LogoService Menü - SnapINverter
  • en
    • Contact
    • Imprint
    • Terms and conditions
    • Data privacy statement
    • 018-08082024
    • General
      • General
      • Safety
      • Firmware version
    • Opening a Service menu
      • Setting menu entries, general
    • Service Basic menu
      • Access code for the Service Basic menu
      • Overview of menu items in the Service Basic menu
      • MPP Tracker 1
      • MPP Tracker 2
      • USB Eventlog
      • Input signal
      • SMS / relay
      • Grounding setting (only Fronius Galvo)
      • Insulation Settings
      • TOTAL reset
    • Service Error Counter menu
      • Access code for the Service Error Counter menu
      • Overview of menu items in the Service Error Counter menu
    • Service Pro menu
      • General
      • Access code for the Service Pro menu
      • Overview of menu items in the Service Pro menu
      • Voltage limit values
      • Frequency limit values
      • NL-MONitor
      • Trip Time Delay
      • Reactive Power Mode
      • Freq dep. Power Red
      • Volt. dep. Power Red
      • Manual Power Reduction
      • Softstart
      • Voltage Fault Ride Through
      • DC-Injection
      • Ripple Control
      • I(delta gr.)F
        Compensation
      • Anti Islanding
      • Grid Quality Factor
      • Rate of change of frequency
      • Ramp Rate
      • Fail-Safe
      • Initial Start Time, Reconnect Time
      • Powerline Communication (Fronius Symo Advanced UL version)
      • DC Arc Fault Protection
    • "Advanced Grid Features": Reactive Power Mode
      • General information about reactive power mode
      • Potential operating range of the inverter in conjunction with reactive power
      • Overview of reactive power control options
      • Const. Cos φ
      • Const. Q Rel
      • Const. Q Abs
      • Ch Cos φ (P)
      • Ch Q (U)
      • Ch Q (P)
      • Lock-In / Lock-Out for characteristic operating mode
    • "Advanced Grid Features": GFDPR - Grid frequency-dependent power reduction P(f)
      • GFDPR - Function description
      • GFDPR - Application example On DisHyst
      • Voltage Fault Ride Through - application example
      • GFDPR - Application example with "alt. Return Grad. 1” and “Alt. Ret. Grad Thr.”
      • GFDPR - Application example with "Return Gradient 2"
    • "Advanced Grid Features": GVDPR Grid voltage-dependent power reduction P(U)
      • GVDPR - Function description
    • "Advanced Grid Features": VFRT - Dynamic grid backup during temporary drops in grid voltage
      • VFRT - Function description
      • VFRT - Regions
      • VFRT - K-Factor
    Service Menü - SnapINverter Service Manual
    General
    General
    The "Service menus" are setup menus for installers and service engineers. The "Service menus" are located at a separate menu level that can only be opened by entering an access code.
    The access code is provided by Fronius.
    The following "Service menus" are described in these instructions:
    • Service Pro menu
    1. General
    General
    • Service Pro menu
    1. General
    Safety
    CAUTION!
    Incorrect settings can cause malfunctions and failures on the inverter.
    Settings may only be made by trained and qualified personnel. Incorrect or omitted settings will result in non-conformance with the standard.
    IMPORTANT! If a status code is shown on the inverter display during the startup phase, the "Service menus" can be opened by pressing the "Menu" button five times and then entering the relevant access code.
    Refer to the safety rules in the inverter Operating Instructions.
    1. General
    Firmware version
    The functions described in these instructions are valid from the following firmware versions:
    • SnapINverter ROW: fro29390.upd and higher
    • SnapINverter US: fro29390.upd and higher
    1Press the "Menu" key    until the screen on the left appearsThe menu level appears
    2Press the unassigned "Menu / Esc" key 5 times
    "Access Code" is displayed in the "CODE" menu; the first digit starts flashing
    3Enter the access code for the Service menu required: Use keys    to select a value for the first digit of the code
    4Press "Enter"
    The second digit flashes
    5Repeat steps 3 and 4 for the second, third, fourth and fifth digits of the access code until...
    ... the selected code starts flashing.
    6Press "Enter"     12345 ... Example codeThe first parameter of the required Service menu is displayed
    1. Opening a Service menu
    4Press "Enter"
    1Open the desired menu
    2Use the 'Up' or 'Down' keys to select the desired menu item
    3Press "Enter"
    The available settings are displayed:
    The first digit of a value to be set flashes:
    4Use the 'Up' or 'Down' buttons to select the desired setting
    5Press the 'Enter' key to save and apply the setting.
    To discard the setting, press the 'Esc' key.
    4Use the 'Up' or 'Down' keys to select a value for the first digit
    5Press "Enter"
    The second digit of the value flashes.
    6Repeat steps 4 and 5 until ...
    the whole value to be set flashes.
    7Press "Enter"
    8Repeat steps 4 - 6 as required for units or other values that are to be set until the appropriate unit or the value flashes.
    9Press the 'Enter' key to save and apply the changes.
    To discard the changes, press the 'Esc' key.
    The currently selected menu item is displayed.
    Service Basic menu
    2 2 7 4 2
    1. Service Basic menu
    2 2 7 4 2
    1)
    The value is applied
    2)
    The function is deactivated
    3)
    Apply the function settings as described in the inverter Operating Instructions
    4)
    Max. and min. voltage values and max. power of feeding in are reset to zero in the TOTAL display mode
    a
    Fronius Galvo
    h
    Fronius Eco
    b
    Fronius Symo 3.0 - 4.5 S
    i
    Fronius Symo 10.0 - 12.0 208-240
    c
    Fronius Symo 3.0 - 8.2 M
    j
    Fronius Symo 10.0 - 24.0 480
    d
    Fronius Symo 10.0 - 20.0 M
    k
    Fronius Symo 15.0 208
    e
    Fronius Symo Hybrid
    l
    Fronius Primo 3.8 - 8.2 (UL version)
    f
    Fronius Primo 3.0 - 8.2
    m
    Fronius Symo Advanced 10.0 - 12.0 208-240
    g
    Fronius Primo 10.0 - 15.0 (UL version)
    n
    Fronius Symo Advanced 15.0 - 24.0 480
    MPP Tracker 1
    DC operating mode
    MPP AUTO
    FIX
    MPP USER
    Dyn. Peak Manager b,c,d,e,f,g,h,i,j,k,l
    ON
    OFF
    2)
    Fixed voltage
    80 - 800 V f,g,l
    120 - 440 V a
    150 - 800 V b,c,d,e,i,j
    325 - 850 V k
    580 - 850 V h
    1)
    1)
    1)
    1)
    1)
    MPPT1 start voltage
    80 - 800 V f,g,l
    120 - 440 V a
    325 - 850 V k
    580 - 850 V h
    1)
    1)
    1)
    1)
    1)
    MPP Tracker 2
    c,d,f,g,i,j,l
    MPP Tracker 2
    ON
    OFF
    2)
    DC operating mode
    MPP AUTO
    FIX
    MPP USER
    Dyn. Peak Manager
    ON
    OFF
    2)
    Fixed voltage
    80 - 800 V f,g,l
    150 - 800 V c,d,i,j,
    1)
    1)
    MPPT2 start voltage
    80 - 800 V f,g,l
    1)
    1)
    USB logbook
    ON
    OFF
    2)
    Auto
    2)
    Input signal
    Mode of operation
    Ext Sig.
    S0-Meter
    OFF
    2)
    Triggering method
    (indicated by selection of "Ext Sig.")
    Ext. Stop
    Warning
    Connection type
    N/C
    N/O
    Grid power limit
    0 - Device rated power
    1)
    Impulse rate
    100 - 20000
    1)
    SMS / relay
    Event delay
    900 - 86,400 s
    1)
    Event counter
    10 - 255
    1)
    Grounding setting
    Fronius Galvo
    Grounding mode
    OFF
    Positive
    Negative
    2)
    Earth current watchdog
    Warning
    Error
    Warn Err
    Switch-off delay
    0 - 9999 hrs
    1)
    Insulation mode b,c,
    d,e,f,g,h,i,j,k,l
    Insulation warning
    ON
    OFF
    2)
    Threshold warning
    0.1 - 10 MOhm b,c,d,e,h
    0.5 - 10 MOhm k
    0.6 - 10 MOhm a,g,i,j
    1 - 10 MOhm f,l
    1)
    1)
    1)
    1)
    Threshold error
    600 kOhm - 10,000 kOhm
    1)
    TOTAL reset
    CONFIRM
    4)
    The display of menu items depends on the respective country setup.
    MPP Tracker 1
    Setting the operating mode of MPP Tracker 1
    Selection options
    DC operating mode / Dyn. Peak Manager / Fixed voltage / MPPT1 start voltage
    DC operating mode
    to adjust how the Maximum Power Point (MPP) Tracker should work
    Selection options
    MPP AUTO / FIX / MPP USER
    MPP AUTO
    normal operating status;
    the inverter automatically searches for the ideal operating point across the complete MPP operating range (if the PV voltage falls below the preset value, the inverter will shut down with STATE 306 (PV output too low))
    FIX
    for entering a fixed DC voltage at which the inverter will operate
    MPP USER
    for entering the start voltage, at which the MPP tracker starts searching for the optimal operating point.
    Dyn. Peak Manager
    for activating or deactivating the Dynamic Peak Manager
    Selection options
    ON / OFF
    Fixed voltage
    for entering the fixed voltage
    Unit
    V
    Setting range
    80 - 800 f,g,l
    120 - 440 a
    150 - 800 b,c,d,e,i,j
    325 - 850 k
    580 - 850 h
    MPPT1 start voltage
    for entering the MPPT1 start voltage
    Unit
    V
    Setting range
    80 - 800 f,g,l
    120 - 440 a
    325 - 850 k
    580 - 850 h
    MPP Tracker 2
    Setting the operating mode of the MPP Tracker 2
    Selection options
    MPP Tracker 2 / DC operating mode / Dyn. Peak Manager / Fixed voltage / MPPT2 start voltage
    MPP Tracker 2
    for activating/deactivating a 2nd MPP tracker
    Setting range
    OFF/ ON
    DC operating mode
    Selection options
    MPP AUTO
    the inverter automatically searches for the ideal operating point across the complete operating range (if the voltage falls below the preset value, the inverter will shut down with STATE 306 (PV output too low))
    FIX
    MPP USER
    for entering the MPP voltage above which the inverter will search for its ideal operating point
    Dyn. Peak Manager
    Selection options
    ON / OFF
    Fixed voltage
    fixed voltage value limits according to power stage set. The value assigned here is assumed for MPP1 and MPP 2
    Unit
    V
    Setting range
    Fronius Primo: 80 - 800
    Fronius Symo (except Fronius Symo 3.0 - 4.5 S): 150 - 800
    MPPT2 start voltage
    for entering the MPPT2 start voltage
    Unit
    V
    Setting range
    80 - 800
    150 - 800
    USB Eventlog
    Activates or deactivates the function for saving to the USB flash drive all occurring status codes, as well as all inverter data, in 5 second values. This data will be saved on the USB flash drive in the EVENT.csv file.
    Selection options
    ON / OFF / Auto
    The "Auto" setting is reserved for future USB modifications and currently has a similar function to the "OFF" setting.
    Input signal
    Activation and setting of the Input signal at the multifunction current interface
    Selection options
    How it works / Triggering method / Connection type / Grid feed-in limit / Pulses per kWh
    (Triggering method and Connection type only visible by selecting "Ext Sig.")
    How it works
    Ext Sig.
    Signal input (e.g. signal contact for the surge protection device)
    S0-Meter
    Counting the pulses of an external S0 meter (input)
    OFF
    Mode of operation deactivated
    Triggering method
    Ext. Stop
    In the event of a signal error, an external stop appears on the display (State 668 - interruption of feed-in).
    Warning
    In the event of a signal error, a warning appears on the display at regular intervals (State 568 - multifunction current interface warning, no interruption of feed-in).
    Connection type
    N/C
    Normally-closed function (n.c. = normally closed)
    N/O
    Normally-open function (n.o. = normally open)
    Grid feed-in limit
    Field for entering the maximum amount of energy to be fed into the grid in W. If this value is exceeded, the inverter regulates down to the set value within the time required by national standards and regulations.
    Setting range
    Pulses per kWh
    Field for entering the pulses per kWh of the S0 meter.
    Setting range
    100 - 20,000
    SMS / relay
    Selection options
    Event delay / Event counter
    Event delay
    for entering the time delay after which an SMS is sent or the relay is to switch
    Unit
    s
    Setting range
    900 - 86400
    Event counter
    for entering the number of errors after which an SMS is sent or the relay is to switch
    Unit
    Setting range
    10 - 255
    Activation and setting of the solar module ground
    Selection options
    Grounding mode / Earth current watchdog(1) / Switch off delay(2)
    (1)
    only displayed if "Positive" or "Negative" is selected under Grounding mode
    (2)
    only displayed if "Warn Err" is activated
    Grounding mode
    for selecting the solar module ground or deactivating this function
    Selection options
    Off / Positive / Negative
    for activating and deactivating the grounding monitoring
    Selection options
    Off / Warning / Error / Warn Err
    Warning
    If there is a grounding fault, a warning that there is no longer a grounding connection appears on the display at regular intervals (no interruption of feed-in). State 502 will subsequently be displayed.
    Error
    The inverter produces an error message if there is a grounding fault with immediate shutdown of the inverter (State 475).
    Warn Err
    If there is a grounding fault, a warning that there is no longer a grounding connection first appears on the display at regular intervals (no interruption of feed-in).
    The inverter will then be switched off after a specified interval (switch off delay). Depending on the selected switch-off delay, STATE 551 is displayed. Once this delay time has passed, the error STATE 471 will be displayed
    Switch off delay
    for setting the delay time (in h) until the inverter will switch off following a grounding fault (unless the fault is rectified in the meantime).
    Unit
    h
    Setting range
    0 - 9999
    IMPORTANT! If the solar module manufacturer has specified that grounding of the solar modules is required, the relevant solar module ground setting must be applied to the inverter. Instructions from the solar module manufacturer on polarity and the required solar module grounding method, as well as national regulations, must be observed.
    The solar module can be grounded to the negative pole in the inverter itself. In this case use of a ground fuse (1 A) is mandatory.
    IMPORTANT! The fuse in the inverter is not used for grounding the solar modules to the positive pole; this has to take place outside the inverter.
    Insulation Settings
    Activation and setting of the insulation settings
    Selection options
    Warning mode / Warning threshold / Error threshold
    Warning mode
    for activating and deactivating the insulation monitoring, with display of a warning without interruption of feed-in if there is an insulation fault
    Selection options
    ON / OFF
    Warning threshold
    for setting an insulation threshold at which the inverter produces a warning (without interruption of feed-in)
    Setting range
    0.1 - 10 b,c,d,e,h
    0.5 - 10 k
    0.6 - 10 a,g,i,j
    1.0 - 10 f,l
    Unit
    MOhm
    Error threshold
    for setting an insulation threshold at which the inverter produces an error message and interrupts grid power feed operation
    Setting range
    600 - 10000
    Unit
    kOhm
    TOTAL reset
    In the LOG menu item, resets the max. and min. voltage values and the max. power of feeding in to zero.
    NOTE!
    Once values have been reset, this action cannot be undone.
    3 7 7 6 7
    1. Service Error Counter menu
    3 7 7 6 7
    State Counter 0-999
    displays all status codes in numerical order
    State Ranking TODAY
    displays all the day's status codes according to their frequency
    State Ranking L.Day (L.Day = Last Day)
    displays all the last day's status codes according to their frequency
    State Ranking ALL
    displays all status codes according to their frequency
    Counter Reset
    Press "Enter" to reset the State Counter.
    This will irretrievably delete all logged values.
    Service Pro menu
    General
    Preconfigured network parameters depend on the country setup. The parameters have been selected to ensure that the inverter is compliant with currently applicable standards.
    In special cases, a qualified electrician or Fronius Service Partner (FSP) can adapt preconfigured country-specific limit values to local grid conditions in the Service Pro menu.
    The modified limit values are permanently saved by the inverter.
    NOTE!
    Modifying the monitoring parameters will immediately result in non-conformance of the inverter with the standards and, for this reason, may only be carried out after consulting the responsible grid operator.
    To reinstate the original settings on the inverter, select the country setup again (Country Setup Menu - access code = 73887), as described in the User Information.
    1. Service Pro menu
    General
    NOTE!
    1. Service Pro menu
    The access code for the Service Pro menu is only provided to Fronius upon written request.
    The relevant request form can be obtained from the national Technical Support team.
    1. Service Pro menu
    n
    Value, dependent on local grid and also partly on country setup
    1)
    The function is activated
    2)
    3)
    6)
    A characteristic is entered with 4 X points and 4 Y points
    a
    Fronius Galvo
    i
    b
    j
    c
    k
    d
    l
    e
    Fronius Symo Hybrid
    m
    f
    n
    g
    o
    Fronius Galvo (UL version)
    h
    Fronius Eco
    p
    Fronius Symo Advanced 10.0 - 20.0
    U Inner Limit Max
    n [V]
    2)
    U IL Max TripTime
    n [cyl]
    2)
    U Inner Limit Min
    n [V]
    2)
    U IL Min TripTime
    n [cyl]
    2)
    U Middle Limit Mode
    2)
    U Middle Limit Max
    n [V]
    2)
    U ML Max TripTime
    n [cyl]
    2)
    U Middle Limit Min
    n [V]
    2)
    U ML Min TripTime
    n [cyl]
    2)
    U Outer Limit Max
    n [V]
    2)
    U OL Max TripTime
    n [cyl]
    2)
    U Outer Limit Min
    n [V]
    2)
    U OL Min TripTime
    n [cyl]
    2)
    U Reconnect max
    n [V]
    2)
    U Reconnect min
    n [V]
    2)
    U Recon. IL max
    n [V]
    2)
    U Recon. IL min
    n [V]
    2)
    U Longtime Limit
    n [V]
    2)
    U Fast Supervisory
    ON
    x
    OFF
    x
    Freq. Inner Limit Max
    n [Hz]
    2)
    Freq IL Max TripTime
    n [cyl]
    2)
    Freq. Inner Limit Min
    n [Hz]
    2)
    Freq IL Min TripTime
    n [cyl]
    2)
    Alt Freq Mode
    ON
    1)
    OFF
    3)
    Alt Freq IL Max
    n [Hz]
    2)
    Alt Freq IL Max TT
    n [cyl]
    2)
    Alt Freq IL Min
    n [Hz]
    2)
    Alt Freq IL Min TT
    n [cyl]
    2)
    Freq Outer Limit Max
    n [Hz]
    2)
    Freq OL Max TripTime
    n [cyl]
    2)
    Freq Outer Limit Min
    n [Hz]
    2)
    Freq OL Min TripTime
    n [cyl]
    2)
    Redundant FAC Check
    ON
    x
    OFF
    x
    Redundant UAC Check
    ON
    x
    OFF
    x
    NL-MONitor
    d,i,j,k,l,o
    NL-MONitor On/Off
    ON
    x
    OFF
    x
    Stingeri,j,k
    x
    1)
    3)
    1)
    NL Uouter Limit Min
    n [Hz]
    2)
    NL U OL Min TripTime
    n [cyl]
    2)
    NL UMiddle Limit Min
    n [Hz]
    2)
    NL U ML Min TripTime
    n [cyl]
    2)
    NL Uinner Limit Min
    n [Hz]
    2)
    NL U IL Min TripTime
    n [cyl]
    2)
    NL Uinner Limit Max
    n [Hz]
    2)
    NL U IL Max TripTime
    n [cyl]
    2)
    NL UMiddle Limit Max
    n [Hz]
    2)
    NL U ML Max TripTime
    n [cyl]
    2)
    NL Uouter Limit Max
    n [Hz]
    2)
    NL U OL Max TripTime
    n [cyl]
    2)
    Freq Reconnect max
    n [Hz]
    2)
    Freq Reconnect min
    n [Hz]
    2)
    Freq Recon. IL max
    n [Hz]
    2)
    Freq Recon. IL min
    n [Hz]
    2)
    Trip Time Delay
    n [cyl]
    2)
    Reactive Power Mode
    React. P. Mode
    Cos φ / P
    x
    Q / U
    x
    Q / P
    x
    OFF
    x
    C. Cos φ
    x
    C. Qrel
    x
    C. Qabs
    x
    1)
    1)
    1)
    3)
    1)
    1)
    1)
    Grid Power Priority
    Reactive
    x
    Active
    x
    1)
    1)
    Const. Cos φ
    2)
    Const. Cos φ TimeC.
    2)
    Const. Q Rel
    2)
    Const. Q Rel TimeC.
    2)
    Const. Q Abs
    2)
    Const. Q Abs TimeC.
    2)
    Ch Cos φ (P) 0-0
    6)
    Ch Cos φ (P) 0-1
    6)
    Ch Cos φ (P) 1-0
    6)
    Ch Cos φ (P) 1-1
    6)
    Ch Cos φ (P) 2-0
    6)
    Ch Cos φ (P) 2-1
    6)
    Ch Cos φ (P) 3-0
    6)
    Ch Cos φ (P) 3-1
    6)
    Ch Cos φ (P) TimeC.
    2)
    Ch Cos φ (P) U-LockIn
    2)
    Ch Cos φ (P) U-LockOut
    2)
    Ch Cos φ (P) P-LockOut
    2)
    Ch Q (U) 0-0
    6)
    Ch Q (U) 0-1
    6)
    Ch Q (U) 1-0
    6)
    Ch Q (U) 1-1
    6)
    Ch Q (U) 2-0
    6)
    Ch Q (U) 2-1
    6)
    Ch Q (U) 3-0
    6)
    Ch Q (U) 3-1
    6)
    Ch Q (U) Init Delay
    2)
    Ch Q (U) Offset Factor
    2)
    Ch Q (U) TimeC.
    2)
    Ch Q (U) P-LockIn
    2)
    Ch Q (U) P-LockOut
    2)
    Ch Q (U) Cos φ Min.
    2)
    Ch Q (P) 0-0
    6)
    Ch Q (P) 0-1
    6)
    Ch Q (P) 1-0
    6)
    Ch Q (P) 1-1
    6)
    Ch Q (P) 2-0
    6)
    Ch Q (P) 2-1
    6)
    Ch Q (P) 3-0
    6)
    Ch Q (P) 3-1
    6)
    Ch Q (P) TimeC.
    2)
    Ch Q (P) U-LockIn
    2)
    Ch Q (P) U-LockOut
    2)
    Ch Q (P) P-LockOut
    2)
    Freq dep. Power Red
    GFDPR ON/OFF
    Off
    x
    On DisHyst
    x
    On
    x
    3)
    1)
    1)
    P-Reduct. Reference
    Pn-Pn*k*x
    x
    Pm-Pn*k*x
    x
    Pm-Pm*k*x
    x
    act. Pwr.
    x
    nom. Pwr.
    x
    3)
    1)
    1)
    1)
    1)
    P-Increa. Reference
    Pn-Pn*k*x
    x
    Pm-Pn*k*x
    x
    Pm-Pm*k*x
    x
    3)
    1)
    1)
    Enable Limit
    50 - 52 Hz
    2)
    Enable Limit Under F.e)
    49,7 - 49,9 Hz
    2)
    Intentional Delay
    0 - 60 s
    2)
    Derating Gradient
    0,01 - 100%/Hz
    2)
    Derating Gradient U.F.e)
    0,01 - 100%/Hz
    2)
    Stop Frequency
    100 - 0 %
    Stop Frequency U.F.e)
    0 - 100 %
    Change Time Constant
    0 - 60 s
    2)
    Frequency Test Time
    0 - 600 s
    2)
    Disable Limit Min.
    50 - 52 Hz
    2)
    Disable Limit Max.
    50 - 52 Hz
    2)
    Alt. Ret. Grad Thr.
    0,01 - 100 %
    2)
    Return Gradient 1
    0,01 - 100 %/s
    2)
    Alt. Return Grad. 1
    0,01 - 100 %/s
    2)
    Use Return Grad. 2
    OFF
    x
    ON
    x
    3)
    1)
    Return Gradient 2
    0,01 - 100 %/s
    2)
    P(f) f transition Of****
    Hz
    2)
    P(f) f transition Uf****
    Hz
    2)
    GVDPR On/Off
    Off
    x
    On
    x
    3)
    1)
    P-Reduct. Reference
    Pn-Pn*k*x
    x
    Pm-Pn*k*x
    x
    Pm-Pm*k*x
    x
    3)
    1)
    1)
    Enable Limit
    208 - 300 V
    2)
    Derating Gradient
    0.01 - 100 %/V
    2)
    Enable Limit UnderV.
    200 - 250 V
    2)
    Derating Gr. UnderV.
    0.01 - 100 %/V
    2)
    0.01 - 600 s
    2)
    Event Message
    OFF
    x
    ON
    x
    3)
    1)
    P(U) Stop Voltage OV***
    0 -311 V (default: 270 V)
    2)
    P(U) Stop Power OV****
    0 -100 % (default: 0 %)
    2)
    P(U) Stop Voltage UV***
    200 -311 V (default: 270 V)
    2)
    P(U) Stop Power UV****
    2)
    Softstart
    Softstart On/Off
    Off
    x
    On acFlt
    x
    On
    x
    3)
    1)
    1)
    Softstart Gradient
    0.01 - 100 %/s
    2)
    Manual Power Reduct.
    2)
    Voltage Ride Through c,d,e,f,g,h,i,j,k,l
    VRT Mode
    OFF
    x
    ON
    x
    3)
    1)
    R1/R2 /R3 Calculation Mode
    Nomin. B.
    x
    Bound. B.
    x
    Off
    x
    Passive
    x
    Zero Cur.
    x
    Act. UBCC
    x
    3)
    1)
    1)
    1)
    1)
    1)
    R1/R2 /R3 Detection Mode (Norm 50549)
    LN-Volt.
    x
    LL-Volt.
    x
    LL+LN-Volt.
    x
    3)
    1)
    1)
    R1/R2 /R3 Static Threshold
    0 - 200 %
    2)
    R1/R2 /R3 k-Factor positive-sequence system
    0 - 10,000
    2)
    0 - 10,000
    2)
    IacReactLim Overexc
    0 - 110 %
    2)
    IacReactLim Underexc
    0 - 110 %
    2)
    Sudden Voltage Change
    OFF
    x
    ON
    x
    Insensitivity Range
    0 - 100 %
    Deactivation Time
    0 - 1000 s
    DC-Injection
    DC-I. InnerLimit M.
    OFF
    x
    Absolute
    x
    Relative
    x
    3)
    1)
    1)
    DC-I. I.L. Absolute
    0 - 10 A
    2)
    DC-I. I.L. Relative
    0 - 10 %
    2)
    DC-I. I.L. TripTime
    0 - 10 s
    2)
    DC-I. OuterLimit M.
    OFF
    x
    Absolute
    x
    Relative
    x
    3)
    1)
    1)
    DC-I. O.L. Absolute
    0 - 10 A
    2)
    DC-I. O.L. Relative
    0 - 10 %
    2)
    DC-I. O.L. TripTime
    0 - 10 s
    2)
    Ripple Control
    Ripple Ctrl. Mode
    OFF
    x
    ON
    x
    3)
    1)
    Ripple Signal Frequency
    2)
    Ripple Grid Inductance
    2)
    IΔF
    Compensation
    IΔF Comp. Mode
    OFF
    x
    ON
    x
    3)
    1)
    ΔUdc Link Voltage
    0 - 200 V
    2)
    Anti Islanding
    Sym Asym
    Sym
    OFF
    2)
    2)
    2)
    Grid Quality Factor
    0.1-10
    2)
    RateOfChangeOfFreq
    ROCOF On / Off
    On
    x
    Off
    x
    1)
    3)
    ROCOF Limit
    ROCOF TripTime
    Power Ramp Rate (only in Country Setup AU)
    Power-Ramp-Up-Mode
    On
    x
    Off
    x
    1)
    3)
    Power-Ramp-Up
    0.00 -100 %/s
    Power-Ramp-Down-Mode
    On
    x
    Off
    x
    1)
    3)
    Power-Ramp-Down
    0.05 -75 %/s
    Fail-Safe
    DM FailSafe Mode
    Off
    x
    Permanent
    x
    3)
    1)
    DM FailSafe Behaviou
    Disconn.
    1)
    Initial Start Time
    1 - 900 s
    2)
    Reconnect Time
    1 - 900 s
    2)
    Powerline Comm.
    p
    Powerline COM Mode
    Off
    x
    SunSpec
    x
    2)
    p
    AFPE Mode
    On
    x
    Off
    x
    1)
    3)
    Automatic Reconnect
    -1 to 4
    1. Service Pro menu
    Graphic illustrating the limits
    IL
    "Inner Limit" - inner limit value
    ML
    "Middle Limit" - middle limit value
    OL
    "Outer Limit" - outer limit value
    (1)
    Trip range
    U Inner Limit Max
    Upper inner grid voltage limit value in V
    U IL Max TripTime
    Trip time A) for exceeding the upper inner grid voltage limit value in cyl B)
    U Inner Limit Min
    Lower inner grid voltage limit value in V
    U IL Min Trip Time
    Trip time A) for falling below the lower inner grid voltage limit value in cyl B)
    U Middle Limit Mode
    0 or 1: 0 = Middle limits are deactivated, 1 = Middle limits are activated
    U Middle Limit Max
    Upper middle grid voltage limit in V
    U ML Max Trip Time
    Trip time for the upper middle grid voltage limit
    U Middle Limit Min
    Lower middle grid voltage limit in V
    U ML Min Trip Time
    Trip time for the lower middle grid voltage limit
    U Outer Limit Max
    Upper outer grid voltage limit value in V
    U OL Max TripTime
    Trip time A) for exceeding the upper outer grid voltage limit value in cyl B)
    U Outer Limit Min
    Lower outer grid voltage limit value in V
    U OL Min Trip Time
    Trip time A) for falling below the lower outer grid voltage limit value in cyl B)
    U Reconnect max
    Upper voltage limit value for reconnection to the public grid following disconnection due to impermissible parameter deviation
    [V]
    U Reconnect min
    Lower voltage limit value for reconnection to the public grid following disconnection due to impermissible parameter deviation
    [V]
    U Recon. IL max
    Upper inner voltage limit value for reconnection to the public grid following disconnection due to impermissible parameter deviation
    [V]
    U Recon. IL min
    Lower inner voltage limit value for reconnection to the public grid following disconnection due to impermissible parameter deviation
    [V]
    U Longtime Limit
    Voltage limit value in V for the 10-minute average voltage value
    U Fast Supervisory
    Fast surge protection cut-out, which can take place within a period.
    A)
    Different trip times can be assigned to the inner limit value IL and outer limit value OL.
    For example: short trip time for a deviation from the outer limit value
    long trip time for a deviation from the inner limit value
    b)
    cyl = grid periods (cycles); 1 cyl corresponds to 20 ms at 50 Hz or 16.66 ms at 60 Hz
    1. Service Pro menu
    IL
    OL
    (1)
    Trip range
    Upper inner grid frequency limit value in Hz
    Trip time A) for exceeding the upper inner grid frequency limit value in cyl B)
    Lower inner grid frequency limit value in Hz
    Trip time A) for falling below the lower inner grid frequency limit value in cyl B)
    Alt Freq Mode
    For activating / deactivating alternative frequency limit values
    ON / OFF
    Alt Freq IL Max
    Alternative upper inner grid frequency limit value in Hz
    Alt Freq IL Max TT
    Trip time A) for exceeding the alternative upper inner grid frequency limit value in cyl B)
    Alt Freq IL Min
    Lower alternative inner grid frequency limit value in Hz
    Alt Freq IL Min TT
    Trip time A) for falling below the alternative lower inner grid frequency limit value in cyl B)
    Upper outer grid frequency limit value in Hz
    Trip time A) for exceeding the upper outer grid frequency limit value in cyl B)
    Lower outer grid frequency limit value in Hz
    Trip time A) for falling below the lower outer grid frequency limit value in cyl B)
    Redundant FAC Check
    Can be switched on or off
    Redundant UAC Check
    Freq Reconnect Max
    Upper grid frequency limit value for reconnection to the public grid following disconnection due to impermissible parameter deviation
    [Hz]
    Freq Reconnect Min
    Lower grid frequency limit value for reconnection to the public grid following disconnection due to impermissible parameter deviation
    [Hz]
    Freq Recon. IL Max
    Upper inner grid frequency limit value for reconnection to the public grid following disconnection due to impermissible parameter deviation
    [Hz]
    Freq Recon. IL Min
    Lower inner grid frequency limit value for reconnection to the public grid following disconnection due to impermissible parameter deviation
    [Hz]
    A)
    b)
    1. Service Pro menu
    NL-MONitor
    For setting the NL-MON (neutral conductor phase monitoring) switch-off values
    Selection options
    NL-MONitor On/Off / NL Uouter Limit Min / NL U OL Min TripTime / NL UMiddle Limit Min / NL U ML Min TripTime / NL Uinner Limit Min / NL U IL Min TripTime / NL Uinner Limit Max / NL U IL Max TripTime / NL UMiddle Limit Max / NL U ML Max TripTime / NL Uouter Limit Max / NL U OL Max TripTime
    NL-MONitor On/Off
    Selection options: ON / OFF / Stinger
    NL Uouter Limit Min
    Specification of the minimum external switch-off value
    Specification of the operating time of the minimum external switch-off value
    Specification of the minimum middle switch-off value
    NL Uinner Limit Min
    Specification of the minimum internal switch-off value
    Specification of the operating time of the minimum internal switch-off value
    NL Uinner Limit Max
    Specification of the maximum internal switch-off value
    Specification of the operating time of the maximum internal switch-off value
    Specification of the maximum middle switch-off value
    Specification of the operating time of the maximum middle switch-off value
    NL Uouter Limit Max
    Specification of the maximum external switch-off value
    Specification of the operating time of the maximum external switch-off value
    1. Service Pro menu
    Trip Time Delay
    additional configurable switch off delay;
    relates to all trip times and increases the trip times by the specified value
    0 - 255 [cyl]
    1. Service Pro menu
    Reactive Power Mode
    for setting special reactive power parameters
    The parameters in this menu item enable the feed-in method of the inverter to be modified.
    IMPORTANT! A detailed explanation of the settings can be found in the "Advanced Grid Features" section under: Reactive Power Mode.
    Selection options
    React. P. Mode / Const. Cosφ / Const. Cosφ TimeC. / Const. Q Rel. / Const. Q Rel. TimeC. / Const. Q Abs. / Const. Q Abs. TimeC. / Ch Cosφ (P) *-* / Ch Cosφ (P) TimeC. / Ch Cosφ (P) U-LockIn / Ch Cosφ (P) U-LockOut / Ch Cosφ (P) P-LockOut / Ch Q (U) *-* / Ch Q (U) Initial Delay / Ch Q (U) Offset Factor / Ch Q (U) TimeC. / Ch Q (U) P-LockIn / Ch Q (U) P-LockOut / Ch Q (U) Cosφ Min. / Ch Q (P) *-* / Ch Q (P) TimeC. / Ch Q (P) U-LockIn / Ch Q (P) U-LockOut / Ch Q (P) P-LockOut
    0-0 / 0-1 / 1-0 / 1-1 / 2-0 / 2-1 / 3-0 / 3-1 respectively
    React. P. Mode
    for activating / deactivating reactive power mode
    Selection options
    Grid Power Priority / C. cosφ / C. Qrel / C. Qabs / cosφ/P / Q/U / Q/P / OFF
    Grid Power Priority
    For setting whether effective power (Active) or reactive power (Reactive) has priority
    C. cosφ
    Constant cos phi specification
    C. Qrel
    Constant specification of the relative reactive power in %
    C. Qabs
    Constant specification of absolute reactive power in VAr
    cosφ/P
    Cos phi specification depending on effective power
    Q/U
    Relative reactive power specification depending on current grid voltage
    Q/P
    Relative reactive power specification depending on effective power
    OFF
    Reactive power mode deactivated
    • first select one of the reactive power modes from the selection options
    • then set the parameters in the relevant reactive power mode
    The reactive power modes:
    Const. Cosφ
    Once "Enter" has been pressed, the value for the cos φ power factor can be set:
    -0.85 (ind.) - +0.85 (cap.) -- Galvo
    -0.70 (ind.) - +0.70 (cap.) -- Symo S, Symo M 8k2,
    Symo Hybrid, Primo 8k2, Primo US 8k2
    -0.00 (ind.) - +0.00 (cap.) -- Symo M 20, Primo 15, Eco, Symo US 12, Symo US 24, Symo US (Eco)
    Const. Cosφ TimeC.
    Time constant at which a new set value of the power factor cos φ is activated
    Const. Q Rel.
    Once "Enter" has been pressed, the value for the reactive power relative to the nominal apparent power can be set.
    Time constant at which a new set value of the relative reactive power is activated
    Const. Q Abs.
    Once "Enter" has been pressed, the value for absolute reactive power can be set from 0 to the max. device output (inductive/capacitive) in VAr.
    Time constant at which a new set value of the absolute reactive power is activated
    Ch Cosφ (P) *-*
    Cosφ (P) characteristic:
    Ch Cosφ (P) TimeC.
    Time constant at which a new set value of the (respective) control is compensated for.
    - Compensation after ~3x the time constant
    Input of a voltage value; when this voltage value is exceeded the Cosφ (P) characteristic is activated.
    80 - 120%
    Input of a voltage value; when this voltage value is undershot the Cosφ (P) characteristic is deactivated.
    80 - 120%
    Input of a power value; when this power value is undershot the Cosφ (P) characteristic is deactivated.
    0 - 100%
    Ch Q (U) *-*
    Q (U) characteristic:
    Delays the application of the Q (U) control after the values Ch Q (U) 1 - x or 2 - x are undershot/exceeded
    0 - 60 s
    Moves the Q (U) characteristic along the Q axis by a factor of -1 to +1
    Ch Q (U) TimeC.
    Ch Q (U) P-LockIn
    Input of a power value; when this power value is exceeded the Q (U) characteristic is activated.
    0 - 100%
    Ch Q (U) P-LockOut
    Input of a power value; when this power value is undershot the Q (U) characteristic is deactivated.
    0 - 100%
    Ch Q (U) Cos. φ Min.
    Input of a minimum cos phi value at which the inverter may feed in power.
    0 - 1.0
    Ch Q (P) *-*
    Q (P) characteristic:
    Ch Q (P) TimeC.
    Ch Q (P) U-LockIn
    Input of a voltage value; when this voltage value is exceeded the Q (P) characteristic is activated.
    80 - 120%
    Ch Q (P) U-LockOut
    Input of a voltage value; when this voltage value is undershot the Q (P) characteristic is deactivated.
    80 - 120%
    Ch Q (P) P-LockOut
    Input of a power value; when this power value is undershot the Q (P) characteristic is deactivated.
    0 - 100%
    4 characteristic points 0 / 1 / 2 / 3 with the coordinates 0 (x) and 1 (y)
    1. Service Pro menu
    Freq dep. Power Red
    Frequency Dependent Power Reduction
    (from grid frequency dependent power reduction)
    When the GFDPR function is enabled and the specified grid frequency limit value is exceeded, the effective power is reduced according to a defined gradient.
    IMPORTANT! A detailed explanation of the settings can be found in the "Advanced Grid Features" section under: GFDPR - Grid frequency-dependent power reduction P(f).
    Selection options
    GFDPR On/Off / P-Reduct. Reference /P-Increa. Reference / Enable Limit / Enable Limit Under F. / Intentional Delay / Derating Gradient / Derating Gradient U.F. / Stop Frequency / Stop Frequency U.F. / Change Time Constant / Frequency Test Time / Disable Limit Min. / Disable Limit Max. / Alt. Ret. Grad Thr. / Return Gradient 1 / alt. Return Grad. 1 / Use Return Grad. 2 / Return Gradient 2 / P(f) f transition Of**** / P(f) f transition Uf****
    GFDPR On/Off
    Activation or deactivation of function
    Selection options
    Off / On DisHyst / On
    Off
    Function deactivated
    On DisHyst
    Function activated, no hysteresis
    On
    Function activated, with hysteresis
    P-Reduct. Reference
    Indicates the reference power for calculating the power reduction in the event of over frequency.
    Selection options
    Pn-Pn*k*x / Pm-Pn*k*x / Pm-Pm*k*x / act. Pwr. / nom. Pwr.
    Pm
    Actual capacity during entry
    Pn
    Nominal output of the device
    k
    Derating Gradient
    x
    Current frequency
    act. Pwr.
    Actual power at the time of entering into over frequency
    nom. Pwr.
    Nominal device output
    P-Increa. Reference
    Indicates the reference power for calculating the power reduction in the event of under frequency.
    Selection options
    Pm
    Pn
    k
    Derating Gradient
    x
    Current frequency
    Enable Limit
    for setting the frequency limit value above which a power reduction takes place
    Enable Limit Under F. (only on hybrid inverters)
    for setting the frequency limit value above which a power increase takes place
    Intentional Delay
    Delays the application of the P (f) control after the Enable Limit is exceeded
    0 - 60 s
    Derating Gradient
    for setting the gradient at which the effective power is reduced
    0.01 - 100%/Hz
    Reference variable
    current power at the start of power reduction
    Derating Gradient U.F. (only on hybrid inverters)
    for setting the gradient at which the effective power is increased
    0.01 - 100%/Hz
    Reference variable
    current power at the start of power increase
    Stop Frequency
    for setting the frequency limit value up to which a power reduction takes place.
    Stop Frequency U.F. (only on hybrid inverters)
    for setting the frequency limit value up to which a power increase takes place
    0 - 60 s
    Frequency Test Time
    for setting the waiting time after which the inverter will increase the power again (once the power has reduced such that the grid frequency is within the permitted frequency range between Disable Limit Max. and Disable Limit Min.).
    0 - 600 s
    for setting the upper / lower frequency range limit value
    Alt. Ret. Grad Thr.
    for setting the threshold above which the "Return Gradient 1" or the "alt. Return Grad. 1" is applied.
    e.g.:
    If the difference between the rated power and the current reduced power is less than or equal to the threshold, "Return Gradient 1" is applied.
    If the difference between the rated power and the current reduced power is greater than the threshold, "alt. Return Grad. 1" is applied.
    0.01 - 100%
    100% means that "Return Gradient 1" is always applied.
    Return Gradient 1
    for setting the rate of change at which the inverter increases the effective power from the current reduced value to the original value.
    0.01 - 100%/s
    Reference variable
    Device rated power
    alt. Return Grad. 1
    for setting the rate of change at which the inverter increases the effective power from the current reduced value to the original value;
    is activated if the difference between the rated power and the current reduced power is greater than the "Alt. Ret. Grad Thr.".
    0.01 - 100%/s
    Reference variable
    Difference between the output at the start of power reduction and the current output
    Use Return Grad. 2
    for activating/deactivating the rate of change at which the inverter increases the effective power from the original value to the device rated power.
    Selection options
    OFF / ON
    OFF
    raising the effective power from the original value to the device rated power takes place according to "Return Gradient 1"
    ON
    raising the effective power from the original value to the device rated power takes place according to "Return Gradient 2"
    Return Gradient 2
    for setting the rate of change at which the inverter increases the effective power from the original value to the device rated power.
    0.01 - 100%/s
    Reference variable
    Device rated power
    Frequency at which the device reaches an output power of 0 W with active battery. If the grid frequency continues to rise, energy is drawn from the public grid and thus the battery is charged. If there is no battery in the system or it is not active, this parameter has no function.
    Frequency at which the device reaches an output power of 0 W with active battery (charging power is reduced). If the grid frequency continues to drop, additional energy is fed into the grid. This energy can come from the module array or from the battery. If there is no battery in the system or it is not active, this parameter has no function.
    1. Service Pro menu
    Voltage Dependent Power Reduction
    (from grid voltage dependent power reduction)
    When the GVDPR function is activated and the specified grid voltage limit value is exceeded, the maximum effective power is reduced.
    The power is reduced by a specified gradient according to the phase with the highest voltage.
    IMPORTANT! A detailed explanation of the settings can be found in the "Advanced Grid Features" section under: GVDPR - Grid voltage-dependent power reduction P(U).
    Selection options
    GVDPR On/Off / P-Reduct. Reference / Enable Limit / Derating Gradient / Enable Limit UnderV. / Derating Gradient UnderV. / Change Time Constant / Event Message / P(U) Stop Voltage OV*** / P(U) Stop Power OV**** / P(U) Stop Voltage UV*** / P(U) Stop Power UV****
    GVDPR On/Off
    Selection options
    Off / On
    Off
    On
    Function activated
    P-Reduct. Reference
    Indicates the reference power for calculating the power reduction in the event of a surge.
    Selection options
    Pm
    Pn
    k
    Derating Gradient
    x
    Current frequency
    act. Pwr.
    Actual power when entering into the surge range
    nom. Pwr.
    Enable Limit
    for setting the grid voltage limit value above which a power reduction takes place
    208 - 300 V
    Derating Gradient
    0.01 - 100%/V
    for setting the grid voltage limit value above which a power increase takes place
    200 - 250 V
    0.01 - 100%/V
    for setting a time constant by which the inverter approaches the limitation target
    0.01 - 600 s
    Event Message
    for activating / deactivating event messages
    Selection options
    OFF / ON
    P(U) Stop Voltage OV****
    Grid voltage limit value up to which the power reduction takes place. The gradient is calculated automatically from the parameters Activation Threshold Overvoltage and Power at Stop Voltage at Overvoltage. The parameters Gradient Overvoltage and Calculation Mode have no function.
    Reference power when the set grid voltage limit value is reached.
    0 - 100% (default: 0%)
    P(U) Stop Voltage UV****
    Grid voltage limit value up to which the charging power of the battery is reduced. The gradient is calculated automatically from the parameters Activation Threshold Undervoltage and Power at Stop Voltage at Undervoltage. The parameters Gradient Undervoltage and Calculation Mode have no function.
    Reference power when the set grid voltage limit value is reached. Only for devices with battery in charging mode.
    1. Service Pro menu
    for manual specification of a max. output power value
    Setting range
    150 - max. W (kW)
    dependent on the inverter size
    1. Service Pro menu
    Softstart
    Activation and deactivation of the Softstart function, setting the gradient for the startup ramp
    Selection options
    Softstart On/Off / Softstart Gradient
    Softstart On/Off
    for activating and deactivating the Softstart function
    Off
    On acFlt
    Function activated;
    The Softstart Gradient is only applied in the event of a prior AC error.
    On
    Function activated;
    The Softstart Gradient is applied whenever start up is energised.
    Softstart Gradient
    for setting the gradient for the startup ramp
    0.01 - 100 %/s
    1. Service Pro menu
    „Voltage Fault Ride Through“
    Function for handling grid faults (grid voltage drops) as part of dynamic grid backup. Three independent voltage ranges can be set with different behaviours.
    IMPORTANT! A detailed explanation of the settings can be found in the "Advanced Grid Features" section under: LVFRT - Dynamic grid backup during temporary drops in grid voltage.
    VRT Mode
    VRT Mode universally switches on or off
    R1/2/3 Calculation Mode
    Off: Behaviour is equivalent to Passive Mode.
    Passive: During the grid fault the inverter behaves passively, i.e. the same alternating current as before the grid fault is fed into the grid.
    Zero Current: During the grid fault the alternating current is adjusted/reduced to zero. The inverter is not disconnected from the grid.
    Active Nominal Based: during the grid fault a pure symmetrical reactive current (positive-sequence system) is fed into the grid for dynamic grid backup. The active current is adjusted to zero. Calculation according to the formula.
    Active Boundary Based: Currently not supported
    Active Unbalanced Compensation Current (Act. UBCC): During the grid fault any asymmetrical reactive current (positive-sequence system and negative-sequence system) is fed into the grid for optimum phased grid backup. If technically possible, an additional active current is fed into the grid. Calculation according to the formula.
    R1/2/3 Detection Mode (only up to firmware version fro33430.upd)
    Mode like an FRT is identified
    Static: The calculated voltage RMS values are used for grid fault detection. A grid fault is identified when one or more grid voltage RMS values exceed or fall below the set static limit.
    Dynamic: is currently not supported
    PosNorm: The positive-sequence system and negative-sequence system voltages are used for grid fault detection. A grid fault is identified when the combination of positive-sequence system and negative-sequence system voltage exceeds or falls below the set static limit.
    Dynamic: Currently not supported
    R1/2/3 Detection Mode (Standard 50549)
    Determines which voltage system is used to detect a grid fault (voltage drop or voltage surge)
    0 = L-N Voltage
    1 = L-L Voltage
    2 = L-L and L-N Voltage
    R1/2/3 Static Threshold
    Static boundary to identify a LVRT or HVRT. Specification in % derived from nominal voltage.
    0 - 200%
    R1/2/3 Dynamic Limit (only up to firmware version fro33430.upd)
    Dynamic boundary to identify a LVRT or HVRT. Calculated based on the 1min floating average value of the grid voltage. Specification in % derived from nominal voltage.
    0 - 200%
    R1/2/3 k-Factor positive-sequence system
    Multiplication factor for calculating the compensation reactive current (positive-sequence system) during the grid fault. Only effective when Mode Active Nominal Based or Active UnbalancedCompensationCurrent (Act. UBCC) is set.
    R1/2/3 k-Factor negative-sequence system
    Multiplication factor for calculating the compensation reactive current (negative-sequence system) during the grid fault. Only effective when CalculationMode Active UnbalancedCompensationCurrent (Act. UBCC) is set.
    FRT Limit Compensation Current overexcited
    Relative limit of the dynamic additional reactive current during Voltage Ride Through for overexcited operation.
    FRT Limit Compensation Current underexcited
    Relative limit of the dynamic additional reactive current during Voltage Ride Through for underexcited operation.
    FRT Sudden Voltage Change Mode
    Activates / deactivates the detection of sudden voltage changes.
    FRT Sudden Voltage Change Insensitivity Range
    Percentage value that a sudden voltage jump must exceed or fall below in order to activate FRT mode.
    FRT Sudden Voltage Change Deactivation Time
    Timeout after detecting a sudden voltage jump, after which the inverter no longer runs in FRT mode and switches back to normal operation.
    1. Service Pro menu
    DC-Injection
    DC-I. InnerLimit Mode
    deactivates/activates the lower set limit values for DC Injection
    Selection options:
    OFF / ABSOLUTE / RELATIVE
    DC-I I.L. Absolute:
    Inner absolute DC Injection limit value
    0 - 10 A
    DC-I I.L. Relative:
    Inner relative DC Injection limit value based on the device nominal current
    0 - 10 %
    DC-I I.L. TripTime:
    Trip time in seconds for violation events when the inner absolute and relative limit value is exceeded
    0 - 10 s
    DC-I. OuterLimit Mode
    Selection options:
    DC-I O.L. Absolute:
    Outer absolute DC Injection limit value
    0 - 10 A
    DC-I O.L. Relative:
    Outer relative DC Injection limit value based on the device nominal current
    0 - 10 %
    DC-I O.L. TripTime:
    Trip time in seconds for violation events when the outer absolute and relative limit value is exceeded
    0 - 10 s
    1. Service Pro menu
    Ripple Control
    In some cases, the inverter may have an unpermissable influence (attenuation, amplification) on ripple control signals. Ripple Control can counteract this behaviour.
    Selection options:
    Mode / Signal Frequency / Grid Inductance
    Mode:
    On / Off
    Signal Frequency:
    Frequency with which the ripple control signal is sent
    Grid Inductance:
    Inductance of the connection point
    1. Service Pro menu
    I(delta gr.)F
    Compensation
    Selection options:
    Mode / Udc Link Voltage
    Mode:
    Using Mode the intermediate circuit voltage can be increased to reduce unavoidable leakage currents in the event of high module capacities to ground
    Udc Link Voltage:
    The intermediate circuit voltage increase is configured to a default value and can be adjusted when necessary using this value
    1. Service Pro menu
    Anti Islanding
    This function activates the stand-alone power system detection. If an undesirable stand-alone operation state is detected, the inverter is shut down.
    Selection options
    OFF / Sym_Asym / Sym
    OFF:
    no active stand-alone operation detection
    Sym_Asym:
    all types of stand-alone operation are detected; on three-phase devices also stand-alone operation on any individual phase.
    Sym:
    only symmetrical stand-alone operation states are detected; on three-phase devices only stand-alone operation on all three phases at the same time.
    On single-phase devices, there is no difference between the settings Sym_Asym and Sym.
    1. Service Pro menu
    Grid Quality Factor
    The preset value corresponds to the quality of the oscillating test circuit required by the relevant standard. The lower the value, the fewer disturbances to the grid. The higher the value, the greater the influence on the grid.
    Setting range
    0 - 10
    1. Service Pro menu
    This function allows the ROCOF (Rate of Change of Frequency) detection and switch-off to be activated and adjusted. In the event of frequency changes that are above a set limit and last longer than the set trip time, the inverter is shut down. ROCOF detection can be used as a passive stand-alone operation detection method.
    Selection options
    ROCOF On/off / ROCOF Limit / ROCOF TripTime
    ROCOF On/off
    for activating and deactivating the ROCOF functionality.
    When the ROCOF functionality is deactivated, a change in frequency does not cause a switch-off event.
    Default setting: Off
    ROCOF TripTime
    Operating time within which the device switches off in case of a too rapid change in frequency
    50 - 16,000 ms (default: 300 ms)
    ROCOF Limit
    Limit value for change in frequency that triggers a switch-off if ROCOF is activated.
    50 - 99,999 mHz/s (default: 2500 mHz/s)
    1. Service Pro menu
    Ramp Rate
    The ramp rates limit the maximum rate of change of the effective power that is triggered by external inputs (e.g. Modbus, DRM, PSC editor). If slower ramp rates are defined by the characteristic mode (e.g. P(U), P(F) or start-up), the lowest rate of change is used.
    The value 0 corresponds to the maximum rate of change.
    1. Service Pro menu
    Fail-Safe
    When starting up the system, the Datamanager and inverter control (ReCerbo PC board) should be synchronised so that both control components are fully ready for use. This allows many problems caused by different system statuses to be avoided.
    The ReCerbo blocks feed-in enabling until the Datamanager has fully booted up and all system-relevant services have started.
    For devices without a Datamanager, the setting must be Off, otherwise the device will not start. When using the dynamic feed-in limitation, the "Permanent" setting can be used to prevent unauthorised feed-in during the start-up phase or in the event of a Datamanager fault.
    Requirements:
    Datamanager version: 3.7.3-2
    ReCerbo version: 0.3.11.10
    Selection options
    DM FailSafe Mode / DM FailSafe Behaviour
    DM FailSafe Mode
    Off / Permanent
    Disconn.
    1. Service Pro menu
    Initial Start Time
     Grid monitoring time before the inverter is started up in s
    1 - 900 s
    Reconnect Time
    Grid monitoring time before the inverter is started up after a grid fault in s
    1 - 900 s
    1. Service Pro menu
    For switching on / off the Powerline Communication (PLC) signal (Keep Alive Signal) according to the SunSpec standard "Communication Signal for Rapid Shutdown".
    Selection options:
    Powerline COM Mode
    Powerline COM Mode
    SunSpec / Off
    1. Service Pro menu
    These parameters can be used to set the behaviour of the Arc Fault Circuit Interrupter at the DC terminals of the inverter. The DC Arc Fault Protection function protects against arcing faults and contact faults. Faults that occur in the current and voltage curve are continuously evaluated and the circuit is switched off when a contact fault is detected. This prevents overheating on faulty contacts and possible fires.
    Parameter
    Range of values
    Description
    "Arc Fault Protection Equipment (AFPE)"
    For activating and deactivating the Arc Fault Circuit Interrupter. The parameter "Automatic reconnects" is only considered when the "Arc Fault Detection (AFD)" is activated.
    Off
    Arcs are not detected.
    On
    The Arc Fault Circuit Interrupter is active.
    "Automatic Reconnects"
    If more arcs have been detected within 24 hours than are defined in "Automatic Reconnects", the inverter will not make any further attempt to start feeding energy into the grid.
    -1
    The 24-hour counter is deactivated. The inverter restarts feeding energy into the grid 5 minutes after each arc detected.
    0 - No Reconnection
    After an arc has been detected, no further attempt is made to start feeding energy into the grid and status code 240 is displayed.
    1 ‑ 4
    After a shutdown due to an arc, 1, 2, 3 or 4 attempts are made within 24 hours to restart feeding energy into the grid. After this number of attempts, no further attempt is made to start feeding energy into the grid and status code 240 is displayed.
    The country setup entered on the inverter ensures that the relevant operating modes and settings for local standards and guidelines are specified.
    However, in some situations it may be worthwhile to adapt the preset country-specific operating modes and settings to the local grid situation.
    This will help to ensure more reliable operation of the inverter in the grid, while enabling the inverter to actively support the public grid. For this purpose, the grid voltage and grid frequency must be within defined limits.
    The voltage and frequency stability can be actively influenced via the inverter by monitoring the feeding of effective power and reactive power into the grid.
    Simply decreasing the effective power in order to reduce high grid voltage levels can reduce the energy generated by the photovoltaic system.
    One alternative is to switch the reactive power between the inverter and the grid. Even though the reactive power is not consumed or converted into effective power and simply oscillates between the inverter and the grid, the current fed in will increase.
    Regardless of the active power and therefore regardless of the energy yield, switching the reactive power can cause the voltage to both rise and to fall:
    • In over-excited mode or capacitive mode, reactive power is supplied to the grid. The grid voltage rises.
    • In under-excited mode or inductive mode, reactive power is taken from the inverter. The grid voltage falls.
    Capacitive mode is shown on the inverter display by a positive sign +.
    Inductive mode is shown on the inverter display by a negative sign -.
    1. "Advanced Grid Features": Reactive Power Mode
    Reactive power mode is restricted by the maximum output current (maximum apparent power) as well as by the operational reactive power limits of the inverter:
    • cos phi = 0.85, Qrel = 53 % (Galvo)
    • cos phi = 0.70, Qrel = 71 % (Symo S, Symo M -8k2, Symo Hybrid, Primo -8k2, Primo US -8k2)
    • cos phi = 0.00, Qrel = 100 % (Symo M -20, Primo US -15, Eco, Symo US -24, Symo US (Eco)
    The figure below shows the potential operating range of the inverter. All valid operating points defined by effective power P and reactive power Q are within the grey area.
    under-excited (inductive)
    over-excited (capacitive)
    Q = Reactive power [VAr]
    P = Effective power [W]
    Sn = Nominal apparent power [VA]
    cos phi = power Pactor
    Qrel = Operative reactive power limit of the inverter [%]
    Example for Fronius Galvo
    For example, fixed values or curves can be specified within the operating range that define the reactive power response of the inverter. Reactive power operation is only possible when a DC supply is present.
    The following options for switching reactive power and for controlling the inverter are available:
    • Const. Cos φ
    • Const. Q Rel
    • Const. Q Abs
    • Ch Cos φ(P)
    • Ch Q (U)
    • Ch Q (P)
    Only one reactive power mode can be used at any one time to control the inverter.
    Const. Cos φ
    Constant specification of power factor cos φ
    Setting range:
    • -0.85 - +0.85 (Galvo)
    • -0.70 - +0.70 (Symo S, Symo M -8k2, Symo Hybrid, Primo -8k2, Primo US -8k2)
    • -0.00 - +0.00 (Symo M -20, Primo US -15, Eco, Symo US -24, Symo US (Eco)
    Example:
    cos φ = -0.9
    cos φ = Power factor
    Const. Q Rel
    Constant specification for relative reactive power in % in relation to the nominal apparent power of the inverter
    Setting range:
    • -53 - 0 - +53 (Galvo)
    • -71 - 0 - +71 (Symo S, Symo M -8k2, Symo Hybrid, Primo -8k2, Primo US -8k2)
    • -100 - 0 - +100 (Symo M -20, Primo US -15, Eco, Symo US -24, Symo US (Eco)
    Example:
    Qrel = -32 %
    Sn = Projected apparent power [VA]
    Const. Q Abs
    Setting range: -n - 0 - +n [VAr]
    n = maximum reactive power that can be set depending on the respective inverter
    Example:
    Qrel = -n1 VAr
    Ch Cos φ (P)
    Specification of the power factor cos φ depending on effective power P
    The characteristic is defined by max. 4 characteristic points 0 - 1 - 2 - 3.
    The coordinates must be entered for the characteristic points on the 0 (x) axis and on the 1 (y) axis.
    • -0,85 - 1 - +0,85 a
    • -0,70 - 1 - +0,70 b,c,e,f,l
    • -0,00 - 1 - +0,00 d,g,h,i,j,k
    Characteristic point
    Coordinates
    Setting range
    0
    0-0 (x)
    P: 0 - 100 %
    0-1 (y)
    cos φ (see table)
    1-0 (x)
    P: 0 - 100 %
    1-1 (y)
    cos φ (see table)
    2-0 (x)
    P: 0 - 100 %
    2-1 (y)
    cos φ (see table)
    3-0 (x)
    P: 0 - 100 %
    3-1 (y)
    cos φ (see table)
    Axis
    Example:
    Curve defined by 4 characteristic points
    0: P = 15 %, cos φ = +0.85
    1: P = 25 %, cos φ = 1
    2: P = 45 %, cos φ = 1
    3: P = 90 %, cos φ = -0.90
    Apparent power limit
    Ch Q (U)
    Specification of relative reactive power depending on grid voltage
    The characteristic is defined by max. four characteristic points 0 - 1 - 2 - 3.
    • -53 - 0 - +53 a
    • -71 - 0 - +71 b,c,e,f,l
    • -100 - 0 - +100 d,g,h,i,j,k
    Coordinates
    Setting range
    0
    0-0 (x)
    U: 80 -120%
    0-1 (y)
    Q (see table)
    1-0 (x)
    U: 80 -120%
    1-1 (y)
    Q (see table)
    2-0 (x)
    U: 80 -120%
    2-1 (y)
    Q (see table)
    3-0 (x)
    U: 80 -120%
    3-1 (y)
    Q (see table)
    Axis
    Example:
    Characteristic defined by four characteristic points
    0: U = 95%, Q = 32%
    1: U = 97% Q = 0%
    2: U = 104%, Q = 0%
    3: U = 105%, Q = -32%
    (1)
    Ch Q (U) P-Lockout = 5%
    (2)
    Ch Q (U) P-Lockin = 30%
    (3)
    Ch Q (U) Cos. φ Min. = 0.9
    * Detail:
    Ch Q (P)
    Specification of relative reactive power depending on effective power
    • -53 - 0 - +53 a
    Coordinates
    Setting range
    0
    0-0 (x)
    P: 0 -100 %
    0-1 (y)
    Q (see table)
    1-0 (x)
    P: 0 -100 %
    1-1 (y)
    Q (see table)
    2-0 (x)
    P: 0 -100 %
    2-1 (y)
    Q (see table)
    3-0 (x)
    P: 0 -100 %
    3-1 (y)
    Q (see table)
    Axis
    Example:
    Characteristic defined by 4 characteristic points
    0: P = 0 %, Q = 0 %
    1: P  = 25 %, Q = 0 %
    2: P = 50 %, Q = 0 %
    3: P = 95 %, Q = -32 %
    The characteristic operating mode for switching reactive power can also be enabled or disabled using the Lock-In / Lock-Out parameters.
    If a defined starting threshold is exceeded (Lock-In), the characteristic operating mode is enabled and the inverter feeds in reactive power according to the relevant characteristic.
    If a defined starting threshold is undershot (Lock-Out), the characteristic operating mode is disabled regardless of whether another parameter has exceeded or is about to exceed the Lock-In threshold. Lock-Out takes priority over Lock-In.
    When the characteristic operating mode is disabled, reactive power is no longer fed into the grid.
    GFDPR = Grid Frequency Dependent Power Reduction
    When the GFDPR function is enabled and the defined grid frequency limit value is exceeded, the effective power is reduced according to a defined gradient.
    Once the grid frequency falls within the permitted frequency range again following successful power reduction, return to full power takes place depending on the country setup as follows:
    • GFDPR ON DisHyst mode
      The inverter increases the power from the current reduced value to the original value in accordance with the same gradient used for power reduction.
    • GFDPR ON mode
      The inverter will not increase the power to the original value until the frequency is in the command value range for a specific length of time.
    1. "Advanced Grid Features": GFDPR - Grid frequency-dependent power reduction P(f)
    • GFDPR ON mode
    GFDPR ON/OFF = On DisHyst
    with Derating Gradient
    (1)
    Enable Limit = 50.3 Hz
    (2)
    Derating Gradient = 84 %/Hz
    (3)
    Enable Limit UnderF.[Hz]
    (4)
    Derating Gradient U.F. [%/Hz]
    Pnom
    Nominal output
    Pm
    Actual power at the moment the limit value is exceeded
    Pred
    Reduced power
    with Stop Frequency
    (1)
    (2)
    Stop Frequency = 50.5 Hz
    (3)
    Enable Limit UnderF. = 49.8 Hz
    (4)
    Stop Frequency U.F. = 49.7 Hz
    Pnom
    Nominal output
    Pm
    Pred
    Reduced power
    GFDPR ON/OFF = On
    (1)
    (2)
    (3)
    Frequency Test Time = 30 s
    (4)
    Disable Limit Max. = 50.1 Hz
    (5)
    Disable Limit Min. = 49.8 Hz
    Pnom
    Nominal output
    Pm
    Pred
    Reduced power
    Example:
    Alt. Ret. Grad Thr. = 25 %
    Pnom
    Nominal output
    Pm
    Pred
    Reduced power
    (1)
    Derating Gradient
    (2)
    Frequency Test Time
    (3)
    Return Gradient 1
    (4)
    alt. Return Grad. 1
    (5)
    Alt. Ret. Grad Thr.
    Pm - Pred </= 25 %
    (6)
    Alt. Ret. Grad Thr.
    Pm - Pred > 25 %
    (7)
    Initial Delay
    At Pred the grid frequency returns to the permissible range.
    After the end of the delay time (2) specified by the standard, the power is increased by one of the following gradients to the output value Pm:
    Curve 1 - black
    The difference between the current power Pm and the reduced power Pred is less than or equal to the value entered for "Alt. Ret. Grad Thr." of 25 % (5).
    This increases the power by the nominal output related gradient "Return Gradient 1" (3) to the output value Pm.
    Curve 2 - grey
    The difference between the current power Pm and the reduced power Pred is greater than the value entered for "Alt. Ret. Grad Thr." of 25 % (5).
    This increases the power by the alternative difference power related gradient "alt. Return Grad. 1" (4) to the output value Pm.
    Pnom
    Nominal output
    Pm
    Actual power
    Pred
    Reduced power
    (1)
    Derating Gradient
    (2)
    Frequency Test Time
    (3)
    Return Gradient 1
    (4)
    Return Gradient 2
    (5)
    Initial Delay
    Settings:
    Use Return Grad. 2 = 1
    Return Gradient 2 = n %/s
    n ... value
    After the end of the delay time (2) specified by the standard, the power is increased by a nominal output related gradient (3) to the output value Pm.
    The power is then increased by one of the other nominal output related gradients (4) to the device nominal output Pnom.
    GVDPR = Gradual Voltage Dependent Power Reduction
    (power reduction dependent on the grid voltage)
    To largely prevent the inverter being switched off when the grid voltage is too high due to the requirements of various standards and directives, the GVDPR function can be used to slightly reduce the power of feeding in, in accordance with the highest phase voltage.
    This makes the yield losses less than they would be if the inverter was completely switched off.
    (1)
    Enable Limit [V]
    (2)
    Derating Gradient [%/V]
    (3)
    Enable Limit UnderV. [V]
    (4)
    Derating Gradient UnderV. [%/V]
    Pnom
    Nominal output
    Pm
    Unom
    Nominal voltage
    Power waveshape depending on grid voltage
    1. "Advanced Grid Features": GVDPR Grid voltage-dependent power reduction P(U)
    (1)
    Enable Limit [V]
    (2)
    (3)
    (4)
    Pnom
    Nominal output
    Pm
    Unom
    Nominal voltage
    VFRT = Voltage Fault Ride Through
    Function for dynamic grid backup during grid faults (voltage drops or rises) in the grid in order to prevent an undesirable shutdown of the feed-in power and the collapse of the system. There are a range of selection options for the function (type of error detection, adjusting the fault limits, optional feeding in of additional compensation reactive currents, etc.).
    Inverters with the VFRT function activated are not disconnected from the grid during grid faults (the duration of such grid faults can, depending on the grid voltage change, last between a few 100 milliseconds and a few minutes) and can therefore immediately feed the full power into the grid when the fault is resolved, without having to wait for the restart time.
    If required by the electricity retailer (or by a country-specific standard), by adjusting the VFRT function accordingly, the inverter can feed an additional compensation reactive current into the grid during the grid fault for targeted grid backup.
    The following variants can also be set:
    • Zero Current: during the grid fault the fed-in alternating current is adjusted to zero.
    • Passive: during the grid fault the alternating current is adjusted to the value before the fault (pre-fault current).
    Example of a possible VFRT specification:
    Voltage drop up to 0% Uc lasting up to 150 ms
    (2) = Time at which failure occurs
    Uc = Nominal voltage
    U  = voltage measured at the terminals of the inverter
    Example of VFRT - Voltage waveshape limiting curves
    • If the voltage is above the limit line (1), the inverter must not switch off.
      Any feeding in of an additional compensation current during the grid fault must be agreed with the grid operator.
    • If the measured voltage is below the limit line (1), the inverter can be disconnected from the grid. The inverter is safely disconnected from the grid according to the set operating times for the inner and outer voltage limit values.
    When the VFRT function is disabled, the inverter does not feed in any dynamic reactive current if the voltage drops rapidly.
    1. "Advanced Grid Features": VFRT - Dynamic grid backup during temporary drops in grid voltage
    VFRT - Regions
    A number of countries differentiate between different grid fault regions, such as the USA and Germany. This means, depending on the extent of the voltage change, a different alternating current calculation method must be used.
    This can be achieved by setting what are known as the VFRT regions accordingly. Three individual regions can be configured. A detection limit, a fault detection mode and a current calculation mode can be selected for each region.
    The detection limit for a region is a relative voltage level and is specified in percent derived from the AC nominal voltage. Values greater than 100% are handled as HVRT (High Voltage Ride Through), values lower than 100% are handled as LVRT (Low Voltage Ride Through).
    The following settings can be made for each region
    • FRT-Mode (0=off, 1=passive, 2 = zero current, 3 = active nominal based, 4 = active boundary based, 5 = Active Unbalanced Compensation Current)
    • Detection Mode (0 = static, 1 = dynamic, 2 = Uac Pos Norm)
    • Static Limit (voltage in % derived from nominal voltage)
    • Dynamic Limit (voltage in % derived from the nominal voltage)
    • k factor positive sequence for active mode
    • k factor negative sequence for active mode
    If the measured grid voltage is within one of the marked areas (regions), the respective current calculation mode is activated.
    VFRT - K-Factor
    The graph describes the characteristic of how an additional compensation reactive current is fed into the grid depending on the measured grid voltage.
    The upper voltage limit at +10% is the detection limit for VFRT-Region1 (HVRT), the lower voltage limit at -10% is the detection limit for VFRT-Region2 (LVRT1).
    Between these two limits (normal voltage range) no grid fault is detected and therefore no additional compensation reactive current is fed into the grid. If the measured grid voltage is below or above the normal voltage range, a compensation reactive current depending on the K-Factor is fed into the grid.
    If there is a voltage drop (LVRT), the inverter is overexcited and as a result supports the grid voltage. In the event of overvoltage (HVRT), the inverter is underexcited and as a result counters a voltage rise.
    The graph and reactive current characteristic apply to compensation reactive currents in the positive-sequence system and negative-sequence system.
    The K-Factor and the upper and lower voltage limits define the voltage level at which feeding in of reactive current is activated and also how high this current value should be.
    When the K-Factor = 0, the inverter does not feed any additional reactive current into the grid in the event of a voltage drop.
    The K-Factor can be determined from the following graph:
    The following calculation rules apply both to positive-sequence system and negative-sequence system compensation reactive currents:
    Un
    Nominal voltage of the inverter
    U0
    Voltage measured at the inverter before the grid fault (pre-fault voltage)
    U
    In
    Nominal current of the inverter
    IB0
    Fed-in reactive current before the grid fault
    IB
    Resulting total reactive current during the grid fault
    Δ IB
    Additional fed-in compensation reactive current during the grid fault
    Δ U = U - U0 ; Δ IB = IB - I0
    (1)
    DeadBand Low
    (2)
    DeadBand High
    (3)
    Required additional reactive current
    (4)
    Voltage drop or voltage rise
    Reactive current droop:
    k =
    Δ IB / In
    Δ U  / Un
    Typical example of set values from the graph:
    Umax = 110%
    Umin = 90%
    k = 2.0