Indicates an immediate danger.
Indicates a possibly dangerous situation.
Indicates the possibility of flawed results and damage to the equipment.
The Operating Instructions must always be kept on hand wherever the device is being used. In addition to the Operating Instructions, all applicable local rules and regulations regarding accident prevention and environmental protection must also be followed.
All safety and danger notices on the deviceThe terminals can reach high temperatures.
Only operate the device when all protection devices are fully functional. If the protection devices are not fully functional, there is a risk ofAny safety devices that are not functioning properly must be repaired by an authorized specialist before the device is switched on.
For the location of the safety and danger notices on the device, refer to the section headed “General” in the Operating Instructions for the device.
Any equipment malfunctions which might impair safety must be remedied immediately before the device is turned on.
The servicing information contained in these Operating Instructions is intended only for the use of qualified service engineers. An electric shock can be fatal. Do not carry out any actions other than those described in the documentation. This also applies to qualified personnel.
All cables and leads must be secured, undamaged, insulated, and adequately dimensioned. Loose connections, scorched, damaged, or under-dimensioned cables and leads must be repaired immediately by an authorized specialist.
Maintenance and repair work must only be carried out by an authorized specialist.
It is impossible to guarantee that externally (aka, third-party) procured parts are designed and manufactured to meet the demands made on them, or that they satisfy safety requirements. Use only original spare parts (also applies to standard parts).
Components that are not in perfect condition must be changed immediately.
The inverter generates a maximum sound power level of < 65 dB(A) (ref. 1 pW) when operating under full load in accordance with IEC 62109-1:2010.
The device is cooled as quietly as possible with the aid of an electronic temperature control system, and depends on the amount of converted power, the ambient temperature, the level of soiling of the device, etc.
It is not possible to provide a workplace-related emission value for this device, because the actual sound pressure level is heavily influenced by the installation situation, the power quality, the surrounding walls and the properties of the room in general.
In certain cases, even though a device complies with the standard limit values for emissions, it may affect the application area for which it was designed (e.g., when there is sensitive equipment at the same location, or if the site where the device is installed is close to either radio or television receivers). If this is the case, then the operator is obliged to take appropriate action to rectify the situation.
The user is responsible for backing up any changes made to the factory settings. The manufacturer accepts no liability for any deleted personal settings.
Copyright of these Operating Instructions remains with the manufacturer.
Text and illustrations were accurate at the time of printing. Fronius reserves the right to make changes. The contents of the Operating Instructions shall not provide the basis for any claims whatsoever on the part of the purchaser. If you have any suggestions for improvement, or can point out any mistakes that you have found in the Operating Instructions, we will be most grateful for your comments.
Device construction:
| (1) | Housing cover |
| (2) | Inverter |
| (3) | Wall bracket |
| (4) | Connection area incl. DC main switch |
| (5) | Data communication area |
| (6) | Data communication cover |
The inverter transforms the direct current generated by the solar modules into alternating AC current. This alternating current is fed into your home system or into the public grid and synchronized with the voltage that is used there.
The inverter has been designed exclusively for use in grid-connected photovoltaic systems. It cannot generate electric power independently of the grid.
The design and function of the inverter provide a maximum level of safety during both installation and operation.
The inverter automatically monitors the public grid. Whenever conditions in the electric grid are inconsistent with standard conditions (for example, grid switch-off, interruption), the inverter will immediately stop operating and interrupt the supply of power into the grid.
Grid monitoring is carried out using voltage monitoring, frequency monitoring and monitoring islanding conditions.
The inverter is fully automatic. Starting at sunrise, as soon as the solar modules generate enough energy, the inverter starts monitoring grid voltage and frequency. As soon as there is a sufficient level of irradiance, the solar inverter starts feeding energy into the grid.
The inverter ensures that the maximum possible power output is drawn from the solar modules at all times.
As there is no longer sufficient energy available to feed power into the grid, the inverter shuts down the grid connection completely and stops operating. All settings and recorded data are saved.
If the inverter temperature exceeds a certain value, the inverter derates automatically the actual output power for self protection.
The cause for a to high inverter temperature can be found in a high ambient temperature or an inadequate heat transfer away (eg for installation in control cabinets without proper heat dissipation).
| (2) | Inverter |
The manufacturer is not responsible for any damage resulting from improper use.
All warranty claims are considered void in such cases.
When configuring the photovoltaic system, make sure that all components are operating completely within their permitted operating range.
All measures recommended by the solar module manufacturer for maintaining solar module properties must be followed.
Follow all grid operator regulations regarding grid power feed and connection methods.
The inverter is equipped with ‘Field adjustable trip points’ and ‘Advanced Grid Features’. For further information, please contact ‘Fronius Technical Support’ at the following email address: pv-support-usa@fronius.com.
FCC
This device corresponds to the limit values for a digital device of class B in accordance with Part 15 of the FCC regulations. The limit values should provide adequate protection against harmful interference in homes. This device creates and uses high frequency energy and can interfere with radio communications when not used in accordance with the instructions. However, there is no guarantee against interference occurring in a particular installation.
If this device interferes with radio or television reception when turning the device on and off, it is recommended that the user solve this with one or more of the following measures:
Industry Canada RSS
The device corresponds to the license-free Industry Canada RSS standards. Operation is subject to the following conditions:
(1) The device may not cause harmful interference
(2) The device must accept any interference received, including interference that may cause undesired operation.
The inverter is fitted with the following safety functions as required by UL 1741 and the National Electrical Code:
Ground fault detector / interrupter (GFDI)
In photovoltaic systems with negatively grounded solar modules, the negative cable from the solar module is connected to the grounding system in the inverter. If a ground fault occurs in the DC wiring, the inverter disconnects from the grid.
Insulation monitoring
In photovoltaic systems with ungrounded solar modules, the inverter checks the resistance between the photovoltaic system's positive or negative pole and the ground potential. In the case of a short circuit between the DC+ or DC- cable and the ground (e.g., due to poorly insulated DC cables or faulty solar modules) the inverter disconnects from the grid.
The inverter is equipped with integrated arc detection/interruption, which detects and extinguishes serial arcs.
For example, a serial arc can occur after the following errors or situations:
If a serial arc is detected, the power is switched off and the grid power feed operation is interrupted. A state code is shown on the display. The state code on the display must be manually reset before the grid power feed operation can be resumed.
The power shutdown also extinguishes the serial arc.
This product is equipped with a communication interface in line with the "Communication Signal for Rapid Shutdown - SunSpec Interoperability Specification”.
Power optimizers and other MLPE features in the photovoltaic system can impair the correct functioning of the arc detection/interruption. When using these kinds of components, the system installer is responsible for ensuring the correct functioning of the arc detection/interruption. Contact your Fronius Technical Support for more information.
There are warning notices and safety symbols on the inside and outside of the inverter. These warning notices and safety symbols must not be removed or painted over. They warn against incorrect operation, as this may result in serious injury and property damage.
| Safety symbols: | ||
| Danger of serious injury and property damage due to incorrect operation | ||
| Do not use the functions described here until you have fully read and understood the following documents:
| Dangerous electrical voltage | ||
| Wait for the capacitors to discharge. | ||
Text of the warning notices:
WARNING!
Danger of electric shock
Do not remove the cover. The device does not contain any user-serviceable parts. Maintenance work must be carried out by a trained service technician.
Both AC and DC voltage sources terminate inside this device. Each circuit must be turned off before carrying out maintenance work.
If the solar module is exposed to light, it will supply a DC voltage to the device.
Risk of electric shock due to energy stored in capacitors. Do not remove the cover until all power supply sources have been switched off for at least 3 minutes.
Grounded system: Normally grounded conductors can become ungrounded and live due to a ground fault.
Ungrounded system: The DC cables in this PV system are not grounded and can be live.
Fronius developed Solar Net to make these system add-ons flexible and capable of being used in a wide variety of different applications. Fronius Solar Net is a data network that enables several inverters to be linked to the system add-ons. | |
Fronius Solar Net is a bus system with ring topology. Just one suitable cable is enough for communication between one or more inverters connected to Fronius Solar Net and a system add-on. | |
In order to clearly define each inverter in Fronius Solar Net, each inverter must also be assigned an individual number. | |
Different system add-ons are automatically recognized by Fronius Solar Net. | |
In order to distinguish between several identical system add-ons, each one must be assigned a unique number. | |
More detailed information on the individual system add-ons can be found in the relevant operating instructions or on the internet at http://www.fronius.com | |
More detailed information on cabling Fronius DATCOM components can be found at: | |
→ http://www.fronius.com/QR-link/4204101938 | |
Information on installing option cards (e.g.: Datamanager) in the inverters and for connecting data communication cables can be found in the installation instructions.
The inverter is equipped with the Wi-Fi enabled system monitoring of the Fronius Data Manager 2.0.
The monitoring system includes the following functions:
Further information about the Fronius Data Manager 2.0 can be found online in the Fronius Data Manager 2.0 operating instructions.
The Fronius Solar.start App makes starting Fronius Datamanager 2.0 for the first time significantly easier. The Fronius Solar.start App is available from the relevant app store.
IMPORTANT! To establish a connection to Fronius Datamanager 2.0, the end device in question (e.g., laptop, tablet) must be configured as follows:
The inverter/Fronius Datamanager Box 2.0 establishes the WLAN access point. The WLAN access point stays open for one hour.
The start page of the Setup wizard appears.
The Technician Wizard is designed for the installer and includes standard-specific settings. Running the Technician Wizard is optional.
If the Technician Wizard is run, it is essential to note down the assigned service password. This service password is required to configure the UC Editor and Meter menu items.
If the Technician Wizard is not run, no specifications for power reduction are set.
The Solar Web Wizard must be run.
The Fronius Solar.web start page appears.
or
The Fronius Datamanager 2.0 website opens.
More detailed information on Fronius Datamanager 2.0 and other start-up options can be found at: | |
→ http://www.fronius.com/QR-link/4204260191EA | |
Item | Description |
(1) | Display |
Control and status LEDs | |
(2) | General status LED (red)
(3) | Status LED (orange)
(4) | Operating LED (green)
Function keys - each has a different function depending on the selection: | |
(5) | "Left/Up" key |
(6) | "Down/Right" key |
(7) | "Menu/Esc" key |
(8) | "Enter" key |
The keys are capacitive by design and wetting them with water may impair their function. For optimal function, wipe the keys with a dry cloth if necessary.
(1) | Display |
(8) | "Enter" key |
Power for the display comes from the AC grid voltage. The display can be available all day long depending on the setting in the Setup menu.
IMPORTANT! The inverter display is not a calibrated measuring instrument.
Slight deviation from the utility company meter is intrinsic to the system. A calibrated meter is required to make calculations for the utility company.
| (*) | Scroll bars |
| (**) | The Energy Manager symbol is displayed, if the Energy Manager function has been activated |
| (***) | WR no. = InverterDATCOM number, Store icon – appears briefly when set values are stored, USB connection – appears if a USB flash drive has been inserted |
If no key is pressed for 2 minutes, the display illumination turns off automatically and the inverter switches to the ‘NOW’ display mode (if the display illumination is set to AUTO).
The inverter can automatically be switched to the ‘NOW’ display mode from any menu level, unless the inverter was manually switched to standby mode.
The current power feed-in is displayed after automatically switching to the ’NOW’ menu item.
1Press the "Menu" |
The display switches to the menu level. | |
2Use the "left" or "right" key | |
3Access the desired menu item by pressing the "Enter" |
NOW | |
LOG | |
GRAPH Press the "Back" key to close the display |
NOW | |
LOG | |
Data displayed in menu item NOW:
AC Output Power (W) |
AC Reactive Power (VAr) |
AC Voltage (V) |
AC Output Current (A) |
AC Frequency (Hz) |
PV Array Voltage (V) |
PV Array Current (A) |
Time / Date |
Data displayed in menu item LOG:
(for the current day, the current calendar year, and since using the inverter for the first time)
AC Energy Yield (kWh / MWh) Due to the variety of different monitoring systems, there can be deviations between the readings of other metering instruments and the readings from the inverter. For determining the energy supplied to the grid, only the readings of the calibrated meter supplied by the electric utility company are relevant. |
AC Maximum output power (W) |
Earnings As was the case for the output energy, readings may differ from those of other instruments. "The Setup Menu" section describes how to set the currency and rate for the energy supplied. |
CO2 savings (g / kg) The value for CO2 savings depends on the power station facilities and corresponds to the CO2 emissions that would be released when generating the same amount of energy. The factory setting is 0.53 kg / kWh (source: DGS – Deutsche Gesellschaft für Sonnenenergie e.V. (German Society for Solar Energy). |
AC Max. Voltage L-N (V) |
PV Array Max. Voltage (V) |
Operating Hours IMPORTANT! The time must be set correctly for day and year values to be displayed properly. |
After completing the entire start-up process (for example, using the Installation Wizard), the inverter is preconfigured depending on the country setup.
The SETUP menu lets you easily customize the inverter’s preset parameters to your needs.
| SETUP |
Because of software updates, certain functions may be available for your device but not described in these Operating Instructions or vice versa.
In addition, individual figures may also differ slightly from the operating elements of your device. These operating elements function in exactly the same way, however.
Accessing the SETUP menu | |
"SETUP" mode selected at the menu level | 1In the menu level, use the "left" or "right" keys |
2Press the "Enter" | |
"Standby" entry | The first entry in the SETUP menu is displayed: |
Scrolling between entries | |
Example: "WiFi Access Point" menu item | 3Use the "up" or "down" keys |
Exiting an entry | |
4To exit an entry, press the "Back" The menu level is displayed | |
The available settings are displayed: |
| The first digit of a value to be set flashes: |
4Use the ‘Up’ and ‘Down’ keys to select the desired setting 5Press the ‘Enter’ key to save and apply the selection. Press the ‘Esc’ key to exit without saving. | 4Use the "Up" and "Down" keys to select a value for the first digit 5Press the "Enter" key The second digit of the value flashes. 6Repeat steps 4 and 5 until... the entire value flashes. | |
| 7Press the "Enter" key 8Repeat steps 4 - 6 for units or other values to be set until the unit or value flashes. 9Press the ‘Enter’ key to save and apply the changes. Press the ‘Esc’ key to exit without saving. | |
The currently selected entry is displayed. |
1Select the ‘Energy yield’ setup menu entry | |
2Press the ‘Enter’ key | |
The overview of adjustable values is displayed. | |
3Use the ‘up’ or ‘down’ keys | |
4Press the ‘Enter’ key | |
The feed-in tariff is displayed | |
5Use the ‘plus’ or ‘minus’ keys | |
6Press the ‘Enter’ key | |
The units position flashes. | |
7Repeat steps 5 and 6 for the units position and the 3 decimal places until ... | |
The set feed-in tariff flashes. | |
8Press the ‘Enter’ key | |
The feed-in tariff is applied and the overview of adjustable values is displayed. | |
9Press the ‘Esc’ | |
The ‘Energy yield’ setup menu entry is displayed. | |
Manual activation/deactivation of the standby mode
The display alternates between ‘STANDBY’ and ‘ENTER.’
The Standby mode is now activated.
The Startup LED lights up orange.
The ‘Standby’ entry is displayed.
The inverter also switches to the Startup phase.
After the grid power feed operation is restored, the Operation Status LED lights up green.
To activate/deactivate the WLAN Access Point. For example, this is required to set up or adjust the system monitoring using the Datamanager web interface. If no Datamanager is detected by the inverter, [not available] is displayed
Setting range | WLAN Access Point |
| Activate WLAN AP? To activate the WLAN Access Point |
| WLAN Access Point The SS-ID (SS) and the password (PW) are displayed. |
| Deactiv. WLAN AP? To deactivate the WLAN Access Point |
| WLAN Access Point Is displayed if no system monitoring is available on the inverter. |
Check the data communication, entry of the inverter number, protocol settings
Setting range | Status/inverter number/protocol type |
Status | |
Inverter Number | |
Setting range | 00 - 99 (00 = inverter address 100) |
Factory setting | 01 |
IMPORTANT! Each inverter must be assigned its own address when using multiple inverters in a data communications system. | |
Protocol Type | |
Setting range | Fronius Solar Net / Interface * |
Factory setting | Fronius Solar Net |
* The interface protocol type only functions without a Fronius Datamanager card. Existing Fronius Datamanager cards must be removed from the inverter. | |
Value settings when using a USB stick
Setting range | Safely remove hardware / software update / logging interval |
IMPORTANT! The time must be set correctly in order for the logging function to work properly.
Software update |
Procedure: 1Download the "froxxxxx.upd" update file (e.g., at http://www.fronius-usa.com; xxxxx stands for the respective version number) |
IMPORTANT! To ensure problem-free updates of inverter software, the USB stick should have no hidden partitions and no encryption (see section "Suitable USB Sticks). |
2Save the update file to the highest data level of the USB stick 3Open the data communication area 4Insert the USB stick with the update file into the USB socket in the data communication area 5In the Setup menu, select the menu item "USB" and then "Update Software" 6Press the "Enter" key 7Wait until a comparison of the current software version on the inverter and the new software version is displayed:
8Press the "Enter" key after every page |
The inverter begins copying the data. |
After the copying is complete the inverter updates the required electronic assemblies one after the other. |
The inverter updates the display in the last step. |
When the software update is complete, the inverter switches to the startup phase and then to grid power feed operation. The USB stick can be removed.. |
Individual settings in the Setup menu are retained when the inverter software is updated. |
Logging Interval |
Unit | Minutes |
Setting range | 30 Min. / 20 Min. / 15 Min. / 10 Min. / 5 Min. / No Log |
Factory setting | 30 Min. |
30 Min. | The logging interval is 30 minutes; new logging data are saved to the USB stick every 30 minutes. |
20 Min. | |
15 Min. | |
10 Min. | |
5 Min. | The logging interval is 5 minutes; new logging data are saved to the USB stick every 5 minutes. |
No Log | No data are saved |
IMPORTANT! The time must be set correctly in order for the logging function to work properly. | |
A floating switch contact (relay) on the inverter can be used to display status codes, the inverter status (e.g. the grid power feed operation) or the Energy Manager functions.
Setting range | Relay Mode / Relay Test / Switch-on Point* / Switch-off Point* |
* is only shown if the “E-Manager” function has been activated under “Relay Mode.”
Relay Mode
Setting range | ALL / Permanent / GAF / OFF / ON / E-manager |
Factory setting | ALL |
Alarm function: | ||
ALL / Permanent: | Switches the floating switch contact for continual and temporary service codes (e.g. brief interruption of grid power feed operation, a service code occurs a certain number of times per day – can be set in the “BASIC” menu) | |
GAF | As soon as “GAF” mode is selected, the relay will be switched on. As soon as the power module reports an error and switches from regular grid power feed operation to an error state, the relay is opened. This way, the relay can be used for fail safe functions. Application example | |
Active output: | ||
ON: | The floating NO switch contact is constantly switched on while the inverter is operating (as long as the display lights up or displays). | |
OFF: | The floating NO switch contact is switched off. | |
Energy Manager: | ||
E-Manager: | You can find additional information on the “Energy Manager” function in the following “Energy Manager” section. | |
Relay test | ||
Switch-on point (only if the “Energy Manager” function is activated) | ||
Factory setting | 1000 W |
Setting range | set switch-off point up to the inverter’s nominal output (W or kW) |
Switch-off point (only if the “Energy Manager” function is activated) | |
Factory setting | 500 |
Setting range | 0 up to the inverter’s set switch-on point (W or kW) |
Setting the time, date, display format, and automatic adjustment for daylight saving time
Setting range | Set time / Set date / Time display format / Date display format / Daylight saving time |
Set time | |
Set date | |
Time display format | |
Setting range | 12hrs/24hrs |
Factory setting | depends on the country setup |
Date display format | |
Setting range | mm/dd/yyyy or dd.mm.yy |
Daylight saving time | |
IMPORTANT! Only use the automatic daylight savings changeover function when there are no LAN or WLAN-compatible system components in a Fronius Solar Net ring (e.g. Fronius Datalogger Web, Fronius Datamanager or Fronius Hybridmanager). | |
Setting range | on/off |
Factory setting | on |
IMPORTANT! The time and date must be set correctly for day and year values to be displayed properly. | |
Setting range | Language / Night Mode / Contrast / Illumination |
Language | |
Setting range | English, German, French, Spanish, Italian, Dutch, Czech, Slovakian, Hungarian, Polish, Turkish, Portuguese, Romanian |
Night mode | |
Setting range | AUTO / ON / OFF |
Factory setting | OFF |
AUTO: | The Fronius DATCOM operation is maintained as long as a Fronius Datamanager is connected to an active, uninterrupted Fronius Solar Net. | |
ON: | The Fronius DATCOM operation is always maintained. The inverter provides an uninterrupted 12 V DC voltage to supply Fronius Solar Net with power. The display is always active. IMPORTANT! When the Fronius DATCOM night mode is ON or on AUTO with connected Fronius Solar Net components, the power consumption of the inverter at night increases to around 7 W. | |
OFF: | No Fronius DATCOM operation at night, the inverter therefore does not require any power to supply electricity to the Fronius Solar Net at night. | |
Contrast | ||
Setting range | 0 - 10 |
Factory setting | 5 |
Since contrast depends on temperature, it may be necessary to adjust the ‘Contrast’ menu item when environmental conditions change. | |
Illumination | |
The ‘Illumination’ menu item only applies to the inverter display background illumination. | |
Factory setting | AUTO |
AUTO: | The inverter display illumination is activated by pressing any key. If no key is pressed for 2 minutes, the display backlight goes out. | |
ON: | The inverter display illumination is permanently on when the inverter is active. | |
OFF: | The inverter display illumination is permanently off. |
Setting range | Currency / Feed-in tariff |
Meter deviation/calibration | |
Currency | |
Setting range | 3-digit, A-Z |
Feed-in tariff | |
Setting range | 2-digit, 3 decimal places |
Factory setting | (depends on the country setup) |
CO2 factor | |
For testing the fan functionality
Setting range | Test fan #1/test fan #2 (depending on the device) |
IMPORTANT! The inverter display does not indicate whether the fan is OK. The fan function can only be checked by listening and feeling.
for checking arc detection/interruption
Setting range | ArcDetector Status/Start Self-test |
Arc.det. Status | |
Start Self-test Test procedure: 1Select "Arc Detection" in the Setup menu 2Press the "Enter" key 3Use the up and down keys to select "Start Self-test" 4Press the "Enter" key The self-test starts. The arc detection/interruption function simulates an arc and sends the corresponding signal to the inverter. The message "Self-test completed and Start AFCI" is shown on the display. 5Confirm the indication by pressing the "Enter" key | |
INFO |
INFO |
Measured values | Display range: | PV Ins. / Fan #1 / U PV1 |
| PV Ins. Fan #1 U PV1 | |
LT status | The status display of the last error that occurred in the inverter can be shown. IMPORTANT! Status codes 306 (Power low) and 307 (DC low) appear naturally every morning and evening due to low solar irradiance. These status codes are not the result of a fault.
Grid status | The last 5 grid errors that occurred can be displayed:
The device is used to display settings relevant to a power supply company. The displayed values depend on the respective country setup or device-specific inverter settings.
Display range | General / Country Setup / MPP Tracker / AC Monitoring / AC Voltage Limits / AC Frequency limits / Q-Mode / AC Power Limits / AC Voltage Derating / Fault Ride Through |
General: | Device type |
Country Setup: | Setup Version Group |
MPP Tracker: | Tracker 1 |
AC Monitoring: | GMTi GMTr ULL LLTrip |
AC Voltage Limits: | UILmax UILmin |
AC Frequency Limits: | FILmaw FILmin |
Q-Mode: | Current power factor cos phi |
AC Power limits: | Max. P AC |
AC Voltage Derating: | Status GVDPRe GVDPRv Message |
Fault Ride Through: | Status – default setting: OFF DB min – default setting: 90% DB max – default setting: 120% k-Fac. default setting: 0 |
Display of version number and serial number of the PC boards installed in the inverter (e.g., for service purposes)
Display range | Display/Display Software/Integrity Checksum/Memory Card/Memory Card #1/Power Stage/Power Stage Software/EMI Filter/Power Stage #3/Power Stage #4 |
The inverter comes equipped with a ‘Key lock’ function.
When the ‘Keylock’ function is active, the Setup menu cannot be accessed, e.g., to protect against setup data being changed by accident.
You must enter code 12321 to activate / deactivate the ‘Key lock’ function.
1Press the ‘Menu’ key | |
The menu level is displayed. 2Press the unassigned ‘Menu/Esc’ key 5 times |
In the ‘CODE’ menu, the ‘Access Code’ is displayed and the first digit flashes. | |
3Enter code 12321: Use the ‘plus’ or ‘minus’ keys | |
The second digit flashes. | |
5Repeat steps 3 and 4 for the second, third, fourth, and fifth digit in the code until... the set code flashes. 6Press the ‘Enter’ key |
In the ‘LOCK’ menu, the ‘Key lock‘ function is displayed. | |
7Use the ‘plus’ or ‘minus’ keys ON = the key lock function is activated (the SETUP menu item cannot be accessed) OFF = the key lock function is deactivated (the SETUP menu item can be accessed) | |
A USB stick connected to the USB A socket can act as a data logger for an inverter.
Logging data saved to the USB stick can at any timeOlder versions (up to Excel 2007) have a row limit of 65536.
Further information on "Data on a USB stick", "Data volume and storage capacity" as well as "Buffer memory" can be found at: | |
® http://www.fronius.com/QR-link/4204260171EN | |
Due to the number of USB thumb drives on the market, we cannot guarantee that every USB thumb drive will be recognized by the inverter.
Fronius recommends using only certified, industrial USB thumb drives (look for the USB-IF logo).
The inverter supports USB thumb drives using the following file systems:
Fronius recommends that the USB thumb drive only be used for recording logging data or for updating the inverter software. USB thumb drives should not contain any other data.
USB symbol on the inverter display, e.g., in the 'NOW' display mode:
When the inverter recognizes a USB thumb drive, the USB symbol will appear at the top right of the display.
When inserting the USB thumb drive, make sure that the USB symbol is displayed (it may also be flashing).
Notice! Please be aware that in outdoor applications the USB thumb drive may only function in a limited temperature range.
Make sure, for example, that the USB thumb drive will also function at low temperatures for outdoor applications.
The USB stick can be used to help end customers update inverter software via the USB menu item in the SETUP menu item: the update file is first saved on the USB stick and then transferred to the inverter. The update file must be saved in the USB stick root directory.
Safety information for removing a USB stick | ||
| IMPORTANT! To prevent a loss of data, the connected USB stick should only be removed under the following conditions:
The following important parameters are set in the Basic menu for the installation and operation of the inverter:
1Press the "Menu" key | ||
| The menu level is displayed. 2Press the unassigned "Menu/Esc" key 5 times |
In the "CODE" menu, the "Access Code" is displayed and the first digit flashes. | ||
3Enter code 22742: Use the up and down keys to select a value for the first digit | ||
4Press the "Enter" key |
The second digit flashes. | ||
| 5Repeat steps 3 and 4 for the second, third, fourth, and fifth digit in the code until... the set code flashes. 6Press the "Enter" key |
| The Basic menu is displayed. | |
7Use the up and down keys to select the desired entry | ||
8Press the "Enter" key to edit the selected entry | ||
9Press "Esc" to exit the Basic menu |
The Basic menu contains the following items:
MPP Tracker 1
USB logbook |
SMS / Relay
Ground Settings
Insulation settings
TOTAL Reset To reset the values to zero, press the "Enter" key. |
Your inverter is equipped with system self diagnosis that automatically identifies a large number of possible operation issues by itself and displays them on the screen. This enables you to know immediately if there are any malfunctions in the inverter or the photovoltaic system or any installation or operating errors.
Whenever the system self diagnosis has identified a particular issue, the respective status code is shown on the screen.
IMPORTANT! Status codes may sometimes appear briefly as a result of the control response from the inverter. If it subsequently continues to operate normally, there has not been a system error.
Status codes in class 1 are typically temporary. Their cause lies in the grid.
Your inverter's first reaction is to disconnect from the grid. Thereafter, the grid will be checked for the duration of the observation period stipulated. If, after the end of this period, no further defect is identified, your inverter resumes grid power feed operation.
Code |
| Description |
| Details |
| Rectification |
102 |
| AC voltage too high |
| Grid conditions are being tested and as soon as they are back within the permissible range, the inverter will resume grid power feed operation. |
| Check grid connections. |
103 |
| AC voltage too low |
105 |
| AC frequency too high |
106 |
| AC frequency too low |
107 |
| AC grid outside of tolerances |
108 |
| Stand alone operation detected |
Code |
| Description |
| Details |
| Rectification |
212 |
| Overvoltage at L1-N |
| Check grid connections. If this status code keeps recurring, contact your system installer. |
213 |
| Undervoltage at L1-N |
222 |
| Overvoltage at L2-N |
223 |
| Undervoltage at L2-N |
240 |
| Arc detected |
| The status code is displayed for approx. 4 seconds. |
241 |
| Arc detected |
| The status code 241 is displayed directly after 240; the inverter disconnects from the grid for safety reasons. |
| If an arc has been detected, check the entire affected PV system for damage before resetting the inverter. |
242 |
| Arc detected |
| Status code 242 is displayed after resetting status code 241. |
| Reset the status code by pressing the "Enter" key. |
245 |
| Arc detector self test failed |
| The inverter disconnects from the grid. |
| Reset AC. |
247 |
| Arc detector current sensor defective |
| If status code persists: contact a Fronius-trained service technician. |
249 |
| Arc detector defective |
Class 3 includes status codes that may appear during grid power feed operation and do not cause permanent interruption of the grid power feed operation.
After automatic disconnection from the grid and waiting for its conditions to return to those stipulated, your inverter will try to resume grid power feed operation.
Code |
| Description |
| Details |
| Rectification |
301 |
| Brief interruption of grid power feed operation due to overcurrent in the inverter. |
| Error is automatically rectified; |
302 |
| Over-current (DC) |
303 |
| Power stage set over temperature |
| Brief interruption of grid power feed operation due to over temperature. |
| If required, clean cool air vents and cooling elements with compressed air. |
304 |
| Interior temperature too high |
306 |
| LOW PV POWER |
| Brief interruption of grid power feed operation. |
| The fault is rectified automatically. |
307 |
| LOW PV VOLTAGE |
IMPORTANT! Status codes 306 (LOW PV POWER) and 307 (LOW PV VOLTAGE) appear naturally every morning and evening due to low solar irradiance. These status codes are not the result of a fault. | ||||||
308 |
| Intermediate circuit overvoltage |
309 |
| DC input voltage too high |
Class 4 status codes may require the intervention of a trained Fronius service technician.
Code |
| Description |
| Details |
| Rectification |
401 |
| No internal communication with power stage set. |
| The inverter will automatically attempt to connect again and, if possible, resume grid power feed operation. |
406 |
| Power stage set temperature sensor defective |
407 |
| Internal temperature sensor defective |
408 |
| DC feed-in detected |
412 |
| The "fixed voltage" setting has been selected instead of MPP voltage operation and the voltage is set to a value that is too low or too high. |
415 |
| Safety cut-out has been triggered by option card or RECERBO |
| Inverter does not feed energy into the grid. |
416 |
| No communication between power stage set and control unit |
425 |
| Communication with the power stage set is not possible |
445 |
| Limit value setting not permitted |
| Inverter does not feed energy into the grid for safety reasons. |
| Update the inverter firmware. |
448 |
| Neutral conductor not connected |
| If this status code keeps recurring, contact your system installer. | |
452 |
| Communication problem between processors |
453 |
| Brief grid voltage error |
454 |
| Brief grid frequency error |
457 | Grid relay stuck | Inverter does not feed energy into the grid. | contact a Fronius-trained service technician. | |||
459 |
| Error receiving measuring signal for the insulation test |
460 |
| Reference power source for the digital signal processor (DSP) is operating outside of tolerances |
472 |
| Fuse for solar module ground is defective |
| Replace fuse for solar module ground. |
475 | Solar module ground, insulation error (connection between solar module and ground) | Inverter does not feed energy into the grid. | If this status code keeps recurring, contact your system installer. | |||
482 |
| Commissioning is not complete |
| Reset AC (switch automatic circuit breaker on and off), carry out full commissioning. |
Class 5 status codes generally do not impair grid power feed operation, but can lead to limitations in grid power feed operation. They will be displayed until the status code is acknowledged by pressing a key (the inverter, however, continues working normally in the background).
Code |
| Description |
| Details |
| Rectification |
502 |
| Insulation error on the solar modules |
| Warning message is shown on the display. |
509 |
| No feed-in within the last 24 hours |
| Acknowledge status code; |
517 |
| Power derating due to excessive temperature |
| If a power derating occurs, a warning message is shown on the display. |
551 |
558 |
| Function incompatibility (one or more PC boards in the inverter are not compatible with each other, e.g., after PC board replacement) |
| Possible error displays or malfunctions in the inverter. |
560 |
| Power derating due to over-frequency |
| The status code is displayed with excessive grid frequency. |
| As soon as the grid frequency returns to the permissible range and the inverter resumes normal operation, the error is rectified automatically. |
566 |
| Arc detector switched off |
| The status code is displayed every day until the arc detector is activated again. |
| No error! |
Class 7 status codes concern the inverter control unit, configuration and data recording, and can directly or indirectly affect grid power feed operation.
Code | Description | Behavior | Remedy |
705 | Conflict when setting the inverter number (e.g., number assigned twice) | - | Correct inverter number in the setup menu |
721 | EEPROM was reinitialized or EEPROM defective | Warning message is shown on the display | Acknowledge status code; |
731 | Initialization error – USB thumb drive is not supported | Warning message is shown on the display | Check or replace the USB thumb drive |
732 | Overcurrent at USB thumb drive | ||
733 | No USB thumb drive inserted | Warning message is shown on the display. | Insert or check the USB thumb drive. |
734 | Update file is not detected or is not available | Warning message is shown on the display | Check the update file (e.g., for the proper file name). |
735 | The update file does not match the device, the update file is too old | Warning message is shown on the display, update process is canceled | Check the update file. |
736 | Write or read error occurred | Warning message is shown on the display | Check the USB thumb drive and the files on the USB thumb drive or replace the USB thumb drive. |
738 | Log file could not be saved (e.g.: USB thumb drive is write-protected or full) | Warning message is shown on the display | Free up memory. Remove write-protection. If necessary, check or replace the USB thumb drive. |
743 | Error occurred during the update | Warning message is shown on the display | Repeat the update process. Check the USB thumb drive. |
745 | Update file defective | Warning message is shown on the display, update process is canceled | Download the update file again. |
751 | Time lost | Warning message is shown on the display | Reset the time and date on the inverter |
752 | Real Time Clock module communication error | ||
757 | Hardware error in the Real Time Clock module | Error message is shown on the display, the inverter does not feed current into the grid | If status code persists: Contact a Fronius-trained service technician |
758 | Internal error: Real Time Clock module is in emergency mode | Inaccurate time, time loss possible (grid power feed operation normal) | |
766 | Emergency power limiter has been activated (max. 750 W) | Error message is shown on the display |
When operating the inverter in extremely dusty environments:
when necessary, clean the cooling elements and fan on the back of the inverter and the supply air openings in the mounting bracket using clean compressed air.
Fronius Galvo |
| 1.5-1 208-240 | 2.0-1 208-240 | ||||||||||||
Input data | |||||||||||||||
Recommended PV system power | 1.2–1.95 kWp | 1.6–2.6 kWp | |||||||||||||
MPP voltage range |
| 120 - 335 V DC | |||||||||||||
Start-up input voltage |
| 140 V | |||||||||||||
Max. input voltage | 420 V DC 1) | ||||||||||||||
Nominal input voltage |
| 260 V | |||||||||||||
Nominal input current |
| 6.2 A | 8.3 A | ||||||||||||
Max. input current | 13.4 A | 17.9 A | |||||||||||||
Max. short circuit current of the solar modules | 20.1 A | 26.8 A | |||||||||||||
Max. continuous utility backfeed current 2) | 0.0 A 3) | ||||||||||||||
Max. continuous backfeed current from other MPPT or battery inputs | 0.0 A 4) | ||||||||||||||
Output data | |||||||||||||||
Nominal output power (Pnom) | at 208 V | 1500 W | 1900 W | ||||||||||||
Pnom at +122 °F (50 °C) | at 208 V | 1500 W | 1900 W | ||||||||||||
Max. output power |
| 1500 W | 2000 W | ||||||||||||
Rated apparent power |
| 1500 VA | 2000 VA | ||||||||||||
Nominal grid voltage |
| 208 V/220 V/240 V | |||||||||||||
Mains voltage tolerance |
| -12%/+10% | |||||||||||||
Operating AC voltage range | at 208 V | 183–229 V | |||||||||||||
Adjustment range for grid voltage | at 208 V | 104–288 V | |||||||||||||
Voltage trip limit accuracy |
| 1% of nominal value | |||||||||||||
Setting range for voltage limit violation tolerance time |
| 0.016–21.0 s 5) | |||||||||||||
Nominal output current | at 208 V | 7.2 A AC | 9.1 A AC | ||||||||||||
Phases |
| 2 | |||||||||||||
Synchronization in-rush current 3) |
| 36.0 A / 9.4 ms | |||||||||||||
Max. output fault current per duration | at 208 V | 248 A/1.2 ms | |||||||||||||
Nominal output frequency |
| 60 Hz | |||||||||||||
Operating frequency range |
| 45.0 - 65.0 Hz | |||||||||||||
Adjustment range for mains frequency |
Frequency trip limit accuracy |
| 0.05 Hz | |||||||||||||
Setting range for frequency limit violation tolerance time |
| 0.016 - 600 s 5) | |||||||||||||
Total harmonic distortion |
| < 4% | |||||||||||||
Power factor (cos phi) |
| 1 | |||||||||||||
General data | |||||||||||||||
Maximum efficiency |
| 95.8% | |||||||||||||
CEC efficiency | at 208 V | 94.0% | 94.5% | ||||||||||||
Self-consumption at night | at 208 V | 0.7 W | |||||||||||||
Self-consumption during operation |
| 8.0 W | |||||||||||||
Cooling |
| Forced-air ventilation | |||||||||||||
Protection class |
| NEMA4X | |||||||||||||
Dimensions h x w x d |
| 24.7 x 16.9 x 8.1 in. | |||||||||||||
Weight |
| 36.05 lbs. | |||||||||||||
Shipping dimensions l x h x w |
| 30.1 x 21.7 x 11.4 in. | |||||||||||||
Shipping weight |
| 43.10 lbs. | |||||||||||||
Permitted ambient temperature |
| -40 °F to +122 °F | |||||||||||||
Permitted storage temperature |
| -40 °F to +158 °F | |||||||||||||
Protection devices | |||||||||||||||
Ground fault monitoring |
| Internal GFDI | |||||||||||||
Stand-alone operation protection |
| Integrated | |||||||||||||
Reverse polarity protection |
Arc Fault Circuit Interrupter/interruption |
Overload performance |
| Operating point shift/active cooling | |||||||||||||
Fronius Galvo |
MPP voltage range |
Max. output power |
Phases |
| 2 | |||||||||||||
| 1 | |||||||||||||
Cooling |
Protection class |
Weight |
Shipping weight |
Fronius Galvo |
| 2.5-1 208-240 | 3.1-1 208-240 | ||||||||||||
Recommended PV system power | 2.0–3.25 kWp | 2.5–4.0 kWp | |||||||||||||
MPP voltage range |
| 165–440 V DC | |||||||||||||
| 185 V | |||||||||||||
Max. input voltage | 550 V DC 1) | ||||||||||||||
| 330 V | |||||||||||||
| 8.0 A | 10.0 A | ||||||||||||
Max. input current | 16.1 A | 20.0 A | |||||||||||||
Max. short circuit current of the solar modules | 24.1 A | 30.1 A | |||||||||||||
Nominal output power (Pnom) | at 208 V | 2500 W | 2930 W | ||||||||||||
Pnom at +122 °F (50 °C) | at 208 V | 2500 W | 2600 W | ||||||||||||
Max. output power |
| 2500 W | 3100 W | ||||||||||||
| 2500 VA | 3100 VA | ||||||||||||
Nominal output current | at 208 V | 12.0 A AC | 14.1 A AC | ||||||||||||
Phases |
| 2 | |||||||||||||
Maximum continuous utility backfeed current 3) |
| 0 A | |||||||||||||
Max. output fault current per duration | at 208 V | 456 A/1.9 ms | |||||||||||||
| 1 | |||||||||||||
| 96.0% | |||||||||||||
CEC efficiency | at 208 V | 95.0% | 95.0% | ||||||||||||
Cooling |
Protection class |
Weight |
Shipping weight |
High temperature |
* Only for AFCI and GFDI and insulation monitoring functions
Detailed warranty conditions specific to your country can be found online:
www.fronius.com/solar/garantie
To take advantage of the full warranty duration for your newly installed Fronius inverter or storage system, register your product at: www.solarweb.com.
Damages claims against Fronius are excluded unless they are based on gross negligence or willful intent on the part of Fronius.
The installer and the operator shall comply with the safety rules given by Fronius and regional applicable guidelines, standards, and regulations in connection with work on photovoltaic systems. The safety rules can be found in the operating instructions provided upon delivery. The installer as well as the operator are fully liable for damages and costs which arise due to noncompliance of this provision.
This Fronius product has an internal Arc Fault Circuit Interrupter (AFCI) Type 1. This component detects and separates serial arcs in your PV system, thus meeting the requirements of standard UL1699B Outline of Investigation for Photovoltaic (PV) DC Arc Fault Circuit Protection (Issue Number 2, January 14, 2013). In addition, Fronius accepts no liability for damages that may result from the occurrence of arcs. Claims against Fronius due to reduced yield or yield loss during the time the inverter is shut down by the AFCI are excluded. Costs that may arise due to inverter being shut down by the AFCI shall be borne by the operator.
Waste electrical and electronic equipment must be collected separately and recycled in an environmentally sound manner in accordance with the European Directive and national law. Used equipment must be returned to the distributor or through a local authorized collection and disposal system. Proper disposal of the used device promotes sustainable recycling of material resources. A failure to observe this may lead to potential health/environmental impacts
