Fronius LogoFronius Mobile Logo
en
      Operating instructionsFronius Verto Plus 15 - 33.3 kW
    • General information
      • Safety information
        • Explanation of warnings and safety instructions
        • Safety instructions and important information
        • Environmental conditions
        • Data on noise emission values
        • EMC measures
        • Backup power
        • Ground conductor
      • Protection of people and equipment
        • Central grid and system protection
        • WSD (wired shutdown)
        • RCMU
        • Insulation monitoring
        • AFCI - Arc Fault Circuit Interrupter (Arc Guard)
        • Safe state
      • General
        • Information on the device
        • How information is presented in the document
        • Target group
        • Data security
        • Privacy policy
        • Copyright
      • Fronius Verto
        • Device concept
        • Scope of supply
        • Enhanced Power Harvest
        • Backup Power Boost
        • Thermal concept
        • Fronius Solar.web
        • Local communication
      • Different operating modes
        • Operating modes – Explanation of symbols
        • Operating mode – Inverter with battery
        • Operating mode – Inverter with battery and several Smart Meters
        • Operating mode – Inverter with battery, AC-coupled to another inverter
        • Operating mode – Inverter with battery and backup power function
        • Operating mode – Inverter with battery and Ohmpilot
        • Operating mode – Inverter with battery, Ohmpilot, and backup power function
        • Operating mode – Inverter with battery and another inverter
        • Operating mode – Inverter with battery, another inverter, and backup power function
        • Energy flow direction of the inverter
        • Operating states (only for battery systems)
      • Energy-saving mode
        • General
        • Switch-off conditions
        • Switch-on conditions
        • Special case
        • Indication of energy saving mode
      • Suitable batteries
        • General
        • Fronius batteries
        • BYD batteries
      • Manual system start
        • Requirements
        • Notification of system shutdown
        • Manual battery start after system shutdown
        • Starting backup power operation after a system shutdown
      • Utilization in accordance with "intended purpose"
        • Intended use
        • Foreseeable misuse
        • Provisions for the photovoltaic system
      • Surge protection device (SPD)
        • Surge protection device SPD
      • Operating controls and connections
        • Connection area
        • Photovoltaic and battery connections
        • Ground electrode bolt
        • Mounting option for third-party components
        • DC disconnector
        • Data communication area
        • Button functions and LED status indicator
        • Schematic internal wiring of IOs
    • Backup power variant - Full Backup
      • General
        • Prerequisites for backup power mode
        • Transitioning from grid power feed operation to backup power mode
        • Transitioning from backup power mode to grid power feed operation
        • Backup power and energy saving mode
      • Automatic switch to backup power with Fronius Backup Controller 3P-35A incl. backup power circuits and 3-pin separation, e.g., Austria or Australia
        • Functions
        • Transition from grid power feed operation to backup power mode
        • Transition from backup power mode to grid power feed operation
        • Parallel Backup
        • Rapid switch mode
      • Automatic switch to backup power including backup power circuits and 3-pin separation, e.g., Austria or Australia
        • Functions
        • Transitioning from grid power feed operation to backup power mode
        • Transitioning from backup power mode to grid power feed operation
      • Automatic switch to backup power mode, all-pin disconnection, e.g., in Germany with Fronius Backup Controller 3PN-35A
        • Functions
        • Transition from grid power feed operation to backup power mode
        • Transition from backup power mode to grid power feed operation
      • Automatic switch to backup power all-pin separation, e.g., Germany, France, Spain
        • Functions
        • Transitioning from grid power feed operation to backup power mode
        • Transitioning from backup power mode to grid power feed operation
      • Automatic switch to backup power all-pin separation, Italy
        • Functions
        • Transitioning from grid power feed operation to backup power mode
        • Transitioning from backup power mode to grid power feed operation
      • Manual switch to backup power 3-pin separation, e.g., Austria / all-pin separation, e.g., Germany
        • Functions
        • Transition from grid power feed operation to backup power mode
        • Transition from backup power mode to grid power feed operation
    • Installation
      • General
        • Tools required
        • Quick-fastener system
        • System component compatibility
      • Installation location and position
        • Choosing the location of the inverter
        • Choosing the location of third-party batteries
        • Installation position of inverter
      • Installing the mounting bracket and attaching the inverter
        • Selecting the mounting material
        • Properties of the mounting bracket
        • Do not deform the mounting bracket
        • Fitting the mounting bracket to a wall
        • Attaching the inverter to the mounting bracket
      • Requirements for connecting the inverter
        • Connecting aluminum cables
        • Different cable types
        • Permitted cables for the electrical grid connection
        • Permitted cables for the electrical DC connection
        • Permitted cables for the electrical BAT connection
        • Permitted cables for the data communication connection
        • Cable diameter of the AC cable
        • Maximum alternating current fuse protection
      • Connecting the inverter to the public grid (AC side)
        • Safety
        • Connecting the inverter to the public grid (AC side)
        • Connecting the inverter to the public grid with the PEN conductor (AC side)
        • Replacing the PG screw joint
      • Connecting solar module strings to the inverter
        • General information about PV modules
        • Safety
        • PV Generator, general
        • Connecting solar module strings to the inverter
      • Connecting the battery to the inverter
        • Safety
        • Connecting the battery on the DC side
      • Connecting backup power - Full Backup
        • Safety
        • Automatic switch to backup power 3-pole disconnection e.g., Austria or Australia
        • Automatic switch to backup power 4-pole disconnection e.g., Germany, France, Spain
        • Automatic switch to backup power 4-pole disconnection e.g., Italy
        • Manual switch to backup power 3-pole disconnection e.g., Austria / 4-pole disconnection e.g., Germany
        • Testing backup power mode
      • Connecting the data communication cables
        • Modbus participants
        • Routing data communication cables
        • Connecting the battery communication cable
        • Terminating resistors
        • Installing the WSD (wired shutdown)
      • Closing and commissioning the inverter
        • Closing the inverter's connection area/housing cover, and commissioning
        • Starting the inverter for the first time
        • Installation with the app
        • Installation with the browser
      • De-energizing the inverter and switching it back on
        • Risk of rupture
        • De-energizing the inverter and switching it back on
    • Settings – User interface of the inverter
      • User settings
        • User login
        • Selecting languages
      • Device configuration
        • Components
        • Functions and I/Os
        • Inverter
      • Energy management
        • Permitted maximum battery charge from the public grid
        • Battery management
        • Examples - Time-dependent battery control
        • Permitted battery control regulations
        • PV power reduction
        • Load management
        • Self-consumption optimization
      • System
        • General
        • Update
        • Setup wizard
        • Restoring factory settings
        • Event log
        • Information
        • License Manager
        • Licensing
        • Support
      • Communication
        • Network
        • Modbus
        • Cloud control
        • Solar API
        • Fronius Solar.web
      • Safety and grid requirements
        • Country setup
        • Requesting inverter codes in Solar.SOS
        • Absolute Generation Limit
        • Import limitation
        • Feed-in limit
        • Feed-in limit – examples
        • Multiple Inverter Control
        • I/O Power Management
        • 4-relay connection example
        • I/O power management settings – 4 relay example
        • 3-relay connection example
        • I/O power management settings – 3 relay example
        • 2-relay connection example
        • I/O power management settings – 2 relay example
        • 1-relay connection example
        • I/O power management settings – 1 relay example
        • Autotest
          (CEI 0-21)
        • Connecting the ripple control receiver with several inverters
    • Appendix
      • Service, maintenance and disposal
        • General
        • Maintenance
        • Cleaning
        • Operation in dusty environments
        • Safety
        • Disposal
      • Warranty provisions
        • Warranty
      • Components for switching to backup power
        • Components for automatic backup power changeover to Full Backup
        • Components for manual backup power changeover to Full Backup
      • Status codes and remedy
        • Display
        • Status codes
      • Technical data
        • Verto Plus 15.0
        • Verto Plus 17.5
        • Verto Plus 20.0
        • Verto Plus 25.0
        • Verto Plus 30.0
        • Verto Plus 33.3
        • Protection devices
        • WLAN
        • Data communication
        • Surge protection device DC SPD type 1+2
        • Explanation of footnotes
        • Integrated DC disconnector
    • System circuit diagrams
      • Fronius Verto Plus and Fronius Reserva
      • Fronius Verto Plus with Fronius Reserva connected in parallel
      • Fronius Verto Plus and Fronius Reserva Pro
      • Fronius Verto Plus with Fronius Reserva Pro connected in parallel
      • Fronius Verto Plus and BYD Battery-Box Premium HV
      • Fronius Verto Plus with 3 BYD Battery-Box Premium HV connected in parallel
      • Fronius Verto Plus and BYD Battery-Box HVS+/HVM+/HVB
      • Fronius Verto Plus with BYD Battery-Box HVS+/HVM+/HVB connected in parallel
    • Circuit diagrams—automatic switch to backup power with Fronius Backup Controller
      • Fronius Backup Controller 4-pin separation, e.g., Germany
      • Fronius Backup Controller 3-pin separation, e.g., Austria
      • Fronius Backup Controller 3-pin separation, parallel backup
    • Circuit diagrams—automatic switch to backup power with third-party components
      • Automatic switch to backup power 3-pin single FRT-capable separation - e.g., Austria
      • Automatic switch to backup power 3-pin single separation - e.g., Australia
      • Automatic switch to backup power 3-pin double separation with ext. grid and system protection
      • Automatic switch to backup power 4-pin single separation - e.g., Germany
      • Automatic switch to backup power 4-pin single FRT-capable separation
      • Automatic switch to backup power 4-pin single separation - e.g., France
      • Automatic switch to backup power 4-pin single separation - e.g., Spain
      • Automatic switch to backup power 4-pin double separation with ext. grid and system protection - e.g., Italy
    • Circuit diagrams—manual switch to backup power with Fronius Backup Switch
      • Manual switch to backup power 3-pin separation, e.g., Austria
      • Manual switch to backup power 3-pin separation with grid and system protection
      • Manual switch to backup power 4-pin separation, e.g., Germany
      • Manual switch to backup power 3-pin separation Parallel Backup with Backup Switch
    • 018-23092026

    Fronius Verto Plus 15 - 33.3 kW

    download
    Fitting the mounting bracket to a wall
    Connecting the inverter to the public grid (AC side)
    Connecting solar module strings to the inverter
    Connecting the battery on the DC side
    Routing data communication cables
    Installation with the app
    ContactImprintTerms of usePrivacy statementCookie policy
    © 2026 Fronius International GmbH
    © 2026 Fronius International GmbH
    ContactImprintTerms of usePrivacy statementCookie policy

    General information

    link_horizontalLink copied

    Safety information

    Explanation of warnings and safety instructions

    Warnings are intended to warn people of possible injuries and to avoid personal injury and damage to the product. They relate to individual actions with and on the product.

    DANGER

    Indicates an immediately dangerous situation.

    Serious injury or death will result if the danger is not avoided.

    Action step to escape the situation.

    WARNING

    Indicates a potentially dangerous situation.

    Serious injury or death may result if the danger is not avoided.

    Action step to escape the situation.

    CAUTION

    Indicates a potentially dangerous situation.

    Minor or moderate injury may result if the danger is not avoided.

    Action step to escape the situation.

    NOTE

    Indicates a situation that may result in property damage.

    If the situation is not avoided, impaired work results, material damage to the product or other property are the possible consequences.

    Action step to avoid the situation.

    Safety instructions are designed to ensure safe product use. They are preventive and help to inform users about the fundamental risks involved when dealing with the product. They do not refer specifically to individual actions with and on the product.

    1. General information

    Safety information

    link_horizontalLink copied

    Explanation of warnings and safety instructions

    Warnings are intended to warn people of possible injuries and to avoid personal injury and damage to the product. They relate to individual actions with and on the product.

    DANGER

    Indicates an immediately dangerous situation.

    Serious injury or death will result if the danger is not avoided.

    Action step to escape the situation.

    WARNING

    Indicates a potentially dangerous situation.

    Serious injury or death may result if the danger is not avoided.

    Action step to escape the situation.

    CAUTION

    Indicates a potentially dangerous situation.

    Minor or moderate injury may result if the danger is not avoided.

    Action step to escape the situation.

    NOTE

    Indicates a situation that may result in property damage.

    If the situation is not avoided, impaired work results, material damage to the product or other property are the possible consequences.

    Action step to avoid the situation.

    Safety instructions are designed to ensure safe product use. They are preventive and help to inform users about the fundamental risks involved when dealing with the product. They do not refer specifically to individual actions with and on the product.

    1. General information
    2. Safety information

    Explanation of warnings and safety instructions

    link_horizontalLink copied

    Warnings are intended to warn people of possible injuries and to avoid personal injury and damage to the product. They relate to individual actions with and on the product.

    DANGER

    Indicates an immediately dangerous situation.

    Serious injury or death will result if the danger is not avoided.

    Action step to escape the situation.

    WARNING

    Indicates a potentially dangerous situation.

    Serious injury or death may result if the danger is not avoided.

    Action step to escape the situation.

    CAUTION

    Indicates a potentially dangerous situation.

    Minor or moderate injury may result if the danger is not avoided.

    Action step to escape the situation.

    NOTE

    Indicates a situation that may result in property damage.

    If the situation is not avoided, impaired work results, material damage to the product or other property are the possible consequences.

    Action step to avoid the situation.

    Safety instructions are designed to ensure safe product use. They are preventive and help to inform users about the fundamental risks involved when dealing with the product. They do not refer specifically to individual actions with and on the product.

    1. General information
    2. Safety information

    Safety instructions and important information

    link_horizontalLink copied

    The device has been manufactured in line with the state of the art and according to recognized safety standards.

    WARNING

    Incorrect operation or misuse

    Serious to fatal injuries to the operator or third parties as well as damage to the device and other property of the operator may result.

    All persons involved in the commissioning, maintenance, and servicing of the device must be appropriately qualified and have knowledge of working with electrical installations.

    Read these operating instructions in full and follow them carefully and precisely.

    The operating instructions must always be kept to hand wherever the device is being used.

    IMPORTANT!
    In addition to the operating instructions, observe the following general and local rules:
    • Accident prevention
    • Fire protection
    • Environmental protection

    IMPORTANT!
    Labels, warning notices, and safety symbols are located on the device. A description can be found in these operating instructions.

    IMPORTANT!
    All safety and danger notices on the device:
    • Must be kept in a legible state
    • Must not be damaged/marked
    • Must not be removed
    • Must not be covered, have anything stuck on them, or painted over

    WARNING

    Tampered-with and non-functioning protection devices

    Serious to fatal injuries as well as damage to the device and other property of the operator may result.

    Never bypass or disable protection devices.

    Any protection devices that are not fully functional must be repaired by an authorized specialist before the device is switched on.

    WARNING

    Loose, damaged, or under-dimensioned cables

    An electric shock can be fatal.

    Use undamaged, insulated, and adequately dimensioned cables.

    Fasten the cables according to the specifications in the operating instructions.

    Loose, damaged, or under-dimensioned cables must be repaired or replaced immediately by an authorized specialist.

    NOTE

    Installations or modifications to the device

    The device may be damaged

    Do not carry out any alterations, installations, or modifications to the device without first obtaining the manufacturer's permission.

    Damaged components must be replaced.

    Only use original spare parts.

    1. General information
    2. Safety information

    Environmental conditions

    link_horizontalLink copied

    Operation or storage of the machine outside the stipulated area will be deemed as not in accordance with the intended purpose.

    For exact information on permitted environmental conditions, please refer to the technical data.

    1. General information
    2. Safety information

    Data on noise emission values

    link_horizontalLink copied

    The sound pressure level of the inverter is indicated in the Technical data.

    The cooling of the device takes place via an electronic temperature control system at the lowest possible noise level and depends on the power used, ambient temperature, and the soiling level of the device, etc.

    It is not possible to provide a workplace-related emission value for this device, because the actual sound pressure level is heavily influenced by the installation situation, the power quality, the surrounding walls, and the properties of the room in general.

    1. General information
    2. Safety information

    EMC measures

    link_horizontalLink copied

    In certain cases, even though a device complies with the standard limit values for emissions, it may affect the application area for which it was designed (e.g., when there is equipment that is susceptible to interference at the same location or if the site where the device is installed is close to either radio or television receivers). If this is the case, the operator is obliged to take action to rectify the situation.

    1. General information
    2. Safety information

    Backup power

    link_horizontalLink copied

    This system has backup power functions. A backup power supply can be established in the event of a failure in the public grid.

    If an automatic backup power supply is installed, attach the backup power supply warning notice (https://www.fronius.com/en/solar-energy/installers-partners/downloads?searchword=42,0409,0275) to the electrical distributor.

    WARNING

    Danger due to electrical voltage on live parts of the PV system

    Depending on the irradiance conditions and the battery state of charge, the backup power supply is automatically deactivated and activated. This can cause the backup power supply to unexpectedly return from standby mode. This can result in serious personal injury and damage to property.

    Disconnect the inverter on the network side before performing maintenance and installation work in the home network.

    Set the integrated DC disconnector on the inverter to the "Off" switch position to end the backup power supply.

    Test the function of the residual current devices for the backup power supply at least every 6 months.
    A description of how to run the test mode can be found in the backup power checklist (https://www.fronius.com/en/solar-energy/installers-partners/downloads?searchword=42,0426,0365).

    Influencing factors on the total output in backup power mode:

    Reactive power
    Electrical loads with a power factor not equal to 1 require active power as well as reactive power. The reactive power places a further load on the inverter. Use the current resulting from the active and reactive power for the correct calculation of the total power. The rated power of the loads is not relevant.

    Devices with a high reactive power are mainly electric motors, such as:

    • Water pumps
    • Circular saws
    • Fans

    High starting/start-up current
    Electrical loads that need to accelerate a large mass generally require a high starting/start-up current. This can be up to ten times the nominal current. The maximum current of the inverter is available for the starting/start-up current. Loads with too high a starting/start-up current cannot, therefore, be started/operated, even though the nominal power of the inverter suggests otherwise. Therefore, consider the connected load power and the starting/start-up current when sizing the backup power circuit.

    Devices with a high starting/start-up current include:

    • Devices with electric motors (e.g., lift platforms, circular saws, workbenches)
    • Devices with a high transmission ratio and flywheel mass
    • Devices with compressors (e.g., compressed air compressors, air-conditioning systems)

    IMPORTANT!
    Very high start-up currents can temporarily distort or interrupt the output voltage. Avoid simultaneous operation of electronic devices in the same backup power circuit.

    Unbalanced load
    When dimensioning three-phase backup power circuits, consider the total output power and the powers per phase of the inverter.

    IMPORTANT!
    Only operate the inverter within the limits of its technical capabilities. Operation outside of its technical capabilities can cause the inverter to shut down.

    1. General information
    2. Safety information

    Ground conductor

    link_horizontalLink copied

    Connection of a point in the device, system, or installation to ground to protect against electric shock in the event of a fault. When installing an inverter from safety class 1 (see Technical data), a ground conductor connection is required.

    When connecting the ground conductor, ensure that it is secured to prevent unintentional disconnection. All of the points listed in the chapter headed Connecting the inverter to the public grid (AC side) on page (→) must be observed. When using cable glands, ensure that the ground conductor is last to be subjected to a load in the event of a failure of the cable gland. The respective national standards and regulations and requirements for minimum cross-section must be observed when connecting the ground conductor.

    1. General information

    Protection of people and equipment

    link_horizontalLink copied

    Central grid and system protection

    The inverter offers the option to use the integrated AC relays as section switches in conjunction with a central grid and system protection unit (in accordance with VDE-AR-N 4105:2018:11 § 6.4.1). For this purpose, integrate the central trigger device (switch) into the WSD chain as described in chapter (→) on page WSD (wired shutdown).

    Grid and system protection for systems with multiple inverters
    • Regional standards and guidelines may require the installation of external grid and system protection for systems >30 kVA.
    • External grid and system protection can be omitted if the following conditions are met:
      • A Fronius Smart Meter IP performs the external voltage measurement.
      • The Fronius Smart Meter IP communicates with the primary device via the MQTT protocol.
      • The On at Smart Meter option is selected in the country setup in the Long Time Average Limit menu for each device. This equates to grid and system protection with remote voltage measurement.
      • On the user interface of the secondary device, the Multiple Inverter Control function is disabled.
    1. General information
    2. Protection of people and equipment

    Central grid and system protection

    link_horizontalLink copied

    The inverter offers the option to use the integrated AC relays as section switches in conjunction with a central grid and system protection unit (in accordance with VDE-AR-N 4105:2018:11 § 6.4.1). For this purpose, integrate the central trigger device (switch) into the WSD chain as described in chapter (→) on page WSD (wired shutdown).

    Grid and system protection for systems with multiple inverters
    • Regional standards and guidelines may require the installation of external grid and system protection for systems >30 kVA.
    • External grid and system protection can be omitted if the following conditions are met:
      • A Fronius Smart Meter IP performs the external voltage measurement.
      • The Fronius Smart Meter IP communicates with the primary device via the MQTT protocol.
      • The On at Smart Meter option is selected in the country setup in the Long Time Average Limit menu for each device. This equates to grid and system protection with remote voltage measurement.
      • On the user interface of the secondary device, the Multiple Inverter Control function is disabled.
    1. General information
    2. Protection of people and equipment

    WSD (wired shutdown)

    link_horizontalLink copied

    The wired shutdown (WSD) interrupts the inverter's grid power feed if the trigger device (switch, e.g., Emergency Stop or fire alarm contact) has been activated.

    If an inverter (slave) fails, it is bypassed and the other inverters continue operating. If a second inverter (slave) or the inverter (master) fails, the operation of the entire WSD chain is interrupted.

    For installation, see Installing the WSD (wired shutdown) on page (→).

    1. General information
    2. Protection of people and equipment

    RCMU

    link_horizontalLink copied

    The inverter is equipped with an RCMU (RCMU = residual current monitoring unit) according to IEC 62109-2 and IEC63112.
    It monitors residual currents from the PV module up to the AC output and disconnects the inverter from the grid when an improper residual current is detected.

    1. General information
    2. Protection of people and equipment

    Insulation monitoring

    link_horizontalLink copied

    In the case of photovoltaic systems with ungrounded PV modules, the inverter checks the resistance between the positive or negative pole of the photovoltaic system and the ground potential before starting grid power feed operation. In the event of a short circuit between the DC+ or DC- cable and ground (e.g., due to inadequately insulated DC cables or defective PV modules), feeding into the public grid is prevented.

    1. General information
    2. Protection of people and equipment

    AFCI - Arc Fault Circuit Interrupter (Arc Guard)

    link_horizontalLink copied

    An AFCI (Arc Fault Circuit Interrupter) protects against arc faults and is a protective device in the event of contact errors. The Arc Fault Circuit Interrupter monitors faults that occur in the current and voltage flow on the DC side and shuts down the circuit with an electronic circuit if a contact error is detected. The function prevents overheating at poor contact points and fires. When delivered, the Arc Guard function is disabled

    In the Technical data chapter, check whether the Arc Fault Circuit Interrupter is available for the device in question.

    WARNING

    Arc faults due to faulty or incorrect DC installation

    Risk of fire as well as serious injuries and damage to the inverter and PV system.

    Connection work must be carried out in accordance with the technical specifications.

    Check the plug connections to ensure that they are in proper condition.

    Professionally repair faulty insulation.

    IMPORTANT! Despite the integrated Arc Fault Circuit Interrupter and arc interruption, damage to the device as well as to other system components may occur (e.g., due to a parallel arc).

    IMPORTANT! Active PV module electronics (e.g., power optimizers) can impair the function of the Arc Fault Circuit Interrupter. We cannot guarantee that the Arc Fault Circuit Interrupter will work correctly in combination with active PV module electronics.

    Reconnection behavior
    The inverter interrupts grid power feed operation and stops PV power generation after an arc has been detected. The configuration in the Country Setup > Safety > DC Arc Fault Protection menu item determines whether or not the inverter automatically resumes PV power generation and grid power feed operation. If more arcs have been detected within 24 hours than are set in Automatic Reconnects, a manual reconnection needs to be performed.

    1. General information
    2. Protection of people and equipment

    Safe state

    link_horizontalLink copied

    In the safe state, the inverter infeed is deactivated and is disconnected from the grid by the AC relay opening. The inverter switches to the safe state when the following events occur:

    1. One of the following safety devices triggers:
      • WSD
      • Insulation monitoring
      • RCMU
      • AFCI
    2. The diagnostic function of the inverter detects a malfunction of these safety devices.

     

    1. General information

    General

    link_horizontalLink copied

    Information on the device

    Technical data, warning notices, labels, and safety symbols are located on and in the inverter. This information must be kept in a legible condition and must not be removed, covered, pasted over, or painted over. They warn against incorrect operation, which may result in serious injury and property damage.

    Symbols on the rating plate:

    CE label – confirms compliance with applicable EU directives and regulations.

    WEEE marking – waste electrical and electronic equipment must be collected separately and recycled in an environmentally sound manner in accordance with the European Directive and national law.

    Safety symbols:

    Integrated switch disconnector on the input side of the inverter with switch-on, switch-off, and isolating function according to IEC 60947-3 and AS 60947.3. The values required by the applicable standard for Ithe solar +60°C are given.

    General warning sign
    Observe the danger shown on the additional sign(s).

    Observe instructions
    Do not use the functions described here until you have fully read and understood the following documents:

    • These operating instructions, especially the safety rules.
    • Read and understand all operating instructions for the system components of the photovoltaic system, especially the safety rules.

    Warning of hot surface
    Take care not to come into contact with hot surfaces.

    Warning of electrical voltage
    Take care not to come into contact with electrical voltage.

    Allow the capacitors of the inverter to discharge (2 minutes).

    Warning notice text:

    WARNING!

    An electric shock can be fatal. Before opening the device, ensure that the input and output sides are de-energized and disconnected.

    1. General information
    2. General

    Information on the device

    link_horizontalLink copied

    Technical data, warning notices, labels, and safety symbols are located on and in the inverter. This information must be kept in a legible condition and must not be removed, covered, pasted over, or painted over. They warn against incorrect operation, which may result in serious injury and property damage.

    Symbols on the rating plate:

    CE label – confirms compliance with applicable EU directives and regulations.

    WEEE marking – waste electrical and electronic equipment must be collected separately and recycled in an environmentally sound manner in accordance with the European Directive and national law.

    Safety symbols:

    Integrated switch disconnector on the input side of the inverter with switch-on, switch-off, and isolating function according to IEC 60947-3 and AS 60947.3. The values required by the applicable standard for Ithe solar +60°C are given.

    General warning sign
    Observe the danger shown on the additional sign(s).

    Observe instructions
    Do not use the functions described here until you have fully read and understood the following documents:

    • These operating instructions, especially the safety rules.
    • Read and understand all operating instructions for the system components of the photovoltaic system, especially the safety rules.

    Warning of hot surface
    Take care not to come into contact with hot surfaces.

    Warning of electrical voltage
    Take care not to come into contact with electrical voltage.

    Allow the capacitors of the inverter to discharge (2 minutes).

    Warning notice text:

    WARNING!

    An electric shock can be fatal. Before opening the device, ensure that the input and output sides are de-energized and disconnected.

    1. General information
    2. General

    How information is presented in the document

    link_horizontalLink copied

    The conventions regarding how information is presented in the document, which are set out below, have been defined in order to increase the readability and comprehensibility of the document.

    Application notes

    IMPORTANT! Indicates application notes and other useful information. It does not indicate a harmful or dangerous situation.

    Software

    Software functions and elements of a graphical user interface (e.g., buttons, menu items) are highlighted in the text with this mark up.

    Example: Click Save.

    Instructions for action

    1Action steps are displayed with consecutive numbering.
    ✓This symbol indicates the result of the action step or the entire instruction.
    1. General information
    2. General

    Target group

    link_horizontalLink copied

    This document provides detailed information and instructions to ensure that people can use the machine safely and efficiently.

    The information is intended for the following groups of people:
    • Technical specialists: People with appropriate qualifications and fundamental knowledge of electronics and mechanics. The activities of a technical specialist include installation, operation, maintenance, and service work.
    • User: People that use the machine in daily operation and want to understand its basic functions.

    Regardless of any qualifications, only perform the activities listed in this document.

    The definition of professional qualifications and their applicability are subject to national law.

    1. General information
    2. General

    Data security

    link_horizontalLink copied
    With regard to data security, the user is responsible for:
    • Backing up any changes made to the factory settings
    • Saving and storing personal settings

    NOTE

    Data security for network and Internet connection

    Unsecured networks and a lack of safeguards can result in data loss and unauthorized access. Observe the following points for safe operation:

    Operate inverters and system components on a private, secure network. A WiFi network is considered secure if security standard WPA 2 is satisfied as a minimum.

    Keep the network devices (e.g., WiFi routers) up to date with the latest technology.

    Keep the software and/or firmware updated.

    Use a wired network to ensure a stable data connection.

    For security reasons, do not make inverters and system components accessible from the Internet via port forwarding or Port Address Translation (PAT).

    Use the solutions provided by Fronius for monitoring and remote configuration.

    The optional communication protocol Modbus TCP/IP1) is an unsecured interface. Only use Modbus TCP/IP if no other secured data communication protocol (MQTT2)) is possible (e.g., compatibility with older Smart Meters).

    1) TCP/IP - Transmission Control Protocol/Internet Protocol
    2) MQTT - Message Queuing Telemetry Protocol

    1. General information
    2. General

    Privacy policy

    link_horizontalLink copied

    When you connect your device (and any associated devices) to the internet, the following device and operating data (device ID/identifier, device IP address, device time, configuration settings, hardware and software information, device status log files, serial number) is sent automatically to

    Fronius International GmbH, Froniusstraße 1, 4643 Pettenbach, Austria, telephone +43(0) 7242241-0, email: contact@fronius.com (controller)

    and stored.

    The processing of this device and operating data is carried out for the purpose of ensuring the operational safety of the device (time synchronization, provision of updates). This processing is therefore necessary for the functionality of the device and thus for the fulfillment of the contract (Art. 6 (1) (b) GDPR).

    If you do not wish to have such data processed, you must manually disable the device's internet connection.

    In addition, the device and operating data is also processed for the purpose of providing services as part of a supplementary digital service for your device (such as solar.web or similar) as soon as you have registered your device with such a digital service (identification). This data is processed to provide the requested digital services and is therefore necessary for the fulfillment of the contract (Art. 6 (1) (b) GDPR).

    Furthermore, this data processing is also carried out for maintenance and support purposes and for handling customer concerns as well as in warranty and guarantee cases (only in individual cases and given connection between device and internet). In this context, the device and operating data may also be passed on to our cooperation partners (third-party providers and suppliers). The processing of this data is necessary for maintenance and support purposes or for processing warranty and guarantee cases and thus for the fulfillment of the contract (Art. 6 (1) (b) GDPR).

    Device and operating data are also processed for analysis and diagnostic purposes in order to gain insights into the functionality of the devices and improve them accordingly. This data processing is based on our legitimate interest (Art. 6 (1) (f) GDPR).

    We store this data for as long as it is necessary to fulfill the existing contract with you. Any storage beyond this is carried out for legal reasons or if we have a legitimate interest in doing so. For more information on data processing for the solar.web-digital service, as well as our general privacy policy and your rights as a data subject, please visit https://www.fronius.com.

    1. General information
    2. General

    Copyright

    link_horizontalLink copied

    Fronius International GmbH retains the copyrights of these operating instructions.

    Text, illustrations, and other media correspond to the technical state of the art at the time of publication. Fronius reserves the right to make changes. If you have any suggestions for improvement or have found a mistake in this document, we would be most grateful for your comments.

    1. General information

    Fronius Verto

    link_horizontalLink copied

    Device concept

    The inverter transforms the direct current generated by the PV modules into alternating current. This alternating current is fed into the public grid and synchronized with the mains voltage in use. Moreover, the solar energy can also be stored in a connected battery for later use.

    The inverter is intended for use in grid-connected photovoltaic systems. The inverter has backup power functions and switches to backup power mode if it has been wired accordingly*.

    The inverter automatically monitors the public grid. Whenever conditions in the electric grid are inconsistent with standard conditions (e.g., grid switch-off, interruption), the inverter will immediately stop producing power and interrupt the supply of power into the grid.
    The grid is monitored by monitoring the voltage, frequency, and islanding conditions.

    After installation and commissioning, the inverter's operation is fully automatic; the inverter draws the maximum possible power from the solar modules.
    Depending on the operating point, this power is used in the home, stored in a battery*, or fed into the grid.

    As soon as the energy provided by the solar modules is no longer sufficient, the power from the battery is fed into the home network. Depending on the setting, power may also be obtained from the public grid in order to charge the battery*.

    When its temperature gets too high, the inverter automatically reduces the output or charging power, or switches off completely, in order to protect itself.
    Reasons for the temperature being too high include a high ambient temperature or insufficient heat dissipation (for example, inadequate heat dissipation when installed in switch cabinets).

    *
    Depending on the device variant, suitable battery, corresponding cabling, settings, and local standards and regulations.
    1. General information
    2. Fronius Verto

    Device concept

    link_horizontalLink copied

    The inverter transforms the direct current generated by the PV modules into alternating current. This alternating current is fed into the public grid and synchronized with the mains voltage in use. Moreover, the solar energy can also be stored in a connected battery for later use.

    The inverter is intended for use in grid-connected photovoltaic systems. The inverter has backup power functions and switches to backup power mode if it has been wired accordingly*.

    The inverter automatically monitors the public grid. Whenever conditions in the electric grid are inconsistent with standard conditions (e.g., grid switch-off, interruption), the inverter will immediately stop producing power and interrupt the supply of power into the grid.
    The grid is monitored by monitoring the voltage, frequency, and islanding conditions.

    After installation and commissioning, the inverter's operation is fully automatic; the inverter draws the maximum possible power from the solar modules.
    Depending on the operating point, this power is used in the home, stored in a battery*, or fed into the grid.

    As soon as the energy provided by the solar modules is no longer sufficient, the power from the battery is fed into the home network. Depending on the setting, power may also be obtained from the public grid in order to charge the battery*.

    When its temperature gets too high, the inverter automatically reduces the output or charging power, or switches off completely, in order to protect itself.
    Reasons for the temperature being too high include a high ambient temperature or insufficient heat dissipation (for example, inadequate heat dissipation when installed in switch cabinets).

    *
    Depending on the device variant, suitable battery, corresponding cabling, settings, and local standards and regulations.
    1. General information
    2. Fronius Verto

    Scope of supply

    link_horizontalLink copied
    (1)
    Mounting bracket (is mounted on the inverter on delivery)
    (2)
    Inverter
    (3)
    Housing cover
    (4)
    Quick Start Guide
    (5)
    Plug set MC4 EVO Store 10 mm² / 4-6 mm²
    1. General information
    2. Fronius Verto

    Enhanced Power Harvest

    link_horizontalLink copied

    With the “Enhanced Power Harvest” function, surplus energy from the PV modules that exceeds the rated power of the inverter can also be stored in the battery.

    Power category

    Surplus energy

    Maximum DC power utilization

    15.0

    150%

    22.5 kW

    17.5

    150%

    26.25 kW

    20.0

    150%

    30 kW

    25.0

    130%

    32.5 kW

    30.0

    130%

    39 kW

    33.3

    117%

    39 kW

    1. General information
    2. Fronius Verto

    Backup Power Boost

    link_horizontalLink copied

    With the “Backup Power Boost” function, the inverter can provide increased power for a short time in backup power mode in order to reliably supply even power-intensive loads.

    Power category

    Max. DC power *

    Max. output current / phase *

    15.0

    30 kVA

    43.5 A (3 phases) / 32 A (1 phase)

    17.5

    30 kVA

    43.5 A (3 phases) / 32 A (1 phase)

    20.0

    30 kVA

    43.5 A (3 phases) / 32 A (1 phase)

    25.0

    50 kVA

    72.5 A (3 phases) / 72.5 A (1 phase)

    30.0

    50 kVA

    72.5 A (3 phases) / 72.5 A (1 phase)

    33.3

    50 kVA

    72.5 A (3 phases) / 72.5 A (1 phase)

    * Sufficient PV and battery power required. Duration max. 5–10 seconds, 400 V AC symmetrical, depending on the environmental conditions.

    1. General information
    2. Fronius Verto

    Thermal concept

    link_horizontalLink copied

    Ambient air is drawn in by the fan on the top and bottom and blown out at the device sides. The even heat dissipation allows several inverters to be installed next to each other.

    NOTE

    Risk due to insufficient cooling of the inverter.

    This may result in a loss of power in the inverter.

    Do not block the fan (for example, with objects that protrude through the touch guard).

    Do not cover the ventilation slots, even partially.

    Make sure that the ambient air can always flow through the inverter's ventilation slots unimpeded.

    1. General information
    2. Fronius Verto

    Fronius Solar.web

    link_horizontalLink copied

    System owners and installers can easily monitor and analyze the PV system using Fronius Solar.web or Fronius Solar.web Premium. With the appropriate configuration, the inverter transmits data such as power, yield, load, and energy balance to Fronius Solar.web. More detailed information can be found at Solar.web - Monitoring & analysis.

    Configuration is carried out via the Setup wizard, see chapter Installation with the app or Installation with the browser.

    Requirements for configuration:
    • Internet connection (download: min. 512 kbit/s, upload: min. 256 kbit/s)*.
    • User account at solarweb.com.
    • Completed configuration using the Setup wizard.
    *
    These specifications do not provide an absolute guarantee of flawless operation. High error rates in the transmission, fluctuating receptions or misfires can have an adverse effect on data transfer. Fronius recommends on-site testing to ensure that the connections meet the minimum requirements.
    1. General information
    2. Fronius Verto

    Local communication

    link_horizontalLink copied

    The inverter can be found via the Multicast DNS (mDNS) protocol. We recommend searching for the inverter using the assigned host name.

    The following data can be called up via mDNS:
    • NominalPower
    • Systemname
    • DeviceSerialNumber
    • SoftwareBundleVersion
    1. General information

    Different operating modes

    link_horizontalLink copied

    Operating modes – Explanation of symbols

    PV module
    generates direct current

    Fronius Verto inverter
    converts the direct current into alternating current and charges the battery. The integrated system monitoring enables the inverter to be integrated into a network by means of WiFi.

    Additional inverter in the system
    converts the direct current into alternating current. However, it cannot charge a battery and is not available in backup power mode.

    Battery
    is coupled to the inverter on the direct current side, and stores electrical energy.

    Fronius Ohmpilot
    for using excess energy to heat water.

    Primary meter
    records the load curve of the system and makes the measured data available for energy profiling in Fronius Solar.web. The primary meter also controls the dynamic power of feeding in.

    Secondary meter
    records the load curve of individual loads (e.g., washing machine, lights, television, heat pump, etc.) in the load branch and makes the measured data available for energy profiling in Fronius Solar.web.

    Loads in the system
    are the loads connected in the system.

    Additional loads and producers in the system
    which are connected to the system by means of a Smart Meter.

    Full Backup
    the inverter is prepared for backup power mode. The backup power function must be implemented in the switch cabinet by the electrician performing the installation. The PV system operates in a stand-alone manner in backup power mode.

    Grid
    supplies the loads in the system if insufficient power is being generated by the PV modules or supplied by the battery.

    1. General information
    2. Different operating modes

    Operating modes – Explanation of symbols

    link_horizontalLink copied

    PV module
    generates direct current

    Fronius Verto inverter
    converts the direct current into alternating current and charges the battery. The integrated system monitoring enables the inverter to be integrated into a network by means of WiFi.

    Additional inverter in the system
    converts the direct current into alternating current. However, it cannot charge a battery and is not available in backup power mode.

    Battery
    is coupled to the inverter on the direct current side, and stores electrical energy.

    Fronius Ohmpilot
    for using excess energy to heat water.

    Primary meter
    records the load curve of the system and makes the measured data available for energy profiling in Fronius Solar.web. The primary meter also controls the dynamic power of feeding in.

    Secondary meter
    records the load curve of individual loads (e.g., washing machine, lights, television, heat pump, etc.) in the load branch and makes the measured data available for energy profiling in Fronius Solar.web.

    Loads in the system
    are the loads connected in the system.

    Additional loads and producers in the system
    which are connected to the system by means of a Smart Meter.

    Full Backup
    the inverter is prepared for backup power mode. The backup power function must be implemented in the switch cabinet by the electrician performing the installation. The PV system operates in a stand-alone manner in backup power mode.

    Grid
    supplies the loads in the system if insufficient power is being generated by the PV modules or supplied by the battery.

    1. General information
    2. Different operating modes

    Operating mode – Inverter with battery

    link_horizontalLink copied

    In order to be able to obtain the highest rate of self-consumption with your photovoltaic system, a battery can be used to store excess energy. The battery is coupled to the inverter on the direct current side. Multiple current conversion is therefore not required, and the efficiency is increased.

    1. General information
    2. Different operating modes

    Operating mode – Inverter with battery and several Smart Meters

    link_horizontalLink copied
    1. General information
    2. Different operating modes

    Operating mode – Inverter with battery, AC-coupled to another inverter

    link_horizontalLink copied
    1. General information
    2. Different operating modes

    Operating mode – Inverter with battery and backup power function

    link_horizontalLink copied

    IMPORTANT!
    In backup power mode, an increased nominal frequency is used in order to prevent undesired parallel operation with other power generators.

    When the hybrid PV system is equipped with all the available features, the inverter can:
    • Supply loads in the house
    • Store excess energy in the battery and/or feed it into the grid
    • Supply connected loads in the event of a power failure
    1. General information
    2. Different operating modes

    Operating mode – Inverter with battery and Ohmpilot

    link_horizontalLink copied
    1. General information
    2. Different operating modes

    Operating mode – Inverter with battery, Ohmpilot, and backup power function

    link_horizontalLink copied

    IMPORTANT!
    In the fully equipped hybrid PV system with a Fronius Ohmpilot, the Ohmpilot cannot be operated in the event of a power failure for regulatory reasons. It is therefore sensible to install the Ohmpilot outside of the backup power branch.

    1. General information
    2. Different operating modes

    Operating mode – Inverter with battery and another inverter

    link_horizontalLink copied

    In the hybrid PV system, batteries may only be connected to an inverter with battery support. Batteries cannot be split between multiple inverters with battery support. Depending on the battery manufacturer, however, several batteries can be combined on one inverter.

    1. General information
    2. Different operating modes

    Operating mode – Inverter with battery, another inverter, and backup power function

    link_horizontalLink copied

    In the hybrid PV system, batteries may only be connected to an inverter with battery support. Batteries cannot be split between multiple inverters with battery support. Depending on the battery manufacturer, however, several batteries can be combined on one inverter.

    1. General information
    2. Different operating modes

    Energy flow direction of the inverter

    link_horizontalLink copied
    (1)
    PV module – inverter – load/grid/battery
    (2)
    Battery – inverter – load/grid*
    (3)
    Grid – inverter – battery*

    * Depending on the settings and local standards and regulations.

    1. General information
    2. Different operating modes

    Operating states (only for battery systems)

    link_horizontalLink copied

    Battery systems distinguish between different operating states. In each case, the relevant current operating state is displayed on the user interface of the inverter or in Fronius Solar.web.

    Operating state

    Description

    Normal operation

    The energy is stored or drawn, as required.

    Min. state of charge (SoC) reached

    The battery has reached the minimum SoC specified by the manufacturer or the set minimum SoC. The battery cannot be discharged further.

    Energy saving mode (standby)

    The system has been put into energy-saving mode. Energy saving mode is automatically ended as soon as sufficient surplus power is available again.

    Start

    The battery system starts from energy-saving mode (standby).

    Forced re-charging

    The inverter recharges the battery, in order to maintain the SoC specified by the manufacturer or the set minimum SoC (protection against deep discharge).

    Calibration charging

    The battery system is charged to the SoC of 100% and then discharged to the SoC of 0%. After 1 hour of waiting time at SoC 0%, the calibration charge is stopped and the battery switches to normal operation.

    Service mode

    The battery system is charged or discharged to the SoC of 30% and the SoC of 30% is maintained until the end of the service mode.

    Deactivated

    The battery is not active. It has either been deactivated, switched off, or the communication between the battery and the inverter has been interrupted.

    1. General information

    Energy-saving mode

    link_horizontalLink copied

    General

    Energy saving mode (standby mode) is used to reduce the self-consumption of the system. Both the inverter and the battery automatically switch to energy saving mode under certain conditions.

    The inverter switches to energy saving mode if the battery is flat and no PV power is available. Only the inverter's communication with the Fronius Smart Meter and Fronius Solar.web is maintained.

    1. General information
    2. Energy-saving mode

    General

    link_horizontalLink copied

    Energy saving mode (standby mode) is used to reduce the self-consumption of the system. Both the inverter and the battery automatically switch to energy saving mode under certain conditions.

    The inverter switches to energy saving mode if the battery is flat and no PV power is available. Only the inverter's communication with the Fronius Smart Meter and Fronius Solar.web is maintained.

    1. General information
    2. Energy-saving mode

    Switch-off conditions

    link_horizontalLink copied

    If all the switch-off conditions are met, the battery switches into energy saving mode within ten minutes. This time delay ensures that the inverter can at least be restarted.

     

    The battery state of charge is less than or equal to the input minimum state of charge.

     

    The current charging or discharging power of the battery is less than 100 W.

     

    Less than 50 W is available for charging the battery. The power of feeding into the public grid is at least 50 W less than the power currently required in the home network.

    The inverter automatically switches into energy saving mode, following the battery.

    1. General information
    2. Energy-saving mode

    Switch-on conditions

    link_horizontalLink copied
    If one of the following conditions is met for at least 30 seconds, energy saving mode is ended:
    • Energy saving mode is no longer permissible owing to a changed setting on the user interface of the inverter.
    • If dynamic power reduction of 0 is set, or if the system is operating in backup power mode, the power of feeding into the public grid is always less than the required power in the home network.
      There is a separate condition for this case (dynamic power reduction < 300 W or active backup power mode):
      • If the PV power is above a specified threshold, energy saving mode is ended.
    • Battery charging from the public grid is requested via the user interface of the inverter.
    • The battery is being recharged in order to restore the minimum state of charge or perform calibration.
    1. General information
    2. Energy-saving mode

    Special case

    link_horizontalLink copied

    If the inverter does not operate for 12 minutes (e.g., fault), or there is an interruption in the electrical connection between the inverter and the battery and there is no backup power mode, the battery switches to energy-saving mode in any case. This reduces self discharge of the battery.

    1. General information
    2. Energy-saving mode

    Indication of energy saving mode

    link_horizontalLink copied
    During energy saving mode:
    • Operating LED of the inverter lights up orange (see Button functions and LED status indicator on page (→)).
    • The user interface of the inverter can be reached.
    • All the available data are saved and transmitted to Solar.web.
    • The real-time data can be seen on Solar.web.

     

    Energy saving mode is shown on the user interface of the inverter and in Solar.web by an "i" beside the battery symbol in the system overview.

    1. General information

    Suitable batteries

    link_horizontalLink copied

    General

    Fronius explicitly points out that the third-party batteries are not Fronius products. Fronius is not the manufacturer, distributor, or retailer of these batteries. Fronius accepts no liability and offers no service or guarantees for these batteries.

    Obsolete firmware/software states may lead to incompatibilities between the inverter and the battery. In this case, the following steps are to be performed:
    1Update battery software—see the battery documentation.
    2Update inverter firmware—see Update on page (→).

    Read this document and the Installation Instructions before installing and commissioning the external battery. The documentation is either enclosed with the external battery or can be obtained from the battery manufacturer or their service partners

    All documents associated with the inverter can be found at the following address:
    https://www.fronius.com/en/solar-energy/installers-partners/service-support/tech-support

    1. General information
    2. Suitable batteries

    General

    link_horizontalLink copied

    Fronius explicitly points out that the third-party batteries are not Fronius products. Fronius is not the manufacturer, distributor, or retailer of these batteries. Fronius accepts no liability and offers no service or guarantees for these batteries.

    Obsolete firmware/software states may lead to incompatibilities between the inverter and the battery. In this case, the following steps are to be performed:
    1Update battery software—see the battery documentation.
    2Update inverter firmware—see Update on page (→).

    Read this document and the Installation Instructions before installing and commissioning the external battery. The documentation is either enclosed with the external battery or can be obtained from the battery manufacturer or their service partners

    All documents associated with the inverter can be found at the following address:
    https://www.fronius.com/en/solar-energy/installers-partners/service-support/tech-support

    1. General information
    2. Suitable batteries

    Fronius batteries

    link_horizontalLink copied

    Fronius Reserva

    Capacity [kWh] 

    6.3 - 15.8

    Number of modules

    2 - 5

    Fronius Verto Plus

    Battery parallel operation*

    Fronius Reserva Pro

    Capacity [kWh] 

    12.0 - 32.0

    Number of modules

    3 - 8

    Fronius Verto Plus

    Battery parallel operation*

    *
    Max. 4 batteries with the same capacity can be combined.
    1. General information
    2. Suitable batteries

    BYD batteries

    link_horizontalLink copied

    BYD Battery-Box Premium HVS

    BYD Battery-Box HVS+

    Capacity [kWh]1)

    5.1 - 12.8

    Number of modules

    2 - 5

    Fronius Verto Plus 

    Battery parallel operation*

    BYD Battery-Box Premium HVM

    BYD Battery-Box HVM+

    Capacity [kWh]

    8.3

    11.0 - 22.1

    Number of modules

    3

    4 - 8

    Fronius Verto Plus

    Battery parallel operation*

    BYD Battery-Box HVB

    Capacity [kWh]

    5.9 - 8.9

    11.8 - 29.6

    Number of modules

    2 - 3

    4 - 10

    Fronius Verto Plus

    Battery parallel operation*

    *
    Max. 3 batteries with the same capacity can be combined. With BYD Battery-Box Premium HVM 22.1 max. 2 batteries can be combined.

    IMPORTANT!
    See the battery manufacturer's documentation for the maximum DC cable length.

    IMPORTANT! The following switch-on sequence for the system must always be followed to ensure reliable operation with a BYD Battery-Box Premium.
    1

    Switch on the battery's automatic circuit breaker.

    2

    Switch on the external AC automatic circuit breaker. Set the DC disconnector (see DC disconnector) to the "On" switch position.

    1. General information

    Manual system start

    link_horizontalLink copied

    Requirements

    There is no energy available from the PV modules or from the public grid. If backup power operation or battery operation are not possible (e.g., deep discharge protection of the battery), the inverter and battery switch off.

    1. General information
    2. Manual system start

    Requirements

    link_horizontalLink copied

    There is no energy available from the PV modules or from the public grid. If backup power operation or battery operation are not possible (e.g., deep discharge protection of the battery), the inverter and battery switch off.

    1. General information
    2. Manual system start

    Notification of system shutdown

    link_horizontalLink copied

    Status codes about the inactive state of the battery are displayed on the user interface of the inverter. A notification via e-mail can be activated in Fronius Solar.web.

    1. General information
    2. Manual system start

    Manual battery start after system shutdown

    link_horizontalLink copied

    As soon as energy is available again, the inverter starts operation automatically; however, the battery must be started manually. The switch-on sequence must be observed for this, see chapter Suitable batteries on page (→).

    1. General information
    2. Manual system start

    Starting backup power operation after a system shutdown

    link_horizontalLink copied

    The inverter requires energy from the battery to start backup power operation. This is done manually on the battery; further information on the power supply for restarting the inverter via the battery can be found in the battery manufacturer's Operating Instructions.

    1. General information

    Utilization in accordance with "intended purpose"

    link_horizontalLink copied

    Intended use

    The inverter is designed to convert direct current from PV modules into alternating current and feed this power into the public grid. A backup power mode* is possible if the wiring is set up accordingly.

    Intended use also means:
    • Carefully reading and following all the instructions as well as complying with the safety and danger notices in the operating instructions
    • Installation in accordance with the chapter headed Installation, from page (→)

    Follow all grid operator regulations regarding energy fed into the grid and connection methods.

    The inverter is a grid-connected inverter with backup power function and is not a stand-alone inverter. The following restrictions in backup power mode must therefore be observed:
    • The inverter may be operated for max. 2000 operating hours in backup power mode
    • The inverter may be operated for more than 2000 operating hours in backup power mode provided 20% of the grid power feed operating time of the inverter is not exceeded at the time in question
    *
    Depending on the device variant, suitable battery, corresponding cabling, settings, and local standards and regulations.
    1. General information
    2. Utilization in accordance with "intended purpose"

    Intended use

    link_horizontalLink copied

    The inverter is designed to convert direct current from PV modules into alternating current and feed this power into the public grid. A backup power mode* is possible if the wiring is set up accordingly.

    Intended use also means:
    • Carefully reading and following all the instructions as well as complying with the safety and danger notices in the operating instructions
    • Installation in accordance with the chapter headed Installation, from page (→)

    Follow all grid operator regulations regarding energy fed into the grid and connection methods.

    The inverter is a grid-connected inverter with backup power function and is not a stand-alone inverter. The following restrictions in backup power mode must therefore be observed:
    • The inverter may be operated for max. 2000 operating hours in backup power mode
    • The inverter may be operated for more than 2000 operating hours in backup power mode provided 20% of the grid power feed operating time of the inverter is not exceeded at the time in question
    *
    Depending on the device variant, suitable battery, corresponding cabling, settings, and local standards and regulations.
    1. General information
    2. Utilization in accordance with "intended purpose"

    Foreseeable misuse

    link_horizontalLink copied
    The following circumstances are considered to be reasonably foreseeable misuse:
    • Any use that is not the intended use or goes beyond the intended use.
    • Alterations to the inverter that are not expressly recommended by Fronius.
    • Installation of components that are not expressly recommended or sold by Fronius.
    1. General information
    2. Utilization in accordance with "intended purpose"

    Provisions for the photovoltaic system

    link_horizontalLink copied

    The inverter is designed exclusively to be connected and used with PV modules.
    Use with other DC generators (e.g., wind generators) is not permitted.

    When configuring the photovoltaic system, make sure that all photovoltaic system components are operating exclusively within their permitted operating range.

    All measures recommended by the PV module manufacturer for maintaining the PV module properties must be followed.

    1. General information

    Surge protection device (SPD)

    link_horizontalLink copied

    Surge protection device SPD

     

    The surge protection device (SPD) protects against temporary overvoltages and diverts surge currents (e.g., lightning strike). Based on an overall lightning protection concept, the SPD contributes to the protection of the photovoltaic system components.

     

    If the surge protection device is triggered, the color of the indicator changes from green to red (mechanical display).

    A triggered SPD must be replaced with a fully functional SPD immediately by an authorized specialist company in order to maintain the full protective function of the device.

     

    It is possible to enable the option of digitally displaying the triggering of an SPD. If you wish to set this function, refer to the PDF "SPD Triggering / Temporary SPD Triggering" in the Service & Support area at www.fronius.com

    IMPORTANT!
    After setting the function described above, the inverter also responds if the 2-pole signal cable of the surge protection device is damaged or is subject to an interruption.

    The following components can be used to replace existing AC SPDs with type 1+2 products:
    • CITEL - DAC1-13S-31-275 (for mains voltages of 380–400 V)
    • CITEL - DAC1-13S-31-320 (for mains voltages of 440–480 V)

    Note: Replacing a device does not automatically result in replacement of the existing SPDs.

    1. General information
    2. Surge protection device (SPD)

    Surge protection device SPD

    link_horizontalLink copied

     

    The surge protection device (SPD) protects against temporary overvoltages and diverts surge currents (e.g., lightning strike). Based on an overall lightning protection concept, the SPD contributes to the protection of the photovoltaic system components.

     

    If the surge protection device is triggered, the color of the indicator changes from green to red (mechanical display).

    A triggered SPD must be replaced with a fully functional SPD immediately by an authorized specialist company in order to maintain the full protective function of the device.

     

    It is possible to enable the option of digitally displaying the triggering of an SPD. If you wish to set this function, refer to the PDF "SPD Triggering / Temporary SPD Triggering" in the Service & Support area at www.fronius.com

    IMPORTANT!
    After setting the function described above, the inverter also responds if the 2-pole signal cable of the surge protection device is damaged or is subject to an interruption.

    The following components can be used to replace existing AC SPDs with type 1+2 products:
    • CITEL - DAC1-13S-31-275 (for mains voltages of 380–400 V)
    • CITEL - DAC1-13S-31-320 (for mains voltages of 440–480 V)

    Note: Replacing a device does not automatically result in replacement of the existing SPDs.

    1. General information

    Operating controls and connections

    link_horizontalLink copied

    Connection area

    (1)
    Push-in WSD (wired shutdown) terminal
    (2)
    Push-in terminals in the data communication area (Modbus)
    (3)
    Push-in terminals in the data communication area (Modbus, digital inputs and outputs)
    (4)
    5-pin AC terminal
       =   
    (5)
    Cable gland/cable connection AC
    (6)
    Surge protection device AC SPD
    (7)
    Optional cable gland
    (8)
    Grounding clamping bolts
    (9)
    Data communication area cable gland/cable connection
    (10)
    DIN rail (installation option for third-party components)
    (11)
    DC connections MC4 and battery connections MC4-Evo stor
    (12)
    Surge protection device DC SPD
    1. General information
    2. Operating controls and connections

    Connection area

    link_horizontalLink copied
    (1)
    Push-in WSD (wired shutdown) terminal
    (2)
    Push-in terminals in the data communication area (Modbus)
    (3)
    Push-in terminals in the data communication area (Modbus, digital inputs and outputs)
    (4)
    5-pin AC terminal
       =   
    (5)
    Cable gland/cable connection AC
    (6)
    Surge protection device AC SPD
    (7)
    Optional cable gland
    (8)
    Grounding clamping bolts
    (9)
    Data communication area cable gland/cable connection
    (10)
    DIN rail (installation option for third-party components)
    (11)
    DC connections MC4 and battery connections MC4-Evo stor
    (12)
    Surge protection device DC SPD
    1. General information
    2. Operating controls and connections

    Photovoltaic and battery connections

    link_horizontalLink copied
    1. General information
    2. Operating controls and connections

    Ground electrode bolt

    link_horizontalLink copied
    The ground electrode bolt    allows additional components to be grounded, such as:
    • AC cable
    • Module mounting system
    • Ground rod

    If further grounding options are required, suitable terminals can be fitted to the DIN rail.

    1. General information
    2. Operating controls and connections

    Mounting option for third-party components

    link_horizontalLink copied

    In the connection area there is space for mounting third-party components. Components up to a maximum width of 14.5 cm (8 DU) can be mounted on the DIN rail. The components must have a temperature resistance of -40 °C to +70 °C.

    1. General information
    2. Operating controls and connections

    DC disconnector

    link_horizontalLink copied

    WARNING

    Disconnecting the battery connections

    The DC disconnector only disconnects the PV connections and not the power supply to the battery. Serious personal injury and damage to the inverter and connected components may result if the battery is under voltage during installation and maintenance work.

    Use the battery disconnecting device to disconnect it from the power supply.

    Install an external disconnecting device between the inverter and battery if required by local regulations.

    The DC disconnector is equipped with two switch settings: 1 (on)/0 (off).

    Secure against being switched on:
    Secure the inverter to prevent it being switched on with a padlock in switch position 0 (off). Comply with the national guidelines in this respect.

    Minimum requirements for padlock:
    • Shackle diameter min. 6 mm
    • Housing size min. 40 mm
    1. General information
    2. Operating controls and connections

    Data communication area

    link_horizontalLink copied

       Operating LED

    Indicates the inverter operating status.

    BAT switch

    Position 1: Setting for connecting compatible batteries (factory setting)
    Position 0:
    not in use

    WSD (wired shutdown) switch

    Defines the inverter as the WSD master or WSD secondary device.

    Position 1: WSD master
    Position 0:
    WSD secondary device

    Modbus 0 (MB0) switch

    Switches the terminating resistor for Modbus 0 (MB0) on/off.

    Position 1: Terminating resistor on (factory setting)
    Position 0: Terminating resistor off

    Modbus 1 (MB1) switch

    Switches the terminating resistor for Modbus 1 (MB1) on/off.

    Position 1: Terminating resistor on (factory setting)
    Position 0: Terminating resistor off

       Optical sensor

    For operating the inverter. See Button functions and LED status indicator.

       Communications LED

    Indicates the inverter connection status.

     Battery Connection (Modbus RJ45)

    Modbus connection for connecting a compatible battery.

    IMPORTANT!

    • This connection only works with hybrid inverters.
    • The connection is connected to Modbus 0.
    • Do not connect any network components (e.g., WiFi router) to this connection.

    LAN 1

    Ethernet connection for data communication (e.g., WiFi router, home network) or, for commissioning with a laptop, see Installation with the browser.

    LAN 2

    Reserved for future functions.

    I/O terminal

    Push-in terminal for digital inputs/outputs. See Permitted cables for the data communication connection.
    The designations (RG0, CL0, 1/5, 2/6, 3/7, 4/8) relate to the Function Demand Response Mode, see Functions and I/Os.

    WSD terminal

    Push-in terminal for the WSD installation. See Installing the WSD (wired shutdown).

    Modbus terminal

    Push-in terminal for the installation of Modbus 0, Modbus 1, 12 V, and GND (ground).

    The inverter establishes the data connection to the connected components via the Modbus terminal. The inputs M0 and M1 can be freely selected. Max. four Modbus participants per input, see Modbus participants.

    1. General information
    2. Operating controls and connections

    Button functions and LED status indicator

    link_horizontalLink copied

    The operating LED indicates the inverter status. In case of faults, follow the individual steps in the Fronius Solar.start app.

    Actuate the optical sensor by touching it with a finger.

    The communication LED indicates the status of the connection. To establish a connection, follow the individual steps in the Fronius Solar.start app.

     

    Sensor functions

    1x    = WiFi access point (AP) is opened.

       Flashes blue

    2x    = WiFi protected setup (WPS) is activated.

       Flashes green

    3 seconds    (max. 6 seconds) = the service message disappears.

       Flashes white (quickly)

     

    LED status indicator

    The inverter is operating correctly.

       Lights up green

    The inverter is performing the grid checks required by the applicable standards for grid power feed operation.

       Flashes green

    The inverter is on standby, is not operating (e.g., no energy fed into the grid at night), or is not configured.

       Lights up yellow

    The inverter displays an error. The inverter is operating correctly.

       Flashes yellow

    The inverter displays a critical status and no energy is fed into the grid.

       Lights up red

    The inverter displays a backup power overload.

       Flashes red

    The network connection is being established via WPS.
    2x    = WPS search mode.

       Flashes green

    The network connection is being established via WiFi AP.
    1x    = WiFi AP search mode (active for 30 minutes).

       Flashes blue

    The network connection is not configured.

       Lights up yellow

    There is a network error, the inverter is operating correctly.

       Lights up red

    The network connection is active.

       Lights up blue

    The inverter is performing an update.

       /    Flash blue

    There is a service message.

       Lights up white

    1. General information
    2. Operating controls and connections

    Schematic internal wiring of IOs

    link_horizontalLink copied

    The V+/ GND pin provides the possibility of feeding in a voltage in the range of 12.5 to 24 V (+ max. 20%) using an external power supply unit. Outputs IO 0 - 5 can then be operated using the external voltage that has been fed in. A maximum of 1 A may be drawn per output, whereby a total of max. 3 A is permitted. The fuse protection must take place externally.

    CAUTION

    Danger from polarity reversal at the terminals due to improper connection of external power supply units.

    This may result in severe damage to the inverter.

    Check the polarity of the external power supply unit with a suitable measuring device before connecting it.

    Connect the cables to the V+/GND outputs while ensuring the correct polarity.

    IMPORTANT!
    If the total output (6 W) is exceeded, the inverter switches off the entire external power supply.

    (1)
    Current limitation

    Backup power variant - Full Backup

    link_horizontalLink copied

    General

    Prerequisites for backup power mode

    The following prerequisites must be met in order to use the inverter’s backup power function:
    • The inverter must support the backup power variant “Full Backup.”
    • A battery suitable for backup power use must be installed and configured.
    • Correct cabling of the backup power system in the electrical installation or usage of a switchover box from Enwitec (see chapter Components for switching to backup power on page (→) or Circuit diagrams—automatic switch to backup power with Fronius Backup Controller on page (→)).
    • An installation with connected neutral conductor.
    • Install and configure the Fronius Smart Meter at the feed-in point.
    • Attach a backup power supply warning (https://www.fronius.com/en/search-page, item number: 42.0409.0275) to the electrical distributor.
    • Apply the necessary settings in the Devices and system components > Functions and pins > Backup Power menu item and activate backup power.
    • Go through the checklist – Backup power (https://www.fronius.com/en/search-page, item number: 42.0426.0365) step by step and confirm.
    1. Backup power variant - Full Backup

    General

    link_horizontalLink copied

    Prerequisites for backup power mode

    The following prerequisites must be met in order to use the inverter’s backup power function:
    • The inverter must support the backup power variant “Full Backup.”
    • A battery suitable for backup power use must be installed and configured.
    • Correct cabling of the backup power system in the electrical installation or usage of a switchover box from Enwitec (see chapter Components for switching to backup power on page (→) or Circuit diagrams—automatic switch to backup power with Fronius Backup Controller on page (→)).
    • An installation with connected neutral conductor.
    • Install and configure the Fronius Smart Meter at the feed-in point.
    • Attach a backup power supply warning (https://www.fronius.com/en/search-page, item number: 42.0409.0275) to the electrical distributor.
    • Apply the necessary settings in the Devices and system components > Functions and pins > Backup Power menu item and activate backup power.
    • Go through the checklist – Backup power (https://www.fronius.com/en/search-page, item number: 42.0426.0365) step by step and confirm.
    1. Backup power variant - Full Backup
    2. General

    Prerequisites for backup power mode

    link_horizontalLink copied
    The following prerequisites must be met in order to use the inverter’s backup power function:
    • The inverter must support the backup power variant “Full Backup.”
    • A battery suitable for backup power use must be installed and configured.
    • Correct cabling of the backup power system in the electrical installation or usage of a switchover box from Enwitec (see chapter Components for switching to backup power on page (→) or Circuit diagrams—automatic switch to backup power with Fronius Backup Controller on page (→)).
    • An installation with connected neutral conductor.
    • Install and configure the Fronius Smart Meter at the feed-in point.
    • Attach a backup power supply warning (https://www.fronius.com/en/search-page, item number: 42.0409.0275) to the electrical distributor.
    • Apply the necessary settings in the Devices and system components > Functions and pins > Backup Power menu item and activate backup power.
    • Go through the checklist – Backup power (https://www.fronius.com/en/search-page, item number: 42.0426.0365) step by step and confirm.
    1. Backup power variant - Full Backup
    2. General

    Transitioning from grid power feed operation to backup power mode

    link_horizontalLink copied
    1. The public grid is monitored by the inverter's internal grid and system protection unit and by the Fronius Smart Meter connected to it.
    2. The public grid fails or specific grid parameters are undershot or exceeded.
    3. The inverter carries out the measures necessary according to the country standard and then switches off.
    4. The inverter starts backup power mode after a checking period.
    5. All loads in the household that are in the backup power circuit are supplied by the battery and the PV modules. The remaining loads are not supplied with power and are safely isolated.
    1. Backup power variant - Full Backup
    2. General

    Transitioning from backup power mode to grid power feed operation

    link_horizontalLink copied
    1. The inverter is operating in backup power mode.
    2. The public grid is functioning correctly again.
    3. The Fronius Smart Meter monitors the grid parameters on the public grid and passes this information to the inverter.
    4. The stability of the restored public grid is determined by checking the measured values of the Fronius Smart Meter.
    5. Backup power mode is terminated automatically or manually depending on the design of the backup power switchover facility.
    6. All circuits are reconnected to the public grid and are supplied by the grid.
    7. The inverter can start grid power feed operation again after performing the grid checks required by the relevant standard.
    1. Backup power variant - Full Backup
    2. General

    Backup power and energy saving mode

    link_horizontalLink copied
    Under the following conditions, the battery and the inverter are switched to energy saving mode after a waiting time of 8-12 minutes and backup power mode is ended:
    • The battery is discharged to the minimum state of charge and no energy is coming from the PV modules.
    • The inverter is set to energy saving mode (standby mode).
    If the battery and inverter are in energy saving mode, the system is reactivated by the following:
    • Enough energy is available from the PV modules.
    • The public grid is functioning again.
    • The battery is switched off and on.
    1. Backup power variant - Full Backup

    Automatic switch to backup power with Fronius Backup Controller 3P-35A incl. backup power circuits and 3-pin separation, e.g., Austria or Australia

    link_horizontalLink copied

    Functions

    IMPORTANT!
    Depending on the installation, the entire house or only selected circuits are supplied with backup power if the public grid fails. The total load of the backup power circuits must not exceed the rated power of the inverter. Note the capacity of the connected battery.

    • Disconnects from the public grid after the required FRT time if the grid parameters are outside the country-specific standards in order to enable backup power mode.
    • Reconnects to the public grid if the grid parameters are within the limits of the country-specific standards.
    • Possibility of a separate backup power circuit or several backup power circuits, which are also supplied during a failure of the public grid. The total load of the backup power circuits must not exceed the rated power of the inverter. The capacity of the connected battery must also be taken into account.
    1. Backup power variant - Full Backup
    2. Automatic switch to backup power with Fronius Backup Controller 3P-35A incl. backup power circuits and 3-pin separation, e.g., Austria or Australia

    Functions

    link_horizontalLink copied

    IMPORTANT!
    Depending on the installation, the entire house or only selected circuits are supplied with backup power if the public grid fails. The total load of the backup power circuits must not exceed the rated power of the inverter. Note the capacity of the connected battery.

    • Disconnects from the public grid after the required FRT time if the grid parameters are outside the country-specific standards in order to enable backup power mode.
    • Reconnects to the public grid if the grid parameters are within the limits of the country-specific standards.
    • Possibility of a separate backup power circuit or several backup power circuits, which are also supplied during a failure of the public grid. The total load of the backup power circuits must not exceed the rated power of the inverter. The capacity of the connected battery must also be taken into account.
    1. Backup power variant - Full Backup
    2. Automatic switch to backup power with Fronius Backup Controller 3P-35A incl. backup power circuits and 3-pin separation, e.g., Austria or Australia

    Transition from grid power feed operation to backup power mode

    link_horizontalLink copied
    1. The public grid is monitored by the inverter's internal grid and system protection and by the connected Fronius Smart Meter.
    2. Failure of the public grid.
    3. The inverter takes the necessary measures according to the country standard and then switches off.
      The Fronius Backup Controller disconnects the backup power circuits and the inverter from the rest of the home network and from the public grid.
    4. Based on the feedback from the Fronius Backup Controller and the measurements at the inverter terminals, the inverter decides that backup power mode can be started.
    5. After all required connection tests have been carried out, the inverter starts in backup power mode.
    6. All loads that are in the backup power circuits are supplied. The remaining loads are not supplied and are safely disconnected.
    1. Backup power variant - Full Backup
    2. Automatic switch to backup power with Fronius Backup Controller 3P-35A incl. backup power circuits and 3-pin separation, e.g., Austria or Australia

    Transition from backup power mode to grid power feed operation

    link_horizontalLink copied
    1. The inverter is operating in backup power mode. The backup power circuits are disconnected from the public grid.
    2. Public grid is available again.
    3. The Fronius Smart Meter measures the grid parameters on the public grid and passes this information on to the inverter.
    4. The stability of the restored public grid is determined by checking the measured values of the Fronius Smart Meter.
    5. The inverter ends backup power mode and de-energizes the outputs.
    6. The inverter gives the Fronius Backup Controller approval to reconnect to the public grid.
    7. All backup power circuits are reconnected to the public grid by the Fronius Backup Controller.
    8. Once the grid checks required by the applicable standards have been performed, the inverter can start feeding power into the grid again.
    1. Backup power variant - Full Backup
    2. Automatic switch to backup power with Fronius Backup Controller 3P-35A incl. backup power circuits and 3-pin separation, e.g., Austria or Australia

    Parallel Backup

    link_horizontalLink copied

    Parallel Backup enables synchronized backup power mode for several inverters. An inverter with connected battery operates as a primary inverter (parallel backup coordinator). The primary inverter controls a maximum of four secondary inverters in the system (parallel backup supporters). After release by the parallel backup coordinator, the parallel backup supporters feed additional available PV power into the backup power circuit. In the event of backup power, this helps to cover the power demand and charge the battery on the primary inverter.

    For the configuration of Parallel Backup on the primary inverter or on the secondary inverters and for the I/O cable extension when using Parallel Backup, see Functions and I/Os.

    The primary inverter:
    • Controls the secondary inverters
    • Controls the Backup Controller, the Backup Switch, or a third-party switchover box
    • Supplies the mains voltage
    • Regulates the frequency routing in the backup power circuit
    Requirements for Parallel Backup:
    • The current software version is installed on the primary and secondary inverters. See Update.
    • The primary and secondary inverters share the same phase assignment.
    • The I/O cabling has been extended for parallel backup. See Connecting backup power - Full Backup
    Parallel backup coordinators can be:
    • Fronius Symo GEN24 6-10 kW Plus
    • Fronius Symo GEN24 6-12 kW Plus SC
    • Fronius Verto Plus 15-20 kW Plus
    • Fronius Verto Plus 25-33.3 kW Plus
    Parallel backup supporters can be:
    • All Fronius Symo GEN24
    • All Fronius Verto
    1. Backup power variant - Full Backup
    2. Automatic switch to backup power with Fronius Backup Controller 3P-35A incl. backup power circuits and 3-pin separation, e.g., Austria or Australia

    Rapid switch mode

    link_horizontalLink copied

    The Rapid switch mode function enables automatic disconnection from the public grid and subsequent synchronous reconnection within 20 ms.

    The Rapid switch mode function can be used together with Parallel Backup. If the functions Parallel Backup and Rapid switch mode are activated on the primary inverter, activate both functions on all secondary inverters. As such, a switchover time of < 20 ms also applies to secondary inverters.

    NOTE

    Material damage due to misconfiguration

    This can result in damage to system components.

    Only activate the Rapid switch mode function on the primary inverter in conjunction with a Fronius Backup Controller 63A.

    Only activate the Rapid switch mode function for secondary inverters if the function is also activated for the primary inverter.

    For the joint use of the Rapid switch mode and Parallel Backup functions the following inverters can be configured as parallel backup coordinators:
    • Fronius Symo GEN24 6-10 kW Plus
    • Fronius Symo GEN24 6-12 kW Plus SC
    • Fronius Verto Plus 15-20 kW Plus
    • Fronius Verto Plus 25-33.3 kW Plus
    For the joint use of the Rapid switch mode and Parallel Backup functions the following inverters can be configured as parallel backup supporters:
    • All Fronius Symo GEN24
    • All Fronius Verto
    1. Backup power variant - Full Backup

    Automatic switch to backup power including backup power circuits and 3-pin separation, e.g., Austria or Australia

    link_horizontalLink copied

    Functions

    • Measuring and transferring the required parameters for energy management and Solar.web by the Fronius Smart Meter.
    • Disconnecting from the public grid to enable operation in backup power mode if the grid parameters are outside the country-specific standards.
    • Reconnecting to the public grid when the grid parameters are within the limits specified by the country-specific standards.
    • Option of having a separate backup power circuit or several backup power circuits that are supplied even during failure of the public grid. The total load of the backup power circuits must not exceed the nominal output of the inverter. Furthermore, the performance of the connected battery must also be considered.
    1. Backup power variant - Full Backup
    2. Automatic switch to backup power including backup power circuits and 3-pin separation, e.g., Austria or Australia

    Functions

    link_horizontalLink copied
    • Measuring and transferring the required parameters for energy management and Solar.web by the Fronius Smart Meter.
    • Disconnecting from the public grid to enable operation in backup power mode if the grid parameters are outside the country-specific standards.
    • Reconnecting to the public grid when the grid parameters are within the limits specified by the country-specific standards.
    • Option of having a separate backup power circuit or several backup power circuits that are supplied even during failure of the public grid. The total load of the backup power circuits must not exceed the nominal output of the inverter. Furthermore, the performance of the connected battery must also be considered.
    1. Backup power variant - Full Backup
    2. Automatic switch to backup power including backup power circuits and 3-pin separation, e.g., Austria or Australia

    Transitioning from grid power feed operation to backup power mode

    link_horizontalLink copied
    1. The public grid is monitored by the inverter's internal grid and system protection unit and by the Fronius Smart Meter connected to it.
    2. Failure of the public grid.
    3. The inverter carries out the measures necessary according to the country standard and then switches off.
      Contactor K1 drops out. This disconnects the backup power circuits and the inverter from the rest of the home network and from the public grid, as the main contacts of contactor K1 open. The inverter activates relay K3, which interrupts the supply to contactor K1. This prevents unintentional activation of contactor K1 and thus a grid connection when voltage is restored in the grid. The NC auxiliary contacts of contactor K1 send feedback to the inverter that the contactor is open (a condition for starting backup power mode).
    4. The NO contact of relay K3 gives additional feedback to the inverter on whether the locking was successfully performed by relay K3.
    5. The inverter decides based on the contactor's feedback as well as the measurements on the inverter terminals that the backup power mode can be activated.
    6. After all the required activation tests have been carried out, the inverter starts backup power mode.
    7. All loads in the backup power circuits are supplied with power. The remaining loads are not supplied with power and are safely isolated.
    1. Backup power variant - Full Backup
    2. Automatic switch to backup power including backup power circuits and 3-pin separation, e.g., Austria or Australia

    Transitioning from backup power mode to grid power feed operation

    link_horizontalLink copied
    1. The inverter is operating in backup power mode. Contactor K1 to the public grid is open.
    2. Public grid available again.
    3. The Fronius Smart Meter monitors the grid parameters on the public grid and passes this information to the inverter.
    4. The stability of the restored public grid is determined by checking the measured values of the Fronius Smart Meter.
    5. The inverter ends backup power mode and disconnects the outputs.
    6. The inverter deactivates K3. Contactor K1 is reactivated.
    7. All circuits are reconnected to the public grid and are supplied by the grid. The inverter does not feed anything into the grid at this time.
    8. The inverter can start grid power feed operation again after performing the grid checks required by the relevant standard.
    1. Backup power variant - Full Backup

    Automatic switch to backup power mode, all-pin disconnection, e.g., in Germany with Fronius Backup Controller 3PN-35A

    link_horizontalLink copied

    Functions

    IMPORTANT!
    Depending on the installation, the entire house or only selected circuits are supplied with backup power if the public grid fails. The total load of the backup power circuits must not exceed the rated power of the inverter. Note the capacity of the connected battery. When using the Fronius Backup Controller 3PN-35A, the data communication area may be loaded with additional loads up to max. 3 W.

    • Disconnects from the public grid after the required FRT time if the grid parameters are outside the country-specific standards in order to enable backup power mode.
    • Reconnects to the public grid if the grid parameters are within the limits of the country-specific standards.
    • Establish a correct ground connection for backup power mode to ensure the functions of the protective devices.
    • Possibility of a separate backup power circuit or several backup power circuits, which are also supplied during a failure of the public grid. The total load of the backup power circuits must not exceed the rated power of the inverter. The capacity of the connected battery must also be taken into account.
    1. Backup power variant - Full Backup
    2. Automatic switch to backup power mode, all-pin disconnection, e.g., in Germany with Fronius Backup Controller 3PN-35A

    Functions

    link_horizontalLink copied

    IMPORTANT!
    Depending on the installation, the entire house or only selected circuits are supplied with backup power if the public grid fails. The total load of the backup power circuits must not exceed the rated power of the inverter. Note the capacity of the connected battery. When using the Fronius Backup Controller 3PN-35A, the data communication area may be loaded with additional loads up to max. 3 W.

    • Disconnects from the public grid after the required FRT time if the grid parameters are outside the country-specific standards in order to enable backup power mode.
    • Reconnects to the public grid if the grid parameters are within the limits of the country-specific standards.
    • Establish a correct ground connection for backup power mode to ensure the functions of the protective devices.
    • Possibility of a separate backup power circuit or several backup power circuits, which are also supplied during a failure of the public grid. The total load of the backup power circuits must not exceed the rated power of the inverter. The capacity of the connected battery must also be taken into account.
    1. Backup power variant - Full Backup
    2. Automatic switch to backup power mode, all-pin disconnection, e.g., in Germany with Fronius Backup Controller 3PN-35A

    Transition from grid power feed operation to backup power mode

    link_horizontalLink copied
    1. The public grid is monitored by the inverter's internal grid and system protection and by the connected Fronius Smart Meter.
    2. Failure of the public grid.
    3. The inverter takes the necessary measures according to the country standard and then switches off.
      The Fronius Backup Controller disconnects the backup power circuits and the inverter from the rest of the home network and from the public grid at all pins. A multiple connection is also established between the neutral conductor and the ground conductor.
    4. Based on the feedback from the Fronius Backup Controller and the measurements at the inverter terminals, the inverter decides that backup power mode can be started.
    5. After all required connection tests have been carried out, the inverter starts in backup power mode.
    6. All loads that are in the backup power circuits are supplied. The remaining loads are not supplied and are safely disconnected.
    1. Backup power variant - Full Backup
    2. Automatic switch to backup power mode, all-pin disconnection, e.g., in Germany with Fronius Backup Controller 3PN-35A

    Transition from backup power mode to grid power feed operation

    link_horizontalLink copied
    1. The inverter is operating in backup power mode. The backup power circuits are disconnected from the public grid.
    2. Public grid is available again.
    3. The Fronius Smart Meter measures the grid parameters on the public grid and passes this information on to the inverter.
    4. The stability of the restored public grid is determined by checking the measured values of the Fronius Smart Meter.
    5. The inverter ends backup power mode and de-energizes the outputs.
    6. The inverter gives the Fronius Backup Controller approval to reconnect to the public grid.
    7. All backup power circuits are reconnected to the public grid by the Fronius Backup Controller.
    8. Once the grid checks required by the applicable standards have been performed, the inverter can start feeding power into the grid again.
    1. Backup power variant - Full Backup

    Automatic switch to backup power all-pin separation, e.g., Germany, France, Spain

    link_horizontalLink copied

    Functions

    • Measuring and transferring the required parameters for energy management and Solar.web by the Fronius Smart Meter.
    • Disconnecting from the public grid to enable operation in backup power mode if the grid parameters are outside the country-specific standards.
    • Reconnecting to the public grid when the grid parameters are within the limits specified by the country-specific standards.
    • Establishing a proper ground connection for backup power mode to ensure the protection devices function correctly.
    • Option of having a separate backup power circuit or several backup power circuits that are supplied even during failure of the public grid. The total load of the backup power circuits must not exceed the rated power of the inverter. Furthermore, the performance of the connected battery must also be considered.
    1. Backup power variant - Full Backup
    2. Automatic switch to backup power all-pin separation, e.g., Germany, France, Spain

    Functions

    link_horizontalLink copied
    • Measuring and transferring the required parameters for energy management and Solar.web by the Fronius Smart Meter.
    • Disconnecting from the public grid to enable operation in backup power mode if the grid parameters are outside the country-specific standards.
    • Reconnecting to the public grid when the grid parameters are within the limits specified by the country-specific standards.
    • Establishing a proper ground connection for backup power mode to ensure the protection devices function correctly.
    • Option of having a separate backup power circuit or several backup power circuits that are supplied even during failure of the public grid. The total load of the backup power circuits must not exceed the rated power of the inverter. Furthermore, the performance of the connected battery must also be considered.
    1. Backup power variant - Full Backup
    2. Automatic switch to backup power all-pin separation, e.g., Germany, France, Spain

    Transitioning from grid power feed operation to backup power mode

    link_horizontalLink copied
    1. The public grid is monitored by the inverter's internal grid and system protection unit and by the Fronius Smart Meter connected to it.
    2. Failure of the public grid.
    3. The inverter carries out the necessary measures according to the country standard and then switches off.
      Contactors K1, K4, and K5 drop out. This disconnects the backup power circuits and the inverter from the rest of the home network and from the public grid, as the main contacts of contactor K1 open (all-pin). The NC auxiliary contacts of contactor K1 send feedback to the inverter that the contactor is open (a condition for starting backup power mode).
    4. The NC main contacts of contactors K4 and K5 are closed, establishing a connection between the neutral conductor and the ground conductor. The two other NC main contacts of contactors K4 and K5 give feedback to the inverter that the ground connection has been established correctly (a condition for starting backup power mode).
    5. The inverter activates relay K3, which interrupts the supply to contactors K1, K4, and K5. This prevents unintentional activation of contactors K1, K4, and K5 and thus a grid connection when voltage is restored in the grid.
    6. The NO contact of relay K3 gives additional feedback to the inverter on whether the locking was successfully performed by relay K3.
    7. The inverter decides based on the contactors' feedback as well as the measurements on the inverter terminals that the backup power mode can be started.
    8. After all the required activation tests have been carried out, the inverter starts backup power mode.
    9. All loads in the backup power circuits are supplied with power. The remaining loads are not supplied with power and are safely isolated.
    1. Backup power variant - Full Backup
    2. Automatic switch to backup power all-pin separation, e.g., Germany, France, Spain

    Transitioning from backup power mode to grid power feed operation

    link_horizontalLink copied
    1. The inverter is operating in backup power mode. Contactor K1 to the public grid is open.
    2. Public grid available again.
    3. The Fronius Smart Meter monitors the grid parameters on the public grid and passes this information to the inverter.
    4. The stability of the restored public grid is determined by checking the measured values of the Fronius Smart Meter.
    5. The inverter ends backup power mode and disconnects the outputs.
    6. The inverter deactivates K3. Power is restored to contactors K1, K4, and K5.
    7. All circuits are reconnected to the public grid and are supplied by the grid. The inverter does not feed anything into the grid at this time.
    8. The inverter can start grid power feed operation again after performing the grid checks required by the relevant standard.
    1. Backup power variant - Full Backup

    Automatic switch to backup power all-pin separation, Italy

    link_horizontalLink copied

    Functions

    • Measuring and transferring the required parameters for energy management and Solar.web by the Fronius Smart Meter.
    • Monitoring of the voltage and frequency grid parameters by the inverter.
    • Disconnecting from the public grid to enable operation in backup power mode if the grid parameters are outside the country-specific standards.
    • Reconnecting to the public grid when the grid parameters are within the limits specified by the country-specific standards.
    • Establishing a correct ground connection for backup power mode.
    • Option of having a separate backup power circuit or several backup power circuits that are supplied even during failure of the public grid. The total load of the backup power circuits must not exceed the nominal output of the inverter. Furthermore, the performance of the connected battery must also be considered.
    1. Backup power variant - Full Backup
    2. Automatic switch to backup power all-pin separation, Italy

    Functions

    link_horizontalLink copied
    • Measuring and transferring the required parameters for energy management and Solar.web by the Fronius Smart Meter.
    • Monitoring of the voltage and frequency grid parameters by the inverter.
    • Disconnecting from the public grid to enable operation in backup power mode if the grid parameters are outside the country-specific standards.
    • Reconnecting to the public grid when the grid parameters are within the limits specified by the country-specific standards.
    • Establishing a correct ground connection for backup power mode.
    • Option of having a separate backup power circuit or several backup power circuits that are supplied even during failure of the public grid. The total load of the backup power circuits must not exceed the nominal output of the inverter. Furthermore, the performance of the connected battery must also be considered.
    1. Backup power variant - Full Backup
    2. Automatic switch to backup power all-pin separation, Italy

    Transitioning from grid power feed operation to backup power mode

    link_horizontalLink copied
    1. The public grid is monitored by the inverter's internal grid and system protection unit and by an external grid and system protection unit.
    2. Failure of the public grid
    3. The inverter carries out the measures necessary according to the country standard and then switches off.
    4. The external grid and system protection unit opens contactors K1 and K2 for grid monitoring. This disconnects the backup power circuits and the inverter from the rest of the home network and from the public grid, as the main contacts of contactors K1 and K2 open (all-pin). To ensure that the public grid has definitely been disconnected, the NC auxiliary contacts of contactor K1 give feedback to the external grid and system protection unit.
    5. The NC main contacts of contactors K4 and K5 are closed, establishing a connection between the neutral conductor and the ground conductor. The two other NC main contacts of contactors K4 and K5 give feedback to the inverter that the ground connection has been established correctly.
    6. The inverter activates relay K3, which activates the remote input of the external grid and system protection unit via an NC contact. This prevents a connection to the public grid when voltage is restored in the grid.
    7. The NO contact of relay K3 gives additional feedback to the inverter on whether the locking was successfully performed by relay K3.
    8. The inverter decides based on the contactor's feedback as well as the measurement on the inverter terminals that the backup power mode can be activated.
    9. The inverter starts backup power mode after a defined checking period.
    10. All loads in the backup power circuits are supplied with power. The remaining loads are not supplied with power and are safely isolated.
    1. Backup power variant - Full Backup
    2. Automatic switch to backup power all-pin separation, Italy

    Transitioning from backup power mode to grid power feed operation

    link_horizontalLink copied
    1. The inverter is operating in backup power mode. The contactors K1 and K2 to the public grid are open.
    2. Public grid available again.
    3. The Fronius Smart Meter monitors the grid parameters on the public grid and passes this information to the inverter.
    4. The stability of the restored public grid is determined by checking the measured values of the Fronius Smart Meter.
    5. On the basis of adjustments that have been carried out, the inverter ends backup power mode and disconnects the outputs.
    6. The inverter deactivates K3. Power is restored to contactors K1, K2, K4, and K5.
    7. All circuits are reconnected to the public grid and are supplied by the grid. The inverter does not feed anything into the grid at this time.
    8. The inverter can start grid power feed operation again after performing the grid checks required by the relevant standard.
    1. Backup power variant - Full Backup

    Manual switch to backup power 3-pin separation, e.g., Austria / all-pin separation, e.g., Germany

    link_horizontalLink copied

    Functions

    • Measuring and transferring the required parameters for energy management and Solar.web by the Fronius Smart Meter.
    • Monitoring of the grid parameters by the inverter.
    • Possibility of manual separation from the public grid if it fails or is deemed unstable.
    • Option of having a separate backup power circuit or several backup power circuits that are supplied even during failure of the public grid. The total load of the backup power circuits must not exceed the rated power of the inverter. Furthermore, the performance of the connected battery must also be considered.
    • If, in the event of a public grid failure, there is no manual switch to backup power mode within the first 10 minutes, this may cause the inverter and the battery to shut down. In order to then start backup power mode, manual switching must take place and a manual system start must be performed, if necessary (see chapter Manual system start on page (→)).
    • It is possible to manually reconnect the inverter and loads in the backup power circuit to the public grid once it is deemed to be stable again. The inverter only starts feed-in mode once the required grid monitoring time has passed.
    1. Backup power variant - Full Backup
    2. Manual switch to backup power 3-pin separation, e.g., Austria / all-pin separation, e.g., Germany

    Functions

    link_horizontalLink copied
    • Measuring and transferring the required parameters for energy management and Solar.web by the Fronius Smart Meter.
    • Monitoring of the grid parameters by the inverter.
    • Possibility of manual separation from the public grid if it fails or is deemed unstable.
    • Option of having a separate backup power circuit or several backup power circuits that are supplied even during failure of the public grid. The total load of the backup power circuits must not exceed the rated power of the inverter. Furthermore, the performance of the connected battery must also be considered.
    • If, in the event of a public grid failure, there is no manual switch to backup power mode within the first 10 minutes, this may cause the inverter and the battery to shut down. In order to then start backup power mode, manual switching must take place and a manual system start must be performed, if necessary (see chapter Manual system start on page (→)).
    • It is possible to manually reconnect the inverter and loads in the backup power circuit to the public grid once it is deemed to be stable again. The inverter only starts feed-in mode once the required grid monitoring time has passed.
    1. Backup power variant - Full Backup
    2. Manual switch to backup power 3-pin separation, e.g., Austria / all-pin separation, e.g., Germany

    Transition from grid power feed operation to backup power mode

    link_horizontalLink copied
    1. The public grid is monitored by the inverter's internal grid and system protection and by the connected Fronius Smart Meter.
    2. Failure of the public grid.
    3. The inverter takes the necessary measures according to the country standard and then switches off.
    4. The user switches the Fronius Backup Switch from switch position 1 (grid operation) via switch position 0 to switch position 2 (backup power mode). This disconnects the backup power circuits and the inverter from the rest of the home network and from the public grid. In the case of all-pole disconnection, the connection of ground conductor and neutral conductor is also made via the main contacts of the switch. Switch position 2 (backup power mode) is fed back to the inverter via a main contact of the Fronius Backup Switch. In addition, when the Fronius Backup Switch switches via switch position 0, the WSD line is interrupted. This causes the inverter to switch off immediately. This behavior is ensured via 2 contacts. The communication between the inverter and the Fronius Smart Meter is optionally prevented via a contact. The suspended communication prevents automatic termination of backup power mode when power returns to the public grid. The inverter then remains in backup power mode until it is manually switched back again.
    5. Based on the feedback for switch position 2 and the measurements at the inverter terminals, the inverter decides that backup power mode can be started.
    6. After all required connection tests have been carried out, the inverter starts in backup power mode.
    7. All loads that are in the backup power circuits are supplied. The remaining loads are not supplied and are safely disconnected.
    1. Backup power variant - Full Backup
    2. Manual switch to backup power 3-pin separation, e.g., Austria / all-pin separation, e.g., Germany

    Transition from backup power mode to grid power feed operation

    link_horizontalLink copied
    1. The inverter is operating in backup power mode. The Fronius Backup Switch is in switch position 2 (backup power mode).
    2. Public grid available again.
    3. The user switches the Fronius Backup Switch from switch position 2 (backup power mode) via switch position 0 to switch position 1 (grid operation). When switching via switch position 0, the inverter switches off immediately. This is ensured by the Fronius Backup Switch. In order to protect sensitive loads, it is recommended to remain in the zero position for at least 1 second during the switchover process from backup power mode to the public grid.
    4. The inverter is connected to the entire home network and to the public grid again.
    5. Communication between the inverter and the Fronius Smart Meter is restored.
    6. Once the grid checks required by the applicable standards have been performed, the inverter can start feeding power into the grid again.

    Installation

    link_horizontalLink copied

    General

    Tools required

    Illustration showing the tools required for the installation and commissioning of the inverter
    • Spirit level
    • Pencil
    • TX20 screwdriver
    • Hex socket torque wrench 5 mm
    • Torque wrench M32, M50
    • Wire stripper for cables and wires
    • Multimeter for measuring voltage
    • Smartphone, tablet, or PC for setting up the inverter
    • Drill driver
    1. Installation

    General

    link_horizontalLink copied

    Tools required

    Illustration showing the tools required for the installation and commissioning of the inverter
    • Spirit level
    • Pencil
    • TX20 screwdriver
    • Hex socket torque wrench 5 mm
    • Torque wrench M32, M50
    • Wire stripper for cables and wires
    • Multimeter for measuring voltage
    • Smartphone, tablet, or PC for setting up the inverter
    • Drill driver
    1. Installation
    2. General

    Tools required

    link_horizontalLink copied
    Illustration showing the tools required for the installation and commissioning of the inverter
    • Spirit level
    • Pencil
    • TX20 screwdriver
    • Hex socket torque wrench 5 mm
    • Torque wrench M32, M50
    • Wire stripper for cables and wires
    • Multimeter for measuring voltage
    • Smartphone, tablet, or PC for setting up the inverter
    • Drill driver
    1. Installation
    2. General

    Quick-fastener system

    link_horizontalLink copied

    Captive screws (1) are used on the housing for fitting or removing the connection area cover. To fit the connection area cover, rotate the screws by half a turn (180°) into the quick-fastener spring (2).

    Close the quick-fastener system (3) using a screwdriver (TX20) and a torque of 0.5-5 Nm.

    NOTE

    Danger when using a drill driver.

    This may result in the destruction of the quick-fastener system due to overtorque.

    Use a screwdriver (TX20).

    Do not turn the screws more than 180°.

    1. Installation
    2. General

    System component compatibility

    link_horizontalLink copied

    All installed components in the PV system must be compatible with each other and have the necessary configuration options. The installed components must not restrict or negatively affect the functioning of the PV system.

    NOTE

    Risk due to components in the PV system that are not and/or only partially compatible.

    Incompatible components can restrict and/or negatively affect the operation and/or functioning of the PV system.

    Only install components recommended by the manufacturer in the PV system.

    Before installation, check the compatibility of components that have not been expressly recommended with the manufacturer.

    1. Installation

    Installation location and position

    link_horizontalLink copied

    Choosing the location of the inverter

    Please observe the following criteria when choosing a location for the inverter:

     

    Only install on a solid, non-flammable surface.

     

    When installing the inverter in a switch cabinet or similar closed environment, ensure adequate heat dissipation by forced-air ventilation.

    When installing the inverter on the outer walls of cattle sheds, it is important to maintain a minimum clearance of 2 m between all sides of the inverter and the ventilation and building openings.

    The following substrates are allowed:
    • Wall installation: Corrugated sheet metal (mounting rails), brick, concrete, or other non-flammable surfaces sufficiently capable of bearing loads
    • Mast or beam: Mounting rails, behind the PV modules directly on the PV mounting system
    • Flat roof (if this is for a film roof, make sure that the films comply with the fire protection requirements and are not highly flammable. Ensure compliance with the national provisions.)
    • Covered parking lot roof (no overhead installation)

    The inverter is suitable for indoor installation.

    The inverter is suitable for outdoor installation.

    Due to its IP 66 protection class, the inverter is not susceptible to water spray from any direction.

    Do not expose the inverter to direct sunlight in order to keep inverter heating as low as possible.

    The inverter should be installed in a protected location, e.g., near the PV modules or under an overhanging roof.

    The inverter must not be installed or operated at more than 4 000 m above sea level.

    The voltage UDCmax must not exceed the following values:
    • Verto 15.0 - 20.0 Plus
      • between 0 and 3000 m: 1000 V
      • between 3001 and 3500 m: 959 V
      • between 3501 and 4000 m: 909 V
      • over 4001: not allowed
    • Verto 25.0 - 33.3 Plus
      • between 0 and 2700 m: 1000 V
      • between 2701 and 3500 m: 922 V
      • between 3501 and 4000 m: 873 V
      • over 4001: not allowed
    Do not install the inverter:
    • Where it may be exposed to ammonia, corrosive gases, acids or salts (e.g., fertilizer storage areas, vent openings for livestock stables, chemical plants, tanneries, etc.)

    During certain operating phases the inverter may produce a slight noise. For this reason it should not be installed in an occupied living area.

    Do not install the inverter in:
    • Areas where there is an increased risk of accidents from farm animals (horses, cattle, sheep, pigs, etc.)
    • Stables or adjoining areas
    • Storage areas for hay, straw, chaff, animal feed, fertilizers, etc.

    The inverter is designed to be dust-proof (IP 66). In areas of high dust accumulation, dust deposits may collect on the cooling surfaces, and thus impair the thermal performance. In this case, cleaning is required regularly. We therefore recommend not installing the inverter in areas and environments with high dust accumulation.

    Do not install the inverter in:
    • Greenhouses
    • Storage or processing areas for fruit, vegetables, or viticulture products
    • Areas used in the preparation of grain, green fodder, or animal feeds
    1. Installation
    2. Installation location and position

    Choosing the location of the inverter

    link_horizontalLink copied

    Please observe the following criteria when choosing a location for the inverter:

     

    Only install on a solid, non-flammable surface.

     

    When installing the inverter in a switch cabinet or similar closed environment, ensure adequate heat dissipation by forced-air ventilation.

    When installing the inverter on the outer walls of cattle sheds, it is important to maintain a minimum clearance of 2 m between all sides of the inverter and the ventilation and building openings.

    The following substrates are allowed:
    • Wall installation: Corrugated sheet metal (mounting rails), brick, concrete, or other non-flammable surfaces sufficiently capable of bearing loads
    • Mast or beam: Mounting rails, behind the PV modules directly on the PV mounting system
    • Flat roof (if this is for a film roof, make sure that the films comply with the fire protection requirements and are not highly flammable. Ensure compliance with the national provisions.)
    • Covered parking lot roof (no overhead installation)

    The inverter is suitable for indoor installation.

    The inverter is suitable for outdoor installation.

    Due to its IP 66 protection class, the inverter is not susceptible to water spray from any direction.

    Do not expose the inverter to direct sunlight in order to keep inverter heating as low as possible.

    The inverter should be installed in a protected location, e.g., near the PV modules or under an overhanging roof.

    The inverter must not be installed or operated at more than 4 000 m above sea level.

    The voltage UDCmax must not exceed the following values:
    • Verto 15.0 - 20.0 Plus
      • between 0 and 3000 m: 1000 V
      • between 3001 and 3500 m: 959 V
      • between 3501 and 4000 m: 909 V
      • over 4001: not allowed
    • Verto 25.0 - 33.3 Plus
      • between 0 and 2700 m: 1000 V
      • between 2701 and 3500 m: 922 V
      • between 3501 and 4000 m: 873 V
      • over 4001: not allowed
    Do not install the inverter:
    • Where it may be exposed to ammonia, corrosive gases, acids or salts (e.g., fertilizer storage areas, vent openings for livestock stables, chemical plants, tanneries, etc.)

    During certain operating phases the inverter may produce a slight noise. For this reason it should not be installed in an occupied living area.

    Do not install the inverter in:
    • Areas where there is an increased risk of accidents from farm animals (horses, cattle, sheep, pigs, etc.)
    • Stables or adjoining areas
    • Storage areas for hay, straw, chaff, animal feed, fertilizers, etc.

    The inverter is designed to be dust-proof (IP 66). In areas of high dust accumulation, dust deposits may collect on the cooling surfaces, and thus impair the thermal performance. In this case, cleaning is required regularly. We therefore recommend not installing the inverter in areas and environments with high dust accumulation.

    Do not install the inverter in:
    • Greenhouses
    • Storage or processing areas for fruit, vegetables, or viticulture products
    • Areas used in the preparation of grain, green fodder, or animal feeds
    1. Installation
    2. Installation location and position

    Choosing the location of third-party batteries

    link_horizontalLink copied

    IMPORTANT!
    Refer to the manufacturer's documents for specifications regarding the suitable location of third-party batteries.

    1. Installation
    2. Installation location and position

    Installation position of inverter

    link_horizontalLink copied

    The inverter is suitable for vertical installation on a vertical wall or column.

    Do not install the inverter:
    • At an angle
    • In the horizontal position
    • With the connection sockets facing upwards
    • On a base

    The inverter is suitable for a horizontal installation position or for installation on a sloping surface.

    Do not install the inverter:
    • On a sloping surface with the connection sockets facing upwards
    • Overhanging with the connection sockets facing down
    • On the ceiling
    1. Installation

    Installing the mounting bracket and attaching the inverter

    link_horizontalLink copied

    Selecting the mounting material

    Use the corresponding fixing materials depending on the subsurface and observe the screw dimension recommendations for the mounting bracket.
    The installer is responsible for selecting the right type of fixing.

    1. Installation
    2. Installing the mounting bracket and attaching the inverter

    Selecting the mounting material

    link_horizontalLink copied

    Use the corresponding fixing materials depending on the subsurface and observe the screw dimension recommendations for the mounting bracket.
    The installer is responsible for selecting the right type of fixing.

    1. Installation
    2. Installing the mounting bracket and attaching the inverter

    Properties of the mounting bracket

    link_horizontalLink copied

    The mounting bracket (illustration) can also be used as a guide.

    The pre-drilled holes on the mounting bracket are intended for screws with a thread diameter of 6-8 mm (0.24-0.32 inches).

    Unevenness on the installation surface (for example, coarse-grained plaster) is largely counterbalanced by the mounting bracket.

    The mounting bracket must be fixed to the four outer tabs (marked in green). The four inner tabs (marked in orange) can be used in addition if required.

    1. Installation
    2. Installing the mounting bracket and attaching the inverter

    Do not deform the mounting bracket

    link_horizontalLink copied

    NOTE

    When attaching the mounting bracket to the wall or to a column, make sure that the mounting bracket is not deformed.

    A deformed mounting bracket may make it difficult to clip/swivel the inverter into position.

    1. Installation
    2. Installing the mounting bracket and attaching the inverter

    Fitting the mounting bracket to a wall

    link_horizontalLink copied

    IMPORTANT!
    When installing the mounting bracket, make sure that it is installed with the arrow pointing upwards.

    1
    1. Installation
    2. Installing the mounting bracket and attaching the inverter

    Attaching the inverter to the mounting bracket

    link_horizontalLink copied

    There are integrated grips on the side of the inverter which facilitate lifting/attaching.

     

    1

    Clip the inverter into the mounting bracket from above. The connections must point downwards.

    Push the lower part of the inverter into the snap-in tabs of the mounting bracket until the inverter audibly clicks into place on both sides.

    Check that the inverter is correctly positioned on both sides.

    1. Installation

    Requirements for connecting the inverter

    link_horizontalLink copied

    Connecting aluminum cables

    Aluminum cables can also be connected to the AC connections.

    NOTE

    When using aluminum cables:

    Follow all national and international guidelines regarding the connection of aluminum cables.

    Grease aluminum wires with appropriate grease to protect them from oxidation.

    Follow the instructions of the cable manufacturer.

    1. Installation
    2. Requirements for connecting the inverter

    Connecting aluminum cables

    link_horizontalLink copied

    Aluminum cables can also be connected to the AC connections.

    NOTE

    When using aluminum cables:

    Follow all national and international guidelines regarding the connection of aluminum cables.

    Grease aluminum wires with appropriate grease to protect them from oxidation.

    Follow the instructions of the cable manufacturer.

    1. Installation
    2. Requirements for connecting the inverter

    Different cable types

    link_horizontalLink copied

    Solid

    Fine-stranded

    Fine-stranded with ferrule and collar

    Fine-stranded with ferrule without collar

    Sectoral

    1. Installation
    2. Requirements for connecting the inverter

    Permitted cables for the electrical grid connection

    link_horizontalLink copied

    Round copper or aluminum conductors with a cross-section of 4 to 35 mm2 can be connected to the terminals of the inverter as described below.

    The torques according to the following table must be observed:

    Cross-section

    Copper

    Aluminum

    35 mm2

    10 Nm

    10 Nm

    14 Nm

    14 Nm

    25 mm2

    8 Nm

    8 Nm

    12 Nm

    10 Nm

    16 mm2

    10 Nm

    10 mm2

    6 Nm

    6 Nm

    6 mm2

    4 mm2

    The grounding must be established with a 6 mm² copper or 16 mm2 aluminum cable as a minimum requirement.

    1. Installation
    2. Requirements for connecting the inverter

    Permitted cables for the electrical DC connection

    link_horizontalLink copied

    Round copper conductors with a cross section of 4-10 mm² can be connected to the MC4 plugs of the inverter.

    Select a sufficiently large cable cross-section based on the actual device output and the installation situation! Observe the data sheet for the plug!

    1. Installation
    2. Requirements for connecting the inverter

    Permitted cables for the electrical BAT connection

    link_horizontalLink copied
    The inverter is provided with 2 MC4-Evo stor plugs for the electrical BAT connection:
    • Plug set MC4 EVO STO 6 mm² - 44.0240.4466,IK
    • Plug set MC4 EVO STO 10 mm² - 44.0240.6688,IK

    Copper conductors with a cross-section of 6 mm² or 10 mm² are to be used for these plugs. Only connecting cables with a flexible stranded wire structure of classes 5 or 6 may be connected. Use only tin-plated copper cables.

    1. Installation
    2. Requirements for connecting the inverter

    Permitted cables for the data communication connection

    link_horizontalLink copied

    Connect round copper conductors to the terminals of the inverter as described below.

    IMPORTANT!
    If several single conductors are connected to an input of the terminal, connect the single conductors with a corresponding ferrule.

    WSD connections

    Distance

    Stripping length

    Cable recommendation

    100 m 109 yd

    10 mm
    0.39 inches

    0.14 - 1.5 mm2
    AWG 26 - 16

    0.14 - 1.5 mm2
    AWG 26 - 16

    0.14 - 1 mm2
    AWG 26 - 18

    0.14 - 1.5 mm2
    AWG 26 - 16

    Min. CAT 5 UTP (unshielded twisted pair)

    Modbus connections

    Distance

    Stripping length

    Cable recommendation

    300 m 328 yd

    10 mm 
    0.39 inches

    0.14 - 1.5 mm2
    AWG 26 - 16

    0.14 - 1.5 mm2
    AWG 26 - 16

    0.14 - 1 mm2
    AWG 26 - 18

    0.14 - 1.5 mm2
    AWG 26 - 16

    Min. CAT 5 STP (shielded twisted pair)

    IO connections

    Distance

    Stripping length

    Cable recommendation

    30 m
    32 yd

    10 mm 
    0.39 inches

    0.14 - 1.5 mm2
    AWG 26 - 16

    0.14 - 1.5 mm2
    AWG 26 - 16

    0.14 - 1 mm2
    AWG 26 - 18

    0.14 - 1.5 mm2
    AWG 26 - 16

    Single conductors possible

    LAN connections

    Fronius recommends using at least CAT 5 STP (shielded twisted pair) cables and a maximum distance of 100 m (109 yd).

    1. Installation
    2. Requirements for connecting the inverter

    Cable diameter of the AC cable

    link_horizontalLink copied

    For a standard M32 cable gland with a large reducer (green):
    Cable diameter from 12-14 mm

    For a standard M32 cable gland with a small reducer (red):
    Cable diameter from 17-19 mm

    For a standard M32 cable gland without a reducer:
    Cable diameter from 20.5-24.5 mm

    For an M50 cable gland:
    Cable diameter from ≤35 mm

    1. Installation
    2. Requirements for connecting the inverter

    Maximum alternating current fuse protection

    link_horizontalLink copied

    NOTE

    A residual current circuit breaker for the AC connecting cable may be required depending on national regulations, the grid operator, and other conditions.

    A type A residual current circuit breaker is generally sufficient in this case. Nevertheless, false alarms can be triggered for the type A residual current circuit breaker in individual cases and depending on local conditions. For this reason, Fronius recommends using a residual current circuit breaker suitable for frequency inverters with a release current of at least 100 mA, taking into account national provisions.

    Verto

    AC power

    Recommended fuse protection

    Max. fuse protection

    15.0

    15 kW

    40 A

    63 A

    17.5

    17.5 kW

    40 A

    63 A

    20.0

    20 kW

    50 A

    63 A

    25.0

    25 kW

    63 A

    63 A

    30.0

    30 kW

    63 A

    63 A

    33.3

    33.3 kW

    63 A

    63 A

    1. Installation

    Connecting the inverter to the public grid (AC side)

    link_horizontalLink copied

    Safety

    WARNING

    Danger from incorrect operation and work that is not carried out properly.

    This can result in severe personal injury and damage to property.

    Read the Installation Instructions and Operating Instructions before installing and commissioning the equipment.

    Only qualified personnel are authorized to commission the inverter and only within the scope of the respective technical regulations.

    WARNING

    Danger from grid voltage and DC voltage from PV modules that are exposed to light.

    An electric shock can be fatal.

    Prior to any connection work, ensure that the inverter is de-energized on the AC side and the DC side.

    Only an authorized electrical engineer is permitted to connect this equipment to the public grid.

    WARNING

    Danger from damaged and/or contaminated terminals.

    This can result in severe personal injury and damage to property.

    Prior to connection work, check the terminals for damage and contamination.

    Remove any contamination while the equipment is de-energized.

    Have defective terminals replaced by an authorized specialist.

    1. Installation
    2. Connecting the inverter to the public grid (AC side)

    Safety

    link_horizontalLink copied

    WARNING

    Danger from incorrect operation and work that is not carried out properly.

    This can result in severe personal injury and damage to property.

    Read the Installation Instructions and Operating Instructions before installing and commissioning the equipment.

    Only qualified personnel are authorized to commission the inverter and only within the scope of the respective technical regulations.

    WARNING

    Danger from grid voltage and DC voltage from PV modules that are exposed to light.

    An electric shock can be fatal.

    Prior to any connection work, ensure that the inverter is de-energized on the AC side and the DC side.

    Only an authorized electrical engineer is permitted to connect this equipment to the public grid.

    WARNING

    Danger from damaged and/or contaminated terminals.

    This can result in severe personal injury and damage to property.

    Prior to connection work, check the terminals for damage and contamination.

    Remove any contamination while the equipment is de-energized.

    Have defective terminals replaced by an authorized specialist.

    1. Installation
    2. Connecting the inverter to the public grid (AC side)

    Connecting the inverter to the public grid (AC side)

    link_horizontalLink copied

    It is not possible to operate the inverter in ungrounded networks, e.g., IT networks (isolated networks without ground conductor).

    In certain system configurations, it is not necessary to connect the neutral conductor. In this system configuration, the neutral conductor status parameter must be set to Not connected on the web interface of the inverter in the Device configuration > Inverter > AC grid menu.

    1

    Switch off the external automatic circuit breakers (AC and battery).
    Make sure that the DC disconnector (see DC disconnector) is set to the "Off" switch position.

    2

    Loosen the 6 screws on the connection area cover by rotating them 180° to the left using a screwdriver (TX20).
    Remove the connection area cover from the device.

    3

    Strip the insulation of the single conductors by 16 mm.
    Select the cable cross-section in accordance with the instructions in Permitted cables for the electrical grid connection from page (→).

    IMPORTANT!
    Only one conductor may be connected to each pin. With a twin ferrule, two conductors can be connected to one pin.

    4
    Connection with neutral conductor
    4
    Connection without neutral conductor

    For more information about the cable gland, see chapter Cable diameter of the AC cable on page (→).

    5
    Connection with neutral conductor
    5
    Connection without neutral conductor

    IMPORTANT! Observe torques – see Permitted cables for the electrical grid connection on page (→).

    IMPORTANT!
    The ground conductor must be dimensioned longer and laid with a movement loop so that it is last loaded in the event of a failure of the cable gland.

    L1
    Phase conductor
    L2
    Phase conductor
    L3
    Phase conductor
    N
    Neutral conductor (optional)
    PE
    Ground conductor
    6

    Fasten the union nut of the cable gland with a torque of 4 Nm.

    1. Installation
    2. Connecting the inverter to the public grid (AC side)

    Connecting the inverter to the public grid with the PEN conductor (AC side)

    link_horizontalLink copied

    It is not possible to operate the inverter in ungrounded networks, e.g., IT networks (isolated networks without ground conductor).

    1

    Switch off the external automatic circuit breakers (AC and battery).
    Make sure that the DC disconnector (see DC disconnector) is set to the "Off" switch position.

    2

    Loosen the 6 screws on the connection area cover by rotating them 180° to the left using a screwdriver (TX20).
    Remove the connection area cover from the device.

    3

    Strip the insulation of the single conductors by 16 mm.
    Select the cable cross-section in accordance with the instructions in Permitted cables for the electrical grid connection from page (→).

    IMPORTANT!
    Only one conductor may be connected to each pin. With a twin ferrule, two conductors can be connected to one pin.

    4

    For more information about the cable gland, see chapter Cable diameter of the AC cable on page (→).

    The PEN conductor must have ends that are permanently marked blue, according to the national regulations.

    Dimension the ground conductor longer and lay it with a movement loop so that it is last loaded in the event of a failure of the cable gland.

    5
    PEN conductor version: Terminal on DIN rail

    Observe torques – see Permitted cables for the electrical grid connection on page (→).

    6
    PEN conductor version: Grounding bolt
    7

    Fasten the union nut of the cable gland with a torque of 4 Nm.

    1. Installation
    2. Connecting the inverter to the public grid (AC side)

    Replacing the PG screw joint

    link_horizontalLink copied
    1. Installation

    Connecting solar module strings to the inverter

    link_horizontalLink copied

    General information about PV modules

    To enable suitable PV modules to be chosen and to use the inverter as efficiently as possible, it is important to bear the following points in mind:

    • If insolation is constant and the temperature is falling, the open circuit voltage of the PV modules will increase. The open circuit voltage must not exceed the max. permissible system voltage. An open circuit voltage above the indicated values will damage the inverter, and all warranty rights will become null and void.
    • The temperature coefficients on the data sheet of the PV modules must be observed.
    • Exact values for sizing the PV modules can be obtained using suitable calculation tools, such as the Fronius Solar.creator.

    IMPORTANT!
    Before connecting up the PV modules, check that the voltage for the PV modules specified by the manufacturer corresponds to the actual measured voltage.

    IMPORTANT!
    The PV modules connected to the inverter must comply with the IEC 61730 Class A standard.

    IMPORTANT!
    Solar module strings must not be grounded.

    1. Installation
    2. Connecting solar module strings to the inverter

    General information about PV modules

    link_horizontalLink copied

    To enable suitable PV modules to be chosen and to use the inverter as efficiently as possible, it is important to bear the following points in mind:

    • If insolation is constant and the temperature is falling, the open circuit voltage of the PV modules will increase. The open circuit voltage must not exceed the max. permissible system voltage. An open circuit voltage above the indicated values will damage the inverter, and all warranty rights will become null and void.
    • The temperature coefficients on the data sheet of the PV modules must be observed.
    • Exact values for sizing the PV modules can be obtained using suitable calculation tools, such as the Fronius Solar.creator.

    IMPORTANT!
    Before connecting up the PV modules, check that the voltage for the PV modules specified by the manufacturer corresponds to the actual measured voltage.

    IMPORTANT!
    The PV modules connected to the inverter must comply with the IEC 61730 Class A standard.

    IMPORTANT!
    Solar module strings must not be grounded.

    1. Installation
    2. Connecting solar module strings to the inverter

    Safety

    link_horizontalLink copied

    WARNING

    Danger from incorrect operation and work that is not carried out properly.

    This can result in severe personal injury and damage to property.

    The commissioning, maintenance, and service work in the inverter's power stage set may only be carried out by Fronius-trained service personnel in accordance with the technical specifications.

    Read the installation instructions and operating instructions before installing and commissioning the equipment.

    WARNING

    Danger from mains voltage and DC voltage from PV modules that are exposed to light.

    This can result in severe personal injury and damage to property.

    All connection, maintenance, and service work should only be carried out when the AC and DC sides have been disconnected from the inverter and are de-energized.

    Only an authorized electrical engineer is permitted to connect this equipment to the public grid.

    WARNING

    Danger of an electric shock due to improperly connected terminals/PV plug connectors.

    An electric shock can be fatal.

    When connecting, ensure that each pole of a string is routed via the same PV input, e.g.:
    + pole string 1 to the input PV 1.1+ and - pole string 1 to the input PV 1.1-

    WARNING

    Danger from damaged and/or contaminated terminals.

    This can result in severe personal injury and damage to property.

    Prior to connection work, check the terminals for damage and contamination.

    Remove any contamination while the equipment is de-energized.

    Have defective terminals replaced by an authorized specialist company.

    1. Installation
    2. Connecting solar module strings to the inverter

    PV Generator, general

    link_horizontalLink copied

    Several independent PV inputs are available. These inputs can be connected to a number of different modules.

    When starting for the first time, set up the PV Generator in accordance with the respective configuration (can also be carried out at a later date in the System configuration menu field under menu item Components).

    1. Installation
    2. Connecting solar module strings to the inverter

    Connecting solar module strings to the inverter

    link_horizontalLink copied
    1
    2

    Use a suitable measuring instrument to check the voltage and polarity of the DC cabling.

    CAUTION

    Danger due to polarity reversal at the terminals.

    This may result in severe damage to the inverter.

    Use a suitable measuring instrument to check the polarity of the DC cabling.

    Use a suitable measuring instrument to check the voltage (max. 1 000 VDC)

    CAUTION

    Risk of damage due to incompatible plug connectors.

    Incompatible plug connectors can cause thermal damage and may cause a fire.

    Only use the original plug connectors (MC4) from Stäubli (formerly Multi-Contact).

    3

    Connect PV cables from the solar modules to the MC4 plugs according to the label

    Unused MC4 plugs on the inverter must be closed by the cover caps supplied with the inverter.

    1. Installation

    Connecting the battery to the inverter

    link_horizontalLink copied

    Safety

    WARNING

    Danger due to incorrect operation and incorrectly performed work.

    This can result in serious injury and damage to property.

    Only a technical specialist is permitted to perform commissioning, maintenance, and service activities for inverters and batteries, and only within the scope of the technical regulations.

    Read the installation instructions and operating instructions from the respective manufacturer before installing and commissioning the equipment.

    WARNING

    Danger from mains voltage and DC voltage from the PV module that are exposed to light, as well as batteries.

    This can result in serious injury and damage to property.

    All connection, maintenance, and service work should only be carried out when the AC and DC sides have been disconnected from the inverter and battery, and are de-energized.

    Only a technical specialist is permitted to connect this equipment to the public grid.

    WARNING

    Danger from damaged and/or contaminated terminals.

    This can result in serious injury and damage to property.

    Prior to connection work, check the terminals for damage and contamination.

    Remove any contamination while the equipment is de-energized.

    Have defective terminals repaired by a technical specialist.

    1. Installation
    2. Connecting the battery to the inverter

    Safety

    link_horizontalLink copied

    WARNING

    Danger due to incorrect operation and incorrectly performed work.

    This can result in serious injury and damage to property.

    Only a technical specialist is permitted to perform commissioning, maintenance, and service activities for inverters and batteries, and only within the scope of the technical regulations.

    Read the installation instructions and operating instructions from the respective manufacturer before installing and commissioning the equipment.

    WARNING

    Danger from mains voltage and DC voltage from the PV module that are exposed to light, as well as batteries.

    This can result in serious injury and damage to property.

    All connection, maintenance, and service work should only be carried out when the AC and DC sides have been disconnected from the inverter and battery, and are de-energized.

    Only a technical specialist is permitted to connect this equipment to the public grid.

    WARNING

    Danger from damaged and/or contaminated terminals.

    This can result in serious injury and damage to property.

    Prior to connection work, check the terminals for damage and contamination.

    Remove any contamination while the equipment is de-energized.

    Have defective terminals repaired by a technical specialist.

    1. Installation
    2. Connecting the battery to the inverter

    Connecting the battery on the DC side

    link_horizontalLink copied

    CAUTION

    Danger due to operation of the battery above the permissible altitude specified by the manufacturer.

    Operating the battery above the permissible altitude can result in restricted operation, loss of operation, and unsafe states of the battery.

    Adhere to the manufacturer's instructions regarding the permissible altitude.

    Operate the battery only at the altitude specified by the manufacturer.

    IMPORTANT!
    Switch off the battery before installation. Observe the maximum DC cable length for the installation of third-party batteries according to the specifications of the manufacturer, see chapter Suitable batteries on page (→).

    * Connect the ground conductor of the battery at an external point (e.g., switch cabinet). Observe the minimum cross-section of the battery ground conductor.

    CAUTION

    Risk of damage due to incompatible plug connectors.

    Incompatible plug connectors can cause thermal damage and may cause a fire.

    Only use the original plug connectors (MC4) from Stäubli (formerly Multi-Contact).

    CAUTION

    Danger due to polarity reversal at the terminals.

    Serious damage to the PV system may result.

    Use a suitable measuring instrument to check the polarity of the DC cabling when the battery is switched on.

    Maintain the maximum voltage for the battery input (see Technical data on page (→)).

    1

    Connect the battery cable to the MC4 Evo Stor plugs according to the label. Refer to the installation instructions of the plug connector manufacturer for the exact procedure.

    Unused MC4 plugs on the inverter must be closed by the cover caps supplied with the inverter.

    CAUTION

    Danger due to overvoltage when using other slots on the terminal.

    This may result in damage to the battery and/or the PV modules due to discharge.

    Only use the slots labeled "BAT" for connecting the battery.

    Information for connection on the battery side can be found in the installation instructions from the relevant manufacturer.

    1. Installation

    Connecting backup power - Full Backup

    link_horizontalLink copied

    Safety

    WARNING

    Danger from incorrect installation, commissioning, operation, or incorrect use.

    This can result in severe personal injury/damage to property.

    Only trained and qualified personnel are authorized to install and commission the system, and only within the scope of the technical regulations.

    The Installation and Operating Instructions must be read carefully prior to use.

    If anything is unclear, contact your vendor immediately.

    IMPORTANT!
    The valid national laws, standards, and provisions, as well as the specifications of the relevant grid operator are to be taken into account and applied.
    It is highly recommended to coordinate the concrete examples implemented and in particular the specific installation with the grid operator to obtain their explicit approval. This obligation applies to system constructors in particular (e.g., installers).
    The examples suggested here show a backup power supply with or without an external protection relay (external grid and system protection unit). The respective grid operator decides whether an external protection relay must be used or not.

    IMPORTANT!
    An uninterruptible power supply (UPS) may only be used to supply individual loads (e.g., computers). Feeding into the power supply of the house network is not permitted. The Installation and Operating Instructions must be read carefully prior to use. If anything is unclear, contact your vendor immediately.

    The examples given in this document (in particular cabling variants and circuit diagrams) are suggestions only. These examples have been carefully developed and tested. They can therefore be used as a basis for real-life installation. Anyone following or using these examples does so at their own risk.

    1. Installation
    2. Connecting backup power - Full Backup

    Safety

    link_horizontalLink copied

    WARNING

    Danger from incorrect installation, commissioning, operation, or incorrect use.

    This can result in severe personal injury/damage to property.

    Only trained and qualified personnel are authorized to install and commission the system, and only within the scope of the technical regulations.

    The Installation and Operating Instructions must be read carefully prior to use.

    If anything is unclear, contact your vendor immediately.

    IMPORTANT!
    The valid national laws, standards, and provisions, as well as the specifications of the relevant grid operator are to be taken into account and applied.
    It is highly recommended to coordinate the concrete examples implemented and in particular the specific installation with the grid operator to obtain their explicit approval. This obligation applies to system constructors in particular (e.g., installers).
    The examples suggested here show a backup power supply with or without an external protection relay (external grid and system protection unit). The respective grid operator decides whether an external protection relay must be used or not.

    IMPORTANT!
    An uninterruptible power supply (UPS) may only be used to supply individual loads (e.g., computers). Feeding into the power supply of the house network is not permitted. The Installation and Operating Instructions must be read carefully prior to use. If anything is unclear, contact your vendor immediately.

    The examples given in this document (in particular cabling variants and circuit diagrams) are suggestions only. These examples have been carefully developed and tested. They can therefore be used as a basis for real-life installation. Anyone following or using these examples does so at their own risk.

    1. Installation
    2. Connecting backup power - Full Backup

    Automatic switch to backup power 3-pole disconnection e.g., Austria or Australia

    link_horizontalLink copied

    IMPORTANT! The cabling variant required by the utility must be clarified with the utility.

    Circuit diagrams
    • Fronius Backup Controller 3-pin separation, e.g., Austria.
    • Automatic switch to backup power 3-pin single FRT-capable separation - e.g., Austria.
    • Automatic switch to backup power 3-pin single separation - e.g., Australia.
    • Fronius Backup Controller 3-pin separation, parallel backup.

    Cabling of the backup power circuits and non-backup power circuits:
    If not all the loads in the home need to be supplied in a backup power situation, the circuits need to be divided into backup power circuits and non-backup power circuits. The total load of the backup power circuits must not exceed the rated power of the inverter.

    Cabling with third-party components
    The backup power circuits and non-backup power circuits must be fused separately according to the required safety measures (e.g., residual current circuit breaker, automatic circuit breaker).
    In backup power mode, only the backup power circuits are disconnected from the grid at 3 pins by contactor K1. In this case the rest of the home network is not supplied.

    Observe the following points
    • The main contacts of contactor K1 must be installed between the Smart Meter and the inverter or the residual current circuit breaker of the backup power circuits.
    • The power supply for contactor K1 is provided by the public grid and must be connected to phase 1 (L1) and fused downstream of the Smart Meter.
    • An NC contact for relay K3 interrupts the supply voltage to contactor K1. This prevents the backup power network of the inverter from being switched to the public grid.
    • The NO contact of relay K3 gives feedback to the inverter that relay K3 has blocked the power.
    • Additional inverters or other AC sources can be installed in the backup power circuit downstream of the main contacts of K1. The sources will not synchronize with the network of the inverter because this backup power network has a frequency of 53 Hz.
    1. Installation
    2. Connecting backup power - Full Backup

    Automatic switch to backup power 4-pole disconnection e.g., Germany, France, Spain

    link_horizontalLink copied
    Circuit diagrams
    • Fronius Backup Controller 4-pin separation, e.g., Germany on page (→).
    • Automatic switch to backup power 4-pin double separation with ext. grid and system protection - e.g., Italy on page (→).
    • Automatic switch to backup power 4-pin single FRT-capable separation on page (→).
    • Automatic switch to backup power 4-pin single separation - e.g., France on page (→).
    • Automatic switch to backup power 4-pin single separation - e.g., Spain on page (→).

    Cabling of the backup power circuits and non-backup power circuits:
    If not all the loads in the home need to be supplied in a backup power situation, the circuits need to be divided into backup power circuits and non-backup power circuits. The total load of the backup power circuits must not exceed the rated power of the inverter.

    Cabling with third-party components
    The backup power circuits and non-backup power circuits must be fused separately according to the required safety measures (e.g., residual current circuit breaker, automatic circuit breaker).
    In backup power mode, only the backup power circuits are disconnected from the grid at all pins by contactor K1, and a ground connection is established for them. In this case the rest of the home network is not supplied.

    Observe the following points
    • The main contacts of contactor K1 must be installed between the Fronius Smart Meter and the inverter or the residual current circuit breakers of the backup power circuits.
    • The supply voltage for contactor K1 is provided by the public grid and must be connected to phase 1 (L1) downstream of the Fronius Smart Meter and fused accordingly.
    • To ensure residual current circuit breakers function in backup power mode, the connection between the neutral conductor and the ground conductor must be implemented in accordance with the respective circuit diagram. An NC contact is used for this purpose for each of the main contacts of contactors K4 and K5. This ensures that the ground connection is established as soon as the public grid connection is no longer available.
    • As with contactor K1, the supply voltage for contactors K4 and K5 is supplied via phase 1 (L1) of the public grid.
    • An NC contact for relay K3 interrupts the supply voltage to contactors K1, K4, and K5. This prevents the ground connection from being immediately disconnected again when power returns to the public grid and the backup power network of the inverter from being switched to the public grid.
    • The NO contact of relay K3 gives feedback to the inverter on whether relay K3 has blocked the power.
    • Additional inverters or other AC sources can be installed in the backup power circuit downstream of the main contacts of K1. The sources will not synchronize with the network of the inverter because this backup power network has a frequency of 53 Hz.
    1. Installation
    2. Connecting backup power - Full Backup

    Automatic switch to backup power 4-pole disconnection e.g., Italy

    link_horizontalLink copied
    Circuit diagram
    • Automatic switch to backup power 4-pin double separation with ext. grid and system protection - e.g., Italy on page (→).

    Cabling of the backup power circuits and non-backup power circuits:

    IMPORTANT!
    For this circuit variant, the Fronius Smart Meter WR must be used.

    The backup power circuits and non-backup power circuits must be fused separately according to the required safety measures (e.g., residual current circuit breaker, automatic circuit breaker).
    In backup power mode, only the backup power circuits are disconnected from the grid by contactors K1 and K2, and a ground connection is established for them. In this case the rest of the home network is not supplied.

    The following points regarding cabling must be considered:
    • The main contacts of contactors K1 and K2 must be installed between the Fronius Smart Meter and the residual current circuit breaker of the inverter or the residual current circuit breakers of the backup power circuits.
    • The supply voltage for contactors K1 and K2 is provided by the public grid and must be connected to phase 1 (L1) downstream of the Fronius Smart Meter and fused accordingly.
    • Actuation of contactors K1 and K2 is carried out by the external grid and system protection.
    • The external grid and system protection unit must be installed downstream of the Fronius Smart Meter. Detailed installation and wiring instructions for external grid and system protection units can be found in the unit's operating instructions.
    • The remote trip input of the external grid and system protection unit must be set to NC according to the manufacturer's operating instructions.
    • To ensure residual current circuit breakers function in backup power mode, the connection between the neutral conductor and the ground conductor must be established as close as possible to the inverter, but in any case upstream of the first residual current circuit breaker. An NC contact is used for this purpose for the main contacts of contactors K4 and K5. This ensures that the ground connection is established as soon as the public grid connection is no longer available.
    • The supply voltage for the contactors K1, K2, K4, and K5 is supplied via phase 1 (L1) of the public grid and is switched via the external grid and system protection unit.
    • An NC contact for relay K3, which activates the remote input of the external grid and system protection unit, interrupts the supply voltage to contactors K1, K2, K4, and K5. This prevents the ground connection from being immediately disconnected again when power returns to the public grid and the backup power network of the inverter from being switched to the public grid.
    • The NO contact of relay K3 gives additional feedback to the inverter on whether relay K3 has blocked the power.
    • Additional inverters or other AC sources can be installed in the backup power circuit downstream of the main contacts of K1 and K2. The sources will not synchronize with the network of the inverter because this backup power network has a frequency of 53 Hz.
    1. Installation
    2. Connecting backup power - Full Backup

    Manual switch to backup power 3-pole disconnection e.g., Austria / 4-pole disconnection e.g., Germany

    link_horizontalLink copied
    Circuit diagrams
    • Manual switch to backup power 3-pin separation, e.g., Austria on page (→).
    • Manual switch to backup power 4-pin separation, e.g., Germany on page (→).

    IMPORTANT!
    The circuit diagrams to be used must be applied in line with the country standard and the implementing regulations of the utility.

    Cabling of the backup power circuits and non-backup power circuits:
    If not all the loads in the home need to be supplied in a backup power situation, the circuits need to be divided into backup power circuits and non-backup power circuits. The total load of the backup power circuits must not exceed the rated power of the inverter.

    The backup power circuits and non-backup power circuits must be fused separately according to the required safety measures (e.g., residual current circuit breaker, automatic circuit breaker).
    In backup power mode, only the backup power circuits and the inverter are disconnected from the grid by changeover switch Q1. In the case of all-pole disconnection, a ground connection is also established. In this case, the loads in the non-backup power circuits are not supplied by the inverter.

    The following points regarding installation must be considered:
    • The changeover switch Q1 must be dimensioned for the fuses installed upstream, the max. occurring amperage, and the max. occurring short circuit current. An auxiliary switching element with 2 NO contacts is required for switch position 1 (grid operation) to match the installed changeover switch Q1.
      The changeover switch Q1 used must fulfil a short-circuit breaking capacity of at least 10 kA according to standard IEC 60947-1. If the short circuit current at the installation point reaches a value above 10 kA, a switch with a corresponding short-circuit breaking capacity must be used.
    • The circuitry is only to be used in household-like applications and systems (small businesses and agriculture) or up to upstream fuses with a nominal current of 63 A.
    • Min. impulse withstand voltage of the changeover switch of 4 kV according to IEC 60947-1.
    • It must be clarified with the utility whether the 3-pole or all-pole disconnection must be used.
    • The protective measure must be tested regularly; if this is not regulated by law, it must be performed annually.
    • Data transfer between the Fronius Smart Meter and the inverter may be interrupted in backup power mode (switch position 2). This is optionally ensured via a NO contact of the auxiliary contact. Interrupting the Smart Meter connection via auxiliary contact Q1.1 is optional and prevents the backup power function from ending when power returns to the public grid. If this does not take place, the inverter interrupts the backup power supply when power returns to the public grid. Failure to manually switch to parallel grid mode within the first 10 minutes of the power returning to the public grid may cause the inverter and battery to shut down. In this case, a manual system start must be carried out (see chapter Manual system start on page (→)). This behavior must be taken into account especially during a test of manual switching, because the inverter does not start backup power mode when there is a grid connection due to Smart Meter data being available.
    • The data communication connection with the Fronius Smart Meter must be established separately from the battery to its dedicated Modbus input so that battery data communication is maintained (see chapter Modbus participants on page (→)).
    • Feedback to the digital inputs (IOs) of the inverter via the changeover switch Q1 (switch position 2) is a starting condition for the inverter's backup power mode.
    • The AC output of the inverter is de-energized when switching via switch position 0. This is ensured by interrupting the WSD line with the 2nd NO contact of the auxiliary contact and the changeover switch Q1 in position 0.
    • The continuous connection between the equipotential bonding rail and the neutral conductor from the inverter must not be interrupted in the case of 3-pole disconnection.
    • In the case of all-pole disconnection, the PE-N conductor connection is made via the main contacts of changeover switch Q1 in duplicate.
    • Additional inverters or other AC sources can be installed in the backup power circuit downstream of the changeover switch Q1. The sources will not synchronize with the backup power network of the inverter in a backup power situation because this is operated at 53 Hz.
    1. Installation
    2. Connecting backup power - Full Backup

    Testing backup power mode

    link_horizontalLink copied
    Testing backup power mode:
    • during first-time installation and configuration
    • after working on the switch cabinet
    • during ongoing operation (recommendation: at least every 6 months)

    A battery charge of min. 30% is recommended for test mode.

    A description of how to run the test mode can be found in the checklist – Backup power (https://www.fronius.com/de/download-center?searchword=42,0426,0365).

    1. Installation

    Connecting the data communication cables

    link_horizontalLink copied

    Modbus participants

    The Modbus inputs M0 and M1 can be freely selected. A maximum of four Modbus participants can be connected to the Modbus terminal on the Modbus inputs M0 and M1.

    IMPORTANT! Only one primary meter, one battery storage system, and one Ohmpilot/Ohmpilot Eco can be connected per inverter. Secondary meters can only be configured if a primary meter is defined in the system.

    Due to the high volume of data transferred, some system components require more than one participant on the Modbus input:

    System component

    Required participants

    Primary meter/secondary meter

    1

    Ohmpilot

    1

    Ohmpilot Eco

    2

    Battery storage

    2

    Possible combination of system components per Modbus input M0/M1

     

    Required Modbus participants

    Number of different system components

    per battery storage system

    per heating solution

    available Modbus inputs*

    3 meters

    0

    0

    1

    1 battery storage system

    2

    0

    2

    1 Ohmpilot

    0

    1

    3

    1 Ohmpilot Eco

    0

    2

    2

    1 battery storage system + 1 Ohmpilot

    2

    1

    1

    1 battery storage system + 1 Ohmpilot Eco

    2

    2

    0

    * Connect one primary meter per inverter to either M0 or M1 and take it into account when assigning participants.

    If the Inverter Control via Modbus function is enabled in the Communication > Modbus menu area, no Modbus participants can be connected. The inverter can either be controlled via Modbus or query system components via Modbus. If both are necessary, use both Modbus inputs.

    Modbus variants

    Modbus 0

    Modbus 1

    Description

    System components

    System components

    System components are connected to both Modbus inputs.

    System components

    Modbus RTU

    System components with inverter control unit, see Modbus

    Modbus RTU

    System components

    System components with inverter control unit, see Modbus

    1. Installation
    2. Connecting the data communication cables

    Modbus participants

    link_horizontalLink copied

    The Modbus inputs M0 and M1 can be freely selected. A maximum of four Modbus participants can be connected to the Modbus terminal on the Modbus inputs M0 and M1.

    IMPORTANT! Only one primary meter, one battery storage system, and one Ohmpilot/Ohmpilot Eco can be connected per inverter. Secondary meters can only be configured if a primary meter is defined in the system.

    Due to the high volume of data transferred, some system components require more than one participant on the Modbus input:

    System component

    Required participants

    Primary meter/secondary meter

    1

    Ohmpilot

    1

    Ohmpilot Eco

    2

    Battery storage

    2

    Possible combination of system components per Modbus input M0/M1

     

    Required Modbus participants

    Number of different system components

    per battery storage system

    per heating solution

    available Modbus inputs*

    3 meters

    0

    0

    1

    1 battery storage system

    2

    0

    2

    1 Ohmpilot

    0

    1

    3

    1 Ohmpilot Eco

    0

    2

    2

    1 battery storage system + 1 Ohmpilot

    2

    1

    1

    1 battery storage system + 1 Ohmpilot Eco

    2

    2

    0

    * Connect one primary meter per inverter to either M0 or M1 and take it into account when assigning participants.

    If the Inverter Control via Modbus function is enabled in the Communication > Modbus menu area, no Modbus participants can be connected. The inverter can either be controlled via Modbus or query system components via Modbus. If both are necessary, use both Modbus inputs.

    Modbus variants

    Modbus 0

    Modbus 1

    Description

    System components

    System components

    System components are connected to both Modbus inputs.

    System components

    Modbus RTU

    System components with inverter control unit, see Modbus

    Modbus RTU

    System components

    System components with inverter control unit, see Modbus

    1. Installation
    2. Connecting the data communication cables

    Routing data communication cables

    link_horizontalLink copied
    IMPORTANT!
    If data communication cables are wired into the inverter, observe the following points:
    • Depending on the number and cross-section of the wired data communication cables, remove the corresponding blanking plugs from the sealing insert and insert the data communication cables.
    • Make sure that you insert the corresponding blanking plugs into any free openings on the sealing insert.

    IMPORTANT!
    Ingress protection rating IP 66 cannot be ensured if blanking plugs are missing or incorrectly inserted.

    1

    Remove the union nut on the cable gland and press the sealing ring with the blanking plugs out from the inside of the device.

    2

    Open up the sealing ring at the location where the blanking plugs are to be removed.

    * Remove the blanking plugs with a sideways motion.

    3

    First, guide the data cables through the union nut of the cable gland and then through the housing opening.

    4

    Insert the sealing ring between the union nut and the housing opening. Press the data cables into the seal's cable guide. Then press in the seal until it reaches the underside of the cable gland.

    5

    Using a cable tie, attach the data cables to the protective cover of the DC surge protection device (SPD). Fasten the union nut of the cable gland with a torque of min. 2.5 - max. 4 Nm.

    1. Installation
    2. Connecting the data communication cables

    Connecting the battery communication cable

    link_horizontalLink copied

    Battery Connection (Modbus RJ45)

    NOTE

    Power supply

    Voltage is present at the connection. If network devices (e.g., WiFi routers) are connected, the device may be damaged.

     

    Only connect batteries to the Battery Connection

    IMPORTANT!
    For this connection version, the BAT switch on Data communication area must be in position 1.

    1Knock out the protective cover
    2Connect the cable to the RJ45 socket
    ✓The LEDs on the RJ45 socket light up red when the battery connection is active.

    Modbus terminal

    IMPORTANT!
    To connect several single conductors to one input of the push-in terminals, connect the conductors with the corresponding ferrules.

    1Strip 10 mm of insulation from the single conductors and fit the ferrules if necessary.
    2

    Plug the cables into the relevant slot and check the hold of the cable.

    IMPORTANT!
    Use a twisted cable pair for data lines that belong together.

    Twist the shielding of the cable and plug it into the "SHIELD" slot.

    IMPORTANT!
    Incorrectly fitted shielding can result in interference in the data communication.

    Ihr Browser kann diesen Film leider nicht anzeigen.
    1.
    Disconnect the terminal.
    2.
    Route the data communication cable. Press in the seal until it reaches the bottom edge of the strain-relief device.

    Wiring proposal recommended by Fronius, see page (→).

    1. Installation
    2. Connecting the data communication cables

    Terminating resistors

    link_horizontalLink copied

    It may be possible for the system to function without terminating resistors. However, owing to interference, the use of terminating resistors according to the following overview is recommended for trouble-free operation.

    For permissible cables and max. distances for the data communication area, refer to the chapter headed Permitted cables for the data communication connection on page (→).

    IMPORTANT!
    Terminating resistors that are not positioned as illustrated can result in interference in the data communication.

    1. Installation
    2. Connecting the data communication cables

    Installing the WSD (wired shutdown)

    link_horizontalLink copied

    IMPORTANT!
    The push-in WSD terminal in the inverter's connection area is delivered with a bypass ex works as standard. The bypass must be removed when installing a trigger device or a WSD chain.

    The WSD switch of the first inverter with connected trigger device in the WSD chain must be in position 1 (master). The WSD switch of all other inverters should be in position 0 (secondary device).

    Max. distance between 2 devices: 100 m
    Max. Number of devices: 28

    * Floating contact of the trigger device (e.g., central grid and system protection). If several floating contacts are used in a WSD chain, these must be connected in series.

    1. Installation

    Closing and commissioning the inverter

    link_horizontalLink copied

    Closing the inverter's connection area/housing cover, and commissioning

    1

    Place the cover on the connection area. Tighten six screws by rotating them 180° to the right using a screwdriver (TX20).

    2

    Clip the housing cover into the inverter from above.
    Press on the lower part of the housing cover and tighten the 2 screws by rotating them 180° to the right using a screwdriver (TX20).

    3

    Turn the DC disconnector (see DC disconnector) to the "On" switch setting. Switch on the external automatic circuit breakers (AC and battery).

     

    4Open the WiFi access point, see chapter Button functions and LED status indicator on page (→)
    1. Installation
    2. Closing and commissioning the inverter

    Closing the inverter's connection area/housing cover, and commissioning

    link_horizontalLink copied
    1

    Place the cover on the connection area. Tighten six screws by rotating them 180° to the right using a screwdriver (TX20).

    2

    Clip the housing cover into the inverter from above.
    Press on the lower part of the housing cover and tighten the 2 screws by rotating them 180° to the right using a screwdriver (TX20).

    3

    Turn the DC disconnector (see DC disconnector) to the "On" switch setting. Switch on the external automatic circuit breakers (AC and battery).

     

    4Open the WiFi access point, see chapter Button functions and LED status indicator on page (→)
    1. Installation
    2. Closing and commissioning the inverter

    Starting the inverter for the first time

    link_horizontalLink copied

    When starting the inverter for the first time, various setup settings must be configured.

    If the setup is canceled before completion, the input data is not saved and the start screen with the installation wizard is shown once again. The data is saved in the event of an interruption, e.g., a power failure. Commissioning is continued at the point at which the interruption occurred after the power supply is restored. If the setup was interrupted, the inverter feeds energy into the grid at maximum 500 W and the operating status LED flashes yellow.

    The country setup can only be set when starting the inverter for the first time. If the country setup needs to be changed at a later date, contact your installer/technical support.

    1. Installation
    2. Closing and commissioning the inverter

    Installation with the app

    link_horizontalLink copied

    The Fronius Solar.start app is required for installation. Depending on the mobile device used to perform the installation, the app is available on the relevant platform.

    1Download and install the Fronius Solar.start app.
    2Open the access point by touching the sensor    .
    ✓Communication LED flashes blue.
    3Open the Fronius Solar.start app and follow the installation wizard. Scan the QR code on the rating plate with a smartphone or tablet to connect to the inverter.
    4Add system components in Fronius Solar.web and commission the PV system.

    The network wizard and product setup can be performed independently. A network connection is required for the Fronius Solar.web installation wizard.

    1. Installation
    2. Closing and commissioning the inverter

    Installation with the browser

    link_horizontalLink copied

    The network wizard and product setup can be performed independently. A network connection is required for the Fronius Solar.web installation wizard.

    WiFi:

    1Open the access point by touching the sensor    .
    ✓Communication LED flashes blue.
    2Establish the connection to the inverter in the network settings (the inverter is displayed with the name "FRONIUS_" and the serial number of the device).
    3Enter the password from the rating plate and confirm.
    IMPORTANT!
    To enter the password, first select the Connect using a security key instead link in order to establish the connection with the password.
    4Enter the IP address 192.168.250.181 in the address bar of the browser and confirm. The installation wizard opens.
    5Follow the installation wizard and complete the installation in the individual areas.
    6Add the system components in Fronius Solar.web and commission the PV system.

    Ethernet:

    1Establish a connection to the inverter (LAN1) using a network cable (min. CAT5 STP).
    2Open the access point by touching the sensor once    .
    ✓Communication LED flashes blue.
    3Enter the IP address 169.254.0.180 in the address bar of the browser and confirm. The installation wizard opens.
    4Follow the installation wizard and complete the installation in the individual areas.
    5Add the system components in Fronius Solar.web and commission the PV system.
    1. Installation

    De-energizing the inverter and switching it back on

    link_horizontalLink copied

    Risk of rupture

    WARNING

    In the case of electrical devices with a high housing protection class, there is a risk of explosion in the event of a fault. Possible causes are defective components that release gases, improperly installed or commissioned devices, or the penetration of gas via lines (conduits).

    This may result in serious personal injury and damage to property.

    Turn off the automatic circuit breaker

    If possible, switch off the DC line in front of the inverter (additional external DC disconnector)

    Turn the DC disconnector to the "OFF" switch setting

    Remove the connection area cover

    Allow the capacitors of the inverter to discharge (2 minutes)

    1. Installation
    2. De-energizing the inverter and switching it back on

    Risk of rupture

    link_horizontalLink copied

    WARNING

    In the case of electrical devices with a high housing protection class, there is a risk of explosion in the event of a fault. Possible causes are defective components that release gases, improperly installed or commissioned devices, or the penetration of gas via lines (conduits).

    This may result in serious personal injury and damage to property.

    Turn off the automatic circuit breaker

    If possible, switch off the DC line in front of the inverter (additional external DC disconnector)

    Turn the DC disconnector to the "OFF" switch setting

    Remove the connection area cover

    Allow the capacitors of the inverter to discharge (2 minutes)

    1. Installation
    2. De-energizing the inverter and switching it back on

    De-energizing the inverter and switching it back on

    link_horizontalLink copied
    Disconnecting the inverter from the power supply:
    1Switch off the automatic circuit breaker (AC and, if present, battery).
    2Turn the DC disconnector to the "Off" switch setting.

    IMPORTANT!
    Wait for the capacitors of the inverter to discharge!

    Switching on the inverter:
    If the inverter has not been in operation for six months or more after installation, it must be tested before commissioning.
    1Turn the DC disconnector to the "On" switch setting.
    2Switch on the automatic circuit breaker (AC and, if present, battery).

    Settings – User interface of the inverter

    link_horizontalLink copied

    User settings

    User login

    1Open the user interface of the inverter in the browser.
    2In the Login menu area, log in with username and password, or, in the User > User Login menu area, log in with username and password.

    IMPORTANT!
    Depending on the authorization of the user, settings can be made in the individual menu areas.

    1. Settings – User interface of the inverter

    User settings

    link_horizontalLink copied

    User login

    1Open the user interface of the inverter in the browser.
    2In the Login menu area, log in with username and password, or, in the User > User Login menu area, log in with username and password.

    IMPORTANT!
    Depending on the authorization of the user, settings can be made in the individual menu areas.

    1. Settings – User interface of the inverter
    2. User settings

    User login

    link_horizontalLink copied
    1Open the user interface of the inverter in the browser.
    2In the Login menu area, log in with username and password, or, in the User > User Login menu area, log in with username and password.

    IMPORTANT!
    Depending on the authorization of the user, settings can be made in the individual menu areas.

    1. Settings – User interface of the inverter
    2. User settings

    Selecting languages

    link_horizontalLink copied
    1In the User > Language menu area, select the desired language.
    1. Settings – User interface of the inverter

    Device configuration

    link_horizontalLink copied

    Components

    All available components of the system can be added via Add component+.

    PV Generator
    Activate the MPP tracker and enter the connected PV output in the relevant field. In the case of combined solar module strings, PV 1 + PV 2 connected in parallel must be activated.

    Meter

    Primary meter

    IMPORTANT!
    For problem-free operation with further energy generators and in Full Backup power mode, it is important to install and configure a Fronius Smart Meter as the primary meter at the feed-in point. The inverter and further generators must be connected to the public grid via the Fronius Smart Meter. Only one primary meter can be configured in the system.

    This setting has an effect on the behavior of the inverter during the night. If the primary meter has been configured, the inverter remains permanently connected to the grid in order to enable it to draw energy from other generators at any time.

    If the primary meter has not been configured, the inverter switches to standby mode as soon as there is no more PV power available. No energy management specification is sent to the battery (e.g., minimum state of charge reached). The message "Power low" is displayed. The inverter starts again as soon as an energy management specification is sent or sufficient PV power is available.

    Secondary meter
    In addition to the primary meter, further secondary meters can be added to the system to record the load curves of individual loads and generators (e.g., heat pump, wind power plant, etc.) and provide the measured data for energy profiling in Fronius Solar.web.


     

    1. After connecting the meter, select a category:
      • Primary meter
      • Secondary meter
    2. Select one of the following device types:
      • Modbus RTU
      • Modbus TCP
      • MQTT (available MQTT device is displayed automatically)

    NOTE

    For communication via MQTT and Modbus TCP, install the inverter and Smart Meter in the same sub-network.

    1. Additionally define the following parameters for the Smart Meter:
      • Application of primary meter (Feed-in point or Load branch)
      • Application of secondary meter (Production meter or Secondary meter)
      • Name
      • Category (e.g., inverter, heat pump)
      • IP Address (for Modbus TCP)
      • Port (for Modbus TCP)
      • Modbus Address (for Modbus RTU and TCP)


    The Watt value for the production meter is the sum of all production meters. The Watt value for the secondary meter is the sum of all secondary meters.

    Battery
    If the SoC Limit Mode is set to Auto, the values SoC Minimum and SoC Maximum are preset according to the technical specifications of the battery manufacturer.

    If the SoC Limit Mode is set to Manual, the values SoC Minimum and SoC Maximum can be changed after consultation with the battery manufacturer within the framework of their technical specifications. In a backup power situation, the set values are not taken into account.

    The setting Allow battery charging from other generators in the home network activates/deactivates charging of the battery from other generators.
    The power consumption of the Fronius inverter can be restricted by specifying a value in the Max. Charging Power from AC field. As a maximum, a power consumption equal to the AC rated power of the Fronius inverter is possible.

    The setting Allow battery charging from public grid + Allow battery charging from other generators in the home network activates/deactivates the charging of the battery from the public grid and, if present, from other generators in the home network.
    The normative or compensatory specifications must be taken into account for this setting. Irrespective of this setting, necessary service-related charging from the public grid is performed (e.g., forced re-charging to protect against deep discharge).

    IMPORTANT!
    Fronius accepts no liability for damage to third-party batteries.

    Ohmpilot
    All the Ohmpilots available in the system are displayed. Select the desired Ohmpilot and add to the system via Add.

    1. Settings – User interface of the inverter
    2. Device configuration

    Components

    link_horizontalLink copied

    All available components of the system can be added via Add component+.

    PV Generator
    Activate the MPP tracker and enter the connected PV output in the relevant field. In the case of combined solar module strings, PV 1 + PV 2 connected in parallel must be activated.

    Meter

    Primary meter

    IMPORTANT!
    For problem-free operation with further energy generators and in Full Backup power mode, it is important to install and configure a Fronius Smart Meter as the primary meter at the feed-in point. The inverter and further generators must be connected to the public grid via the Fronius Smart Meter. Only one primary meter can be configured in the system.

    This setting has an effect on the behavior of the inverter during the night. If the primary meter has been configured, the inverter remains permanently connected to the grid in order to enable it to draw energy from other generators at any time.

    If the primary meter has not been configured, the inverter switches to standby mode as soon as there is no more PV power available. No energy management specification is sent to the battery (e.g., minimum state of charge reached). The message "Power low" is displayed. The inverter starts again as soon as an energy management specification is sent or sufficient PV power is available.

    Secondary meter
    In addition to the primary meter, further secondary meters can be added to the system to record the load curves of individual loads and generators (e.g., heat pump, wind power plant, etc.) and provide the measured data for energy profiling in Fronius Solar.web.


     

    1. After connecting the meter, select a category:
      • Primary meter
      • Secondary meter
    2. Select one of the following device types:
      • Modbus RTU
      • Modbus TCP
      • MQTT (available MQTT device is displayed automatically)

    NOTE

    For communication via MQTT and Modbus TCP, install the inverter and Smart Meter in the same sub-network.

    1. Additionally define the following parameters for the Smart Meter:
      • Application of primary meter (Feed-in point or Load branch)
      • Application of secondary meter (Production meter or Secondary meter)
      • Name
      • Category (e.g., inverter, heat pump)
      • IP Address (for Modbus TCP)
      • Port (for Modbus TCP)
      • Modbus Address (for Modbus RTU and TCP)


    The Watt value for the production meter is the sum of all production meters. The Watt value for the secondary meter is the sum of all secondary meters.

    Battery
    If the SoC Limit Mode is set to Auto, the values SoC Minimum and SoC Maximum are preset according to the technical specifications of the battery manufacturer.

    If the SoC Limit Mode is set to Manual, the values SoC Minimum and SoC Maximum can be changed after consultation with the battery manufacturer within the framework of their technical specifications. In a backup power situation, the set values are not taken into account.

    The setting Allow battery charging from other generators in the home network activates/deactivates charging of the battery from other generators.
    The power consumption of the Fronius inverter can be restricted by specifying a value in the Max. Charging Power from AC field. As a maximum, a power consumption equal to the AC rated power of the Fronius inverter is possible.

    The setting Allow battery charging from public grid + Allow battery charging from other generators in the home network activates/deactivates the charging of the battery from the public grid and, if present, from other generators in the home network.
    The normative or compensatory specifications must be taken into account for this setting. Irrespective of this setting, necessary service-related charging from the public grid is performed (e.g., forced re-charging to protect against deep discharge).

    IMPORTANT!
    Fronius accepts no liability for damage to third-party batteries.

    Ohmpilot
    All the Ohmpilots available in the system are displayed. Select the desired Ohmpilot and add to the system via Add.

    1. Settings – User interface of the inverter
    2. Device configuration

    Functions and I/Os

    link_horizontalLink copied
    Backup power
    In backup power mode, select one of the following settings:
    • Parallel Backup support
    • Full Backup
    • Off
    The Full Backup power mode is available under the following conditions:
    • The required I/O assignments for backup power are configured.
    • A Fronius Smart Meter is installed and configured at the feed-in point.
    • A suitable battery is connected to the inverter.

    IMPORTANT! For configuration of the backup power mode Full Backup, observe the instructions in chapter Safety.

    Parallel Backup
    Parallel Backup enables the additional use of PV power in backup power mode, which secondary inverters make available in the system.

    Configuration for all inverters in Parallel Backup operation:
    1Under Device Configuration > Inverter in the Backup power menu, set the same Backup power frequency offset.
    Configuration on the primary inverter:
    1In the Backup power mode drop-down menu, select the Full Backup option.
    2Select the parallel backup coordinator slider.
    Configuration on the secondary inverter:
    1In the Backup power mode drop-down menu, select the Parallel backup supporter option.
    ✓Parallel Backup has been configured.

    Backup Nominal Voltage
    Select the voltage for backup power mode.

    SoC warning level
    In backup power mode, a warning is emitted when this residual battery capacity is reached.

    Reserve Capacity
    The set value results in a residual capacity (depending on the battery capacity) that is reserved for backup power situations. The battery does not discharge below the reserve capacity in grid connected mode. In backup power mode, the manually set value of SoC Minimum is not taken into account. The battery discharges up to the automatically preset, minimum state of charge. This value is specified by the battery manufacturer.

    System preservation during night
    To ensure continuous backup power operation even during the night, the inverter calculates a residual capacity for system preservation depending on the battery capacity. When the calculated limit value is reached, the inverter and the battery switch to standby mode. This is maintained for a period of 16 hours. Connected loads are no longer supplied. The battery discharges up to the preset minimum state of charge.

    Rapid switch mode

    Disconnection from the grid and synchronized reconnection each take place within 20 ms.

    NOTE

    Material damage due to misconfiguration

    This can result in damage to system components.

    Only activate the Rapid switch mode function on the primary inverter in conjunction with a Fronius Backup Controller 63A.

    Only activate the Rapid switch mode function for secondary inverters if the function is also activated for the primary inverter.

    Configuration on the inverter:
    1Enable the Rapid switch mode slider.

    Load Management
    Select up to four pins for the load management. Further settings for the load management are available in the Load Management menu item.
    Default: Pin 1

    Australia - Demand Response Modes (DRM)
    Activate the slider if DRM is required. Configure the pins for control via DRM as follows:

    Mode

    Description

    Information

    DRM Pin

    I/O pin

    DRM0

    Inverter disconnects from the grid

    DRM0 occurs in the event of an interruption or short circuit on the REF GEN or COM LOAD lines, or in the event of invalid combinations of DRM1 - DRM8.
    The grid relays open.

    REF GEN
    COM LOAD

    IO4
    IO5

    DRM1

    Import Pnom ≤ 0% without disconnection from grid

    currently not supported

    DRM 1/5

    IN6

    DRM2

    Import Pnom ≤ 50%

    currently not supported

    DRM 2/6

    IN7

    DRM3

    Import Pnom ≤ 75% &
    +Qrel* ≥ 0%

    currently not supported

    DRM 3/7

    IN8

    DRM4

    Import Pnom ≤ 100%

    currently not supported

    DRM 4/8

    IN9

    DRM5

    Export Pnom ≤ 0% without disconnection from grid

    currently not supported

    DRM 1/5

    IN6

    DRM6

    Export Pnom ≤ 50%

    currently not supported

    DRM 2/6

    IN7

    DRM7

    Export Pnom ≤ 75% &
    -Qrel* ≥ 0%

    currently not supported

    DRM 3/7

    IN8

    DRM8

    Export Pnom ≤ 100%

    currently not supported

    DRM 4/8

    IN9

    The percentage specifications always relate to the rated device power.

    IMPORTANT! If the Australia - Demand Response Modes (DRM) function is activated and no DRM control is connected, the inverter switches to standby mode.

    Battery Grid Import Limit (§ 14a EnWG)
    Define a pin for the implementation of the regulatory requirement per § 14a EnWG.

    1. Settings – User interface of the inverter
    2. Device configuration

    Inverter

    link_horizontalLink copied

    Force standby
    When this function is activated, the supply of energy from the inverter into the grid is interrupted. This makes it possible to shut down the inverter without power and protect its components. The standby function is automatically deactivated when the inverter is restarted.

    Fan test

    IMPORTANT!
    For settings in this menu item, select the Technician user, enter the password for the Technician user, and confirm. Settings may only be made by trained and qualified personnel!

    This function can be used to check whether the fans of the inverter are working correctly based on acoustics, for example after replacing a fan.

    1Click Start fan test
    ✓The inverter successively activates all fans that are running at partial load during the test phase to avoid unnecessary noise. The inverter is in standby during this time.
    ✓The test takes around 30 seconds per fan. The inverter then switches back to normal operation. The test can be stopped manually using the Stop fan test function.

    AC network

    Parameter

    Value range

    Description

    Neutral conductor status

    Not connected

    The neutral conductor is not required in the system configuration and is therefore not connected.

    Connected

    The neutral conductor is connected.

    PV 1 to PV 3

    Parameter

    Value range

    Description

    Mode

    Off

    The MPP tracker is deactivated.

    Auto

    The inverter uses the voltage at which the max. possible output of the MPP tracker is possible.

    Fixed

    The MPP tracker uses the voltage defined in UDC fixed.

    UDC fixed

    150‑870 V

    The inverter uses the fixed voltage that is used on the MPP tracker.

    Dynamic Peak Manager

    Off

    Function is deactivated.

    On

    The entire solar module string is checked for optimization potential and determines the best possible voltage for the supply of energy from the inverter into the grid.

    Ripple control signal
    Ripple control signals are signals that are sent by the energy company in order to switch controllable loads on and off. Depending on the installation situation, ripple control signals can be dampened or amplified by the inverter. This can be counteracted if necessary by applying the following settings.

    Parameter

    Value range

    Description

    Reduction of influence

    Off

    Function is deactivated.

    On

    Function is activated.

    Frequency of the ripple control signal

    100‑3,000 Hz

    The frequency specified by the energy company must be entered here.

    Grid inductance

    0.00001‑0.005 H

    The value measured at the infeed point must be entered here.

    Measures to prevent FI/RCMU false alarms
    (when using a 30 mA residual current circuit breaker)

    NOTE

    A residual current circuit breaker for the AC connecting cable may be required depending on national regulations, the grid operator, and other conditions.

    A type A residual current circuit breaker is generally sufficient in this case. Nevertheless, false alarms can be triggered for the type A residual current circuit breaker in individual cases and depending on local conditions. For this reason, Fronius recommends using a residual current circuit breaker suitable for frequency inverters with a release current of least 100 mA, taking into account national provisions.

    Parameter

    Value range

    Description

    Leakage current factor to reduce RCMU/FI false tripping

    0‑0.25
    (default: 0.16)

    By reducing the setting value, the leakage current is reduced and the intermediate circuit voltage is increased, which slightly lowers the efficiency.

    • A setting value of 0.16 ensures optimum efficiency.
    • A setting value of 0 enables minimum leakage currents.

    Shutdown before 30 mA FI triggers

    Off

    The function for reducing false tripping of the residual current circuit breaker is deactivated.

    On

    The function for reducing false tripping of the residual current circuit breaker is activated.

    Rated non-tripping fault current limit value

    0.015‑0.3

    Value of the non-tripping residual current specified by the manufacturer for the residual current circuit breaker at which the residual current circuit breaker does not switch off under specified conditions.

    Insulation warning

    Parameter

    Value range

    Description

    Insulation warning

    Off

    The insulation warning is deactivated.

    On

    The insulation warning is activated.
    A warning is output in the event of an insulation fault.

    Insulation measurement mode

     

    Exact

    Insulation monitoring takes place with the highest degree of accuracy and the measured insulation resistance is displayed on the user interface of the inverter.

    Fast

    Insulation monitoring takes place with a lesser degree of accuracy, whereby the time to take the insulation measurement is shortened and the insulation value is not displayed on the user interface of the inverter.

    Threshold for the insulation warning

    100
    10,000 kΩ

    If the value drops below the threshold, status code 1083 is displayed on the user interface of the inverter.

    Backup power

    Parameter

    Value range

    Description

    Backup power nominal voltage

    220‑240 V

    The nominal phase voltage that is output in backup power mode.

    Backup power frequency offset

    -5-+5 Hz

    The setting value can be used to reduce or increase the backup power frequency (see Technical data) by the offset value. The default value is +3 Hz. Connected loads (e.g., Fronius Ohmpilot) detect that backup power mode is active based on the change in frequency and react accordingly (e.g., by activating power saving mode).


    IMPORTANT!

    If there is another AC source in the system, the backup power frequency must not be changed. The default value (+3 Hz) prevents other AC sources from feeding in parallel to the inverter in emergency power mode and triggering power surges and the shutdown of the system's own backup power grid.

    Backup power undervoltage protection limit value U< [pu]

    0‑2%V

    This set value represents the limit value for shutting down backup power mode.
    e.g., set value 0.9 = 90% of the nominal voltage.

    Backup power undervoltage protection time U<

    0.04‑20 s

    Trip time for falling below the backup power undervoltage protection limit value.

    Backup power surge protection limit value U> [pu]

    0‑2%V

    This set value represents the limit value for shutting down backup power mode.
    e.g., set value 1.1 = 110% of the nominal voltage.

    Backup power surge protection time U>

    0.04‑20 s

    Trip time for exceeding the backup power surge protection limit value.

    Fast undervoltage protection / ground fault protection limit value U<< [pu]

    0-100%V

    Defines the voltage limit value below which rapid undervoltage protection or protection against ground faults is triggered. Typically, a value such as 0.3 pu (30% of the nominal voltage) is set here.

    Fast undervoltage protection / ground fault protection time U<<

    0‑10 s

    Defines the maximum time (in seconds) for which the voltage may be below the set limit value before the inverter switches off. This value must be ≤ 0.4 s in accordance with ÖVE E 8101.

    Backup power restart delay

    0‑600 s

    Waiting time for restarting backup power mode following a shutdown.

    Backup power restart attempts

    1‑10

    The max. number of automated restart attempts. Once the max. number of automated restart attempts has been reached, service message 1177 must be manually acknowledged.

    External frequency monitoring in backup power mode
    (only for Italy)

     

    Off

    Function is deactivated

    On

    For Full Backup power mode in Italy, external frequency monitoring must be activated. The mains frequency is checked before ending backup power mode. If the mains frequency is within the permitted limits, the loads are connected to the public grid.

    Backup power short circuit switch-off time

    0.001‑60 s

    If a short circuit occurs during backup power mode, backup power mode is interrupted within the set time.

    1. Settings – User interface of the inverter

    Energy management

    link_horizontalLink copied

    Permitted maximum battery charge from the public grid

    In Germany, new rules for charging batteries came into force on January 1, 2024. When applying §14a EnWG, the charging current must be reduced to a maximum of 4.2 kW by the grid operator for dimming controllable load equipment in accordance with §14a EnWG.

    In order to document implementation of the control command, the inverter can be connected to Fronius Solar.web and ensure a permanent Internet connection. In addition, in the menu item Device configuration > Functions & I/Os, activate the Battery Grid Import Limit (§ 14a EnWG).

    1. Settings – User interface of the inverter
    2. Energy management

    Permitted maximum battery charge from the public grid

    link_horizontalLink copied

    In Germany, new rules for charging batteries came into force on January 1, 2024. When applying §14a EnWG, the charging current must be reduced to a maximum of 4.2 kW by the grid operator for dimming controllable load equipment in accordance with §14a EnWG.

    In order to document implementation of the control command, the inverter can be connected to Fronius Solar.web and ensure a permanent Internet connection. In addition, in the menu item Device configuration > Functions & I/Os, activate the Battery Grid Import Limit (§ 14a EnWG).

    1. Settings – User interface of the inverter
    2. Energy management

    Battery management

    link_horizontalLink copied

    State of charge settings
    If the SoC Limit Mode is set to Auto, the values SoC Minimum and SoC Maximum are preset according to the technical specifications of the battery manufacturer.

    If the SoC Limit Mode is set to Manual, the values SoC Minimum and SoC Maximum can be changed. Change the values SoC Minimum and SoC Maximum only after consultation with the battery manufacturer within the framework of their technical specifications. In a backup power situation, the set values are not taken into account.

    If Battery charging from other sources is activated, the following options are available:
    • The setting From other generators in the home network and from public grid activates/deactivates the charging of the battery from the public grid and, if present, from other generators in the home network.
      Take into account the normative or compensatory specifications for this setting. Irrespective of this setting, necessary service-related charging from the public grid is performed (e.g., forced re-charging to protect against deep discharge).
    • The setting From other generators in the home network activates/deactivates charging of the battery from other generators.
      The power consumption of the Fronius inverter can be restricted by specifying a value in the Max. Charging Power from AC field. As a maximum, a power consumption equal to the AC rated power of the Fronius inverter is possible.

    SoC warning level
    In backup power mode, a warning is emitted when this residual battery capacity is reached.

    Reserve Capacity
    The set value results in a residual capacity (depending on the battery capacity) that is reserved for backup power situations. The battery does not discharge below the reserve capacity in grid connected mode.

    IMPORTANT! Fronius accepts no liability for damage to third-party batteries.

    Time-dependent battery control
    Using the Time-dependent battery control, it is possible to specify, restrict, or prevent the charging or discharging of the battery at/to a defined power.

    Battery Management is influenced, for example, by the following settings:
    • Permitted battery charging from the public grid
    • Power limit of the inverter, battery storage, or overall system
    • Control specifications via Modbus
    • Self-consumption optimization

    IMPORTANT! The defined rules for battery control have the second lowest priority after Self-Consumption Optimization. Depending on the configuration, the rules may not be fulfilled due to other settings.

    The following values can be selected for the Time-dependent battery control rules:
    • Max. charging power
      The maximum charging power of the battery is the value set in the Power input field.
    • Min. charging power
      The minimum charging power of the battery is the value set in the Power input field.
    • Max. discharge power
      The maximum discharge power of the battery is the value set in the Power input field.
    • Min. discharge power
      The minimum discharge power of the battery is the value set in the Power input field.

    The timing of when the rule applies is set in the Time input fields and by selecting the days of the week.

    It is not possible to define a time window beyond midnight (00:00).
    Example: Two entries are needed to set a rule of 22:00 to 06:00: "22:00 - 23:59" and "00:00 - 06:00"

    Service Mode
    If Service Mode is activated, the battery system is charged or discharged to the state of charge of 30%. The state of charge of 30% is maintained until the end of service mode.

    IMPORTANT! Service Mode is only available for Fronius battery systems.

    1. Settings – User interface of the inverter
    2. Energy management

    Examples - Time-dependent battery control

    link_horizontalLink copied

    The following examples serve to explain the energy flows. Efficiency levels are not taken into account.

    Battery system

    PV system to inverter

    1000 W

    Power into the battery

    500 W

    Power output (AC) of the inverter

    500 W

    Set target value at feed-in point

    0 W

    Infeed into the public grid

    0 W

    Consumption in home

    500 W

     

    Battery system without photovoltaics, including second generator in the house

    Power into the battery

    1500 W

    Power consumption (AC) of the inverter

    1500 W

    Second generator in home network

    2000 W

    Set target value at feed-in point

    0 W

    Infeed into the public grid

    0 W

    Consumption in home

    500 W

     

    Battery system including second generator in the house

    PV system to inverter

    1000 W

    Power into the battery

    2500 W

    Power consumption (AC) of the inverter

    1500 W

    Second generator in home network

    2000 W

    Set target value at feed-in point

    0 W

    Infeed into the public grid

    0 W

    Consumption in home

    500 W

    1. Settings – User interface of the inverter
    2. Energy management

    Permitted battery control regulations

    link_horizontalLink copied

    A regulation always consists of a restriction or specification, and the time and days of the week when the regulation is active. The time of regulations with the same restriction (e.g., max. charging power) must not overlap.

    Max. charging and discharging limits
    One max. charging and one max. discharging power can be configured at the same time.

    Specify charging range
    It is possible to define a charging range using a min. and max. charging limit. In this case, it is not possible to discharge the battery.

    Specify discharging range
    It is possible to define a discharging range using a min. and max. discharging limit. In this case, it is not possible to charge the battery.

    Specify a defined charge
    It is possible to specify a defined charging power by setting the min. and max. charging power to the same value.

    Specify a defined discharge
    It is possible to specify a defined discharging power by setting the min. and max. discharging power to the same value.

    Possible applications

    • Time-dependent energy tariffs
    • Battery reservation in the event of market-specific power limitation
    • Time-dependent storage reservation for a backup power situation
    1. Settings – User interface of the inverter
    2. Energy management

    PV power reduction

    link_horizontalLink copied

    The regulations in the Battery Management menu area enable optimal use of the energy generated. In some situations, the PV power cannot be used in full due to the time-dependent battery control.

    Example

    Fronius inverter (max. output power)

    6000 W

    Defined discharge of the battery

    6000 W

    PV power

    1000 W

    In this case, the inverter reduces the PV power to 0 W, since the output power of the inverter is max. 6000 W. The inverter is already being fully utilized through discharging the battery.

    1. Settings – User interface of the inverter
    2. Energy management

    Load management

    link_horizontalLink copied

    Priorities
    If additional components (e.g., battery, Fronius Ohmpilot) are present in the system, the priorities can be set here. Devices having higher priority are actuated first, and subsequently, if there is still excess energy available, the other devices.

    IMPORTANT!
    If there is a Fronius Wattpilot in the photovoltaic system, it is considered to be a load. The priority for the load management of the Fronius Wattpilot must be configured in the Fronius Solar.wattpilot app.

    Rules
    It is possible for up to four different load management rules to be defined. At the same threshold values, the rules are activated in succession. For deactivation, this is done in reverse; the I/O last switched on is the first to be switched off. In the case of different thresholds, the I/O with the lowest threshold is switched on first, followed by the second lowest, and so on.

    I/Os controlled by the produced power are always prioritized over a battery and Fronius Ohmpilot. That is to say that an I/O can switch on and result in the battery no longer being charged or the Fronius Ohmpilot no longer being activated.

    IMPORTANT!
    An I/O is activated/deactivated after 60 seconds.

    Load
    • Control is Off (deactivated).
    • Control is effected by the Power Production.
    • Control is effected by Power Surplus (with feed-in limits). This option can only be selected if a meter has been connected. Control is effected using the actual power of feeding in with respect to the grid.
    Thresholds
    • On: For entering an effective power limit, at which the output is activated.
    • Off: For entering an effective power limit, at which the output is deactivated.
    Duration
    • Field for activating the Minimum duration per on-signal for which the output is to be activated for each switch-on process.
    • Field for activating the Maximum duration per day.
    • Field for activating the Desired duration for which the output is to be activated in total per day (several switch-on processes are allowed for).
    1. Settings – User interface of the inverter
    2. Energy management

    Self-consumption optimization

    link_horizontalLink copied

    Self-Consumption Optimization
    Set the operating mode to Manual or Automatic. The inverter always adjusts to the set Target value at feed-in point. In Automatic operating mode (factory setting), an adjustment is made to 0 W at the feed-in point (max. self-consumption).

    The Target value at feed-in point also applies if a further source feeds into this Smart Meter. In this case, however:
    • The Fronius Smart Meter must be installed and configured at the feed-in point.
    • The Allow battery charging from other generators in the home network function must be activated in the Components > Battery menu area.

    Target value at feed-in point
    If Manual has been selected under Self-Consumption Optimization, the Operation Mode (Consumption/Feed-in) and the Target value at feed-in point can be set.

    IMPORTANT!
    Self-Consumption Optimization has lower priority than Battery Management.

    1. Settings – User interface of the inverter

    System

    link_horizontalLink copied

    General

    1Enter the name of the system in the input field PV System Name (max. 30 characters).
    2Select the Timezone Region and Timezone Location in the drop-down lists.
    3Click Save.
    ✓System name, time zone, and time zone location are saved.
    1. Settings – User interface of the inverter
    2. System

    General

    link_horizontalLink copied
    1Enter the name of the system in the input field PV System Name (max. 30 characters).
    2Select the Timezone Region and Timezone Location in the drop-down lists.
    3Click Save.
    ✓System name, time zone, and time zone location are saved.
    1. Settings – User interface of the inverter
    2. System

    Update

    link_horizontalLink copied

    All available updates for inverters and other Fronius devices are provided on the product pages and in the "Fronius Download Search" area at www.fronius.com .

    Update
    1Drag the firmware file into the Drag & drop file here field, or select via Browse file.
    ✓Update is started.
    1. Settings – User interface of the inverter
    2. System

    Setup wizard

    link_horizontalLink copied

    The guided setup wizard can be accessed here.

    1. Settings – User interface of the inverter
    2. System

    Restoring factory settings

    link_horizontalLink copied

    All settings
    Resets all configuration data, apart from the country setup. Changes to the country setup may only be made by authorized personnel.

    All settings without network
    Resets all configuration data, apart from the country setup and the network settings. Changes to the country setup may only be made by authorized personnel.

    1. Settings – User interface of the inverter
    2. System

    Event log

    link_horizontalLink copied

    Current messagesAll current events of the linked system components are displayed here.

    IMPORTANT!
    Depending on the type of event, this must be confirmed via the "tick" button so that it can be further processed.

    History
    All events of the linked system components that are no longer present are displayed here.

    1. Settings – User interface of the inverter
    2. System

    Information

    link_horizontalLink copied

    All the information regarding the system and the current settings is displayed and provided for download in this menu area.

    1. Settings – User interface of the inverter
    2. System

    License Manager

    link_horizontalLink copied

    The power data and functional scope of the inverter are stored in the license file.
    If the inverter, DC power stage set PC board, or data communication area is replaced, the license file must also be replaced.

    1. Settings – User interface of the inverter
    2. System

    Licensing

    link_horizontalLink copied
    Licensing - online (recommended)
    This requires an Internet connection and a completed Fronius Solar.web configuration.
    1Finish all installation work (refer to the chapter headed Closing the inverter's connection area/housing cover, and commissioning on page (→)).
    2Establish a connection to the user interface of the inverter.
    3Enter the serial number and verification code (VCode) of the defective and replacement device. The serial number and VCode can be found on the rating plate of the inverter (refer to the chapter headed Information on the device on page (→)).
    4Click the Start online licensing button.
    5Skip past the Terms and conditions of use and Network settings menu items by clicking Next.
    ✓License activation is started.
    Licensing - offline
    There must be no Internet connection in this case. If offline licensing is carried out while there is an active Internet connection, the license file is automatically loaded onto the inverter, resulting in the following error when the license file is uploaded: "The license has already been installed and the wizard can be closed".
    1Finish all installation work (refer to the chapter headed Closing the inverter's connection area/housing cover, and commissioning on page (→)).
    2Establish a connection to the user interface of the inverter.
    3Enter the serial number and verification code (VCode) of the defective and replacement device. The serial number and VCode can be found on the rating plate of the inverter (refer to the chapter headed Information on the device on page (→)).
    4Click the Start offline licensing button.
    5Download the service file onto the mobile device by clicking the Download service file button.
    6Open licensemanager.solarweb.com and log in with username and password.
    7Drag the service file into the Drag service file here or click to upload field or click to upload it.
    8Download the newly generated license file onto the mobile device by clicking the Download license file button.
    9Switch to the user interface of the inverter and drag the license file into the Drag & drop license file here field or select via Choose license file.
    ✓License activation is started.
    1. Settings – User interface of the inverter
    2. System

    Support

    link_horizontalLink copied
    Activating the support user
    1Click the Enable Support User Account button.
    ✓The support user is activated.

    IMPORTANT!
    The support user exclusively enables Fronius Technical Support to configure settings on the inverter via a secure connection. Access is deactivated by clicking the Terminate Support User Session button.

    Generating support info (for Fronius Support)
    1Click the Generate support info button.
    2The sdp.cry file is downloaded automatically. For manual download, click the Download support info button.
    ✓The sdp.cry file is saved in the downloads.
    Activating remote access
    1Click the Activate Remote Access button.
    ✓Remote access is activated for Fronius Support.

    IMPORTANT!
    The remote access exclusively enables Fronius Technical Support to access the inverter via a secure connection. In this case, diagnostics data are transmitted, which are used for troubleshooting. The remote access can be activated only upon request by Fronius Support.

    1. Settings – User interface of the inverter

    Communication

    link_horizontalLink copied

    Network

    Server addresses for data transfer
    If a firewall is used for outgoing connections, allow the below protocols, server addresses, and ports for successful data transfer, see:
    https://www.fronius.com/~/downloads/Solar%20Energy/Firmware/SE_FW_Changelog_Firewall_Rules_EN.pdf

    When using FRITZ!Box products, configure Internet access without any restrictions or limitations. Do not set the DHCP Lease Time (validity) to 0 (=infinite).

    LAN:

    Establishing a connection:
    1Enter the host name.
    2Select the connection type: Automatic or Static.
    3For the Static connection type, enter the IP address, subnet mask, DNS, and gateway.
    4Click the Connect button.
    ✓The connection is established.

    After establishing the connection, check the connection status.

    WiFi:

    Establishing a connection via WPS:
      ☐

      Activate the access point of the inverter. This is opened by touching the sensor    > Communications LED flashes blue

    Ihr Browser kann diesen Film leider nicht anzeigen.
    1.
    Establish the connection to the inverter in the network settings (the inverter is displayed with the name "FRONIUS_" and the serial number of the device).
    2.
    Enter the password from the rating plate and confirm.
    IMPORTANT!
    To enter the password, first select the Connect using a security key instead link in order to establish the connection with the password.
    3.
    Enter the IP address 192.168.250.181 in the address bar of the browser and confirm.
    4.
    In the Communication > Network > WLAN > WPS menu area, click the Activate button.
    5.
    Activate WPS on the WiFi router (see WiFi router documentation).
    6.
    Click on the Start button. The connection is established automatically.
    7.
    Log in to the user interface of the inverter.
    8.
    Check the network details and connection to Fronius Solar.web.
    1Establish the connection to the inverter in the network settings (the inverter is displayed with the name "FRONIUS_" and the serial number of the device).
    2Enter the password from the rating plate and confirm.
    IMPORTANT!
    To enter the password, first select the Connect using a security key instead link in order to establish the connection with the password.
    3Enter the IP address 192.168.250.181 in the address bar of the browser and confirm.
    4In the Communication > Network > WLAN > WPS menu area, click the Activate button.
    5Activate WPS on the WiFi router (see WiFi router documentation).
    6Click on the Start button. The connection is established automatically.
    7Log in to the user interface of the inverter.
    8Check the network details and connection to Fronius Solar.web.

    After connecting, the status of the connection should be checked.

    Selecting and connecting to a WiFi network:
    The networks found are displayed in the list. Click the refresh button    to perform a new search for available WiFi networks. If necessary, restrict the selection list further via the Search network input field.
    1Select network from the list.
    2Select the connection type: Automatic or Static.
    3For the Automatic connection type, enter the WiFi password and host name.
    4For the Static connection type, enter the IP address, subnet mask, DNS, and gateway.
    5Click the Connect button.
    ✓The connection is established.

    After establishing the connection, check the connection status.

    Access point:

    The inverter serves as the access point. A PC or mobile device connects directly to the inverter. Connecting to the Internet is not possible. Assign a Network Name (SSID) and Network Key (PSK) to establish a connection. Assign a Network Key (PSK) with at least 20 characters, consisting of upper and lower case letters, special characters, and numbers, to protect the device from unauthorized access.
    It is possible to operate a connection via WiFi and via the access point at the same time.

    1. Settings – User interface of the inverter
    2. Communication

    Network

    link_horizontalLink copied

    Server addresses for data transfer
    If a firewall is used for outgoing connections, allow the below protocols, server addresses, and ports for successful data transfer, see:
    https://www.fronius.com/~/downloads/Solar%20Energy/Firmware/SE_FW_Changelog_Firewall_Rules_EN.pdf

    When using FRITZ!Box products, configure Internet access without any restrictions or limitations. Do not set the DHCP Lease Time (validity) to 0 (=infinite).

    LAN:

    Establishing a connection:
    1Enter the host name.
    2Select the connection type: Automatic or Static.
    3For the Static connection type, enter the IP address, subnet mask, DNS, and gateway.
    4Click the Connect button.
    ✓The connection is established.

    After establishing the connection, check the connection status.

    WiFi:

    Establishing a connection via WPS:
      ☐

      Activate the access point of the inverter. This is opened by touching the sensor    > Communications LED flashes blue

    Ihr Browser kann diesen Film leider nicht anzeigen.
    1.
    Establish the connection to the inverter in the network settings (the inverter is displayed with the name "FRONIUS_" and the serial number of the device).
    2.
    Enter the password from the rating plate and confirm.
    IMPORTANT!
    To enter the password, first select the Connect using a security key instead link in order to establish the connection with the password.
    3.
    Enter the IP address 192.168.250.181 in the address bar of the browser and confirm.
    4.
    In the Communication > Network > WLAN > WPS menu area, click the Activate button.
    5.
    Activate WPS on the WiFi router (see WiFi router documentation).
    6.
    Click on the Start button. The connection is established automatically.
    7.
    Log in to the user interface of the inverter.
    8.
    Check the network details and connection to Fronius Solar.web.
    1Establish the connection to the inverter in the network settings (the inverter is displayed with the name "FRONIUS_" and the serial number of the device).
    2Enter the password from the rating plate and confirm.
    IMPORTANT!
    To enter the password, first select the Connect using a security key instead link in order to establish the connection with the password.
    3Enter the IP address 192.168.250.181 in the address bar of the browser and confirm.
    4In the Communication > Network > WLAN > WPS menu area, click the Activate button.
    5Activate WPS on the WiFi router (see WiFi router documentation).
    6Click on the Start button. The connection is established automatically.
    7Log in to the user interface of the inverter.
    8Check the network details and connection to Fronius Solar.web.

    After connecting, the status of the connection should be checked.

    Selecting and connecting to a WiFi network:
    The networks found are displayed in the list. Click the refresh button    to perform a new search for available WiFi networks. If necessary, restrict the selection list further via the Search network input field.
    1Select network from the list.
    2Select the connection type: Automatic or Static.
    3For the Automatic connection type, enter the WiFi password and host name.
    4For the Static connection type, enter the IP address, subnet mask, DNS, and gateway.
    5Click the Connect button.
    ✓The connection is established.

    After establishing the connection, check the connection status.

    Access point:

    The inverter serves as the access point. A PC or mobile device connects directly to the inverter. Connecting to the Internet is not possible. Assign a Network Name (SSID) and Network Key (PSK) to establish a connection. Assign a Network Key (PSK) with at least 20 characters, consisting of upper and lower case letters, special characters, and numbers, to protect the device from unauthorized access.
    It is possible to operate a connection via WiFi and via the access point at the same time.

    1. Settings – User interface of the inverter
    2. Communication

    Modbus

    link_horizontalLink copied

    The inverter communicates with system components (e.g., Fronius Smart Meter) and other inverters via Modbus. The primary device (Modbus Client) sends control commands to the secondary device (Modbus Server). The control commands are executed by the secondary device.

    RTU Server
    The following input fields and functions are available for communication via Modbus RTU:

     

    Meter address offset
    The value entered (1-247) is the identification number (unit ID) assigned to the meter.
    Factory setting: 200

     

    Inverter address
    The value entered (1-247) is the identification number (unit ID) assigned to the inverter.
    Factory setting: 1

     

    SunSpec Model Type
    There are two different settings, depending on the SunSpec model.

    float: SunSpec Inverter Model 111, 112, 113 or 211, 212, 213.
    int + SF: SunSpec Inverter Model 101, 102, 103 or 201, 202, 203.

     

    Interface
    Select one of the two interfaces Modbus 0 (M0) RTU or Modbus 1 (M1) RTU.

     

    Baud Rate
    The baud rate influences the speed of the transmission between the individual components connected in the system. When selecting the baud rate, it should be ensured that this is the same on the transmit and receive side.

     

    Parity
    The parity bit can be used for parity checks. This is used to identify transmission errors. In this case, a parity bit can ensure a specified number of bits. The value (0 or 1) of the parity bit must be calculated at the transmitter, and is checked at the receiver using the same calculation. The calculation of the parity bit can be carried out for even or odd parity.

     

    Allow Control
    If this option is activated, the inverter is controlled via Modbus.
    Inverter control includes the following functions:
    • On/off
    • Power reduction
    • Setting a constant power factor (cos phi)
    • Setting a constant reactive power
    • Battery control settings with battery

    TCP Server
    The following input fields and functions are available for communication via Modbus TCP:

     

    Meter address offset
    The value entered (1-247) is the identification number (unit ID) assigned to the meter.
    Factory setting: 200

     

    SunSpec Model Type
    There are two different settings, depending on the SunSpec model.

    float: SunSpec Inverter Model 111, 112, 113 or 211, 212, 213.
    int + SF: SunSpec Inverter Model 101, 102, 103 or 201, 202, 203.

     

    Modbus port
    Number of the TCP port (502 or 1502) to be used for Modbus communication.

     

    Meter Address
    The value entered is the identification number (unit ID) assigned to the meter, which can be found on the user interface of the inverter in the Communication > Modbus menu area.
    Factory setting: 200

     

    Allow Control
    If this option is activated, the inverter is controlled via Modbus.
    Inverter control includes the following functions:
    • On/off
    • Power reduction
    • Setting a constant power factor (cos phi)
    • Setting a constant reactive power
    • Battery control settings with battery

     

    Restrict Control
    Restrict the control of the inverter to a device with a fixed IP address.

    1. Settings – User interface of the inverter
    2. Communication

    Cloud control

    link_horizontalLink copied

    The utility/energy supplier can influence the output power of the inverter with Cloud control. This requires the inverter to have an active Internet connection.

    Parameter

    Display

    Description

    Cloud control

    Off

    Cloud control of the inverter is deactivated.

    On

    Cloud control of the inverter is activated.

    Profile

    Value range

    Description

    Allow cloud control for regulatory purposes (Technician)

    Deactivated/Activated

    The function may be mandatory for proper operation of the system.*

    Allow cloud control for Virtual Power Plants (Customer)

    Deactivated/Activated

    If the Allow remote control for regulatory purposes (technician) function is activated (technician access required), the Allow remote control for virtual power plants function is automatically activated and cannot be deactivated.*

    * Cloud control
    A virtual power plant is an interconnection of multiple generators. This virtual power plant can be controlled by means of the cloud control via the Internet. An active inverter Internet connection is a prerequisite for this. System data are transferred.

    1. Settings – User interface of the inverter
    2. Communication

    Solar API

    link_horizontalLink copied

    The Solar API is an IP-based, open JSON interface. If enabled, IOT devices in the local network may access inverter information without authentication. For security reasons, the interface is disabled in the factory. Activate the interface manually if it is required for a third-party application (e.g., EV charger, smart home solutions, etc.). If there is a Fronius Wattpilot in the network, the inverter automatically activates the Solar API.

    Fronius recommends using Fronius Solar.web for monitoring and analyzing the inverter and connected system components.

    In the event of a firmware update to version 1.14.x, the Solar API setting is applied. In systems with a version below 1.14.x, the Solar API is activated; with higher versions, it is deactivated but can be switched on and off via the menu.

    Manually activating the Fronius Solar API
    On the user interface of the inverter in the Communication > Solar API menu area, activate the function Activate communication via Solar API.

    1. Settings – User interface of the inverter
    2. Communication

    Fronius Solar.web

    link_horizontalLink copied

    In this menu, you can agree to the technically necessary data processing or reject it.

    In addition, the transfer of analysis data and remote configuration via Fronius Solar.web can be enabled or disabled.

    1. Settings – User interface of the inverter

    Safety and grid requirements

    link_horizontalLink copied

    Country setup

    WARNING

    Danger from unauthorized fault analyses and repair work.

    This can result in serious injury and damage to property.

    Fault analyses and repair work on the PV system may only be carried out by installers/service technicians from authorized specialist companies in accordance with national standards and regulations.

    NOTE

    Risk due to unauthorized access.

    Incorrectly set parameters can have a negative effect on the public grid and/or the grid power feed operation of the inverter and result in the loss of standard conformity.

    Parameters may only be adjusted by installers/service technicians from authorized specialist companies.

    Do not give the access code to third parties and/or unauthorized persons.

    NOTE

    Risk due to incorrectly set parameters.

    Incorrectly set parameters can have a negative effect on the public grid and/or cause inverter malfunctions and failures and result in the loss of standard conformity.

    Parameters may only be adjusted by installers/service technicians from authorized specialist companies.

    Parameters may only be adjusted if this has been approved or requested by the utility.

    Any parameter adjustments must be made in compliance with nationally applicable standards and/or directives as well as the specifications of the utility.

    The Country Setup menu area is intended exclusively for installers/service technicians from authorized specialist companies. To apply for the access code required for this menu area, see chapter Requesting inverter codes in Solar.SOS.

    The selected country setup for the country in question contains preset parameters in accordance with nationally applicable standards and requirements. Changes may need to be made to the selected country setup depending on local grid conditions and the specifications of the utility.

    1. Settings – User interface of the inverter
    2. Safety and grid requirements

    Country setup

    link_horizontalLink copied

    WARNING

    Danger from unauthorized fault analyses and repair work.

    This can result in serious injury and damage to property.

    Fault analyses and repair work on the PV system may only be carried out by installers/service technicians from authorized specialist companies in accordance with national standards and regulations.

    NOTE

    Risk due to unauthorized access.

    Incorrectly set parameters can have a negative effect on the public grid and/or the grid power feed operation of the inverter and result in the loss of standard conformity.

    Parameters may only be adjusted by installers/service technicians from authorized specialist companies.

    Do not give the access code to third parties and/or unauthorized persons.

    NOTE

    Risk due to incorrectly set parameters.

    Incorrectly set parameters can have a negative effect on the public grid and/or cause inverter malfunctions and failures and result in the loss of standard conformity.

    Parameters may only be adjusted by installers/service technicians from authorized specialist companies.

    Parameters may only be adjusted if this has been approved or requested by the utility.

    Any parameter adjustments must be made in compliance with nationally applicable standards and/or directives as well as the specifications of the utility.

    The Country Setup menu area is intended exclusively for installers/service technicians from authorized specialist companies. To apply for the access code required for this menu area, see chapter Requesting inverter codes in Solar.SOS.

    The selected country setup for the country in question contains preset parameters in accordance with nationally applicable standards and requirements. Changes may need to be made to the selected country setup depending on local grid conditions and the specifications of the utility.

    1. Settings – User interface of the inverter
    2. Safety and grid requirements

    Requesting inverter codes in Solar.SOS

    link_horizontalLink copied

    The Country Setup menu area is intended exclusively for installers/service technicians from authorized specialist companies. The inverter access code required for this menu area can be requested in the Fronius Solar.SOS portal.

    Requesting inverter codes in Fronius Solar.SOS:
    Ihr Browser kann diesen Film leider nicht anzeigen.
    1.
    Open solar-sos.fronius.com in the browser
    2.
    Log in with your Fronius account
    3.
    At the top right, click on the drop-down menu   
    4.
    Select the Show inverter codes menu item
    5.
    A contract page appears on which the request for the access code to change the grid parameters for Fronius inverters is located
    6.
    Accept the terms and conditions of use by checking Yes, I have read and agree to the terms of use and click Confirm & Save
    7.
    After that, the codes can be retrieved in the drop-down menu at the top right under Show inverter codes
    1Open solar-sos.fronius.com in the browser
    2Log in with your Fronius account
    3At the top right, click on the drop-down menu   
    4Select the Show inverter codes menu item
    ✓A contract page appears on which the request for the access code to change the grid parameters for Fronius inverters is located
    5Accept the terms and conditions of use by checking Yes, I have read and agree to the terms of use and click Confirm & Save
    6After that, the codes can be retrieved in the drop-down menu at the top right under Show inverter codes

    CAUTION

    Risk due to unauthorized access.

    Incorrectly set parameters can have a negative effect on the public grid and/or the grid power feed operation of the inverter and result in the loss of standard conformity.

    Parameters may only be adjusted by installers/service technicians from authorized specialist companies.

    Do not give the access code to third parties and/or unauthorized persons.

    1. Settings – User interface of the inverter
    2. Safety and grid requirements

    Absolute Generation Limit

    link_horizontalLink copied

    Activating this function limits the output power of the inverter to the specified value in watts.

    1. Settings – User interface of the inverter
    2. Safety and grid requirements

    Import limitation

    link_horizontalLink copied

    Energy companies or grid operators can prescribe import limitations for inverters. The amperage is limited to the set value.

    1Under Limit select Current Limitation.
    2Enter the limit value in amperes.
    3Click on Save.
    1. Settings – User interface of the inverter
    2. Safety and grid requirements

    Feed-in limit

    link_horizontalLink copied

    Energy companies or utilities can prescribe feed-in limits for inverters (e.g., max. 70% of the kWp or max. 5 kW). The inverter limits the active power at the grid connection point (installation location of the Fronius Smart Meter or primary meter) to the set value.

    The inverter takes account of self-consumption in the household before the power is reduced. An individual limit can be set.

    In order to minimize the yield losses due to the feed-in limit, the power available from the module array can be:

    • Used for controllable system components, such as Fronius Ohmpilot or Fronius Wattpilot
    • Used by loads controlled via I/Os
    • Stored in a battery

    If these possibilities have been exhausted, the power drawn from the module array is reduced to such an extent that the feed-in limit is not exceeded.

    Installation variants with an inverter, Fronius Smart Meter, and system components are listed under Different operating modes.

    Total DC power of the system
    The input field for the total DC power of the entire system in Wp. Always enter this value if the Maximum grid feed-in power is specified in %.

    Power Control disabled
    The inverter converts all available PV energy.

    Power Control enabled
    Feeding in limited with the following selection options:

    • Total Power Limit
      Set the value of the permissible total power of feeding in for the photovoltaic system.
    • Limit per phase – asymmetric generation
      The inverter determines the optimum per phase. The inverter regulates the individual phases in such a way that none of the phases exceeds the set value.
    • Limit per phase – weakest phase
      The inverter measures each individual phase. If the permissible feed-in limit is exceeded on one phase, the inverter symmetrically reduces the total power for all phases until the limit is reached.

    IMPORTANT! Implement the settings for Limit per phase if national standards and regulations require a limitation of the single-phase power. Set the value for the permissible power of feeding in for each phase.

    IMPORTANT! Power Control settings are automatically applied for the dynamic feed-in limit of I/O power management. Total Power Limit is the default configuration.

    Dynamic feed-in limit (Soft Limit)
    If this value is exceeded, the inverter readjusts down to the set value.

    Export Limit Protection (PAV,E protection)
    This function monitors compliance with the feed-in limit. If Dynamic feed-in limit (Soft Limit) is enabled, the inverter controls the power of feeding in in such a way that this function is usually not enabled. If the specified limit values and the switch-off times are exceeded, this protection function disconnects the inverter from the grid.

    The Maximum grid feed-in power (PAV,E) in the case of an asymmetric feed-in (Limit per phase – asymmetric generation or Limit per phase – weakest phase) can be combined with the export limit protection (PAV,E protection) function. The Maximum grid feed-in power is calculated as follows: Maximum grid feed-in power per phase (PAV,E) x 3.

    The export limit protection (PAV,E protection) function is only possible if a Smart Meter IP configured with MQTT is installed at the feed-in point.

    Export Limit Protection (Hard Limit Trip)
    IMPORTANT!
    This function is only available if Dynamic feed-in limit (Soft Limit) is enabled.

    Maximum grid feed-in power
    Input field for the Maximum grid feed-in power in W or % (setting range: ‑10% to 100%).
    If there is no meter in the system or if the primary meter has failed, the inverter limits its output power to the set value.

    If this value is exceeded, the inverter switches off within max. 5 s. This value must be higher than the value set for Export Limit Control (Soft Limit).

    If required, enable the fail-safe function Reduce inverter power to 0% if meter connection has been lost. When this function is enabled, the inverter activates standby mode. No feed-in takes place.

    The use of WiFi for communication between the Fronius Smart Meter and the inverter is not recommended with the fail-safe function activated at the same time. Even short-term disconnections can cause the inverter to shut down. This problem arises with weak WiFi signal strengths, a slow or overloaded WiFi connection, and automatic channel selection of the router.

    1. Settings – User interface of the inverter
    2. Safety and grid requirements

    Feed-in limit – examples

    link_horizontalLink copied

    "Total Power Limit"
    (feed-in limit 0 kW)

    Explanation
    No power (0 kW) may be fed into the public grid at the grid feed-in point. The load requirement in the home network (12 kW) is supplied by the power generated by the inverter.

    "Limit per phase – asymmetric generation"
    (feed-in limit 0 kW per phase) – asymmetric

    Explanation
    The load requirement in the home network per phase is determined and supplied.

    "Limit per phase – asymmetric generation"
    (feed-in limit 1 kW per phase) – asymmetric

    Explanation
    The load requirement in the home network per phase is determined and supplied. In addition, the excess production (1 kW per phase) is fed into the public grid in accordance with the maximum permitted feed-in limit.

    "Limit per phase – weakest phase"
    (feed-in limit 0 kW per phase) – symmetrical

    Explanation
    The weakest phase in the load requirement in the home network is determined (phase 1 = 2 kW). The result of the weakest phase (2 kW) is applied to all phases. Phase 1 (2 kW) can be supplied. Phase 2 (4 kW) and phase 3 (6 kW) cannot be supplied, power from the public grid is required (phase 2 = 2 kW, phase 3 = 4 kW).

    "Limit per phase – weakest phase"
    (feed-in limit 1 kW per phase) – symmetrical

    Explanation
    The weakest phase in the load requirement in the home network is determined (phase 1 = 2 kW) and the max. permitted feed-in limit (1 kW) is added. The result of the weakest phase (2 kW) is applied to all phases. Phase 1 (2 kW) can be supplied. Phase 2 (4 kW) and phase 3 (6 kW) cannot be supplied, power from the public grid is required (phase 2 = 1 kW, phase 3 = 3 kW).

    1. Settings – User interface of the inverter
    2. Safety and grid requirements

    Multiple Inverter Control

    link_horizontalLink copied

    IMPORTANT! To view and change settings in this menu item, select the Technician user. Enter and confirm the password for the Technician user. Settings in this menu area may only be made by technical specialists.

    The inverter can be used as a primary device to control dynamic feed-in limits for additional Fronius inverters (secondary devices) so that feed-in limits prescribed by energy companies or utilities can be centrally managed. This control refers to the Soft Limit feed-in limit, see Feed-in limit. To do so, the following requirements must be met:

    • A Fronius Smart Meter is configured as a primary meter and connected to the master.
    • Power Control is enabled and configured in the Feed-in limit menu on the user interface of the primary device. The power control limit is set to Total Power Limit.
    • Master and secondary device(s) are physically connected to the same network router via LAN.
    • If Use Modbus TCP is enabled, the inverter control via Modbus TCP must be activated and configured for all secondary devices.

    IMPORTANT! Only one primary meter is required for the primary device.

    IMPORTANT! If an inverter with a battery is connected, use this inverter as the primary device for Multiple Inverter Control.

    Example connection diagram for Multiple Inverter Control
    System limits
    • Systems with a maximum of 20 inverters (1 primary device + 19 secondary devices) are supported if the Use Modbus TCP function is enabled. Otherwise, a maximum of one primary device and two secondary devices are supported.
    • The control system is designed for photovoltaic systems with a total output of up to 300 kW.
    • In the case of larger system capacities, the control times in the system are extended.
    • The use of a plant controller is recommended for systems >300 kW.

    External grid and system protection
    Regional standards and guidelines may require the installation of external grid and system protection for systems >30 kVA (see Central grid and system protection).

    Multiple Inverter Control is available for the following device combinations:

    Primary devices

    Secondary devices

    GEN24, Verto, Tauro

    • GEN24
    • Verto
    • Tauro
    • Argeno
    • SnapINverter with Fronius Datamanager 2.0*
    * Up to four additional SnapINverters can be connected to each SnapINverter with Fronius Datamanager 2.0.

    Primary meter
    One Fronius Smart Meter acts as the only primary meter and is connected directly to the primary device. This Smart Meter measures the total output power of all inverters into the grid and passes this information to the primary device.

    Primary device
    Configure the feed-in limit on the user interface of the inverter:

    1In the Safety and Grid Regulations > Feed-in limit menu area, enable the Power Control function and select Total Power Limit.
    2Configure the country-specific settings.
    3In the Safety and Grid Regulations > Multiple Inverter Control menu area, enable the Multiple Inverter Control function.
    The primary device automatically scans the network for available secondary devices.
    ✓A list shows the inverters found.

    To perform the search again, press the Refresh button.   

    If Use Modbus TCP is enabled, it is also possible to select Fronius SnapINverters with Datamanager 2.0 and Fronius Argeno with Use Inverter.

    4Enable Use Inverter against all secondary devices to which a common feed-in limit applies. Click Use all Inverters to enable the function for the primary device and all secondary devices.

    The status of the inverters listed is displayed as follows:
    • Inactive: Secondary device is not configured for the power control or a firmware update is required.
    • Disconnected: Secondary device is configured, network connection not possible.
    • Connected: Secondary device is configured and accessible via the network of the primary device.
    5In the Safety and Grid Regulations > I/O Power Management menu area, set the controlling priorities as follows:
    1. I/O Power Management
    2. Feed-in limit
    3. Modbus Control
    Adding Fronius Argeno and other inverters manually
    1In the Multiple Inverter Control menu, select the Multiple Inverter Control function.
    2Select additional inverters and click + Add.
    3Enter the name, hostname or IP address, and the Modbus address of the secondary device.
    4Click Add.

    For more information on configuring the Fronius Argeno or Fronius Datamanager 2.0 as a secondary device, refer to the respective operating instructions.

    Secondary device
    Each secondary device takes over the settings for the feed-in limit from the primary device. A secondary device does not transmit any data for the feed-in limit to the primary device. To do so, the following requirements must be met:

    • Multiple Inverter Control is enabled and configured in the Multiple Inverter Control menu on the user interface of the primary device.

    Set the following configurations for the feed-in limit on the secondary device:

    User interface secondary device GEN24 / Verto / Tauro
    1Select the user Technician and enter the password for the user Technician.

    Only carry out work steps 2 and 3 if Use Modbus TCP is enabled on the primary device.

    2In the Communication > Modbus menu area, enable TCP Server mode and the Allow Control function.
    3For a fail-safe scenario, in the Safety and Grid Regulations > I/O Power Management menu area, set the controlling priorities as follows:
    1. Modbus Control
    2. Feed-in limit
    3. I/O Power Management
    4In the Safety and Grid Regulations > Feed-in limit menu area, select and edit the following settings:
    • Enable the Power Control function.
    • Select Total Power Limit and specify the Total DC power of the system in watts.
    • Enable the Dynamic feed-in limit (Soft Limit) and enter a value of 0 W for the Maximum grid feed-in power.
    • Enable the Reduce inverter power to 0% if meter connection has been lost function.
    1. Settings – User interface of the inverter
    2. Safety and grid requirements

    I/O Power Management

    link_horizontalLink copied

    General
    Settings relevant to the grid operator are defined as rules under this menu item. This relates to an effective power limit in % or watts and/or a power factor specification. To view and change settings, select the Technician user, and enter and confirm the password. Only technical specialists may make settings in this menu area.

    Under Rules, expand a menu area (e.g., Rule 1). Configure the following settings:

    Limitation

    IMPORTANT!
    A dynamic feed-in limit for several inverters can be configured under Feed-in limit. I/O power management rules are transferred from the inverter (primary device) to connected inverters in the system (secondary devices).

    Select the following rules for power management:

    • I/O Generation Limit (%): The total output power of the connected inverter is statically limited to the defined value of the absolute rated power.
    • Export Limit Control (W): The active power fed in at the grid connection point is limited to the set value (e.g., 5000 watts). The output powers of the inverters (primary and secondary devices) are dynamically adjusted depending on their self-consumption.
    • Shutdown single device: The inverter stops grid power feed operation and switches to standby mode.

    IMPORTANT!
    The rules for shutdown apply to this device and cannot be applied to other inverters in the system.

    Input pattern (assignment of individual I/Os)
    1 click = white, contact open
    2 clicks = blue, contact closed
    3 clicks = gray, not used

     

    Power Factor (cos φ) (define value)

    Impedance response

    • Capacitive
    • Inductive

    DNO Feedback
    If the rule is activated, always configure the DNO Feedback output, e.g., for operating a signal device.

    The Import and Export of defined rules can be carried out in the data format *.fpc. The rules and pin assignments in the following connection examples are not the only possible configurations. For pin assignment, take into account the available connections at the Data communication area and settings of the device configuration.

    If there is an active rule for the control of the inverter, the device indicates this in the overview of the user interface under Device State.

    Controlling Priorities
    Used to set controlling priorities for I/O Power Management (DRM or ripple control receiver), the feed-in limit, and control via Modbus.

    1 = highest priority, 3 = lowest priority

    Local priorities of the I/O power management, the feed-in limit, and the Modbus interface are deactivated by cloud control commands (regulatory purposes and virtual power plants) – see Cloud control – and by backup power.

    In terms of controlling priorities, the device differentiates between power control and inverter shutdown. Inverter shutdown always takes precedence over power control. An inverter shutdown command is always executed and does not need to be prioritized.

    Power control
    • I/O Power Management (DRM/ripple control receiver signal) – according to command
    • Export Limitation (Soft Limit) – always active
    • Modbus (generation limit) – according to command
    Inverter shutdown
    • Shutdown single device
    • Export Limitation (Hard Limit)
    • Modbus (shutdown command) – according to command
    1. Settings – User interface of the inverter
    2. Safety and grid requirements

    4-relay connection example

    link_horizontalLink copied

    Connect the ripple control signal receiver and the I/O terminals of the inverter to one another as shown in the connection diagram.
    For distances greater than 10 m between the inverter and the ripple control signal receiver, use a shielded data communication cable (CAT 5 or higher) with twisted cable pairs. Connect the shielding on one side to the terminal of the data communication area (SHIELD).

    (1)
    Ripple control signal receiver with 4 relays for effective power limitation.
    (2)
    I/O connection terminals of the data communication area.
    Use pre-configured file for 4-relay operation:
    1Download the file (.fpc) under 4-relay operation to the mobile device.
    2Upload the file (.fpc) in the I/O Power Management menu area by clicking the Import button.
    3Click Save.
    ✓The settings for 4-relay operation are saved.
    1. Settings – User interface of the inverter
    2. Safety and grid requirements

    I/O power management settings – 4 relay example

    link_horizontalLink copied
    1. Settings – User interface of the inverter
    2. Safety and grid requirements

    3-relay connection example

    link_horizontalLink copied

    Connect the ripple control signal receiver and the I/O terminals of the inverter to one another as shown in the connection diagram.
    For distances greater than 10 m between the inverter and the ripple control signal receiver, use a shielded data communication cable (CAT 5 or higher) with twisted cable pairs. Connect the shielding on one side to the terminal of the data communication area (SHIELD).

    (1)
    Ripple control signal receiver with 3 relays for effective power limitation.
    (2)
    I/O connection terminals of the data communication area.
    Use pre-configured file for 3-relay operation:
    1Download the file (.fpc) under 3-relay operation to the mobile device.
    2Upload the file (.fpc) in the I/O Power Management menu area by clicking the Import button.
    3Click Save.
    ✓The settings for 3-relay operation are saved.
    1. Settings – User interface of the inverter
    2. Safety and grid requirements

    I/O power management settings – 3 relay example

    link_horizontalLink copied
    1. Settings – User interface of the inverter
    2. Safety and grid requirements

    2-relay connection example

    link_horizontalLink copied

    Connect the ripple control signal receiver and the I/O terminals of the inverter to one another as shown in the connection diagram.
    For distances greater than 10 m between the inverter and the ripple control signal receiver, use a shielded data communication cable (CAT 5 or higher) with twisted cable pairs. Connect the shielding on one side to the terminal of the data communication area (SHIELD).

    (1)
    Ripple control signal receiver with 2 relays for effective power limitation.
    (2)
    I/O connection terminals of the data communication area.
    Use pre-configured file for 2-relay operation:
    1Download the file (.fpc) under 2-relay operation to the mobile device.
    2Upload the file (.fpc) in the I/O Power Management menu area by clicking the Import button.
    3Click Save.
    ✓The settings for 2-relay operation are saved.
    1. Settings – User interface of the inverter
    2. Safety and grid requirements

    I/O power management settings – 2 relay example

    link_horizontalLink copied
    1. Settings – User interface of the inverter
    2. Safety and grid requirements

    1-relay connection example

    link_horizontalLink copied

    Connect the ripple control signal receiver and the I/O terminals of the inverter to one another as shown in the connection diagram.
    For distances greater than 10 m between the inverter and the ripple control signal receiver, use a shielded data communication cable (CAT 5 or higher) with twisted cable pairs. Connect the shielding on one side to the terminal of the data communication area (SHIELD).

    (1)
    Ripple control signal receiver with 1 relay for effective power limitation.
    (2)
    I/O connection terminals of the data communication area.
    Use pre-configured file for 1-relay operation:
    1Download the file (.fpc) under 1-relay operation to the mobile device.
    2Upload the file (.fpc) in the I/O Power Management menu area by clicking the Import button.
    3Click Save.
    ✓The settings for 1-relay operation are saved.
    1. Settings – User interface of the inverter
    2. Safety and grid requirements

    I/O power management settings – 1 relay example

    link_horizontalLink copied
    1. Settings – User interface of the inverter
    2. Safety and grid requirements

    Autotest
    (CEI 0-21)

    link_horizontalLink copied

    Description
    The Autotest makes it possible to check the Italian protection function, required by the applicable standard for monitoring the voltage and frequency limit values of the inverter during commissioning. In normal operation, the inverter constantly checks the real-time actual value of the voltage and frequency of the grid.
    Once the Autotest has started, different individual tests are carried out automatically, in succession. Depending on the grid conditions, the duration of the test is approximately 15 minutes.

    IMPORTANT!
    In Italy, the inverter may only be commissioned following a successfully completed Autotest (CEI 0-21). If an Autotest is not passed, grid power feed operation may not take place. Once the Autotest is started, it must be completed successfully. The Autotest cannot be started during backup power mode.

    Umax

    Test for checking the maximum voltage in the phase conductors

    Umin

    Test for checking the minimum voltage in the phase conductors

    fmax

    Test for checking the maximum mains frequency

    fmin

    Test for checking the minimum mains frequency

    fmax alt

    Test for checking an alternative maximum mains frequency

    fmin alt

    Test for checking an alternative minimum mains frequency

    U outer min

    Test for checking the minimum outer voltages

    U longT.

    Test for checking the 10 min. voltage average

    Print to PDF
    1Click the Print to PDF button.
    2Enter the file name into the input field and click on the Print button.
    ✓The PDF is created and shown.

    Note on the Autotest
    The limit values are set in the Safety and Grid Regulations > Country Setup> Grid Support Functions menu area.
    The Country Setup menu area is intended exclusively for installers/service technicians from authorized specialist companies. The inverter access code required for this menu area can be requested in the Fronius Solar.SOS portal (see chapter Requesting inverter codes in Solar.SOS on page (→)).

    1. Settings – User interface of the inverter
    2. Safety and grid requirements

    Connecting the ripple control receiver with several inverters

    link_horizontalLink copied

    The grid operator may request the connection of one or more inverters to a ripple control receiver in order to limit the active power and/or the power factor of the photovoltaic system.

    Connection diagram for ripple control receiver with several inverters
    Connect the following Fronius inverters to a ripple control receiver via a distributor (coupling relay):
    • Symo GEN24
    • Primo GEN24
    • Tauro
    • Verto
    • SnapINverter (only devices with Fronius Datamanager 2.0)

    On the user interface of each inverter connected to the ripple control receiver, set the same parameters for I/O power management.

    Appendix

    link_horizontalLink copied

    Service, maintenance and disposal

    General

    The inverter is designed so that it does not require additional maintenance work. Nevertheless, a few points must be considered during operation to ensure that the inverter works perfectly.

    1. Appendix

    Service, maintenance and disposal

    link_horizontalLink copied

    General

    The inverter is designed so that it does not require additional maintenance work. Nevertheless, a few points must be considered during operation to ensure that the inverter works perfectly.

    1. Appendix
    2. Service, maintenance and disposal

    General

    link_horizontalLink copied

    The inverter is designed so that it does not require additional maintenance work. Nevertheless, a few points must be considered during operation to ensure that the inverter works perfectly.

    1. Appendix
    2. Service, maintenance and disposal

    Maintenance

    link_horizontalLink copied

    Maintenance and service work may only be carried out by a technical specialist.

    1. Appendix
    2. Service, maintenance and disposal

    Cleaning

    link_horizontalLink copied

    Wipe the inverter, if necessary, with a damp cloth.
    Do not use cleaning agents, scouring agents, solvents, or similar products to clean the inverter.

    1. Appendix
    2. Service, maintenance and disposal

    Operation in dusty environments

    link_horizontalLink copied

    NOTE

    If the inverter is operated in dusty environments, dirt may build up on the heat sink and fan.

    This may result in a loss of power due to insufficient cooling of the inverter.

    Make sure that the ambient air can always flow through the inverter's ventilation slots unimpeded.

    Remove any build-ups of dirt from the heat sink and the fan.

    1

    Switch off power to the inverter and wait for the capacitors to discharge (2 minutes) and the fan to shut down.
    Turn the DC disconnector to the "off" switch setting.

    2

    Remove any build-up of dirt on the heat sink and fan using compressed air, a cloth, or a brush.

    NOTE

    Risk due to damage to the fan bearing in the event of incorrect cleaning.

    Excessive speeds and the application of pressure to the fan bearing can cause damage.

    Block the fan and clean with compressed air.

    When using a cloth or brush, clean the fan without applying any pressure.

    To start up the inverter again, follow the steps listed above in reverse order.

    1. Appendix
    2. Service, maintenance and disposal

    Safety

    link_horizontalLink copied

    WARNING

    Danger from mains voltage and DC voltage from PV modules.

    This can result in serious injury and damage to property.

    The connection area must only be opened by an authorized electrician.

    The separate power stage set area must only be opened by Fronius-trained service technicians.

    Prior to any connection work, disconnect the inverter on the AC side and the DC side.

    WARNING

    Danger due to residual voltage from capacitors.

    This can result in serious injury and damage to property.

    Allow the capacitors of the inverter to discharge (2 minutes).

    1. Appendix
    2. Service, maintenance and disposal

    Disposal

    link_horizontalLink copied
    In accordance with the EU Directive and national law, the following products must be disposed of separately and recycled:
    • Waste electrical and electronic equipment
    • Used batteries (portable batteries, industrial batteries)

    Used equipment and batteries must be returned to the distributor or an authorized local collection system. Do not dispose of batteries with domestic waste. Protect batteries from high temperatures, direct sunlight, moisture and corrosive environments.

    Arrange for the safe collection and proper disposal of damaged, leaking or used batteries by a battery recycling company or the Fronius Service Partner.

    In addition, it should be noted that batteries contain substances that, if disposed of improperly, can have a significant negative impact on the environment as well as on human health and the safety of persons, in particular due to the leakage of hazardous substances such as heavy metals or electrolytes, which can contaminate soil, water and air.

    This ensures environmental protection and the sustainable use of natural resources.

    Packaging materials
    • Collect separately
    • Observe local regulations
    • Compress the cardboard box to reduce volume
    1. Appendix

    Warranty provisions

    link_horizontalLink copied

    Warranty

    Detailed warranty conditions specific to your country can be found at https://www.fronius.com/en/download-center?searchword=Warranty+conditions .

    If there is a warranty for the relevant product, register the product at https://warranty.fronius.com/ and activate or extend the warranty.

    1. Appendix
    2. Warranty provisions

    Warranty

    link_horizontalLink copied

    Detailed warranty conditions specific to your country can be found at https://www.fronius.com/en/download-center?searchword=Warranty+conditions .

    If there is a warranty for the relevant product, register the product at https://warranty.fronius.com/ and activate or extend the warranty.

    1. Appendix

    Components for switching to backup power

    link_horizontalLink copied

    Components for automatic backup power changeover to Full Backup

    Fronius components
    With the following Fronius components, no additional components are required for the automatic changeover to backup power. If components are not available depending on national availability, automatic changeover to backup power can be implemented with the following third-party components.

     Product

    Item number

    Fronius Backup Controller 3P-35A*

    4,240,047,CK

    Fronius Smart Meter 63A-3

    43,0001,1473

    Fronius Smart Meter 50kA-3

    43,0001,1478

    Fronius Smart Meter TS 65A-3

    43,0001,0044

    Fronius Smart Meter TS 5kA-3

    43,0001,0046

    Fronius Smart Meter WR

    43,0001,3591

    * Only compatible with Fronius Verto 15.0 - 20.0 Plus.

    Third-party components
    Manufacturers/types other than the product examples listed are permissible, provided that they meet the same technical and functional requirements.

    Grid and system protection

    Manufacturer/type

    Bender GmbH & Co. KG VMD460-NA-D-2
    Tele Haase Steuergeräte Ges.m.b.H. RE-NA003-M64

    K1 and K2 - AC installation contactor with auxiliary contact

    Number of pins

    3-pin or 4-pin
    (depending on the cabling variant)

    Rated current

    depending on the house connection

    Coil voltage

    230 VAC

    Rated frequency

    50 / 60 Hz

    Coil fuse

    6 A

    Min. short circuit current

    3 kA (contacts)

    Test standard

    IEC 60947-4-1

    Auxiliary contact

    Number of NC contacts

    1

    Switching voltage

    12 - 230 V @ 50 / 60 Hz

    Min. nominal current

    1 A

    Min. short circuit current

    1 kA

    Manufacturer/type

    ISKRA IK63-40 / Schrack BZ326461

    Buffer power supply - Fault Ride Through cabling variant

    Manufacturer/type

    BKE JS-20-240/DIN_BUF

    K1 and K2 - DC installation contactor with auxiliary contact (Fault Ride Through)

    Number of pins

    3-pin or 4-pin
    (depending on the cabling variant)

    Rated current

    depending on the house connection

    Coil voltage

    24 VDC

    Min. short circuit current

    3 kA (contacts)

    Test standard

    IEC 60947-4-1

    Auxiliary contact

    Number of NC contacts

    1

    Switching voltage

    24 VDC

    Min. nominal current

    1 A

    Min. short circuit current

    1 kA

    Manufacturer/type

    Finder 22.64.0.024.4710

    K3 - Modular relay

    Number of changeover contacts

    2

    Coil voltage

    12 VDC

    Test standard

    IEC 60947-4-1

    Manufacturer/type

    Finder 22.23.9.012.4000 / Schrack relay RT424012 (bracket RT17017, relay base RT78725)

    K4 and K5 - Installation contactor

    Number of NC contacts

    2 (25 A)

    Coil voltage

    230 V AC (2P)

    Rated frequency

    50 / 60 Hz

    Coil fuse

    6 A

    Min. short circuit current

    3 kA (contacts)

    Test standard

    IEC 60947-4-1

    Manufacturer/type

    ISKRA IKA225-02

    1. Appendix
    2. Components for switching to backup power

    Components for automatic backup power changeover to Full Backup

    link_horizontalLink copied

    Fronius components
    With the following Fronius components, no additional components are required for the automatic changeover to backup power. If components are not available depending on national availability, automatic changeover to backup power can be implemented with the following third-party components.

     Product

    Item number

    Fronius Backup Controller 3P-35A*

    4,240,047,CK

    Fronius Smart Meter 63A-3

    43,0001,1473

    Fronius Smart Meter 50kA-3

    43,0001,1478

    Fronius Smart Meter TS 65A-3

    43,0001,0044

    Fronius Smart Meter TS 5kA-3

    43,0001,0046

    Fronius Smart Meter WR

    43,0001,3591

    * Only compatible with Fronius Verto 15.0 - 20.0 Plus.

    Third-party components
    Manufacturers/types other than the product examples listed are permissible, provided that they meet the same technical and functional requirements.

    Grid and system protection

    Manufacturer/type

    Bender GmbH & Co. KG VMD460-NA-D-2
    Tele Haase Steuergeräte Ges.m.b.H. RE-NA003-M64

    K1 and K2 - AC installation contactor with auxiliary contact

    Number of pins

    3-pin or 4-pin
    (depending on the cabling variant)

    Rated current

    depending on the house connection

    Coil voltage

    230 VAC

    Rated frequency

    50 / 60 Hz

    Coil fuse

    6 A

    Min. short circuit current

    3 kA (contacts)

    Test standard

    IEC 60947-4-1

    Auxiliary contact

    Number of NC contacts

    1

    Switching voltage

    12 - 230 V @ 50 / 60 Hz

    Min. nominal current

    1 A

    Min. short circuit current

    1 kA

    Manufacturer/type

    ISKRA IK63-40 / Schrack BZ326461

    Buffer power supply - Fault Ride Through cabling variant

    Manufacturer/type

    BKE JS-20-240/DIN_BUF

    K1 and K2 - DC installation contactor with auxiliary contact (Fault Ride Through)

    Number of pins

    3-pin or 4-pin
    (depending on the cabling variant)

    Rated current

    depending on the house connection

    Coil voltage

    24 VDC

    Min. short circuit current

    3 kA (contacts)

    Test standard

    IEC 60947-4-1

    Auxiliary contact

    Number of NC contacts

    1

    Switching voltage

    24 VDC

    Min. nominal current

    1 A

    Min. short circuit current

    1 kA

    Manufacturer/type

    Finder 22.64.0.024.4710

    K3 - Modular relay

    Number of changeover contacts

    2

    Coil voltage

    12 VDC

    Test standard

    IEC 60947-4-1

    Manufacturer/type

    Finder 22.23.9.012.4000 / Schrack relay RT424012 (bracket RT17017, relay base RT78725)

    K4 and K5 - Installation contactor

    Number of NC contacts

    2 (25 A)

    Coil voltage

    230 V AC (2P)

    Rated frequency

    50 / 60 Hz

    Coil fuse

    6 A

    Min. short circuit current

    3 kA (contacts)

    Test standard

    IEC 60947-4-1

    Manufacturer/type

    ISKRA IKA225-02

    1. Appendix
    2. Components for switching to backup power

    Components for manual backup power changeover to Full Backup

    link_horizontalLink copied

    Product

    Item number

    Fronius Smart Meter 63A-3

    43,0001,1473

    Fronius Smart Meter TS 65A-3

    43,0001,0044

    Fronius Backup Switch 1P/3P-63A

    4,050,221

    Fronius Backup Switch 1PN/3PN-63A

    4,050,220

    1. Appendix

    Status codes and remedy

    link_horizontalLink copied

    Display

    Status codes are displayed on the user interface of the inverter in the System > Event Log menu area or in the user menu under Notifications and in Fronius Solar.web*.

    *
    If configured accordingly, see chapter Fronius Solar.web on page (→).
    1. Appendix
    2. Status codes and remedy

    Display

    link_horizontalLink copied

    Status codes are displayed on the user interface of the inverter in the System > Event Log menu area or in the user menu under Notifications and in Fronius Solar.web*.

    *
    If configured accordingly, see chapter Fronius Solar.web on page (→).
    1. Appendix
    2. Status codes and remedy

    Status codes

    link_horizontalLink copied
    1030 – WSD Open (operating LED: flashes red)
    Cause:A device that is connected in the WSD chain has interrupted the signal line (e.g., surge protection device) or the bypass installed ex works as standard has been removed and no trigger device has been installed.
    Remedy:If the SPD surge protection device has tripped, the inverter must be repaired by an authorized specialist.
    OR:Install the bypass installed ex works as standard or a trigger device.
    OR:Turn the WSD (wired shutdown) switch to position 1 (WSD primary device).

    WARNING

    Danger from work that is not carried out properly.

    This can result in serious injury and damage to property.

    The installation and connection of an SPD surge protection device may only be carried out by Fronius-trained service personnel in accordance with the technical specifications.

    Observe safety rules.

    1. Appendix

    Technical data

    link_horizontalLink copied

    Verto Plus 15.0

     

    DC input data

    Maximum input voltage
    (at 1000 W/m²/-10 °C in an open circuit)

    1000 VDC

    Start-up input voltage

    150 VDC

    MPP voltage range

    150–870 VDC

    MPP voltage range (at full power)

    210–870 VDC

    Number of MPP controllers

    3

    Maximum input current (IDC max)
    PV1/PV2/PV3
    per string


    28/28/28 A
    28 A

    Maximum total short circuit current 8)
    PV1/PV2/PV3
    per string

    150 A
    50/50/50 A
    50 A

    Total maximum array power (PPV max)
    PV1/PV2/PV3

    22.5 kWp
    20/20/20 kWp

    DC overvoltage category

    2

    Max. inverter backfeed current to the array 3)

    0 A4)

    Maximum capacity of the PV generator against earth

    3000 nF

    Limit value of the insulation resistance test between module array and ground (on delivery) 7)

    34 kΩ

    Adjustable range of the insulation resistance test between module array and ground 6)

    34–10,000 kΩ

    Limit value and trip time of sudden residual current monitoring (on delivery)

    30 mA/300 ms
    60 mA/150 ms
    90 mA/40 ms

    Limit value and trip time of continuous residual current monitoring (on delivery)

    300 mA/300 ms

    Adjustable range of continuous residual current monitoring 6)

    30–1000 mA

    Cyclical repetition of insulation resistance test (on delivery)

    24 h

    Adjustable range for cyclical repetition of insulation resistance test

    -

    DC input data
    Battery 8)

    Maximum voltage 11)

    700 V

    Min. voltage

    150 V

    Maximum current

    50 A

    Maximum output

    22.5 kW

    DC inputs

    1

    Output data

    Grid voltage range

    176–528 VAC

    Rated grid voltage

    220/230 VAC 1)
    253/257 VAC 1)

    Rated power

    15 kW

    Maximum usable DC power – inverter 10)

    22.5 kW

    Rated apparent power

    15 kVA

    Rated frequency

    50/60 Hz 1)

    Maximum output current/phase

    32.3 A

    Initial symmetrical short circuit current/phase IK"

    32.3 A

    Power factor (cos phi)

    0-1 ind./cap.2)

    Grid connection

    3~ (N)PE 380/220 VAC
    3~ (N)PE 400/230 VAC
    3~ (N)PE 440/253 VAC
    3~ (N)PE 480/277 VAC

    Earthing systems

    TT (allowed if UN_PE < 30 V)
    TN-S (allowed)
    TN-C-S (allowed)
    IT (not allowed)

    Maximum output power

    15 kW

    Rated output current/phase

    22.7 / 21.7 / 19.7 / 18.1 A

    Total harmonic distortion

    < 3%

    AC overvoltage category

    3

    Current (inrush) 5)

    24.72 A peak /
    6.82 A rms over 1.99 ms 4)

    Maximum output fault current/duration

    24.38 A / 38.72 ms

    AC output data
    Full Backup 8)

    Maximum output current/phase
    3 phases
    1 phase

    32.3 A
    43.5 A (AC boost for 5–10 s)
    32 A (AC boost for 5–10 s)

    Rated power

    15 kW
    30 kVA (AC boost for 5–10 s)

    Rated output current (per phase)

    32.3 A (maximum asymmetry 25 A)

    Nominal grid voltage

    3~ (N)PE 380/220 VAC
    3~ (N)PE 400/230 VAC
    3~ (N)PE 440/253 VAC
    3~ (N)PE 480/277 VAC

    Nominal frequency for Full Backup

    53 / 63 Hz 1)

    Switching time

    < 35 s

    Switching time with rapid switch mode

    < 20 ms

    Power factor cos phi 2)

    0-1 ind./cap.2)

    General data

    Night-time power loss = standby consumption

    16 W

    European Efficiency (180 / 600 / 870 VDC)

    96.65% / 97.35% / 96.58%

    Maximum efficiency

    98.03%

    Protective class

    1

    EMC emission class

    B

    Pollution degree

    3

    Permitted ambient temperature

    -40 °C to +60 °C

    Permitted storage temperature

    -40 °C to +70 °C

    Relative humidity

    0–100%

    Sound pressure level

    50.3 dB(A) (ref. 20 µPA)

    Ingress protection rating

    IP66

    Dimensions (height × width × depth)

    865 × 574 × 279 mm

    Weight

    43 kg

    Weight with packaging

    50.7 kg

    Inverter topology

    Non-insulated, transformerless

    1. Appendix
    2. Technical data

    Verto Plus 15.0

    link_horizontalLink copied

     

    DC input data

    Maximum input voltage
    (at 1000 W/m²/-10 °C in an open circuit)

    1000 VDC

    Start-up input voltage

    150 VDC

    MPP voltage range

    150–870 VDC

    MPP voltage range (at full power)

    210–870 VDC

    Number of MPP controllers

    3

    Maximum input current (IDC max)
    PV1/PV2/PV3
    per string


    28/28/28 A
    28 A

    Maximum total short circuit current 8)
    PV1/PV2/PV3
    per string

    150 A
    50/50/50 A
    50 A

    Total maximum array power (PPV max)
    PV1/PV2/PV3

    22.5 kWp
    20/20/20 kWp

    DC overvoltage category

    2

    Max. inverter backfeed current to the array 3)

    0 A4)

    Maximum capacity of the PV generator against earth

    3000 nF

    Limit value of the insulation resistance test between module array and ground (on delivery) 7)

    34 kΩ

    Adjustable range of the insulation resistance test between module array and ground 6)

    34–10,000 kΩ

    Limit value and trip time of sudden residual current monitoring (on delivery)

    30 mA/300 ms
    60 mA/150 ms
    90 mA/40 ms

    Limit value and trip time of continuous residual current monitoring (on delivery)

    300 mA/300 ms

    Adjustable range of continuous residual current monitoring 6)

    30–1000 mA

    Cyclical repetition of insulation resistance test (on delivery)

    24 h

    Adjustable range for cyclical repetition of insulation resistance test

    -

    DC input data
    Battery 8)

    Maximum voltage 11)

    700 V

    Min. voltage

    150 V

    Maximum current

    50 A

    Maximum output

    22.5 kW

    DC inputs

    1

    Output data

    Grid voltage range

    176–528 VAC

    Rated grid voltage

    220/230 VAC 1)
    253/257 VAC 1)

    Rated power

    15 kW

    Maximum usable DC power – inverter 10)

    22.5 kW

    Rated apparent power

    15 kVA

    Rated frequency

    50/60 Hz 1)

    Maximum output current/phase

    32.3 A

    Initial symmetrical short circuit current/phase IK"

    32.3 A

    Power factor (cos phi)

    0-1 ind./cap.2)

    Grid connection

    3~ (N)PE 380/220 VAC
    3~ (N)PE 400/230 VAC
    3~ (N)PE 440/253 VAC
    3~ (N)PE 480/277 VAC

    Earthing systems

    TT (allowed if UN_PE < 30 V)
    TN-S (allowed)
    TN-C-S (allowed)
    IT (not allowed)

    Maximum output power

    15 kW

    Rated output current/phase

    22.7 / 21.7 / 19.7 / 18.1 A

    Total harmonic distortion

    < 3%

    AC overvoltage category

    3

    Current (inrush) 5)

    24.72 A peak /
    6.82 A rms over 1.99 ms 4)

    Maximum output fault current/duration

    24.38 A / 38.72 ms

    AC output data
    Full Backup 8)

    Maximum output current/phase
    3 phases
    1 phase

    32.3 A
    43.5 A (AC boost for 5–10 s)
    32 A (AC boost for 5–10 s)

    Rated power

    15 kW
    30 kVA (AC boost for 5–10 s)

    Rated output current (per phase)

    32.3 A (maximum asymmetry 25 A)

    Nominal grid voltage

    3~ (N)PE 380/220 VAC
    3~ (N)PE 400/230 VAC
    3~ (N)PE 440/253 VAC
    3~ (N)PE 480/277 VAC

    Nominal frequency for Full Backup

    53 / 63 Hz 1)

    Switching time

    < 35 s

    Switching time with rapid switch mode

    < 20 ms

    Power factor cos phi 2)

    0-1 ind./cap.2)

    General data

    Night-time power loss = standby consumption

    16 W

    European Efficiency (180 / 600 / 870 VDC)

    96.65% / 97.35% / 96.58%

    Maximum efficiency

    98.03%

    Protective class

    1

    EMC emission class

    B

    Pollution degree

    3

    Permitted ambient temperature

    -40 °C to +60 °C

    Permitted storage temperature

    -40 °C to +70 °C

    Relative humidity

    0–100%

    Sound pressure level

    50.3 dB(A) (ref. 20 µPA)

    Ingress protection rating

    IP66

    Dimensions (height × width × depth)

    865 × 574 × 279 mm

    Weight

    43 kg

    Weight with packaging

    50.7 kg

    Inverter topology

    Non-insulated, transformerless

    1. Appendix
    2. Technical data

    Verto Plus 17.5

    link_horizontalLink copied

     

    DC input data

    Maximum input voltage
    (at 1000 W/m²/-10 °C in an open circuit)

    1000 VDC

    Start-up input voltage

    150 VDC

    MPP voltage range

    150–870 VDC

    MPP voltage range (at full power)

    245–870 VDC

    Number of MPP controllers

    3

    Maximum input current (IDC max)
    PV1/PV2/PV3
    per string


    28/28/28 A
    28 A

    Maximum total short circuit current 8)
    PV1/PV2/PV3
    per string

    150 A
    50/50/50 A
    50 A

    Total maximum array power (PPV max)
    PV1/PV2/PV3

    26.25 kWp
    20/20/20 kWp

    DC overvoltage category

    2

    Max. inverter backfeed current to the array 3)

    0 A4)

    Maximum capacity of the PV generator against earth

    3600 nF

    Limit value of the insulation resistance test between module array and ground (on delivery) 7)

    34 kΩ

    Adjustable range of the insulation resistance test between module array and ground 6)

    34–10,000 kΩ

    Limit value and trip time of sudden residual current monitoring (on delivery)

    30 mA/300 ms
    60 mA/150 ms
    90 mA/40 ms

    Limit value and trip time of continuous residual current monitoring (on delivery)

    300 mA/300 ms

    Adjustable range of continuous residual current monitoring 6)

    30–1000 mA

    Cyclical repetition of insulation resistance test (on delivery)

    24 h

    Adjustable range for cyclical repetition of insulation resistance test

    -

    DC input data
    Battery 8)

    Maximum voltage 11)

    700 V

    Minimum voltage

    150 V

    Maximum current

    50 A

    Maximum output

    26.25 kW

    DC inputs

    1

    Output data

    Grid voltage range

    176–528 VAC

    Rated grid voltage

    220/230 VAC 1)
    253/257 VAC 1)

    Rated power

    17.5 kW

    Maximum usable DC power – inverter 10)

    26.25 kW

    Rated apparent power

    17.5 kVA

    Rated frequency

    50/60 Hz 1)

    Maximum output current/phase

    32.3 A

    Initial symmetrical short circuit current/phase IK"

    32.3 A

    Power factor (cos phi)

    0-1 ind./cap.2)

    Grid connection

    3~ (N)PE 380/220 VAC
    3~ (N)PE 400/230 VAC
    3~ (N)PE 440/253 VAC
    3~ (N)PE 480/277 VAC

    Earthing systems

    TT (allowed if UN_PE < 30 V)
    TN-S (allowed)
    TN-C-S (allowed)
    IT (not allowed)

    Maximum output power

    17.5 kW

    Rated output current/phase

    26.5 / 25.4 / 23.0 / 21.1 A

    Total harmonic distortion

    < 3%

    AC overvoltage category

    3

    Current (inrush) 5)

    24.72 A peak / 6.82 A rms over 1.99 ms 4)

    Maximum output fault current/duration

    24.38 A / 38.72 ms

    AC output data
    Full Backup 8)

    Maximum output current/phase
    3 phases
    1 phase

    32.3 A
    43.5 A (AC boost for 5–10 s)
    32 A (AC boost for 5–10 s)

    Rated power

    17.5 kW
    30 kVA (AC boost for 5–10 s)

    Rated output current (per phase)

    32.3 A (maximum asymmetry 25 A)

    Nominal grid voltage

    3~ (N)PE 380/220 VAC
    3~ (N)PE 400/230 VAC
    3~ (N)PE 440/253 VAC
    3~ (N)PE 480/277 VAC

    Nominal frequency for Full Backup

    53/63 Hz 1)

    Switching time

    < 35 s

    Switching time with rapid switch mode

    < 20 ms

    Power factor cos phi 2)

    0-1 ind./cap.2)

    General data

    Night-time power loss = standby consumption

    16 W

    European Efficiency (210 / 600 / 870 VDC)

    96.87% / 97.54% / 96.88%

    Maximum efficiency

    98.06%

    Protective class

    1

    EMC emission class

    B

    Pollution degree

    3

    Permitted ambient temperature

    -40 °C to +60 °C

    Permitted storage temperature

    -40 °C to +70 °C

    Relative humidity

    0–100%

    Sound pressure level

    50.3 dB(A) (ref. 20 µPA)

    Ingress protection rating

    IP66

    Dimensions (height × width × depth)

    865 × 574 × 279 mm

    Weight

    43 kg

    Weight with packaging

    50.7 kg

    Inverter topology

    Non-insulated, transformerless

    1. Appendix
    2. Technical data

    Verto Plus 20.0

    link_horizontalLink copied

     

    DC input data

    Maximum input voltage
    (at 1000 W/m²/-10 °C in an open circuit)

    1000 VDC

    Start-up input voltage

    150 VDC

    MPP voltage range

    150–870 VDC

    MPP voltage range (at full power)

    275–870 VDC

    Number of MPP controllers

    3

    Maximum input current (IDC max)
    PV1/PV2/PV3
    per string


    28/28/28 A
    28 A

    Maximum total short circuit current 8)
    PV1/PV2/PV3
    per string

    150 A
    50/50/50 A
    50 A

    Total maximum array power (PPV max)
    PV1/PV2/PV3

    30.0 kWp
    20/20/20 kWp

    DC overvoltage category

    2

    Max. inverter backfeed current to the array 3)

    0 A4)

    Maximum capacity of the PV generator against earth

    5000 nF

    Limit value of the insulation resistance test between module array and ground (on delivery) 7)

    34 kΩ

    Adjustable range of the insulation resistance test between module array and ground 6)

    34–10,000 kΩ

    Limit value and trip time of sudden residual current monitoring (on delivery)

    30 mA/300 ms
    60 mA/150 ms
    90 mA/40 ms

    Limit value and trip time of continuous residual current monitoring (on delivery)

    300 mA/300 ms

    Adjustable range of continuous residual current monitoring 6)

    30–1000 mA

    Cyclical repetition of insulation resistance test (on delivery)

    24 h

    Adjustable range for cyclical repetition of insulation resistance test

    -

    DC input data
    Battery 8)

    Maximum voltage 11)

    700 V

    Min. voltage

    150 V

    Maximum current

    50 A

    Maximum output

    30 kW

    DC inputs

    1

    Output data

    Grid voltage range

    176–528 VAC

    Rated grid voltage

    220/230 VAC 1)
    253/257 VAC 1)

    Rated power

    20 kW

    Maximum usable DC power – inverter 10)

    30 kW

    Rated apparent power

    20 kVA

    Rated frequency

    50/60 Hz 1)

    Maximum output current/phase

    32.3 A

    Initial short circuit current/phase IK

    32.3 A

    Power factor (cos phi)

    0-1 ind./cap.2)

    Grid connection

    3~ (N)PE 380/220 VAC
    3~ (N)PE 400/230 VAC
    3~ (N)PE 440/253 VAC
    3~ (N)PE 480/277 VAC

    Earthing systems

    TT (allowed if UN_PE < 30 V)
    TN-S (allowed)
    TN-C-S (allowed)
    IT (not allowed)

    Maximum output power

    20 kW

    Rated output current/phase

    30.3 / 29 / 26.2 / 24.1 A

    Total harmonic distortion

    < 3%

    AC overvoltage category

    3

    Current (inrush) 5)

    24.72 A peak / 6.82 A rms over 1.99 ms 4)

    Maximum output fault current/duration

    24.38 A / 38.72 ms

    AC output data
    Full Backup 8)

    Maximum output current/phase
    3 phases
    1 phase

    32.3 A
    43.5 A (AC boost for 5–10 s)
    32 A (AC boost for 5–10 s)

    Rated power

    20 kW
    30 kVA (AC boost for 5–10 s)

    Rated output current (per phase)

    32.3 A (maximum asymmetry 25 A)

    Nominal grid voltage

    3~ (N)PE 380/220 VAC
    3~ (N)PE 400/230 VAC
    3~ (N)PE 440/253 VAC
    3~ (N)PE 480/277 VAC

    Nominal frequency for Full Backup

    53/63 Hz 1)

    Switching time

    < 35 s

    Switching time with rapid switch mode

    < 20 ms

    Power factor cos phi 2)

    0-1 ind./cap.2)

    General data

    Night-time power loss = standby consumption

    16 W

    European Efficiency (240 / 600 / 870 VDC)

    97.08% / 97.95% / 96.93%

    Maximum efficiency

    98.15%

    Protective class

    1

    EMC emission class

    B

    Pollution degree

    3

    Permitted ambient temperature

    -40 °C to +60 °C

    Permitted storage temperature

    -40 °C to +70 °C

    Relative humidity

    0–100%

    Sound pressure level

    50.3 dB(A) (ref. 20 µPA)

    Ingress protection rating

    IP66

    Dimensions (height × width × depth)

    865 × 574 × 279 mm

    Weight

    43 kg

    Weight with packaging

    50.7 kg

    Inverter topology

    Non-insulated, transformerless

    1. Appendix
    2. Technical data

    Verto Plus 25.0

    link_horizontalLink copied

     

    DC input data

    Maximum input voltage
    (at 1000 W/m²/-10 °C in an open circuit)

    1000 VDC

    Start-up input voltage

    150 VDC

    MPP voltage range

    150–870 VDC

    MPP voltage range (at full power)

    350–870 VDC

    Number of MPP controllers

    3

    Maximum input current (IDC max)
    PV1/PV2/PV3
    per string


    28/28/28 A
    28 A

    Maximum total short circuit current 8)
    PV1/PV2/PV3
    per string

    150 A
    50/50/50 A
    50 A

    Total maximum array power (PPV max)
    PV1/PV2/PV3

    37.5 kWp
    20/20/20 kWp

    DC overvoltage category

    2

    Max. inverter backfeed current to the array 3)

    0 A4)

    Maximum capacity of the PV generator against earth

    5400 nF

    Limit value of the insulation resistance test between module array and ground (on delivery) 7)

    34 kΩ

    Adjustable range of the insulation resistance test between module array and ground 6)

    34–10,000 kΩ

    Limit value and trip time of sudden residual current monitoring (on delivery)

    30 mA/300 ms
    60 mA/150 ms
    90 mA/40 ms

    Limit value and trip time of continuous residual current monitoring (on delivery)

    300 mA/300 ms

    Adjustable range of continuous residual current monitoring 6)

    30–1000 mA

    Cyclical repetition of insulation resistance test (on delivery)

    24 h

    Adjustable range for cyclical repetition of insulation resistance test

    -

    DC input data
    Battery 8)

    Maximum voltage 11)

    700 V

    Min. voltage

    150 V

    Maximum current

    50 A

    Maximum output

    35 kW

    DC inputs

    1

    Output data

    Grid voltage range

    176–528 VAC

    Rated grid voltage

    220/230 VAC 1)
    253/257 VAC 1)

    Rated power

    25 kW

    Maximum usable DC power – inverter 10)

    32.5 kW

    Rated apparent power

    25 kVA

    Rated frequency

    50/60 Hz 1)

    Maximum output current/phase

    53.7 A

    Initial short circuit current/phase IK

    53.7 A

    Power factor (cos phi)

    0-1 ind./cap.2)

    Grid connection

    3~ (N)PE 380/220 VAC
    3~ (N)PE 400/230 VAC
    3~ (N)PE 440/253 VAC
    3~ (N)PE 480/277 VAC

    Earthing systems

    TT (allowed if UN_PE < 30 V)
    TN-S (allowed)
    TN-C-S (allowed)
    IT (not allowed)

    Maximum output power

    25 kW

    Rated output current/phase

    37.9 / 36.2 / 32.8 / 30.1 A

    Total harmonic distortion

    < 3%

    AC overvoltage category

    3

    Current (inrush) 5)

    24.72 A peak / 6.82 A rms over 1.99 ms 4)

    Maximum output fault current/duration

    53.74 A/13.51 ms

    AC output data
    Full Backup 8)

    Maximum output current/phase
    3 phases
    1 phase

    53.7 A
    72.5 A (AC boost for 5–10 s)
    72.5 A (AC boost for 5–10 s)

    Rated power

    25 kW
    50 kVA (AC boost for 5–10 s)

    Rated output current (per phase)

    53.7 A

    Nominal grid voltage

    3~ (N)PE 380/220 VAC
    3~ (N)PE 400/230 VAC
    3~ (N)PE 440/253 VAC
    3~ (N)PE 480/277 VAC

    Nominal frequency for Full Backup

    53/63 Hz 1)

    Switching time

    < 35 s

    Switching time with rapid switch mode

    < 20 ms

    Power factor cos phi 2)

    0-1 ind./cap.2)

    General data

    Night-time power loss = standby consumption

    16 W

    European Efficiency (300 / 600 / 870 VDC)

    97.24% / 97.74% / 97.11%

    Maximum efficiency

    98.16%

    Protective class

    1

    EMC emission class

    B

    Pollution degree

    3

    Permitted ambient temperature

    -40 °C to +60 °C

    Permitted storage temperature

    -40 °C to +70 °C

    Relative humidity

    0–100%

    Sound pressure level

    56.7 dB(A) (ref. 20 µPA)

    Ingress protection rating

    IP66

    Dimensions (height × width × depth)

    865 × 574 × 279 mm

    Weight

    43 kg

    Weight with packaging

    50.7 kg

    Inverter topology

    Non-insulated, transformerless

    1. Appendix
    2. Technical data

    Verto Plus 30.0

    link_horizontalLink copied

     

    DC input data

    Maximum input voltage
    (at 1000 W/m²/-10 °C in an open circuit)

    1000 VDC

    Start-up input voltage

    150 VDC

    MPP voltage range

    150–870 VDC

    MPP voltage range (at full power)

    400–870 VDC

    Number of MPP controllers

    3

    Maximum input current (IDC max)
    PV1/PV2/PV3
    per string


    28/28/28 A
    28 A

    Maximum total short circuit current 8)
    PV1/PV2/PV3
    per string

    150 A
    50/50/50 A
    50 A

    Total maximum array power (PPV max)
    PV1/PV2/PV3

    45 kWp
    20/20/20 kWp

    DC overvoltage category

    2

    Max. inverter backfeed current to the array 3)

    0 A4)

    Maximum capacity of the PV generator against earth

    6000 nF

    Limit value of the insulation resistance test between module array and ground (on delivery) 7)

    34 kΩ

    Adjustable range of the insulation resistance test between module array and ground 6)

    34–10,000 kΩ

    Limit value and trip time of sudden residual current monitoring (on delivery)

    30 mA/300 ms
    60 mA/150 ms
    90 mA/40 ms

    Limit value and trip time of continuous residual current monitoring (on delivery)

    300 mA/300 ms

    Adjustable range of continuous residual current monitoring 6)

    30–1000 mA

    Cyclical repetition of insulation resistance test (on delivery)

    24 h

    Adjustable range for cyclical repetition of insulation resistance test

    -

    DC input data
    Battery 8)

    Maximum voltage 11)

    700 V

    Min. voltage

    150 V

    Maximum current

    50 A

    Maximum output

    35 kW

    DC inputs

    1

    Output data

    Grid voltage range

    176–528 VAC

    Rated grid voltage

    220/230 VAC 1)
    253/257 VAC 1)

    Rated power

    29.99 kW

    Maximum usable DC power – inverter 10)

    39 kW

    Rated apparent power

    29.99 kVA

    Rated frequency

    50/60 Hz 1)

    Maximum output current/phase

    53.7 A

    Initial short circuit current/phase IK

    53.7 A

    Power factor (cos phi)

    0-1 ind./cap.2)

    Grid connection

    3~ (N)PE 380/220 VAC
    3~ (N)PE 400/230 VAC
    3~ (N)PE 440/253 VAC
    3~ (N)PE 480/277 VAC

    Earthing systems

    TT (allowed if UN_PE < 30 V)
    TN-S (allowed)
    TN-C-S (allowed)
    IT (not allowed)

    Maximum output power

    29.99 kW

    Rated output current/phase

    45.5 / 43.5 / 39.4 / 36.1 A

    Total harmonic distortion

    < 3%

    AC overvoltage category

    3

    Current (inrush) 5)

    24.72 A peak / 6.82 A rms over 1.99 ms 4)

    Maximum output fault current/duration

    53.74 A/13.51 ms

    AC output data
    Full Backup 8)

    Maximum output current/phase
    3 phases
    1 phase

    53.7 A
    72.5 A (AC boost for 5–10 s)
    72.5 A (AC boost for 5–10 s)

    Rated power

    29.99 kW
    50 kVA (AC boost for 5–10 s)

    Rated output current (per phase)

    53.7 A

    Nominal grid voltage

    3~ (N)PE 380/220 VAC
    3~ (N)PE 400/230 VAC
    3~ (N)PE 440/253 VAC
    3~ (N)PE 480/277 VAC

    Nominal frequency for Full Backup

    53/63 Hz 1)

    Switching time

    < 35 s

    Switching time with rapid switch mode

    < 20 ms

    Power factor cos phi 2)

    0-1 ind./cap.2)

    General data

    Night-time power loss = standby consumption

    16 W

    European Efficiency (360 / 600 / 870 VDC)

    97.35% / 97.96% / 97.57%

    Maximum efficiency

    98.15%

    Protective class

    1

    EMC emission class

    B

    Pollution degree

    3

    Permitted ambient temperature

    -40 °C to +60 °C

    Permitted storage temperature

    -40 °C to +70 °C

    Relative humidity

    0–100%

    Sound pressure level

    56.7 dB(A) (ref. 20 µPA)

    Ingress protection rating

    IP66

    Dimensions (height × width × depth)

    865 × 574 × 279 mm

    Weight

    43 kg

    Weight with packaging

    50.7 kg

    Inverter topology

    Non-insulated, transformerless

    1. Appendix
    2. Technical data

    Verto Plus 33.3

    link_horizontalLink copied

     

    DC input data

    Maximum input voltage
    (at 1000 W/m²/-10 °C in an open circuit)

    1000 VDC

    Start-up input voltage

    150 VDC

    MPP voltage range

    150–870 VDC

    MPP voltage range (at full power)

    410–870 VDC

    Number of MPP controllers

    3

    Maximum input current (IDC max)
    PV1/PV2/PV3
    per string


    28/28/28 A
    28 A

    Maximum total short circuit current 8)
    PV1/PV2/PV3
    per string

    150 A
    50/50/50 A
    50 A

    Total maximum array power (PPV max)
    PV1/PV2/PV3

    50 kWp
    20/20/20 kWp

    DC overvoltage category

    2

    Max. inverter backfeed current to the array 3)

    0 A4)

    Maximum capacity of the PV generator against earth

    6660 nF

    Limit value of the insulation resistance test between module array and ground (on delivery) 7)

    34 kΩ

    Adjustable range of the insulation resistance test between module array and ground 6)

    34–10,000 kΩ

    Limit value and trip time of sudden residual current monitoring (on delivery)

    30 mA/300 ms
    60 mA/150 ms
    90 mA/40 ms

    Limit value and trip time of continuous residual current monitoring (on delivery)

    300 mA/300 ms

    Adjustable range of continuous residual current monitoring 6)

    30–1000 mA

    Cyclical repetition of insulation resistance test (on delivery)

    24 h

    Adjustable range for cyclical repetition of insulation resistance test

    -

    DC input data
    Battery 8)

    Maximum voltage 11)

    700 V

    Min. voltage

    150 V

    Maximum current

    50 A

    Maximum output

    35 kW

    DC inputs

    1

    Output data

    Grid voltage range

    176–528 VAC

    Rated grid voltage

    220/230 VAC 1)
    253/257 VAC 1)

    Rated power

    33.3 kW

    Maximum usable DC power – inverter 10)

    39 kW

    Rated apparent power

    33.3 kVA

    Rated frequency

    50/60 Hz 1)

    Maximum output current/phase

    53.7 A

    Initial short circuit current/phase IK

    53.7 A

    Power factor (cos phi)

    0-1 ind./cap.2)

    Grid connection

    3~ (N)PE 380/220 VAC
    3~ (N)PE 400/230 VAC
    3~ (N)PE 440/253 VAC
    3~ (N)PE 480/277 VAC

    Earthing systems

    TT (allowed if UN_PE < 30 V)
    TN-S (allowed)
    TN-C-S (allowed)
    IT (not allowed)

    Maximum output power

    33.3 kW

    Rated output current/phase

    50.5 / 48.3 / 43.7 / 40.1 A

    Total harmonic distortion

    < 3%

    AC overvoltage category

    3

    Current (inrush) 5)

    24.72 A peak / 6.82 A rms over 1.99 ms 4)

    Maximum output fault current/duration

    53.74 A/13.51 ms

    AC output data
    Full Backup 8)

    Maximum output current/phase
    3 phases
    1 phase

    53.7 A
    72.5 A (AC boost for 5–10 s)
    72.5 A (AC boost for 5–10 s)

    Rated power

    33.3 kW
    50 kVA (AC boost for 5–10 s)

    Rated output current (per phase)

    53.7 A

    Nominal grid voltage

    3~ (N)PE 380/220 VAC
    3~ (N)PE 400/230 VAC
    3~ (N)PE 440/253 VAC
    3~ (N)PE 480/277 VAC

    Nominal frequency for Full Backup

    53/63 Hz 1)

    Switching time

    < 35 s

    Switching time with rapid switch mode

    < 20 ms

    Power factor cos phi 2)

    0-1 ind./cap.2)

    General data

    Night-time power loss = standby consumption

    16 W

    European Efficiency (400 / 600 / 870 VDC)

    97.42% / 97.95% / 97.56%

    Maximum efficiency

    98.15%

    Protective class

    1

    EMC emission class

    B

    Pollution degree

    3

    Permitted ambient temperature

    -40 °C to +60 °C

    Permitted storage temperature

    -40 °C to +70 °C

    Relative humidity

    0–100%

    Sound pressure level

    56.7 dB(A) (ref. 20 µPA)

    Ingress protection rating

    IP66

    Dimensions (height × width × depth)

    865 × 574 × 279 mm

    Weight

    43 kg

    Weight with packaging

    50.7 kg

    Inverter topology

    Non-insulated, transformerless

    1. Appendix
    2. Technical data

    Protection devices

    link_horizontalLink copied

    DC disconnector

    Integrated

    Cooling principle

    Controlled forced-air ventilation

    RCMU 9)

    Integrated

    RCMU classification

    The software class of the safety platform(s) is defined as a class B control function (single-channel with periodic self-test) in accordance with IEC 60730 Annex H.

    DC isolation measurement 9)

    integrated 2)

    Overload performance

    Operating point shift
    Power limitation

    Active anti-islanding method

    Frequency point shift method

    AFCI

    optional

    AFPE (AFCI) classification (according to IEC 63027) 9)

    F-I-AFPE-1-4/2-2
    Full coverage
    Integrated
    AFPE
    1 monitored string per input port
    4/2 input ports per channel (AFPE1 for MPP1 & MPP2: 4, AFPE2 for MPP3 & MPP3: 2)
    2 monitored channels

    1. Appendix
    2. Technical data

    WLAN

    link_horizontalLink copied

    Frequency range

    2412 - 2462 MHz

    Channels / power used

    Channel: 1-11 b,g,n HT20
    Channel: 3-9 HT40
    <18 dBm

    Modulation

    802.11b: DSSS (1Mbps DBPSK, 2Mbps DQPSK, 5.5/11Mbps CCK)
    802.11g: OFDM (6/9Mbps BPSK, 12/18Mbps QPSK, 24/36Mbps 16-QAM, 48/54Mbps 64-QAM)
    802.11n: OFDM (6.5 BPSK, QPSK, 16-QAM, 64-QAM)

    1. Appendix
    2. Technical data

    Data communication

    link_horizontalLink copied

    WiFi SMA-RP connection
    (FCC ID: QKWPILOT1 / IC ID: 12270A-PILOT1)

    802.11b/g/n (WPA, WPA2)
    Frequency: 2.4 GHz

    Ethernet (LAN)

    RJ 45, 10/100 Mbit

    Wired shutdown (WSD)

    Max. 28 devices/WSD chain
    Max. distance between two devices = 100 m

    Modbus RTU SunSpec (2x)

    RS485 2-wire

    Battery connection (only for Verto Plus devices)

    Modbus O / RJ 45 / 12 V power supply

    Voltage level of digital inputs

    Low: min. 0 V-max. 1.8 V
    High: min. 4.5 V-max. 28.8 V

    Input currents of digital inputs

    depending on the input voltage;
    input resistance = 70 kOhm

    Total power for digital output (with internal supply)

    6 W at 12 V

    Power per digital output
    (with external supply)

    1 A at >12.5 V - 24 V
    (max. 3 A in total)

    Datalogger/web server

    Integrated

    1. Appendix
    2. Technical data

    Surge protection device DC SPD type 1+2

    link_horizontalLink copied

    General data

    Rated discharge current (In)
    - 8/20 µs pulses

    20 kA

    Protection level (Up)

    4 kV

    Short circuit strength PV (Iscpv)

    9 kA

    Disconnector

    Thermal disconnector

    Integrated

    External fuse

    None

    Mechanical properties

    Disconnection indicator

    Mechanical indicator

    Remote communication of the connection interruption

    Output on the changeover contact

    Housing material

    Thermoplastic UL-94-V0

    Test standards

    IEC 61643-31 / EN 61643-31

    1. Appendix
    2. Technical data

    Explanation of footnotes

    link_horizontalLink copied
    1)
    The values provided are standard values. If required, the inverter is customized for a specific country.
    2)
    Depending on the country setup or device-specific settings
    (ind. = inductive; cap. = capacitive)
    3)
    Maximum current from a defective PV module to all other PV modules. From the inverter itself to the PV side of the inverter, this is 0 amperes.
    4)
    Assured by the electrical design of the inverter
    5)
    Peak current when turning on the inverter
    6)
    The values provided are standard values. These values must be adjusted according to requirements and PV output.
    7)
    The value provided is a maximum value. If this value is exceeded, this may impair the function.
    8)
    ISC PV = ISC max ≥ I SC (STC) x 1.25 acc. to e.g.: IEC 60364-7-712, NEC 2020, AS/NZS 5033:2021
    9)
    Software class B (single-channel with periodic self-test) according to IEC 60730-1 Appendix H.
    10)
    Max. power that can be used in parallel for the output power (AC) and the battery charging power (DC).
    1. Appendix
    2. Technical data

    Integrated DC disconnector

    link_horizontalLink copied

    General data

    Product name

    Benedict LSA32 E 8237

    Rated insulation voltage

    1000 VDC

    Rated impulse withstand voltage

    8 kV

    Suitability for insulation

    Yes, DC only

    Utilization category and/or PV utilization category

    according to IEC/EN 60947-3 utilization category DC-PV2

    Rated short-time withstand current (Icw)

    Rated short-time withstand current (Icw): 1000 A

    Rated short-circuit capacity (Icm)

    Rated short-circuit capacity (Icm): 1000 A

    Rated operating current and rated breaking capacity

    Rated operating voltage (Ue)

    Rated operating current (Ie)

    I(make) / I(break)

    Rated operating current (Ie)

    I(make) / I(break)

    ≤ 500 VDC

    14 A

    56 A

    28 A

    112 A

    600 VDC

    11.5 A

    46 A

    28 A

    112 A

    700 VDC

    7.5 A

    30 A

    28 A

    112 A

    800 VDC

    5.75 A

    23 A

    23 A

    92 A

    900 VDC

    4.75 A

    19 A

    20 A

    80 A

    1000 VDC

    4 A

    16 A

    13 A

    52 A

    Number of pins

    1

    1

    2

    2

    System circuit diagrams

    link_horizontalLink copied

    Fronius Verto Plus and Fronius Reserva

    1. System circuit diagrams

    Fronius Verto Plus and Fronius Reserva

    link_horizontalLink copied
    1. System circuit diagrams

    Fronius Verto Plus with Fronius Reserva connected in parallel

    link_horizontalLink copied
    1. System circuit diagrams

    Fronius Verto Plus and Fronius Reserva Pro

    link_horizontalLink copied
    1. System circuit diagrams

    Fronius Verto Plus with Fronius Reserva Pro connected in parallel

    link_horizontalLink copied
    1. System circuit diagrams

    Fronius Verto Plus and BYD Battery-Box Premium HV

    link_horizontalLink copied
    1. System circuit diagrams

    Fronius Verto Plus with 3 BYD Battery-Box Premium HV connected in parallel

    link_horizontalLink copied
    1. System circuit diagrams

    Fronius Verto Plus and BYD Battery-Box HVS+/HVM+/HVB

    link_horizontalLink copied
    1. System circuit diagrams

    Fronius Verto Plus with BYD Battery-Box HVS+/HVM+/HVB connected in parallel

    link_horizontalLink copied

    Circuit diagrams—automatic switch to backup power with Fronius Backup Controller

    link_horizontalLink copied

    Fronius Backup Controller 4-pin separation, e.g., Germany

    1. Circuit diagrams—automatic switch to backup power with Fronius Backup Controller

    Fronius Backup Controller 4-pin separation, e.g., Germany

    link_horizontalLink copied
    1. Circuit diagrams—automatic switch to backup power with Fronius Backup Controller

    Fronius Backup Controller 3-pin separation, e.g., Austria

    link_horizontalLink copied
    1. Circuit diagrams—automatic switch to backup power with Fronius Backup Controller

    Fronius Backup Controller 3-pin separation, parallel backup

    link_horizontalLink copied

    Circuit diagrams—automatic switch to backup power with third-party components

    link_horizontalLink copied

    Automatic switch to backup power 3-pin single FRT-capable separation - e.g., Austria

    1. Circuit diagrams—automatic switch to backup power with third-party components

    Automatic switch to backup power 3-pin single FRT-capable separation - e.g., Austria

    link_horizontalLink copied
    1. Circuit diagrams—automatic switch to backup power with third-party components

    Automatic switch to backup power 3-pin single separation - e.g., Australia

    link_horizontalLink copied
    1. Circuit diagrams—automatic switch to backup power with third-party components

    Automatic switch to backup power 3-pin double separation with ext. grid and system protection

    link_horizontalLink copied
    1. Circuit diagrams—automatic switch to backup power with third-party components

    Automatic switch to backup power 4-pin single separation - e.g., Germany

    link_horizontalLink copied
    1. Circuit diagrams—automatic switch to backup power with third-party components

    Automatic switch to backup power 4-pin single FRT-capable separation

    link_horizontalLink copied
    1. Circuit diagrams—automatic switch to backup power with third-party components

    Automatic switch to backup power 4-pin single separation - e.g., France

    link_horizontalLink copied
    1. Circuit diagrams—automatic switch to backup power with third-party components

    Automatic switch to backup power 4-pin single separation - e.g., Spain

    link_horizontalLink copied
    1. Circuit diagrams—automatic switch to backup power with third-party components

    Automatic switch to backup power 4-pin double separation with ext. grid and system protection - e.g., Italy

    link_horizontalLink copied

    Circuit diagrams—manual switch to backup power with Fronius Backup Switch

    link_horizontalLink copied

    Manual switch to backup power 3-pin separation, e.g., Austria

    1. Circuit diagrams—manual switch to backup power with Fronius Backup Switch

    Manual switch to backup power 3-pin separation, e.g., Austria

    link_horizontalLink copied
    1. Circuit diagrams—manual switch to backup power with Fronius Backup Switch

    Manual switch to backup power 3-pin separation with grid and system protection

    link_horizontalLink copied
    1. Circuit diagrams—manual switch to backup power with Fronius Backup Switch

    Manual switch to backup power 4-pin separation, e.g., Germany

    link_horizontalLink copied
    1. Circuit diagrams—manual switch to backup power with Fronius Backup Switch

    Manual switch to backup power 3-pin separation Parallel Backup with Backup Switch

    link_horizontalLink copied