Indicates immediate danger.
This may result in serious injury and damage to property.
Commissioning of the hybrid system may only be carried out by trained personnel in accordance with the technical regulations.
Read the Installation and Operating Instructions before installing and commissioning the equipment.
A surge protection device must only ever be installed and connected by a qualified electrical engineer.
Follow the safety rules.
Ensure that both the AC side and the DC side of the inverter are de-energised before carrying out any installation and connection work.
Fire prevention
Danger due to poor or unprofessional installation.
This may result in damage to inverters and other live photovoltaic system components.
Poor or unprofessional installation can cause overheating of cables and terminal connections and result in arcs. These can cause heat damage, which in turn may lead to fires.
Observe the following when connecting AC and DC cables:
Tighten all terminals to the torque specified in the Operating Instructions
Tighten all grounding terminals (PE / GND), including free ones, to the torque specified in the Operating Instructions
Do not overload cables
Check cables for damage and verify that they are laid correctly
Take note of the safety instructions, Operating Instructions and any local connection regulations
Using fastening screws, always screw the inverter firmly to the mounting bracket to the torque specified in the Operating Instructions.
Ensure that the fastening screws are tight before starting the inverter!
Note! Fronius will not accept any costs associated with production downtimes, installer costs, etc., that may arise as the result of a detected arc and its consequences. Fronius accepts no liability for fires that can occur despite the presence of the integrated arc detection/extinguishing system (e.g. fires caused by a parallel arc).
Note! After an arc has been detected, the entire photovoltaic system must be checked for possible damage before resetting the inverter.
Observe the manufacturer's connection, installation and operating instructions at all times. To reduce the hazard potential to a minimum, perform all installation and connection work carefully according to the instructions and regulations.
Refer to the device Operating Instructions / Installation Instructions for the tightening torques to be used at the relevant terminal connections.
Fronius shall not be liable for any damage resulting from such action.
No warranty claims will be entertained.
When designing the photovoltaic system, ensure that all of its components are operated within their permitted operating ranges at all times.
Observe all the measures recommended by the solar module manufacturer to ensure that the solar module retains its properties in the long term.
Observe the stipulations of the power supply company concerning energy fed into the grid, emergency power mode and the operation of storage systems.
The Fronius Symo Hybrid is a grid-connected inverter with an emergency power function – it is not a stand-alone inverter. The following restrictions must therefore be observed in emergency power mode:
| The inverter is suitable for indoor installation. | |
| The inverter is suitable for outdoor installation. Because of its IP 65 protection class, the inverter is resistant to water jets from any direction and can also be used in damp environments. | |
| In order to minimise the heating up of the inverter, do not expose it to direct insolation. Install the inverter in a protected location, e.g. in the vicinity of the solar modules or beneath the eaves. | |
| UDCmax at an altitude of: IMPORTANT! The inverter must not be installed or used at altitudes above 3400 m. | |
| Do not install the inverter in:
| During certain operating phases the inverter may produce a slight noise. For this reason it should not be installed in an occupied living area. | |
Install only on a solid surface | ||
Max. ambient temperatures: -13 °F / +140 °F (-25 °C / +60 °C) | ||
Relative humidity: 0-100% | ||
The airflow within the inverter is from the right to the top (cold air taken in from the right, hot air dissipated out of the top). | ||
If the inverter is installed in a switch cabinet or a similar sealed area, then forced-air ventilation must be provided to ensure adequate heat dissipation. | ||
If the inverter is to be installed on the outer wall of a cattle shed, maintain a minimum all-round clearance of 2 m between the inverter and all ventilation and other openings in the building. |
| The inverter is suitable for vertical installation on a vertical wall or column. | |
| The inverter is suitable for a horizontal installation position. | |
| The inverter is suitable for installation on a sloping surface. | |
| Do not install the inverter on a sloping surface with its connection sockets at the top. | |
| Do not install the inverter at an angle on a vertical wall or column. | |
| Do not install the inverter horizontally on a vertical wall or pillar. | |
| Do not install the inverter on a vertical wall or pillar with its connection sockets facing upwards. | |
| Do not install the inverter overhanging with the connection sockets at the top. | |
| Do not install the inverter overhanging with the connection sockets at the bottom. | |
| Do not install the inverter on the ceiling. |
Danger due to residual voltage in capacitors.
This may result in an electric shock.
Wait for the capacitors to discharge. The discharge time is five minutes.
Danger due to dirt or water on the terminals and contacts of the inverter's connection area.
This may result in damage to the inverter.
When drilling, ensure that terminals and contacts in the connection area do not become dirty or wet.
The mounting bracket without a power stage set does not conform to the protection class of the inverter as a whole, and therefore must not be installed without a power stage set.
The mounting bracket should be protected from dirt and moisture during installation.
Degree of protection IP 20 applies to the mounting bracket with no inverter and the venting duct.
Important! Different fixings may be required to fit the mounting bracket depending on the type of underlying surface. Fixings are therefore not included in the scope of supply of the inverter. The installer is responsible for selecting the right type of fixing.
To install the inverter, the manufacturer recommends the use of steel or aluminium screws with a diameter of 6 - 8 mm.
Danger from inadequate ground conductor connection.
The housing screws provide a suitable ground conductor connection for grounding the housing and must NOT be replaced by any other screws that do not provide a reliable ground conductor connection.
Note! When fitting the mounting bracket to the wall, ensure that the mounting bracket does not become warped or deformed.
Note! When mounting the mounting bracket on the wall, ensure that the mounting bracket does not become warped or deformed.
When installing the inverter on a mast or support, Fronius recommends the "Pole Clamp" kit from Rittal GmbH (order no. SZ 2584.000).
This kit enables the inverter to be installed on round or rectangular masts with the following diameters: Æ from 40 to 190 mm (round mast), ÿ from 50 to 150 mm (rectangular mast)
The mounting bracket must be affixed at a minimum of four points.
Incorrect operation or poorly executed work can cause serious injury or damage.
Commissioning of the hybrid system may only be carried out by trained personnel in accordance with the technical regulations. Read the Installation and Operating Instructions before installing and commissioning the equipment.
Danger due to grid voltage and DC voltage from solar modules that are exposed to light.
Ensure that both the AC side and the DC side of the inverter are de-energised before carrying out any connection work.
Only an authorised electrical engineer is permitted to connect this equipment to the public grid.
Danger due to grid voltage and DC voltage from solar modules or battery.
The DC main switch is only to be used to de-energise the power stage set. The connection area is still live when the DC main switch is switched off.
Ensure that the power stage set and connection area are disconnected from one another before carrying out any maintenance or service tasks.
The power stage set is only to be disconnected from the mounting bracket once it is de-energised.
Maintenance and servicing in the power stage set of the inverter must only be carried out by Fronius-trained service technicians.
Risk of damage to the inverter as the result of incorrectly tightened terminals.
Incorrectly tightened terminals can cause heat damage to the inverter that may result in a fire. When connecting AC and DC cables, ensure that all the terminals are tightened to the specified torque.
To provide the best possible grid monitoring, the resistance in the leads to the AC-side terminals should be as low as possible.
The following types of AC cable can be connected to the AC terminals of the inverter:
The AC-side terminals are suitable for connecting single-wire, round aluminium cables. Because of the formation of a non-conductive oxide layer due to the reaction of aluminium with air, the following points must be considered when connecting aluminium cables:
Always follow the cable manufacturer instructions when using aluminium cables.
When designing cable cross-sections, take local regulations into account.
Connection conditions:
IMPORTANT! Do not use brushes, files or emery paper, as the aluminium particles get trapped and can be transferred to other conductors.
IMPORTANT!Repeat the procedure if the cable has been disconnected and is to be re-connected.
For a standard M32 metric screw joint with a reducer:
Cable diameter from 7-15 mm
When using an M32 metric screw joint (reducer removed):
cable diameter from 11-21 mmWith cable diameters greater than 21 mm, the M32 screw joint must be replaced by an M32 screw joint with a larger clamping area – item number: 42,0407,0780 – strain-relief device M32 x 1.5 KB 18–25.
IMPORTANT! The PE ground conductor of the AC cable must be laid in such a way that it is the last to be disconnected in the event that the strain-relief device should fail.
This can be ensured, for example, by making it somewhat longer and by laying it in a loop.
If AC cables are laid over the shaft of the DC main switch or across the connection block of the DC main switch, they may be damaged when the inverter is swung in, or they may even prevent the inverter from being swung in.
IMPORTANT! Do not lay AC cables over the shaft of the DC main switch or across the connection block of the DC main switch.
If overlength AC or DC cables are to be laid in loops in the connection area, attach the cables with cable ties to the eyelets provided on the top and bottom of the connection block.
Inverter | Phases | AC output | Maximum output overcurrent protection | Recommended fuse rating |
Symo Hybrid 3.0 | 3 + N | 3000 W | 4 x C 25 A | 4 x C 16 A |
Symo Hybrid 4.0 | 3 + N | 4000 W | 4 x C 25 A | 4 x C 16 A |
Symo Hybrid 5.0 | 3 + N | 5000 W | 4 x C 25 A | 4 x C 16 A |
Local regulations, the electricity retailer or other factors may require an earth-leakage circuit breaker in the AC connection lead.
For this situation, a type A earth-leakage circuit breaker with a tripping current of at least 100 mA is generally adequate. In particular cases, and depending on local factors, however, the type A earth-leakage circuit breaker may trip at the wrong time. For this reason, Fronius recommends that an earth-leakage circuit breaker that is suitable for frequency converters should be used.
Risk of damage to inverter from overload.
The maximum amperage when connecting to a single DC terminal is 32 A.
Connect the DC+ and DC- cables to the DC+ and DC- terminals on the inverter, taking care to ensure that the polarity is correct.
The maximum DC input voltage must not exceed 1000 V DC.
The solar modules connected to the inverter must comply with the IEC 61730 Class A standard.
When photovoltaic modules are exposed to light they supply current to the inverter.
To enable suitable solar modules to be chosen and to use the inverter as efficiently as possible, it is important to bear the following points in mind:
Note! Before connecting up the solar modules, check that the voltage for the solar modules specified by the manufacturer corresponds to the actual measured voltage.
Max. cross-section of each DC cable:
10 mm²
Min. cross-section of each DC cable:
2.5 mm²
The DC cables can be connected to the DC terminals without ferrules.
To ensure effective strain relief of the solar module strings, only use cables with identical cross-sections.
In the case of a DC cable with a cross-section of 16 mm², ferrules can be either not used or only used to a limited extent depending on the type of ferrule and crimping.
The DC-side terminals are suitable for connecting single-wire, round aluminium cables. Because of the formation of a non-conductive oxide layer due to the reaction of aluminium with air, the following points must be considered when connecting aluminium cables:
Note! Always follow the cable manufacturer instructions when using aluminium cables.
Note! When designing cable cross-sections, take local regulations into account.
IMPORTANT! Repeat the procedure if the cable has been disconnected and is to be re-connected.
The hybrid inverter is a transformerless device. The individual poles of the solar modules must not be grounded.
Risk of possible damage to the inverter!
Check the polarity and voltage of the solar module strings before making the connection. The voltage must not exceed the following values:
when installed between 0 and 2000 m above sea level: 1000 V
when installed between 2001 and 2500 m above sea level: 900 V
when installed between 2501 and 3000 m above sea level: 815 V
when installed between 3001 and 3400 m above sea level: 750 V
Only break out as many target break points as there are cables.
If DC cables are laid over the shaft of the DC main switch or across the connection block of the DC main switch, they may be damaged when the inverter is swung in or they may even prevent the inverter from being swung in.
IMPORTANT! Do not lay DC cables over the shaft of the DC main switch or across the connection block of the DC main switch.
IMPORTANT! Operating the inverter with a free broken-out option card slot is not permitted.
An appropriate blanking cover (42,0405,2020) to cover the slot is available from Fronius as an option.
IMPORTANT! If data communication cables are wired into the inverter, observe the following points:
The terminating resistor must be set according to how the individual devices are configured (see diagram below).
*) The R 120 Ohm terminating resistor is supplied with the Fronius Smart Meter A DC connection and ground connection must also be established between the battery and the inverter. The connection of the individual lines was illustrated in the preceding chapters. The installer is responsible for choosing the cables. |
Cabling variant 1:
Cabling variant 2:
The side sections of the housing lid are designed to function as holding and carrying handles.
Note! For safety reasons, the inverter is fitted with a latch that prevents the inverter from being swung into the mounting bracket unless the DC main switch is switched off.The fastening screws in the data communication area of the inverter are used for securing the inverter to the mounting bracket. Correctly tightened fastening screws are a prerequisite if proper contact is to be established between the inverter and mounting bracket.
Danger due to incorrectly tightened fastening screws.
This may result in arcs occurring when the inverter is in operation, which may lead to fire.
Always use the specified torque when tightening the fastening screws.
When starting the inverter for the first time, it is necessary to select various setup settings.
If setup is interrupted before it is complete, it can be restarted by means of an AC reset. An AC reset can be carried out by switching the automatic circuit breaker off and on again.
The country setup can only be set when using the inverter for the first time. If the country setup needs to be changed at a later date, please contact your Technical Support team.
* Country setup examples | ||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||||
If there are additional inverters in the system, these should be installed outside of the emergency power circuit, but within that for the Fronius Smart Meter.
1Press the "Menu" key | ||
| The menu level appears. 2Press the unassigned "Menu / Esc" key 5 times |
'Access Code' is displayed in the 'CODE' menu; the first digit starts flashing. | ||
3Enter the access code for the CONFIG menu: Use the 'Up' and 'Down' keys to select a value for the first digit of the code | ||
4Press the 'Enter' key |
The second digit flashes. | ||
5Repeat steps 3 and 4 for the second, third, fourth and fifth digits of the access code until... | ||
the selected code starts flashing. | ||
6Press the 'Enter' key | ||
The first parameter of the CONFIG menu is displayed |
1Use the 'Up' and 'Down' keys to select the Alternative (emergency power) setup | ||
2Press the 'Enter' key |
The Fronius Ohmpilot is not suitable for emergency power mode.
If a Fronius Ohmpilot is used, it should be installed outside of the emergency power circuit
Danger from incorrect operation
Do not use the functions described here until you have fully read and understood the Operating Instructions of every system component:
Do not use the functions described here until you have read and understood all the safety rules.
IMPORTANT! Knowledge of networking systems is required in order to install Fronius system monitoring.
IMPORTANT! Starting up the Fronius system monitoring function for the first time is made considerably easier with the Fronius Solar.start app. The Fronius Solar.start app is available in the respective app stores.
Or visit |
https://wizard.solarweb.com to select the desired menu item | |
IMPORTANT! In order to establish a connection to Fronius system monitoring, the end device in question (e.g. laptop, tablet, etc.) must be set up as follows:
The inverter establishes the WLAN access point. The WLAN access point remains open for 1 hour.
Installation using the Solar.start app 2Download the Fronius Solar.start App 3Run the Fronius Solar.start app |
| Installation using a web browser 2Connect the end device to the WLAN access point SSID = FRONIUS_239.xxxxx (4-8 digits)
3Enter the following in the browser: http://datamanager or 192.168.250.181 (IP address for WLAN connection) or 169.254.0.180 (IP address for LAN connection) |
The Setup wizard start page is displayed.
If you run the technician wizard, always remember to make a note of the assigned service password. This service password is required to enter settings in the "System overview" and "DNO Editor" menus as well as for advanced battery settings.
If the technician wizard is not run, no specifications regarding power reduction are set and hybrid mode is not possible (charging and discharging of the battery)
Danger of deep discharge of an unactivated battery
This may result in permanent damage to the battery.
The Solar Web wizard needs to be run in order to activate the battery and, if necessary, the Smart Meter.
The Fronius Solar.start homepage
or
the Fronius system monitoring web page is displayed.
The solar web wizard consists of 5 steps:
1. General
General system data (e.g. system name) is entered here
2. Service password
Enter (and make a note of) the service password
3. IO assignment
Settings for the IO interface are entered (see also "Fronius Energy Package - IO assignment" Operating Instructions)
4. System overview
Settings for the entire PV system are entered (see also "Fronius Energy Package - System overview" Operating Instructions)
5. Dynamic power
Settings for dynamic power reduction are entered (see also "Fronius Energy Package - Dynamic power reduction" Operating Instructions)
Once you have worked your way through the Solar Web wizard, an automatic process is triggered to calibrate all the components. This involves charging the Fronius Solar Battery fully. After that, the system automatically starts in the set operating mode.
This calibration charging process is also performed automatically during actual operation after a number of charging and discharging cycles. When this calibration charge is performed depends on a number of different factors, such as the average state of charge or the energy throughput through the battery. The time can therefore vary depending on the time of year as well.
If the "permit battery charging from PSC grid" setting is deactivated, this calibration charging process relies exclusively on energy from the photovoltaic system when operating under normal conditions. Depending on the insolation conditions and size of the systems concerned, the charging process can take a very long time.
If the "permit battery charging from PSC grid" setting is activated, the calibration charging process is performed by drawing a constant current from the photovoltaic system and DSO (distribution system operator) grid.
IMPORTANT! The automatic process for fully charging the battery may result in energy being drawn from the DSO grid. The process can take several hours and cannot be aborted.
Note! When installed outdoors in a horizontal position: once a year, check that all screw joints are tight!
Maintenance and servicing may only be carried out by Fronius-trained service technicians.
Clean the inverter as required with a damp cloth.
Do not use cleaning agents, abrasives solvents or similar to clean the inverter.