Fronius LogoFronius Mobile Logo
en
      Operating instructionsFronius Primo GEN24 7.7 - 10.0 kW 208 - 240 / 7.7 - 10.0 kW 208 - 240 Plus
    • General information
      • Safety information
        • Safety
        • Explanation of warnings and safety instructions
        • General
        • Environmental conditions
        • Electromagnetic fields
        • EMC measures
        • Backup power
        • Ground conductor
      • Protection of people and equipment
        • Rapid shutdown
        • Power Line Communication (PLC) transmitter
        • Additional external AC and/or DC disconnect
        • WSD (wired shutdown)
        • RCMU
        • Insulation Monitoring
        • AFCI - Arc Fault Circuit Interrupter (Arc Guard)
        • Standby state
        • Surge protection device
      • General
        • Information on the device
        • How information is presented in the document
        • Qualified personnel
        • Data security
        • Privacy policy
        • Copyright
        • Territorial Limitations
      • Fronius Primo GEN24 208 - 240
        • Function overview
        • Scope of supply
        • Fronius UP
        • Intended use
        • Thermal concept
        • Fronius Solar.web
        • Local communication
      • Different operating modes
        • Operating modes - Explanation of symbols
        • Operating mode - Inverter with Smart Meter
        • Operating mode - Inverter with battery and several Smart Meters
        • Operating mode – Inverter with battery, AC-coupled to another inverter
        • Operating mode - Inverter with battery and backup power function
        • Operating mode - Inverter with battery, additional inverter, and backup power function
        • Energy flow direction of the inverter
        • Operating states (only for battery systems)
      • Energy-saving mode
        • General
        • Switch-off conditions
        • Switch-on conditions
        • Special case
        • Indication of energy saving mode
      • Suitable batteries
        • General
        • Limitations in operation
      • Operating controls and connections
        • Connection area
        • Connection area divider
        • Ground electrode terminal
        • DC disconnector
        • Data communication area
        • Button functions and LED status indicator
        • Schematic internal wiring of IOs
      • Manual system start
        • Requirements
        • Notification of system shutdown
        • Manual battery start after system shutdown
        • Starting backup power operation after a system shutdown
    • Backup power
      • PV Point (OP)
        • Explanation - PV Point (OP)
        • PV Point (OP)
        • PV Point Comfort
      • Essential Backup
        • Prerequisites for backup power mode
        • Transitioning from grid power feed operation to backup power mode
        • Transitioning from backup power mode to grid power feed operation
        • Backup power and energy saving mode
    • Installation
      • General
        • Quick-fastener system
      • Installation location and position
        • Choosing the location of the inverter
        • Installation position of the inverter
      • Knockouts
        • Preparing knockouts for connection
      • Installing the mounting bracket and attaching the inverter
        • Selecting the mounting material
        • Properties of the mounting bracket
        • Do not deform the mounting bracket
        • Fitting the mounting bracket to a wall
        • Attaching the mounting bracket to mounting rails
        • Attaching the inverter to the mounting bracket
      • Requirements for connecting the inverter
        • Different cable types
        • Permitted cables for the electrical connection
        • Permitted cables for the data communication connection
        • Cable diameter for push-in terminals
        • Maximum alternating current fuse protection
      • Connecting the inverter to the public grid (AC side)
        • Safety
        • Suitable AC grids
        • Connecting the inverter to the public grid (AC side)
      • Connecting solar module strings to the inverter
        • General information about PV modules
        • Safety
        • PV Generator, general
        • Module array configuration 7.7 ‑ 10.0 kW
        • Connecting solar module strings to the inverter
      • Connecting the battery to the inverter
        • Safety
        • Connecting the battery on the DC side
      • Connecting backup power - PV Point (OP)
        • Safety
        • Connecting backup power - PV Point (OP)
        • Testing backup power mode
      • Connecting the data communication cables
        • Modbus participants
        • Routing data communication cables
        • Connecting the battery communication cable
        • Terminating resistors
        • Installing the WSD (wired shutdown)
      • Closing and commissioning the inverter
        • Closing the inverter's connection area/housing cover, and commissioning
        • Starting the inverter for the first time
        • Installation with the app
        • Installation with the browser
      • De-energizing the inverter and switching it back on
        • De-energizing the inverter and switching it back on
    • Settings – User interface of the inverter
      • User settings
        • User login
        • Selecting languages
      • Device configuration
        • Components
        • Functions and
          I/Os
        • Inverter
      • Energy management
        • Energy management
        • Examples - Time-dependent battery control
        • Permitted battery control regulations
        • PV power reduction
        • Load management
      • System
        • General
        • Update
        • Setup wizard
        • Restoring factory settings
        • Configuration Report
        • Event log
        • Information
        • License Manager
        • Licensing
        • Support
      • Communication
        • Network
        • Modbus
        • Cloud control
        • Fronius Solar API
      • Safety and grid requirements
        • Country setup
        • Requesting inverter codes in Solar.SOS
        • Absolute Generation Limit
        • ESS Modes (UL3141)
        • Feed-in limit
        • Dynamic feed-in limitation with multiple inverters
        • I/O Power Management
        • Connection diagram - 4 relays
        • I/O power management settings - 4 relays
        • Connection diagram - 3 relays
        • I/O power management settings - 3 relays
        • Connection diagram - 2 relays
        • I/O power management settings - 2 relays
        • Connection diagram - 1 relay
        • I/O power management settings - 1 relay
    • Options
      • PV Point Comfort
        • Safety
        • Scope of supply
        • De-energizing the inverter
        • Install PV Point Comfort
        • Starting up the inverter
        • Configuring the PV Point Comfort
        • Testing backup power mode
    • Appendix
      • Service, maintenance and disposal
        • General
        • Cleaning
        • Maintenance
        • Safety
        • Operation in dusty environments
        • Disposal
      • Warranty provisions
        • Warranty
      • Status codes and remedy
        • Display
        • Status codes
      • Technical data
        • Fronius Primo GEN24 7.7 208 - 240 / 7.7 208 - 240 Plus
        • Technical data for Fronius Primo GEN24 10.0 208 - 240 / 10.0 208 - 240 Plus
        • WLAN
        • Explanation of footnotes
        • Integrated DC disconnector
    • System circuit diagrams
      • Fronius Primo GEN24 and RENON Xtreme HV1.0
      • Fronius Primo GEN24 with two RENON Xtreme HV1.0 connected in parallel
      • Fronius Primo GEN24 with three RENON Xtreme HV1.0 connected in parallel
    • Circuit diagrams—PV Point
      • Emergency power terminal—PV Point (OP)
      • PV Point Comfort
    • Dimensions of the inverter
      • Fronius Primo GEN24 7.7 - 10.0 208-240
    • 022-10062026

    Fronius Primo GEN24 7.7 - 10.0 kW 208 - 240 / 7.7 - 10.0 kW 208 - 240 Plus

    download
    Fitting the mounting bracket to a wall
    Connecting the inverter to the public grid (AC side)
    Connecting solar module strings to the inverter
    Routing data communication cables
    Installation with the app
    ContactImprintTerms of usePrivacy statementCookie policy
    © 2026 Fronius International GmbH
    © 2026 Fronius International GmbH
    ContactImprintTerms of usePrivacy statementCookie policy

    General information

    link_horizontalLink copied

    Safety information

    Safety

    IMPORTANT!
    This unit must be operated in accordance with the technical specifications datasheet. This document is available on the corporate website of the manufacturer.

    CAUTION

    Danger from crushing due to the incorrect handling of attachments and connection parts.

    Injuries to limbs may result.

    To avoid muscle strain or injury, use proper lifting techniques and if required use a lifting aid.

    When lifting up, putting down, and attaching the inverter, use the integrated grips.

    When fitting any attachments, ensure that no limbs are located between the attachment and the inverter.

    Do not hold onto the terminals when locking and unlocking.

    1. General information

    Safety information

    link_horizontalLink copied

    Safety

    IMPORTANT!
    This unit must be operated in accordance with the technical specifications datasheet. This document is available on the corporate website of the manufacturer.

    CAUTION

    Danger from crushing due to the incorrect handling of attachments and connection parts.

    Injuries to limbs may result.

    To avoid muscle strain or injury, use proper lifting techniques and if required use a lifting aid.

    When lifting up, putting down, and attaching the inverter, use the integrated grips.

    When fitting any attachments, ensure that no limbs are located between the attachment and the inverter.

    Do not hold onto the terminals when locking and unlocking.

    1. General information
    2. Safety information

    Safety

    link_horizontalLink copied

    IMPORTANT!
    This unit must be operated in accordance with the technical specifications datasheet. This document is available on the corporate website of the manufacturer.

    CAUTION

    Danger from crushing due to the incorrect handling of attachments and connection parts.

    Injuries to limbs may result.

    To avoid muscle strain or injury, use proper lifting techniques and if required use a lifting aid.

    When lifting up, putting down, and attaching the inverter, use the integrated grips.

    When fitting any attachments, ensure that no limbs are located between the attachment and the inverter.

    Do not hold onto the terminals when locking and unlocking.

    1. General information
    2. Safety information

    Explanation of warnings and safety instructions

    link_horizontalLink copied

    Warnings are intended to warn people of possible injuries and to avoid personal injury and damage to the product. They relate to individual actions with and on the product.

    DANGER

    Indicates an immediately dangerous situation.

    Serious injury or death will result if the danger is not avoided.

    Action step to escape the situation.

    WARNING

    Indicates a potentially dangerous situation.

    Serious injury or death may result if the danger is not avoided.

    Action step to escape the situation.

    CAUTION

    Indicates a potentially dangerous situation.

    Minor or moderate injury may result if the danger is not avoided.

    Action step to escape the situation.

    NOTE

    Indicates a situation that may result in property damage.

    If the situation is not avoided, impaired work results, material damage to the product or other property are the possible consequences.

    Action step to avoid the situation.

    Safety instructions are designed to ensure safe product use. They are preventive and help to inform users about the fundamental risks involved when dealing with the product. They do not refer specifically to individual actions with and on the product.

    1. General information
    2. Safety information

    General

    link_horizontalLink copied
    This device has been manufactured with quality control procedures and is in compliance with established safety regulations. However, improper use or misuse may pose potential risks including:
    • Serious or fatal injury to the operator or third parties
    • Damage to the device and other material assets belonging to the property owner
    All personnel involved in commissioning, maintenance, and servicing of the device must:
    • Be suitably qualified to perform electrical work, as defined by the NFPA 70
    • Have knowledge of and experience in dealing with electrical installations
    • Have fully read and precisely followed these Operating Instructions

    All installations must comply with national and local electrical codes and standards.

    In addition to the Operating Instructions, all applicable local regulations regarding accident prevention and environmental protection must also be followed.

    All safety and danger notices on the device:
    • Must be kept in a legible state
    • Must not be damaged
    • Must not be removed
    • Must not be covered, pasted or painted over
    Only operate the device when all protection devices are fully functional. If the protection devices are not fully functional, there is a danger of:
    • Serious or fatal injury to the operator or third parties
    • Damage to the device and other material assets belonging to the property owner

    Any safety devices that are not fully functional must be repaired by an authorized specialist before the device is switched on.

    Never bypass or disable protection devices.

    For the location of the safety and danger notices on the device, refer to the chapter headed "Warning notices on the device" in the Operating Instructions for your device.

    Any equipment malfunctions which impair safety must be remedied before the device is turned on.

    1. General information
    2. Safety information

    Environmental conditions

    link_horizontalLink copied

    Operation or storage of the machine outside the stipulated area will be deemed as not in accordance with the intended purpose.

    For exact information on permitted environmental conditions, please refer to the technical data.

    1. General information
    2. Safety information

    Electromagnetic fields

    link_horizontalLink copied

    During operation, due to the high electrical voltages and currents, local electromagnetic fields (EMF) are generated. These occur in the immediate vicinity of the inverter and the Fronius system components. Electromagnetic fields are also present in the area of the PV modules and their supply lines.

    As long as the intended use and a minimum distance of 20 cm are observed, all limit values for human exposure are observed.

    If the limit values are complied with, according to current scientific knowledge, no negative health effects from EMF exposure are to be expected. For persons with prostheses1) or active physical aids2), there is a possible health risk in the vicinity of photovoltaic system components. To avoid possible health risks, consult with the responsible doctor.

    1) e.g., implants or metal parts

    2) e.g., pacemaker, insulin pump, hearing aid, etc.

    1. General information
    2. Safety information

    EMC measures

    link_horizontalLink copied

    In certain cases, even though a device complies with the standard limit values for emissions, it may affect the application area for which it was designed (e.g., when there is equipment that is susceptible to interference at the same location or if the site where the device is installed is close to either radio or television receivers). If this is the case, the operator is obliged to take action to rectify the situation.

    1. General information
    2. Safety information

    Backup power

    link_horizontalLink copied

    This system has backup power functions, which enable a replacement power supply to be established in the event of a failure of the public grid.

    Where an automatic backup power supply is installed, a backup power warning notice (https://www.fronius.com/en/search-page, item number: 42,0409,0275) must be fitted on the electrical distributor.

    Maintenance and installation work in the home network requires both disconnection on the utility side and deactivation of the replacement power mode by opening the integrated DC disconnector on the inverter.

    The function of the residual current devices for the backup power supply must be checked at regular intervals (according to the manufacturer's instructions), but at least twice a year.
    A description on how to perform the test operation can be found in the backup power checklist (https://www.fronius.com/en/search-page, item number: 42,0426,0365).

    Depending on the insolation conditions and the battery state of charge, the backup power supply is automatically deactivated and activated. This can cause the backup power supply to unexpectedly return from standby mode. Therefore, installation work can only be performed on the home network when the backup power supply is deactivated.

    Influencing factors on the total power in backup power mode:

    Reactive power
    Electrical loads with a power factor not equal to 1 also require reactive power in addition to effective power. The reactive power also loads the inverter. Therefore, to correctly calculate the actual total power, it is not the rated power of the load that is relevant, but the current caused by effective and reactive power.

    Devices with a high reactive power are mainly electric motors such as:

    • Water pumps
    • Circular saws
    • Blowers and fans

    High starting current
    Electrical loads that need to accelerate a large mass usually require a high starting current. This can be up to 10 times higher than the nominal current. The maximum current of the inverter is available for the starting current. Loads with starting currents that are too high therefore cannot be started/operated, even though the nominal output of the inverter suggests that they can. When dimensioning the backup power circuit, the connected load power and any starting current must also be taken into account.

    Devices with high starting currents are, for example:

    • Devices with electric motors (e.g., lifting platform, circular saws, planing bench)
    • Devices with large transmission ratio and flywheel mass
    • Devices with compressors (e.g., compressed air compressors, air conditioning systems)

    IMPORTANT!
    Very high starting currents can cause short-term distortion or a drop in output voltage. The simultaneous operation of electronic devices in the same backup power supply system should be avoided.

    IMPORTANT!
    The inverter may only be operated within the limits of its technical capabilities. Operation outside of its technical capabilities can cause the inverter to shut down.

    1. General information
    2. Safety information

    Ground conductor

    link_horizontalLink copied

    Connection of a point in the device, system, or installation to ground to protect against electric shock in the event of a fault. When installing an inverter from safety class 1 (see Technical data), a ground conductor connection is required.

    When connecting the ground conductor, ensure that it is secured to prevent unintentional disconnection. All of the points listed in the chapter headed Connecting the inverter to the public grid (AC side) on page (→) must be observed. When using cable glands, ensure that the ground conductor is last to be subjected to a load in the event of a failure of the cable gland. The respective national standards and regulations and requirements for minimum cross-section must be observed when connecting the ground conductor.

    1. General information

    Protection of people and equipment

    link_horizontalLink copied

    Rapid shutdown

    Two different types of rapid shutdown (RSD) can be triggered depending on the configuration and on-site installation:
    • Via external buttons: One or more external buttons can be installed on the WSD (wired shutdown) interface of the Data communication area on page (→). Pressing one of these buttons interrupts the communication from the inverter to the rapid shutdown devices attached to the PV modules, only if they correspond to the SunSpec standard for rapid shutdown. The terminals are discharged to < 30 VDC  and < 15 VAC  within 30 seconds after RSD initiation.
    • Via the loss of the grid connection: An automatic rapid shutdown can also occur if the grid connection is lost. The inverter identifies a failure of the grid connection and terminals are discharged to < 30 VDC  and < 15 VAC. The inverter also interrupts the communication to the shutdown devices of the PV modules if they correspond to the SunSpec standard for rapid shutdown.

    WARNING

    Limited rapid shutdown function in backup power mode (PV Point and Essential Backup)

    If PV Point or Essential Backup is configured, rapid shutdown cannot be triggered via the loss of grid connection. This can result in serious personal injury and damage to the PV system.

    A WSD switch must be installed for all backup power modes (PV-Point and Essential Backup) (see Installing the WSD (wired shutdown)). The rapid shutdown is then triggered via WSD.


    When an RSD occurs, an entry appears in the Event Log menu: RsdTriggeredByLossOfAc (interruption by AC breaker) or RsdTriggeredBySwitch (interruption by WSD circuit)

    In case a module-level shutdown equipment within the PV array is used in combination with the inverter, this labeling has to be used acording to NEC (Section 690.12), CSA C22.1 (Section 64-218):

    In case a string-level shutdown equipment at the PV array is used in combination with the inverter, this labeling has to be used acording to NEC (Section 690.12), CSA C22.1 (Section 64-218):

    Warning - The installer is responsible for the correct labeling of the PV system. The rapid shutdown requirement of the inverter is not affected by the FRT (fault ride through) capability, so the inverter is „Grid support interactive compatible“.

    Warning - This photovoltaic rapid shutdown equipment (PVRSE) does not perform all of the functions of a complete photovoltaic rapid shutdown system (PVRSS). This PVRSE must be installed with other equipment to from a complete PVRSS that meets the requirements of NEC (NFPA 70) section 690.12 for controlled conductors outside the array. Other equipment installed in or on this PV system may adversly affect the operation of the PVRSS. It is the responsibility of the installer to ensure that the completed PV system meets the rapid shutdown functional requirements. This equipment must be installed according to the manufacturer´s installation instructions.

    Self-test
    A self-test of the RSD function can be performed manually or automatically. The automatic self-test relates only to the discharge circuit of the RSD function. All other RSD circuit components are produced so as to be fail-safe.

    Sequence of automatic self-test:
    In each startup procedure—prior to connection to the public grid—when there is sufficient DC voltage (40 V) the discharge circuit is activated for 10 ms and the feedback pin is checked prior to and during charging.

    Sequence of manual self-test:
    A manual self-test can be triggered by an interruption in the grid connection (e.g., AC breaker) or by the WSD trigger device (see also WSD (wired shutdown) on page (→)).

    The discharge must be measured and checked using a multimeter.

    1. General information
    2. Protection of people and equipment

    Rapid shutdown

    link_horizontalLink copied
    Two different types of rapid shutdown (RSD) can be triggered depending on the configuration and on-site installation:
    • Via external buttons: One or more external buttons can be installed on the WSD (wired shutdown) interface of the Data communication area on page (→). Pressing one of these buttons interrupts the communication from the inverter to the rapid shutdown devices attached to the PV modules, only if they correspond to the SunSpec standard for rapid shutdown. The terminals are discharged to < 30 VDC  and < 15 VAC  within 30 seconds after RSD initiation.
    • Via the loss of the grid connection: An automatic rapid shutdown can also occur if the grid connection is lost. The inverter identifies a failure of the grid connection and terminals are discharged to < 30 VDC  and < 15 VAC. The inverter also interrupts the communication to the shutdown devices of the PV modules if they correspond to the SunSpec standard for rapid shutdown.

    WARNING

    Limited rapid shutdown function in backup power mode (PV Point and Essential Backup)

    If PV Point or Essential Backup is configured, rapid shutdown cannot be triggered via the loss of grid connection. This can result in serious personal injury and damage to the PV system.

    A WSD switch must be installed for all backup power modes (PV-Point and Essential Backup) (see Installing the WSD (wired shutdown)). The rapid shutdown is then triggered via WSD.


    When an RSD occurs, an entry appears in the Event Log menu: RsdTriggeredByLossOfAc (interruption by AC breaker) or RsdTriggeredBySwitch (interruption by WSD circuit)

    In case a module-level shutdown equipment within the PV array is used in combination with the inverter, this labeling has to be used acording to NEC (Section 690.12), CSA C22.1 (Section 64-218):

    In case a string-level shutdown equipment at the PV array is used in combination with the inverter, this labeling has to be used acording to NEC (Section 690.12), CSA C22.1 (Section 64-218):

    Warning - The installer is responsible for the correct labeling of the PV system. The rapid shutdown requirement of the inverter is not affected by the FRT (fault ride through) capability, so the inverter is „Grid support interactive compatible“.

    Warning - This photovoltaic rapid shutdown equipment (PVRSE) does not perform all of the functions of a complete photovoltaic rapid shutdown system (PVRSS). This PVRSE must be installed with other equipment to from a complete PVRSS that meets the requirements of NEC (NFPA 70) section 690.12 for controlled conductors outside the array. Other equipment installed in or on this PV system may adversly affect the operation of the PVRSS. It is the responsibility of the installer to ensure that the completed PV system meets the rapid shutdown functional requirements. This equipment must be installed according to the manufacturer´s installation instructions.

    Self-test
    A self-test of the RSD function can be performed manually or automatically. The automatic self-test relates only to the discharge circuit of the RSD function. All other RSD circuit components are produced so as to be fail-safe.

    Sequence of automatic self-test:
    In each startup procedure—prior to connection to the public grid—when there is sufficient DC voltage (40 V) the discharge circuit is activated for 10 ms and the feedback pin is checked prior to and during charging.

    Sequence of manual self-test:
    A manual self-test can be triggered by an interruption in the grid connection (e.g., AC breaker) or by the WSD trigger device (see also WSD (wired shutdown) on page (→)).

    The discharge must be measured and checked using a multimeter.

    1. General information
    2. Protection of people and equipment

    Power Line Communication (PLC) transmitter

    link_horizontalLink copied

    The inverter is equipped with a Power Line Communication (PLC) transmitter on the DC side. Its function is to ensure rapid shutdown in accordance with National Electric Code NEC 2023 Art. 690.12 and Canadian Electrical Code CSA C22.1:24 Art. 64-218. The PLC is implemented according to the specification “Communication Signal for Rapid Shutdown – SunSpec Interoperability Specification” (depending on national grid setup). Please visit www.sunspec.org for details.

    To ensure compliance with all applicable regulations in your country and to ensure optimal reception among all recipients, please follow the recommendations below:
    • Keep the distance between the DC+ and DC- conductors as small as possible
    • Avoid cable loops caused by cables that are too long (coil effect)
    • Use metal cable ducts where possible
    • Do not place DC cables from different inverters in the same cable duct or cable tray
    1. General information
    2. Protection of people and equipment

    Additional external AC and/or DC disconnect

    link_horizontalLink copied

    Depending on the installation, an additional external AC and/or DC disconnect may be required if the inverter is installed in a location not easily accessible to utility or first responders. Contact your local authorities for additional information.

    1. General information
    2. Protection of people and equipment

    WSD (wired shutdown)

    link_horizontalLink copied

    The wired shutdown (WSD) interrupts the inverter's grid power feed if the trigger device (switch, e.g., Emergency Stop or fire alarm contact) has been activated.

    If the installation location requires inverter shutdown when the building fire alarm system is activated, the Wired Shut Down connection on the inverter can be used and connected to the building fire alarm system.

    If an inverter (secondary device) fails, it is bypassed and the other inverters continue operating. If a second inverter (secondary device) or the inverter (primary device) fails, the operation of the entire WSD chain is interrupted.

    For installation, see Installing the WSD (wired shutdown) on page (→).

    If the installation location requires inverter shutdown when the building fire alarm system is activated, the Wired Shut Down connection on the inverter can be used and connected to the building fire alarm system.

    1. General information
    2. Protection of people and equipment

    RCMU

    link_horizontalLink copied

    The inverter is equipped with an RCMU (RCMU = residual current monitoring unit) according to UL1741 CRD 3rd Edition (Non-Isolated EPS Interactive PV Inverters).
    It monitors residual currents from the PV module up to the AC output and disconnects the inverter from the grid when an improper residual current is detected. If five faults are detected within a period of 24 hours, grid power feed operation can also be permanently interrupted until a manual reconnection has been performed.

    1. General information
    2. Protection of people and equipment

    Insulation Monitoring

    link_horizontalLink copied

    In the case of PV systems with ungrounded PV source circuits, the inverter checks the resistance between the positive or negative pole of the PV system and the ground potential before feeding energy into the grid. In the event of a short circuit between the DC+ or DC- cable and ground (e.g. due to inadequately insulated DC cables or damaged solar modules), the inverter is prevented from feeding energy into the grid.

    1. General information
    2. Protection of people and equipment

    AFCI - Arc Fault Circuit Interrupter (Arc Guard)

    link_horizontalLink copied

    An AFCI (arc fault circuit interrupter) protects against arc faults in accordance with National Electric Code NEC 2023 Art. 690.11 and Canadian Electrical Code CSA C22.1:24 Art. 64-216 and, in the narrower sense, is a protection device in the event of contact errors. The AFCI evaluates faults that occur in the current and voltage flow on the DC side using an electronic circuit and shuts down the circuit if a contact error is detected. This significantly reduces potential overheating and fire risk at poor contact points.

    CAUTION

    Danger from faulty or incorrect DC installation.

    This may result in a risk of damage and, as a consequence, risk of fire in the PV system due to prohibited thermal loads that occur during an arc.

    Check the plug connections to ensure that they are correct.

    Repair faulty insulation correctly.

    Perform connection work in line with the instructions.

    IMPORTANT!
    Fronius will not bear any costs for production downtimes, installation costs, etc., which may arise due to a detected electric arc and its consequences. Fronius accepts no liability for damage which may occur despite the integrated Arc Fault Circuit Interrupter/interruption (e.g., due to a parallel arc).

    IMPORTANT!
    Active PV module electronics (e.g., power optimizers) can impair the function of the Arc Fault Circuit Interrupter. Fronius cannot guarantee the correct function of the Arc Fault Circuit Interrupter in combination with active PV module electronics.

    Reconnection behavior
    Grid power feed operation is interrupted for at least 5 minutes after an arc has been detected. Depending on the configuration, grid power feed operation is then automatically resumed. If several arcs are detected within a period of 24 hours, grid power feed operation can also be permanently interrupted until a manual reconnection has been performed.

    1. General information
    2. Protection of people and equipment

    Standby state

    link_horizontalLink copied

    If one of the following safety devices is triggered, the inverter switches to the standby state:

    • Rapid shutdown
    • WSD
    • RCMU
    • Insulation monitoring
    • AFCI

    In the standby state, the inverter no longer feeds in and is disconnected from the grid by the opening of the AC relay.

    1. General information
    2. Protection of people and equipment

    Surge protection device

    link_horizontalLink copied

    The inverter is equipped with an integrated surge protection device according to UL1741 3rd Edition, CSA-C22.2 No.107.1-16 on the DC (Category II) and AC (Category IV) side. The surge protection device protects the system against damage caused by overvoltage.

    If the integrated surge protection devices become damaged due to prolonged overvoltage exposure, the damage may not be covered under the terms of warranty. See warranty terms for more information.

    1. General information

    General

    link_horizontalLink copied

    Information on the device

    Warning notices and safety symbols are located on the inverter. These warning notices and safety symbols must not be removed or painted over. They warn against incorrect operation, as this may result in serious injury and property damage.

    Symbols on the rating plate:

    Devices marked with the CSA certification mark satisfy the requirements of the relevant product standards for Canada and the USA.

    This equipment has been tested and found to comply with the limits for a Class B digital device, pursuant to part 15 of the FCC rules.

    These limits are designed to provide reasonable protection against harmful interference in a residential installation. This equipment generates, uses and can radiate radio frequency energy and, if not installed and used in accordance with the instructions, may cause harmful interference to radio communications.

    Any changes or modification not expressly approved by the party responsible could void the user's authority to operate the device.

    This device complies with Industry Canada licence-exempt RSS standard(s) and part 15 of the FCC Rules. Operation is subject to the following two conditions:

    1. This device may not cause interference, and
    2. This device must accept any interference, including interference that may cause undesired operation of the device.

    Safety symbols:

    Danger of serious injury and property damage due to incorrect operation

    Do not use the functions described here until you have fully read and understood the following documents:

    • These Operating Instructions
    • All Operating Instructions for the system components of the photovoltaic system, especially the safety rules

    Dangerous electrical voltage

    Allow the capacitors of the inverter to discharge (2 minutes).

    Warning notice text:

    WARNING!

    An electric shock can be fatal. Before opening the device, ensure that the input and output sides are de-energized.

    1. General information
    2. General

    Information on the device

    link_horizontalLink copied

    Warning notices and safety symbols are located on the inverter. These warning notices and safety symbols must not be removed or painted over. They warn against incorrect operation, as this may result in serious injury and property damage.

    Symbols on the rating plate:

    Devices marked with the CSA certification mark satisfy the requirements of the relevant product standards for Canada and the USA.

    This equipment has been tested and found to comply with the limits for a Class B digital device, pursuant to part 15 of the FCC rules.

    These limits are designed to provide reasonable protection against harmful interference in a residential installation. This equipment generates, uses and can radiate radio frequency energy and, if not installed and used in accordance with the instructions, may cause harmful interference to radio communications.

    Any changes or modification not expressly approved by the party responsible could void the user's authority to operate the device.

    This device complies with Industry Canada licence-exempt RSS standard(s) and part 15 of the FCC Rules. Operation is subject to the following two conditions:

    1. This device may not cause interference, and
    2. This device must accept any interference, including interference that may cause undesired operation of the device.

    Safety symbols:

    Danger of serious injury and property damage due to incorrect operation

    Do not use the functions described here until you have fully read and understood the following documents:

    • These Operating Instructions
    • All Operating Instructions for the system components of the photovoltaic system, especially the safety rules

    Dangerous electrical voltage

    Allow the capacitors of the inverter to discharge (2 minutes).

    Warning notice text:

    WARNING!

    An electric shock can be fatal. Before opening the device, ensure that the input and output sides are de-energized.

    1. General information
    2. General

    How information is presented in the document

    link_horizontalLink copied

    The conventions regarding how information is presented in the document, which are set out below, have been defined in order to increase the readability and comprehensibility of the document.

    Application notes

    IMPORTANT! Indicates application notes and other useful information. It does not indicate a harmful or dangerous situation.

    Software

    Software functions and elements of a graphical user interface (e.g., buttons, menu items) are highlighted in the text with this mark up.

    Example: Click Save.

    Instructions for action

    1Action steps are displayed with consecutive numbering.
    ✓This symbol indicates the result of the action step or the entire instruction.
    1. General information
    2. General

    Qualified personnel

    link_horizontalLink copied

    The servicing information contained in these Operating Instructions is intended only for the use of qualified personnel as defined by the NFPA 70. An electric shock can be fatal. Do not carry out any actions other than those described in the documentation.

    All cables and leads must be secured, undamaged, insulated, and adequately dimensioned. Loose connections, scorched, damaged, or under-dimensioned cables and leads must be repaired immediately by qualified personnel.

    Maintenance and repair work must only be carried out by an authorized specialist.

    It is impossible to guarantee that externally (aka, third-party) procured parts are designed and manufactured to meet the demands made on them, or that they satisfy safety requirements. Use only original spare parts (also applies to standard parts).

    Do not carry out any alterations, installations, or modifications to the device without first obtaining the manufacturer's permission.

    Components that are not in perfect condition must be changed immediately.

    1. General information
    2. General

    Data security

    link_horizontalLink copied
    With regard to data security, the user is responsible for:
    • Backing up any changes made to the factory settings
    • Saving and storing personal settings

    NOTE

    Data security for network and Internet connection

    Unsecured networks and a lack of safeguards can result in data loss and unauthorized access. Observe the following points for safe operation:

    Operate inverters and system components on a private, secure network. A WiFi network is considered secure if security standard WPA 2 is satisfied as a minimum.

    Keep the network devices (e.g., WiFi routers) up to date with the latest technology.

    Keep the software and/or firmware updated.

    Use a wired network to ensure a stable data connection.

    For security reasons, do not make inverters and system components accessible from the Internet via port forwarding or Port Address Translation (PAT).

    Use the solutions provided by Fronius for monitoring and remote configuration.

    The optional communication protocol Modbus TCP/IP1) is an unsecured interface. Only use Modbus TCP/IP if no other secured data communication protocol (MQTT2)) is possible (e.g., compatibility with older Smart Meters).

    1) TCP/IP - Transmission Control Protocol/Internet Protocol
    2) MQTT - Message Queuing Telemetry Protocol

    1. General information
    2. General

    Privacy policy

    link_horizontalLink copied

    When you connect your device (and any associated devices) to the internet, the following device and operating data (device ID/identifier, device IP address, device time, configuration settings, hardware and software information, device status log files, serial number) is sent automatically to

    Fronius International GmbH, Froniusstraße 1, 4643 Pettenbach, Austria, telephone +43(0) 7242241-0, email: contact@fronius.com (controller)

    and stored.

    The processing of this device and operating data is carried out for the purpose of ensuring the operational safety of the device (time synchronization, provision of updates). This processing is therefore necessary for the functionality of the device and thus for the fulfillment of the contract (Art. 6 (1) (b) GDPR).

    If you do not wish to have such data processed, you must manually disable the device's internet connection.

    In addition, the device and operating data is also processed for the purpose of providing services as part of a supplementary digital service for your device (such as solar.web or similar) as soon as you have registered your device with such a digital service (identification). This data is processed to provide the requested digital services and is therefore necessary for the fulfillment of the contract (Art. 6 (1) (b) GDPR).

    Furthermore, this data processing is also carried out for maintenance and support purposes and for handling customer concerns as well as in warranty and guarantee cases (only in individual cases and given connection between device and internet). In this context, the device and operating data may also be passed on to our cooperation partners (third-party providers and suppliers). The processing of this data is necessary for maintenance and support purposes or for processing warranty and guarantee cases and thus for the fulfillment of the contract (Art. 6 (1) (b) GDPR).

    Device and operating data are also processed for analysis and diagnostic purposes in order to gain insights into the functionality of the devices and improve them accordingly. This data processing is based on our legitimate interest (Art. 6 (1) (f) GDPR).

    We store this data for as long as it is necessary to fulfill the existing contract with you. Any storage beyond this is carried out for legal reasons or if we have a legitimate interest in doing so. For more information on data processing for the solar.web-digital service, as well as our general privacy policy and your rights as a data subject, please visit https://www.fronius.com.

    1. General information
    2. General

    Copyright

    link_horizontalLink copied

    Fronius International GmbH retains the copyrights of these operating instructions.

    Text, illustrations, and other media correspond to the technical state of the art at the time of publication. Fronius reserves the right to make changes. If you have any suggestions for improvement or have found a mistake in this document, we would be most grateful for your comments.

    1. General information
    2. General

    Territorial Limitations

    link_horizontalLink copied

    This product is intended for use and sale outside the Province of Québec. It does not meet the French language documentation and labeling requirements of Québec's Charter of the French Language. Accordingly, Fronius International GmbH does not offer this product for sale to, or for delivery to, any address within the Province of Québec.

    By placing an order, the customer represents and warrants that they are not purchasing the product for use or resale within Québec. Fronius International GmbH disclaims all liability and warranty obligations for any products operated in Québec in violation of these restrictions.

    1. General information

    Fronius Primo GEN24 208 - 240

    link_horizontalLink copied

    Function overview

    Function

    Primo GEN24

    Primo GEN24 Plus

    Backup power variant - PV Point (OP)

    Battery connection*

    Available as an option**

    Backup power variant - Essential Backup

    Available as an option**

    *
    For suitable batteries, see chapter Suitable batteries.
    **
    The functions are optionally available via Fronius UP (see chapter Fronius UP).
    1. General information
    2. Fronius Primo GEN24 208 - 240

    Function overview

    link_horizontalLink copied

    Function

    Primo GEN24

    Primo GEN24 Plus

    Backup power variant - PV Point (OP)

    Battery connection*

    Available as an option**

    Backup power variant - Essential Backup

    Available as an option**

    *
    For suitable batteries, see chapter Suitable batteries.
    **
    The functions are optionally available via Fronius UP (see chapter Fronius UP).
    1. General information
    2. Fronius Primo GEN24 208 - 240

    Scope of supply

    link_horizontalLink copied
    (1)
    Mounting bracket (illustration)
    (2)
    Inverter
    (3)
    Housing cover
    (4)
    Quick Start Guide
    1. General information
    2. Fronius Primo GEN24 208 - 240

    Fronius UP

    link_horizontalLink copied

    With Fronius UP*, optionally available functions can be added to the inverter by the authorized specialist company (see chapter Function overview).

    *
    The availability of Fronius UP is country-specific. Click here for further information on availability.
    1. General information
    2. Fronius Primo GEN24 208 - 240

    Intended use

    link_horizontalLink copied

    The inverter is designed to convert direct current from PV modules into alternating current and feed this power into the public grid. A backup power mode* is possible if the wiring is set up accordingly.

    Intended use also means:
    • Carefully reading and following all the instructions as well as complying with the safety and danger notices in the operating instructions
    • Installation in accordance with the chapter headed Installation, from page (→)

    Follow all grid operator regulations regarding energy fed into the grid and connection methods.

    The inverter is a grid-connected inverter with backup power function and is not a stand-alone inverter. The following restrictions in backup power mode must therefore be observed:
    • The inverter may be operated for max. 2000 operating hours in backup power mode
    • The inverter may be operated for more than 2000 operating hours in backup power mode provided 20% of the grid power feed operating time of the inverter is not exceeded at the time in question
    *
    Depending on the device variant, suitable battery, corresponding cabling, settings, and local standards and regulations.
    1. General information
    2. Fronius Primo GEN24 208 - 240

    Thermal concept

    link_horizontalLink copied

    Ambient air is drawn in at the front of the device by the fan and blown out at the sides. The even heat dissipation allows several inverters to be installed next to each other.

    NOTE

    Risk due to insufficient cooling of the inverter.

    This may result in a loss of power in the inverter.

    Do not block the fan (e.g., with objects that protrude through the touch guard).

    Do not cover the ventilation slots, even partially.

    Make sure that the ambient air can always flow through the inverter's ventilation slots unimpeded.

    1. General information
    2. Fronius Primo GEN24 208 - 240

    Fronius Solar.web

    link_horizontalLink copied

    System owners and installers can easily monitor and analyze the PV system using Fronius Solar.web or Fronius Solar.web Premium. With the appropriate configuration, the inverter transmits data such as power, yield, load, and energy balance to Fronius Solar.web. More detailed information can be found at Solar.web - Monitoring & analysis.

    Configuration is carried out via the Setup wizard, see chapter Installation with the app or Installation with the browser.

    Requirements for configuration:
    • Internet connection (download: min. 512 kbit/s, upload: min. 256 kbit/s)*.
    • User account at solarweb.com.
    • Completed configuration using the Setup wizard.
    *
    These specifications do not provide an absolute guarantee of flawless operation. High error rates in the transmission, fluctuating receptions or misfires can have an adverse effect on data transfer. Fronius recommends on-site testing to ensure that the connections meet the minimum requirements.
    1. General information
    2. Fronius Primo GEN24 208 - 240

    Local communication

    link_horizontalLink copied

    The inverter can be found via the Multicast DNS (mDNS) protocol. We recommend searching for the inverter using the assigned host name.

    The following data can be called up via mDNS:
    • NominalPower
    • Systemname
    • DeviceSerialNumber
    • SoftwareBundleVersion
    1. General information

    Different operating modes

    link_horizontalLink copied

    Operating modes - Explanation of symbols

    PV module
    generates direct current.

    Fronius GEN24 inverter
    converts direct current into alternating current and charges the battery (battery support is required to charge the battery, see Function overview on page(→)). The integrated system monitoring enables the inverter to be integrated into a network by means of WLAN.

    Additional inverter in the system
    converts the direct current into alternating current. However, it cannot charge a battery and is not available in backup power mode.

    Battery
    is coupled to the inverter on the direct current side and stores electrical energy.

    Primary meter
    records the system's load curve and provides measurement data for energy profiling in Fronius Solar.web. The primary meter also controls the dynamic feed-in control.

    Secondary meter
    records the load curve of individual loads (e.g., washing machine, lamps, TV, heat pump, etc.) in the consumption branch and provides measurement data for energy profiling in Fronius Solar.web.

    Loads in the system
    are the loads connected in the system.

    Additional loads and producers in the system
    are connected to the system by means of a Smart Meter.

    PV Point
    is a non-uninterruptible 1‑phase backup power circuit that supplies electrical devices with up to 1.56 kW if sufficient power is available from the PV modules or the battery.

    Essential Backup
    the inverter is prepared for backup power mode. The backup power mode must be implemented in the switch cabinet by the electrician performing the installation. The PV system operates in a stand-alone manner in backup power mode.

    Grid
    supplies the loads in the system if insufficient power is being generated by the PV modules or supplied by the battery.

    1. General information
    2. Different operating modes

    Operating modes - Explanation of symbols

    link_horizontalLink copied

    PV module
    generates direct current.

    Fronius GEN24 inverter
    converts direct current into alternating current and charges the battery (battery support is required to charge the battery, see Function overview on page(→)). The integrated system monitoring enables the inverter to be integrated into a network by means of WLAN.

    Additional inverter in the system
    converts the direct current into alternating current. However, it cannot charge a battery and is not available in backup power mode.

    Battery
    is coupled to the inverter on the direct current side and stores electrical energy.

    Primary meter
    records the system's load curve and provides measurement data for energy profiling in Fronius Solar.web. The primary meter also controls the dynamic feed-in control.

    Secondary meter
    records the load curve of individual loads (e.g., washing machine, lamps, TV, heat pump, etc.) in the consumption branch and provides measurement data for energy profiling in Fronius Solar.web.

    Loads in the system
    are the loads connected in the system.

    Additional loads and producers in the system
    are connected to the system by means of a Smart Meter.

    PV Point
    is a non-uninterruptible 1‑phase backup power circuit that supplies electrical devices with up to 1.56 kW if sufficient power is available from the PV modules or the battery.

    Essential Backup
    the inverter is prepared for backup power mode. The backup power mode must be implemented in the switch cabinet by the electrician performing the installation. The PV system operates in a stand-alone manner in backup power mode.

    Grid
    supplies the loads in the system if insufficient power is being generated by the PV modules or supplied by the battery.

    1. General information
    2. Different operating modes

    Operating mode - Inverter with Smart Meter

    link_horizontalLink copied
    1. General information
    2. Different operating modes

    Operating mode - Inverter with battery and several Smart Meters

    link_horizontalLink copied
    1. General information
    2. Different operating modes

    Operating mode – Inverter with battery, AC-coupled to another inverter

    link_horizontalLink copied
    1. General information
    2. Different operating modes

    Operating mode - Inverter with battery and backup power function

    link_horizontalLink copied

    IMPORTANT!
    For backup power mode, a Backup Frequency Offset can be set for loads in the backup power circuit (see Inverter).

    In the fully equipped hybrid PV system, the inverter can:
    • Supply loads in the house
    • Store excess energy in the battery and/or feed it into the grid
    • Supply connected loads in the event of a power failure
    1. General information
    2. Different operating modes

    Operating mode - Inverter with battery, additional inverter, and backup power function

    link_horizontalLink copied

    In the hybrid photovoltaic system, batteries must only be connected to one inverter with battery support. Batteries cannot be split between multiple inverters with battery support. However, depending on the battery manufacturer, several batteries can be combined on one inverter.

    1. General information
    2. Different operating modes

    Energy flow direction of the inverter

    link_horizontalLink copied
    (1)
    PV module – inverter – load/grid/battery
    (2)
    Battery – inverter – load/grid*
    (3)
    Grid – inverter – load/battery*

    * Charging the battery from the public grid depends on the settings and local standards and regulations.

    1. General information
    2. Different operating modes

    Operating states (only for battery systems)

    link_horizontalLink copied

    Battery systems distinguish between different operating states. In each case, the relevant current operating state is displayed on the user interface of the inverter or in Fronius Solar.web.

    Operating state

    Description

    Normal operation

    The energy is stored or drawn, as required.

    Min. state of charge (SoC) reached

    The battery has reached the minimum SoC specified by the manufacturer or the set minimum SoC. The battery cannot be discharged further.

    Energy saving mode (standby)

    The system has been put into energy-saving mode. Energy saving mode is automatically ended as soon as sufficient surplus power is available again.

    Start

    The battery system starts from energy-saving mode (standby).

    Forced re-charging

    The inverter recharges the battery, in order to maintain the SoC specified by the manufacturer or the set minimum SoC (protection against deep discharge).

    Calibration charging

    The battery system is charged to the SoC of 100% and then discharged to the SoC of 0%. After 1 hour of waiting time at SoC 0%, the calibration charge is stopped and the battery switches to normal operation.

    Service mode

    The battery system is charged or discharged to the SoC of 30% and the SoC of 30% is maintained until the end of the service mode.

    Deactivated

    The battery is not active. It has either been deactivated, switched off, or the communication between the battery and the inverter has been interrupted.

    1. General information

    Energy-saving mode

    link_horizontalLink copied

    General

    Energy saving mode (standby mode) is used to reduce the self-consumption of the system. Both the inverter and the battery automatically switch to energy saving mode under certain conditions.

    The inverter switches to energy saving mode if the battery is flat and no PV power is available. Only the inverter's communication with the Fronius Smart Meter and Fronius Solar.web is maintained.

    1. General information
    2. Energy-saving mode

    General

    link_horizontalLink copied

    Energy saving mode (standby mode) is used to reduce the self-consumption of the system. Both the inverter and the battery automatically switch to energy saving mode under certain conditions.

    The inverter switches to energy saving mode if the battery is flat and no PV power is available. Only the inverter's communication with the Fronius Smart Meter and Fronius Solar.web is maintained.

    1. General information
    2. Energy-saving mode

    Switch-off conditions

    link_horizontalLink copied

    If all the switch-off conditions are met, the battery switches into energy saving mode within ten minutes. This time delay ensures that the inverter can at least be restarted.

     

    The battery state of charge is less than or equal to the input minimum state of charge.

     

    The current charging or discharging power of the battery is less than 100 W.

     

    Less than 50 W is available for charging the battery. The power of feeding into the public grid is at least 50 W less than the power currently required in the home network.

    The inverter automatically switches into energy saving mode, following the battery.

    1. General information
    2. Energy-saving mode

    Switch-on conditions

    link_horizontalLink copied
    If one of the following conditions is met for at least 30 seconds, energy saving mode is ended:
    • Energy saving mode is no longer permissible owing to a changed setting on the user interface of the inverter.
    • If dynamic power reduction of 0 is set, or if the system is operating in backup power mode, the power of feeding into the public grid is always less than the required power in the home network.
      There is a separate condition for this case (dynamic power reduction < 300 W or active backup power mode):
      • If the PV power is above a specified threshold, energy saving mode is ended.
    • Battery charging from the public grid is requested via the user interface of the inverter.
    • The battery is being recharged in order to restore the minimum state of charge or perform calibration.
    1. General information
    2. Energy-saving mode

    Special case

    link_horizontalLink copied

    If the inverter does not operate for 12 minutes (e.g., fault), or there is an interruption in the electrical connection between the inverter and the battery and there is no backup power mode, the battery switches to energy-saving mode in any case. This reduces self discharge of the battery.

    1. General information
    2. Energy-saving mode

    Indication of energy saving mode

    link_horizontalLink copied
    During energy saving mode:
    • Operating LED of the inverter lights up orange (see Button functions and LED status indicator on page (→)).
    • The user interface of the inverter can be reached.
    • All the available data are saved and transmitted to Solar.web.
    • The real-time data can be seen on Solar.web.

     

    Energy saving mode is shown on the user interface of the inverter and in Solar.web by an "i" beside the battery symbol in the system overview.

    1. General information

    Suitable batteries

    link_horizontalLink copied

    General

    Fronius explicitly points out that the third-party batteries are not Fronius products. Fronius is not the manufacturer, distributor, or retailer of these batteries. Fronius accepts no liability and offers no service or guarantees for these batteries.

    Install third-party batteries (part of a ESS (energy storage system)) according to applicable local and national codes.

    Obsolete firmware/software states may lead to incompatibilities between the inverter and the battery. In this case, the following steps are to be performed:
    1Update battery software—see the battery documentation.
    2Update inverter firmware—see Update on page (→).

    Read this document and the Installation Instructions before installing and commissioning the external battery. The documentation is either enclosed with the external battery or can be obtained from the battery manufacturer or their service partners

    All documents associated with the inverter can be found at the following address:
    https://www.fronius.com/en/solar-energy/installers-partners/service-support/tech-support

    1. General information
    2. Suitable batteries

    General

    link_horizontalLink copied

    Fronius explicitly points out that the third-party batteries are not Fronius products. Fronius is not the manufacturer, distributor, or retailer of these batteries. Fronius accepts no liability and offers no service or guarantees for these batteries.

    Install third-party batteries (part of a ESS (energy storage system)) according to applicable local and national codes.

    Obsolete firmware/software states may lead to incompatibilities between the inverter and the battery. In this case, the following steps are to be performed:
    1Update battery software—see the battery documentation.
    2Update inverter firmware—see Update on page (→).

    Read this document and the Installation Instructions before installing and commissioning the external battery. The documentation is either enclosed with the external battery or can be obtained from the battery manufacturer or their service partners

    All documents associated with the inverter can be found at the following address:
    https://www.fronius.com/en/solar-energy/installers-partners/service-support/tech-support

    1. General information
    2. Suitable batteries

    Limitations in operation

    link_horizontalLink copied

    If the DC voltage exceeds 403 V, the battery can no longer be charged or discharged. The voltage of 403 V is rarely exceeded during normal operation of the inverter.

    When the output power of the inverter is reduced, the operating point shifts towards higher DC voltages. The following conditions during normal operation can lead to the DC voltage of 403 V being exceeded:
    • Overdimensioning of the module array.
    • Feed-in limitation (e.g., zero feed-in).
    • Specifications of the grid operator (e.g., mains voltage-dependent power reduction).
    • Backup power mode. If the 403 V voltage is exceeded during backup power, backup power operation may be restricted. Therefore, an open-circuit voltage of max. 403 V is recommended.
    1. General information

    Operating controls and connections

    link_horizontalLink copied

    Connection area

     

    (1)
    2 x 5-pin DC push-in terminal
    (2)
    Push-in WSD (wired shutdown) terminal
    (3)
    Push-in terminals in the data communication area (Modbus, digital inputs and outputs)
    (4)
    3-pin push-in terminal for PV Point (OP)
    (5)
    4-pin AC push-in terminal
    (6)
    6-pin ground electrode terminal
    (7)
    Connection area divider
    (8)
    AC conduit connection (Ø ½ - 1 inch / 13 - 25 mm) (Ø ½ - 1¼ inch / 13 - 32 mm)
    (9)
    Ground spike conduit connection (Ø ⅝ inch / 16 mm)
    (10)
    DatCom conduit connection (Ø ½ - ¾ inch / 13 - 19 mm)
    (11)
    Data communication area conduit connection (Ø ⅝ - ¾ inch / 16 - 19 mm)
    (12)
    Drain valve
    (13)
    DC conduit connection (Ø ½ - 1 inch / 13 - 25 mm)
    1. General information
    2. Operating controls and connections

    Connection area

    link_horizontalLink copied

     

    (1)
    2 x 5-pin DC push-in terminal
    (2)
    Push-in WSD (wired shutdown) terminal
    (3)
    Push-in terminals in the data communication area (Modbus, digital inputs and outputs)
    (4)
    3-pin push-in terminal for PV Point (OP)
    (5)
    4-pin AC push-in terminal
    (6)
    6-pin ground electrode terminal
    (7)
    Connection area divider
    (8)
    AC conduit connection (Ø ½ - 1 inch / 13 - 25 mm) (Ø ½ - 1¼ inch / 13 - 32 mm)
    (9)
    Ground spike conduit connection (Ø ⅝ inch / 16 mm)
    (10)
    DatCom conduit connection (Ø ½ - ¾ inch / 13 - 19 mm)
    (11)
    Data communication area conduit connection (Ø ⅝ - ¾ inch / 16 - 19 mm)
    (12)
    Drain valve
    (13)
    DC conduit connection (Ø ½ - 1 inch / 13 - 25 mm)
    1. General information
    2. Operating controls and connections

    Connection area divider

    link_horizontalLink copied

    The connection area divider separates the high-voltage conductors (DC and AC) from the signal lines. To make it easier to reach the connection area, the divider can be removed for the connection work, and must be re-inserted.

    (1)
    Integrated cable duct
    (2)
    Recesses for removing the connection area divider
    (3)
    Snap tabs for locking/unlocking
    (4)
    Defined breaking point for the DatCom connection

    The integrated cable duct (1) allows for the lines to be laid from one area of the inverter to the other. As a result, multiple inverters can be easily installed next to each other.

    1. General information
    2. Operating controls and connections

    Ground electrode terminal

    link_horizontalLink copied

    The ground electrode terminal    provides the option of grounding additional components, such as:

    • AC cable
    • Module mounting system
    • Ground spike
    1. General information
    2. Operating controls and connections

    DC disconnector

    link_horizontalLink copied

    The DC disconnector has 3 switch settings:

    (1)
    Locked/off (turned to the left)
    (2)
    Off
    (3)
    On

    IMPORTANT!
    In switch settings (1) and (3), the inverter can be secured to prevent it from being switched on/off using a standard padlock. The national guidelines must be complied with in this respect.

    1. General information
    2. Operating controls and connections

    Data communication area

    link_horizontalLink copied

       Operating LED

    Indicates the inverter operating status.

    BAT switch

    Position 1: Setting for connecting compatible batteries (factory setting)
    Position 0:
    not in use

    WSD (wired shutdown) switch

    Defines the inverter as the WSD master or WSD slave.

    Position 1: WSD master
    Position 0:
    WSD slave

    Modbus 0 (MB0) switch

    Switches the terminating resistor for Modbus 0 (MB0) on/off.

    Position 1: Terminating resistor on (factory setting)
    Position 0: Terminating resistor off

    Modbus 1 (MB1) switch

    Switches the terminating resistor for Modbus 1 (MB1) on/off.

    Position 1: Terminating resistor on (factory setting)
    Position 0: Terminating resistor off

       Optical sensor

    For operating the inverter. See chapter Button functions and LED status indicator on page (→).

       Communications LED

    Indicates the inverter connection status.

     Battery Connection (Modbus RJ45)

    Modbus connection for connecting a compatible battery.

    IMPORTANT!

    • This connection only works with hybrid inverters.
    • The connection is connected to Modbus 0.
    • Do not connect any network components (e.g., WiFi router) to this connection.

    LAN 1

    Ethernet connection for data communication (e.g., WiFi router, home network) or, for commissioning with a laptop, see chapter Installation with the browser on page (→)).

    LAN 2

    Reserved for future functions.

    I/O terminal

    Push-in terminal for digital inputs/outputs. See chapter Permitted cables for the data communication connection on page (→).

    WSD terminal

    Push-in terminal for the WSD installation. See chapter WSD (wired shutdown) on page (→).

    Modbus terminal

    Push-in terminal for the installation of Modbus 0, Modbus 1, 12 V, and GND (ground).

    The inverter establishes the data connection to the connected components via the Modbus terminal. The inputs M0 and M1 can be freely selected. Max. 4 Modbus participants per input; see chapter Modbus participants on page (→).

    1. General information
    2. Operating controls and connections

    Button functions and LED status indicator

    link_horizontalLink copied

    The status of the inverter is shown via the operating status LED. In the event of faults, carry out the individual steps in the Fronius Solar.start app.

    The optical sensor is actuated by touching with a finger.

    The status of the connection is shown via the communication LED. To establish the connection, carry out the individual steps in the Fronius Solar.start app.

     

    Sensor functions

    1x    = WLAN Access Point (AP) is opened.

       Flashing blue

    2x    = WLAN Protected Setup (WPS) is activated.

       Flashing green

    3 seconds    (max. 6 seconds) = the service message is acknowledged.

       Flashing white (rapidly)

     

    LED status indicator

    The inverter is operating correctly.

       Lights up green

    The inverter is performing the grid checks required by the applicable standards for feed-in mode.

       Flashing green

    The inverter is in standby, is not operational (e.g. no feed-in at night) or is not configured.

       Lights up yellow

    The inverter indicates a non-critical status.

       Flashing yellow

    The inverter indicates a critical status and there is no grid power feed process.

       Lights up red

    The inverter indicates a backup power overload.

       Flashing red

    The network connection is being established via WPS.
    2x    = WPS search mode.

       Flashing green

    The network connection is being established via WLAN AP.
    1x    = WLAN AP search mode (active for 30 minutes).

       Flashing blue

    The network connection is not configured.

       Lights up yellow

    The inverter is operating correctly, a network fault is indicated.

       Lights up red

    The network connection is active.

       Lights up blue

    The inverter is performing an update.

       /    Flashing blue

    There is a service message.

       Lights up white

    1. General information
    2. Operating controls and connections

    Schematic internal wiring of IOs

    link_horizontalLink copied

    The V+/ GND pin provides the possibility of feeding in a voltage in the range of 12.5 to 24 V (+ max. 20%) using an external power supply unit. Outputs IO 0 - 5 can then be operated using the external voltage that has been fed in. A maximum of 1 A may be drawn per output, whereby a total of max. 3 A is permitted. The fuse protection must take place externally.

    CAUTION

    Danger from polarity reversal at the terminals due to improper connection of external power supply units.

    This may result in severe damage to the inverter.

    Check the polarity of the external power supply unit with a suitable measuring device before connecting it.

    Connect the cables to the V+/GND outputs while ensuring the correct polarity.

    IMPORTANT!
    If the total output (6 W) is exceeded, the inverter switches off the entire external power supply.

    (1)
    Current limitation
    1. General information

    Manual system start

    link_horizontalLink copied

    Requirements

    There is no energy available from the PV modules or from the public grid. If backup power operation or battery operation are not possible (e.g., deep discharge protection of the battery), the inverter and battery switch off.

    1. General information
    2. Manual system start

    Requirements

    link_horizontalLink copied

    There is no energy available from the PV modules or from the public grid. If backup power operation or battery operation are not possible (e.g., deep discharge protection of the battery), the inverter and battery switch off.

    1. General information
    2. Manual system start

    Notification of system shutdown

    link_horizontalLink copied

    Status codes about the inactive state of the battery are displayed on the user interface of the inverter. A notification via e-mail can be activated in Fronius Solar.web.

    1. General information
    2. Manual system start

    Manual battery start after system shutdown

    link_horizontalLink copied

    As soon as energy is available again, the inverter starts operation automatically; however, the battery must be started manually. The switch-on sequence must be observed for this, see chapter Suitable batteries on page (→).

    1. General information
    2. Manual system start

    Starting backup power operation after a system shutdown

    link_horizontalLink copied

    The inverter requires energy from the battery to start backup power operation. This is done manually on the battery; further information on the power supply for restarting the inverter via the battery can be found in the battery manufacturer's Operating Instructions.

    Backup power

    link_horizontalLink copied

    PV Point (OP)

    Explanation - PV Point (OP)

    With the default settings, the inverter can provide 120V at the PV Point. A corresponding configuration must be set up during commissioning.

    At the selected output voltage, a maximum of 13 A AC continuous current is available. The maximum continuous output is 1560 W.

    Example:
    120 V *13 A = 1560 W

    In backup power mode, some electrical appliances cannot function properly as start-up currents are too high (e.g., fridges and freezers). In backup power mode, we recommend switching off non-essential loads. Overload capacity of 35% is possible for a duration of 5 seconds, depending on the current power of the PV module.

    There is a brief interruption when switching from grid-connected mode to backup power mode. As a result, the backup power function cannot be used as an uninterruptible power supply, for computers, for example.

    If no energy from the PV modules is available in backup power mode, backup power mode ends automatically. Backup power mode restarts again automatically once sufficient energy can once again be provided by the PV modules.

    In the event of excessive loads, backup power mode is stopped and the "Backup power overload" status code is displayed on the inverter's LED status indicator. The maximum power in backup power mode specified in the technical data must be observed.

    1. Backup power

    PV Point (OP)

    link_horizontalLink copied

    Explanation - PV Point (OP)

    With the default settings, the inverter can provide 120V at the PV Point. A corresponding configuration must be set up during commissioning.

    At the selected output voltage, a maximum of 13 A AC continuous current is available. The maximum continuous output is 1560 W.

    Example:
    120 V *13 A = 1560 W

    In backup power mode, some electrical appliances cannot function properly as start-up currents are too high (e.g., fridges and freezers). In backup power mode, we recommend switching off non-essential loads. Overload capacity of 35% is possible for a duration of 5 seconds, depending on the current power of the PV module.

    There is a brief interruption when switching from grid-connected mode to backup power mode. As a result, the backup power function cannot be used as an uninterruptible power supply, for computers, for example.

    If no energy from the PV modules is available in backup power mode, backup power mode ends automatically. Backup power mode restarts again automatically once sufficient energy can once again be provided by the PV modules.

    In the event of excessive loads, backup power mode is stopped and the "Backup power overload" status code is displayed on the inverter's LED status indicator. The maximum power in backup power mode specified in the technical data must be observed.

    1. Backup power
    2. PV Point (OP)

    Explanation - PV Point (OP)

    link_horizontalLink copied

    With the default settings, the inverter can provide 120V at the PV Point. A corresponding configuration must be set up during commissioning.

    At the selected output voltage, a maximum of 13 A AC continuous current is available. The maximum continuous output is 1560 W.

    Example:
    120 V *13 A = 1560 W

    In backup power mode, some electrical appliances cannot function properly as start-up currents are too high (e.g., fridges and freezers). In backup power mode, we recommend switching off non-essential loads. Overload capacity of 35% is possible for a duration of 5 seconds, depending on the current power of the PV module.

    There is a brief interruption when switching from grid-connected mode to backup power mode. As a result, the backup power function cannot be used as an uninterruptible power supply, for computers, for example.

    If no energy from the PV modules is available in backup power mode, backup power mode ends automatically. Backup power mode restarts again automatically once sufficient energy can once again be provided by the PV modules.

    In the event of excessive loads, backup power mode is stopped and the "Backup power overload" status code is displayed on the inverter's LED status indicator. The maximum power in backup power mode specified in the technical data must be observed.

    1. Backup power
    2. PV Point (OP)

    PV Point (OP)

    link_horizontalLink copied

    WARNING

    Limited rapid shutdown function in backup power mode (PV Point and Essential Backup)

    If PV Point or Essential Backup is configured, rapid shutdown cannot be triggered via the loss of grid connection. This can result in serious personal injury and damage to the PV system.

    A WSD switch must be installed for all backup power modes (PV-Point and Essentail Backup) (see Installing the WSD (wired shutdown)). The rapid shutdown is then triggered via WSD.

    With the PV Point, in the event of a failure of the public grid, electrical devices can be connected to the Opportunity Power (OP) terminal and supplied with a maximum power of 1.56 kW, if enough power is available in the PV modules. In grid-connected operation, the OP terminal is not supplied with voltage, therefore the connected loads will not be supplied with power in this operating mode.

    IMPORTANT!
    A grid switchover with relay is not possible.

    1. Backup power
    2. PV Point (OP)

    PV Point Comfort

    link_horizontalLink copied

    WARNING

    Limited rapid shutdown function in backup power mode (PV Point and Essential Backup)

    If PV Point or Essential Backup is configured, rapid shutdown cannot be triggered via the loss of grid connection. This can result in serious personal injury and damage to the PV system.

    A WSD switch must be installed for all backup power modes (PV-Point and Essentail Backup) (see Installing the WSD (wired shutdown)). The rapid shutdown is then triggered via WSD.

    With the PV Point, in the event of a failure of the public grid, electrical devices can be connected to the Opportunity Power (OP) terminal and supplied with a maximum power of 1.56 kW, if enough power is available in the PV modules.

    IMPORTANT!
    A grid switchover with relay is not possible.

    1. Backup power

    Essential Backup

    link_horizontalLink copied

    Prerequisites for backup power mode

    IMPORTANT!
    If several backup power variants are available, please note that only one backup power variant may be installed and configured.

    In order to use the inverter's backup power function, the following prerequisites must be fulfilled:
    • The inverter must support the backup power variant - Essential Backup (see chapter Function overview on page (→)).
    • A battery suitable for backup power use must be installed and configured.
    • Correct cabling of the backup power system in the electrical installation or usage of a switch box
    • IMPORTANT! The inverter provides a nominal output current of 240 V in backup power mode. The switch box must reduce the current to 120 V.
    • Mount and configure the Fronius Smart Meter at the feed-in point.
    • Attach a warning notice for the backup power supply (https://www.fronius.com/en/search-page, item number: 42,0409,0275) on the electrical distributor.
    • Apply the necessary settings in the "Devices and system components" → "Functions and pins" → "Backup Power" menu area and activate backup power.
    1. Backup power
    2. Essential Backup

    Prerequisites for backup power mode

    link_horizontalLink copied

    IMPORTANT!
    If several backup power variants are available, please note that only one backup power variant may be installed and configured.

    In order to use the inverter's backup power function, the following prerequisites must be fulfilled:
    • The inverter must support the backup power variant - Essential Backup (see chapter Function overview on page (→)).
    • A battery suitable for backup power use must be installed and configured.
    • Correct cabling of the backup power system in the electrical installation or usage of a switch box
    • IMPORTANT! The inverter provides a nominal output current of 240 V in backup power mode. The switch box must reduce the current to 120 V.
    • Mount and configure the Fronius Smart Meter at the feed-in point.
    • Attach a warning notice for the backup power supply (https://www.fronius.com/en/search-page, item number: 42,0409,0275) on the electrical distributor.
    • Apply the necessary settings in the "Devices and system components" → "Functions and pins" → "Backup Power" menu area and activate backup power.
    1. Backup power
    2. Essential Backup

    Transitioning from grid power feed operation to backup power mode

    link_horizontalLink copied
    1. The public grid is monitored by the inverter's internal grid and system protection unit and by the Fronius Smart Meter connected to it.
    2. The public grid fails or specific grid parameters are undershot or exceeded.
    3. The inverter carries out the measures necessary according to the country standard and then switches off.
    4. The inverter starts backup power mode after a checking period.
    5. All loads in the household that are in the backup power circuit are supplied by the battery and the PV modules. The remaining loads are not supplied with power and are safely isolated.
    1. Backup power
    2. Essential Backup

    Transitioning from backup power mode to grid power feed operation

    link_horizontalLink copied
    1. The inverter is operating in backup power mode.
    2. The public grid is functioning correctly again.
    3. The Fronius Smart Meter monitors the grid parameters on the public grid and passes this information to the inverter.
    4. The stability of the restored public grid is determined by checking the measured values of the Fronius Smart Meter.
    5. Backup power mode is terminated automatically or manually depending on the design of the backup power switchover facility.
    6. All circuits are reconnected to the public grid and are supplied by the grid.
    7. The inverter can start grid power feed operation again after performing the grid checks required by the relevant standard.
    1. Backup power
    2. Essential Backup

    Backup power and energy saving mode

    link_horizontalLink copied
    Under the following conditions, the battery and the inverter are switched to energy saving mode after a waiting time of 8-12 minutes and backup power mode is ended:
    • The battery is discharged to the minimum state of charge and no energy is coming from the PV modules.
    • The inverter is set to energy saving mode (standby mode).
    If the battery and inverter are in energy saving mode, the system is reactivated by the following:
    • Enough energy is available from the PV modules.
    • The public grid is functioning again.
    • The battery is switched off and on.

    Installation

    link_horizontalLink copied

    General

    Quick-fastener system

    NOTE

    Danger when using a drill driver.

    This may result in the destruction of the quick-fastener system due to overtorque.

    Use a screwdriver (TX20).

    Do not turn the screws more than 180°.

    A quick-fastener system (3) is used to mount the connection area cover and front cover. The system is opened and closed with a half-rotation (180°) of the captive screw (1) into the quick-fastener spring (2).

    The system is independent of torque.

    1. Installation

    General

    link_horizontalLink copied

    Quick-fastener system

    NOTE

    Danger when using a drill driver.

    This may result in the destruction of the quick-fastener system due to overtorque.

    Use a screwdriver (TX20).

    Do not turn the screws more than 180°.

    A quick-fastener system (3) is used to mount the connection area cover and front cover. The system is opened and closed with a half-rotation (180°) of the captive screw (1) into the quick-fastener spring (2).

    The system is independent of torque.

    1. Installation
    2. General

    Quick-fastener system

    link_horizontalLink copied

    NOTE

    Danger when using a drill driver.

    This may result in the destruction of the quick-fastener system due to overtorque.

    Use a screwdriver (TX20).

    Do not turn the screws more than 180°.

    A quick-fastener system (3) is used to mount the connection area cover and front cover. The system is opened and closed with a half-rotation (180°) of the captive screw (1) into the quick-fastener spring (2).

    The system is independent of torque.

    1. Installation

    Installation location and position

    link_horizontalLink copied

    Choosing the location of the inverter

    NOTE

    Risk from unsuitable choice of location for the inverter.

    Failure or restricted operation of the inverter may result.

    Adhere to the instructions relating to the location, according to this chapter

    Adhere to national provisions and guidelines when installing the inverter.

    Please note the following criteria when choosing a location for the inverter:

     

    Only install on a solid, non-flammable surface.

     

    Max. ambient temperatures:
    -40 °F - +140 °F / -40 °C - 60 °C

     

    Relative humidity:
    0 - 100%

     

    When installing the inverter in a switch cabinet or similar closed environment, it is necessary to make sure that the hot air that develops will be dissipated by forced-air ventilation.

    For more detailed information on inverter dimensions, refer to the chapter headed Dimensions of the inverter on page (→).

    When installing the inverter on the outer walls of cattle sheds, it is important to maintain a minimum clearance of 6.5 ft between all sides of the inverter and the ventilation and building openings.

    The following substrates are permissible for installation:
    • Walls ( non-flammable surfaces sufficiently capable of bearing loads):
      • Corrugated metal walls [mounting rails]
      • Brick walls
      • Concrete walls
      • Vinyl siding walls
      • Wood siding walls
      • Stucco wall
    • Poles (installed using mounting rails, behind the PV modules directly on the PV mounting system)
    • Covered parking lot roofs (no overhead installation)

     

    The inverter is suitable for indoor installation.

     

    The inverter is suitable for outdoor installation.

    When properly installed, the inverter has a Type 4X protection class, is not susceptible to spraying water on any side and can also be operated in moist environments.

     

    In order to keep inverter heating as low as possible, do not expose the inverter to direct sunlight. The inverter should be installed in a protected location, e.g., near the PV modules or under an overhanging roof.

     

    IMPORTANT! The inverter must not be installed or operated at more than 13,123 ft / 4001 m above sea level.

     

    Do not install the inverter:

    • Where it may be exposed to ammonia, corrosive gases, acids or salts (e.g., fertilizer storage areas, vent openings for livestock stables, chemical plants, tanneries, etc.)

     

    During certain operating phases the inverter may produce a slight noise. For this reason it should not be installed in an occupied living area.

     

    Do not install the inverter in:

    • Areas where there is an increased risk of accidents from farm animals (horses, cattle, sheep, pigs, etc.)
    • Stables or adjoining areas
    • Storage areas for hay, straw, chaff, animal feed, fertilizers, etc.

     

    The inverter is essentially designed to be dustproof (Type 4X). In areas of high dust accumulation, dust deposits may collect on the cooling surfaces, and thus impair the thermal performance. Regular cleaning is required in this case; see the chapter headed Operation in dusty environments on page (→). We therefore recommend not installing the inverter in areas and environments with high dust accumulation.

     

    Do not install the inverter in:

    • Greenhouses
    • Storage or processing areas for fruit, vegetables or viticulture products
    • Areas used in the preparation of grain, green fodder or animal feeds
    1. Installation
    2. Installation location and position

    Choosing the location of the inverter

    link_horizontalLink copied

    NOTE

    Risk from unsuitable choice of location for the inverter.

    Failure or restricted operation of the inverter may result.

    Adhere to the instructions relating to the location, according to this chapter

    Adhere to national provisions and guidelines when installing the inverter.

    Please note the following criteria when choosing a location for the inverter:

     

    Only install on a solid, non-flammable surface.

     

    Max. ambient temperatures:
    -40 °F - +140 °F / -40 °C - 60 °C

     

    Relative humidity:
    0 - 100%

     

    When installing the inverter in a switch cabinet or similar closed environment, it is necessary to make sure that the hot air that develops will be dissipated by forced-air ventilation.

    For more detailed information on inverter dimensions, refer to the chapter headed Dimensions of the inverter on page (→).

    When installing the inverter on the outer walls of cattle sheds, it is important to maintain a minimum clearance of 6.5 ft between all sides of the inverter and the ventilation and building openings.

    The following substrates are permissible for installation:
    • Walls ( non-flammable surfaces sufficiently capable of bearing loads):
      • Corrugated metal walls [mounting rails]
      • Brick walls
      • Concrete walls
      • Vinyl siding walls
      • Wood siding walls
      • Stucco wall
    • Poles (installed using mounting rails, behind the PV modules directly on the PV mounting system)
    • Covered parking lot roofs (no overhead installation)

     

    The inverter is suitable for indoor installation.

     

    The inverter is suitable for outdoor installation.

    When properly installed, the inverter has a Type 4X protection class, is not susceptible to spraying water on any side and can also be operated in moist environments.

     

    In order to keep inverter heating as low as possible, do not expose the inverter to direct sunlight. The inverter should be installed in a protected location, e.g., near the PV modules or under an overhanging roof.

     

    IMPORTANT! The inverter must not be installed or operated at more than 13,123 ft / 4001 m above sea level.

     

    Do not install the inverter:

    • Where it may be exposed to ammonia, corrosive gases, acids or salts (e.g., fertilizer storage areas, vent openings for livestock stables, chemical plants, tanneries, etc.)

     

    During certain operating phases the inverter may produce a slight noise. For this reason it should not be installed in an occupied living area.

     

    Do not install the inverter in:

    • Areas where there is an increased risk of accidents from farm animals (horses, cattle, sheep, pigs, etc.)
    • Stables or adjoining areas
    • Storage areas for hay, straw, chaff, animal feed, fertilizers, etc.

     

    The inverter is essentially designed to be dustproof (Type 4X). In areas of high dust accumulation, dust deposits may collect on the cooling surfaces, and thus impair the thermal performance. Regular cleaning is required in this case; see the chapter headed Operation in dusty environments on page (→). We therefore recommend not installing the inverter in areas and environments with high dust accumulation.

     

    Do not install the inverter in:

    • Greenhouses
    • Storage or processing areas for fruit, vegetables or viticulture products
    • Areas used in the preparation of grain, green fodder or animal feeds
    1. Installation
    2. Installation location and position

    Installation position of the inverter

    link_horizontalLink copied

    The inverter is suitable for vertical installation on a vertical wall or column.

    The inverter is suitable for installation on a sloping surface (min. slope of underside 10°).

    Do not install the inverter on a sloping surface with the connections upwards.

    Do not install the inverter in a sloping position on a vertical wall or column.

    Do not install the inverter in a horizontal position on a vertical wall or column.

    Do not install the inverter with the connections upwards on a vertical wall or column.

    Do not install the inverter overhanging with the connections upwards.

    Do not install the inverter overhanging with the connections downwards.

    Do not install the inverter on the ceiling.

    1. Installation

    Knockouts

    link_horizontalLink copied

    Preparing knockouts for connection

    IMPORTANT! The knockouts must be drilled out using a step drill bit only. The maximum conduit sizes are ½ - 1 inch / 13 - 25 mm.

    IMPORTANT! Void warranty if the conduit holes are drilled improperly.

    • Use suitable eye protection when drilling out the knockouts.
    • Avoid drilling too far to ensure the connection area is not damaged.
    • When drilling out the knockouts at the back, place the inverter on an even surface with the back upwards so that shavings and pieces of plastic can fall out of the inverter.
    • If necessary, deburr the knockouts with a suitable tool and remove the drilling residues from the inverter.

    NOTE

    Condensation within the conduits can damage the inverter or components of the photovoltaic systems.

    To avoid undesirable air circulation and condensation in the conduits:

    Attach appropriate conduits to all knockouts that have been drilled open.

    When installing outdoors, only use waterproof conduit fittings and conduits.

    Seal the conduits in accordance with the pictures above on both sides.

    Conduit fittings and conduits are not part of the scope of supply for the inverter.

    1. Installation
    2. Knockouts

    Preparing knockouts for connection

    link_horizontalLink copied

    IMPORTANT! The knockouts must be drilled out using a step drill bit only. The maximum conduit sizes are ½ - 1 inch / 13 - 25 mm.

    IMPORTANT! Void warranty if the conduit holes are drilled improperly.

    • Use suitable eye protection when drilling out the knockouts.
    • Avoid drilling too far to ensure the connection area is not damaged.
    • When drilling out the knockouts at the back, place the inverter on an even surface with the back upwards so that shavings and pieces of plastic can fall out of the inverter.
    • If necessary, deburr the knockouts with a suitable tool and remove the drilling residues from the inverter.

    NOTE

    Condensation within the conduits can damage the inverter or components of the photovoltaic systems.

    To avoid undesirable air circulation and condensation in the conduits:

    Attach appropriate conduits to all knockouts that have been drilled open.

    When installing outdoors, only use waterproof conduit fittings and conduits.

    Seal the conduits in accordance with the pictures above on both sides.

    Conduit fittings and conduits are not part of the scope of supply for the inverter.

    1. Installation

    Installing the mounting bracket and attaching the inverter

    link_horizontalLink copied

    Selecting the mounting material

    Use the corresponding fixing materials depending on the subsurface and observe the screw dimension recommendations for the mounting bracket.
    The installer is responsible for selecting the right type of fixing.

    1. Installation
    2. Installing the mounting bracket and attaching the inverter

    Selecting the mounting material

    link_horizontalLink copied

    Use the corresponding fixing materials depending on the subsurface and observe the screw dimension recommendations for the mounting bracket.
    The installer is responsible for selecting the right type of fixing.

    1. Installation
    2. Installing the mounting bracket and attaching the inverter

    Properties of the mounting bracket

    link_horizontalLink copied

    The mounting bracket (illustration) can also be used as a guide.

    The pre-drilled holes on the mounting bracket are intended for screws with a thread diameter of 6-8 mm (0.24-0.32 inches). The distance from the left to the right pre-drilled hole is 406 mm (16 inches).

    Unevenness on the mounting surface (e.g. coarse-textured plaster) is largely compensated by the mounting bracket.

    1. Installation
    2. Installing the mounting bracket and attaching the inverter

    Do not deform the mounting bracket

    link_horizontalLink copied

    NOTE

    When attaching the mounting bracket to the wall or to a column, make sure that the mounting bracket is not deformed.

    A deformed mounting bracket may make it difficult to clip/swivel the inverter into position.

    1. Installation
    2. Installing the mounting bracket and attaching the inverter

    Fitting the mounting bracket to a wall

    link_horizontalLink copied

    IMPORTANT!
    When installing the mounting bracket, make sure that it is installed with the arrow pointing upwards.

    1
    2
    3
    1. Installation
    2. Installing the mounting bracket and attaching the inverter

    Attaching the mounting bracket to mounting rails

    link_horizontalLink copied

    IMPORTANT!
    The mounting bracket must be affixed at a minimum of four points.

    1. Installation
    2. Installing the mounting bracket and attaching the inverter

    Attaching the inverter to the mounting bracket

    link_horizontalLink copied
    1

    Lift the inverter by the integrated side handles.

    2

    Clip the inverter into the mounting bracket from above. The connections must point downwards.

    Press the lower area of the inverter into the snap-in tabs on the mounting bracket until the inverter engages on both sides with an audible click.

    3Check that the inverter is correctly in position on both sides.
    1. Installation

    Requirements for connecting the inverter

    link_horizontalLink copied

    Different cable types

    Single-core

    Multi-stranded

    Fine-stranded

    Fine-stranded with ferrule and collar

    Fine-stranded with ferrule without collar

    Single-core cable type
    Multi-stranded cable type
    Fine-stranded cable type
    Fine-stranded with ferrule and collar cable type
    Fine-stranded with ferrule without collar cable type
    1. Installation
    2. Requirements for connecting the inverter

    Different cable types

    link_horizontalLink copied

    Single-core

    Multi-stranded

    Fine-stranded

    Fine-stranded with ferrule and collar

    Fine-stranded with ferrule without collar

    Single-core cable type
    Multi-stranded cable type
    Fine-stranded cable type
    Fine-stranded with ferrule and collar cable type
    Fine-stranded with ferrule without collar cable type
    1. Installation
    2. Requirements for connecting the inverter

    Permitted cables for the electrical connection

    link_horizontalLink copied
    "Round copper conductors can be connected to the terminals of the inverter as described below":
    • Copper: round, solid
    • Copper: round, fine-stranded

    Grid connections with push-in terminal *

    Select a sufficiently large cable cross-section based on the actual device output.

    Number of pins

    4

    AWG 12–6 / 4 - 16 mm²

    AWG 12–6 / 4 - 16 mm²

    AWG 12–6 / 4 - 16 mm²

    AWG 12–6 / 4 - 16 mm²

    AWG 12–6 / 4 - 16 mm²

    Grid connections for backup power with push-in terminal *

    Select a sufficiently large cable cross-section based on the actual device output.

    Number of pins

    3

    AWG 16–8 / 1.5 - 10 mm²

    AWG 16–8 / 1.5 - 10 mm²

    AWG 16–8 / 1.5 - 10 mm²

    AWG 16–8 / 1.5 - 10 mm²

    AWG 16–8 / 1.5 - 10 mm²

    PV connections with push-in terminal

    Select a sufficiently large cable cross-section based on the actual device output.

    Number of pins

    2 x 5

    AWG 14–8 / 2.5 - 10 mm²

    AWG 14–8 / 2.5 - 10 mm²

    AWG 14–8 / 2.5 - 10 mm²

    AWG 14–8 / 2.5 - 10 mm²

    AWG 14–8 / 2.5 - 10 mm²

    Ground electrode terminal (6-pin)

    Select a sufficiently large cable cross-section based on the actual device output.

    Number of pins

    2

    AWG 14–6 / 2.5 - 16 mm²

    AWG 14–6 / 2.5 - 16 mm²

    AWG 14–6 / 2.5 - 16 mm²

    AWG 14–6 / 2.5 - 16 mm²

    AWG 14–6 / 2.5 - 16 mm²

    4

    AWG 14–8 / 2.5 - 10 mm²

    AWG 14–8 / 2.5 - 10 mm²

    AWG 14–8 / 2.5 - 10 mm²

    AWG 14–8 / 2.5 - 10 mm²

    AWG 14–8 / 2.5 - 10 mm²

    *
    According to product standards UL1741 3rd Edition, Table 20.1 and CSA-C22.2 No.107.1-16
    1. Installation
    2. Requirements for connecting the inverter

    Permitted cables for the data communication connection

    link_horizontalLink copied
    Cables with the following design can be connected to the terminals of the inverter:
    • Copper: round, solid
    • Copper: round, fine-stranded

    IMPORTANT!
    If several single conductors are connected to an input of the push-in terminal, connect the single conductors with a corresponding ferrule.

    WSD connections with push-in terminal

    Distance

    Stripping length

    Cable recommendation

    100 m 109 yd

    10 mm
    0.39 inch

    0.14-1.5 mm2
    AWG 26-16

    0.14-1.5 mm2
    AWG 26-16

    0.14-1 mm2
    AWG 26-18

    0.14 -1.5 mm2
    AWG 26-16

    Min. CAT 5 UTP (unshielded twisted pair)

    Modbus connections with push-in terminal

    Distance

    Stripping length

    Cable recommendation

    300 m 328 yd

    10 mm 
    0.39 inch

    0.14-1.5 mm2
    AWG 26-16

    0.14-1.5 mm2
    AWG 26-16

    0.14-1 mm2
    AWG 26-18

    0.14-1.5 mm2
    AWG 26-16

    Min. CAT 5 STP (shielded twisted pair)

    IO connections with push-in terminal

    Distance

    Stripping length

    Cable recommendation

    30 m
    32 yd

    10 mm 
    0.39 inch

    0.14-1.5 mm2
    AWG 26-16

    0.14-1.5 mm2
    AWG 26-16

    0.14-1 mm2
    AWG 26-18

    0.14-1.5 mm2
    AWG 26-16

    Single conductors possible

    LAN connections

    Fronius recommends using at least CAT 5 STP (shielded twisted pair) cables and a maximum distance of 100 m (109 yd).

    1. Installation
    2. Requirements for connecting the inverter

    Cable diameter for push-in terminals

    link_horizontalLink copied

    Cable diameter for connection to the push-in terminal: 0.27 inches

    IMPORTANT
    For double-insulated cables with a cable diameter above 0.27 inches, the outer layer of insulation must be removed for the connection to the push-in terminal.

    1. Installation
    2. Requirements for connecting the inverter

    Maximum alternating current fuse protection

    link_horizontalLink copied

    The national regulations of the grid operator or other factors may require a ground fault protection of equipment (GFPE) in the AC connection lead.

    For this situation, a GFPE is generally adequate. Nevertheless, false alarms can be triggered for the GFPE in individual cases and depending on local conditions. For this reason, in accordance with national legislation, Fronius recommends that a GFPE with a tripping current of at least 100 mA suitable for frequency converters be used.

    IMPORTANT! The inverter can be fused with max. an automatic circuit breaker 65 A.

    Inverter

    Phases

    Maximum fuse rating

    Recommended fuse rating ( 208V / 220V / 240 V)

    Primo GEN24 7.7 208-240

    1

    65 A

    50 A / 45 A / 40 A

    Primo GEN24 10.0 208-240

    1

    65 A

    60 A / 60 A / 55 A

    1. Installation

    Connecting the inverter to the public grid (AC side)

    link_horizontalLink copied

    Safety

    WARNING

    Danger from incorrect operation and work that is not carried out properly.

    This can result in severe personal injury and damage to property.

    Read the Installation Instructions and Operating Instructions before installing and commissioning the equipment.

    Only qualified personnel are authorized to commission the inverter and only within the scope of the respective technical regulations.

    WARNING

    Danger from grid voltage and DC voltage from PV modules that are exposed to light.

    An electric shock can be fatal.

    Prior to any connection work, ensure that the inverter is de-energized on the AC side and the DC side.

    Only qualified personnel may connect this equipment to the public grid

    WARNING

    Danger from damaged and/or contaminated terminals.

    This can result in severe personal injury and damage to property.

    Prior to connection work, check the terminals for damage and contamination.

    Remove any contamination while the equipment is de-energized.

    Have defective terminals replaced by an authorized technician.

    1. Installation
    2. Connecting the inverter to the public grid (AC side)

    Safety

    link_horizontalLink copied

    WARNING

    Danger from incorrect operation and work that is not carried out properly.

    This can result in severe personal injury and damage to property.

    Read the Installation Instructions and Operating Instructions before installing and commissioning the equipment.

    Only qualified personnel are authorized to commission the inverter and only within the scope of the respective technical regulations.

    WARNING

    Danger from grid voltage and DC voltage from PV modules that are exposed to light.

    An electric shock can be fatal.

    Prior to any connection work, ensure that the inverter is de-energized on the AC side and the DC side.

    Only qualified personnel may connect this equipment to the public grid

    WARNING

    Danger from damaged and/or contaminated terminals.

    This can result in severe personal injury and damage to property.

    Prior to connection work, check the terminals for damage and contamination.

    Remove any contamination while the equipment is de-energized.

    Have defective terminals replaced by an authorized technician.

    1. Installation
    2. Connecting the inverter to the public grid (AC side)

    Suitable AC grids

    link_horizontalLink copied
    1. Installation
    2. Connecting the inverter to the public grid (AC side)

    Connecting the inverter to the public grid (AC side)

    link_horizontalLink copied

    NOTE

    In grid configurations with neutral conductors, the neutral conductor must be connected in order to operate the inverter.

    It is not possible to operate the inverter in ungrounded grids, e.g., IT grids (insulated grids without ground conductor). The grid power feed operation of the inverter can be adversely affected by an insufficiently dimensioned neutral conductor.

    Make sure that the grid's neutral conductor is grounded.

    Ensure the neutral conductor and live conductor are the same size.

    IMPORTANT! The ground conductor/grounding of the AC cable must be laid so that it is disconnected last in the event of a failure.

    1

    Turn off the automatic circuit breaker. Set the DC disconnector to the "Off" switch position.

    2

    Loosen the five screws of the connection area cover by rotating them 180° to the left using a screwdriver (TX20).
    Remove the connection area cover from the device.

    3

    Press the latch on the back of the terminal and remove the AC terminal.

    4

    Guide the mains cable from below through the cable gland on the right side.

    IMPORTANT!
    The ground conductor must be dimensioned longer and laid with a movement loop so that it is last loaded in the event of a failure of the cable gland.

    5

    Strip the insulation of the single conductors by 0.75 inches.
    The cable cross-section must be selected in accordance with the instructions in Permitted cables for the electrical connection from page (→).

    6

    Lift to open the terminal's operating lever and insert the stripped single conductor into the slot provided as far as it will go.
    Then close the terminal's operating lever until it engages.

    Only one conductor may be connected to each pin.

    The AC cables can be connected to the AC terminals without ferrules.

    L1
    Phase conductor
    Nsens
    Neutral conductor*
    L2
    Phase conductor

    * Valid for grid configurations with neutral conductors.

    7

    Fasten the grounding cable to the ground electrode terminal using a screwdriver (TX20) and a torque of 1.475 ft lbs / 2 Nm.
    Insert the AC terminal into the AC slot until it engages.

    1. Installation

    Connecting solar module strings to the inverter

    link_horizontalLink copied

    General information about PV modules

    To enable suitable PV modules to be chosen and to use the inverter as efficiently as possible, it is important to bear the following points in mind:

    • If insolation is constant and the temperature is falling, the open-circuit voltage of the PV modules will increase. The open-circuit voltage must not exceed the max. permissible system voltage. An open-circuit voltage above the indicated values will damage the inverter, and all warranty rights will become null and void.
    • The temperature coefficients on the data sheet of the PV modules must be observed.
    • Exact values for sizing the PV modules can be obtained using suitable calculation tools, such as the Fronius Solar.creator.

    IMPORTANT! Before connecting up the PV modules, check that the voltage for the PV modules specified by the manufacturer corresponds to the actual measured voltage.

    IMPORTANT!
    Solar module strings must not be grounded.

    1. Installation
    2. Connecting solar module strings to the inverter

    General information about PV modules

    link_horizontalLink copied

    To enable suitable PV modules to be chosen and to use the inverter as efficiently as possible, it is important to bear the following points in mind:

    • If insolation is constant and the temperature is falling, the open-circuit voltage of the PV modules will increase. The open-circuit voltage must not exceed the max. permissible system voltage. An open-circuit voltage above the indicated values will damage the inverter, and all warranty rights will become null and void.
    • The temperature coefficients on the data sheet of the PV modules must be observed.
    • Exact values for sizing the PV modules can be obtained using suitable calculation tools, such as the Fronius Solar.creator.

    IMPORTANT! Before connecting up the PV modules, check that the voltage for the PV modules specified by the manufacturer corresponds to the actual measured voltage.

    IMPORTANT!
    Solar module strings must not be grounded.

    1. Installation
    2. Connecting solar module strings to the inverter

    Safety

    link_horizontalLink copied

    WARNING

    Danger from incorrect operation and work that is not carried out properly.

    This can result in severe personal injury and damage to property.

    The commissioning, maintenance, and service work in the inverter's power stage set may only be carried out by Fronius-trained service personnel in accordance with the technical specifications.

    Read the installation instructions and operating instructions before installing and commissioning the equipment.

    WARNING

    Danger from mains voltage and DC voltage from PV modules that are exposed to light.

    This can result in severe personal injury and damage to property.

    All connection, maintenance, and service work should only be carried out when the AC and DC sides have been disconnected from the inverter and are de-energized.

    Only an authorized electrical engineer is permitted to connect this equipment to the public grid.

    WARNING

    Danger of an electric shock due to improperly connected terminals/PV plug connectors.

    An electric shock can be fatal.

    When connecting, ensure that each pole of a string is routed via the same PV input, e.g.:
    + pole string 1 to the input PV 1.1+ and - pole string 1 to the input PV 1.1-

    WARNING

    Danger from damaged and/or contaminated terminals.

    This can result in severe personal injury and damage to property.

    Prior to connection work, check the terminals for damage and contamination.

    Remove any contamination while the equipment is de-energized.

    Have defective terminals replaced by an authorized specialist company.

    1. Installation
    2. Connecting solar module strings to the inverter

    PV Generator, general

    link_horizontalLink copied

    Two independent PV inputs (PV 1 and PV 2) are available. These inputs can be connected to a different number of modules.

    When starting for the first time, set up the PV Generator in accordance with the respective configuration (can also be carried out at a later date in the Device Configuration > Components menu area).

    1. Installation
    2. Connecting solar module strings to the inverter

    Module array configuration 7.7 ‑ 10.0 kW

    link_horizontalLink copied

    IMPORTANT!
    The installation must be carried out in accordance with the nationally applicable standards and directives.If the Arc Fault Circuit Interrupter integrated in the inverter is used for the arc detection requirement according to IEC 63027, the solar module strings must not be combined in front of the inverter.

    Current equal to or less than 22 A (Idcmax).

    Module array settings:
    PV 1: ON
    PV 2: OFF

    IMPORTANT!
    The maximum current load of a single terminal is 22 A.

    PV 1 less than or equal to 41.25 A (ISC PV1)
    PV 2 less than or equal to 36 A (ISC PV2)

    Module array settings:
    PV 1: ON
    PV 2: ON

    IMPORTANT!
    It is not allowed to connect PV1 and PV2 in parallel, as otherwise currents of over 22A per terminal connection could flow.

    1. Installation
    2. Connecting solar module strings to the inverter

    Connecting solar module strings to the inverter

    link_horizontalLink copied
    1

    Disconnect connections from the solar module strings (+/-).

    2

    Guide the DC cables through the electrical installation tube.

    IMPORTANT!
    Guide the cables through the electrical installation tube before stripping them in order to avoid twisting/bending single wires.

    3

    WARNING

    Danger from loose and/or incorrectly clamped single conductors in the terminal.

    This can result in severe personal injury and damage to property.

    Only connect one single conductor at each slot provided in the terminal.

    Check that the single conductors are secure in the terminal.

    Make sure that the single conductor has been fully inserted into the terminal and that no single wires are protruding out of the terminal.

    4

    Select the cable cross-section in accordance with the instructions in Permitted cables for the electrical connection from page (→).
    Strip the insulation of the single conductors by 0.47 inches.

    5

    Lift to open the terminal's operating lever and insert the stripped single conductor into the slot provided, in each case as far as it will go. Then close the operating lever until it engages.

    6

    Connect the solar module strings (+/-).

    7


    Use a suitable measuring instrument to check the voltage and polarity of the DC cabling. Remove both DC terminals from the slots.

    CAUTION

    Danger due to polarity reversal at the terminals.

    This may result in severe damage to the inverter.

    Use a suitable measuring instrument to check the polarity of the DC cabling.

    Use a suitable measuring instrument to check the voltage (max. 600 VDC)

    8

    Insert the DC terminals into the respective slot until they engage.

    1. Installation

    Connecting the battery to the inverter

    link_horizontalLink copied

    Safety

    WARNING

    Danger due to incorrect operation and incorrectly performed work.

    This can result in serious injury and damage to property.

    Only a technical specialist is permitted to perform commissioning, maintenance, and service activities for inverters and batteries, and only within the scope of the technical regulations.

    Read the installation instructions and operating instructions from the respective manufacturer before installing and commissioning the equipment.

    WARNING

    Danger from mains voltage and DC voltage from the PV module that are exposed to light, as well as batteries.

    This can result in serious injury and damage to property.

    All connection, maintenance, and service work should only be carried out when the AC and DC sides have been disconnected from the inverter and battery, and are de-energized.

    Only a technical specialist is permitted to connect this equipment to the public grid.

    WARNING

    Danger from damaged and/or contaminated terminals.

    This can result in serious injury and damage to property.

    Prior to connection work, check the terminals for damage and contamination.

    Remove any contamination while the equipment is de-energized.

    Have defective terminals repaired by a technical specialist.

    1. Installation
    2. Connecting the battery to the inverter

    Safety

    link_horizontalLink copied

    WARNING

    Danger due to incorrect operation and incorrectly performed work.

    This can result in serious injury and damage to property.

    Only a technical specialist is permitted to perform commissioning, maintenance, and service activities for inverters and batteries, and only within the scope of the technical regulations.

    Read the installation instructions and operating instructions from the respective manufacturer before installing and commissioning the equipment.

    WARNING

    Danger from mains voltage and DC voltage from the PV module that are exposed to light, as well as batteries.

    This can result in serious injury and damage to property.

    All connection, maintenance, and service work should only be carried out when the AC and DC sides have been disconnected from the inverter and battery, and are de-energized.

    Only a technical specialist is permitted to connect this equipment to the public grid.

    WARNING

    Danger from damaged and/or contaminated terminals.

    This can result in serious injury and damage to property.

    Prior to connection work, check the terminals for damage and contamination.

    Remove any contamination while the equipment is de-energized.

    Have defective terminals repaired by a technical specialist.

    1. Installation
    2. Connecting the battery to the inverter

    Connecting the battery on the DC side

    link_horizontalLink copied

    CAUTION

    Danger due to operation of the battery above the permissible altitude as specified by the manufacturer.

    Operating the battery above the permissible altitude can result in restricted operation, failure of the operation, and unsafe states of the battery.

    Adhere to the manufacturer's instructions regarding the permissible altitude.

    Operate the battery only at the altitude specified by the manufacturer.

    IMPORTANT!
    Prior to installing a battery, ensure that the battery is switched off. The max. DC cable length for the installation of external batteries must be taken into account according to the manufacturer's specifications, see chapter Suitable batteries on page (→).

    1

    Manually push the battery cables through the DC bushings.

    * The battery ground conductor must be connected to the ground electrode terminal of the inverter,

    IMPORTANT!
    Before stripping the insulation, push the cables through the DC bushings to prevent individual wires being bent or broken.

    2

    Remove the DC push-in terminals from the slots.

    WARNING

    Danger due to individual conductors in the terminal that are loose and/or improperly connected.

    This can result in serious injury and damage to property.

    Only connect one single conductor in the slot provided for each terminal.

    Check that the single conductor is held securely in the terminal.

    Ensure that all of the single conductor is within the terminal and that no individual wire strands are sticking out of the terminal.

    3

    Select the cable cross-section in accordance with the instructions in Permitted cables for the electrical connection from page (→).
    Strip the insulation of the single conductors by 0.47 inches.

    4

    Lift to open the terminal's operating lever and insert the stripped single conductor into the slot provided, in each case as far as it will go. Then close the operating lever until it engages.

    CAUTION

    Danger due to overvoltage when using other slots on the terminal.

    This may result in damage to the battery and/or the PV modules due to discharge.

    Only use the slots labeled "BAT" for connecting the battery.

    5

    CAUTION

    Danger due to polarity reversal at the terminals.

    Serious damage to the PV system may result.

    Use a suitable measuring instrument to check the polarity of the DC cabling when the battery is switched on.

    The maximum voltage for the battery input must not be exceeded (see Technical data on page (→)).

    6

    Insert the DC terminals into the respective slot until they engage.

    IMPORTANT! Information for the battery-side connection can be found in the installation instructions from the relevant manufacturer.

    1. Installation

    Connecting backup power - PV Point (OP)

    link_horizontalLink copied

    Safety

    WARNING

    Danger from incorrect installation, commissioning, operation or incorrect use.

    This can result in severe personal injury and damage to property.

    Single 120 / 220 / 240 volt supply. Do not connect multi-wire branch circuits!

    Only trained and qualified personnel are authorized to install and commission the system, and only within the scope of the technical regulations.

    The Installation Instructions and Operating Instructions must be read carefully prior to use.

    If anything is unclear, contact your vendor immediately.

    WARNING

    Danger from damaged and/or contaminated terminals.

    This can result in severe personal injury and damage to property.

    Prior to connection work, check the terminals for damage and contamination.

    Remove any contamination while the equipment is de-energized.

    Have defective terminals replaced by an authorized technician.

    WARNING

    Limited rapid shutdown function in backup power mode (PV Point and Essential Backup)

    If PV Point or Essential Backup is configured, rapid shutdown cannot be triggered via the loss of grid connection. This can result in serious personal injury and damage to the PV system.

    A WSD switch must be installed for all backup power modes (PV-Point and Essential Backup) (see Installing the WSD (wired shutdown)). The rapid shutdown is then triggered via WSD.

    NOTE

    Power supply via the PV point is dependent on the available PV power

    If the PV modules are not supplying enough power, interruptions may occur.

    Do not connect any loads that require an interruption-free supply.

    IMPORTANT!
    The valid national laws, standards, and provisions, as well as the specifications of the relevant grid operator are to be taken into account and applied.
    It is highly recommended that the specific installation be agreed with the grid operator and explicitly approved by this operator. This obligation applies to system constructors in particular (e.g., installers).

    1. Installation
    2. Connecting backup power - PV Point (OP)

    Safety

    link_horizontalLink copied

    WARNING

    Danger from incorrect installation, commissioning, operation or incorrect use.

    This can result in severe personal injury and damage to property.

    Single 120 / 220 / 240 volt supply. Do not connect multi-wire branch circuits!

    Only trained and qualified personnel are authorized to install and commission the system, and only within the scope of the technical regulations.

    The Installation Instructions and Operating Instructions must be read carefully prior to use.

    If anything is unclear, contact your vendor immediately.

    WARNING

    Danger from damaged and/or contaminated terminals.

    This can result in severe personal injury and damage to property.

    Prior to connection work, check the terminals for damage and contamination.

    Remove any contamination while the equipment is de-energized.

    Have defective terminals replaced by an authorized technician.

    WARNING

    Limited rapid shutdown function in backup power mode (PV Point and Essential Backup)

    If PV Point or Essential Backup is configured, rapid shutdown cannot be triggered via the loss of grid connection. This can result in serious personal injury and damage to the PV system.

    A WSD switch must be installed for all backup power modes (PV-Point and Essential Backup) (see Installing the WSD (wired shutdown)). The rapid shutdown is then triggered via WSD.

    NOTE

    Power supply via the PV point is dependent on the available PV power

    If the PV modules are not supplying enough power, interruptions may occur.

    Do not connect any loads that require an interruption-free supply.

    IMPORTANT!
    The valid national laws, standards, and provisions, as well as the specifications of the relevant grid operator are to be taken into account and applied.
    It is highly recommended that the specific installation be agreed with the grid operator and explicitly approved by this operator. This obligation applies to system constructors in particular (e.g., installers).

    1. Installation
    2. Connecting backup power - PV Point (OP)

    Connecting backup power - PV Point (OP)

    link_horizontalLink copied

    All loads that are to be supplied via the OP terminal must be protected by means of a ground fault circuit interrupter.
    In order to ensure the ground fault circuit interrupter operates properly, a connection must be established between the neutral conductor N' (OP) and equipment grounding (GND).

    Wiring proposal recommended by Fronius, see page (→).

    1

    Turn off the automatic circuit breaker. Set the DC disconnector to the "Off" switch position.

    2

    Loosen the five screws of the connection area cover by rotating them 180° to the left using a screwdriver (TX20).
    Remove the connection area cover from the device.

    CAUTION

    Danger from faulty or incorrect bores.

    This may lead to injuries to the eyes and hands as a result of flying debris and sharp edges, as well as damage to the inverter.

    When drilling, wear suitable protective goggles.

    Only use a step drill when drilling.

    Ensure that nothing on the inside of the device is damaged (e.g., the connection block).

    Adapt the diameter of the bore to match the corresponding connection.

    Deburr the bores using a suitable tool.

    Remove the drilling residues from the inverter.

    3

    Drill out the knockout with a step drill.

    4Insert the conduit into the knockout and fasten it using the torque specified by the manufacturer. Seal the conduit as per the chapter headed Preparing knockouts for connection on page (→).
    5

    Guide the mains cable through the conduit from below.
    Remove the OP terminal.

    WARNING

    Danger from loose and/or incorrectly clamped single conductors in the terminal.

    This can result in serious injury and damage to property.

    Only connect one single conductor at each slot provided in the terminal.

    Check that the single conductors are secure in the terminal.

    Make sure that the single conductor has been fully inserted into the terminal and that no single wires are protruding out of the terminal.

    6

    Strip the insulation of the single conductors by 0.47 inches / 12 mm.
    The cable cross-section must be between AWG 16 and AWG 8.

    Lift to open the terminal's operating lever and insert the stripped single conductor into the slot provided, all the way up to the stop. Then close the operating lever until it engages.

    7

    Lift to open the terminal's operating lever and insert the stripped single conductor into the slot provided, in each case as far as it will go. Then close the operating lever until it engages.

    8
    L1´
    Phase conductor
    N´
    Neutral conductor
    N´
    Ground conductor

    The ground conductor must have a cross-section of AWG 14-8.

    9

    Fasten the ground conductor and PEN conductor to the ground electrode terminal using a screwdriver (TX20) and a torque of 1.47 ft-lbs / 2 Nm.

    10

    Insert the OP terminal into the OP slot until it engages.

    1. Installation
    2. Connecting backup power - PV Point (OP)

    Testing backup power mode

    link_horizontalLink copied
    Testing backup power mode:
    • during first-time installation and configuration
    • after working on the switch cabinet
    • during ongoing operation (recommendation: at least every 6 months)

    A battery charge of min. 30% is recommended for test mode.

    A description of how to run the test mode can be found in the checklist – Backup power (https://www.fronius.com/de/download-center?searchword=42,0426,0365).

    1. Installation

    Connecting the data communication cables

    link_horizontalLink copied

    Modbus participants

    Inputs M0 and M1 can be selected for this purpose. A maximum of 4 Modbus participants can be connected to the Modbus terminal on inputs M0 and M1.

    IMPORTANT! Only one primary meter and one battery can be connected per inverter. Due to the high data transfer of the battery, the battery occupies 2 participants. If the "Inverter control via Modbus" function is activated in the "Communication” → "Modbus" menu, no Modbus participants are possible. It is not possible to send and receive data at the same time.

    Example 1:

    Input

    Battery

    Quantity
    Primary meter

    Quantity
    Secondary meter

    Modbus 0
    (M0)

    0

    4

    0

    2

    0

    1

    Modbus 1
    (M1)

    1

    3

    Example 2:

    Input

    Battery

    Quantity
    Primary meter

    Quantity
    Secondary meter

    Modbus 0
    (M0)

    1

    3

    Modbus 1
    (M1)

    0

    4

    0

    2

    0

    1

    1. Installation
    2. Connecting the data communication cables

    Modbus participants

    link_horizontalLink copied

    Inputs M0 and M1 can be selected for this purpose. A maximum of 4 Modbus participants can be connected to the Modbus terminal on inputs M0 and M1.

    IMPORTANT! Only one primary meter and one battery can be connected per inverter. Due to the high data transfer of the battery, the battery occupies 2 participants. If the "Inverter control via Modbus" function is activated in the "Communication” → "Modbus" menu, no Modbus participants are possible. It is not possible to send and receive data at the same time.

    Example 1:

    Input

    Battery

    Quantity
    Primary meter

    Quantity
    Secondary meter

    Modbus 0
    (M0)

    0

    4

    0

    2

    0

    1

    Modbus 1
    (M1)

    1

    3

    Example 2:

    Input

    Battery

    Quantity
    Primary meter

    Quantity
    Secondary meter

    Modbus 0
    (M0)

    1

    3

    Modbus 1
    (M1)

    0

    4

    0

    2

    0

    1

    1. Installation
    2. Connecting the data communication cables

    Routing data communication cables

    link_horizontalLink copied
    1

    Drill out the knockout with a step drill.

    2Insert the conduit into the hole and fasten it using the torque specified by the manufacturer. Seal the conduit as per the chapter headed Preparing knockouts for connection on page (→).
    3Run the data communication cables through the electrical installation tube from below.
    1. Installation
    2. Connecting the data communication cables

    Connecting the battery communication cable

    link_horizontalLink copied
    1

    Strip 10 mm/ 0.39 inch from the single conductors and mount the ferrules if necessary.

    IMPORTANT!
    Connect the individual conductors to an appropriate ferrule if several individual conductors are connected to one input of the push-in terminals.

    2

    Insert the cable into the respective slot and check the cable is securely retained.

    IMPORTANT! Use a twisted cable pair for corresponding data cables.

    Twist the cable shield and insert into the "Shield" slot.

    IMPORTANT! Improperly fitted shielding can cause data communication problems.

    Ihr Browser kann diesen Film leider nicht anzeigen.
    1.
    Disconnect the terminal.
    2.
    Lay the data communication cable. Press in the seal until it reaches the underside of the cable gland.

    For the wiring proposal recommended by Fronius, see page (→).

    1. Installation
    2. Connecting the data communication cables

    Terminating resistors

    link_horizontalLink copied

    It may be possible for the system to function without terminating resistors. However, owing to interference, the use of terminating resistors according to the following overview is recommended for trouble-free operation.

    For permissible cables and max. distances for the data communication area, refer to the chapter headed Permitted cables for the data communication connection on page (→).

    IMPORTANT!Terminating resistors that are not positioned as illustrated can result in interference in the data communication.

    1. Installation
    2. Connecting the data communication cables

    Installing the WSD (wired shutdown)

    link_horizontalLink copied

    WARNING

    Limited rapid shutdown function in backup power mode (PV Point and Essential Backup)

    If PV Point or Essential Backup is configured, rapid shutdown cannot be triggered via the loss of grid connection. This can result in serious personal injury and damage to the PV system.

    A WSD switch must be installed for all backup power modes (PV-Point and Essential Backup) (see Installing the WSD (wired shutdown)). The rapid shutdown is then triggered via WSD.

    IMPORTANT! The push-in WSD terminal in the inverter's connection area is delivered with a bypass ex works as standard. The bypass must be removed when installing a trigger device or a WSD chain.

     

    Installing a Rapid Shutdown Initiator Switch

    If a rotary switch for initiating the Rapid Shutdown is needed (e.g. as an Emergency Stop for backup systems), install the Fronius Rapid Shutdown Initiator Switch (42,0440,0338) as described below:

    1Open the front face of the enclosure by loosening two screws.
    2Mount the enclosure with two screws (max. diameter 0.17 inch / 4.3 mm). The installer is responsible for selecting the right type of fixing.
    3Create wiring conduit in the top/bottom portion of the enclosure.
    4

    Connect signal wires (AWG 12).

    5

    Mount the switch in the enclosure.

    6Close the enclosure.
    7

    Connect signal wires with the push-in WSD terminal.

    WSD Chain

    The WSD switch of the first inverter with connected trigger device in the WSD chain must be in position 1 (master). The WSD switch of all other inverters should be in position 0 (slave).

    Max. distance between two devices: 109 yd / 100 m
    max. number of devices: 28

    * Floating contact of the trigger device (e.g., central grid and system protection). If several floating contacts are used in a WSD chain, these must be connected in series.

    1. Installation

    Closing and commissioning the inverter

    link_horizontalLink copied

    Closing the inverter's connection area/housing cover, and commissioning

    NOTE

    The housing cover is fitted with a lock for safety reasons, which allows the housing cover on the inverter to be pivoted only when the DC disconnector is switched off.

     

    Only clip and pivot the housing cover onto the inverter when the DC disconnector is switched off.

    Do not use excessive force to clip in and pivot the housing cover.

    1

    Place the cover on the connection area. Tighten the five screws by rotating them 180° to the right in the indicated order using a screwdriver (TX20).

    2

    Clip the housing cover into the inverter from above.
    Press on the lower part of the housing cover and tighten the 2 screws by rotating them 180° to the right using a screwdriver (TX20).

    3

    Turn the DC disconnector to the "On" switch position. Switch on the automatic circuit breaker. For systems with a battery, observe the switch-on sequence as per chapter Suitable batteries on page (→).

    IMPORTANT! Open WLAN Access Point with the optical sensor, see chapter Button functions and LED status indicator on page (→)

    1. Installation
    2. Closing and commissioning the inverter

    Closing the inverter's connection area/housing cover, and commissioning

    link_horizontalLink copied

    NOTE

    The housing cover is fitted with a lock for safety reasons, which allows the housing cover on the inverter to be pivoted only when the DC disconnector is switched off.

     

    Only clip and pivot the housing cover onto the inverter when the DC disconnector is switched off.

    Do not use excessive force to clip in and pivot the housing cover.

    1

    Place the cover on the connection area. Tighten the five screws by rotating them 180° to the right in the indicated order using a screwdriver (TX20).

    2

    Clip the housing cover into the inverter from above.
    Press on the lower part of the housing cover and tighten the 2 screws by rotating them 180° to the right using a screwdriver (TX20).

    3

    Turn the DC disconnector to the "On" switch position. Switch on the automatic circuit breaker. For systems with a battery, observe the switch-on sequence as per chapter Suitable batteries on page (→).

    IMPORTANT! Open WLAN Access Point with the optical sensor, see chapter Button functions and LED status indicator on page (→)

    1. Installation
    2. Closing and commissioning the inverter

    Starting the inverter for the first time

    link_horizontalLink copied

    When starting the inverter for the first time, various setup settings must be configured.

    If the setup is canceled before completion, the input data is not saved and the start screen with the installation wizard is shown once again. The data is saved in the event of an interruption, e.g., a power failure. Commissioning is continued at the point at which the interruption occurred after the power supply is restored. If the setup was interrupted, the inverter feeds energy into the grid at maximum 500 W and the operating status LED flashes yellow.

    The country setup can only be set when starting the inverter for the first time. If the country setup needs to be changed at a later date, contact your installer/technical support.

    1. Installation
    2. Closing and commissioning the inverter

    Installation with the app

    link_horizontalLink copied

    The Fronius Solar.start app is required for installation. Depending on the mobile device used to perform the installation, the app is available on the relevant platform.

    1Download and install the Fronius Solar.start app.
    2Open the access point by touching the sensor    .
    ✓Communication LED flashes blue.
    3Open the Fronius Solar.start app and follow the installation wizard. Scan the QR code on the rating plate with a smartphone or tablet to connect to the inverter.
    4Add system components in Fronius Solar.web and commission the PV system.

    The network wizard and product setup can be performed independently. A network connection is required for the Fronius Solar.web installation wizard.

    1. Installation
    2. Closing and commissioning the inverter

    Installation with the browser

    link_horizontalLink copied

    The network wizard and product setup can be performed independently. A network connection is required for the Fronius Solar.web installation wizard.

    WiFi:

    1Open the access point by touching the sensor    .
    ✓Communication LED flashes blue.
    2Establish the connection to the inverter in the network settings (the inverter is displayed with the name "FRONIUS_" and the serial number of the device).
    3Enter the password from the rating plate and confirm.
    IMPORTANT!
    To enter the password, first select the Connect using a security key instead link in order to establish the connection with the password.
    4Enter the IP address 192.168.250.181 in the address bar of the browser and confirm. The installation wizard opens.
    5Follow the installation wizard and complete the installation in the individual areas.
    6Add the system components in Fronius Solar.web and commission the PV system.

    Ethernet:

    1Establish a connection to the inverter (LAN1) using a network cable (min. CAT5 STP).
    2Open the access point by touching the sensor once    .
    ✓Communication LED flashes blue.
    3Enter the IP address 169.254.0.180 in the address bar of the browser and confirm. The installation wizard opens.
    4Follow the installation wizard and complete the installation in the individual areas.
    5Add the system components in Fronius Solar.web and commission the PV system.
    1. Installation

    De-energizing the inverter and switching it back on

    link_horizontalLink copied

    De-energizing the inverter and switching it back on

    Disconnecting the inverter from the power supply:
    1Turn off the automatic circuit breaker.
    2Turn the DC disconnector to the "off" switch setting.

    IMPORTANT! Wait for the capacitors of the inverter to discharge (2 minutes). The DC disconnector interrupts the power supply to the photovoltaic and battery connections.

    Switching on the inverter:
    If the inverter has not been in operation for six months or more, test it before starting up. For systems with a battery, observe the switch-on sequence in chapter Suitable batteries.
    1Turn the DC disconnector to the "on" switch setting.
    2Turn on the automatic circuit breaker.
    1. Installation
    2. De-energizing the inverter and switching it back on

    De-energizing the inverter and switching it back on

    link_horizontalLink copied
    Disconnecting the inverter from the power supply:
    1Turn off the automatic circuit breaker.
    2Turn the DC disconnector to the "off" switch setting.

    IMPORTANT! Wait for the capacitors of the inverter to discharge (2 minutes). The DC disconnector interrupts the power supply to the photovoltaic and battery connections.

    Switching on the inverter:
    If the inverter has not been in operation for six months or more, test it before starting up. For systems with a battery, observe the switch-on sequence in chapter Suitable batteries.
    1Turn the DC disconnector to the "on" switch setting.
    2Turn on the automatic circuit breaker.

    Settings – User interface of the inverter

    link_horizontalLink copied

    User settings

    User login

    1Open the user interface of the inverter in the browser.
    2In the Login menu area, log in with username and password, or, in the User > User Login menu area, log in with username and password.

    IMPORTANT!
    Depending on the authorization of the user, settings can be made in the individual menu areas.

    1. Settings – User interface of the inverter

    User settings

    link_horizontalLink copied

    User login

    1Open the user interface of the inverter in the browser.
    2In the Login menu area, log in with username and password, or, in the User > User Login menu area, log in with username and password.

    IMPORTANT!
    Depending on the authorization of the user, settings can be made in the individual menu areas.

    1. Settings – User interface of the inverter
    2. User settings

    User login

    link_horizontalLink copied
    1Open the user interface of the inverter in the browser.
    2In the Login menu area, log in with username and password, or, in the User > User Login menu area, log in with username and password.

    IMPORTANT!
    Depending on the authorization of the user, settings can be made in the individual menu areas.

    1. Settings – User interface of the inverter
    2. User settings

    Selecting languages

    link_horizontalLink copied
    1In the User > Language menu area, select the desired language.
    1. Settings – User interface of the inverter

    Device configuration

    link_horizontalLink copied

    Components

    Select "Add component+" to add all available components to the system.

    PV Generator
    Activate the MPP tracker and enter the connected PV power in the associated field. For combined solar module strings, "PV 1 + PV 2 connected in parallel" must be activated.

    Battery
    If the SoC mode is set to "Automatic", the values "Minimum SoC" and "Maximum SoC" are preset according to the technical specifications of the battery manufacturer.

    If the SoC mode is set to "Manual", the values "Minimum SoC" and "Maximum SoC" may be changed after consultation with the battery manufacturer within the scope of their technical specifications. In the event of a power outage requiring backup power, the set values are not taken into account.

    Charging of the battery from other external producers is enabled/disabled using the "Allow battery charging from additional producers in home network" setting.

    Charging of the battery from the public grid is enabled/disabled using the "Allow battery charging from public grid" setting.
    The normative or feed-in tariff rules must be taken into account with this setting. The setting does not affect the charging of the battery by other producers within the home. It merely relates to the process of drawing charging energy from the public grid. Regardless of this setting, any charging from the public grid that is required for service reasons (e.g., necessary re-charging to protect against deep discharge) is still performed.

    IMPORTANT!
    Fronius accepts no liability for damage to third-party batteries.

    Primary meter
    To ensure smooth operation in conjunction with other energy producers and in Essential Backup backup power mode, it is important to install the Fronius Smart Meter at the feed-in point. The inverter and other producers must be connected to the public grid via the Fronius Smart Meter.
    This setting also affects the behavior of the inverter at night. If the function is deactivated, the inverter switches to Standby mode as soon as there is no more PV power available, provided that no energy management command is sent to the battery (e.g., minimum state of charge reached). The message "Power low" is displayed. The inverter restarts as soon as an energy management command is sent or sufficient PV power is available.
    If the function is activated, the inverter remains permanently connected to the grid so that energy can be drawn from other producers at any time.
    After connecting the meter, the position must be configured. A different Modbus address needs to be set for each Smart Meter.
    The watt value on the generator meter is the sum of all generator meters. The watt value on the consumption meter is the value of all secondary meters.

    1. Settings – User interface of the inverter
    2. Device configuration

    Components

    link_horizontalLink copied

    Select "Add component+" to add all available components to the system.

    PV Generator
    Activate the MPP tracker and enter the connected PV power in the associated field. For combined solar module strings, "PV 1 + PV 2 connected in parallel" must be activated.

    Battery
    If the SoC mode is set to "Automatic", the values "Minimum SoC" and "Maximum SoC" are preset according to the technical specifications of the battery manufacturer.

    If the SoC mode is set to "Manual", the values "Minimum SoC" and "Maximum SoC" may be changed after consultation with the battery manufacturer within the scope of their technical specifications. In the event of a power outage requiring backup power, the set values are not taken into account.

    Charging of the battery from other external producers is enabled/disabled using the "Allow battery charging from additional producers in home network" setting.

    Charging of the battery from the public grid is enabled/disabled using the "Allow battery charging from public grid" setting.
    The normative or feed-in tariff rules must be taken into account with this setting. The setting does not affect the charging of the battery by other producers within the home. It merely relates to the process of drawing charging energy from the public grid. Regardless of this setting, any charging from the public grid that is required for service reasons (e.g., necessary re-charging to protect against deep discharge) is still performed.

    IMPORTANT!
    Fronius accepts no liability for damage to third-party batteries.

    Primary meter
    To ensure smooth operation in conjunction with other energy producers and in Essential Backup backup power mode, it is important to install the Fronius Smart Meter at the feed-in point. The inverter and other producers must be connected to the public grid via the Fronius Smart Meter.
    This setting also affects the behavior of the inverter at night. If the function is deactivated, the inverter switches to Standby mode as soon as there is no more PV power available, provided that no energy management command is sent to the battery (e.g., minimum state of charge reached). The message "Power low" is displayed. The inverter restarts as soon as an energy management command is sent or sufficient PV power is available.
    If the function is activated, the inverter remains permanently connected to the grid so that energy can be drawn from other producers at any time.
    After connecting the meter, the position must be configured. A different Modbus address needs to be set for each Smart Meter.
    The watt value on the generator meter is the sum of all generator meters. The watt value on the consumption meter is the value of all secondary meters.

    1. Settings – User interface of the inverter
    2. Device configuration

    Functions and
    I/Os

    link_horizontalLink copied

    Backup power
    Off, PV Point, or Essential Backup can be selected for backup power mode.
    Essential Backup backup power mode can only be activated once the required I/O assignments have been configured for backup power. In addition, a meter must be mounted and configured at the feed-in point for Essential Backup backup power mode.

    IMPORTANT!
    When configuring PV Point backup power mode, the information in chapter Safety on page (→) must be observed.

    Backup power nominal voltage
    When backup power mode is activated, the nominal voltage of the public grid must be selected.

    State of charge warning limit
    A warning is output when the residual capacity of the battery specified here is reached in backup power mode.

    Reserve capacity
    The set value results in a residual capacity (depending on the capacity of the battery) that is reserved for backup power. The battery is not discharged below the residual capacity in grid-connected operation. In backup power mode, the manually set value Minimum SoC is not taken into account. If there is a power outage, the battery is always discharged down to the automatically preset minimum SoC in accordance with the technical specifications of the battery manufacturer.

    Load management
    Up to 4 pins can be selected for load management here. Additional load management settings are available in the Load management menu item.
    Default: Pin 1

    1. Settings – User interface of the inverter
    2. Device configuration

    Inverter

    link_horizontalLink copied

    Enforce Standby
    When the function is activated, the feed-in mode of the inverter is interrupted. This enables a powerless shutdown of the inverter and protects its components. When the inverter is restarted, the standby function is automatically deactivated.

    Fan test

    IMPORTANT!
    To view and change settings in this menu item, select the user Technician, and enter and confirm the password for the user Technician. Settings may only be made by trained and qualified personnel.

    This function can be used to check whether the fans of the inverter are working correctly based on acoustics, for example after replacing a fan.

    1Click Start fan test
    ✓The inverter successively activates all fans that are running at partial load during the test phase to avoid unnecessary noise. The inverter is in standby during this time.

    The test takes around 30 seconds per fan. The inverter then switches back to normal operation. The test can be stopped manually using the Stop fan test function.

    PV 1 and PV 2

    Parameter

    Value range

    Description

    Mode

    Off

    The MPP tracker is deactivated.

    Auto

    The inverter uses the voltage at which the max. possible output of the MPP tracker is possible.

    Fixed

    The MPP tracker uses the voltage defined in UDC fixed.

    UDC fixed

    80 ‑ 530 V

    The inverter uses the fixed voltage that is used on the MPP tracker.

    Dynamic Peak Manager

     

    Off

    Function is deactivated.

    On

    The entire solar module string is checked for optimization potential and determines the best possible voltage for the supply of energy from the inverter into the grid.

    On (MLSD)

    The function is optimized for systems with Module Level Shutdown devices (MLSD) and not suitable for PV optimizers.

    Ripple control signal
    Ripple control signals are signals that are sent by the energy company in order to switch controllable loads on and off. Depending on the installation situation, ripple control signals can be dampened or amplified by the inverter. This can be counteracted if necessary by applying the following settings.

    Parameter

    Value range

    Description

    Reduction of influence

    Off

    Function is deactivated.

    On

    Function is activated.

    Frequency of the ripple control signal

    100 ‑ 3000 Hz

    The frequency specified by the energy company must be entered here.

    Grid inductance

    0.00001 ‑ 0.005 H

    The value measured at the infeed point must be entered here.

    Measure against RCD false triggers
    (when using a 30 mA residual current circuit breaker)

    NOTE

    A residual current circuit breaker for the AC connecting cable may be required depending on national regulations, the grid operator, and other conditions.

    A type A residual current circuit breaker is generally sufficient in this case. Nevertheless, false alarms can be triggered for the type A residual current circuit breaker in individual cases and depending on local conditions. For this reason, Fronius recommends using a residual current circuit breaker suitable for frequency inverters with a release current of least 100 mA, taking into account national provisions.

    Parameter

    Wertebereich

    Beschreibung

    Leakage current factor to reduce RCMU/RCD false trips

    0 ‑ 0,25
    (default: 0,16)

    Reducing the setting value reduces the leakage current and raises the intermediate circuit voltage, which slightly reduces the efficiency.

    • Setting value 0.16 enables optimumefficiency.
    • Setting value 0 enables minimalleakage currents.

    Switch-Off before 30mA RCD Trip

    Off

    The function for reducing false tripping of the residual current circuit breaker is deactivated.

    On

    The function for reducing false tripping of the residual current circuit breaker is activated.

    Rated residual non-operating current threshold

    0,015 ‑ 0,3

    The value of residual non-operating current, assigned to the residual current circuit breaker by the manufacturer, at which the residual current circuit breaker does not operate under specified conditions.

    Insulation warning

    Parameter

    Value range

    Description

    Insulation warning

    Off

    The insulation warning is deactivated.

    On

    The insulation warning is activated.
    A warning is output in the event of an insulation fault.

    Insulation measurement mode

     

    Exact

    Insulation monitoring takes place with the highest degree of accuracy and the measured insulation resistance is displayed on the user interface of the inverter.

    Fast

    Insulation monitoring takes place with a lesser degree of accuracy, whereby the time to take the insulation measurement is shortened and the insulation value is not displayed on the user interface of the inverter.

    Threshold for the insulation warning

    100000 ‑
    10000000 Ω

    If the value drops below the threshold, status code 1083 is displayed on the user interface of the inverter.

    Backup power

    Parameter

    Value range

    Description

    Backup power nominal voltage

    120 ‑ 240 V

    The nominal phase voltage that is output in backup power mode.

    Backup power undervoltage protection limit value U< [pu]

    0 ‑ 2 % V

    This set value represents the limit value for shutting down backup power mode.
    e. g., set value 0.9 = 90 % of the nominal voltage.

    Backup Frequency Offset

    -5 - +5 Hz

    The setting value can be used to reduce or increase the nominal backup power frequency (see Technical data) by the offset value. The default value is +3 Hz. Connected loads detect that backup power mode is active based on the change in frequency and react accordingly (e.g., by activating energy saving mode)

    IMPORTANT

    If another AC source is available in the system, the backup power frequency must not be changed. The standard value (+3 Hz) prevents further AC sources from feeding in parallel to the inverter in backup power mode and triggering overvoltages as well as switching off their own backup power supply.

    Backup power undervoltage protection time U<

    0.04 ‑ 20 s

    Trip time for falling below the backup power undervoltage protection limit value.

    Backup power surge protection limit value U> [pu]

    0 ‑ 2 % V

    This set value represents the limit value for shutting down backup power mode.
    e. g., set value 1.1 = 110 % of the nominal voltage.

    Backup power surge protection time U>

    0.04 ‑ 20 s

    Trip time for exceeding the backup power surge protection limit value.

    Backup power restart delay

    0 ‑ 600 s

    Waiting time for restarting backup power mode following a shutdown.

    Backup power restart attempts

    1 ‑ 10

    The max. number of automated restart attempts. Once the max. number of automated restart attempts has been reached, service message 1177 must be manually acknowledged.

    Backup power short circuit switch-off time

    0.001 ‑ 60 s

    If a short circuit occurs during backup power mode, backup power mode is interrupted within the set time.

    1. Settings – User interface of the inverter

    Energy management

    link_horizontalLink copied

    Energy management

    "Self-Consumption Optimization"
    Set the operating mode to "Manual" or "Automatic". The inverter always regulates to the set "Target Value at Feed-In Point". In the "Automatic" operating mode (factory setting), an adjustment is made to 0 W at the feed-in point (maximum self-consumption).

    The "Target Value at Feed-In Point" also applies if a further source feeds into this Smart Meter. However, in this case:
    • The Fronius Smart Meter must be installed and configured at the feed-in point.
    • The "Allow battery charging from additional producers in home network" function must be activated in the "Components" → "Battery" menu area.

    "Target Value at Feed-In Point"
    If "Manual" has been selected under Self-Consumption Optimization, the "Operating Mode" ("Consumption"/"Feed-In") and the "Target Value at Feed-In Point" can be set.

    IMPORTANT!
    "Self-Consumption Optimization" has lower priority than "Battery Management".

    External producers (only possible with active battery)
    If further decentralized producers are installed in the house, and these are incorporated into the self-consumption control of the Fronius Hybrid inverter, the setting "Allow battery charging from additional producers in home network" must be activated in the menu area "Device Configuration" → "Components" (see Components on page (→)
    .This means that energy can be drawn from the home network and fed into the battery via the Fronius inverter (battery support required). You can restrict how much power is consumed by the Fronius inverter by specifying the maximum AC power (AC max.). A maximum power consumption of the AC rated power of the Fronius inverter is possible.

    "Battery Management"
    Using the time-dependent battery control, it is possible to prevent or restrict charging/discharging of the battery and to specify a defined charging power.

    Battery management is influenced by the following settings, for example:
    • Permitted battery charging from the public grid
    • Power limitation of the inverter, energy storage device, or overall system
    • Control specifications via Modbus
    • Self-Consumption Optimization

    IMPORTANT!
    The defined rules for battery control have the second lowest priority after Self-Consumption Optimization. Depending on the configuration, the rules may not be satisfied due to other settings.

    The following values can be selected for the rules of the time-dependent battery control:
    • "Max. charging power"
      The battery is charged to the maximum level with the value set in the "Power" input field.
      If no feed-in to the public grid and/or direct consumption in the house is possible, the set "Max. charging power" value is ignored and the energy generated is charged into the battery.
    • "Min. charging power"
      The battery is charged as a minimum by the value set in the input field "Power".
    • "Max. discharge power"
      The battery is discharged at most by the value set in the input field "Power".
    • "Min. discharge power"
      The battery is discharged as a minimum by the value set in the input field "Power".

    The timing for when the rule applies is set in the "Time" input fields and by selecting the relevant "Weekdays".

    It is not possible to define a time window over midnight (0:00 am).
    Example: To set a control from 10 pm to 6 am, two inputs are required: "10 pm-11:59 pm" and "0:00 am-06 am".

    1. Settings – User interface of the inverter
    2. Energy management

    Energy management

    link_horizontalLink copied

    "Self-Consumption Optimization"
    Set the operating mode to "Manual" or "Automatic". The inverter always regulates to the set "Target Value at Feed-In Point". In the "Automatic" operating mode (factory setting), an adjustment is made to 0 W at the feed-in point (maximum self-consumption).

    The "Target Value at Feed-In Point" also applies if a further source feeds into this Smart Meter. However, in this case:
    • The Fronius Smart Meter must be installed and configured at the feed-in point.
    • The "Allow battery charging from additional producers in home network" function must be activated in the "Components" → "Battery" menu area.

    "Target Value at Feed-In Point"
    If "Manual" has been selected under Self-Consumption Optimization, the "Operating Mode" ("Consumption"/"Feed-In") and the "Target Value at Feed-In Point" can be set.

    IMPORTANT!
    "Self-Consumption Optimization" has lower priority than "Battery Management".

    External producers (only possible with active battery)
    If further decentralized producers are installed in the house, and these are incorporated into the self-consumption control of the Fronius Hybrid inverter, the setting "Allow battery charging from additional producers in home network" must be activated in the menu area "Device Configuration" → "Components" (see Components on page (→)
    .This means that energy can be drawn from the home network and fed into the battery via the Fronius inverter (battery support required). You can restrict how much power is consumed by the Fronius inverter by specifying the maximum AC power (AC max.). A maximum power consumption of the AC rated power of the Fronius inverter is possible.

    "Battery Management"
    Using the time-dependent battery control, it is possible to prevent or restrict charging/discharging of the battery and to specify a defined charging power.

    Battery management is influenced by the following settings, for example:
    • Permitted battery charging from the public grid
    • Power limitation of the inverter, energy storage device, or overall system
    • Control specifications via Modbus
    • Self-Consumption Optimization

    IMPORTANT!
    The defined rules for battery control have the second lowest priority after Self-Consumption Optimization. Depending on the configuration, the rules may not be satisfied due to other settings.

    The following values can be selected for the rules of the time-dependent battery control:
    • "Max. charging power"
      The battery is charged to the maximum level with the value set in the "Power" input field.
      If no feed-in to the public grid and/or direct consumption in the house is possible, the set "Max. charging power" value is ignored and the energy generated is charged into the battery.
    • "Min. charging power"
      The battery is charged as a minimum by the value set in the input field "Power".
    • "Max. discharge power"
      The battery is discharged at most by the value set in the input field "Power".
    • "Min. discharge power"
      The battery is discharged as a minimum by the value set in the input field "Power".

    The timing for when the rule applies is set in the "Time" input fields and by selecting the relevant "Weekdays".

    It is not possible to define a time window over midnight (0:00 am).
    Example: To set a control from 10 pm to 6 am, two inputs are required: "10 pm-11:59 pm" and "0:00 am-06 am".

    1. Settings – User interface of the inverter
    2. Energy management

    Examples - Time-dependent battery control

    link_horizontalLink copied

    The following examples serve to explain the energy flows. Efficiency levels are not taken into account.

    Battery system

    PV system to inverter

    1000 W

    Power into the battery

    500 W

    Power output (AC) of the inverter

    500 W

    Set target value at feed-in point

    0 W

    Infeed into the public grid

    0 W

    Consumption in home

    500 W

     

    Battery system without photovoltaics, including second generator in the house

    Power into the battery

    1500 W

    Power consumption (AC) of the inverter

    1500 W

    Second generator in home network

    2000 W

    Set target value at feed-in point

    0 W

    Infeed into the public grid

    0 W

    Consumption in home

    500 W

     

    Battery system including second generator in the house

    PV system to inverter

    1000 W

    Power into the battery

    2500 W

    Power consumption (AC) of the inverter

    1500 W

    Second generator in home network

    2000 W

    Set target value at feed-in point

    0 W

    Infeed into the public grid

    0 W

    Consumption in home

    500 W

    1. Settings – User interface of the inverter
    2. Energy management

    Permitted battery control regulations

    link_horizontalLink copied

    A regulation always consists of a restriction or specification, and the time and days of the week when the regulation is active. The time of regulations with the same restriction (e.g., max. charging power) must not overlap.

    Max. charging and discharging limits
    One max. charging and one max. discharging power can be configured at the same time.

    Specify charging range
    It is possible to define a charging range using a min. and max. charging limit. In this case, it is not possible to discharge the battery.

    Specify discharging range
    It is possible to define a discharging range using a min. and max. discharging limit. In this case, it is not possible to charge the battery.

    Specify a defined charge
    It is possible to specify a defined charging power by setting the min. and max. charging power to the same value.

    Specify a defined discharge
    It is possible to specify a defined discharging power by setting the min. and max. discharging power to the same value.

    Possible applications

    • Time-dependent energy tariffs
    • Battery reservation in the event of market-specific power limitation
    • Time-dependent storage reservation for a backup power situation
    1. Settings – User interface of the inverter
    2. Energy management

    PV power reduction

    link_horizontalLink copied

    The regulations in the Battery Management menu area enable optimal use of the energy generated. Situations may arise, in which PV power is not used in full due to the time-dependent battery control.

    Example

    Fronius inverter (max. output power)

    6000 W

    Defined discharge of the battery

    6000 W

    PV power

    1000 W

    In this case, the inverter would have to reduce the PV power to 0 W, since the output power of the inverter is max. 6000 W and the device is already being fully utilized through discharging.

    The power control with battery management is automatically adjusted such that no PV power is lost. In this example, the inverter reduces the discharging of the battery to 5000 watts. The 1000 W photovoltaic power is used in this way.

    1. Settings – User interface of the inverter
    2. Energy management

    Load management

    link_horizontalLink copied

    "Rules"
    It is possible for up to four different load management rules to be defined. At the same threshold values, the rules are activated in succession. For deactivation, this is done in reverse; the I/O last switched on is the first to be switched off. In the case of different thresholds, the I/O with the lowest threshold is switched on first, followed by the second lowest, and so on.

    IMPORTANT!
    An I/O is activated/deactivated after 60 seconds.

    "Load"
    • Control is "Off" (deactivated).
    • Control is effected by the "Power generated".
    • Control is effected by "Excess power" (with feed-in limits). This option can only be selected if a meter has been connected. Control is effected using the actual power of feeding in with respect to the grid.
    "Thresholds"
    • "On": For entering an effective power limit, at which the output is activated.
    • "Off": For entering an effective power limit, at which the output is deactivated.
    "Runtimes"
    • Field for activating the "Minimum runtime per switch-on process" for which the output is to be activated for each switch-on process.
    • Field for activating the "Maximum runtime per day".
    • Field for activating the "Target runtime" for which the output is to be activated in total per day (several switch-on processes are allowed for).
    1. Settings – User interface of the inverter

    System

    link_horizontalLink copied

    General

    1Enter the name of the system in the input field PV System Name (max. 30 characters).
    2Select the Timezone Region and Timezone Location in the drop-down lists.
    3Click Save.
    ✓System name, time zone, and time zone location are saved.
    1. Settings – User interface of the inverter
    2. System

    General

    link_horizontalLink copied
    1Enter the name of the system in the input field PV System Name (max. 30 characters).
    2Select the Timezone Region and Timezone Location in the drop-down lists.
    3Click Save.
    ✓System name, time zone, and time zone location are saved.
    1. Settings – User interface of the inverter
    2. System

    Update

    link_horizontalLink copied

    All available updates for inverters and other Fronius devices are provided on the product pages and in the "Fronius Download Search" area at www.fronius.com .

    Update
    1Drag the firmware file into the Drag & drop file here field, or select via Browse file.
    ✓Update is started.
    1. Settings – User interface of the inverter
    2. System

    Setup wizard

    link_horizontalLink copied

    The guided setup wizard can be accessed here.

    1. Settings – User interface of the inverter
    2. System

    Restoring factory settings

    link_horizontalLink copied

    All settings
    Resets all configuration data, apart from the country setup. Changes to the country setup may only be made by authorized personnel.

    All settings without network
    Resets all configuration data, apart from the country setup and the network settings. Changes to the country setup may only be made by authorized personnel.

    1. Settings – User interface of the inverter
    2. System

    Configuration Report

    link_horizontalLink copied

    After the guided setup wizard is finished, a configuration report according to the standards of the Electric Power Research Institute (EPRI) can be created.This function can also be retrieved in the System menu. The report serves as essential documentation to verify that the appropriate settings in compliance with utility requirements have been applied.

    The filename contains the serial number of the inverter and can be changed individually. Click the button to download the report either as a csv or a pdf file.

    1. Settings – User interface of the inverter
    2. System

    Event log

    link_horizontalLink copied

    Current messagesAll current events of the linked system components are displayed here.

    IMPORTANT!
    Depending on the type of event, this must be confirmed via the "tick" button so that it can be further processed.

    History
    All events of the linked system components that are no longer present are displayed here.

    1. Settings – User interface of the inverter
    2. System

    Information

    link_horizontalLink copied

    All the information regarding the system and the current settings is displayed and provided for download in this menu area.

    1. Settings – User interface of the inverter
    2. System

    License Manager

    link_horizontalLink copied

    The power data and functional scope of the inverter are stored in the license file.
    If the inverter, power stage set PC board, or data communication area is replaced, the license file must also be replaced.

    1. Settings – User interface of the inverter
    2. System

    Licensing

    link_horizontalLink copied
    Licensing - online (recommended)
    This requires an Internet connection and a completed Fronius Solar.web configuration.
    1Finish all installation work (refer to the chapter headed Closing the inverter's connection area/housing cover, and commissioning on page (→)).
    2Establish a connection to the user interface of the inverter.
    3Enter the serial number and verification code (VCode) of the defective and replacement device. The serial number and VCode can be found on the rating plate of the inverter (refer to the chapter headed Information on the device on page (→)).
    4Click the Start online licensing button.
    5Skip past the Terms and conditions of use and Network settings menu items by clicking Next.
    ✓License activation is started.
    Licensing - offline
    There must be no Internet connection in this case. If offline licensing is carried out while there is an active Internet connection, the license file is automatically loaded onto the inverter, resulting in the following error when the license file is uploaded: "The license has already been installed and the wizard can be closed".
    1Finish all installation work (refer to the chapter headed Closing the inverter's connection area/housing cover, and commissioning on page (→)).
    2Establish a connection to the user interface of the inverter.
    3Enter the serial number and verification code (VCode) of the defective and replacement device. The serial number and VCode can be found on the rating plate of the inverter (refer to the chapter headed Information on the device on page (→)).
    4Click the Start offline licensing button.
    5Download the service file onto the mobile device by clicking the Download service file button.
    6Open licensemanager.solarweb.com and log in with username and password.
    7Drag the service file into the Drag service file here or click to upload field or click to upload it.
    8Download the newly generated license file onto the mobile device by clicking the Download license file button.
    9Switch to the user interface of the inverter and drag the license file into the Drag & drop license file here field or select via Choose license file.
    ✓License activation is started.
    1. Settings – User interface of the inverter
    2. System

    Support

    link_horizontalLink copied
    Activating the support user
    1Click the Enable Support User Account button.
    ✓The support user is activated.

    IMPORTANT!
    The support user exclusively enables Fronius Technical Support to configure settings on the inverter via a secure connection. Access is deactivated by clicking the Terminate Support User Session button.

    Generating support info (for Fronius Support)
    1Click the Generate support info button.
    2The sdp.cry file is downloaded automatically. For manual download, click the Download support info button.
    ✓The sdp.cry file is saved in the downloads.
    Activating remote access
    1Click the Activate Remote Access button.
    ✓Remote access is activated for Fronius Support.

    IMPORTANT!
    The remote access exclusively enables Fronius Technical Support to access the inverter via a secure connection. In this case, diagnostics data are transmitted, which are used for troubleshooting. The remote access can be activated only upon request by Fronius Support.

    1. Settings – User interface of the inverter

    Communication

    link_horizontalLink copied

    Network

    Server addresses for data transfer
    If a firewall is used for outgoing connections, allow the below protocols, server addresses, and ports for successful data transfer, see:
    https://www.fronius.com/~/downloads/Solar%20Energy/Firmware/SE_FW_Changelog_Firewall_Rules_EN.pdf

    When using FRITZ!Box products, configure Internet access without any restrictions or limitations. Do not set the DHCP Lease Time (validity) to 0 (=infinite).

    LAN:

    Establishing a connection:
    1Enter the host name.
    2Select the connection type: Automatic or Static.
    3For the Static connection type, enter the IP address, subnet mask, DNS, and gateway.
    4Click the Connect button.
    ✓The connection is established.

    After establishing the connection, check the connection status.

    WiFi:

    Establishing a connection via WPS:
      ☐

      Activate the access point of the inverter. This is opened by touching the sensor    > Communications LED flashes blue

    Ihr Browser kann diesen Film leider nicht anzeigen.
    1.
    Establish the connection to the inverter in the network settings (the inverter is displayed with the name "FRONIUS_" and the serial number of the device).
    2.
    Enter the password from the rating plate and confirm.
    IMPORTANT!
    To enter the password, first select the Connect using a security key instead link in order to establish the connection with the password.
    3.
    Enter the IP address 192.168.250.181 in the address bar of the browser and confirm.
    4.
    In the Communication > Network > WLAN > WPS menu area, click the Activate button.
    5.
    Activate WPS on the WiFi router (see WiFi router documentation).
    6.
    Click on the Start button. The connection is established automatically.
    7.
    Log in to the user interface of the inverter.
    8.
    Check the network details and connection to Fronius Solar.web.
    1Establish the connection to the inverter in the network settings (the inverter is displayed with the name "FRONIUS_" and the serial number of the device).
    2Enter the password from the rating plate and confirm.
    IMPORTANT!
    To enter the password, first select the Connect using a security key instead link in order to establish the connection with the password.
    3Enter the IP address 192.168.250.181 in the address bar of the browser and confirm.
    4In the Communication > Network > WLAN > WPS menu area, click the Activate button.
    5Activate WPS on the WiFi router (see WiFi router documentation).
    6Click on the Start button. The connection is established automatically.
    7Log in to the user interface of the inverter.
    8Check the network details and connection to Fronius Solar.web.

    After connecting, the status of the connection should be checked.

    Selecting and connecting to a WiFi network:
    The networks found are displayed in the list. Click the refresh button    to perform a new search for available WiFi networks. If necessary, restrict the selection list further via the Search network input field.
    1Select network from the list.
    2Select the connection type: Automatic or Static.
    3For the Automatic connection type, enter the WiFi password and host name.
    4For the Static connection type, enter the IP address, subnet mask, DNS, and gateway.
    5Click the Connect button.
    ✓The connection is established.

    After establishing the connection, check the connection status.

    Access point:

    The inverter serves as the access point. A PC or mobile device connects directly to the inverter. Connecting to the Internet is not possible. Assign a Network Name (SSID) and Network Key (PSK) to establish a connection. Assign a Network Key (PSK) with at least 20 characters, consisting of upper and lower case letters, special characters, and numbers, to protect the device from unauthorized access.
    It is possible to operate a connection via WiFi and via the access point at the same time.

    1. Settings – User interface of the inverter
    2. Communication

    Network

    link_horizontalLink copied

    Server addresses for data transfer
    If a firewall is used for outgoing connections, allow the below protocols, server addresses, and ports for successful data transfer, see:
    https://www.fronius.com/~/downloads/Solar%20Energy/Firmware/SE_FW_Changelog_Firewall_Rules_EN.pdf

    When using FRITZ!Box products, configure Internet access without any restrictions or limitations. Do not set the DHCP Lease Time (validity) to 0 (=infinite).

    LAN:

    Establishing a connection:
    1Enter the host name.
    2Select the connection type: Automatic or Static.
    3For the Static connection type, enter the IP address, subnet mask, DNS, and gateway.
    4Click the Connect button.
    ✓The connection is established.

    After establishing the connection, check the connection status.

    WiFi:

    Establishing a connection via WPS:
      ☐

      Activate the access point of the inverter. This is opened by touching the sensor    > Communications LED flashes blue

    Ihr Browser kann diesen Film leider nicht anzeigen.
    1.
    Establish the connection to the inverter in the network settings (the inverter is displayed with the name "FRONIUS_" and the serial number of the device).
    2.
    Enter the password from the rating plate and confirm.
    IMPORTANT!
    To enter the password, first select the Connect using a security key instead link in order to establish the connection with the password.
    3.
    Enter the IP address 192.168.250.181 in the address bar of the browser and confirm.
    4.
    In the Communication > Network > WLAN > WPS menu area, click the Activate button.
    5.
    Activate WPS on the WiFi router (see WiFi router documentation).
    6.
    Click on the Start button. The connection is established automatically.
    7.
    Log in to the user interface of the inverter.
    8.
    Check the network details and connection to Fronius Solar.web.
    1Establish the connection to the inverter in the network settings (the inverter is displayed with the name "FRONIUS_" and the serial number of the device).
    2Enter the password from the rating plate and confirm.
    IMPORTANT!
    To enter the password, first select the Connect using a security key instead link in order to establish the connection with the password.
    3Enter the IP address 192.168.250.181 in the address bar of the browser and confirm.
    4In the Communication > Network > WLAN > WPS menu area, click the Activate button.
    5Activate WPS on the WiFi router (see WiFi router documentation).
    6Click on the Start button. The connection is established automatically.
    7Log in to the user interface of the inverter.
    8Check the network details and connection to Fronius Solar.web.

    After connecting, the status of the connection should be checked.

    Selecting and connecting to a WiFi network:
    The networks found are displayed in the list. Click the refresh button    to perform a new search for available WiFi networks. If necessary, restrict the selection list further via the Search network input field.
    1Select network from the list.
    2Select the connection type: Automatic or Static.
    3For the Automatic connection type, enter the WiFi password and host name.
    4For the Static connection type, enter the IP address, subnet mask, DNS, and gateway.
    5Click the Connect button.
    ✓The connection is established.

    After establishing the connection, check the connection status.

    Access point:

    The inverter serves as the access point. A PC or mobile device connects directly to the inverter. Connecting to the Internet is not possible. Assign a Network Name (SSID) and Network Key (PSK) to establish a connection. Assign a Network Key (PSK) with at least 20 characters, consisting of upper and lower case letters, special characters, and numbers, to protect the device from unauthorized access.
    It is possible to operate a connection via WiFi and via the access point at the same time.

    1. Settings – User interface of the inverter
    2. Communication

    Modbus

    link_horizontalLink copied

    Modbus RTU interface 0 / 1
    If one of the two Modbus RTU interfaces is set to Slave, the following input fields are available:

    "Baud rate"
    The baud rate influences the transmission speed between the individual components connected in the system. When selecting the baud rate, ensure that it is the same at both the sending and receiving end.

    "Parity"
    The parity bit can be used to check the parity. It detects transmission errors. A parity bit can safeguard a specific number of bits. The value (0 or 1) of the parity bit must be calculated by the sender and is checked by the recipient using the same calculation. The parity bit can be calculated for even and odd parity.

    "SunSpec Model Type"
    Depending on the SunSpec model, there are two different settings.

    float: SunSpec Inverter Model 111, 112, 113 or 211, 212, 213 or 701, 702, 703, 704, 705, 706, 707, 708, 709, 710, 711, 712, 713
    int + SF: SunSpec Inverter Model 101, 102, 103 or 201, 202, 203 or 701, 702, 703, 704, 705, 706, 707, 708, 709, 710, 711, 712, 713

    "Meter address"
    The value entered is the identification number (Unit ID) assigned to the meter.Can be found on the user interface of the inverter in the “Communication” → “Modbus” menu.
    Factory setting: 200

    "Meter address"
    The value entered is the identification number (Unit ID) assigned to the meter.
    Can be found on the user interface of the inverter in the “Communication” → “Modbus” menu.
    Factory setting: 1

    Slave as Modbus TCP
    If the function "Slave as Modbus TCP" is activated, the following input fields are available:

    "Modbus port"
    Number of the TCP port that is to be used for Modbus communication.

    "SunSpec Model Type"
    Depending on the SunSpec model, there are two different settings.

    float: SunSpec Inverter Model 111, 112, 113 or 211, 212, 213 or 701, 702, 703, 704, 705, 706, 707, 708, 709, 710, 711, 712, 713
    int + SF: SunSpec Inverter Model 101, 102, 103 or 201, 202, 203 or 701, 702, 703, 704, 705, 706, 707, 708, 709, 710, 711, 712, 713

    "Meter address"
    The value entered is the identification number (Unit ID) assigned to the meter.Can be found on the user interface of the inverter in the “Communication” → “Modbus” menu.
    Factory setting: 200

    "Meter address"
    The value entered is the identification number (Unit ID) assigned to the meter. Can be found on the user interface of the inverter in the “Communication” → “Modbus” menu.
    Factory setting: This value is invariably defined as 1.

    Inverter control via Modbus
    If this option is activated, the inverter is controlled via Modbus.
    Inverter control includes the following functions:
    • on/off
    • Power reduction
    • Specification of a constant power factor (cos phi)
    • Specification of a constant reactive power value
    1. Settings – User interface of the inverter
    2. Communication

    Cloud control

    link_horizontalLink copied

    The utility/energy supplier can influence the output power of the inverter with Cloud control. This requires the inverter to have an active Internet connection.

    Parameter

    Display

    Description

    Cloud control

    Off

    Cloud control of the inverter is deactivated.

    On

    Cloud control of the inverter is activated.

    Profile

    Value range

    Description

    Allow cloud control for regulatory purposes (Technician)

    Deactivated/Activated

    The function may be mandatory for proper operation of the system.*

    Allow cloud control for Virtual Power Plants (Customer)

    Deactivated/Activated

    If the Allow remote control for regulatory purposes (technician) function is activated (technician access required), the Allow remote control for virtual power plants function is automatically activated and cannot be deactivated.*

    * Cloud control
    A virtual power plant is an interconnection of multiple generators. This virtual power plant can be controlled by means of the cloud control via the Internet. An active inverter Internet connection is a prerequisite for this. System data are transferred.

    1. Settings – User interface of the inverter
    2. Communication

    Fronius Solar API

    link_horizontalLink copied

    The Fronius Solar API is an IP-based, open JSON interface. If it is activated, IOT devices in the local network can access inverter information without authentication. For security reasons, the interface is deactivated ex works and must be activated if it is required for a third-party application (e.g., EV charger, Smart Home solutions, etc.).

    For monitoring, Fronius recommends using Fronius Solar.web, which offers secure access to the inverter status and production information.

    In the event of a firmware update to version 1.14.x, the setting is taken from the Fronius Solar API. In systems with a version below 1.14.x, the Solar API is activated; with higher versions, it is deactivated but can be switched on and off via the menu

    Activating the Fronius Solar API

    Activate the “Activate communication via Solar API” function in the menu area “Communication” → “Solar API” on the user interface of the inverter.

    1. Settings – User interface of the inverter

    Safety and grid requirements

    link_horizontalLink copied

    Country setup

    WARNING

    Danger from unauthorized fault analyses and repair work.

    This can result in serious injury and damage to property.

    Fault analyses and repair work on the PV system may only be carried out by installers/service technicians from authorized specialist companies in accordance with national standards and regulations.

    NOTE

    Risk due to unauthorized access.

    Incorrectly set parameters can have a negative effect on the public grid and/or the grid power feed operation of the inverter and result in the loss of standard conformity.

    Parameters may only be adjusted by installers/service technicians from authorized specialist companies.

    Do not give the access code to third parties and/or unauthorized persons.

    NOTE

    Risk due to incorrectly set parameters.

    Incorrectly set parameters can have a negative effect on the public grid and/or cause inverter malfunctions and failures and result in the loss of standard conformity.

    Parameters may only be adjusted by installers/service technicians from authorized specialist companies.

    Parameters may only be adjusted if this has been approved or requested by the utility.

    Any parameter adjustments must be made in compliance with nationally applicable standards and/or directives as well as the specifications of the utility.

    The Country Setup menu area is intended exclusively for installers/service technicians from authorized specialist companies. To apply for the access code required for this menu area, see chapter Requesting inverter codes in Solar.SOS.

    The selected country setup for the country in question contains preset parameters in accordance with nationally applicable standards and requirements. Changes may need to be made to the selected country setup depending on local grid conditions and the specifications of the utility.

    1. Settings – User interface of the inverter
    2. Safety and grid requirements

    Country setup

    link_horizontalLink copied

    WARNING

    Danger from unauthorized fault analyses and repair work.

    This can result in serious injury and damage to property.

    Fault analyses and repair work on the PV system may only be carried out by installers/service technicians from authorized specialist companies in accordance with national standards and regulations.

    NOTE

    Risk due to unauthorized access.

    Incorrectly set parameters can have a negative effect on the public grid and/or the grid power feed operation of the inverter and result in the loss of standard conformity.

    Parameters may only be adjusted by installers/service technicians from authorized specialist companies.

    Do not give the access code to third parties and/or unauthorized persons.

    NOTE

    Risk due to incorrectly set parameters.

    Incorrectly set parameters can have a negative effect on the public grid and/or cause inverter malfunctions and failures and result in the loss of standard conformity.

    Parameters may only be adjusted by installers/service technicians from authorized specialist companies.

    Parameters may only be adjusted if this has been approved or requested by the utility.

    Any parameter adjustments must be made in compliance with nationally applicable standards and/or directives as well as the specifications of the utility.

    The Country Setup menu area is intended exclusively for installers/service technicians from authorized specialist companies. To apply for the access code required for this menu area, see chapter Requesting inverter codes in Solar.SOS.

    The selected country setup for the country in question contains preset parameters in accordance with nationally applicable standards and requirements. Changes may need to be made to the selected country setup depending on local grid conditions and the specifications of the utility.

    1. Settings – User interface of the inverter
    2. Safety and grid requirements

    Requesting inverter codes in Solar.SOS

    link_horizontalLink copied

    The Country Setup menu area is intended exclusively for installers/service technicians from authorized specialist companies. The inverter access code required for this menu area can be requested in the Fronius Solar.SOS portal.

    Requesting inverter codes in Fronius Solar.SOS:
    Ihr Browser kann diesen Film leider nicht anzeigen.
    1.
    Open solar-sos.fronius.com in the browser
    2.
    Log in with your Fronius account
    3.
    At the top right, click on the drop-down menu   
    4.
    Select the Show inverter codes menu item
    5.
    A contract page appears on which the request for the access code to change the grid parameters for Fronius inverters is located
    6.
    Accept the terms and conditions of use by checking Yes, I have read and agree to the terms of use and click Confirm & Save
    7.
    After that, the codes can be retrieved in the drop-down menu at the top right under Show inverter codes
    1Open solar-sos.fronius.com in the browser
    2Log in with your Fronius account
    3At the top right, click on the drop-down menu   
    4Select the Show inverter codes menu item
    ✓A contract page appears on which the request for the access code to change the grid parameters for Fronius inverters is located
    5Accept the terms and conditions of use by checking Yes, I have read and agree to the terms of use and click Confirm & Save
    6After that, the codes can be retrieved in the drop-down menu at the top right under Show inverter codes

    CAUTION

    Risk due to unauthorized access.

    Incorrectly set parameters can have a negative effect on the public grid and/or the grid power feed operation of the inverter and result in the loss of standard conformity.

    Parameters may only be adjusted by installers/service technicians from authorized specialist companies.

    Do not give the access code to third parties and/or unauthorized persons.

    1. Settings – User interface of the inverter
    2. Safety and grid requirements

    Absolute Generation Limit

    link_horizontalLink copied

    Activating this function limits the output power of the inverter to the specified value in watts.

    1. Settings – User interface of the inverter
    2. Safety and grid requirements

    ESS Modes (UL3141)

    link_horizontalLink copied

    NOTE

    This system is equipped with a power control system (PCS) according to UL3141. All PCS controlled busbars or conductors shall be protected with suitably rated overcurrent devices appropriately sized for the busbar rating or conductor ampacity.

    The Application Guide for the ESS modes is available at the following link:
    https://www.fronius.com/~/downloads/Solar%20Energy/Whitepaper/SE_WP_Fronius_GEN24_Plus_ESS_Modes_EN.pdf

    1. Settings – User interface of the inverter
    2. Safety and grid requirements

    Feed-in limit

    link_horizontalLink copied

    Energy companies or grid operators can prescribe feed-in limits for inverters (e.g., max. 70% of the kWp or max. 5 kW). The inverter limits the effective power at the grid connection point (installation location of the Fronius Smart Meter or primary meter) to the set value.

    The inverter takes account of self-consumption in the household before the power is reduced. An individual limit can be set.

    In order to minimize yield losses due to the power of feeding in limitation, the power available from the module array can be:

    • Used for (controllable) loads such as Fronius Ohmpilot, Fronius Wattpilot, I/O-controlled loads
    • Stored in a battery

    If these possibilities have been exhausted, the power drawn from the module array is reduced to such an extent that the set feed in limit is not exceeded.

    Installation variants with an inverter, Fronius Smart Meter, and system components are listed under Different operating modes.

    Total DC power of the system
    Input field for the total DC power of the entire system in Wp.
    This value is used if the Maximum grid feed-in power is specified in %.

    Power Control deactivated
    The inverter converts all available PV energy.

    Power Control activated
    Feeding in limited with the following selection options:

    • Total Power Limit
      The entire photovoltaic system is limited to a fixed feed-in limit. Set a value for the permissible total power of feeding in.

    IMPORTANT!
    Power Control settings are automatically applied for the dynamic feed-in limit of I/O power management. Total Power Limit is the default configuration.

    Export Limit Control (Soft Limit)
    If this value is exceeded, the inverter readjusts down to the set value within the time required by the national standards and regulations.

    Maximum grid feed-in power
    Input field for the Maximum grid feed-in power in W or % (setting range: -10 to 100%).
    If there is no meter in the system or if the primary meter has failed, the inverter limits its output power to the set value.

    Export Limit Protection (Hard Limit Trip)

    IMPORTANT!

    This function is only available if Export Limit Control (Soft Limit) is activated.

    If this value is exceeded, the inverter switches off within max. 5 seconds. This value must be higher than the value set for Export Limit Control (Soft Limit).

    Activate the function Reduce inverter power to 0% if meter connection has been lost for control in the event of a fail-safe. When this function is enabled, the inverter activates standby mode. No feed-in takes place.

    The use of WiFi for communication between the Fronius Smart Meter and the inverter is not recommended for the fail-safe function. Even short-term disconnections can cause the inverter to shut down. This problem is particularly common with weak WiFi signal strengths, a slow or overloaded WiFi connection, and automatic channel selection of the router.

    Limit multiple inverters (only Soft Limit)
    Control of the dynamic feed-in limit for several inverters, for details on configuration, see Dynamic feed-in limitation with multiple inverters.

    Example: Feed-in limit
    (not taking into account the efficiency)

    PV system to Fronius inverter:

    5000 W

    Consumption in home:

    1000 W

    Maximum permitted power of feeding in of the entire system:

    60% = 3000 W

     

     

    Situation 1: Battery charging is activated

    Power at the grid feed-in point:

    0 W

    Power at the inverter output:

    1000 W

    Power into the battery:

    3000 W

     

     

    Situation 2: Battery charging is deactivated

    Power at the grid feed-in point

    3000 W

    Power at the inverter output:

    4000 W

    Power into the battery:

    0 W

    In this example, a feed-in limit to the grid of 3000 W is set. Loads that are located between the inverter and grid feed-in point are supplied and adjusted by means of additional feed-in of the inverter.

    1. Settings – User interface of the inverter
    2. Safety and grid requirements

    Dynamic feed-in limitation with multiple inverters

    link_horizontalLink copied

    IMPORTANT! To view and change settings in this menu item, select the user Technician, and enter and confirm the password for the user Technician. Settings in this menu area may only be made by trained and qualified personnel.

    The inverter can be used as a primary device to control dynamic feed-in limits for additional Fronius inverters (secondary devices) so that feed-in limits prescribed by energy companies or utilities can be centrally managed. This control refers to the Soft Limit feed-in limit (see Feed-in limit). The following requirements must be met:
    • Power Control and the Limit multiple inverters (only Soft Limit and I/O Power Management) function are activated and configured on the user interface of the primary device.
    • Primary device and secondary device(s) are physically connected to the same network router via LAN.
    • Inverter Control via Modbus TCP is activated and configured for all secondary devices.
    • The Fronius Smart Meter is configured as a primary meter and connected to the primary device.

    IMPORTANT! Only one primary meter is required for the primary device.

    IMPORTANT! If an inverter with a battery is connected, it must be used as the primary device for dynamic feed-in limits.

    Example connection diagram for dynamic feed-in limitation with multiple inverters
    System limits
    • Systems with a maximum of 20 inverters (1 primary device + 19 secondary devices) are supported.
    • The control is designed for photovoltaic systems with a total output of up to 300 kW.
    • In the case of larger system capacities, the control times in the system are extended.
    • For systems >300 kW, the use of a plant controller is recommended.

    Dynamic feed-in limitation is available with the following device combinations:

    Primary device

    Secondary devices

    Fronius Primo GEN24

    Fronius Primo GEN24, Fronius SnapINverter with Fronius Datamanager 2.0*

    * Up to four additional SnapINverters can be connected to each SnapINverter with Fronius Datamanager 2.0

    Primary meter
    The Fronius Smart Meter acts as the only primary meter and is connected directly to the primary device. The Smart Meter monitors the total output power of all inverters into the grid and passes this information to the primary device via Modbus.

    Primary device

    The feed-in limitation is configured on the user interface of the inverter:
    1In the Safety and Grid Regulations > Export Limitation menu area, activate the Power Control function and select Total Power Limit.
    2Configure the country-specific settings.
    3In the Safety and Grid Regulations > Export Limitation menu area, activate the Limit multiple inverters (only Soft Limit and I/O Power Limit) function.

    The primary device automatically scans the network for available secondary devices. A list of the inverters found is displayed. Click Refresh to perform the search again.

    4Activate Use Inverter against all secondary devices to which an export limitation applies. Click Use all inverters to enable the function for the primary device and all secondary devices.The status of the inverters listed is displayed as follows:
    • Inactive: Secondary device is not configured for the power control.
    • Disconnected: Secondary device is configured, network connection not possible.
    • Connected: Secondary device is configured and accessible via the network of the primary device.
    5In the Safety and Grid Regulations > I/O Power Management menu area, set the controlling priorities as follows:
    1. I/O Power Limit
    2. Export Limitation
    3. Modbus
    Adding an inverter manually
    1Select the Additional inverters menu area.
    2Enter the name, host name, and IP address and the Modbus address of the secondary device.
    3Click Add inverter.

    Secondary device
    A secondary device takes over the export limitation of the primary device. No data are sent to the primary device for the export limitation. The following configurations must be set for the power control:

    User interface secondary device GEN24 / Verto / Tauro
    1Select the user Technician and enter the password for the user Technician.
    2In the Modbus menu area, activate the TCP Server mode and the Allow Control function.
    3For a fail-safe scenario, in the Safety and Grid Regulations > I/O Power Management menu area, set the controlling priorities as follows:
    1. Modbus
    2. Export Limitation
    3. I/O Power Limit
    4In the Safety and Grid Regulations > Export Limitation menu area, select and edit the following settings:
    • Activate the Power Control function
    • Select Total Power Limit and specify the total DC power of the entire system in W
    • Enable Export Limit Control (Soft Limit) and enter a value of 0 W for the Maximum grid feed-in power.
    • Enable the Reduce inverter power to 0% if meter connection has been lost function
    1. Settings – User interface of the inverter
    2. Safety and grid requirements

    I/O Power Management

    link_horizontalLink copied

    General
    Settings relevant to the grid operator are defined as rules under this menu item. This relates to an effective power limit in % or watts and/or a power factor specification.

    IMPORTANT!
    To view and change settings in this menu item, select the user Technician, and enter and confirm the password for the user Technician. Only technical specialists may make settings in this menu area.

    Under Rules, expand a menu area (e.g., Rule 1). Configure the following settings:

    Limitation

    IMPORTANT!
    A dynamic feed-in limit for several inverters can be configured under Feed-in limit. I/O power management rules are transferred from the inverter (primary device) to connected inverters in the system (secondary devices).

    Select the following rules for power management:

    • I/O Generation Limit (%): The total output power of the connected inverter is statically limited to the defined value of the absolute rated power.
    • Export Limit Control (W): The effective power fed in at the grid connection point is limited to the set value (e.g., 5000 watts). The output powers of the inverters (primary and secondary devices) are dynamically adjusted depending on their self-consumption.
    • Shutdown single device: The inverter stops grid power feed operation and switches to standby mode.

    IMPORTANT!
    The rules for shutdown apply to this device and cannot be applied to other inverters in the system.

    Input pattern (assignment of individual I/Os)
    1 click = white, contact open
    2 clicks = blue, contact closed
    3 clicks = gray, not used

    Power Factor (cos φ) (define value)

    Impedance response

    • Capacitive
    • Inductive

    DNO Feedback
    If the rule is activated, always configure the DNO Feedback output, e.g., for operating a signal device.

    The Import and Export of defined rules can be carried out in the data format *.fpc.

    If there is an active rule for the control of the inverter, the device indicates this in the overview of the user interface under Device State.

    Controlling Priorities
    Used to set controlling priorities for I/O Power Management (DRM or ripple control receiver), the feed-in limit, and control via Modbus.

    1 = highest priority, 3 = lowest priority

    Local priorities of the I/O Power Management, the feed-in limit, and the Modbus interface are deactivated by cloud control commands (regulatory purposes and virtual power plants) – see Cloud control on page (→) – and by backup power.

    In terms of control priorities, the device differentiates between power control and inverter shutdown. Inverter shutdown always takes precedence over power control. An inverter shutdown command is always executed and does not need to be prioritized.

    Power control
    • I/O Power Management (DRM/ripple control receiver signal)—according to command
    • Export Limitation (Soft Limit)—always active
    • Modbus (generation limit)—according to command
    Inverter shutdown
    • Shutdown single device
    • Export Limitation (Hard Limit)
    • Modbus (shutdown command) – according to command
    1. Settings – User interface of the inverter
    2. Safety and grid requirements

    Connection diagram - 4 relays

    link_horizontalLink copied

    The ripple control signal receiver and the I/O terminal of the inverter can be connected to one another as shown in the connection diagram.
    For distances of over 11 yd between the inverter and the ripple control signal receiver, a CAT 5 cable is recommended as a minimum and the shielding must be connected on one side at the push-in terminal of the data communication area (SHIELD).

    (1)
    Ripple control signal receiver with 4 relays for effective power limitation.
    (2)
    I/Os of the data communication area.
    Use pre-configured file for 4-relay operation:
    1Download the file (.fpc) under 4-relay operation to the mobile device.
    2Upload the file (.fpc) in the "I/O power management" menu field by clicking the "Import" button.
    3Click "Save".

    The settings for 4-relay operation are saved.

    1. Settings – User interface of the inverter
    2. Safety and grid requirements

    I/O power management settings - 4 relays

    link_horizontalLink copied
    1. Settings – User interface of the inverter
    2. Safety and grid requirements

    Connection diagram - 3 relays

    link_horizontalLink copied

    The ripple control signal receiver and the I/O terminal of the inverter can be connected to one another as shown in the connection diagram.
    For distances of over 11 yd between the inverter and the ripple control signal receiver, a CAT 5 cable is recommended as a minimum and the shielding must be connected on one side at the push-in terminal of the data communication area (SHIELD).

    (1)
    Ripple control signal receiver with 3 relays for effective power limitation.
    (2)
    I/Os of the data communication area.
    Use pre-configured file for 3-relay operation:
    1Download the file (.fpc) under 3-relay operation to the mobile device.
    2Upload the file (.fpc) in the "I/O power management" menu field by clicking the "Import" button.
    3Click "Save".

    The settings for 3-relay operation are saved.

    1. Settings – User interface of the inverter
    2. Safety and grid requirements

    I/O power management settings - 3 relays

    link_horizontalLink copied
    1. Settings – User interface of the inverter
    2. Safety and grid requirements

    Connection diagram - 2 relays

    link_horizontalLink copied

    The ripple control signal receiver and the I/O terminal of the inverter can be connected to one another as shown in the connection diagram.
    For distances of over 11 yd between the inverter and the ripple control signal receiver, a CAT 5 cable is recommended as a minimum and the shielding must be connected on one side at the push-in terminal of the data communication area (SHIELD).

    (1)
    Ripple control signal receiver with 2 relays for effective power limitation.
    (2)
    I/Os of the data communication area.
    Use pre-configured file for 2-relay operation:
    1Download the file (.fpc) under 2-relay operation to the mobile device.
    2Upload the file (.fpc) in the "I/O power management" menu field by clicking the "Import" button.
    3Click "Save".

    The settings for 2-relay operation are saved.

    1. Settings – User interface of the inverter
    2. Safety and grid requirements

    I/O power management settings - 2 relays

    link_horizontalLink copied
    1. Settings – User interface of the inverter
    2. Safety and grid requirements

    Connection diagram - 1 relay

    link_horizontalLink copied

    The ripple control signal receiver and the I/O terminal of the inverter can be connected to one another as shown in the connection diagram.
    For distances of over 10 m between the inverter and the ripple control signal receiver, a CAT 5 cable is recommended as a minimum and the shielding must be connected on one side at the push-in terminal of the data communication area (SHIELD).

    (1)
    Ripple control signal receiver with 1 relay for effective power limitation.
    (2)
    I/Os of the data communication area.
    Use pre-configured file for 1-relay operation:
    1Download the file (.fpc) under 1-relay operation to the mobile device.
    2Upload the file (.fpc) in the "I/O power management" menu field by clicking the "Import" button.
    3Click "Save".

    The settings for 1-relay operation are saved.

    1. Settings – User interface of the inverter
    2. Safety and grid requirements

    I/O power management settings - 1 relay

    link_horizontalLink copied

    Options

    link_horizontalLink copied

    PV Point Comfort

    Safety

    WARNING

    Danger due to electrical voltage on live parts of the photovoltaic system.

    This can result in serious injury and damage to property.

    Disconnect live parts of the photovoltaic system on all pins and on all sides.

    Secure against re-activation in accordance with national regulations.

    Allow the capacitors of the inverter to discharge (2 minutes).

    Check that the inverter is de-energized with a suitable measuring device.

    WARNING

    Danger due to work that has been carried out incorrectly.

    This can result in serious injury and damage to property.

    Installing and connecting an option must only be carried out by service personnel trained by Fronius and only within the scope of the respective technical regulations.

    Follow the safety rules.

    WARNING

    Danger due to damaged and/or contaminated terminals.

    This can result in serious injury and damage to property.

    Before making any connections, check the terminals for damage and contamination.

    Remove contamination in the de-energized state.

    Have defective terminals repaired by an authorized specialist.

    CAUTION

    Danger due to electrostatic discharge (ESD).

    This may result in damage to electronic components.

    Pay attention to the ESD marking on the product and/or on the packaging.

    Take ESD protection measures (grounding, neutralizing, and shielding).

    NOTE

    The continuous supply via the PV Point depends on the available PV power.

    If the solar modules are not supplying enough power, interruptions may occur.

    Do not connect any loads that require an uninterruptible supply.

    IMPORTANT!
    The valid national laws, standards, and provisions, as well as the specifications of the relevant grid operator are to be taken into account and applied.
    It is highly recommended that the specific installation be agreed with the grid operator and explicitly approved by this operator. This obligation applies to system constructors in particular (e.g., installers).

    1. Options

    PV Point Comfort

    link_horizontalLink copied

    Safety

    WARNING

    Danger due to electrical voltage on live parts of the photovoltaic system.

    This can result in serious injury and damage to property.

    Disconnect live parts of the photovoltaic system on all pins and on all sides.

    Secure against re-activation in accordance with national regulations.

    Allow the capacitors of the inverter to discharge (2 minutes).

    Check that the inverter is de-energized with a suitable measuring device.

    WARNING

    Danger due to work that has been carried out incorrectly.

    This can result in serious injury and damage to property.

    Installing and connecting an option must only be carried out by service personnel trained by Fronius and only within the scope of the respective technical regulations.

    Follow the safety rules.

    WARNING

    Danger due to damaged and/or contaminated terminals.

    This can result in serious injury and damage to property.

    Before making any connections, check the terminals for damage and contamination.

    Remove contamination in the de-energized state.

    Have defective terminals repaired by an authorized specialist.

    CAUTION

    Danger due to electrostatic discharge (ESD).

    This may result in damage to electronic components.

    Pay attention to the ESD marking on the product and/or on the packaging.

    Take ESD protection measures (grounding, neutralizing, and shielding).

    NOTE

    The continuous supply via the PV Point depends on the available PV power.

    If the solar modules are not supplying enough power, interruptions may occur.

    Do not connect any loads that require an uninterruptible supply.

    IMPORTANT!
    The valid national laws, standards, and provisions, as well as the specifications of the relevant grid operator are to be taken into account and applied.
    It is highly recommended that the specific installation be agreed with the grid operator and explicitly approved by this operator. This obligation applies to system constructors in particular (e.g., installers).

    1. Options
    2. PV Point Comfort

    Safety

    link_horizontalLink copied

    WARNING

    Danger due to electrical voltage on live parts of the photovoltaic system.

    This can result in serious injury and damage to property.

    Disconnect live parts of the photovoltaic system on all pins and on all sides.

    Secure against re-activation in accordance with national regulations.

    Allow the capacitors of the inverter to discharge (2 minutes).

    Check that the inverter is de-energized with a suitable measuring device.

    WARNING

    Danger due to work that has been carried out incorrectly.

    This can result in serious injury and damage to property.

    Installing and connecting an option must only be carried out by service personnel trained by Fronius and only within the scope of the respective technical regulations.

    Follow the safety rules.

    WARNING

    Danger due to damaged and/or contaminated terminals.

    This can result in serious injury and damage to property.

    Before making any connections, check the terminals for damage and contamination.

    Remove contamination in the de-energized state.

    Have defective terminals repaired by an authorized specialist.

    CAUTION

    Danger due to electrostatic discharge (ESD).

    This may result in damage to electronic components.

    Pay attention to the ESD marking on the product and/or on the packaging.

    Take ESD protection measures (grounding, neutralizing, and shielding).

    NOTE

    The continuous supply via the PV Point depends on the available PV power.

    If the solar modules are not supplying enough power, interruptions may occur.

    Do not connect any loads that require an uninterruptible supply.

    IMPORTANT!
    The valid national laws, standards, and provisions, as well as the specifications of the relevant grid operator are to be taken into account and applied.
    It is highly recommended that the specific installation be agreed with the grid operator and explicitly approved by this operator. This obligation applies to system constructors in particular (e.g., installers).

    1. Options
    2. PV Point Comfort

    Scope of supply

    link_horizontalLink copied

    The PV Point Comfort is available as an option and can be retrofitted to the inverter.

    For technical data, see chapter Technical data on page (→).

    1. Insulation film
    2. PV Point Comfort
    3. 4 pcs TX20 screws
    4. Quick Start Guide
    1. Options
    2. PV Point Comfort

    De-energizing the inverter

    link_horizontalLink copied
    1

    Turn off the automatic circuit breaker. Set the DC disconnector to the "off" switch position.

    2Disconnect connections from the solar module strings (+/-).
    3

    Disconnect connections from the solar module strings (+/-). Switch off the battery connected to the inverter.

    Wait for the capacitors of the inverter to discharge (2 minutes).

    1. Options
    2. PV Point Comfort

    Install PV Point Comfort

    link_horizontalLink copied

    CAUTION

    Danger due to insufficiently dimensioned ground conductor.

    Damage to the inverter due to thermal overload can result.

    The national standards and guidelines must be observed for dimensioning the ground conductor.

    1

    Loosen the 2 screws on the underside of the housing cover by rotating them 180° to the left using a screwdriver (TX20). Then lift the housing cover away from the inverter at the bottom and detach from above.

    2

    Loosen the 5 screws of the connection area cover by rotating them 180° to the left using a screwdriver (TX20).
    Remove the connection area cover from the device.

    3

    Press the lock on the back of the terminal and remove the AC terminals.

    4

    Disconnect the single conductors from the AC terminal (only necessary if the installation already exists).

    5

    Loosen the ground conductor (PE) from the ground electrode terminal using a screwdriver (TX20).

    6

    Loosen the ground conductor (PE) from the conduit using a flathead screwdriver (1/8“).

    7

    Remove the mains cable from the inverter.

    8

    Insert the insulating film on the right side of the ground electrode terminal.

    9

    Insert the PC board into the inverter.

    10

    Fasten the PC board with the 4 screws (TX20) supplied and tighten to a torque of 10.6 in-lb / 1.2 Nm.

    11

    Strip the single conductors according to the specifications based on the power category of the inverter.
    The cable cross-section must be selected according to the specifications for the respective power category of the inverter (see chapter Permitted cables for the electrical connection on page (→)).

    12

    Strip the insulation of the single conductors by 3/8 inch / 10 mm. Insert the stripped single conductor into the slot provided, all the way up to the stop.

    13

    Strip the single conductors (Primo 3.8 ‑ 6 kW = 1/2 inch / 12 mm, Primo 7.7 ‑ 10 kW = 3/4 inch / 19 mm). Lift to open the AC terminal's operating lever and insert the stripped single conductor into the slot provided, all the way up to the stop. Then close the operating lever until it engages.

    IMPORTANT!
    The PEN connection must be designed according to the national provisions.

    14

    Fasten the PEN conductor to the second input of the ground electrode terminal from the top using a screwdriver (TX20) and a torque of 16‑18 in-lb / 1.8‑2.0 Nm.

    15

    Strip the single conductors according to the specifications based on the power category of the inverter.
    The cable cross-section must be selected according to the specifications for the respective power category of the inverter (see chapter Permitted cables for the electrical connection on page (→)).

    IMPORTANT!
    If necessary, an automatic circuit breaker of max. 16 A can also be used for protection. In backup power operation, a maximum of 13 A can be provided. The residual current circuit breaker and automatic circuit breaker must be designed according to the national provisions.

    16

    Connect the phase/neutral conductors to the terminals provided. Fasten the ground conductor to the third input of the ground electrode terminal from the top using a screwdriver (TX20) and a torque of 16‑18 in-lb / 1.8‑2.0 Nm.

    IMPORTANT!
    The ground conductor must be connected with a movement loop so that if the cable gland fails, the ground conductor is disconnected last.

    17

    Connect the stripped phase/neutral conductors to the terminals provided.

    18

    Insert the terminals into the respective slot until they engage.

    19

    Place the cover on the connection area. Tighten the five screws by rotating them 180° to the right in the indicated order using a screwdriver (TX20).

    20

    Clip the housing cover onto the inverter from above.
    Press on the lower part of the housing cover and tighten the two screws by rotating them 180° to the right using a screwdriver (TX20).

    1. Options
    2. PV Point Comfort

    Starting up the inverter

    link_horizontalLink copied
    1

    Connect the solar module strings (+/-). Switch on the battery connected to the inverter.

    2

    Set the DC disconnector to the "on" switch position. Turn on the automatic circuit breaker.

    1. Options
    2. PV Point Comfort

    Configuring the PV Point Comfort

    link_horizontalLink copied

    Firmware version 1.25.2 or higher is required to commission the PV Point Comfort. Outdated firmware versions could lead to incompatibilities between the inverter and PV Point Comfort. In this case, the inverter firmware should be updated in accordance with the chapter headed Update on page (→).

    1Call up the user interface of the inverter.
    - Open web browser.
    - In the browser's address bar, enter the IP address (IP address for WLAN: 192.168.250.181, IP address for LAN: 169.254.0.180) or enter and confirm the host and domain name of the inverter.
    ✓The user interface of the inverter is displayed.
    2Click on the Device Configuration button.
    3Log in to the login area with user Technician and the technician password.
    4Go to the Device Configuration > Functions and I/Os menu area.
    5Enable the Backup Power function.
    6Select PV Point mode in the Backup Power Mode drop-down list.
    7Select 120 V under PV Point Nominal Voltage.
    8Click the Save button to save the settings.
    ✓The PV Point backup power mode has been configured.
    1. Options
    2. PV Point Comfort

    Testing backup power mode

    link_horizontalLink copied
    Testing backup power mode:
    • during first-time installation and configuration
    • after working on the switch cabinet
    • during ongoing operation (recommendation: at least every 6 months)

    A battery charge of min. 30% is recommended for test mode.

    A description of how to run the test mode can be found in the checklist – Backup power (https://www.fronius.com/de/download-center?searchword=42,0426,0365).

    Appendix

    link_horizontalLink copied

    Service, maintenance and disposal

    General

    The inverter is designed so that it does not require additional maintenance work. Nevertheless, a few points must be considered during operation to ensure that the inverter works perfectly.

    1. Appendix

    Service, maintenance and disposal

    link_horizontalLink copied

    General

    The inverter is designed so that it does not require additional maintenance work. Nevertheless, a few points must be considered during operation to ensure that the inverter works perfectly.

    1. Appendix
    2. Service, maintenance and disposal

    General

    link_horizontalLink copied

    The inverter is designed so that it does not require additional maintenance work. Nevertheless, a few points must be considered during operation to ensure that the inverter works perfectly.

    1. Appendix
    2. Service, maintenance and disposal

    Cleaning

    link_horizontalLink copied

    Wipe the inverter, if necessary, with a damp cloth.
    Do not use cleaning agents, scouring agents, solvents, or similar products to clean the inverter.

    1. Appendix
    2. Service, maintenance and disposal

    Maintenance

    link_horizontalLink copied

    Maintenance and service work may only be carried out by a technical specialist.

    1. Appendix
    2. Service, maintenance and disposal

    Safety

    link_horizontalLink copied

    The DC disconnector is used only to switch off power to the power stage set. When the DC disconnector is turned off, the connection area is still energized.

    WARNING

    Danger from mains voltage and DC voltage from PV modules.

    This can result in severe personal injury and damage to property.

    The connection area must only be opened by an authorized electrician.

    The separate power stage set area must only be opened by Fronius-trained service technicians.

    Prior to any connection work, ensure that the inverter is de-energized on the AC side and the DC side.

    WARNING

    Danger of residual voltage from capacitors.

    This can result in severe personal injury and damage to property.

    Allow the capacitors of the inverter to discharge (2 minutes).

    1. Appendix
    2. Service, maintenance and disposal

    Operation in dusty environments

    link_horizontalLink copied

    NOTE

    If the inverter is operated in dusty environments, dirt may build up on the heat sink and fan.

    This may result in a loss of power due to insufficient cooling of the inverter.

    Make sure that the ambient air can always flow through the inverter's ventilation slots unimpeded.

    Remove any build-ups of dirt from the heat sink and the fan.

    1

    Switch off power to the inverter and wait for the specified time until the capacitors have discharged and the fan has shut down.
    Turn the DC disconnector to the "Off" switch setting.

    2

    Loosen the screws on the underside of the housing cover by rotating them 180° to the left using a screwdriver (TX20). Then lift the housing cover away from the inverter at the bottom and detach from above.

    3

    Remove any build-up of dirt on the heat sink and fan using compressed air, a cloth, or a brush.

    NOTE

    Risk due to damage to the fan bearing in the event of incorrect cleaning.

    Excessive speeds and the application of pressure to the fan bearing can cause damage.

    Block the fan and clean with compressed air.

    When using a cloth or brush, clean the fan without applying any pressure.

    To start up the inverter again, follow the steps listed above in reverse order.

    1. Appendix
    2. Service, maintenance and disposal

    Disposal

    link_horizontalLink copied
    In accordance with the EU Directive and national law, the following products must be disposed of separately and recycled:
    • Waste electrical and electronic equipment
    • Used batteries (portable batteries, industrial batteries)

    Used equipment and batteries must be returned to the distributor or an authorized local collection system. Do not dispose of batteries with domestic waste. Protect batteries from high temperatures, direct sunlight, moisture and corrosive environments.

    Arrange for the safe collection and proper disposal of damaged, leaking or used batteries by a battery recycling company or the Fronius Service Partner.

    In addition, it should be noted that batteries contain substances that, if disposed of improperly, can have a significant negative impact on the environment as well as on human health and the safety of persons, in particular due to the leakage of hazardous substances such as heavy metals or electrolytes, which can contaminate soil, water and air.

    This ensures environmental protection and the sustainable use of natural resources.

    Packaging materials
    • Collect separately
    • Observe local regulations
    • Compress the cardboard box to reduce volume
    1. Appendix

    Warranty provisions

    link_horizontalLink copied

    Warranty

    Detailed warranty conditions specific to your country can be found at https://www.fronius.com/en/download-center?searchword=Warranty+conditions .

    If there is a warranty for the relevant product, register the product at https://warranty.fronius.com/ and activate or extend the warranty.

    1. Appendix
    2. Warranty provisions

    Warranty

    link_horizontalLink copied

    Detailed warranty conditions specific to your country can be found at https://www.fronius.com/en/download-center?searchword=Warranty+conditions .

    If there is a warranty for the relevant product, register the product at https://warranty.fronius.com/ and activate or extend the warranty.

    1. Appendix

    Status codes and remedy

    link_horizontalLink copied

    Display

    Status codes are displayed on the user interface of the inverter in the System > Event Log menu area or in the user menu under Notifications and in Fronius Solar.web*.

    *
    If configured accordingly, see chapter Fronius Solar.web on page (→).
    1. Appendix
    2. Status codes and remedy

    Display

    link_horizontalLink copied

    Status codes are displayed on the user interface of the inverter in the System > Event Log menu area or in the user menu under Notifications and in Fronius Solar.web*.

    *
    If configured accordingly, see chapter Fronius Solar.web on page (→).
    1. Appendix
    2. Status codes and remedy

    Status codes

    link_horizontalLink copied
    1030 – WSD Open (operating LED: flashes red)
    Cause:A device that is connected in the WSD chain has interrupted the signal line (e.g., surge protection device) or the bypass installed ex works as standard has been removed and no trigger device has been installed.
    Remedy:If the SPD surge protection device has tripped, the inverter must be repaired by an authorized specialist.
    OR:Install the bypass installed ex works as standard or a trigger device.
    OR:Turn the WSD (wired shutdown) switch to position 1 (WSD primary device).

    WARNING

    Danger from work that is not carried out properly.

    This can result in serious injury and damage to property.

    The installation and connection of an SPD surge protection device may only be carried out by Fronius-trained service personnel in accordance with the technical specifications.

    Observe safety rules.

    1173 – ArcContinuousFault (operating LED: flashes red)
    Cause:An electric arc has been identified on the PV system, and the maximum number of automatic connections within 24 hours has been reached.
    Remedy:Keep the sensor pressed on the inverter for 3 seconds  (max. 6 seconds).
    OR:On the user interface of the inverter, in the System > Event Log menu area, confirm the status 1173 - ArcContinuousFault.
    OR:On the user interface of the inverter, in the Notifications user menu, confirm the status 1173 - ArcContinuousFault.

    CAUTION

    Danger from damaged components of the PV system

    Serious personal injury/damage to property may result.

    Before the status 1173 - ArcContinuousFault is confirmed, the entire photovoltaic system affected must be checked for any possible damage.

    Damaged components must be repaired by qualified specialists.

    1191 – AfciDataTransfer (operating LED: flashes yellow)
    Cause:An electric arc has been identified on the PV system.
    Remedy:No action required.
    1. Appendix

    Technical data

    link_horizontalLink copied

    Fronius Primo GEN24 7.7 208 - 240 / 7.7 208 - 240 Plus

    DC input data

    MPP voltage range

    260 - 480 V

    Max. input voltage at 1000 W/m²/14 °F in an open circuit

    600 V

    Min. input voltage

    65 V

    Start-up input voltage

    80 V

    Nominal PV power

    at 208 V
    at 220 V
    at 240 V

    7960 W
    7960 W
    7920 W

    Nominal input voltage

    at 208 V
    at 220 V
    at 240 V

    365 V
    365 V
    385 V

    Max. PV array power

    at 208 V
    at 220 V
    at 240 V

    11520 W
    11520 W
    11520 W

    Nominal input current

    at 208 V
    at 220 V
    at 240 V

    21.8 A
    21.8 A
    20.6 A

    Max. input current
    PV 1
    PV 2


    22 A
    22 A

    Max. short circuit current for module array (ISC PV)
    PV 1
    PV 2


    41.25 A
    36 A

    Max. total short circuit current for module array
    (ISC PV1 + ISC PV2 = ISC max)


    77.25 A

    Max. continuous utility backfeed current 1)

    0.0 A

    AC output data

    Max. output power

    at 208 V
    at 220 V
    at 240 V

    7680 W
    7680 W
    7680 W

    Max. output power at +140 °F (60 °C) V min / V max

    at 208 V
    at 220 V
    at 240 V

    5060 W / 5940 W
    6230 W / 5510 W
    5490 W / 6810 W

    Nominal AC voltage

    208 V/220 V/240 V

    Voltage trip limit accuracy

    1% of nominal value

    Max. continuous output current at Vnom

    at 208 V
    at 220 V
    at 240 V

    36.9 A
    34.9 A
    32.0 A

    Output overcurrent protection

    at 208 V
    at 220 V
    at 240 V

    50.0 A
    45.0 A
    40.0 A

    Phases

    1

    Max. output fault current per duration (peak / rms over duration)

    at 208 V
    at 220 V
    at 240 V

    682 A / 20.1 A over 396 ms
    676 A / 35.4 A over 120 ms
    698 A / 20.4 A over 339 ms

    Nominal output frequency

    60 Hz

    Setting range for mains frequency

    45.0 - 66.0 Hz

    Frequency trip limit accuracy

    0.05 Hz

    Total harmonic distortion

    < 3.0%

    Power factor (cos phi)

    0.8 - 1 ind./cap. 2)

    Max. permitted mains impedance Zmax at PCC (mOhm)3)

    None

    General data

    Maximum efficiency

    at 208 V
    at 220 V
    at 240 V

    97.2 %
    97.2 %
    97.5 %

    CEC efficiency

    at 208 V
    at 220 V
    at 240 V

    96.5 %
    96.5 %
    97.0 %

    Night tare loss

    at 208 V
    at 220 V 
    at 240 V

    9.2 W
    9.2 W
    9.2 W

    Cooling

    Controlled forced-air ventilation

    Protection class

    Type 4X

    Dimensions H × W × D

    23.0 × 20.8 × 7.1 inches (583 x 529 x 180 mm)

    Weight

    49.05 lbs. (22.25 kg)

    Shipping dimensions H × W × D

    25.8 × 23.5 × 10.4 inches (654 x 598 x 263 mm)

    Shipping weight

    57.10 lbs.(25.9 kg)

    Inverter topology

    non-isolated, no transformer

    Permitted ambient temperature

    -40 °F - +140 °F

    (-40 °C - +60 °C)

    Permissible humidity

    0 - 100%
    (incl. condensation)

    EMC emission class

    B

    DC/AC overvoltage (according to UL1741 3rd Edition, CSA-C22.2 No.107.1-16)

    2/4

    Pollution degree

    2

    Safety class (according to IEC 62103)

    1

    Protection devices

    DC isolation measurement

    Error/shutdown at RISO < 500 kOhm

    DC overload performance

    Operating point shift, power limiter

    DC disconnector

    Integrated

    DC reverse polarity protection

    Integrated

    Arc Fault Circuit Interrupter

    AFCI type 1 integrated, according to UL1699B:2024 and F-I-AFPE-1-4-1 according to IEC63027:2023

    Rapid shutdown

    Integrated, in accordance with UL1741 and CSA C22.2 No.330-23

    RCMU

    Integrated

    Active anti-islanding method

    Integrated

    Behavior in the event of overheating

    Power limiter, active cooling

    Output data PV Point

    Nominal AC voltage PV Point

    1~NPE 120 V

    Nominal output power PV Point

    at 120 V

    1560 W

    Max. continuous output current

    at 120 V

    13.0 A

    Nominal output frequency

    63 Hz

    Power factor

    0 - 1 ind. / cap.2)

    Switching time

    <22 s.

    Data communication

    WLAN SMA-RP connection
    (FCC ID: QKWPILOT1 / IC ID: 12270-PILOT1 / IFETEL:RCPFRTP20-1349) (FCC ID: QKWPILOT1 / IC ID: 12270-PILOT1)

    802.11b/g/n (WPA, WPA2)

    Ethernet (LAN)

    RJ 45, 10/100 Mbit

    Wired shutdown (WSD)

    max. 28 devices/WSD chain

    max. distance
    master → slave = 109 yd / 100 m
    slave → slave = 109 yd / 100 m

    Modbus RTU SunSpec (2x)

    RS485 2-wire

    Battery Connection

    Modbus O / RJ 45 / 12 V power supply

    Voltage level of digital inputs

    low: min. 0 V - max. 1.8 V
    high: min. 4.5 V - max. 28.8 V

    Input currents of digital inputs

     

    depending on the input voltage;
    input resistance = 70 kOhm

    Total power for digital output
    (internal supply)

    6 W at 12 V
    (USB not connected)

    Power per digital output
    (external supply)

    1 A at >12.5 V - 24 V
    (max. 3 A in total)

    DC Input data battery4)

    Min. voltage

    150 V

    Max. voltage

    455 V

    Max. current

    22 A

    Max. input

    7680 W

    DC Inputs

    1

    Output data Essential Backup5)

    Nominal output power Essential Backup

    at 120 V
    at 220 V
    at 240 V

    7680 W
    7680 W
    7680 W

    Max. continuous output current

    at 120 V
    at 220 V
    at 240 V

    36.9 A
    34.9 A
    32.0 A

    Nominal output frequency

    63 Hz

    Power factor

    0.8 - 1 ind. / cap.2)

    Switching time

    <17 s.

    1. Appendix
    2. Technical data

    Fronius Primo GEN24 7.7 208 - 240 / 7.7 208 - 240 Plus

    link_horizontalLink copied

    DC input data

    MPP voltage range

    260 - 480 V

    Max. input voltage at 1000 W/m²/14 °F in an open circuit

    600 V

    Min. input voltage

    65 V

    Start-up input voltage

    80 V

    Nominal PV power

    at 208 V
    at 220 V
    at 240 V

    7960 W
    7960 W
    7920 W

    Nominal input voltage

    at 208 V
    at 220 V
    at 240 V

    365 V
    365 V
    385 V

    Max. PV array power

    at 208 V
    at 220 V
    at 240 V

    11520 W
    11520 W
    11520 W

    Nominal input current

    at 208 V
    at 220 V
    at 240 V

    21.8 A
    21.8 A
    20.6 A

    Max. input current
    PV 1
    PV 2


    22 A
    22 A

    Max. short circuit current for module array (ISC PV)
    PV 1
    PV 2


    41.25 A
    36 A

    Max. total short circuit current for module array
    (ISC PV1 + ISC PV2 = ISC max)


    77.25 A

    Max. continuous utility backfeed current 1)

    0.0 A

    AC output data

    Max. output power

    at 208 V
    at 220 V
    at 240 V

    7680 W
    7680 W
    7680 W

    Max. output power at +140 °F (60 °C) V min / V max

    at 208 V
    at 220 V
    at 240 V

    5060 W / 5940 W
    6230 W / 5510 W
    5490 W / 6810 W

    Nominal AC voltage

    208 V/220 V/240 V

    Voltage trip limit accuracy

    1% of nominal value

    Max. continuous output current at Vnom

    at 208 V
    at 220 V
    at 240 V

    36.9 A
    34.9 A
    32.0 A

    Output overcurrent protection

    at 208 V
    at 220 V
    at 240 V

    50.0 A
    45.0 A
    40.0 A

    Phases

    1

    Max. output fault current per duration (peak / rms over duration)

    at 208 V
    at 220 V
    at 240 V

    682 A / 20.1 A over 396 ms
    676 A / 35.4 A over 120 ms
    698 A / 20.4 A over 339 ms

    Nominal output frequency

    60 Hz

    Setting range for mains frequency

    45.0 - 66.0 Hz

    Frequency trip limit accuracy

    0.05 Hz

    Total harmonic distortion

    < 3.0%

    Power factor (cos phi)

    0.8 - 1 ind./cap. 2)

    Max. permitted mains impedance Zmax at PCC (mOhm)3)

    None

    General data

    Maximum efficiency

    at 208 V
    at 220 V
    at 240 V

    97.2 %
    97.2 %
    97.5 %

    CEC efficiency

    at 208 V
    at 220 V
    at 240 V

    96.5 %
    96.5 %
    97.0 %

    Night tare loss

    at 208 V
    at 220 V 
    at 240 V

    9.2 W
    9.2 W
    9.2 W

    Cooling

    Controlled forced-air ventilation

    Protection class

    Type 4X

    Dimensions H × W × D

    23.0 × 20.8 × 7.1 inches (583 x 529 x 180 mm)

    Weight

    49.05 lbs. (22.25 kg)

    Shipping dimensions H × W × D

    25.8 × 23.5 × 10.4 inches (654 x 598 x 263 mm)

    Shipping weight

    57.10 lbs.(25.9 kg)

    Inverter topology

    non-isolated, no transformer

    Permitted ambient temperature

    -40 °F - +140 °F

    (-40 °C - +60 °C)

    Permissible humidity

    0 - 100%
    (incl. condensation)

    EMC emission class

    B

    DC/AC overvoltage (according to UL1741 3rd Edition, CSA-C22.2 No.107.1-16)

    2/4

    Pollution degree

    2

    Safety class (according to IEC 62103)

    1

    Protection devices

    DC isolation measurement

    Error/shutdown at RISO < 500 kOhm

    DC overload performance

    Operating point shift, power limiter

    DC disconnector

    Integrated

    DC reverse polarity protection

    Integrated

    Arc Fault Circuit Interrupter

    AFCI type 1 integrated, according to UL1699B:2024 and F-I-AFPE-1-4-1 according to IEC63027:2023

    Rapid shutdown

    Integrated, in accordance with UL1741 and CSA C22.2 No.330-23

    RCMU

    Integrated

    Active anti-islanding method

    Integrated

    Behavior in the event of overheating

    Power limiter, active cooling

    Output data PV Point

    Nominal AC voltage PV Point

    1~NPE 120 V

    Nominal output power PV Point

    at 120 V

    1560 W

    Max. continuous output current

    at 120 V

    13.0 A

    Nominal output frequency

    63 Hz

    Power factor

    0 - 1 ind. / cap.2)

    Switching time

    <22 s.

    Data communication

    WLAN SMA-RP connection
    (FCC ID: QKWPILOT1 / IC ID: 12270-PILOT1 / IFETEL:RCPFRTP20-1349) (FCC ID: QKWPILOT1 / IC ID: 12270-PILOT1)

    802.11b/g/n (WPA, WPA2)

    Ethernet (LAN)

    RJ 45, 10/100 Mbit

    Wired shutdown (WSD)

    max. 28 devices/WSD chain

    max. distance
    master → slave = 109 yd / 100 m
    slave → slave = 109 yd / 100 m

    Modbus RTU SunSpec (2x)

    RS485 2-wire

    Battery Connection

    Modbus O / RJ 45 / 12 V power supply

    Voltage level of digital inputs

    low: min. 0 V - max. 1.8 V
    high: min. 4.5 V - max. 28.8 V

    Input currents of digital inputs

     

    depending on the input voltage;
    input resistance = 70 kOhm

    Total power for digital output
    (internal supply)

    6 W at 12 V
    (USB not connected)

    Power per digital output
    (external supply)

    1 A at >12.5 V - 24 V
    (max. 3 A in total)

    DC Input data battery4)

    Min. voltage

    150 V

    Max. voltage

    455 V

    Max. current

    22 A

    Max. input

    7680 W

    DC Inputs

    1

    Output data Essential Backup5)

    Nominal output power Essential Backup

    at 120 V
    at 220 V
    at 240 V

    7680 W
    7680 W
    7680 W

    Max. continuous output current

    at 120 V
    at 220 V
    at 240 V

    36.9 A
    34.9 A
    32.0 A

    Nominal output frequency

    63 Hz

    Power factor

    0.8 - 1 ind. / cap.2)

    Switching time

    <17 s.

    1. Appendix
    2. Technical data

    Technical data for Fronius Primo GEN24 10.0 208 - 240 / 10.0 208 - 240 Plus

    link_horizontalLink copied

    DC input data

    MPP voltage range

    260 - 480 V

    Max. input voltage at 1000 W/m²/14 °F in an open circuit

    600 V

    Min. input voltage

    65 V

    Start-up input voltage

    80 V

    Nominal PV power

    at 208 V
    at 220 V
    at 240 V

    9790 W
    10360 W
    10310 W

    Max. PV array power

    at 208 V
    at 220 V
    at 240 V

    13500 W
    13000 W
    15000 W

    Nominal input voltage

    at 208 V
    at 220 V
    at 240 V

    365 V
    365 V
    385 V

    Nominal input current

    at 208 V
    at 220 V
    at 240 V

    26.8 A
    28.4 A
    26.8 A

    Max. input current
    PV 1
    PV 2


    22 A
    22 A

    Max. short circuit current for module array (ISC PV)
    PV 1
    PV 2


    41.25 A
    36 A

    Max. total short circuit current for module array
    (ISC PV1 + ISC PV2 = ISC max)


    77.25 A

    Max. continuous utility backfeed current 1)

    0.0 A

    AC output data

    Max. output power

    at 208 V
    at 220 V
    at 240 V

    9450 W
    10,000 W
    10,000 W

    Max. output power  at +140 °F (60 °C) V min / V max

    at 208 V
    at 220 V
    at 240 V

    5060 W / 5940 W
    6230 W / 5510 W
    5490 W / 6810 W

    Nominal AC voltage

    208 V/220 V/240 V

    Voltage trip limit accuracy

    1% of nominal value

    Max. continuous output current at Vnom

    at 208 V
    at 220 V
    at 240 V

    45.45 A
    45.45 A
    41.7 A

    Output overcurrent protection

    at 208 V
    at 220 V
    at 240 V

    60 A
    60 A
    55 A

    Phases

    1

    Max. output fault current per duration (peak / rms over duration)

    at 208 V
    at 220 V
    at 240 V

    682 A/ 20.1 A over 396 ms
    676 A/ 35.4 A over 120 ms
    698 A/ 20.4 A over 339 ms

    Nominal output frequency

    60 Hz

    Setting range for mains frequency

    45.0 - 66.0 Hz

    Frequency trip limit accuracy

    0.05 Hz

    Total harmonic distortion

    < 3.0%

    Power factor (cos phi)

    0.8 - 1 ind./cap. 2)

    Max. permitted mains impedance Zmax at PCC (mOhm)3)

    None

    General data

    Maximum efficiency

    at 208 V
    at 220 V
    at 240 V

    97.2 %
    97.2 %
    97.5 %

    CEC efficiency

    at 208 V
    at 220 V
    at 240 V

    96.5%
    96.5%
    97.0%

    Night tare loss

    at 208 V
    at 220 V 
    at 240 V

    8.4 W
    8.4 W
    8.5 W

    Cooling

    Controlled forced-air ventilation

    Protection class

    Type 4X

    Dimensions H × W × D

    23.0 × 20.8 × 7.1 inches (583 x 529 x 180 mm)

    Weight

    49.05 lbs. (22.25 kg)

    Shipping dimensions W × H × D

    25.8 × 23.5 × 10.4 inches (654 x 598 x 264 mm)

    Shipping weight

    57.10 lbs. (25.9 kg)

    Inverter topology

    non-isolated, no transformer

    Permitted ambient temperature

    -40 °F - +140 °F(-40 °C - +60 °C)

    Permissible humidity

    0 - 100%
    (incl. condensation)

    EMC emission class

    B

    DC/AC overvoltage (according to UL1741 3rd Edition, CSA-C22.2 No.107.1-16)

    2/4

    Pollution degree

    2

    Safety class (according to IEC 62103)

    1

    Protection devices

    DC isolation measurement

    Error/shutdown at RISO < 500 kOhm

    DC overload performance

    Operating point shift, power limiter

    DC disconnector

    Integrated

    DC reverse polarity protection

    Integrated

    Arc Fault Circuit Interrupter

    AFCI type 1 integrated, according to UL1699B:2024 and F-I-AFPE-1-4-1 according to IEC63027:2023

    Rapid shutdown

    Integrated, in accordance with UL1741 and CSA C22.2 No.330-23

    RCMU

    Integrated

    Active anti-islanding method

    Integrated

    Behavior in the event of overheating

    Power limiter, active cooling

    Output data PV Point

    Nominal AC voltage PV Point

    1~NPE 120 V

    Nominal output power PV Point

    at 120 V

    1560 W

    Max. continuous output current

    at 120 V

    13.0 A

    Nominal output frequency

    63 Hz

    Power factor

    0 - 1 ind. / cap.2)

    Switching time

    <22 s.

    Data communication

    WLAN SMA-RP connection
    (FCC ID: QKWPILOT1 / IC ID: 12270-PILOT1 / IFETEL:RCPFRTP20-1349) (FCC ID: QKWPILOT1 / IC ID: 12270-PILOT1)

    802.11b/g/n (WPA, WPA2)

    Ethernet (LAN)

    RJ 45, 10/100 Mbit

    Wired shutdown (WSD)

    max. 28 devices/WSD chain

    max. distance
    master → slave = 109 yd / 100 m
    slave → slave = 109 yd / 100 m

    Modbus RTU SunSpec (2x)

    RS485 2-wire

    Battery Connection

    Modbus O / RJ 45 / 12 V power supply

    Voltage level of digital inputs

    low: min. 0 V - max. 1.8 V
    high: min. 4.5 V - max. 28.8 V

    Input currents of digital inputs

     

    depending on the input voltage;
    input resistance = 70 kOhm

    Total power for digital output
    (internal supply)

    6 W at 12 V
    (USB not connected)

    Power per digital output
    (external supply)

    1 A at >12.5 V - 24 V
    (max. 3 A in total)

    DC Input data battery4)

    Min. voltage

    150 V

    Max. voltage

    455 V

    Max. current

    22 A

    Max. input

    10000 W

    DC Inputs

    1

    Output data Essential Backup 5)

    Nominal output power Essential Backup

    at 120 V
    at 220 V
    at 240 V

    9450 W
    10000 W
    10000 W

    Max. continuous output current

    at 120 V
    at 220 V
    at 240 V

    45.5 A
    45.5 A
    41.7 A

    Nominal output frequency

    63 Hz

    Power factor

    0.8 - 1 ind. / cap.2)

    Switching time

    <17 s.

    1. Appendix
    2. Technical data

    WLAN

    link_horizontalLink copied

    Frequency range

    2412 - 2462 MHz

    Channels / power used

    Channel: 1-11 b,g,n HT20
    Channel: 3-9 HT40
    <18 dBm

    Modulation

    802.11b: DSSS (1Mbps DBPSK, 2Mbps DQPSK, 5.5/11Mbps CCK)
    802.11g: OFDM (6/9Mbps BPSK, 12/18Mbps QPSK, 24/36Mbps 16-QAM, 48/54Mbps 64-QAM)
    802.11n: OFDM (6.5 BPSK, QPSK, 16-QAM, 64-QAM)

    1. Appendix
    2. Technical data

    Explanation of footnotes

    link_horizontalLink copied
    1)
    The maximum current from the inverter to the PV module if an error occurs in the inverter. Guaranteed by the electrical design of the inverter.
    2)
    Depending on the country setup or device-specific settings
    (ind. = inductive; cap. = capacitive).
    3)
    Assured by the electrical design of the inverter.
    4)
    The inverter can be upgraded to a GEN24 Plus Hybrid device in the future through the UP.storage software upgrade. This upgrade activates battery functionality, enabling the possibility of a Essential Backup power solution. However, external grid switching devices are required for this functionality. The technical specifications for battery operation and Essential Backup operation are detailed below.
    5)
    For Essential Backup, additional external components are required for grid separation.
    1. Appendix
    2. Technical data

    Integrated DC disconnector

    link_horizontalLink copied

    General data

    Product name

    Benedict LS32 E 7905

    Rated insulation voltage

    1000 VDC

    Rated impulse withstand voltage

    8 kV

    Suitability for insulation

    Yes, DC only

    Utilization category and/or PV utilization category

    according to IEC/EN 60947-3 utilization category DC-PV2

    Rated short-time withstand current (Icw)

    Rated short-time withstand current (Icw): 1000 A

    Rated short-circuit capacity (Icm)

    Rated short-circuit capacity (Icm): 1000 A

    Rated operating current and rated breaking capacity

    Rated operating voltage (Ue)

    Rated operating current (Ie)

    I(make) / I(break)

    Rated operating current (Ie)

    I(make) / I(break)

    ≤ 500 VDC

    14 A

    56 A

    36 A

    144 A

    600 VDC

    8 A

    32 A

    30 A

    120 A

    Number of pins

    1

    1

    2

    2

    System circuit diagrams

    link_horizontalLink copied

    Fronius Primo GEN24 and RENON Xtreme HV1.0

    1. System circuit diagrams

    Fronius Primo GEN24 and RENON Xtreme HV1.0

    link_horizontalLink copied
    1. System circuit diagrams

    Fronius Primo GEN24 with two RENON Xtreme HV1.0 connected in parallel

    link_horizontalLink copied
    1. System circuit diagrams

    Fronius Primo GEN24 with three RENON Xtreme HV1.0 connected in parallel

    link_horizontalLink copied

    Circuit diagrams—PV Point

    link_horizontalLink copied

    Emergency power terminal—PV Point (OP)

    1. Circuit diagrams—PV Point

    Emergency power terminal—PV Point (OP)

    link_horizontalLink copied
    1. Circuit diagrams—PV Point

    PV Point Comfort

    link_horizontalLink copied

    Dimensions of the inverter

    link_horizontalLink copied

    Fronius Primo GEN24 7.7 - 10.0 208-240

    1. Dimensions of the inverter

    Fronius Primo GEN24 7.7 - 10.0 208-240

    link_horizontalLink copied