Indicates a situation where damage could occur.
If you see any of the symbols depicted in the "Safety rules" chapter, special care is required.
Danger from crushing due to the incorrect handling of attachments and connection parts.
Injuries to limbs may result.
When lifting up, putting down and attaching the inverter, use the integrated grips.
When fitting attachments, ensure that no limbs are located between the attachment and the inverter.
Do not hold onto the individual poles on the terminals when locking and unlocking.
In addition to the Operating Instructions, all applicable local rules and regulations regarding accident prevention and environmental protection must also be followed.
All safety and danger notices on the device:Any safety devices that are not fully functional must be repaired by an authorized specialist before the device is switched on.
For the location of the safety and danger notices on the device, refer to the chapter headed "Warning notices on the device" in the Operating Instructions for your device.
Faults that could compromise safety must be remedied before switching on the device.
The servicing information contained in these operating instructions is intended only for the use of qualified service engineers. An electric shock can be fatal. Do not carry out any actions other than those described in the documentation. This also applies to qualified personnel.
All cables and leads must be secured, undamaged, insulated and adequately dimensioned. Loose connections, scorched, damaged or inadequately dimensioned cables and leads must be immediately repaired by authorised personnel.
Maintenance and repair work must only be carried out by an authorised specialist.
It is impossible to guarantee that bought-in parts are designed and manufactured to meet the demands made on them, or that they satisfy safety requirements. Use only original spare parts (also applies to standard parts).
Components that are not in perfect condition must be changed immediately.
The sound power level of the inverter is specified in the Technical data.
The device is cooled as quietly as possible with the aid of an electronic temperature control system; this depends on the amount of converted power, the ambient temperature, the level of soiling of the device, etc.
It is not possible to provide a workplace-related emission value for this device because the actual sound pressure level is heavily influenced by the installation situation, the grid quality, the surrounding walls and the properties of the room in general.
In certain cases, even though a device complies with the standard limit values for emissions, it may affect the application area for which it was designed (e.g. when there is sensitive equipment at the same location, or if the site where the device is installed is close to either radio or television receivers). If this is the case, then the operator is obliged to take appropriate action to rectify the situation.
This system has backup power functions. This enables a replacement power supply to be established in the event of a failure in the public grid.
Where an automatic backup power supply is installed, a backup power warning notice (https://www.fronius.com/en/search-page, item number: 42,0409,0275) must be fitted on the electrical distributor.
Maintenance and installation work in the home network requires both disconnection on the utility side and deactivation of the replacement power mode by opening the integrated DC disconnector on the inverter.
Depending on the insolation conditions and the battery state of charge, the backup power supply is automatically deactivated and activated. This can cause the backup power supply to unexpectedly return from standby mode. Therefore, installation work can only be performed on the home network when the backup power supply is deactivated.
Influencing factors on the total power in backup power mode:
Reactive power
Electrical loads with a power factor not equal to 1 also require reactive power in addition to effective power. The reactive power also loads the inverter. Therefore, to correctly calculate the actual total power, it is not the rated power of the load that is relevant, but the current caused by effective and reactive power.
Devices with a high reactive power are mainly electric motors such as:
High starting current
Electrical loads that need to accelerate a large mass usually require a high starting current. This can be up to 10 times higher than the nominal current. The maximum current of the inverter is available for the starting current. Loads with too high starting currents therefore cannot be started/operated, even though the nominal power of the inverter suggests that they can. When dimensioning of the backup power circuit, the connected load power and any starting current must also be taken into account.
Devices with high starting currents are, for example:
IMPORTANT!
Very high starting currents can cause short-term distortion or a drop in output voltage. The simultaneous operation of electronic devices in the same backup power supply system should be avoided.
Load unbalance
When dimensioning three-phase backup power networks, the total output power and the power output per phase of the inverter must be taken into account.
IMPORTANT!
The inverter may only be operated within the limits of its technical capabilities. Operation outside of its technical capabilities can cause the inverter to shut down.
The user is responsible for the safekeeping of any changes made to the factory settings. The manufacturer accepts no liability for any deleted personal settings.
The text and illustrations are all technically correct at the time of printing. We reserve the right to make changes. The contents of the operating instructions shall not provide the basis for any claims whatsoever on the part of the purchaser. If you have any suggestions for improvement, or can point out any mistakes that you have found in the instructions, we will be most grateful for your comments.
Connection of a point in the device, system or installation to earth to protect against electric shock in the event of a fault. When installing a safety class 1 inverter (see Technical data), the ground conductor connection is required.
When connecting the ground conductor, ensure that it is secured against accidental disconnection. All the points listed in the chapter Connecting the inverter to the public grid (AC side) on page (→) must be observed. It must be ensured that when using the strain relief devices, the ground conductor is the last to be disconnected in the event of a possible failure. When connecting the ground conductor, the minimum cross-section requirements specified by the respective national standards and guidelines must be observed.
The inverter transforms the direct current generated by the PV modules into alternating current. This alternating current is fed into the public grid and synchronized with the mains voltage in use. Moreover, the solar energy can also be stored in a connected battery for later use.
The inverter is intended for use in grid-connected photovoltaic systems. The inverter has backup power functions and switches to backup power mode if it has been wired accordingly*.
The inverter automatically monitors the public grid. Whenever conditions in the electric grid are inconsistent with standard conditions (for example, grid switch-off, interruption), the inverter will immediately stop producing power and interrupt the supply of power into the grid.
The grid is monitored by monitoring the voltage, frequency and islanding conditions.
After installation and commissioning, the inverter's operation is fully automatic;
the inverter draws the maximum possible power from the PV modules.
Depending on the operating point, this power is used in the home, stored in a battery* or fed into the grid.
As soon as the energy provided by the PV modules is no longer sufficient, the power from the battery is fed into the home. Depending on the setting, power may also be obtained from the public grid in order to charge the battery*.
When its temperature gets too high, the inverter automatically reduces the output or charging power, or switches off completely, in order to protect itself.
Reasons for the temperature being too high include a high ambient temperature or insufficient heat dissipation (for example, inadequate heat dissipation when installed in switch cabinets).
* | Depending on the device variant, suitable battery, appropriate wiring, settings and local standards and guidelines. |
Function | Symo GEN24 | Symo GEN24 Plus |
Backup power variant - PV Point (OP) | ||
Battery connection* | Available as an option** | |
Backup power variant - Full Backup | Available as an option** |
* | For suitable batteries, see chapter Suitable battery. |
** | The functions are optionally available via Fronius UP (see chapter Fronius UP). |
With Fronius UP*, the inverter can be expanded by the authorised specialist to include optionally available functions (see chapter Function overview).
* | The availability of Fronius UP varies from country to country. For more information on Fronius UP and availability, see Installation guide: Fronius GEN24 & GEN24 Plus. |
(1) | Housing cover |
(2) | Inverter |
(3) | Mounting bracket (illustration) |
(4) | Quick Start guide |
(5) | 2x ferrite ring with holder |
The manufacturer is not responsible for any damage resulting from improper use.
All warranty claims are considered void in such cases.
When configuring the photovoltaic system, make sure that all components of the photovoltaic system are operating exclusively within their permissible operating range.
Observe all measures recommended by the PV module manufacturer to permanently maintain the PV module properties.
Observe the grid operator's regulations for energy fed into the grid and connection methods.
Ambient air is drawn in by the fan on the front side and blown out at the device sides. The even heat dissipation allows several inverters to be installed next to each other.
Risk due to insufficient cooling of the inverter.
This may result in a loss of power in the inverter.
Do not block the fan (for example, with objects that protrude through the touch guard).
Do not cover the ventilation slots, even partially.
Make sure that the ambient air can always flow through the inverter's ventilation slots unimpeded.
With Fronius Solar.web or Fronius Solar.web Premium, the PV system can be easily monitored and analysed by the system owner and installer. If configured accordingly, the inverter transmits data such as power, yields, load, and energy balance to Fronius Solar.web. For more information see Solar.web - monitoring & analysis.
Configuration is carried out via the setup wizard, see chapter Installation with the app on page (→) or Installation using the web browser on page (→).
Prerequisites for configuration:* | The information given does not constitute an absolute guarantee of faultless function. High error rates in the transmission, reception fluctuations or transmission drop-outs can have a negative effect on the data transfer. Fronius recommends testing the Internet connection on site according to the minimum requirements. |
PV module | |
Fronius GEN24 inverter | |
Additional inverter in the system | |
Battery | |
Fronius Ohmpilot | |
Primary meter | |
Secondary meter | |
Loads in the PV system | |
Additional loads and generators in the system | |
PV Point | |
Full Backup | |
Grid |
PV module | |
Battery | |
Primary meter | |
Secondary meter | |
PV Point | |
Full Backup | |
Grid |
In order to be able to obtain the highest rate of self-consumption with your PV system, a battery can be used to store excess energy. The battery is coupled to the inverter on the direct current side. Multiple current conversion is therefore not required, and the efficiency is increased.
IMPORTANT!
In backup power mode, an increased nominal frequency is used in order to prevent undesired parallel operation with other power generators.
IMPORTANT!
In the fully equipped hybrid PV system with a Fronius Ohmpilot, the Ohmpilot cannot be operated in the event of a power failure for regulatory reasons. It is therefore sensible to install the Ohmpilot outside of the backup power branch.
In the hybrid photovoltaic system, batteries must only be connected to one inverter with battery support. Batteries cannot be split between multiple inverters with battery support. However, depending on the battery manufacturer, several batteries can be combined on one inverter.
In the case of hybrid inverters, there are four different energy flow directions:
(1) | Solar module – inverter – load/grid |
(2) | Solar module – inverter – battery* |
(3) | Battery – inverter – load/grid* |
(4) | Grid – inverter – battery* |
* depending on the settings and local standards and regulations.
Battery systems distinguish different operating states. In this case, the relevant current operating state is displayed on the website of the inverter or in Solar.web.
Operating state | Description |
Normal operation | Energy is stored or drawn, as required. |
Min. state of charge (SOC) achieved | Battery has reached the minimum SOC set or specified by the manufacturer. The battery cannot be discharged any further. |
Energy saving mode (standby) | The system has been put into energy saving mode. Energy saving mode is automatically ended as soon as sufficient excess energy is available again. |
Start | The storage system starts from energy saving mode (standby). |
Forced re-charging | The inverter re-charges the battery, in order to maintain the set minimum SOC (state of charge) or the SOC specified by the manufacturer (protection against deep discharge). |
Deactivated | The battery is not active. It has either been deactivated/switched off, or an error means that no communication with the battery is possible. |
Energy saving mode (standby mode) is used to reduce the self-consumption of the system. Both the inverter and the battery automatically switch to energy saving mode under certain conditions.
The inverter switches to energy saving mode if the battery is flat and no PV power is available. Only the inverter's communication with the Fronius Smart Meter and Fronius Solar.web is maintained.
If all the switch-off conditions are met, the battery switches into energy saving mode within ten minutes. This time delay ensures that the inverter can at least be restarted.
| The battery state of charge is less than or equal to the input minimum state of charge. | |
| The current charging or discharging power of the battery is less than 100 W. | |
| Less than 50 W is available for charging the battery. The power of feeding into the public grid is at least 50 W less than the power currently required in the home network. |
The inverter automatically switches into energy saving mode, following the battery.
If the inverter does not operate for 12 minutes (e.g. fault), or there is an interruption in the electrical connection between the inverter and the battery and there is no backup power mode, the battery switches to energy-saving mode in any case. This reduces self discharge of the battery.
Energy saving mode is shown on the website of the inverter and in Solar.web by an "i" beside the battery symbol in the system overview.
Fronius explicitly points out that the third-party batteries are not Fronius products. Fronius is not the manufacturer, distributor or retailer of these batteries. Fronius accepts no liability and offers no service or guarantees for these batteries.
Obsolete firmware/software states may lead to incompatibilities between the inverter and the battery. In this case, the following steps are to be performed:Before installation and commissioning, read this document and the Installation Instructions for the external battery.
All the documents relating to the inverter can be found at the following address:
The documentation for the BYD Battery-Box Premium is enclosed with the third-party battery or can be obtained from the battery manufacturer and its service partners.
BYD Battery-Box Premium HVS | 5.1 | 7.7 | 10.2 | 12.8 |
Fronius Symo GEN24 6.0 - 10.0* | ||||
Fronius Symo GEN24 6.0 - 10.0 Plus | ||||
Number of battery modules | 2 | 3 | 4 | 5 |
Battery parallel operation** |
BYD Battery-Box Premium HVM | 8.3 | 11.0 | 13.8 | 16.6 | 19.3 | 22.1 |
Fronius Symo GEN24 6.0 - 10.0* | ||||||
Fronius Symo GEN24 6.0 - 10.0 Plus | ||||||
Number of battery modules | 3 | 4 | 5 | 6 | 7 | 8 |
* | Battery support optionally available. |
** | Max. 3 batteries with the same capacity can be combined. Max. 2 batteries can be combined with BYD Battery-Box Premium HVM 22.1. |
Switch on the battery.
Set the DC disconnector to the "On" switch position. Switch on the automatic circuit breaker.
There is no energy available from the PV modules or from the public grid. If backup power operation or battery operation are not possible (e.g. deep discharge protection of the battery), the inverter and battery switch off.
Status codes about the inactive state of the battery are displayed on the user interface of the inverter or sent via Solar.web by means of SMS or e-mail (only if notification via Solar.web is configured accordingly).
As soon as energy is available again, the inverter starts operation automatically; however the battery must be started manually. The switch-on sequence must be observed for this, see chapter Suitable battery on page (→).
The inverter requires energy from the battery to start backup power operation. This is done manually on the battery; further information on the power supply for restarting the inverter via the battery can be found in the battery manufacturer's Operating Instructions.
The inverter offers the option to use the integrated AC relays as coupling switches in conjunction with a central grid and system protection unit (in accordance with VDE-AR-N 4105:2018:11 §6.4.1). For this purpose, the central trigger device (switch) must be integrated into the WSD chain as described in the chapter "WSD (Wired Shut Down)".
The wired shutdown (WSD) interrupts the inverter feeding energy into the grid if the trigger device (switch) has been activated.
If an inverter (secondary device) fails, it is bypassed and the other inverters continue operating. If a second inverter (secondary device) or the inverter (primary device) fails, the operation of the entire WSD chain is interrupted.
For installation, see Installing the WSD (wired shutdown) on page (→).
The inverter is equipped with a universal current-sensitive residual current monitoring unit (RCMU = Residual Current Monitoring Unit) in accordance with IEC 62109-2.
This device monitors residual currents from the PV module to the AC output of the inverter and disconnects the inverter from the grid in the event of unauthorised residual current.
The inverter is equipped with an integrated surge protective device on the DC and AC side in accordance with IEC 62109-2. The surge protective device protects the system against damage in the event of an overvoltage.
(1) | 2 x 4-pin DC push-in terminal |
(2) | Push-in WSD (wired shutdown) terminal |
(3) | Push-in terminals in the data communication area (Modbus, digital inputs and outputs) |
(4) | 3-pin push-in terminal for PV point (OP) |
(5) | 5-pin AC push-in terminal |
(6) | Cable gland/strain-relief device AC |
(7) | 6-pin ground electrode terminal |
(8) | Cable gland/strain-relief device in the data communication area |
(9) | Connection area divider |
(10) | 10 x DC cable glands |
(11) | Optional cable gland (M16) |
(12) | Optional cable gland (M16 - M20) |
(13) | Optional cable gland (M16 - M32) |
(14) | Optional cable gland (M16 - M25) |
The connection area divider separates the high-voltage conductors (DC and AC) from the signal lines. To make it easier to reach the connection area, the divider can be removed for the connection work, and must be re-inserted.
(1) | Integrated cable duct |
(2) | Recesses for removing the connection area divider |
(3) | Snap tabs for locking/unlocking |
(4) | Defined breaking point for the Datcom connection |
The integrated cable duct (1) allows for the lines to be laid from one area of the inverter to the other. As a result, multiple inverters can be easily installed next to each other.
The ground electrode terminal Allows additional components to be earthed, such as:
The DC disconnector has three switch settings:
(1) | Locked/off (turned to the left) |
(2) | Off |
(3) | On |
Modbus terminal |
| Push-in terminal for the installation of Modbus 0, Modbus 1, 12 V and GND (ground). |
WSD (wired shutdown) switch |
| Defines the inverter as a WSD primary device or WSD secondary device. |
Modbus 0 (MB0) switch |
| Switches the terminating resistor for Modbus 0 (MB0) on/off. |
Modbus 1 (MB1) switch |
| Switches the terminating resistor for Modbus 1 (MB1) on/off. |
| To operate the inverter. See chapter Button functions and LED status indicator on page (→). |
| Indicates the inverter connection status. |
| Indicates the inverter operating status. |
LAN 1 |
| Ethernet connection for data communication (e.g. WLAN router, home network or for commissioning with a laptop see chapter Installation using the web browser on page (→)). |
LAN 2 |
| Ethernet port for internal use only (support). |
WSD terminal |
| Push-in terminal for the WSD installation. See chapter "WSD (wired shutdown)" on page (→). |
USB |
| Power supply max. 1 A at 5 V. Software updates and data recording via USB is not possible. |
IOs terminal |
| Push-in terminal for digital inputs/outputs. See chapter Permitted cables for the data communication area on page (→). |
On the V+/GND pin, it is possible to feed in a voltage of around 12.5 - 24 V (+ max. 20%) with an external power supply. The outputs IO 0 - 5 can then be operated with the external voltage. A maximum of 1 A can be drawn per output, with a maximum of 3 A allowed in total. The fuse protection must be located externally.
Risk of polarity reversal at the terminals due to improper connection of external power supplies.
This may result in severe damage to the inverter.
Check the polarity of the external power supply with a suitable measuring device before connecting it.
Connect the cables to the V+/GND outputs with the correct polarity.
IMPORTANT!
If the total output (6 W) is exceeded, the inverter switches off the entire external power supply.
(1) | Power limitation |
IMPORTANT!
If several backup power variants are available, please note that only one backup power variant may be installed and configured.
With the PV Point, in the event of a failure of the public grid, single-phase electrical devices can be connected to the Opportunity Power (OP) terminal and supplied with a maximum power of 3 kW, if enough power is available from the solar modules or an optional battery. In grid-connected operation, the OP terminal is not supplied with voltage, therefore the connected loads will not be supplied with power in this operating mode.
IMPORTANT!
A relay-based network switching setup is not possible.
IMPORTANT!
IMPORTANT!
IMPORTANT!
IMPORTANT!
The inverter can provide 120 to 240 V at the PV Point. A corresponding configuration must be set up during commissioning.
At 120 to 240 V output voltage, a maximum of 13 A AC continuous current is available.
For example:
120 V = max. 1.5 kW
230 V = max. 3 kW
In backup power mode, some electrical appliances cannot function properly as starting currents are too high (for example, fridges and freezers). It is recommended to switch off non-essential loads during backup power mode. Overload capacity of 35% is possible for a duration of 5 seconds, depending on the capacity of the solar modules and/or the battery at that moment in time.
There is a brief interruption when switching from grid-connected mode to backup power mode. For this reason, the backup power function cannot be used as an uninterruptible power supply, for example for computers.
If no energy from the battery or the solar modules is available in backup power mode, backup power mode ends automatically. If sufficient energy becomes available from the solar modules once again, backup power mode starts again automatically.
In the event of excessive consumption, backup power mode is stopped and the "backup power overload" status code is displayed on the inverter's LED status indicator. The maximum power in backup power mode according to the technical data must be observed.
IMPORTANT!
IMPORTANT!
IMPORTANT!
A quick-lock system (3) is used to mount the connection area cover and front cover. The system is opened and closed with a half-rotation (180°) of the captive screw (1) into the quick-lock spring (2).
The system is independent of torque.
Danger when using a drill driver.
This may result in the destruction of the quick-lock system due to overtorque.
Use a screwdriver (TX20).
Do not turn the screws more than 180°.
Technical data, warning notices and safety symbols are affixed to the inverter. These warning notices and safety symbols must not be removed or painted over. They warn against incorrect operation which can lead to serious injury and damage.
A 4-digit number (coded production date) is printed on the rating plate at the very bottom, from which the production date can be calculated.
If you subtract the value 11 from the first two digits, you get the production year. The last two digits stand for the calendar week in which the device was produced.
Example:
Value on rating plate = 3206
32 - 11 = 21 → Production year 2021
06 = Calendar week 06
Symbols on the rating plate: | |
CE mark – confirms compliance with applicable EU directives and regulations. | |
UKCA mark – confirms compliance with applicable UK directives and regulations. | |
WEEE mark – waste electrical and electronic equipment must be collected separately and recycled in an environmentally sound manner in accordance with the European Directive and national law. | |
RCM mark – tested in accordance with the requirements of Australia and New Zealand. | |
ICASA mark – tested in accordance with the requirements of the Independent Communications Authority of South Africa. | |
CMIM mark – tested in accordance with IMANOR requirements for import regulations and compliance with Moroccan standards. |
Safety symbols: | |
Risk of serious injury and property damage due to incorrect operation. | |
Dangerous electrical voltage. | |
Allow the capacitors of the inverter to discharge (2 minutes). |
Warning notice text:
WARNING!
An electric shock can be fatal. Before opening the device, it must be disconnected and de-energized at the input and output.
Please note the following criteria when choosing a location for the inverter:
| Only install on a solid, non-flammable surface. | |
| Max. ambient temperatures: | |
| Relative humidity: | |
| If the inverter is installed in a switch cabinet or similar enclosed space, ensure sufficient heat dissipation with forced-air ventilation. | |
When installing the inverter on the outer walls of cattle sheds, it is important to keep a minimum clearance of 2 m between all sides of the inverter and air vents and building openings. | ||
The following surfaces are permissible for installation:
| The inverter is suitable for indoor installation. | |
| The inverter is suitable for outdoor installation. Because of its IP 66 protection class, the inverter is resistant to water jets from any direction and can also be used in damp environments. | |
| In order to minimise the heating up of the inverter, do not expose it to direct insolation. The inverter should be installed in a protected location, for example, near the solar modules or under an overhanging roof. | |
| IMPORTANT! | |
| Do not install the inverter in:
| During certain operating phases the inverter may produce a slight noise. For this reason it should not be installed in an occupied living area. | |
| The inverter is essentially designed to be dustproof (IP 66). In areas of high dust accumulation, dust deposits may collect on the cooling surfaces, and thus impair the thermal performance. Regular cleaning is required in this case, see chapter Operation in dusty environments on page (→). We therefore recommend not installing the inverter in areas and environments with high dust accumulation. | |
| IMPORTANT! | |
IMPORTANT!
Refer to the manufacturer's documents for the suitable location for third-party batteries.
| The inverter is suitable for vertical installation on a vertical wall or column. | |
| The inverter is suitable for a horizontal installation position. | |
| The inverter is suitable for installation on a sloping surface. | |
| Do not install the inverter on a sloping surface with its connection sockets at the top. | |
| Do not install the inverter at an angle on a vertical wall or column. | |
| Do not install the inverter horizontally on a vertical wall or pillar. | |
| Do not install the inverter on a vertical wall or pillar with its connection sockets facing upwards. | |
| Do not install the inverter overhanging with the connection sockets at the top. | |
| Do not install the inverter overhanging with the connection sockets at the bottom. | |
| Do not install the inverter on the ceiling. |
Use the corresponding fixing materials depending on the subsurface and observe the screw dimension recommendations for the mounting bracket.
The installer is responsible for selecting the right type of fixing.
The separate mounting bracket (illustration) is also used as the gauge.
The pre-drilled holes on the mounting bracket are intended for screws with a thread diameter of 6 - 8 mm (0.24 - 0.32 inches).
Unevenness on the installation surface (for example, coarse-grained plaster) is largely counterbalanced by the mounting bracket.
When fitting the mounting bracket to the wall or column, ensure that the mounting bracket does not become deformed.
A deformed mounting bracket may make it difficult to clip/swivel the inverter into position.
IMPORTANT!
When installing the mounting bracket, make sure that it is installed with the arrow pointing upwards.
When installing the inverter on a mast or beam, Fronius recommends using the "Pole clamp" (order no. SZ 2584.000) mounting kit from Rittal GmbH.
The "Pole clamp" kit covers the following dimensions:
IMPORTANT!
The mounting bracket must be affixed at a minimum of four points.
There are integrated grips on the side of the inverter which facilitate lifting/attaching.
Clip the inverter into the mounting bracket from above. The connections must point downwards.
The lower area of the inverter is pushed into the snap-in tabs until the inverter audibly clicks into place on both sides.
Check that the inverter is correctly positioned on both sides.
Cables with the following design can be connected to the terminals of the inverter:
Grid connections with push-in terminal | ||||||||||||
Number of pins | Solid | Multi-stranded | Fine-stranded | Fine-stranded with ferrules‐ | ||||||||
5 | 2.5 - 10 mm2 | 2.5 - 10 mm2 | 2.5 - 10 mm2 | 2.5 - 6 mm2 |
Grid connections backup power with push-in terminal | ||||||||||||
3 | 1.5 - 10 mm2 | 1.5 - 10 mm2 | 1.5 - 10 mm2 | 1.5 - 6 mm2 |
PV/BAT connections with push-in terminal | ||||||||||||
2 x 4 | 4 - 10 mm2 | 4 - 10 mm2 | 4 - 10 mm2 | 4 - 6 mm2 |
Ground electrode terminal | ||||||||||||
2 | 2.5 - 16 mm2 | 2.5 - 16 mm2 | 2.5 - 16 mm2 | 2.5 - 16 mm2 | ||||||||
4 | 2.5 - 10 mm2 | 2.5 - 10 mm2 | 2.5 - 10 mm2 | 2.5 - 10 mm2 |
* | According to product standard IEC 62109, the ground conductor must correspond to the phase cross-section for phase cross-sections ≤16 mm²; for phase cross-sections >16 mm², it must correspond to at least 16 mm². |
** | The cable cross section must be dimensioned in accordance with the installation situation and the specifications of the battery manufacturer. |
IMPORTANT!
Connect the individual conductors to an appropriate ferrule if several individual conductors are connected to one input of the push-in terminals.
WSD connections with push-in terminal | ||||||
Distance | Stripping length | Solid | Fine-stranded | Fine-stranded with ferrules with collar | Fine-stranded with ferrules without collar | Cable recommendation |
100 m 109 yd | 10 mm | 0.14-1.5 mm2 | 0.14-1.5 mm2 | 0.14-1 mm2 | 0.14-1.5 mm2 | min. CAT 5 UTP (unshielded twisted pair) |
Modbus connections with push-in terminal | ||||||
300 m 328 yd | 10 mm | 0.14-1.5 mm2 | 0.14-1.5 mm2 | 0.14-1 mm2 | 0.14-1.5 mm2 | min. CAT 5 STP (shielded twisted pair) |
IO connections with push-in terminal | ||||||
30 m | 10 mm | 0.14-1.5 mm2 | 0.14-1.5 mm2 | 0.14-1 mm2 | 0.14-1.5 mm2 | Single conductor possible |
LAN connections |
Fronius recommends using at least CAT 5 STP (shielded twisted pair) cables and a maximum distance of 100 m (109 yd). |
For a standard M32 metric screw joint with a reducer:
Cable diameter from 7-15 mm
When using an M32 metric screw joint (reducer removed):
cable diameter from 11-21 mmWith cable diameters greater than 21 mm, the M32 screw joint must be replaced by an M32 screw joint with a larger clamping area – item number: 42,0407,0780 – strain-relief device M32 x 1.5 KB 18–25.
Cable diameter for the strain-relief device: max. 9 mm.
Cable diameter for the connection to the push-in terminal: max. 6 mm
IMPORTANT!
For double-insulated cables with a cable diameter over 6 mm, the external insulation layer must be removed to connect to the push-in terminal.
National regulations, the grid operator's specifications or other factors may require a residual current circuit breaker in the AC connection lead.
For this situation, a type A residual-current circuit breaker is generally adequate. Nevertheless, false alarms can be triggered for the type A residual current circuit breaker in individual cases and depending on local conditions. For this reason, in accordance with national legislation, Fronius recommends that a residual current circuit breaker with a tripping current of at least 100 mA suitable for frequency converters be used.
IMPORTANT!
The inverter can be used with max. an automatic circuit breaker C 32 A.
Inverter | Phases | AC output | Maximum fuse rating | Recommended fuse rating |
Fronius Symo GEN24 6 kW | 3 | 6000 W | C 32 A | C 16 A |
Fronius Symo GEN24 8 kW | 3 | 8000 W | C 32 A | C 25 A |
Fronius Symo GEN24 10 kW | 3 | 10,000 W | C 32 A | C 32 A |
Read the Installation and Operating Instructions before installing and commissioning the equipment.
Only qualified personnel are authorised to commission your inverter and only within the scope of the respective technical regulations.
Danger due to grid voltage and DC voltage from solar modules that are exposed to light.
Prior to any connection work, disconnect the inverter on the AC side and the DC side.
Only an authorised electrical engineer is permitted to connect this equipment to the public grid.
Danger due to damaged and/or contaminated terminals.
Before making any connections, check the terminals for damage and contamination.
Remove contamination in the de-energized state.
Have defective terminals repaired by an authorised specialist.
The neutral conductor must be connected in order to operate the inverter.
It is not possible to operate the inverter in unearthed grids, such as IT grids (insulated grids without ground conductor).
Make sure that the grid's neutral conductor is grounded.
IMPORTANT!
The ground conductor of the AC cable must be laid in such a way that it is the last to be disconnected in the event that the strain-relief device should fail.
This can be ensured by making it somewhat longer and by laying it in a loop.
Turn off the automatic circuit breaker.
Make sure that the DC disconnector is in the "Off" switch setting.
Loosen the five screws of the connection area cover by rotating them 180° to the left using a screwdriver (TX20).
Remove the connection area cover from the device.
Press the lock on the back of the terminal and remove the AC terminal.
Route the mains cable from below through the strain-relief device located on the right side and the ferrite core.
IMPORTANT!
The ground conductor must not be routed through the ferrite core and must be connected with a loop so that if the strain relief device fails, the ground conductor is disconnected last.
For more information on the strain relief device, see chapter Cross section of the AC cable on page (→).
Strip the insulation of the single conductors by 12 mm.
The cable cross section must be selected in accordance with the instructions in Permitted cables from page (→).
Lift to open the terminal's operating lever and insert the stripped single conductor into the slot provided as far as it will go. Then close the operating lever until it engages.
IMPORTANT!
Only one conductor may be connected to each pin. The AC cables can be connected to the AC terminal without ferrules.
L1 | Phase conductor |
L2 | Phase conductor |
L3 | Phase conductor |
N | Neutral conductor |
PE | Ground conductor |
Insert the AC terminal into the AC slot until it engages. Fasten the union nut of the strain-relief device with a torque of 6-7 Nm.
To enable suitable solar modules to be chosen and to use the inverter as efficiently as possible, it is important to bear the following points in mind:
IMPORTANT!
Before connecting up the solar modules, check that the voltage for the solar modules specified by the manufacturer corresponds to the actual measured voltage.
IMPORTANT!
The solar modules connected to the inverter must comply with the IEC 61730 Class A standard.
IMPORTANT!
Solar module strings must not be earthed.
IMPORTANT!
IMPORTANT!
IMPORTANT!
Incorrect operation or poorly executed work can cause serious injury or damage.
Commissioning as well as maintenance and service work in the power module of the inverter must only be carried out by service personnel trained by Fronius and only within the scope of the respective technical regulations. Read the Installation and Operating Instructions before installing and commissioning the equipment.
Ensure that the AC and DC side of the inverter are de-energised before carrying out any connection/maintenance or service tasks.
2 independent PV inputs (PV 1 and PV 2) are available. These can be connected to a different number of modules.
When using for the first time, set up the PV generator according to the respective configuration (also possible later in the “System configuration” menu under the “Components” menu item).
IMPORTANT!
The installation must be carried out in accordance with the nationally applicable standards and directives. If the Arc Fault Circuit Interrupter integrated in the inverter is used for the requirement according to IEC 63027 for arc detection, the solar module strings must not be combined in front of the inverter.
PV generator settings:
PV 1: ON
PV 2: OFF
PV 1: ON
PV 2: OFF
PV 1: ON
PV 2: OFF
PV 1 + PV 2 (connected in parallel): ON
IMPORTANT!
The maximum current load of a single terminal is 25 A. PV connection strings with a total current of more than 25 A must be split between both PV inputs upstream of the terminals (≤ 56.25 A). The plug connection for splitting the total current must be sufficiently dimensioned, suitable and correctly installed. Splitting the current by bridging from PV 1 to PV 2 at the terminal is not permitted.
PV 1: ON
PV 2: ON
Push the DC cables through the DC bushings by hand.
IMPORTANT!
Before stripping the insulation, push the cables through the DC bushings to prevent individual wires being bent or broken.
Select the cable cross section in accordance with the instructions in Permitted cables from page (→).
Strip the insulation of the single conductors by 12 mm. Lift to open the terminal's operating lever and insert the stripped single conductor into the slot provided, in each case as far as it will go. Then close the operating lever until it engages.
No multi-wire connections are possible with this terminal type.
Only one conductor may be connected to each pin. The DC cables can be connected to the DC terminals without ferrules.
Use a suitable measuring instrument to check the voltage and polarity of the DC cabling. Remove both DC terminals from the slots.
Danger due to polarity reversal at the terminals.
Use a suitable measuring instrument to check the polarity of the DC cabling.
Use a suitable measuring instrument to check the voltage (max. 1000 VDC)
Insert the DC terminals into the respective slot until they engage. Fasten the screws of the cable guide to the housing using a screwdriver (TX20) and a torque of 1.3-1.5 Nm.
Do not use a drill driver as this could cause overturning.
A possible consequence of overturning is, for example, damaging the strain-relief device.
Commissioning as well as maintenance and service work on the inverter and battery must only be carried out by service personnel trained by the respective inverter or battery manufacturer and only within the scope of the respective technical regulations. Read the Installation and Operating Instructions provided by the respective manufacturer before installing and commissioning the equipment.
Danger due to grid voltage and DC voltage from solar modules that are exposed to light and from batteries.
Ensure that the AC and DC side of the inverter and the battery are de-energised before carrying out any connection/maintenance or service tasks.
Risk due to operation of the battery above the permissible altitude as specified by the manufacturer.
Operating the battery above the permissible altitude can result in restricted operation, failure of the operation, and unsafe states of the battery.
Adhere to the manufacturer's instructions regarding the permissible altitude.
Operate the battery only at the altitude specified by the manufacturer.
IMPORTANT!
Prior to installing a battery, ensure that the battery is switched off. Refer to the manufacturer's documents for the max. length of the DC cables for installing third-party batteries.
Manually push the BAT cables through the DC bushings.
* Connect the ground conductor of the battery to an external point (e.g. switch cabinet). In doing so, the minimum cross section of the battery's ground conductor must be observed.
IMPORTANT!
Risk due to overvoltage when using other slots on the terminal.
This may result in damage to the battery and/or the solar module due to discharge.
Only use the designated slots for battery connection.
Serious substantive damage to the PV system may result.
Use a suitable measuring instrument to check the polarity of the DC cabling when the battery is switched on.
The maximum voltage for the battery input must not be exceeded (see Technical data on page (→)).
IMPORTANT!
Information for connection on the battery side can be found in the Installation Instructions from the relevant manufacturer.
IMPORTANT!
The valid national laws, standards and provisions, as well as the specifications of the relevant grid operator are to be taken into account and applied.
It is highly recommended that the specific installation be agreed with the grid operator and explicitly approved by this operator. This obligation applies to system constructors in particular (e.g. installers).
The continuous supply via the PV Point depends on the available PV power.
If the solar modules are not supplying enough power, interruptions may occur.
Do not connect any loads that require an interruption-free supply.
Danger from incorrect installation, commissioning, operation or incorrect use.
This can result in severe personal injury/damage to property.
Only trained and qualified personnel are authorised to install and commission the system, and only within the scope of the technical regulations.
The Installation and Operating Instructions must be read carefully prior to use.
If anything is unclear, contact your vendor immediately.
IMPORTANT!
All loads that have to be supplied via the OP terminal must be protected by means of a residual current circuit breaker.
In order to ensure the residual current circuit breaker operates properly, a connection must be established between the neutral conductor N´ (OP) and the earth.
For the Circuit Diagram recommended by Fronius, see Circuit Diagram - PV Point (OP) on page (→).
Switch off the automatic circuit breaker and DC disconnector.
Danger from faulty or incorrect holes.
This may lead to injuries to the eyes and hands as a result of flying debris and sharp edges, as well as damage to the inverter.
When drilling, wear suitable protective goggles.
Only use a step drill when drilling.
Ensure that nothing is damaged inside the device (for example connection block).
Adapt the diameter of the hole to match the corresponding connection.
Deburr the holes using a suitable tool.
Remove the drilling residues from the inverter.
Drill out the optional cable guide with a step drill.
Insert the strain-relief device into the hole and secure to the torque specified by the manufacturer.
Guide the mains cable through the strain-relief device from below.
Remove the OP terminal.
The cable cross section must be between 1.5 mm2 and 10 mm2. Lift to open the terminal's operating lever and insert the stripped single conductor into the slot provided, all the way up to the stop. Then close the operating lever until it engages.
Only one conductor may be connected to each pin. The conductors can be connected without ferrules.
L1´ | Phase conductor |
N´ | Neutral conductor |
N´ | PEN conductor |
The PEN conductor must be produced with ends that are permanently marked blue, according to the national provisions, and have a cross section of 10 mm².
Fasten the ground conductor and PEN conductor to the ground electrode terminal using a screwdriver (TX20) and a torque of 1.8-2 Nm.
Insert the OP terminal into the OP slot until it engages. Tighten the union nut of the strain-relief device to the torque specified by the manufacturer.
The examples given in this document (in particular cabling variants and Circuit Diagrams) are suggestions only. These examples have been carefully developed and tested. They can therefore be used as a basis for real-life installation. Anyone following or using these examples does so at their own risk.
IMPORTANT!
It is highly recommended to coordinate the concrete examples implemented and in particular the specific installation with the grid operator to obtain their explicit approval. This obligation applies to system constructors in particular (e.g. installers).
The examples suggested here show a backup power supply with or without an external protection relay (external grid and system protection unit). Whether an external protection relay must be used or not is the decision of the respective grid operator.
IMPORTANT!
No uninterruptible power supply (UPS) must be operated in the backup power circuit. The Installation and Operating Instructions must be read carefully prior to use. If anything is unclear, contact your vendor immediately.
IMPORTANT!
IMPORTANT!
Circuit Diagram
The Circuit Diagram for the 3-pin double separation - e.g. Austria, can be found on page (→) in the appendix of this document.
The Circuit Diagram for the 3-pin single separation - e.g. Australia, can be found in the appendix of this document on page (→).
Cabling of backup power circuit and non-backup power circuits
If not all the loads in the home need to be supplied in a backup power situation, the circuits need to be divided into backup power circuits and non-backup power circuits. The total load of the backup power circuits must not exceed the nominal output of the inverter.
The backup power circuits and non-backup power circuits must be fused separately according to the required safety measures (residual-current circuit breaker, automatic circuit breaker, etc.).
In backup power mode, only the backup power circuits are disconnected from the grid by contactors K1 and K2, 3-pin. The rest of the home network is not supplied with power in this case.
Circuit Diagram
The Circuit Diagram for the 4-pin double separation - e.g. Germany, can be found in the appendix of this document on page (→)
The Circuit Diagram for the 4-pin single separation - e.g. France and Spain, can be found in the appendix of this document on page (→).
In backup power mode, only the backup power circuits are disconnected at all pins from the grid by contactors K1 and K2; an earth connection is only established for these circuits. The rest of the home network is not supplied with power in this case.
Circuit Diagram
The Circuit Diagram for the 4-pin double separation with ext. grid and system protection - e.g. Italy, can be found on page (→) in the appendix of this document.
Backup power circuit and non-backup power circuits
IMPORTANT!
Fronius Smart Meter US-480 must be used for these circuit variants.
In backup power mode, only the backup power circuits are disconnected from the grid by contactors K1 and K2; an earth connection is only established for these circuits. The rest of the home network is not supplied with power in this case.
Backup power mode should be tested once it has been installed and set up for the first time. A battery state of charge of over 30% is recommended when in test mode.
A description on how to run test mode can be found in the backup power checklist (https://www.fronius.com/en/search-page, item number: 42,0426,0365).
The inputs M0 and M1 can be selected for this purpose. A maximum of 4 Modbus participants can be connected to the Modbus terminal on inputs M0 and M1.
IMPORTANT!
Only one primary meter, one battery and one Ohmpilot can be connected per inverter. Due to the high data transfer of the battery, the battery occupies 2 participants. If the "Inverter control via Modbus" function is activated in the "Communication” "Modbus" menu, no Modbus participants are possible. It is not possible to send and receive data at the same time.
Example 1:
Input | Battery | Fronius | Quantity | Quantity |
Modbus 0 (M0) | 0 | 4 | ||
0 | 2 | |||
0 | 1 | |||
Modbus 1 (M1) | 1 | 3 |
Example 2:
Modbus 0 (M0) | 1 | 3 | ||
Modbus 1 (M1) | 0 | 4 | ||
0 | 2 | |||
0 | 1 |
IMPORTANT!
Example 1:
0 | 2 | |||
0 | 1 | |||
Example 2:
0 | 2 | |||
0 | 1 |
IMPORTANT!
Should the blanking plugs be missing or improperly fitted, then protection class IP66 cannot be guaranteed.
Undo the strain-relief device union nut and push out the sealing ring and the blanking plug from the inside of the device.
Open up the sealing ring at the location where the blanking plug is to be removed.
* Liberate the blanking plug by moving it sideways.
Guide the data cables first through the strain-relief device union nut and then through the housing opening.
Insert the sealing ring between the union nut and the housing opening. Press the data cables into the seal's cable guide. Then press in the seal until it reaches the underside of the strain-relief device.
Fasten the union nut of the strain-relief device with a torque of min. 2.5 - max. 4 Nm.
Strip 10 mm from the single conductors and mount the ferrules if necessary.
IMPORTANT!
Insert the cable into the respective slot and check the cable is securely retained.
IMPORTANT!
Use only twisted pairs for connecting "Data +/-" and "Enable +/-", see section Permitted cables for the data communication area on page (→).
Twist the cable shield and insert into the "SHIELD" slot.
IMPORTANT!
Improperly fitted shielding can cause data communication problems.
For the wiring proposal recommended by Fronius, see page (→).
It may be possible for the system to function without terminating resistors. However, owing to interference, the use of terminating resistors according to the following overview is recommended for trouble-free functioning.
For permissible cable and max. distances see chapter Permitted cables for the data communication area on page (→).
IMPORTANT!
Terminating resistors that are not positioned as illustrated can result in interference in the data communication. If the terminating resistor on the battery cannot be deactivated, the battery is to be set up at the bus end (see option 2, 3).
IMPORTANT!
The push-in WSD terminal in the inverter's connection area is delivered with a bypass ex works as standard. The bypass must be removed when installing a trigger device or a WSD chain.
The WSD switch of the first inverter with connected trigger device in the WSD chain must be in position 1 (primary device). The WSD switch of all other inverters should be in the 0 (secondary device) position.
Max. distance between two devices: 100 m
Max. number of devices: 28
* Floating contact of the trigger device (e.g. central grid and system protection). If several floating contacts are used in a WSD chain, they must be connected in series.
The housing cover is fitted with a lock for safety reasons, which allows the housing cover on the inverter to be pivoted only when the DC disconnector is switched off.
Only clip and pivot the housing cover onto the inverter when the DC disconnector is switched off.
Do not use excessive force to clip in and pivot the housing cover.
Place the cover on the connection area. Tighten the five screws by rotating them 180° to the right in the indicated order using a screwdriver (TX20).
Clip the housing cover onto the inverter from above.
Press on the lower part of the housing cover and tighten the two screws 180° to the right using a Torx screwdriver (TX20).
Turn the DC disconnector to the "On" switch position. Switch on the automatic circuit breaker. For systems with a battery, observe the switch-on sequence according to chapter Suitable battery on page (→).
IMPORTANT! Open WLAN access point with the optical sensor, see chapter Button functions and LED status indicator on page (→)
When using the inverter for the first time, various setup settings must be configured.
If the setup process is cancelled before the process is complete, any data that has been input up to this point is lost and the start screen with the installation wizard is shown again. If the process is interrupted, such as in the event of a power outage, the data is saved. Commissioning may be continued from the point at which the process was interrupted once the power supply has been restored. If the setup was interrupted, the inverter feeds energy into the grid at maximum 500 W and the operating status LED flashes yellow.
The country setup can only be set when using the inverter for the first time. If the country setup needs to be changed at a later date, please contact your installer / Technical Support team.
The status of the inverter is shown via the operating status LED. In the event of faults, carry out the individual steps in the Fronius Solar.start app. | |
The optical sensor is actuated by touching with a finger. | |
The status of the connection is shown via the communication LED. To establish the connection, carry out the individual steps in the Fronius Solar.start app. |
Sensor functions | ||
| 1x | |
| 2x | |
| 3 seconds |
LED status indicator | ||
| The inverter is operating correctly. | |
| The inverter starts. | |
| The inverter is in standby, is not operational (e.g. no feed-in at night) or is not configured. | |
| The inverter indicates a non-critical status. | |
| The inverter indicates a critical status and there is no grid power feed process. | |
| The inverter indicates a backup power overload. | |
| The network connection is being established via WPS. | |
| The network connection is being established via WLAN AP. | |
| The network connection is not configured. | |
| The inverter is operating correctly, a network fault is indicated. | |
| The inverter is performing an update. |
The "Fronius Solar.start" app is needed for this installation method. Depending on the end device with which the installation will be carried out, download the app for the respective platform.
The network wizard and the product setup can be carried out independently of each other. A network connection is required for the Solar.web installation wizard.
WLAN:
Ethernet:
To start up the inverter again, follow the steps listed above in reverse order.
IMPORTANT!
Depending on the user's authorization, settings can be executed in the individual menus.
IMPORTANT!
IMPORTANT!
Select "Add component+" to add all available components to the system.
PV generator
Activate the MPP tracker and enter the connected PV power in the associated field. For combined solar module strings, "PV 1 + PV 2 connected in parallel" must be activated.
Battery
If the SoC mode is set to "Automatic", the values "Minimum SoC" and "Maximum SoC" are preset according to the technical specifications of the battery manufacturer.
If the SoC mode is set to "Manual", the values "Minimum SoC" and "Maximum SoC" may be changed after consultation with the battery manufacturer within the scope of their technical specifications. In the event of a power outage, the set values are not taken into account.
Using the "Allow battery charging from additional producers in home network" setting, charging of the battery from other external producers is enabled/disabled.
Using the "Allow battery charging from public grid" setting, charging of the battery from the public grid is enabled/disabled.
The normative or feed-in tariff rules must be taken into account with this setting. The setting does not affect the charging of the battery by other producers within the home. It merely relates to the process of drawing charging energy from the public grid. Regardless of this setting, any charging from the public grid that is required for service reasons (e.g. necessary re-charging to protect against deep discharge) is still performed.
IMPORTANT!
Fronius accepts no liability for damage to third-party batteries.
Primary meter
To ensure smooth operation in conjunction with other energy producers and in Full Backup backup power mode, it is important to install the Fronius Smart Meter at the feed-in point. The inverter and other producers must be connected to the public grid via the Fronius Smart Meter.
This setting also affects the behaviour of the inverter at night. If the function is deactivated, the inverter switches to Standby mode as soon as there is no more PV power available, provided that no energy management command is sent to the battery (e.g. minimum state of charge reached). The message "Power low" is displayed. The inverter restarts as soon as an energy management command is sent or sufficient PV power is available.
If the function is activated, the inverter remains permanently connected to the grid so that energy can be drawn from other producers at any time.
After connecting the meter, the position must be configured. A different Modbus address needs to be set for each Smart Meter.
The Watt value on the generator meter is the sum of all generator meters. The Watt value on the consumption meter is the value of all secondary meters.
Ohmpilot
All Ohmpilots available in the system are displayed. Select the desired Ohmpilot and add it to the system via "Add".
PV generator
Battery
IMPORTANT!
Primary meter
Ohmpilot
Backup power
"Off", "PV Point" or "Full Backup" can be selected for backup power mode.
Full Backup can only be activated once the required I/O assignments have been configured for backup power. In addition, a meter must be mounted and configured at the feed-in point for Full Backup backup power mode.
IMPORTANT!
When configuring "PV Point" backup power mode, the information in chapter Safety on page (→) must be observed.
When configuring "Full Backup" backup power mode, the information in chapter Safety on page (→) must be observed.
Backup power nominal voltage
When backup power mode is activated, the nominal voltage of the public grid must be selected.
State of charge warning limit
A warning is output when the residual capacity of the battery specified here is reached in backup power mode.
Reserve capacity
The set value results in a residual capacity (depending on the capacity of the battery) that is reserved for backup power. The battery is not discharged below the residual capacity in grid-connected operation. In backup power mode, the manually set value "Minimum SoC" is not taken into account. If there is a power outage, the battery is always discharged down to the automatically preset minimum SoC in accordance with the technical specifications of the battery manufacturer.
Load management
Up to four pins can be selected for load management here. Additional load management settings are available in the "Load management" menu item.
Default: Pin 1
The pins for control via DRM can be set here:
Mode | Description | Information | DRM pin | I/O pin |
DRM0 | Inverter disconnects itself from the grid | DRM0 occurs if there is an interruption or short circuit on the REF GEN or COM LOAD leads, or if the combinations DRM1 - DRM8 are invalid. | REF GEN | IO4 |
DRM1 | Import Pnom ≤ 0% without disconnection from the grid | currently not supported | DRM 1/5 | IN6 |
DRM2 | Import Pnom ≤ 50% | currently not supported | DRM 2/6 | IN7 |
DRM3 | Import Pnom ≤ 75% & | currently not supported | DRM 3/7 | IN8 |
DRM4 | Import Pnom ≤ 100% | currently not supported | DRM 4/8 | IN9 |
DRM5 | Export Pnom ≤ 0% without disconnection from the grid | currently not supported | DRM 1/5 | IN6 |
DRM6 | Export Pnom ≤ 50% | currently not supported | DRM 2/6 | IN7 |
DRM7 | Export Pnom ≤ 75% & | currently not supported | DRM 3/7 | IN8 |
DRM8 | Export Pnom ≤ 100% | currently not supported | DRM 4/8 | IN9 |
The percentages always refer to the nominal device output. |
IMPORTANT!
If the Demand Response Mode (DRM) function is enabled and no DRM control is connected, the inverter switches to Standby mode.
Here you can enter a value for the apparent power input and the apparent power output for the Australia country setup.
"Enforce Standby"
When the function is activated, the feed-in mode of the inverter is interrupted. This enables a powerless shutdown of the inverter and protects its components. When the inverter is restarted, the standby function is automatically deactivated.
"PV 1" and "PV 2"
Parameter | Range of values | Description |
"Mode" | Off | The MPP tracker is deactivated. |
Auto | The inverter uses the voltage at which the max. possible power of the MPP tracker is possible. | |
Fix | The MPP tracker uses the voltage defined in the "UDC fix". | |
"UDC fix" | 80 ‑ 530 V | The inverter uses the fixed preset voltage used at the MPP tracker. |
"Dynamic Peak Manager" | Off | The function is deactivated. |
On | The entire solar module string is checked for optimisation potential and determines the best possible voltage for feed-in mode. |
"Ripple Control"
Ripple control signals are signals sent out by the energy company to switch controllable loads on and off. Depending on the installation situation, ripple control signals may be attenuated or amplified by the inverter. The settings below can be used to counteract this if necessary.
"Reduction of Influence" | Off | The function is deactivated. |
On | The function is activated. | |
"Frequency of Ripple Control Signal" | 100 ‑ 3000 Hz | The frequency specified by the energy company must be entered here. |
"Grid Inductance" | 0.00001 ‑ 0.005 H | The value measured at the feed-in point must be entered here. |
"Measure against RCD false triggers"
(when using a 30 mA residual current circuit breaker)
For this situation, a type A residual current circuit breaker is generally adequate. Nevertheless, false alarms can be triggered for the type A residual current circuit breaker in individual cases and depending on local conditions. For this reason, in accordance with national legislation, Fronius recommends that a residual current circuit breaker with a tripping current of at least 100 mA suitable for frequency converters be used.
"Switch-Off before 30mA RCD Trip" (only for Primo GEN24) | 0 | No measures to prevent false tripping. |
1 | The inverter switches off at 15 mA before the residual current circuit breaker trips. | |
"Leakage Current Factor" (only for Symo GEN24) | 0 ‑ 0.25 | Reducing the setting value reduces the leakage current and raises the intermediate circuit voltage, which slightly reduces the efficiency. Setting value 0.16 enables optimum efficiency. |
"Iso Warning"
"Iso Warning" | Off | The isolation warning is deactivated. |
On | The isolation warning is activated. | |
"Iso Alternative Mode"
| Accurate | Isolation monitoring is performed with the highest accuracy and the measured insulation resistance is displayed on the user interface of the inverter. |
Fast | Isolation monitoring is performed with lower accuracy, which shortens the duration of the isolation measurement, and the isolation value is not displayed on the user interface of the inverter. | |
"Isolation Warning Threshold" | 100,000 ‑ | If this threshold is undershot, status code 1083 is displayed on the user interface of the inverter. |
"Backup Power"
"Backup Nominal Voltage" | 220 ‑ 240 V | Is the nominal phase voltage output in backup power mode. |
"Backup Undervoltage Protection Limit U< [pu]" | 0 ‑ 2%V | The setting value is used to set the limit value for switching off backup power mode, |
"Backup Undervoltage Protection Time U<" | 0.04 ‑ 20 s | Triggering time for falling below the backup power undervoltage protection limit value. |
"Backup Overvoltage Protection Limit U> [pu]" | 0 ‑ 2%V | The setting value is used to set the limit value for switching off backup power mode, |
"Backup Overvoltage Protection Time U>" | 0.04 ‑ 20 s | Triggering time for exceeding the backup power overvoltage protection limit value. |
"Backup Restart Delay" | 0 ‑ 600 s | Is the waiting time for resumption of backup power mode after a shutdown. |
"Backup Restart Attempts" | 1 ‑ 10 | Is the max. number of automatic restart attempts. When the max. number of automatic restart attempts is reached, the service message 1177 must be acknowledged manually. |
"Backup External Frequency Check"
| Off | The function is deactivated |
On | For backup power mode (Full Backup) in Italy, the external frequency check must be activated. Before ending backup power mode, the grid frequency is checked. When the grid frequency is in the allowed limit range, the loads are connected to the public grid. | |
"Backup Short Circuit Trip Time" | 0.001 ‑ 60 s | If a short circuit occurs in backup power mode, this mode is interrupted within the set time. |
Self-consumption optimisation
The inverter always adjusts to the set target value on the Smart Meter. In the "automatic" operating mode (factory setting), an adjustment is made to 0 W at the feed-in point (maximum self-consumption).
The self-consumption optimisation has lower priority than the battery control specifications.
Self-consumption optimization
Switch self-consumption optimization to automatic or manual.
Target value on Smart Meter
If a manual selection is made under self-consumption optimisation, the target value on the Smart Meter and the reference/feed-in can be selected here.
External producers (only possible with active battery and inverter with battery connection)
If further decentralised producers are installed in the house, and these are incorporated into the self-consumption regulation of the Fronius Hybrid inverter, this setting must be activated. This means that energy can be drawn from the household network and fed into the battery via the Fronius GEN24 inverter. You can restrict how much power is consumed by the Fronius GEN24 inverter by specifying the maximum AC power (AC max.). A maximum power consumption of the AC rated power of the Fronius GEN24 inverter is possible.
Priorities
If additional components (e.g. battery, Ohmpilot) are present in the system, the priorities can be set here. Devices having higher priority are actuated first, and subsequently, if there is still excess energy available, the other devices.
Load management
It is possible for up to four different load management rules to be defined. At the same threshold values, the rules are activated in succession. For deactivation, this is done in reverse; the I/O last switched on is the first to be switched off. In the case of different thresholds, the I/O with the lowest threshold is switched on first, followed by the second lowest, and so on.
I/Os controlled by the produced power are always prioritised over a battery and Ohmpilot. That is to say that an I/O can switch on and result in the battery no longer being charged or the Ohmpilot no longer being activated.
An I/O is activated or deactivated only after 60 seconds.
ControlAll available updates are made available on the product page and in the "Download search" area under www.fronius.com .
The update will start.
The guided setup wizard can be accessed here.
All settings
All configuration data is reset with the exception of the country setup. Changes to the country setup may only be carried out by authorized personnel.
All settings with no network
All configuration data is reset with the exception of the country setup and the network settings. Changes to the country setup may only be carried out by authorized personnel.
Current events
All current events of the connected system components are shown here.
IMPORTANT!
Depending on the type of event, these must be confirmed via the "tick" button in order to be processed further.
Archived
All events of the connected system components that no longer exist are shown here.
This menu displays all system information and the current settings.
The PDF is created and displayed.
The licence file contains the performance data and the scope of functions of the inverter. When replacing the inverter, power stage set or data communication area, the licence file must also be replaced.
The licence activation starts.
The support user is activated.
IMPORTANT!
The support user only allows Fronius Technical Support to implement settings on the inverter via a secure connection. The button "End support user access" deactivates the access.
The sdp.cry file is saved in the downloads.
Remote maintenance access for the Fronius Support team is enabled.
IMPORTANT!
Remote maintenance access gives Fronius Technical Support exclusive access to the inverter via a secure connection. Diagnostic data is transmitted here that can be used for troubleshooting purposes. Only enable remote maintenance access following a request from the Fronius Support team.
LAN:
The connection is established.
WLAN:
The connection is established automatically.
Access point:
The inverter acts as the access point. A PC or smart device connects directly with the inverter. It is not possible to connect to the internet. The "Network name (SSID)" and "Network key (PSK)" can be assigned in this menu.
It is possible to operate a connection via WLAN and via access point simultaneously.
LAN:
WLAN:
Access point:
Modbus RTU interface 0 / 1
If one of the two Modbus RTU interfaces is set to Slave, the following input fields are available:
"Baud rate"
The baud rate influences the transmission speed between the individual components connected in the system. When selecting the baud rate, ensure that it is the same at both the sending and receiving end.
"Parity"
The parity bit can be used to check the parity. It detects transmission errors. A parity bit can safeguard a specific number of bits. The value (0 or 1) of the parity bit must be calculated by the sender and is checked by the recipient using the same calculation. The parity bit can be calculated for even and odd parity.
"SunSpec Model Type"
Depending on the SunSpec model, there are two different settings.
float: SunSpec Inverter Model 111, 112, 113 or 211, 212, 213.
int + SF: SunSpec Inverter Model 101, 102, 103 or 201, 202, 203.
"Meter address"
The value entered is the identification number (Unit ID) assigned to the meter. Can be found on the user interface of the inverter in the Communication - Modbus menu.
Factory setting: 200
"Inverter address"
(Unit ID) assigned to the inverter. Can be found on the user interface of the inverter in the Communication - Modbus menu.
Factory setting: 1
Slave as Modbus TCP
If the function "Slave as Modbus TCP" is activated, the following input fields are available:
"Modbus port"
Number of the TCP port that is to be used for Modbus communication.
"Meter address"
"Inverter address"
The value entered is the identification number (Unit ID) assigned to the inverter. Can be found on the user interface of the inverter in the Communication - Modbus menu.
Factory setting: This value is invariably defined as 1.
The Fronius Solar API is an Ethernet-based, open JSON interface. When enabled, IOT devices on the local network can access inverter information without authentication. For security reasons, the interface is deactivated at the factory and should not be activated if it is not required for a third-party application (e.g. EV charger, smart home solutions, etc.).
For monitoring, Fronius recommends using Fronius Solar.web instead, which provides secure access to inverter status and production information.
When performing a firmware update to version 1.14.x, the setting (activated/deactivated) of the Fronius Solar API is adopted.
The "Country setup" menu area is intended exclusively for installers/service technicians from authorised specialist companies. The access code must be requested from the national/international Fronius point of contact using an application form.
The selected country setup for the respective country contains preset parameters according to the nationally applicable standards and requirements. Depending on local grid conditions and the specifications of the energy provider, adjustments to the selected country setup may be necessary.
Risk due to unauthorised access.
Incorrectly set parameters can negatively influence the public grid and/or the feed-in of power into mains by the inverter, and lead to a loss of conformity with the standard.
The parameters may only be adjusted by installers/service technicians from authorised specialist companies.
Do not give the access code to third parties and/or unauthorised persons.
Risk due to incorrectly set parameters.
Incorrectly set parameters can negatively influence the public grid and/or cause faults and failures on the inverter, and lead to the loss of standard conformity.
The parameters may only be adjusted if the energy provider permits or requires this.
Only adjust the parameters taking into account the nationally applicable standards and/or directives and the specifications of the energy provider.
Energy companies or grid operators may stipulate feed-in limitations for an inverter (e.g. max. 70% of kWp or max. 5 kW).
The feed-in limitation takes account of self-consumption by the household before the power of an inverter is reduced:
With the inverter, any PV power that is not allowed to be fed into the public grid is used to charge the battery instead and/or used by the Fronius Ohmpilot so that it does not go to waste. The feed-in limitation is only active if the power of feeding in is higher than the set power reduction.
"Off"
The inverter converts the entire available PV power and feeds it into the public grid.
"Limit for entire system"
The entire PV system is limited in accordance with a set power limit. The value of the permissible total feed-in power must be set.
"Limit per phase"
Each individual phase is measured. If the permissible feed-in limit is exceeded on one phase, the total power of the inverter is reduced until the value on the affected phase is permissible again (see example below). This setting is only necessary if required by national standards and regulations. The value of the permissible power of feeding in per phase must be set.
Example: "Limit per phase" (setting value: 2000 W) | ||||
| Phase 1 | Phase 2 | Phase 3 | Total |
Max. possible production [W] | 2000 | 2000 | 2000 | 6000 |
Set value | 1000 | 3000 | ||
Load demand in the household network [W] | 2000 | 3000 | 5000 | 10000 |
Load coverage in the household network via PV system [W] | 1000 | 3000 | ||
Purchase from the public grid [W] | 1000 | 2000 | 4000 | 7000 |
"Total DC system power"
Input field for the total DC system power in Wp.
This value is used if the "Maximum permitted feed-in power of the entire system" is specified in %.
Input field for the "Maximum permitted feed-in power of the entire system" in W or % (setting range: -10 to 100%).
If there is no meter in the system or if a meter has failed, the inverter limits the power of feeding in to the set value.
Example: Feed-in limitation | |
PV system to Fronius inverter | 5000 W |
Loads in the house | 1000 W |
Maximum permitted feed-in power of the entire system | 60% = 3000 W |
Case 1: The battery can be charged | |
Power at grid feed-in point | 0 W |
Power at inverter output | 1000 W |
Power into the battery | 3000 W |
Case 2: The battery cannot be charged | |
Power at grid feed-in point | 3000 W |
Power at inverter output | 4000 W |
Power into the battery | 0 W |
In this example, no more than 3000 W may be fed into the public grid at the grid feed-in point. However, any loads that are located between the inverter and the grid feed-in point can be supplied by additional power from the inverter. |
"Hard Limit"
If this value is exceeded, the inverter switches off within max. 5 seconds. This value must be higher than the value set for "Soft Limit".
"Soft Limit"
If this value is exceeded, the inverter will regulate down to the set value within the time required by national standards and regulations.
Example 1: Fronius SnapINverter ≤ Fronius Symo GEN24
Only one primary meter is required for the Fronius Symo GEN24 inverter.
The power values shown are an example. Inverter configurations with power values other than those shown in the example are possible, taking into account the criteria for this example.
IMPORTANT!
Zero feed-in is not possible when using 2 inverters.
Example 2a: Fronius SnapINverter > Fronius Symo GEN24
Two primary meters are required for the inverters.
IMPORTANT!
With two primary meters at the feed-in point without a secondary meter, Fronius SnapINverter and Fronius Symo GEN24 inverters cannot be displayed as a combined PV system in Solar.web. Two individual PV systems must be created in Solar.web.
Example 2b: Fronius SnapINverter > Fronius Symo GEN24
Two primary meters and one secondary meter are required for the inverters.
IMPORTANT!
In order to be able to record all PV system data in Solar.web in full, only the Fronius Symo GEN24 inverter may be created in this PV system. The Fronius SnapINverter data is transmitted from the secondary meter to the Fronius Symo GEN24 inverter and thus displayed in the Solar.web.
We recommend that you set up the Fronius SnapINverter as a separate additional PV system in Solar.web for servicing and maintenance work (e.g. status codes, online updates, etc.).
General
In this menu item, settings relevant for an electricity company (DNO) are made. An effective power limitation in % and/or a power factor limitation can be set.
IMPORTANT!
The service password must be entered in order to adjust settings in this menu item. Settings in this menu area must only be made by trained and qualified personnel.
"Input pattern" (assignment of individual I/Os)
1 click = white (contact open)
2 clicks = blue (contact closed)
3 x clicks = grey (not used)
"Power factor (cos φ)"
"ind" = inductive
"cap" = capacitive
"DNO feedback"
when the rule is enabled, output “DNO feedback” (pin 1 recommended) must be configured (e.g. for operating a signalling device).
For "Import" or "Export", the data format *.fpc is supported.
Control priorities
For setting the control priorities for the ripple control signal receiver, the feed-in limitation and control via Modbus.
1 = highest priority, 3 = lowest priority
The ripple control signal receiver and the I/Os terminal of the inverter can be connected to one another in accordance with the connection diagram.
If the distance between the inverter and the ripple control signal receiver exceeds 10 m, at least a CAT 5 cable is recommended and the shield must be connected at one end to the push-in terminal of the data communication area (SHIELD).
(1) | Ripple control signal receiver with 4 relays, for effective power limitation. |
(2) | I/Os of the data communication area. |
The settings for 4-relay mode are stored.
(1) | Ripple control signal receiver with 3 relays, for effective power limiting. |
The settings for 3-relay mode are stored.
(1) | Ripple control signal receiver with 2 relays, for effective power limitation. |
The settings for 2-relay mode are stored.
(1) | Ripple control signal receiver with 1 relay, for effective power limiting. |
The settings for 1-relay mode are stored.
Description
The 'Autotest' can be used to check the protective function required by the Italian standard for monitoring the voltage and frequency limits as well as the trip limits of the inverter during commissioning. During normal operation, the inverter constantly checks the current voltage and frequency actual value of the grid.
After the start of the autotest, various individual tests run automatically one after the other. Depending on grid conditions, the duration of the test is approx. 15 minutes.
IMPORTANT!
The inverter may only be commissioned in Italy after a successful autotest (CEI 0-21). If the autotest is not passed, no feed-in operation may take place. If the autotest is started once, it must be completed successfully. The autotest cannot be started during emergency power mode.
VAC inner limit max |
| Test to check the maximum voltage in the phases |
VAC inner limit min |
| Test to check the minimum voltage in the phases |
FAC inner limit max |
| Test to check the maximum frequency |
FAC inner limit min |
| Test to check the minimum frequency |
FAC alternativ inner limit max |
| Test to check the maximum alternative frequency |
FAC alternativ inner limit min |
| Test to check the minimum alternative frequency |
VAC outer limit min |
VAC long time limit |
| Test to check the 10 min average voltage in the phases |
Note on autotest
The limit values are set in the menu area 'Grid Code'.
The access code for the 'Grid Code' menu area corresponds to the installer code (PROFI menu) and is only made available to Fronius following a written request. An appropriate application form is available from national technical support.
A surge protective device (SPD) protects against temporary overvoltages and dissipates surge currents (e.g. lightning strike). Building on an overall lightning protection concept, the SPD helps to protect your PV system components.
For detailed information on the wiring diagram of the surge protective device, see chapter Wiring diagram - surge protective device SPD on page (→).
If the surge protective device is triggered, the colour of the indicator changes from green to red (mechanical display) and the operation LED of the inverter lights up red (see chapter Button functions and LED status indicator on page (→)). The error code "1030 WSD Open " is displayed on the inverter's website in the System " → " Event Log " menu or in the user menu under "Notifications as well as in Fronius Solar.web. In this case, the inverter must be repaired by an authorised specialist.
IMPORTANT!
The inverter also switches off if the 2-pin signal cable of the surge protective device is interrupted or damaged.
IMPORTANT!
IMPORTANT!
The surge protective device (SPD) is an optional extra and can be retrofitted to the inverter.
For technical data, see chapter "Technical data" on page (→).
Danger due to electrical voltage on live parts of the PV system.
Disconnect live parts of the PV system on all pins and on all sides.
Secure against re-activation in accordance with national regulations.
Check that the inverter is de-energised with a suitable measuring device.
Installing and connecting a surge protective device (SPD) must only be carried out by service personnel trained by Fronius and only within the scope of the respective technical regulations.
Follow the safety rules.
Turn off the automatic circuit breaker. Set the DC disconnector to the "Off" switch position.
Disconnect connections from the solar module strings (+/-). Switch off the battery connected to the inverter.
Wait for the capacitors of the inverter to discharge (2 minutes).
Risk due to insufficiently dimensioned ground conductor.
Damage to the inverter due to thermal overload can result.
The national standards and guidelines must be observed for dimensioning the ground conductor.
Loosen the two screws on the underside of the housing cover by rotating them 180° to the left using a screwdriver (TX20). Then lift the housing cover away from the inverter at the bottom and detach from above.
Remove the connection area divider by pressing the snap tabs.
Remove the DC push-in terminals from the slots and disconnect them from the cables (only necessary if the installation already exists).
Connect the supplied PV+/PV- cables to the respective connections.
IMPORTANT!
Note the labelling of the cables when connecting.
Connect the supplied cables to the respective connectors on the PC board.
IMPORTANT!
The plugs must be connected onto the PC board as far as they will go.
Insert the PC board into the inverter and secure with the four screws (TX20) supplied at a torque of 1.0 ‑ 1.2 Nm.
IMPORTANT!
Depending on national standards and guidelines, a larger cross section of the ground conductor may be required.
Dimension the cable cross section of the ground conductor according to the national standards and guidelines and fit a ring cable lug (inner diameter: 4 mm, outer diameter: max. 10 mm) as well as a corresponding ferrule. Fasten the ground conductor to the PC board with a torque of 1.5 Nm.
Fasten the ground conductor to the first input from the bottom of the ground electrode terminal using a screwdriver (TX20) and a torque of 1.8 - 2 Nm.
IMPORTANT!
The use of other inputs can make it difficult to insert the connection area divider or damage the ground conductor.
Strip the insulation on the single conductors by 12 mm and secure to the corresponding slot of the terminal on the PC board with a torque of 1.2 - 1.5 Nm.
IMPORTANT!
The cable cross-section must be selected according to the specifications for the respective inverter power category (see chapter Permitted cables on page (→)).
Push the DC push-in terminals into the corresponding slot until there is an audible click.
Re-insert the connection area divider.
* Lay the ground conductor in the integrated cable duct.
IMPORTANT!
When inserting the connection area divider, be careful not to kink, pinch, crush or otherwise damage the ground conductor.
Remove the factory installed bypass on the push-in WSD terminal.
Connect the signal cable to the push-in WSD terminal on the IN- and IN+ slots, observing the labelling.
Check whether the WSD switch is in position 1, adjust if necessary (factory setting: position 1).
Press on the lower part of the housing cover and tighten the two screws by rotating them 180° to the right using a screwdriver (TX20).
Connect the solar module strings (+/-). Switch on the battery connected to the inverter.
Set the DC disconnector to the "On" switch position. Switch on the automatic circuit breaker.
The inverter is designed in such a way that no additional maintenance work builds up. Nevertheless, a few points must be considered during operation to ensure that the inverter works perfectly.
Maintenance and servicing may only be carried out by Fronius-trained service technicians.
Clean the inverter as required with a damp cloth.
Do not use cleaning agents, abrasives solvents or similar to clean the inverter.
The DC disconnector is used only to switch off power to the power stage set. When the DC disconnector is turned off, the connection area is still energized.
Danger from grid voltage and DC voltage from solar modules.
The connection area must only be opened by an authorised electrician.
The separate power stage set area must only be opened by Fronius-trained service technicians.
Danger of residual voltage from capacitors.
Allow the capacitors of the inverter to discharge (2 minutes).
If the inverter is operated in dusty environments, dirt may build up on the heat sink and fan.
This may result in a loss of power due to insufficient cooling of the inverter.
Make sure that the ambient air can always flow through the inverter's ventilation slots unimpeded.
Remove any build-ups of dirt from the heat sink and the fan.
Switch off power to the inverter and wait for the specified time (2 minutes) until the capacitors have discharged and the fan has shut down.
Turn the DC disconnector to the "Off" switch position.
Loosen the screws on the underside of the housing cover by rotating them 180° to the left using a screwdriver (TX20). Then lift the housing cover away from the inverter at the bottom and detach from above.
Remove any build-up of dirt on the heat sink and fan using compressed air, a cloth, or a brush.
Risk due to damage to the fan bearing from improper cleaning.
Excessive speed and pressure on the fan bearing can cause damage.
Block the fan and clean it with compressed air.
When using a cloth or brush, clean the fan without applying pressure to the fan.
Waste electrical and electronic equipment must be collected separately and recycled in an environmentally responsible manner in accordance with the European Directive and national law. Used equipment must be returned to the distributor or through a local, authorised collection and disposal system. Proper disposal of the old device promotes sustainable recycling of material resources. Ignoring this may lead to potential health/environmental impacts.
Detailed, country-specific warranty terms are available on the internet:
www.fronius.com/solar/warranty
To obtain the full warranty period for your newly installed Fronius inverter or storage system, please register at: www.solarweb.com.
Device name | Current converter | Item number |
Fronius Smart Meter 63A-3 | 43,0001,1473 | |
Fronius Smart Meter 50kA-3 | 43,0001,1478 | |
Fronius Smart Meter TS 65A-3 | 43,0001,0044 | |
Fronius Smart Meter TS 5kA-3 | 43,0001,0046 | |
Fronius Smart Meter 480 V-3 UL | 43,0001,3530 |
K1 and K2 - installation contactor with auxiliary contact | |||
Number of pins | 3-pin or 4-pin | ||
Rated current | depending on house connection | ||
Coil voltage | 230 V AC | ||
Rated frequency | 50/60 Hz | ||
Coil fuse | 6 A | ||
Min. short circuit current | 3 kA (make contacts) | ||
Test standard | IEC 60947-4-1 | ||
Auxiliary contact | |||
Number of NC contacts | 1 | ||
Switching voltage | 12-230 V @ 50/60 Hz | ||
Min. nominal current | 1 A | ||
Min. short circuit current | 1 kA | ||
Examples of contactors and relays | ISKRA IK63-40 / Schrack BZ326461 |
K3 - modular relay | |||
Number of changeover contacts | 2 | ||
Coil voltage | 12 V DC | ||
Examples of contactors and relays | Finder 22.23.9.012.4000 / Schrack relay RT424012 (bracket RT17017, relay base RT78725) |
K4 and K5 - installation contactor | |||
Number of NC contacts | 2 (25 A) | ||
Coil voltage | 230 V AC (2P) | ||
Examples of contactors and relays | ISKRA IKA225-02 |
Cause: | A device connected in the WSD chain has interrupted the signal line (e.g. a surge protective device) or the bypass ex works has been removed and no trigger device has been installed. |
Display: | On the inverter website in the "System" → "Event Log" menu or in the user menu under "Notifications" or in Fronius Solar.web. |
Remedy: | If the SPD surge protective device is triggered, the inverter must be repaired by an authorised specialist. |
OR: | Install the bypass ex works or a trigger device. |
OR: | Set the WSD (wired shutdown) switch to position 1 (WSD primary device). |
WARNING!Danger due to work that has been carried out incorrectly. This can result in serious injury and damage to property. Installing and connecting a surge protective device (SPD) must only be carried out by service personnel trained by Fronius and only within the scope of the respective technical regulations. Follow the safety rules. |
DC input data | |
MPP voltage range | 174 - 800 V |
Max. connected load (PPV max) |
Max. processable PV power |
Max. input voltage | 1000 V |
Feed-in start-up input voltage in grid operation 5) | 80 V |
Max. input current |
Max. short circuit current of solar modules (ISC PV) |
Max. short circuit current |
Max. inverter backfeed current to the array 3) | 37.5 A |
Number of inputs - PV 1 | 2 |
Number of inputs - PV 2 | 1 |
Max. capacity of the PV generator against earth | 1200 nF |
DC input data battery 8) | |
Max. voltage | 531 V / 700 V * |
Min. voltage | 160 V |
Max. current | 22 A |
Max. output | 6000 W |
DC inputs | 1 |
AC input/output data | |
Rated power (Pnom) | 6000 W |
Max. output power | 6000 W |
Rated apparent power | 6000 W |
Nominal grid voltage | 3 ~ NPE 220 V / 380 V |
3 ~ NPE 230 V / 400 V | |
Min. grid voltage | 154 V 1) |
Max. grid voltage | 280 V 1) |
Max. output current | 16.4 A |
Nominal output current (at 230 V) | 8.7 A |
Current (inrush) 6) | 9.9 A / 4 ms |
Nominal frequency | 50 / 60 Hz 1) |
Nominal frequency for Full Backup | 53 / 63 Hz 1) |
Total harmonic distortion | < 3.5% |
Power factor cos phi 2) | 0 - 1 (adjustable) |
0.7 - 1 (recommended) | |
Max. permitted mains impedance Zmax on PCC 4) | None |
Max. output fault current per period | 80.7 A / 10 ms |
AC output data PV Point | |
Max. output power | 4133 W (for 5 s) |
Rated power | 3000 W |
Nominal output current | 13 A |
Nominal grid voltage | 1 ~ NPE 220 V / 230 V / 240 V |
Nominal frequency | 53 / 63 Hz 1) |
Switchover time | < 90 s |
Power factor cos phi 2) | 0 - 1 |
AC output data Full Backup 8) | |
Max. output power | 12400 W (for 5 s) |
Max. output power (per phase) | 4133 W (for 5 s) |
Rated power | 6000 W |
Rated power (per phase) 7) | 3680 W |
Nominal output current (per phase) | 16 A |
General data | |
Maximum efficiency | 98.2% |
European efficiency (Umpp nom) | 97.7% |
European efficiency (Umpp max) | 97.3% |
European efficiency (Umpp min) | 96.5% |
Self-consumption at night | ≤ 10 W |
Cooling | Controlled forced-air ventilation |
Protection class | IP 66 |
Dimensions H x W x D | 595 × 529 × 180 mm |
Weight | 24 kg |
Permitted ambient temperature | -25 °C - +60 °C |
Permissible humidity | 0 - 100% (incl. condensation) |
EMC emission class | B |
DC/AC overvoltage category | 2/3 |
Pollution degree | 2 |
Sound pressure | 47 dB(A) |
Safety class (according to IEC62103) | 1 |
Protection devices | |
DC isolation measurement | Warning / shutdown at RISO < 100 kOHM |
Overload performance | Operating point shift, power limiter |
DC disconnector | Integrated |
RCMU | Integrated |
Data communication | |
WLAN SMA-RP connection | 802.11b/g/n (WPA, WPA2) |
Ethernet (LAN) | RJ 45, 10/100 MBit |
USB (type A socket) | max. 1 A at 5 V (IO connection not connected) |
Wired shutdown (WSD) | max. 28 devices/WSD chain |
max. distance between two devices = 100 m | |
Modbus RTU SunSpec (2x) | RS485 2-wire |
Voltage level of digital inputs | low: min. 0 V - max. 1.8 V |
high: min. 4.5 V - max. 28.8 V | |
Input currents of digital inputs | depending on the input voltage; |
Total power for digital output (for internal supply) | 6 W at 12 V (USB not connected) |
Power per digital output | 1 A at >12.5 V - 24 V |
Datalogger/web server | Integrated |
DC input data | |
DC inputs | 1 |
General data | |
Weight | 24 kg |
RCMU | Integrated |
DC input data | |
MPP voltage range | 224 - 800 V |
Max. capacity of the PV generator against earth | 1600 nF |
Max. output | 8000 W |
DC inputs | 1 |
Rated power (Pnom) | 8000 W |
Max. output power | 8000 W |
Rated apparent power | 8000 W |
Nominal output current (at 230 V) | 11.6 A |
Rated power | 8000 W |
General data | |
European efficiency (Umpp nom) | 97.8% |
European efficiency (Umpp max) | 97.5% |
European efficiency (Umpp min) | 96.9% |
Weight | 24 kg |
RCMU | Integrated |
DC input data | |
MPP voltage range | 278 - 800 V |
Max. capacity of the PV generator against earth | 2000 nF |
Max. output | 10000 W |
DC inputs | 1 |
Rated power (Pnom) | 10000 W |
Max. output power | 10000 W |
Rated apparent power | 10000 W |
Nominal output current (at 230 V) | 14.5 A |
Rated power | 10000 W |
General data | |
European efficiency (Umpp nom) | 97.9% |
European efficiency (Umpp max) | 97.7% |
European efficiency (Umpp min) | 97.1% |
Weight | 24 kg |
RCMU | Integrated |
General data | |
Continuous operating current (Icpv) | < 0.1 mA |
Rated discharge current (In) | 20 kA |
Lightning surge current (limp) | 6.25 kA |
Protection level (Up) | 4 kV |
Short-circuit strength PV (Iscpv) | 15 kA |
Disconnector | |
Thermal disconnector | Integrated |
External fuse | None |
Mechanical properties | |
Disconnection indicator | Mechanical indicator (red) |
Remote communication of the connection interruption | Output on the changeover contact |
Housing material | Thermoplastic UL-94-V0 |
Test standards | IEC 61643-31 / DIN EN 50539-11 |
1) | The values stated are defaults; the inverter is configured specifically to suit the requirements of the relevant country. |
2) | Depending on the country setup or device-specific settings (ind. = inductive; cap. = capacitive). |
3) | Maximum current from a defective PV module to all other PV modules. From the inverter itself to the PV side of the inverter it is 0 A. |
4) | Guaranteed by the electrical configuration of the inverter. |
5) | For backup power mode (PV Point) without battery, a minimum voltage of 150 V is required. |
6) | Current peak when switching on the inverter. |
7) | The sum of the nominal output power per phase must not exceed the nominal output power of the inverter. |
General data | ||||
Product name | Benedict LS32 E 7905 | |||
Rated insulation voltage | 1000 VDC | |||
Rated impulse withstand voltage | 8 kV | |||
Suitability for isolation | Yes, DC only | |||
Utilization category and/or PV utilization category | according to IEC/EN 60947-3 Category of utilization DC-PV2 | |||
Rated short-time withstand current (Icw) | Rated short-time withstand current (Icw): 1000 A | |||
Rated short-circuit making capacity (Icm) | Rated short-circuit making capacity (Icm): 1000 A | |||
Rated operational current and rated breaking capacity | ||||
Rated operational voltage (Ue) | Rated operational current (Ie) | I(make) / I(break) | rated operational current (Ie) | I(make) / I(break) |
≤ 500 VDC | 14 A | 56 A | 36 A | 144 A |
600 VDC | 8 A | 32 A | 30 A | 120 A |
700 VDC | 3 A | 12 A | 26 A | 88 A |
800 VDC | 3 A | 12 A | 17 A | 68 A |
900 VDC | 2 A | 8 A | 12 A | 48 A |
1000 VDC | 2 A | 8 A | 6 A | 24 A |
Number of poles | 1 | 1 | 2 | 2 |