en
      Operating instructionsFronius Symo Advanced UL
    • Safety rules
      • Explanation of safety instructions
      • General
      • Environmental conditions
      • Target group
      • Data Regarding Noise Emission Values
      • EMC measures
      • Safety symbols
      • Disposal
      • Data security
      • Copyright
    • General
      • Device concept
      • Software version
      • Intended Use
      • Information on ‘Field-adjustable trip points’ and ‘Advanced Grid Features’
      • FCC / RSS Compliance
      • Territorial Limitations
      • Insulation Monitor/Interruption, Insulation Monitoring
      • Arc detection/interruption
      • Power Line Communication (PLC) transmitter
      • String fuses
      • Criteria for the Proper Selection of String Fuses
    • Data Communication and Fronius Solar Net
      • Fronius Solar Net and data interface
      • Data Communication Area
      • Explanation of Multifunctional Power Interface
      • 'Fronius Solar Net' LED description
      • Example
      • Fail-Safe
    • Fronius Datamanager 2.0
      • Controls, Connections, and Indicators on the Fronius Datamanager 2.0
      • Fronius Datamanager 2.0 at night or when insufficient DC voltage is available
      • Safety
      • Installing Inverters with Fronius Datamanager 2.0 in Fronius Solar Net
      • Starting for the first time
      • More Detailed Information on Fronius Datamanager 2.0
    • Keys and symbols
      • Keys and Symbols
      • Display
    • Navigation in the Menu Level
      • Activate the display illumination
      • Automatic Deactivation of Display Illumination / Switching to the "NOW" Display Mode
      • Access the menu level
      • Values Displayed in the NOW Menu
      • Values Displayed in the LOG Menu
    • The SETUP menu item
      • Presetting
      • Software Updates
      • Navigation in the SETUP Menu
      • General Menu Item Settings
      • Application Example: Setting the Feed-In Tariff
    • Menu Items in the Setup Menu
      • Standby
      • WLAN Access Point
      • DATCOM
      • USB
      • Relay (Floating Switch Contact)
      • Energy Manager
        (in the Relay Menu)
      • Time/Date
      • Display Settings
      • Energy yield
      • Fan
      • Arc Detection
    • The INFO menu item
      • Measured values
      • LT Status
      • Grid Status
      • Device information
      • Version
    • Switching the key lock on and off
      • General
      • Switching the Key Lock On and Off
    • USB Stick as a Data Logger and for Updating Inverter Software
      • USB Thumb Drive as a Data Logger
      • Suitable USB Thumb Drives
      • USB thumb drive for updating inverter software
      • Removing the USB Stick
    • The Basic menu
      • Accessing the Basic Menu
      • Basic Menu Entries
    • Status Diagnosis and Troubleshooting
      • Displaying status codes
      • Total Failure of the Display
      • Class 1 status codes
      • Class 2 Status Codes
      • Class 3 Status Codes
      • Class 4 status codes
      • Class 5 state codes
      • Class 6 Status Codes
      • Class 7 Status Codes
      • Class 10–12 Status Codes
      • Customer service
      • Operation in dusty environments
    • Technical data
      • General data and protection devices 10.0-3 208-240 / 24.0-3 208-240
      • Technical data Fronius Symo Advanced 10.0-3 208-240 / 12.0-3 208-240
      • Technical data Symo Advanced 15.0-3 480
      • Technical data Fronius Symo Advanced 20.0-3 208-240 - 22.7-3 208-240
      • Technical data Fronius Symo Advanced 24.0-3 208-240
      • Relevant standards and directives
      • RCMU
    • Terms and conditions of warranty and disposal
      • Fronius manufacturer's warranty
      • Disposal
    • 028-02032026
    download
    ContactsImprintT&CsData privacy statement
    Safety rules
    link_horizontalLink copied
    WARNING!
    CAUTION!
    Indicates a potentially harmful situation.
    NOTE!
    Indicates a possibility of flawed work results and possible damage to the equipment.
    Please pay special attention when one of the symbols from the "Safety rules" chapter appears in these instructions.
    1. Safety rules
    WARNING!
    CAUTION!
    NOTE!
    1. Safety rules
    General
    The device has been manufactured using state-of-the-art technology and according to recognized safety standards. If used incorrectly or misused, however, it can cause
    • serious or fatal injury to the operator or a third party,
    • and damage to the device and other material assets belonging to the operating company.
    All persons involved in start-up operation, maintenance and servicing of the device must
    • be suitably qualified,
    • have knowledge of and experience in dealing with electrical installations and
    • have fully read and precisely followed these Operating Instructions.
    The Operating Instructions must always be kept on hand wherever the device is being used. In addition to the Operating Instructions, all applicable local rules and regulations regarding accident prevention and environmental protection must also be followed.
    All safety and danger notices on the device
    • must be kept in a legible state
    • must not be damaged/marked
    • must not be removed
    • must not be covered, pasted, or painted over.
    The terminals can reach high temperatures.
    Only operate the device when all protection devices are fully functional. If the protection devices are not fully functional, there is a risk of
    Any safety devices that are not functioning properly must be repaired by an authorized specialist before the device is switched on.
    For the location of the safety and danger notices on the device, refer to the section headed “General” in the Operating Instructions for the device.
    Any equipment malfunctions which might impair safety must be remedied immediately before the device is turned on.
    1. Safety rules
    Operation or storage of the device outside the stipulated area will be deemed as not in accordance with the intended use.
    1. Safety rules
    Target group
    This document provides detailed information and instructions to ensure that all users can use the device safely and efficiently.
    • The information is intended for the following groups of people:
      • Technical specialists: People with appropriate qualifications and fundamental electronic and mechanical knowledge, who are responsible for the installation, operation, and maintenance of the device.
      • End users: People that use the device in daily operation and want to understand its basic functions.
    • Regardless of any qualifications, only perform the activities listed in this document.
    • All persons involved in the commissioning, maintenance, and servicing of the device must be appropriately qualified and have knowledge of working with electrical installations.
    • The definition of professional qualifications and their applicability are subject to national law.
    1. Safety rules
    The cooling of the device takes place via an electronic temperature control system at the lowest possible noise level and depends on the power used, ambient temperature and the soiling level of the device, etc.
    It is not possible to provide a workplace-related emission value for this device, because the actual sound pressure level is heavily influenced by the installation situation, the power quality, the surrounding walls and the properties of the room in general.
    1. Safety rules
    EMC measures
    1. Safety rules
    Safety symbols
    1. Safety rules
    Disposal
    1. Safety rules
    Data security
    • saving and storing personal settings.
    1. Safety rules
    Copyright
    General
    Device concept
    Unit design:
    (1)
    Housing cover
    (2)
    Inverter
    (3)
    Mounting bracket
    (4)
    Connection area including DC main switch
    (5)
    (6)
    Data communication cover
    The inverter transforms the direct current generated by the solar modules into alternating current. This alternating current is fed into the public grid and synchronized with the mains voltage in use.
    The inverter has been designed exclusively for use in grid-connected photovoltaic systems. It cannot generate electric power independently of the grid.
    The inverter automatically monitors the public grid. Whenever conditions in the electric grid are inconsistent with standard conditions (e.g., grid switch-off, interruption), your inverter will immediately stop operating and interrupt the supply of power into the grid.
    The grid is monitored by monitoring the voltage, monitoring the frequency and monitoring islanding conditions.
    The inverter is fully automatic. The inverter starts monitoring the grid as soon as the solar modules are generating enough energy after sunrise. The inverter resumes the grid power feed operation when there is sufficient direct sunlight.
    The control system of the inverter ensures that the maximum possible power output is drawn from the solar modules at all times.
    As soon as there is no longer sufficient energy available for the grid power feed operation, the inverter shuts down the power electronics connection to the grid completely and stops operating. All settings and recorded data are saved.
    When its temperature gets too high, the inverter automatically reduces the current output power in order to protect itself.
    Reasons for the temperature being too high include a high ambient temperature or insufficient heat dissipation (e.g., inadequate heat dissipation when installed in switch cabinets).
    1. General
    Device concept
    Unit design:
    (1)
    Housing cover
    (2)
    Inverter
    (3)
    Mounting bracket
    (4)
    (5)
    (6)
    1. General
    Software version
    The features described in these instructions are valid from the following software version: fro28500.upd
    Minor deviations from the described features are possible in newer or older software versions.
    1. General
    Intended Use
    The inverter is designed exclusively to convert direct current from solar modules into alternating current and feed this power into the public grid.
    The following are deemed to be not in conformity with its intended purpose:
    • Utilization for any other purpose, or in any other manner
    • Alternations to the inverter are not expressly recommended by Fronius
    • Installation of components that are not expressly recommended or sold by Fronius.
    The manufacturer is not responsible for any damage resulting from improper use.
    All warranty claims are considered void in such cases.
    Proper use also means
    • carefully reading and obeying the instructions and all the safety and danger notices in the Operating and Installation Instructions
    • compliance with the maintenance operations
    • installation as specified in the Installation Instructions
    When configuring the photovoltaic system, make sure that all components are operating completely within their permitted operating range.
    All measures recommended by the solar module manufacturer for maintaining solar module properties must be followed.
    Follow all grid operator regulations regarding grid power feed and connection methods.
    1. General
    The inverter is equipped with ‘Field adjustable trip points’ and ‘Advanced Grid Features’. For further information, please contact ‘Fronius Technical Support’ at the following email address: pv-support-usa@fronius.com.
    1. General
    FCC
    This device corresponds to the limit values for a digital device of class B in accordance with Part 15 of the FCC regulations. The limit values should provide adequate protection against harmful interference in homes. This device creates and uses high frequency energy and can interfere with radio communications when not used in accordance with the instructions. However, there is no guarantee against interference occurring in a particular installation.
    If this device interferes with radio or television reception when turning the device on and off, it is recommended that the user solve this with one or more of the following measures:
    • adjust or reposition the receiving antenna
    • increase the distance between the device and the receiver
    • connect the device to another circuit, which does not include the receiver
    • for further support, please contact the retailer or an experienced radio/TV technician.
    Industry Canada RSS
    The device corresponds to the license-free Industry Canada RSS standards. Operation is subject to the following conditions:
    (1) The device may not cause harmful interference
    (2) The device must accept any interference received, including interference that may cause undesired operation.
    1. General
    This product is intended for use and sale outside the Province of Québec. It does not meet the French language documentation and labeling requirements of Québec's Charter of the French Language. Accordingly, Fronius Internation GmbH does not offer this product for sale to, or for delivery to, any address within the Province of Québec.
    By placing an order, the customer represents and warrants that they are not purchasing the product for use or resale within Québec. Fronius International GmbH disclaims all liability and warranty obligations for any products operated in Québec in violation of these restrictions.
    1. General
    The inverter is equipped with the following safety features as required by UL 1741 and the National Electrical Code:
    Insulation monitor (IMI/RCMU)
    The IMI (isolation monitor interruptor) feature is performed by the RCMU (residual current monitoring unit) feature in the inverter. This feature automatically monitors whether a leakage current exists in the grid power feed operation. The inverter is disconnected from the grid if a defined leakage current is exceeded.
    NOTE!
    Automatic reconnection no longer occurs after the device is disconnected from the grid five times as a result of exceeding the defined leakage current value.
    The State Code 607 shown on the display must be acknowledged to reconnect.
    Insulation monitoring of ungrounded solar modules
    In the case of grid connected photovoltaic systems with ungrounded solar modules, the inverter checks the insulation resistance between the positive and negative pole in relation to the earth potential before energy is fed into the grid. The inverter issues a state code if the insulation resistance is too low. The inverter is therefore not permitted to start feeding energy into the grid.
    1. General
    The inverter is equipped with integrated arc detection/interruption, which detects and extinguishes serial arcs.
    For example, a serial arc can occur after the following errors or situations:
    • Poorly-connected plug connections on the solar module
    • Poor or defective cable connections on the solar module side, which enable a connection against the earth potential
    • Defective solar modules due to problems in the junction box or production errors, such as high resistance solder connections in individual solar cells
    • Cables incorrectly connected to an inverter’s input terminals
    If a serial arc is detected, the power is switched off and the grid power feed operation is interrupted. A state code is shown on the display. The state code on the display must be manually reset before the grid power feed operation can be resumed.
    The power shutdown also extinguishes the serial arc.
    NOTE!
    This product is equipped with a communication interface in line with the "Communication Signal for Rapid Shutdown - SunSpec Interoperability Specification”.
    Power optimizers and other MLPE features in the photovoltaic system can impair the correct functioning of the arc detection/interruption. When using these kinds of components, the system installer is responsible for ensuring the correct functioning of the arc detection/interruption. Contact your Fronius Technical Support for more information.
    1. General
    The inverter is equipped with a Power Line Communication (PLC) transmitter on the DC side. Its function is to ensure rapid shutdown in accordance with National Electric Code NEC 2023 Art. 690.12 and Canadian Electrical Code CSA C22.1:24 Art. 64-218. The PLC is implemented according to the specification “Communication Signal for Rapid Shutdown – SunSpec Interoperability Specification” (depending on national grid setup). Please visit www.sunspec.org for details.
    To ensure compliance with all applicable regulations in your country and to ensure optimal reception among all recipients, please follow the recommendations below:
    • Keep the distance between the DC+ and DC- conductors as small as possible
    • Avoid cable loops caused by cables that are too long (coil effect)
    • Use metal cable ducts where possible
    • Do not place DC cables from different inverters in the same cable duct or cable tray
    1. General
    There are warning notices and safety symbols on the inside and outside of the inverter. These warning notices and safety symbols must not be removed or painted over. They warn against incorrect operation, as this may result in serious injury and property damage.
    Safety symbols:
    Danger of serious injury and property damage due to incorrect operation
    • All Operating Instructions for the system components of the photovoltaic system, especially the safety rules
    Dangerous electrical voltage
    Wait for the capacitors to discharge.
    Text of the warning notices:
    WARNING!
    Risk of electric shock!
    Non-insulated inverter
    Do not remove the cover. The device does not contain any user-serviceable parts. Maintenance work must be carried out by a trained service technician.
    Both AC and DC voltage sources terminate inside this device. Each circuit must be turned off before carrying out maintenance work.
    If the solar module is exposed to light, it will supply a DC voltage to the device.
    Risk of electric shock due to energy stored in capacitors. Do not remove the cover until all power supply sources have been switched off for at least 5 minutes.
    Ungrounded system: The DC cables in this PV system are not grounded and can be live.
    1. General
    String fuses
    Only valid for the device types with the "Ecofuse" option:
    The use of string fuses provides additional fuse protection for solar modules.
    The maximum short circuit current ISC, the maximum module backfeed current IR, and the specification of the maximum string fuse value in the module data sheet of the respective solar module are decisive factors in the protection of the solar module.
    The maximum short circuit current ISC per terminal is 15 A.
    The string fuse release current can be set to greater than 15 A if required. However, a release current of 20 A must not be exceeded.
    If the inverter is being operated with an external string collection box, the DC connector kit 25 (item numbers 42,0201,4479 for DC+ and 42,0201,4480 for DC-) must be used. In this case the solar modules are externally protected in the string collection box and the metal bolts should be used in the inverter.
    National regulations regarding fuse protection must be observed. The electrical engineer carrying out the installation is responsible for the correct choice of string fuses.
    CAUTION!
    Danger due to defective fuses.
    This can result in fires.
    Always replace defective fuses with new equivalent fuses.
    The inverter is delivered with metal bolts as standard.
    1. General
    In order to prevent premature tripping of the fuse during normal operation, it is recommended that the following criteria be met per individual solar module string when fusing-protecting the solar module strings:
    • IN > 1.5 x ISC
    • VN >/= maximum open circuit voltage of pv generator
    • Fuse dimensions: Diameter 10 x 38 mm
    IN
    Nominal current of the fuse
    ISC
    Short circuit current for standard test conditions (STC) according to solar module data sheet
    VN
    Nominal voltage of the fuse
    NOTE!
    The nominal current value of the fuse must not exceed the maximum fuse protection value specified in the solar module manufacturer's data sheet.
    If a maximum fuse protection value is not specified, please request it from the solar module manufacturer.
    Fronius developed Solar Net to make these system add-ons flexible and capable of being used in a wide variety of different applications. Fronius Solar Net is a data network that enables several inverters to be linked to the system add-ons.
    Fronius Solar Net is a bus system with ring topology. Just one suitable cable is enough for communication between one or more inverters connected to Fronius Solar Net and a system add-on.
    In order to clearly define each inverter in Fronius Solar Net, each inverter must also be assigned an individual number.
    You can assign individual numbers as per the "SETUP Menu" section.
    Different system add-ons are automatically recognized by Fronius Solar Net.
    In order to distinguish between several identical system add-ons, each one must be assigned a unique number.
    More detailed information on the individual system add-ons can be found in the relevant operating instructions or on the internet at http://www.fronius.com
    More detailed information on cabling Fronius DATCOM components can be found at:
    → http://www.fronius.com/QR-link/4204101938
    1. Data Communication and Fronius Solar Net
    Depending on the version, the inverter can be fitted with the Fronius Datamanager plug-in card (8).
    Item
    Description
    (1)
    Switchable multifunctional power interface.
    For a more detailed explanation, see the section entitled "Explanation of Multifunctional Power Interface" which follows
    Use the 2-pin mating connector supplied with the inverter to connect to the multifunctional power interface.
    (2)
    (3)
    Fronius Solar Net/interface protocol IN connection
    Fronius Solar Net/interface protocol OUT connection
    Fronius Solar Net/interface protocol input and output for connecting to other DATCOM components (e.g., inverter, Fronius Sensor Box, etc.)
    When linking several DATCOM components, a termination plug must be placed on each free IN and/or OUT connection of a DATCOM component.
    Two termination plugs are supplied with inverters with Fronius Datamanager plug-in card.
    (4)
    ‘Fronius Solar Net’ LED
    indicates whether a power supply is available for Fronius Solar Net
    (5)
    ‘Data transfer’ LED
    flashes when accessing the USB thumb drive. The USB thumb drive must not be removed during this time.
    (6)
    USB A socket
    for connecting a USB flash drive with a maximum size of
    65 x 30 mm (2.6 x 2.1 in.)
    The USB thumb drive can act as a data logger for an inverter. The USB thumb drive is not part of the scope of supply for the inverter.
    (7)
    Floating switch contact (relay) with mating connector
    max. 250 V AC / 4 A AC
    max. 30 V DC / 1 A DC
    max. 1.5 mm² (AWG 16) cable cross section
    Pin 1 = NO contact (Normally Open)
    Pin 2 = root (Common)
    Pin 3 = NC contact (Normally Closed)
    For a more detailed explanation, see the “Menu items in the setup menu/relay” section.
    Use the mating connector supplied with the inverter to connect to the floating switch contact.
    (8)
    Fronius Datamanager with WLAN antenna
    or
    cover for option card slot
    (9)
    Cover for option card slot
    Different switching variants can be connected to the multifunctional power interface. These variants cannot be operated at the same time, however. For example, if an S0 counter is connected to the multifunctional power interface, a signal contact for surge protection cannot be connected, and vice versa.
    Pin 1 = measurement input: max. 20 mA, 100-ohm measurement resistor (apparent ohmic resistance)
    Pin 2 = max. short circuit current 15 mA, max. open circuit voltage 16 V DC or GND
    Switching Variant 1: Signal Contact for Surge Protection
    The DC SPD (surge protection) option issues a warning or error on the display, depending on the setting in the basic menu (signal input submenu). More detailed information on the DC SPD option can be found in the Installation Instructions.
    Switching Variant 2: S0 Counter
    A counter for recording self-consumption per S0 can be connected directly to the inverter. This S0 counter can be placed at the feed-in point or in the consumption branch. A dynamic power reduction can be set under the DSO Editor menu subitem in the settings on the Fronius Datamanager website (see Fronius Datamanager 2.0 Operating Instructions on the homepage at www.fronius.com)
    IMPORTANT! Connecting an S0 meter to the inverter may require an inverter firmware update.
    Requirements for the S0 meter:
    • Must meet standard IEC 62053-31 Class B
    • Max. voltage: 15 V DC
    • Max. current when ON: 15 mA
    • Min. current when ON: 2 mA
    • Max. current when OFF: 0.15 mA
    Recommended max. impulse rate of S0 meter:
    PV power kWp [kW]
    Max. impulse rate per kWp
    30
    1,000
    20
    2,000
    10
    5,000
    ≤ 5.5
    10,000
    The ‘Fronius Solar Net‘ LED is illuminated:
    Power supply for the data communication within the Fronius Solar Net/interface protocol is OK
    The ‘Fronius Solar Net‘ LED flashes briefly every 5 seconds:
    Error in the data communication in the Fronius Solar Net
    • Overcurrent (current flow > 3 A, e.g. due to a short circuit in Fronius Solar Net ring)
    • Undervoltage (no short circuit, voltage in Fronius Solar Net < 6.5 V, e.g. if too many DATCOM components are in Fronius Solar Net and the electrical supply is insufficient)
      In this case, an additional power supply is required for the Fronius DATCOM components using an external power supply (43,0001,1194) on one of the Fronius DATCOM components.
      Check other DATCOM components to detect any undervoltage present.
    After a shutdown due to overcurrent or undervoltage, the inverter tries to restore the energy supply in the Fronius Solar Net every 5 seconds so long as there is an error.
    Once the error has been corrected, power is restored to Fronius Solar Net within 5 seconds.
    Example
    Logging and archiving inverter and sensor data using a Fronius Datamanager and Fronius Sensor Box:
    Data network with three inverters and one Fronius Sensor Box:
    - inverter 1 with Fronius Datamanager
    - inverter 2 and 3 without Fronius Datamanager.
    = termination plug
    External communication (Fronius Solar Net) takes place in the inverter via the data communication area. The data communication area has two RS-422 interfaces: an input and an output. RJ45 plug connectors are used to establish the connection.
    IMPORTANT! Only one Fronius Datamanager in primary operation is permitted per Fronius Solar Net Ring. Switch other Fronius Datamanagers to secondary operation or remove them (see chapter "Controls, connections, and indicators on the Fronius Datamanager 2.0").
    Unused option card slots can be closed by replacing the cover (item number - 42,0405,2094), or an inverter without Fronius Datamanager (light version) can be used.
    Fail-Safe
    In the Fronius Solar Net ring (a combination of several inverters), the Fail-Safe function prevents inadmissible feeding of the connected inverters in the start-up phase or during operation. For this purpose, a signal is transmitted from the primary inverter with built-in data manager to the secondary inverters (Lite devices).
    The function is activated as soon as the data manager fails or the Solar Net connection is interrupted. In this case, the signal is not transmitted to the secondary inverters. All devices switch off with status 710.
    The following requirements must be met to enable the Fail-Safe to function correctly:
    • For all inverters in the Solar Net ring, Fail-Safe Mode must be set to Permanent and Fail-Safe Behaviour to Disconnect.
    • The inverter with data manager must be located in the last position of the ring line.
    Correct wiring
    Function in the event of a fault
    Faults occur at the beginning and end of the Solar Net ring – the primary inverter stops sending the signal, and secondary inverters switch off with status 710.
    Faults occur at the beginning and end of the Solar Net ring or between the connected inverters – the primary inverter stops sending the signal, and secondary inverters switch off with status 710.
    No.
    Function
    (1)
    IP switch
    For changing the IP address:
    Switch position A
    Specified IP address and opening the WLAN Access Point
    Fronius Datamanager 2.0 uses fixed IP address 169.254.0.180 for a direct connection to a PC via LAN.
    If the IP switch is set to position A, an Access Point for a direct WLAN-connection to Fronius Datamanager 2.0 is also opened.
    Access data for this Access Point:
    Network name: FRONIUS_240.XXXXXX
    Key: Enter the password shown on the inverter display.
    Fronius Datamanager 2.0 can be accessed:
    • via DNS name "http://datamanager"
    • via IP address 169.254.0.180 for the LAN interface
    • via IP address 192.168.250.181 for the WLAN Access Point
    Switch position B
    Assigned IP address
    Fronius Datamanager 2.0 operates using an assigned IP address (factory setting DHCP dynamic).
    The IP address can be set at the Fronius Datamanager 2.0 website.
    (2)
    WLAN LED
    • Flashes green: Fronius Datamanager 2.0 is in service mode
      (IP switch on the Fronius Datamanager 2.0 plug-in card is set to position A or service mode was activated via the inverter display, the WLAN Access Point is opened)
    • Lights up green: There is an existing WLAN connection
    • Alternately flashes green/red: The length of time for which the WLAN Access Point is open after activation (1 hour) has been exceeded
    • Lights up red: There is no existing WLAN connection
    • Flashes red: Faulty WLAN connection
    • Does not light up: Fronius Datamanager 2.0 is in slave mode
    (3)
    Fronius Solar.web connection LED
    • Lights up green: There is an existing connection to Fronius Solar.web
    • Lights up red: There is no existing connection to Fronius Solar.web, but one is required
    • Does not light up: No connection to Fronius Solar.web is required
    (4)
    Supply LED
    • Lights up green: Sufficient power supply from Fronius Solar Net; Fronius Datamanager 2.0 is operational.
    • Does not light up: No power or insufficient power supply from Fronius Solar Net - an external power supply is required
      or
    • Flashes red: During an update process
      IMPORTANT! Do not interrupt the power supply during an update process.
    • Lights up red: Update process failed
    (5)
    Connection LED
    • Lights up green: There is an active connection within Fronius Solar Net
    • Lights up red: There is an interrupted connection within Fronius Solar Net
    (6)
    LAN connection socket
    Ethernet interface colored blue for connecting the Ethernet cable
    (7)
    I/Os
    Digital inputs and outputs
    Modbus RTU 2-wire (RS-485):
    D-
    Modbus data -
    D+
    Modbus data +
    Int./ext. power supply
    GND
    Uint/Uext
    Output for internal voltage 12.8 V
    or
    input for external supply voltage
    > 12.8 - 24 V DC (+ 20%)
    Digital inputs: 0 - 3, 4 - 9
    Voltage level: low = min. 0 V - max. 1.8 V; high = min. 3 V - max. 24V DC (+ 20%)
    Input currents: dependent on input voltage; input resistance = 46 kOhm
    Digital outputs: 0 - 3
    Switching capacity when supplied by the Fronius Datamanager 2.0 plug-in card: 3.2 W in total for all 4 digital outputs
    Switching capacity when supplied by an external power supply with min. 12.8 - max. 24 V DC (+ 20%), connected to Uint/Uext and GND: 1 A, 12.8 - 24 V DC (depending on the external power supply) per digital output
    The connection to the I/Os is made via the supplied mating connector.
    (8)
    Antenna plug
    For screwing on the WLAN antenna
    (9)
    Modbus termination switch (for Modbus RTU)
    Internal bus termination with 120-ohm resistance (yes/no)
    Switch in "ON” position: Termination resistance of 120 Ohm active
    Switch in "OFF” position: No termination resistance active
    IMPORTANT! The termination resistance must be active for the first and last device in an RS-485 bus.
    (10)
    Fronius Solar Net master/slave switch
    For switching between master and slave mode within a Fronius Solar Net ring
    IMPORTANT! All LEDs on the Fronius Datamanager 2.0 plug-in card are off in slave mode.
    1. Fronius Datamanager 2.0
    No.
    Function
    (1)
    IP switch
    Switch position A
    Switch position B
    Assigned IP address
    (2)
    WLAN LED
    (3)
    (4)
    Supply LED
      or
    (5)
    Connection LED
    (6)
    (7)
    I/Os
    D-
    Modbus data -
    D+
    Modbus data +
    GND
    Uint/Uext
    or
    (8)
    Antenna plug
    (9)
    (10)
    The night mode parameter in the display settings in the Setup menu is preset to “OFF” ex-factory.
    As a result, the Fronius Datamanager 2.0 is not available at night or if insufficient DC voltage is available.
    To activate the Fronius Datamanager 2.0, switch the inverter on the AC side off and back on again and press any function key on the inverter’s display within 90 seconds.
    Also refer to the “Menu items in the Setup menu”, “Display settings” (night mode) chapter.
    Safety
    CAUTION!
    DATCOM components and/or the PC/laptop may be seriously damaged if the Ethernet or Fronius Solar Net cables are connected incorrectly to the Fronius Datamanager 2.0
    The Ethernet cable should only be inserted into the LAN connection socket (colored blue).
    The Fronius Solar Net cable should only be inserted into the Fronius Solar Net IN connection socket (colored red).
    Fronius Solar Net termination plug, if only one inverter with Fronius Datamanager 2.0 is linked to a PC
    Fronius Solar Net cable, if an inverter with installed Fronius Datamanager 2.0 is linked to a PC and other DATCOM components
    A LAN cable is not included in the scope of supply
    Connection between Fronius Datamanager 2.0 and PC via LAN or WLAN
    1Insert and lay the Ethernet cable in the inverter like a data communication cable in accordance with the Operating Instructions for the inverter
    2Insert the Ethernet cable into the LAN connection socket
    3Insert the Ethernet cable into the PC/laptop or into a suitable network connection socket
    4If only one inverter with Fronius Datamanager 2.0 is linked to a PC:
    Insert the Fronius Solar Net termination plug into the Fronius Solar Net IN and Solar Net OUT connection sockets
    If other Fronius DATCOM components are connected to the network, besides the inverter with Fronius Datamanager 2.0:
    Insert the Fronius Solar Net cable into the Fronius Solar Net IN connection socket of Fronius Datamanager 2.0
    5Connect the other Fronius DATCOM components
    IMPORTANT! A Fronius Solar Net termination plug must be inserted into the empty Fronius Solar Net connection sockets of the last Fronius DATCOM component.
    When starting the Fronius Datamanager 2.0 for the first time,
    • the Fronius Datamanager 2.0 plug-in card must be installed in the inverter,
      or
    • there must be a Fronius Datamanager Box 2.0 in the Fronius Solar Net ring.
    IMPORTANT! In order to establish a connection to Fronius Datamanager 2.0, “Obtain IP address automatically (DCHP)” must be activated on the end device in question (e.g. laptop, tablet).
    NOTE!
    If the photovoltaic system has only one inverter, steps 1 and 2 below can be skipped.
    In this case, starting for the first time will commence with step 3.
    1Connect inverter with Fronius Datamanager 2.0 or Fronius Datamanager Box 2.0 to the Fronius Solar Net
    2When networking several inverters in Fronius Solar Net:Set the Fronius Solar Net master / slave switch on the Fronius Datamanager 2.0 plug-in card correctly
    • One inverter with Fronius Datamanager 2.0 = master
    • All other inverters with Fronius Datamanager 2.0 = slave (the LEDs on the Fronius Datamanager 2.0 plug-in cards and boxes are not illuminated)
    3Switch the device to Service mode
    • Activate the WLAN Access Point via the Setup menu on the inverter
    The inverter establishes the WLAN access point. The WLAN access point remains open for 1 hour. The protection switch on the Fronius Datamanager 2.0 can remain in switch position A due to the activation of the WLAN Access Point.
    Installation using a web browser
    4Connect the end device to the WLAN access pointSSID = FRONIUS_240.xxxxx (5-8 digits)
    • Search for a network with the name "FRONIUS_240.xxxxx"
    • Establish a connection to this network
    • Enter password from the inverter display
    (Alternatively, connect the end device and inverter using an Ethernet cable.)
    5Enter the following in the browser:
    http://datamanager
    or
    192.168.250.181 (IP address for WLAN connection)
    or
    169.254.0.180 (IP address for LAN connection)
    The Setup wizard start page is displayed.
    The technician wizard is intended for the installer and contains standard-specific settings. Running the technician wizard is optional.
    If the technician wizard is run, it is vital to note the service password that is issued. This service password is necessary for setting the "DNO Editor" menu item.
    If the technician wizard is not run, no specifications regarding power reduction are set.
    Running the Fronius Solar.web wizards is mandatory.
    6Run the Fronius Solar.web wizards and follow the instructions
    The Fronius Solar.web homepage is displayed,
    or
    the Fronius Datamanager 2.0 web page is displayed.
    7Where necessary, run the technician wizard and follow the instructions
    More detailed information on Fronius Datamanager 2.0 and other start-up options can be found at:
    → http://www.fronius.com/QR-link/4204260191EA
    Keys and symbols
    Keys and Symbols
    Item
    Description
    (1)
    Display
    for displaying values, settings and menus
    Control and Status LEDs
    (2)
    Initializing LED (red) is illuminated,
    • during the initialization phase when starting-up the inverter
    • permanently if a hardware defect occurs when starting up the inverter in the initialization phase
    (3)
    Status LED (orange) is illuminated, if
    • the inverter is in the automatic startup or self test phase after the initialization phase (as soon as the solar modules yield sufficient power output after sunrise)
    • State codes are shown on the inverter display
    • if the inverter has been set to standby operation in the setup menu (= manual shutoff of grid power feed operation)
    • if the inverter software is being updated
    (4)
    Operating LED (green) is illuminated,
    • if the photovoltaic system is operating without errors after the inverter’s automatic start-up phase
    • as long as energy is being fed into the grid
    Function keys - each has a different function depending on the selection:
    (5)
    ‘Left/Up’ key
    for navigating left and up
    (6)
    ‘Down/Right’ key
    for navigating down and right
    (7)
    'Menu/Esc' key
    for switching to the menu level
    to exit the Setup menu
    (8)
    'Enter' key
    for confirming a selection
    The keys have a capacitive function. Wetting the keys with water may impair their function. For optimal function, wipe the keys with a dry cloth if necessary.
    1. Keys and symbols
    Keys and Symbols
    Item
    Description
    (1)
    Display
    (2)
    (3)
    (4)
    (5)
    ‘Left/Up’ key
    (6)
    ‘Down/Right’ key
    (7)
    'Menu/Esc' key
    (8)
    'Enter' key
    1. Keys and symbols
    Display
    Power for the display comes from the mains voltage. Depending on the setting selected in the Setup menu, the display can be kept on all day. (For night mode, see section Display Settings)
    IMPORTANT! The display of the inverter is not a calibrated measuring device.
    A slight deviation from the utility meter of the energy company is system-related. A calibrated meter will be needed to calculate the bills for the energy company.
    Display area, display mode
    Display area, setup mode
    Scroll bar
    Energy Manager icon
    is displayed when the "Energy Manager" function is activated
    For more information, see section Relay (Floating Switch Contact)
    Inv. no. = Inverter DATCOM number,
    Save symbol - appears briefly while set values are being saved,
    USB connection - appears if a USB flash drive has been connected
    1Press any key.
    The display illumination is activated.
    The SETUP menu, under the ‘Display settings - illumination’ entry, offers a choice between a permanently lit or permanently dark display.
    1. Navigation in the Menu Level
    1Press any key.
    If no key is pressed for 2 minutes, the display illumination turns off automatically and the inverter switches to the ‘NOW’ display mode (if the display illumination is set to AUTO).
    The inverter can automatically be switched to the ‘NOW’ display mode from any menu level, unless the inverter was manually switched to standby mode.
    The current power feed-in is displayed after automatically switching to the ’NOW’ menu item.
    1Press the ‘Esc’   key
    The display switches to the menu level.
    2Use the ‘left’ or ‘right’ key   to select the desired menu item
    3Access the desired menu item by pressing the ‘Enter’   key
    The menu items
    • NOW
      shows current data
    • LOG
      shows data recorded from today, from the current calendar year and since the inverter was started for the first time
    • GRAPH
      daily characteristic curve graphically represents the course of the output power during the day. The time axis is automatically scaled. Press the ‘Back’ key to close the display
    • SETUP
      setup menu
    • INFO
      information on the device and software
    Output power (W) - depending on the device type (MultiString), the individual output power values for MPP Tracker 1 and MPP Tracker 2 (MPPT1 / MPPT2) are displayed after the Enter key    is pressed
    AC reactive power (VAr)
    Grid voltage (V)
    Output current (A)
    Grid frequency (Hz)
    Solar voltage (V) - U PV1 of MPP Tracker 1 and U PV2 of MPP Tracker 2 (MPPT1/MPPT2), if MPP Tracker 2 is activated (see ‘The Basic menu’ - ‘The Basic menu entries’)
    Solar current (A) - I PV1 of MPP Tracker 1 and I PV2 of MPP Tracker 2 (MPPT1/MPPT2), if MPP Tracker 2 is activated (see ‘The Basic menu’ - ‘The Basic menu entries’)
    Time/date - time and date on the inverter or in the Fronius Solar Net ring
    Amount of energy fed (kWh/MWh)
    amount of energy fed into the grid during the observation period.
    After pressing the Enter key   the individual output powers for MPP Tracker 1 and MPP Tracker 2 (MPPT1/MPPT2) are displayed, if MPP Tracker 2 is activated (see ‘The Basic menu’ - ‘The Basic menu entries’)
    Due to the variety of different monitoring systems, deviations may exist between the readings of other measuring instruments and the readings from the inverter. Only the readings of the calibrated meter supplied by the electricity company are relevant for determining the energy supplied to the grid.
    Maximum output power (W)
    highest amount of energy fed into the grid during the observation period.
    Earnings
    money earned during the observation period
    As was the case for the output energy, readings may differ from those of other instruments.
    The setting of the currency and charge rate is described in the “‘Energy yield’ subitem in the Setup menu”.
    The factory setting depends on the country setup.
    CO2 savings
    carbon dioxide saved during the observation period
    The CO2 factor setting is described in the “‘CO2 factor’ subitem in the Setup menu” section.
    Maximum mains voltage (V) [phase - neutral or phase - phase display]
    maximum mains voltage measured during the observation period
    The individual mains voltages are listed after the Enter key   is pressed
    Maximum solar voltage (V)
    maximum solar module voltage measured during the observation period.
    After pressing the Enter key    the voltage values for MPP Tracker 1 and MPP Tracker 2 (MPPT1/MPPT2) are displayed, if MPP Tracker 2 is activated (see ‘The Basic menu’ - ‘The Basic menu entries’)
    Operating Hours
    indicates how long the inverter has been operating (HH:MM).
    IMPORTANT! The time must be set correctly for day and year values to be displayed properly.
    The SETUP menu item
    Presetting
    After completing the entire start-up process (for example, using the Installation Wizard), the inverter is preconfigured depending on the country setup.
    The SETUP menu lets you easily customize the inverter’s preset parameters to your needs.
    1. The SETUP menu item
    Presetting
    Software Updates
    IMPORTANT! Because of software updates, certain functions may be available for your device but not described in these operating instructions or vice versa. In addition, individual figures may also differ from the operating elements of your device. However, the function of these operating elements is identical.
    Accessing the SETUP Menu
    1In the menu level, use the ‘left’ or ‘right’ keys    to select the ‘SETUP’ menu
    2Press the ‘Enter’ key
    The first entry in the SETUP menu is displayed:
    ‘Standby'
    Scrolling between Entries
    3Use the ‘up’ or ‘down’ keys    to scroll between the available entries
    Exiting an Entry
    4To exit an entry, press the "Back" key
    The menu level is displayed
    • the inverter switches from any item within the menu level to the ‘NOW’ menu (exception: ‘Standby’ setup menu),
    • the display illumination turns off, unless the illumination has been set to ON in the display setting (see Display Settings - Illumination).
    • The power being fed in is shown or the current state code is displayed.
    1Access the desired menu
    2Use the ‘Up’ and ‘Down’ keys to select the desired entry
    3Press the "Enter" key
    The available settings are displayed:
    The first digit of a value to be set flashes:
    4Use the ‘Up’ and ‘Down’ keys to select the desired setting
    5Press the ‘Enter’ key to save and apply the selection.
    Press the ‘Esc’ key to exit without saving.
    4Use the "Up" and "Down" keys to select a value for the first digit
    5Press the "Enter" key
    The second digit of the value flashes.
    6Repeat steps 4 and 5 until...
    the entire value flashes.
    7Press the "Enter" key
    8Repeat steps 4 - 6 for units or other values to be set until the unit or value flashes.
    9Press the ‘Enter’ key to save and apply the changes.
    The currently selected entry is displayed.
    1Select the ‘Energy yield’ setup menu entry
    The overview of adjustable values is displayed.
    3Use the ‘up’ or ‘down’ keys    to select the ‘Feed-in tariff’
    4Press the ‘Enter’ key
    The feed-in tariff is displayed
    The tens digits flashes.
    5Use the ‘plus’ or ‘minus’ keys    to select a value for the tens digit
    6Press the ‘Enter’ key
    The units position flashes.
    7Repeat steps 5 and 6 for the units position and the 3 decimal places until ...
    The set feed-in tariff flashes.
    8Press the ‘Enter’ key
    The feed-in tariff is applied and the overview of adjustable values is displayed.
    9Press the ‘Esc’
    The ‘Energy yield’ setup menu entry is displayed.
    Standby
    Manual activation/deactivation of the standby mode
    • No energy is fed into the grid.
    • The Startup LED lights up orange.
    • The display switches between STANDBY/ENTER
    • In standby mode, no other menu item can be accessed or set in the menu level.
    • The automatic switching to the ‘NOW’ menu item after 2 minutes if no key is pressed is not activated.
    • The standby mode can only be deactivated manually by pressing the ‘Enter’ key.
    • The grid power feed operation can be resumed at any time by pressing the ‘Enter’ key, if no error (state code) is displayed
    Setting the standby mode (manual shutoff for feeding energy into the grid):
    1Select the ‘Standby’ entry
    2Press the ‘Enter’ function key
    The display alternates between ‘STANDBY’ and ‘ENTER.’
    The Standby mode is now activated.
    Restoring the grid power feed operation:
    In Standby mode, the display alternates between ‘STANDBY’ and ‘ENTER’.
    1Press the ‘Enter’ function key    to restore the grid power feed operation
    The ‘Standby’ entry is displayed.
    The inverter also switches to the Startup phase.
    After the grid power feed operation is restored, the Operation Status LED lights up green.
    1. Menu Items in the Setup Menu
    Standby
    WLAN Access Point
    To activate/deactivate the WLAN Access Point. For example, this is required to set up or adjust the system monitoring using the Datamanager web interface. If no Datamanager is detected by the inverter, [not available] is displayed
    Setting range
    WLAN Access Point
    [stopped]
    Activate WLAN AP?
    To activate the WLAN Access Point   Press the Enter key
    WLAN Access Point
    [active]
    The SS-ID (SS) and the password (PW) are displayed.
    Deactiv. WLAN AP?
    To deactivate the WLAN Access Point   Press the Enter key
    WLAN Access Point
    [not available]
    Is displayed if no system monitoring is available on the inverter.
    DATCOM
    Check the data communication, entry of the inverter number, protocol settings
    Setting range
    Status/inverter number/protocol type
    Status
    Displays data communication available via Fronius Solar Net or an error that occurred in data communication
    Inverter Number
    Number setting (address) of the inverter in a setup with multiple inverters
    Setting range
    00 - 99 (00 = inverter address 100)
    Factory setting
    01
    IMPORTANT! Each inverter must be assigned its own address when using multiple inverters in a data communications system.
    Protocol Type
    Defines the communication protocol used to transmit data:
    Setting range
    Fronius Solar Net / Interface *
    Factory setting
    Fronius Solar Net
    * The interface protocol type only functions without a Fronius Datamanager card. Existing Fronius Datamanager cards must be removed from the inverter.
    USB
    Performing firmware updates or saving inverter detail values on a USB thumb drive
    Setting range
    Safely remove hardware / software update / logging interval
    To remove a USB thumb drive from the USB A socket on the data communication rack without losing data.
    The USB thumb drive can be removed:
    • When OK is displayed
    • When the "Data Transfer" LED is no longer flashing or lit
    Software update
    For updating inverter firmware using a USB thumb drive.
    Procedure:
    1Obtain the "froxxxxx.upd" firmware update file
    (e.g. at http://www.fronius.com; xxxxx stands for the respective version number)
    NOTE!
    To ensure problem-free updates of inverter software, the USB thumb drive should have no hidden partitions and no encryption (see the chapter "Suitable USB Thumb Drives").
    2Save the firmware update file to the highest data level of the USB thumb drive
    3Open the lid of the data communication area on the inverter
    4Insert the USB thumb drive with the firmware update file into the USB socket in the inverter data communication area
    5In the Setup menu, go to "USB" and select "Software Update"
    6Press the "Enter" key
    7Wait until the comparisons of the current software version on the inverter and the new firmware version are displayed:
    • First page: Recerbo software (LCD), key controller software (KEY), country setup version (Set)
    • Second page: Software power module (PS1, PS2)
    8Press the "Enter" function key at the end of each page
    The inverter begins copying the data.
    "BOOT" and the save progress (%) of the individual tests are displayed until the data for all electronic components has been copied.
    Once the data has been copied, the inverter updates the required electronic components in succession.
    "BOOT", the affected component, and the update progress (%) are displayed.
    The inverter updates the display in the last step.
    The display remains dark for approx. 1 minute, the control and status LEDs flash.
    Once the firmware update is complete, the inverter switches to the Startup phase and then to grid power feed operation. Remove the USB thumb drive using the "Safely remove hardware" function.
    Individual settings in the Setup menu are retained when the inverter firmware is updated.
    Logging interval
    Activating/deactivating the USB logging function, as well as setting the logging interval
    Unit
    Minutes
    Setting range
    30 Min. / 20 Min. / 15 Min. / 10 Min. / 5 Min. / No Log
    Factory setting
    30 Min.
    30 Min.
    The logging interval is 30 minutes; new logging data is saved to the USB thumb drive every 30 minutes.
    20 Min.
    15 Min.
    10 Min.
    5 Min.
    The logging interval is 5 minutes; new logging data is saved to the USB thumb drive every 5 minutes.
    No Log
    No data is saved
    IMPORTANT! The time must be set correctly in order for the USB logging function to work properly. The time setting is handled in the "Setup menu items" - "Time/Date" point.
    A floating switch contact (relay) on the inverter can be used to display status codes, the inverter status (e.g. the grid power feed operation) or the Energy Manager functions.
    Setting range
    Relay Mode / Relay Test / Switch-on Point* / Switch-off Point*
    * is only shown if the “E-Manager” function has been activated under “Relay Mode.”
    Relay Mode
    The following functions can be displayed via the relay mode:
    • Alarm function (Permanent / ALL / GAF)
    • Active output (ON / OFF)
    • Energy Manager (E-Manager)
    Setting range
    ALL / Permanent / GAF / OFF / ON / E-manager
    Factory setting
    ALL
    Alarm function:
    ALL / Permanent:
    Switches the floating switch contact for continual and temporary service codes (e.g. brief interruption of grid power feed operation, a service code occurs a certain number of times per day – can be set in the “BASIC” menu)
    GAF
    As soon as “GAF” mode is selected, the relay will be switched on. As soon as the power module reports an error and switches from regular grid power feed operation to an error state, the relay is opened. This way, the relay can be used for fail safe functions.
    Application example
    When using single-phase inverters at a multi-phase location a phase equalization might be necessary. If an error occurs with one or more inverters and the connection to the grid is disconnected, the other inverters must also be disconnected in order to maintain phase equilibrium. The “GAF” relay function can be used with the datamanager or an external protective device to detect or signal that an inverter is not being supplied or is disconnected from the grid, and that the remaining inverters should also be disconnected from the grid via remote control.
    Active output:
    ON:
    The floating NO switch contact is constantly switched on while the inverter is operating (as long as the display lights up or displays).
    OFF:
    The floating NO switch contact is switched off.
    Energy Manager:
    E-Manager:
    You can find additional information on the “Energy Manager” function in the following “Energy Manager” section.
    Relay test
    Function test to confirm whether the floating switch contact switches
    Switch-on point (only if the “Energy Manager” function is activated)
    to set the effective power limit from which the floating switch contact is switched on
    Factory setting
    1000 W
    Setting range
    set switch-off point up to the inverter’s nominal output (W or kW)
    Switch-off point (only if the “Energy Manager” function is activated)
    to set the effective power limit from which the floating switch contact is switched off
    Factory setting
    500
    Setting range
    0 up to the inverter’s set switch-on point (W or kW)
    Energy Manager
    (in the Relay Menu)
    The "Energy Manager" function can be used to control the floating switch contact so that this acts as an actuator.
    A load connected to the floating switch contact can therefore be controlled by assigning a switch-on or switch-off point depending on the feed-in power (effective power).
    The floating switch contact is automatically switched off:
    • When no current is being fed into the public grid by the inverter
    • When the inverter is manually switched to standby mode
    • When there is an effective power assignment < 10% of the inverter's rated power output
    To activate the Energy Manager function, select "E-Manager" and press the "Enter" key.
    When the "Energy Manager" function is activated, the "Energy Manager" icon is shown at the top left of the display:
       when the floating NO switch contact is switched off (open contact)
       when the floating NC switch contact is switched on (closed contact)
    To deactivate the "Energy Manager" function, select another function (ALL / Permanent / OFF / ON) and press the "Enter" key.
    NOTE!
    Information on setting the switch-on and switch-off point
    Too small a difference between the switch-on point and switch-off point as well as fluctuations in effective power can lead to multiple switching cycles.
    To avoid frequent switching on and off, the difference between the switch-on point and the switch-off point should be at least 100 - 200 W.
    When selecting the switch-off point, consider the power consumption of the connected load.
    When selecting the switch-on point, consider the weather conditions and the expected solar radiation.
    Application example
    Switch-on point = 2,000 W, switch off point = 1,800 W
    If the inverter supplies 2,000 W or more, the inverter's floating switch contact is switched on.
    If the inverter output falls below 1,800 W, the floating switch contact is switched off.
    This makes it possible to quickly implement interesting application options, such as operating a heat pump or an air-conditioning system using as much self-produced power as possible
    Time/Date
    Setting the time, date, display format, and automatic adjustment for daylight saving time
    Setting range
    Set time / Set date / Time display format / Date display format / Daylight saving time
    Set time
    Setting the time (hh:mm:ss or hh:mm am/pm, depending on the setting under Time display format)
    Set date
    Setting the date (dd.mm.yyyy or mm/dd/yyyy, depending on the setting under Date display format)
    Time display format
    For specifying the format in which the time is displayed
    Setting range
    12hrs/24hrs
    Factory setting
    Date display format
    For specifying the format in which the date is displayed
    Setting range
    mm/dd/yyyy or dd.mm.yy
    Factory setting
    Activating/deactivating the automatic adjustment for daylight saving time
    IMPORTANT! Only use the automatic daylight savings changeover function when there are no LAN or WLAN-compatible system components in a Fronius Solar Net ring (e.g. Fronius Datalogger Web, Fronius Datamanager or Fronius Hybridmanager).
    Setting range
    on/off
    Factory setting
    on
    IMPORTANT! The time and date must be set correctly for day and year values to be displayed properly.
    Display Settings
    Setting range
    Language / Night Mode / Contrast / Illumination
    Language
    Setting the display language
    Setting range
    English, German, French, Spanish, Italian, Dutch, Czech, Slovakian, Hungarian, Polish, Turkish, Portuguese, Romanian
    Night mode
    Night mode controls the Fronius DATCOM and the inverter’s display operation at night or when insufficient DC voltage is available
    Setting range
    AUTO / ON / OFF
    Factory setting
    OFF
    AUTO:
    The Fronius DATCOM operation is maintained as long as a Fronius Datamanager is connected to an active, uninterrupted Fronius Solar Net.
    The inverter display is dark during the night and can be activated by pressing any function key.
    ON:
    The Fronius DATCOM operation is always maintained. The inverter provides an uninterrupted 12 V DC voltage to supply Fronius Solar Net with power. The display is always active.
    IMPORTANT! When the Fronius DATCOM night mode is ON or on AUTO with connected Fronius Solar Net components, the power consumption of the inverter at night increases to around 7 W.
    OFF:
    No Fronius DATCOM operation at night, the inverter therefore does not require any power to supply electricity to the Fronius Solar Net at night.
    The inverter display is deactivated at night and the Fronius Datamanager is not available. To activate the Fronius Datamanager, switch the inverter on the AC side off and back on and press any function key on the inverter’s display within 90 seconds.
    Contrast
    Set the contrast on the inverter display
    Setting range
    0 - 10
    Factory setting
    5
    Since contrast depends on temperature, it may be necessary to adjust the ‘Contrast’ menu item when environmental conditions change.
    Illumination
    Preset the inverter display illumination
    The ‘Illumination’ menu item only applies to the inverter display background illumination.
    Setting range
    AUTO / ON / OFF
    Factory setting
    AUTO
    AUTO:
    The inverter display illumination is activated by pressing any key. If no key is pressed for 2 minutes, the display backlight goes out.
    ON:
    The inverter display illumination is permanently on when the inverter is active.
    OFF:
    The inverter display illumination is permanently off.
    Energy yield
    The following settings can be changed/performed:
    • Meter deviation/calibration
    • Currency
    • Feed-in tariff
    • CO2 factor
    Setting range
    Currency / Feed-in tariff
    Meter calibration
    Currency
    Set the currency
    Setting range
    3-digit, A-Z
    Feed-in tariff
    Set the charge rate for the remuneration for energy fed into the grid
    Setting range
    2-digit, 3 decimal places
    Factory setting
    (depends on the country setup)
    CO2 factor
    Set the CO2 factor for the energy fed into the grid
    Fan
    For testing the fan functionality
    Setting range
    Test fan #1/test fan #2 (depending on the device)
    • Select the desired fan using the "Up" and "Down" keys
    • Pressing the "Enter" key starts the test for the selected fan.
    • The fan runs until the menu is exited by pressing the "Esc" key.
    IMPORTANT! The inverter display does not indicate whether the fan is OK. The fan function can only be checked by listening and feeling.
    Arc Detection
    for checking arc detection/interruption
    Setting range
    ArcDetector Status/Start Self-test
    Arc.det. Status
    displays the current status of arc detection/interruption
    Start Self-test
    self-test to check whether the inverter interrupts grid power feed operation when an arc is detected.
    Test procedure:
    1Select "Arc Detection" in the Setup menu
    2Press the "Enter" key
    3Use the up and down keys to select "Start Self-test"
    4Press the "Enter" key
    The self-test starts. The arc detection/interruption function simulates an arc and sends the corresponding signal to the inverter.
    If the test is successful, the inverter disconnects from the grid and stops grid power feed operation.
    The message "Self-test completed and Start AFCI" is shown on the display.
    5Confirm the indication by pressing the "Enter" key
    The INFO menu item
    Measured values
    PV Iso.
    Insulation resistance of the photovoltaic system
    Ext. lim.
    External limitation
    U PV 1 / U PV 2*
    Real-time DC voltage at the DC input terminals, even if no energy is being fed in by the inverter (from first or second MPP Tracker)
    * MPP Tracker 2 must be activated - ON - via the Basic menu
    GVDPR
    Grid voltage-dependent power reduction
    Fan #1
    Percentage value of fan target power
    1. The INFO menu item
    Measured values
    PV Iso.
    Ext. lim.
    External limitation
    U PV 1 / U PV 2*
    GVDPR
    Fan #1
    LT Status
    IMPORTANT! STATE 306 (Power low) and STATE 307 (DC low) state codes naturally appear every morning and evening due to low solar radiation. These state codes at this time are not the result of a fault.
    The status display of the last error that occurred in the inverter can be shown.
    • After pressing the ‘Enter’ key, the power stage set status and the last error that occurred are displayed
    • Use the ‘Up’ and ‘Down’ keys to scroll through the list
    • Press the ‘Back’ key to exit the status and error list
    Grid Status
    The last 5 grid errors that occurred can be displayed:
    • After pressing the "Enter" key, the last 5 grid errors that occurred are displayed
    • Use the "up" and "down" keys to scroll through the list
    • Press the "Back" key to exit the grid error display
    Device information
    The device is used to display settings relevant to a grid operator. The displayed values depend on the respective country setup or device-specific inverter settings.
    Display range
    General / Country-specific setting / MPP Tracker / Grid monitoring / Grid voltage limits / Grid frequency limits / Q-mode / AC power limit / AC voltage derating / Fault ride through
    General:
    Device type - the precise name of the inverter
    Fam. - the inverter's inverter family
    Serial number - the inverter's serial number
    Country-specific setting:
    Setup - set country setup
    Version - country setup version
    Origin activated - indicates that the normal country setup is activated.
    Altern. activated - indicates that the alternative country setup is activated (only for Fronius Symo Hybrid)
    Group - inverter software update group
    MPP Tracker:
    Tracker 1 - displays the set tracking behavior (MPP AUTO / MPP USER / FIX)
    Tracker 2 - displays the set tracking behavior (MPP AUTO / MPP USER / FIX)
    Grid monitoring:
    GMTi - Grid Monitoring Time - inverter start-up time in sec. (seconds)
    GMTr - Grid Monitoring Time reconnect - reconnection time in sec. (seconds) after a grid error
    ULL - U (voltage) Longtime Limit - voltage limit value in V (Volt) for the 10-minute mean voltage
    LLTrip - Longtime Limit Trip - trip time for the ULL, monitoring how quickly the inverter must be switched off
    Grid voltage limits - inner limit value:
    UMax - upper inner grid voltage value in V (Volt)
    TTMax - Trip Time Max - trip time for exceeding the upper inner grid voltage limit value in cyl*
    UMin - lower inner grid voltage value in V (Volt)
    TTMin - Trip Time Min - trip time for falling below the lower inner grid voltage limit value in cyl*
    *cyl = grid periods (cycles); 1 cyl equals 20 ms at 50 Hz or 16.66 ms at 60 Hz
    Grid voltage limits - outer limit value
    UMax - upper outer grid voltage value in V (Volt)
    TTMax - Trip Time Max - trip time for exceeding the upper outer grid voltage limit value in cyl*
    UMin - lower outer grid voltage value in V (Volt)
    TTMin - Trip Time Min - trip time for falling below the lower outer grid voltage limit value in cyl*
    Grid frequency limits:
    FILmax - upper inner grid frequency value in Hz (Hertz)
    FILmin - lower inner grid frequency value in Hz (Hertz)
    FOLmax - upper outer grid frequency value in Hz (Hertz)
    FOLmin - lower outer grid frequency value in Hz (Hertz)
    Q-Mode:
    Indicates the current reactive power setting on the inverter (e.g. OFF, Q/P...)
    AC power limit, including indication of SoftStart and/or AC grid frequency derating:
    Max P AC - maximum output power, which can be changed with the "Manual Power Reduction" function
    GPIS - Gradual Power Incrementation at Startup - indicates (%/sec) whether the SoftStart function is activated on the inverter
    GFDPRe - Grid Frequency Dependent Power Reduction enable limit - displays the set grid frequency value in Hz (Hertz) from when a power reduction occurs
    GFDPRv - Grid Frequency Dependent Power Reduction derating gradient - displays the set grid frequency value in %/Hz to indicate the extent of the power reduction
    AC voltage derating:
    GVDPRe - Grid Voltage Depending Power Reduction enable limit - threshold in V from which the voltage-dependent power reduction starts
    GVDPRv - Grid Voltage Depending Power Reduction derating gradient - reduction gradient in %/V at which the power is reduced
    Message - shows whether the dispatch of an info message via Fronius Solar Net is activated
    Version
    link_horizontalLink copied
    Display of version number and serial number of the PC boards installed in the inverter (e.g., for service purposes)
    Display range
    Display/Display Software/Integrity Checksum/Memory Card/Memory Card #1/Power Stage/Power Stage Software/EMI Filter/Power Stage #3/Power Stage #4
    Switching the key lock on and off
    General
    The inverter comes equipped with a ‘Key lock’ function.
    When the ‘Keylock’ function is active, the Setup menu cannot be accessed, e.g., to protect against setup data being changed by accident.
    You must enter code 12321 to activate / deactivate the ‘Key lock’ function.
    1. Switching the key lock on and off
    General
    Switching the Key Lock On and Off
    1Press the ‘Menu’ key
    The menu level is displayed.
    2Press the unassigned ‘Menu/Esc’ key
    5 times
    In the ‘CODE’ menu, the ‘Access Code’ is displayed and the first digit flashes.
    3Enter code 12321: Use the ‘plus’ or ‘minus’ keys    to select the first digit of the code
    The second digit flashes.
    5Repeat steps 3 and 4 for the second, third, fourth, and fifth digit in the code until...
    the set code flashes.
    In the ‘LOCK’ menu, the ‘Key lock‘ function is displayed.
    7Use the ‘plus’ or ‘minus’ keys    to switch the key lock on or off:
    ON = the key lock function is activated (the SETUP menu item cannot be accessed)
    OFF = the key lock function is deactivated (the SETUP menu item can be accessed)
    USB Stick as a Data Logger and for Updating Inverter Software
    USB Thumb Drive as a Data Logger
    A USB thumb drive connected to the USB A socket can act as a data logger for an inverter.
    Logging data saved to the USB thumb drive can, at any time,
    • be imported into the Fronius Solar.access software via the included FLD file,
    • be viewed directly in third-party applications (e.g., Microsoft® Excel) via the included CSV file.
    Older Excel versions (up to Excel 2007) have a row limit of 65536.
    More detailed information on data on the USB thumb drive, data amounts and memory capacity, and buffer memory can be found at:
    → http://www.fronius.com/QR-link/4204260202EA
    1. USB Stick as a Data Logger and for Updating Inverter Software
    Due to the number of USB thumb drives on the market, we cannot guarantee that every USB thumb drive will be recognized by the inverter.
    Fronius recommends using only certified, industrial USB thumb drives (look for the USB-IF logo).
    The inverter supports USB thumb drives using the following file systems:
    • FAT12
    • FAT16
    • FAT32
    Fronius recommends that the USB thumb drive only be used for recording logging data or for updating the inverter software. USB thumb drives should not contain any other data.
    USB symbol on the inverter display, e.g., in the 'NOW' display mode:
    When the inverter recognizes a USB thumb drive, the USB symbol will appear at the top right of the display.
    When inserting the USB thumb drive, make sure that the USB symbol is displayed (it may also be flashing).
    IMPORTANT! Please be aware that in outdoor applications the USB thumb drive may only function in a limited temperature range.
    Make sure, for example, that the USB thumb drive will also function at low temperatures for outdoor applications.
    USB thumb drive for updating inverter software
    The USB thumb drive can be used even by end customers to update the software of the inverter. The update file is saved to the USB thumb drive beforehand and transmitted from there to the inverter, and the update process is started through the Setup menu.
    Removing the USB Stick
    Safety information for removing a USB stick
    IMPORTANT! To prevent a loss of data, the connected USB stick should only be removed under the following conditions:
    • via the SETUP and "Safely remove USB / hardware" menu items
    • when the "Data Transfer" LED is no longer flashing or illuminated.
    The Basic menu
    Accessing the Basic Menu
    5 times
    In the "CODE" menu, the "Access Code" is displayed; the first digit flashes.
    3Enter code 22742: Use the ‘plus’ or ‘minus’ keys    to select the first digit of the code
    5Repeat steps 3 and 4 for the second, third, fourth, and fifth digit of the code until...
    The Basic menu is displayed.
    7Use the ‘plus’ or ‘minus’ keys    to select the desired entry
    8Press the ‘Enter’ key    to edit the selected entry
    9Press the ‘Esc’ key
    1. The Basic menu
    5 times
    1. The Basic menu
    Basic Menu Entries
    The Basic menu contains the following parameters important for the installation and operation of the inverter:
    MPP Tracker 1
    • DC operating mode: MPP AUTO / FIX / MPP USER
      • MPP AUTO: normal operating status; the inverter automatically searches for the optimal operating point
      • FIX: enter a fixed DC voltage used by the inverter. Enter the fixed voltage value in the fixed voltage point.
      • MPP USER: enter the lower MPP voltage from which the inverter searches for its optimal operating point. Enter this start value for the MPPT start voltage.
    • Dynamic Peak Manager: ON/OFF
    • Fixed voltage: enter the fixed voltage for the FIX function
    • MPPT start voltage: enter the start voltage for the MPP USER function
    USB Logbook
    Activate or deactivate the function for saving all error messages on a USB thumb drive
    AUTO (no function; reserved for future applications) / OFF (deactivates the USB logbook function (factory setting)) / ON (activates the USB logbook function)
    Signal Input (multifunctional power interface)
    • Function: Ext Sig. / S0-Meter / OFF
      only if the Ext Sig. function is selected:
      • Trigger type: Warning (warning is shown on the display - STATE 568) / Ext. Stop (inverter is switched off - STATE 668)
      • Connection type: N/C (normally closed) / N/O (normally open)
    SMS/Relay
    • Event delay
      to enter the delay time after which an SMS is sent or the relay switches
      900 - 86,400 seconds
    • Event counter:
      to enter the number of events that lead to a signal:
      10 - 255
    More information is provided under ‘Setup menu items’ - ‘Relays’
    Insulation Setting
    • Insulation warning: ON / OFF - to activate and deactivate the insulation monitoring that displays a warning without interrupting the grid power feed operation in case of an insulation error
    • Threshold warning: to set an insulation threshold below which the inverter issues a warning (without interrupting the grid power feed operation); the STATE 502 state code is displayed
    • Threshold error: to set an insulation threshold below which the inverter displays an error message and interrupts the grid power feed operation; the STATE 475 state code is displayed (not available in all countries)
    TOTAL Reset
    resets the max. and min. voltage values and the max. power of feeding in to zero in the LOG menu.
    Once values are reset, this action cannot be undone.
    To reset the values to zero, press the "Enter" key.
    "CONFIRM" is displayed.
    Press the "Enter" key again.
    The values are reset and the menu is displayed
    Status Diagnosis and Troubleshooting
    Displaying status codes
    Your inverter is equipped with system self diagnosis that automatically identifies a large number of possible operation issues by itself and displays them on the screen. This enables you to know immediately if there are any malfunctions in the inverter or the photovoltaic system or any installation or operating errors.
    Whenever the system self diagnosis has identified a particular issue, the respective status code is shown on the screen.
    IMPORTANT! Status codes may sometimes appear briefly as a result of the control response from the inverter. If it subsequently continues to operate normally, there has not been a system error.
    1. Status Diagnosis and Troubleshooting
    Total Failure of the Display
    If the display remains dark for a long time after sunrise:
    • Check the AC voltage at the inverter's connections:
      the AC voltage must be 208/220/240/440/480 V (+10%/-12%) depending on the grid.
    Class 1 status codes
    Status codes in class 1 are typically temporary. Their cause lies in the grid.
    Example: The grid frequency is too high and the inverter is not permitted to feed energy into the grid because this would not comply with a standard. No device fault has occurred.
    The inverter will first respond by disconnecting from the grid. Then, the grid will be checked for the duration of the observation period stipulated. If, after the end of this period, no further defect is identified, your inverter resumes operating and feeding energy into the grid.
    The GPIS soft start function is activated depending on the country setup:
    According to national guidelines, the output power of the inverter increases continuously after a shutdown due to an AC error.
    Code
    Description
    Behavior
    Remedy
    102
    AC voltage too high
    Grid conditions are being tested and as soon as they are within the permissible range again, the inverter will resume feeding energy into the grid.
    Check grid connections.
    If this status code keeps recurring, contact your system installer.
    103
    AC voltage too low
    105
    AC frequency too high
    106
    AC frequency too low
    107
    No AC grid detected
    108
    Stand-alone operation detected
    112
    RCMU error
    Class 2 Status Codes
    Code
    Description
    Behavior
    Remedy
    212
    Overvoltage on L1
    Check grid connections;**)
    213
    Undervoltage on L1
    222
    Overvoltage on L2
    223
    Undervoltage on L2
    232
    Overvoltage on L3
    233
    Undervoltage on L3
    240
    Arc detected
    The status code is displayed for approx. 4 seconds
    241
    Arc detected
    Status code 241 is displayed immediately after 240. The inverter disconnects from the grid for safety reasons.
    Before an inverter can be reset following a detected electric arc, check the entire affected photovoltaic system for damage.
    Reset the status code by pressing the "Enter" key.
    242
    Arc detected
    Status code 242 is displayed immediately after status code 241 is reset.
    The inverter restarts feeding energy into the grid.
    245
    Arc Detector self-test failed
    The inverter disconnects from the grid.
    Carry out AC reset;
    The test is repeated. *)
    247
    Arc Detector current sensor faulty
    249
    Arc Detector faulty
    *) If status code persists: Contact a Fronius-trained service technician
    **) Fault is corrected automatically. If this status code keeps recurring, contact your system installer
    Class 3 Status Codes
    Class 3 comprises status codes that may appear during feed-in operation and that do not cause a permanent interruption of the operation of feeding energy into the grid.
    After automatic disconnection from the grid and waiting for its conditions to return to those stipulated, your inverter will try to resume feed-in operation.
    Code
    Description
    Behavior
    Remedy
    301
    Overcurrent (AC)
    Short interruption of grid power feed operation.
    The inverter returns to the startup phase.
    302
    Overcurrent (DC)
    303
    Overtemperature DC module
    Purge cooling air openings and cooling elements; **)
    304
    Overtemperature AC module
    305
    No feed-in despite closed relay
    306
    There is insufficient PV power for grid power feed operation
    Wait for sufficient solar radiation;
    307
    DC low
    DC input voltage is too low for grid power feed operation
    IMPORTANT! Status codes 306 (Power low) and 307 (DC low) appear naturally every morning and evening due to low solar irradiance. These status codes are not the result of a fault.
    308
    Intermediate circuit voltage too high
    309
    DC input voltage MPPT1 too high
    311
    DC strings polarity reversed
    313
    DC input voltage MPPT2 too high
    314
    Timeout current sensor calibration
    315
    AC current sensor fault
    316
    InterruptCheck fail
    325
    Overtemperature in connection area
    326
    Fan 1 error
    327
    Fan 2 error
    Class 4 status codes
    Class 4 status codes may require the intervention of a trained Fronius service technician.
    Code
    Description
    Behavior
    Remedy
    401
    Communication with power module is not possible
    The inverter will automatically attempt to connect again and, if possible, resume grid power feed operation
    406
    AC module temperature sensor faulty (L1)
    407
    AC module temperature sensor faulty (L2)
    408
    Direct component measured in the supply grid too high
    412
    The "fixed voltage" setting has been selected instead of MPP voltage operation and the voltage is set to a value that is too low or too high.
    415
    Safety cut-out triggered by option card or RECERBO
    Inverter does not feed current into the grid.
    416
    No communication between power module and control unit
    417
    ID problem with hardware
    Update inverter firmware; *)
    419
    Unique ID conflict
    420
    Communication with Hybridmanager is not possible
    421
    Error HID range
    425
    Communication with the power module is not possible
    426–428
    Possible hardware defect
    431
    Software problem
    Carry out AC reset (switch automatic circuit breaker off and on); update inverter firmware; *)
    436
    Function incompatibility (one or more PC boards in the inverter are not compatible with each other, e.g., after PC board replacement)
    437
    Power module problem
    438
    443
    Intermediate circuit voltage too low or unsymmetrical
    445
    • Compatibility error (e.g., due to a PC board replacement)
    • Invalid power module configuration
    447
    Insulation fault
    448
    Neutral conductor not connected
    450
    No guard found
    451
    Memory error detected
    452
    Communication error between processors
    453
    Grid voltage and power module do not match
    454
    Grid frequency and power module do not match
    456
    Anti-islanding function has stopped running properly
    457
    Grid voltage relay error
    Check AC cable *)
    458
    Error during measuring signal detection
    459
    Error during measuring signal detection for insulation test
    460
    Reference voltage source for the digital signal processor (DSP) is operating outside of tolerances
    461
    Error in DSP data memory
    462
    Error in DC feed-in monitoring routine
    463
    AC polarity reversed, AC connector plugged in incorrectly
    474
    RCMU sensor faulty
    475
    Insulation error (connection between solar module and grounding)
    476
    Supply voltage for driver too low
    479
    Intermediate circuit voltage relay switched off
    480,
    481
    482
    Setup interrupted after initial commissioning
    Restart setup after AC reset (switch automatic circuit breaker off and on)
    483
    Voltage UDCfix for MPP2 string is outside of valid range
    Check MPP settings; *)
    485
    CAN transmission buffer is full
    Carry out AC reset (switch automatic circuit breaker off and on); *)
    489
    Permanent overvoltage at intermediate circuit capacitor (status code 479 appears 5x one after the other)
    **) If status code persists: Contact your system installer
    Class 5 state codes
    Class 5 state codes generally do not impair grid power feed operation, but can lead to limitations. They will be displayed until the state code is acknowledged by pressing a key (the inverter, however, continues working normally in the background).
    Code
    Description
    Behavior
    Remedy
    502
    Insulation fault on solar modules
    Warning message is shown on the display
    509
    No feed-in within the last 24 hours
    Acknowledge state code;
    Check whether all conditions for problem-free grid power feed operation are met (e.g., whether solar modules are covered with snow); **)
    515
    Communication with filter not possible
    Warning message on the display
    516
    Communication with memory unit not possible
    Warning message of memory unit
    517
    Power derating due to excessive temperature
    A warning message is shown on the display when a power derating occurs
    Purge cooling air openings and cooling elements if necessary;
    Error is corrected automatically; **)
    518
    Internal DSP malfunction
    519
    520
    No feed-in within the last 24 hours from MPPT1
    Check whether all conditions for problem-free grid power feed operation are met (e.g., whether solar modules are covered with snow); *)
    522
    DC low String 1
    523
    DC low String 2
    558,
    559
    560
    Power derating due to over-frequency
    Displayed when grid frequency is too high; the power is reduced.
    As soon as the grid frequency returns to the permissible range and the inverter is back to normal operation, the error is automatically corrected; **)
    564
    566
    Arc Detector switched off
    (e.g. in the event of external arc monitoring)
    This state code is displayed every day until the Arc Detector is reactivated.
    No error!
    Confirm the state code by pressing the ‘Enter’ key
    568
    Incorrect input signal at the multifunctional power interface
    The state code is displayed in the event of an incorrect input signal at the multifunctional power interface and in the event of the following setting:
    Basic menu / signal input / function = Ext. signal, trigger type = Warning
    check the devices connected to the multifunctional power interface; **)
    572
    Power limitation due to power module
    Power is limited by the power module
    573
    Undertemperature warning
    581
    Setup "Special Purpose Utility-Interactive" (SPUI) is activated
    The inverter is no longer compatible with standards IEEE1547 and IEEE1574.1 because the islanding function is deactivated, frequency-dependent power reduction is activated, and the frequency and voltage limits are being changed
    No error!
    *) If state code persists: Contact a Fronius-trained service technician
    **) If state code persists: Contact your system installer
    Class 6 Status Codes
    Class 6 status codes may require the intervention of a trained Fronius service technician.
    Code
    Description
    Behavior
    Remedy
    601
    CAN bus is full
    Inverter does not feed energy into the grid.
    603
    AC module temperature sensor faulty (L3)
    The inverter will automatically attempt to connect again and, if possible, resume feeding energy into the grid
    604
    DC module temperature sensor faulty
    607
    RCMU fault
    Reset the status code by pressing the "Enter" key. The inverter resumes feeding energy into the grid; if the status code keeps recurring, check the entire affected photovoltaic system for any damage; **)
    608
    Class 7 Status Codes
    Class 7 status codes concern the inverter control unit, configuration and data recording, and can directly or indirectly affect grid power feed operation.
    Code
    Description
    Behavior
    Remedy
    701–704
    Provides information about the internal processor status
    705
    Conflict when setting the inverter number (e.g., number assigned twice)
    Correct inverter number in the setup menu
    706–716
    721
    EEPROM was reinitialized
    Acknowledge status code; *)
    722–730
    731
    Initialization error – USB flash drive is not supported
    Check or replace USB flash drive
    Check the USB flash drive file system; *)
    732
    Initialization error – overcurrent at USB flash drive
    733
    No USB flash drive inserted
    Insert or check USB flash drive; *)
    734
    Update file is not detected or is not available
    Check update file (e.g., for the proper file name)
    735
    The update file does not match the device, the update file is too old
    Warning message is shown on the display, update process is canceled
    Check update file;
    if required, download the correct update file for the device (e.g., at
    http://www.fronius.com); *)
    736
    Write or read error occurred
    Check the USB flash drive and the files on the USB flash drive or replace the USB flash drive.
    Remove the USB flash drive only when the "Data Transfer" LED is no longer flashing or lit.; *)
    737
    File could not be opened
    Remove and reinsert the USB flash drive, check or replace the USB flash drive
    738
    Log file could not be saved (e.g., USB flash drive is write-protected or full)
    Free up memory, remove write-protection; if required, check or replace USB flash drive; *)
    740
    Initialization error – error in USB flash drive file system
    Check USB flash drive; reformat it on a PC to FAT12, FAT16 or FAT32
    741
    Error when recording logging data
    743
    Error occurred during the update
    Repeat update process, check USB flash drive; *)
    745
    Update file defective
    Download update file again; check or replace USB flash drive; *)
    746
    Restart update after waiting 2 minutes; *)
    751
    Time lost
    Reset the time and date on the inverter; *)
    752
    Real Time Clock module communication error
    753
    Internal error: Real Time Clock module is in emergency mode
    inaccurate time, time loss possible (grid power feed operation normal)
    754–755
    757
    Hardware error in the Real Time Clock module
    Error message on the display; the inverter does not feed current into the grid
    758
    760
    Internal hardware error
    Error message on display
    761–765
    766
    Emergency power limiter has been activated (max. 750 W)
    767
    768
    Power limit different in the hardware modules
    772
    Memory unit unavailable
    773
    Software update group 0 (invalid country setup)
    775
    PMC power stage set unavailable
    Press the ‘"Enter" key to confirm the error; *)
    776
    Invalid device type
    781–794
    Class 10–12 Status Codes
    1000–1299 – Gives information regarding the internal processor program status
    Description
    This is of no concern if the inverter is functioning without problems and it appears only in the "PS Status" setup parameter. In the event of an actual fault, this status code supports Fronius Technical Support in the failure analysis.
    Customer service
    IMPORTANT! Please contact your Fronius dealer or a Fronius-trained service technician if:
    • An error appears frequently or for a long period of time
    • An error appears that is not listed in the tables
    Operation in dusty environments
    When operating the inverter in extremely dusty environments:
    when necessary, clean the cooling elements and fan on the back of the inverter and the supply air openings in the mounting bracket using clean compressed air.
    Technical data
    General data and protection devices 10.0-3 208-240 / 24.0-3 208-240
    General data
    Cooling
    Controlled forced-air ventilation
    Protection class
    NEMA 4X
    Dimensions h x w x d
    28.5 x 20.1 x 8.9 in.
    725 x 510 x 225 mm
    Permitted ambient temperature
    -40 °F to +140 °F (-40 °C to +60 °C)
    Permitted storage temperature
    -40 °F to +158 °F (-40 °C to +70 °C)
    Permissible humidity
    0 - 100%
    Noise emission
    65 dB(A) (ref. 1pW)
    Protection devices
    Reverse polarity protection
    Integrated
    Stand-alone operation protection
    Integrated
    Arc Fault Circuit Interrupter/interruption
    Integrated
    Photovoltaic insulation monitoring
    Integrated
    High temperature
    Operating point shift/active cooling
    1. Technical data
    General data
    Cooling
    Protection class
    NEMA 4X
    725 x 510 x 225 mm
    0 - 100%
    Noise emission
    65 dB(A) (ref. 1pW)
    Protection devices
    Integrated
    Integrated
    Integrated
    Integrated
    High temperature
    1. Technical data
    Technical data Fronius Symo Advanced 10.0-3 208-240 / 12.0-3 208-240
    10.0-3 208-240
    12.0-3 208-240
    Input data
    MPP voltage range
    300 - 500 V DC
    Input voltage range (at 1000 W/m²/14 °F in an open circuit)
    200 - 600 V DC
    Max. input current (MPP1/MPP2)
    (MPP1 + MPP2)
    25.0/16.5 A
    41.5 A
    Max. short circuit current of solar modules (ISC PV) (MPP1/MPP2)
    37.5 / 24.8 A
    Max. inverter backfeed current to the array 1)
    0.0 A 2)
    Output data
    Nominal output power (Pnom)
    9995 W
    11,995 W
    Max. output power (+104 °F)
    9995 W
    11,995 W
    Max. output power (+140 °F)
    at 208 V
    8000 W
    8000 W
    at 220 V
    8600 W
    8600 W
    at 240 V
    8600 W
    8600 W
    Rated apparent power
    9995 VA
    11,995 VA
    Phases
    3 ~ NPE
    Nominal grid voltage
    at 208 V
    120/208 V
    at 220 V
    127/220 V
    at 240 V
    120/240 V
    Operating range AC voltage
    -12 to +10%
    Adjustment range for grid voltage
    60 - 152 V/104 - 288 V
    Max. continuous output current at Vnom
    at 208 V
    27.7 A
    33.3 A
    at 220 V
    26.2 A
    31.5 A
    at 240 V
    24.0 A
    28.9 A
    Recommended min. AC overcurrent protection
    at 208 V
    35.0 A
    45.0 A
    at 220 V
    35.0 A
    40.0 A
    at 240 V
    30.0 A
    40.0 A
    Max. output fault current per duration
    43.1 A / 158.4 ms
    Nominal frequency
    50/60 Hz
    Total harmonic distortion
    < 1.5%
    < 1.75%
    Power factor (cos phi)
    0 - 1 ind./cap.3)
    General data
    Maximum efficiency
    97.00%
    CEC efficiency
    at 208 V
    96.50%
    96.50%
    at 240 V
    96.50%
    96.50%
    Weight (full/lite version)
    90.4/89.5 lbs. (41.0/40.6 kg)
    1)
    The maximum current from the inverter to the solar modules if an error occurs on the inverter.
    2)
    Assured by the electrical design of the inverter
    3)
    ind. = inductive cap. = capacitive
    1. Technical data
    Technical data Symo Advanced 15.0-3 480
    15.0-3 480
    Input data
    MPP voltage range
    350 - 800 V DC
    200 - 1000 V DC
    (MPP1 + MPP2)
    33.0/25.0 A
    51 A
    49.5/37.5 A
    0.0 A 2)
    Output data
    14,995 W
    14,995 W
    at 440 V
    12,200 W
    at 480 V
    14,400 W
    14,995 VA
    Phases
    3 ~ NPE
    at 440 V
    254 V / 440 V
    at 480 V
    277 V / 480 V
    -12 to +10%
    127–322 V/220–558 V
    at 440 V
    19.7 A
    at 480 V
    18.0 A
    at 440 V
    25.0 A
    at 480 V
    25.0 A
    30.9 A / 150.4 ms
    Nominal frequency
    50/60 Hz
    < 1.5%
    0 - 1 ind./cap.3)
    General data
    Maximum efficiency
    98.00%
    CEC efficiency
    at 480 V
    97.00%
    95.7/95.0 lbs. (43.4/43.1 kg)
    1)
    2)
    3)
    1. Technical data
    Technical data Fronius Symo Advanced 20.0-3 208-240 - 22.7-3 208-240
    20.0-3 480
    22.7-3 480
    Input data
    MPP voltage range
    450 - 800 V DC
    500 - 800 V DC
    200 - 1000 V DC
    (MPP1 + MPP2)
    33.0/25.0 A
    51 A
    49.5/37.5 A
    0.0 A 2)
    Output data
    19,995 W
    22,727 W
    19,995 W
    22,727 W
    at 440 V
    12,200 W
    12,200 W
    at 480 V
    14,400 W
    14,400 W
    19,995 VA
    22,727 VA
    Phases
    3 ~ NPE
    at 440 V
    254 V / 440 V
    at 480 V
    277 V / 480 V
    -12 to +10%
    127–322 V/220–558 V
    at 440 V
    26.2 A
    29.8 A
    at 480 V
    24.0 A
    27.3 A
    at 440 V
    35.0 A
    40.0 A
    at 480 V
    30.0 A
    35.0 A
    30.9 A / 150.4 ms
    Nominal frequency
    50/60 Hz
    < 1%
    < 1.25%
    0 - 1 ind./cap.3)
    General data
    Maximum efficiency
    98.00%
    CEC efficiency
    at 480 V
    97.50%
    97.50%
    1)
    2)
    3)
    1. Technical data
    Technical data Fronius Symo Advanced 24.0-3 208-240
    24.0-3 480
    Input data
    MPP voltage range
    500 - 800 V DC
    200 - 1000 V DC
    (MPP1 + MPP2)
    33.0/25.0 A
    51 A
    49.5/37.5 A
    0.0 A 2)
    Output data
    23,995 W
    23,995 W
    at 480 V
    14,400 W
    23,995 VA
    Phases
    3 ~ NPE
    at 480 V
    277 V / 480 V
    -12 to +10%
    127–322 V/220–558 V
    at 480 V
    28.9 A
    at 480 V
    40 A
    30.9 A / 150.4 ms
    Nominal frequency
    50/60 Hz
    < 1%
    0 - 1 ind./cap.3)
    General data
    Maximum efficiency
    98.00%
    CEC efficiency
    at 480 V
    97.50%
    1)
    2)
    3)
    1. Technical data
    Relevant standards and directives
    Circuit for Preventing Stand Alone Operation
    The inverter has a permissible circuit for preventing stand alone operation.
    Grid Failure
    The standard measurement and safety procedures integrated into the inverter ensure that the power feed is immediately interrupted in the event of a grid failure (shut-off by the utility or damage to lines).
    1. Technical data
    RCMU
    RCMU = Residual Current Monitoring Unit
    The inverter is equipped with an RCMU according to Austrian standard ÖVE/ÖNORM E 8001-4-712.
    It monitors residual currents from the solar module to the inverter grid connection and disconnects the inverter from the grid when an improper residual current is detected.
    Additional residual current protection may be needed depending on the installation's protection system or the requirements of the utility company. In this case, use a type B residual current circuit breaker with a release current of at least 100 mA.
    Terms and conditions of warranty and disposal
    Fronius manufacturer's warranty
    Detailed warranty conditions specific to your country can be found at www.fronius.com/solar/garantie .
    To secure the full warranty period for the newly installed Fronius product, it is necessary to register at www.solarweb.com .
    1. Terms and conditions of warranty and disposal
    Disposal
    Waste electrical and electronic equipment must be collected separately and recycled in an environmentally sound manner in accordance with the European Directive and national law. Used equipment must be returned to the distributor or through a local authorized collection and disposal system. Proper disposal of the used device promotes sustainable recycling of material resources. A failure to observe this may lead to potential health/environmental impacts