connection to the Fronius Smart Meter (max. 1 A).
    (2)
    Push-in terminal for digital inputs/outputs. (I/Os).
    (3)
    3-pin push-in terminal for the supply from the public grid.
    (4)
    4-pin push-in terminal for the loads in the backup power circuit.
    (5)
    4-pin push-in terminal for the generators in the backup power circuit.
    1. Control elements and connections
    Connection area
    (1)
    (2)
    (3)
    (4)
    (5)
    I/O pin
    Parameter
    Description
    IO 0
    Enable backup power locking
    Before the inverter switches to backup power mode, the pin IO 0 must be active (value = 1).
    IN 6
    Grid relay open feedback
    If the mains voltage is too low or the relay K3 is closed and therefore the relays K1, K2 and K4 are open, the auxiliary contacts of the mains isolation relays are closed and the pin IN 6 is active (value = 1).
    IN 7
    Locking feedback
    When relay K3 is activated, the auxiliary contact of relay K3 closes and pin IN 7 is active (value = 1). The inverter receives feedback that relay K3 is closed.
    The LED status indicator shows the operating status and the Fronius Backup Controller.
    Symbol
    LED status
    Description
    Grid
    LED
    Lights up green
    The "Grid" LED indicates that all connected loads and generators in the backup power circuit are being supplied by or are connected to the public grid.
    Full Backup
    LED
    Lights steady blue
    The "Full Backup" LED indicates that all connected loads and generators in the backup power circuit are safely disconnected from the public grid and that the Full Backup power supply is active.
    Installation
    Single-core
    Multi-stranded
    Fine-stranded
    Fine-stranded with ferrule and collar
    Fine-stranded with ferrule without collar
    Single-core cable type
    Multi-stranded cable type
    Fine-stranded cable type
    Fine-stranded with ferrule and collar cable type
    Fine-stranded with ferrule without collar cable type
    1. Installation
    Single-core
    Multi-stranded
    Fine-stranded
    1. Installation
    2. Prerequisites for connecting the Backup Controller
    Single-core
    Multi-stranded
    Fine-stranded
    1. Installation
    Round copper conductors can be connected to the terminals as described below.
    Push-in terminals for the supply from the public grid.*
    Select a sufficiently large cable cross-section based on the actual connected output.
    2.5 - 10 mm2
    2.5 - 10 mm2
    2.5 - 10 mm2
    2.5 - 6 mm2
    2.5 - 6 mm2
    Push-in terminals for the loads/generators in the backup power circuit.*
    2.5 - 10 mm2
    2.5 - 10 mm2
    2.5 - 10 mm2
    2.5 - 6 mm2
    2.5 - 6 mm2
    Push-in terminal for the neutral conductor connection to the Fronius Smart Meter (max. 1 A)
    1 - 4 mm2
    1 - 4 mm2
    1 - 4 mm2
    1 - 2.5 mm2
    1 - 2.5 mm2
    1. Installation
    Round copper conductors can be connected to the push-in terminals for digital inputs/outputs (I/Os) as described below.
    IO connections with push-in terminal
    Max.
    distance
    Stripping length
    Cable recommendation
    30 m *
    32 yd *
    10 mm
    0.39 inch
    0.14 - 1.5 mm2
    AWG 26 - 16
    0.14 - 1.5 mm2
    AWG 26 - 16
    0.14 - 1 mm2
    AWG 26 - 18
    0.14 - 1.5 mm2
    AWG 26 - 16
    Single conductor possible
    Fronius recommends at least CAT 5 STP (shielded twisted pair) cables and a maximum distance of 30 m (32 yd).
    1. Installation
    Requirements
    The following components must be installed in the switch cabinet to permit the safe operation of the Fronius Backup Controller:
    • Upstream overcurrent protection as specified in chapter Technical data on page (→).
    • A surge protective device (SPD) as specified in chapter Technical data on page (→).
    1. Installation
    Installation
    Safety
    WARNING!
    Danger from short circuits due to foreign bodies in the housing.
    An electric shock can cause serious injury or death.
    Cover vents during installation.
    WARNING!
    Danger due to incorrect operation and incorrectly performed work.
    This can result in serious injury and damage to property.
    Commissioning as well as maintenance and service work on the inverter and battery must only be carried out by service personnel trained by the respective inverter or battery manufacturer and only within the scope of the respective technical regulations.
    Read the installation and operating instructions provided by the respective manufacturer before installing and commissioning the equipment.
    WARNING!
    Danger due to grid voltage and DC voltage from solar modules that are exposed to light and from batteries.
    Ensure that the AC and DC side of the inverter and the battery are de-energised before carrying out any connection, maintenance or service tasks.
    Only an authorised electrical engineer is permitted to connect this equipment to the public grid.
    WARNING!
    Danger due to damaged and/or contaminated terminals.
    Before making any connections, check the terminals for damage and contamination.
    Remove contamination in the de-energized state.
    Have defective terminals repaired by an authorised specialist.
    1. Installation
    2. Installation
    Safety
    WARNING!
    WARNING!
    WARNING!
    WARNING!
    1. Installation
    2. Installation
    1
    Turn off the automatic circuit breaker. Set the DC disconnector to the "Off" switch position.
    2
    Switch off the battery connected to the inverter.
    Wait for the capacitors of the inverter to discharge (2 minutes).
    1. Installation
    2. Installation
    Installation
    Mount the device on a 35 mm DIN rail.
    The Fronius Backup Controller can be mounted on a 35 mm DIN rail. The housing comprises 8 modules according to DIN 43880 and conforms to unit size 2.
    1. Installation
    2. Installation
    WARNING!
    Danger due to individual conductors in the terminal that are loose and/or improperly connected.
    Only connect one single conductor in the slot provided for each terminal.
    Check that the single conductor is held securely in the terminal.
    Ensure that all of the single conductor is within the terminal and that no individual wires are sticking out of the terminal.
    1
    Strip the insulation of the single conductors by 12 mm.
    Select the cable cross-section in accordance with the instructions in Permissible cables for the electrical connection from page (→).
    2
    Lift the operating levers of the terminals to open. Insert the stripped single conductors into the slot provided in the terminal, in each case as far as it will go.
    3
    Close the terminal operating levers until they engage.
    1. Installation
    2. Installation
    WARNING!
    1
    2
    IMPORTANT!
    The neutral conductor must be connected to the public grid.
    3
    1. Installation
    2. Installation
    WARNING!
    1
    2
    IMPORTANT!
    3
    1. Installation
    2. Installation
    WARNING!
    1
    Strip the insulation of the single conductors by 10 mm.
    2
    Lift the operating levers of the terminals to open. Insert the stripped single conductor into the slot provided in the terminal as far as it will go.
    3
    Close the operating lever of the terminal until it engages.
    1. Installation
    2. Installation
    IMPORTANT!
    Further information on successful commissioning.
    Observe the following information on connecting the data communication cable to the Backup Controller.
    • Use network cables of type CAT5 STP or higher.
    • Use a mutual twisted cable pair for corresponding data lines.
    • Use double-insulated or sheathed data lines when they are close to bare conductors.
    • Use shielded twisted pair cables to avoid faults.
    Connection overview of the data communication cables between the Fronius Smart Meter, Fronius Backup Controller and Fronius GEN24 inverter.
    Start-up
    1
    Switch on the battery connected to the inverter.
    2
    Set the DC disconnector to the "On" switch position. Switch on the automatic circuit breaker.
    1. Start-up
    1
    2
    1. Start-up
    General
    IMPORTANT!
    Settings under the "Device configuration" → "Functions and I/Os" menu item are only to be made by trained and qualified personnel! The service password must be entered in order to access the "Device configuration" menu item.
    1. Start-up
    1Access the user interface of the inverter.
    - Open your web browser.
    - In the address bar of the browser, enter the IP address (IP address for WLAN: 192.168.250.181, IP address for LAN: 169.254.0.180) or the host and domain name of the inverter and confirm.
    - The user interface of the inverter is displayed.
    2Log in to the login area with the "Technician" user and the technician password.
    3In the "Device configuration" menu, click on the "Functions and I/Os" button.
    4Enable "Backup power" mode.
    5Select "Full Backup" mode in the "Backup power mode" drop-down list.
    6Click the "Save" button to save the settings.
    The Full Backup backup power mode has been configured.
    1. Start-up
    Testing backup power mode is recommended:
    • During the initial installation and configuration
    • After working on the switch cabinet
    • During ongoing operation (recommendation: at least once a year)
    For test mode, a battery charge of min. 30% is recommended.
    A description on how to run test mode can be found in the backup power checklist (https://www.fronius.com/en/search-page, item number: 42,0426,0365).
    Appendix
    Cleaning
    Clean the Backup Controller as required with a damp cloth.
    Do not use cleaning agents, abrasives, solvents or similar to clean the Backup Controller.
    1. Appendix
    Cleaning
    1. Appendix
    Maintenance
    Maintenance and servicing may only be carried out by Fronius-trained service technicians.
    1. Appendix
    Disposal
    Waste electrical and electronic equipment must be collected separately and recycled in an environmentally responsible manner in accordance with the EU Directive and national law. Used equipment must be returned to the distributor or through a local, authorised collection and disposal system. Correct disposal of the used device promotes sustainable recycling of resources and prevents negative effects on health and the environment.
    Packaging materials
    • Collect separately
    • Observe locally valid regulations
    • Compress the cardboard box to reduce volume
    1. Appendix
    Detailed, country-specific warranty conditions are available at www.fronius.com/solar/warranty.
    To obtain the full warranty period for your newly installed Fronius product, please register at www.solarweb.com.
    1. Appendix
    Technical data
    General data
    Mains supply type
    TN-S / TN-C-S
    Housing
    Mounting
    35 mm DIN rail
    Weight
     625 g
    Protection class
    IP 20
    Fault Ride Through (FRT)
    According to EN 50549-10
    Short-circuit breaking capacity
    Class PC
    Permitted ambient temperature
    -20 to +60 °C
    Permissible humidity
    50% relative humidity at 40 °C
    Max. altitude
    2000 m
    Vibrations
    Not permitted
    Rated values
    Nominal voltage
    230 / 400 V 3-pole or 3-pole + N
    Nominal current
    35 A
    Duty cycle
    100% at AC-32
    Rated power
    24 kVA
    Grid frequency
    50 Hz
    Power loss (at nominal current)
    15 W
    Overvoltage category
    III
    Electromagnetic compatibility
    Immunity
    According to EN 61000-6-2 2019-12-01
    Emissions
    According to EN 61000-6-3 2020-07
    Circuit diagram
    Circuit diagram
    1. Circuit diagram
    Circuit diagram
    1. Circuit diagram
    2. Fronius Backup Controller 3-pin separation, e.g. Austria
    Circuit diagram
    Dimensions
    1. Dimensions
    1. Dimensions
    2. Dimensions - Fronius Backup Controller 3P-35A