Indicates immediate danger.
The Operating Instructions must always be at hand wherever the device is being used. In addition to the Operating Instructions, attention must also be paid to any generally applicable and local regulations regarding accident prevention and environmental protection.
All safety and danger notices on the device:The terminals can reach high temperatures.
Only operate the device when all protection devices are fully functional. If the protection devices are not fully functional, there is a danger of:Any safety devices that are not fully functional must be repaired by an authorised specialist before the device is switched on.
For the location of the safety and danger notices on the device, refer to the section headed "General remarks" in the Operating Instructions for the device.
Any equipment malfunctions which might impair safety must be remedied before the device is turned on.
The servicing information contained in these operating instructions is intended only for the use of qualified service engineers. An electric shock can be fatal. Do not carry out any actions other than those described in the documentation. This also applies to qualified personnel.
All cables and leads must be secured, undamaged, insulated and adequately dimensioned. Loose connections, scorched, damaged or inadequately dimensioned cables and leads must be immediately repaired by authorised personnel.
Maintenance and repair work must only be carried out by an authorised specialist.
It is impossible to guarantee that bought-in parts are designed and manufactured to meet the demands made on them, or that they satisfy safety requirements. Use only original spare parts (also applies to standard parts).
Components that are not in perfect condition must be changed immediately.
The text and illustrations are all technically correct at the time of printing. We reserve the right to make changes. The contents of the operating instructions shall not provide the basis for any claims whatsoever on the part of the purchaser. If you have any suggestions for improvement, or can point out any mistakes that you have found in the instructions, we will be most grateful for your comments.
The user is responsible for the safekeeping of any changes made to the factory settings. The manufacturer accepts no liability for any deleted personal settings.
The Fronius Smart Meter TS is a bidirectional electricity meter which optimises self-consumption and records the household's load curve. In conjunction with the Fronius inverter, Fronius Datamanager and Fronius data interface, the Fronius Smart Meter TS provides a clear overview of a user's own power consumption.
The meter measures the power flow to the loads or to the grid and forwards the information via the Modbus RTU/RS485 communication to the Fronius inverter and the Fronius Datamanager.
Observe and follow safety instructions!
Failure to observe the safety instructions will result in damage to personnel and equipment.
Switch off the power supply before establishing a mains connection.
Observe the safety instructions.
Technical data, markings and safety symbols are located on the Fronius Smart Meter TS. These must NOT be removed or painted over. They warn against incorrect operation which can lead to serious injury and damage.
Markings: | |
The devices comply with all the requisite and relevant standards and guidelines that form part of the relevant EU Directive, and are therefore permitted to display the CE mark. | |
Insulated (protection class II) | |
Regulatory Compliance Mark (RCM) | |
To comply with European Directive 2012/19/EU on Waste Electrical and Electronic Equipment and its implementation as national law, electrical equipment that has reached the end of its life must be collected separately and returned to an approved recycling facility. Any device that you no longer require must be returned to your distributor or disposed of at an approved collection and recycling facility in your area. Ignoring this European Directive may have potentially adverse effects on the environment and your health! | |
RoHS (Restriction of Hazardous Substances) |
Safety symbols: | |
Danger of serious injury and property damage due to incorrect operation. | |
Dangerous electrical voltage. |
The Fronius Smart Meter TS is a fixed piece of equipment for public grids of TN/TT systems and records self-consumption and/or individual loads in the system. The Fronius Smart Meter TS is required for systems with a battery storage system and/or a Fronius Ohmpilot installed for communication between the individual components. The installation is carried out on an indoor DIN rail with corresponding back-up fuses, which are adapted to the cable cross-sections of the copper conductors and to the maximum current of the meter. The Fronius Smart Meter TS must only be operated in accordance with the specifications in the enclosed documentation and in accordance with local laws, regulations, provisions, standards and within the limits of technical possibilities. Any use of the product other than as described in the intended use shall be deemed to be not in accordance with the intended purpose. The available documentation forms part of the product and must be read, observed and kept in good condition. It must also be accessible at all times at the place of installation. The available documents do not replace regional, state, provincial or national laws, or regulations or standards that apply to the installation, electrical safety and use of the product. Fronius International GmbH assumes no responsibility for compliance with or non-compliance with these laws or regulations in connection with the installation of the product.
Interventions on the Fronius Smart Meter TS, e.g. modifications and alterations, are not permitted. Unauthorised interventions will void the warranty and warranty claims and, as a rule, void the user's authority to operate the equipment. The manufacturer shall not be liable for any damage resulting from such use.
Reasonably foreseeable misuse:
The Fronius Smart Meter TS is not suitable for the supply of life-sustaining medical devices or for the billing of subtenants.
(1) | 2x seal wire |
(2) | 2x connection cover |
(3) | Fronius Smart Meter TS 5kA-3 |
(4) | Quick Start guide |
The Fronius Smart Meter TS can be installed in the following positions in the system:
Positioning at the feed-in point:
Positioning at consumption point:
For use as a secondary meter to measure individual loads and producers, see chapter Multi-meter system - Fronius SnapINverter on page (→).
The Fronius Smart Meter TS has accuracy class 1 when measuring active energy (EN IEC 62053-21) in the voltage ranges 400 - 480 VLL or 230 -277 VLN. Within the voltage ranges 173 - 400 VLL or 100 - 230 VLN the accuracy class is 2 (active energy according to EN IEC 62053-21, reactive energy according to EN IEC 62053-23). For further details see Technical data on page (→).
The Fronius Smart Meter TS can be mounted on a 35 mm DIN rail. The housing comprises 3 modules according to DIN 43880.
The Fronius Smart Meter TS is a hard-wired device and requires a disconnecting device (circuit breaker, switch or disconnector) and overcurrent‑protection (automatic‑circuit breaker).
The Fronius Smart Meter TS consumes 10 - 30 mA, the nominal capacity of the disconnecting devices and the overcurrent‑protection is determined by the wire thickness, the mains voltage and the required breaking capacity.
IMPORTANT!
An auxiliary power supply is required to operate the Fronius Smart Meter TS. The fuse (F) must comply with the national standards and guidelines as well as the dimensions of the conductors.
IMPORTANT!
Always switch off the power supply before connecting the mains voltage inputs to the Fronius Smart Meter TS.
The measuring inputs of the current transformers must be earthed on one side as shown in the circuit diagram.
Connect each voltage cable to the terminal strip as shown in the graphics below.
General
Do not use current transformers with a voltage output.
Current transformers are directional. If they are mounted backwards or with swapped wires, the measured power will be negative.
Primary current
Maximum current per phase. A current converter with a primary current greater than the maximum expected current per phase should be selected. The closer the expected current is to this value, the more precise the measurement will be.
Secondary current
The current transformer must supply alternating current at a nominal current of 1 or 5 A. The nominal values for the current transformer are listed in the current transformer data sheet.
Power
The Fronius Smart Meter TS needs 0.5 VA to carry out its measurements. Losses also occur on the outgoing and return leads. The power of the current converter must be greater than the sum total of the power of the Fronius Smart Meter TS and the leads. The higher the power, the better.
Line resistances at different cross-sections (copper wires) | ||||||
Secondary current | Cross-section | Line resistances at different lead lengths (outgoing and return lead) | ||||
0.5 m | 1.0 m | 2.5 m | 5 m | 10 m | ||
5 | 1.5 | 0.3 VA | 0.6 VA | 1.5 VA | 2.9 VA | 5.8 VA |
5 | 2.5 | 0.2 VA | 0.4 VA | 0.9 VA | 1.8 VA | 3.6 VA |
5 | 4 | - | - | 0.6 VA | 1.1 VA | 2.2 VA |
Example
The length of the outgoing and return lead (0.5 m each) between the Fronius Smart Meter TS and the current transformer is a total of 1 m and has a copper cable cross-section of 1.5 mm²; the line resistance is therefore 0.6 VA according to the table above. The self-consumption of the Fronius Smart Meter TS is 0.5 VA.
Line resistance 0.6 VA + self-consumption 0.5 VA = 1.1 VA
→ A current transformer with a rating of 1.5 VA, 5 VA or higher is suitable here.
Accuracy class
Use Class 1 or better (Class 0.5 / 0.2, etc.). Class 1 is equivalent to a deviation of ± 1% of the secondary current at maximum power.
Mounting
Rigid or hinged
"Rigid" is usually cheaper with better power and accuracy values. Hinged current transformers can be opened for attachment to the conductor. To prevent it being opened inadvertently, a plastic cable tie can be secured to the current transformer. Hinged current transformers can be installed in a system without interrupting the voltage.
Only voltage transformers with a voltage range from 220 to 480 V (phase - phase) and from 100 to 277 V (phase - neutral conductor) may be used. The voltage transformers must be connected to terminals 1, 2, 3 and N at the point of direct voltage measurement.
Connect the data communication connections of the Fronius Smart Meter TS to the Modbus interface of the Fronius inverter using a network cable (type CAT5 or higher).
Several Smart Meters can be installed in the system, see chapter Multi-meter system - Fronius SnapINverter on page (→).
To avoid interference, the terminating resistor must be used (see chapter Connecting the terminating resistor on page (→)).
Inverter in the system | |
Meter - Fronius Smart Meter TS | |
Modbus RTU slave | |
Terminating resistor |
The terminating resistor is integrated in the Fronius Smart Meter TS and is manufactured with a bridge between the M and T connections (T = termination).
Due to interference, it is recommended that terminating resistors are used as illustrated below to ensure proper functioning.
* The terminating resistor is integrated in the Fronius Smart Meter TS and is manufactured with a bridge between the M and T connections (T = termination).
Insert the connection covers into the guides and press firmly.
IMPORTANT!
When fitting the connection covers, ensure that the cables are not kinked, pinched, crushed or otherwise damaged.
Grid | |
Utility meter | |
Primary meter | |
Secondary meter | |
Producer meter | |
Loads in the system | |
Additional loads in the system | |
Additional producers in the system | |
A maximum of 4 Modbus participants can be connected to the Modbus terminal.
IMPORTANT!
Only one primary meter, one battery and one Ohmpilot can be connected per inverter. Due to the high data transfer of the battery, the battery occupies 2 participants.
Example:
Input | Battery | Fronius | Quantity | Quantity |
Modbus | 1 | 0 | ||
1 | 1 | |||
1 | 2 | |||
1 | 3 |
If several Fronius Smart Meter TS are installed, a separate address must be set for each (see Setting the address on the Fronius Smart Meter TS on page (→)). The primary meter is always assigned address 1. All the other meters are numbered consecutively with the address range from 2 to 14. Different Fronius Smart Meter power categories can be used in combination.
IMPORTANT!
Max. Use 3 secondary meters in the system. To avoid interference, it is recommended to install the terminating resistors according to chapter Connecting the terminating resistor on page (→).
The inputs M0 and M1 can be selected for this purpose. A maximum of 4 Modbus participants can be connected to the Modbus terminal on inputs M0 and M1.
IMPORTANT!
Example 1:
Modbus 0 (M0) | 0 | 4 | ||
0 | 2 | |||
0 | 1 | |||
Modbus 1 (M1) | 1 | 3 |
Example 2:
Modbus 0 (M0) | 1 | 3 | ||
Modbus 1 (M1) | 0 | 4 | ||
0 | 2 | |||
0 | 1 |
IMPORTANT!
Max. Use 7 secondary meters in the system. To avoid interference, it is recommended to install the terminating resistors according to chapter Connecting the terminating resistor on page (→).
Image | Screen | Description |
00 |
01 |
02 |
03 |
04 |
05 |
06 |
07 |
08 |
09 |
10 |
11 |
12 |
13 |
14 |
15 |
16 |
18 |
19 |
20 |
* | Displayed when easy connection mode is activated (measurement = A). This value indicates the total energy without considering the direction. |
** | Factory setting - displayed when drawn and delivered energy are measured separately (measurement = b). |
Screen | Code | Description | Values |
PASS*** | P1 | Enter the current password | 2633* |
nPASS | P2 | Password change ** | Four digits (0000-9999) |
SYStEM | P3 | Type of system | 3Pn*: three-phase system, 4-core |
Ct rAtIo | P4 | Current transformer ratio | from 1* to 1000 |
Ut rAtIo | P5 | Voltage transformer ratio | from 1* to 1000 |
MEASurE | P6 | Measurement mode ** | A: easy connection, measures all energy without taking the direction into account. |
InStALL | P7 | Connection check | On: activated |
P int | P8 | Average power calculation interval (minutes) | 1* - 30 |
MOdE | P9 | Display mode ** | Full*: full display |
tArIFF | P10 | Tariff management ** | On: activated |
HoME | P11 | Screen showing measured variables displayed at startup and after 120 seconds of inactivity ** | For full display (Mode = Full): 0* - 19 |
AddrESS*** | P14 | Modbus address | 1* - 247 |
bAUd | P15 | Baud rate (kBit/s) ** | 9.6* / 19.2 / 38.4 / 57.6 / 115.2 |
PArITY | P16 | Parity ** | Even/No* |
STOP bit | P16-2 | Only if parity = No. Stop bit. ** | 1* / 2 |
rESET | P17 | Activation of the reset function for energy tariffs, maximum requested power and part values of active and reactive energy (the latter are only transmitted via the serial interface) ** | No*: reset function deactivated. |
End | P18 | Returns to the measured variables start screen | None |
* | Factory settings |
** | The settings can be protected by changing the default password (password cannot be reset). |
*** | Settings that need to be configured. |
Only the transformation ratio of the current and voltage transformers must be set. All other parameters are preset at the factory.
Symbol | Name | Event | Function |
Up | 1 x | Scroll one screen forward, increase the value by 1 | |
Down | 1 x | Scroll one screen back, decrease the value by 1 | |
Enter | 2 seconds | Call up settings, confirm value |
IMPORTANT!
The password cannot be reset.
Ratio of current transformers1) (0001 - 10002)).
Ratio of voltage transformers1), 3) (001.0 - 10002)).
1) Important! Changing the transformation ratios will reset the counters in the Fronius Smart Meter TS to 0.
2) Transformation ratio in the current transformer x Transformation ratio of the voltage transformers = max. 1000
3)Changeover only when using voltage transformers (direct voltage measurement VT = 1)
IMPORTANT! Settings under the "Meter" menu item are only to be made by trained and qualified personnel!
The service password must be entered in order to access the "Meter" menu item.
Three-phase or single-phase Fronius Smart Meter TS can be used. In both cases, the selection is made under the "Fronius Smart Meter" item. The Fronius Datamanager automatically identifies the meter type.
A primary meter and several secondary meters can be selected. The primary meter needs to be configured first before a secondary meter can be selected.
Access point:
The Fronius Datamanager start page is displayed.
LAN:
The Fronius Smart Meter TS is configured as a primary meter.
The "Current general view" menu area displays the power of the PV modules, self-consumption, the energy fed into the grid and the battery charge (if available).
The Fronius Smart Meter TS is configured as a secondary meter.
IMPORTANT! Settings under the "Device configuration" menu item are only to be made by trained and qualified personnel!
The service password must be entered in order to access the "Device configuration" menu item.
Three-phase or single-phase Fronius Smart Meter TS can be used. In both cases, the selection is made under the "Components" menu area. The meter type is determined automatically.
WLAN:
The network wizard and the product setup can be carried out independently of each other. A network connection is required for the Solar.web installation wizard.
Ethernet:
Modbus transmission speed: 9600 baud
Parity bit:none
Measuring input | |
Nominal voltage (3-phase) | 400 - 480 V |
Nominal voltage (1-phase) | 230 - 277 V |
Voltage transformer ratio (kVT) | 1 - 1000 |
Self-consumption - voltage path | 10 VA |
Nominal frequency | 50 - 60 Hz |
Nominal current, lb | 1 A + 5 A |
Maximum current, Imax | 6 A |
Starting current | 10 mA |
Current transformer ratio (kCT) | 1 - 1000 |
Short-time overload | 5 lmax / 0.5 s |
Self-consumption - current path (max. current) | 0.3 W per phase |
Maximum value kVT x kCT | 1000 (CT/5A) |
Current distortion factor | in acc. with EN IEC 62053-21 |
Power factor | active cosφ 0.5 ind - 0.8 cap, |
Energy | |
Max. display | As per table |
Resolution | As per table |
LED indicator | 1 pulse / 0.1 Wh |
Active energy accuracy | Class 1 |
Reactive energy accuracy | Class 2 |
Response time after switch-on | < 5 s |
kCT x kVT | Maximum display |
| Resolution |
1 - 9.9 | 9 9 9 9 9 9 . 9 9 | kWh / kvarh | 10 Wh / varh |
10 - 99.9 | 9 9 9 9 9 9 9 . 9 | kWh / kvarh | 100 Wh / varh |
100 - 999.9 | 9 9 9 9 9 9 9 9 | kWh / kvarh | 1 kWh / varh |
≥ 1000 | 9 9 9 9 9 9 . 9 9 | MWh / kvarh | 10 kWh / varh |
Average power | |
Measured variable | Effective power |
Calculation | Average value over set period of time |
Integration time | 5 / 8 / 10 / 15 / 20 / 30 / 60 minutes |
Output | |
RS485 communication | |
Standard | RS485 - 3 conductors |
Transmission | Serial, asynchronous |
Protocol | Modbus RTU |
Addresses | 1 - 255 |
Number of bits | 8 |
Stop bit | 1 |
Parity bit | None - even - odd |
Baud rate | 9600, 19200, 38400 bit/s |
Response time | ≤ 200 ms |
Insulation (EN IEC 62052-11, EN IEC 62053-21) | |
Installation category | III |
Pollution degree | 2 |
Insulation voltage | 4 kV RMS |
Impulse withstand voltage | 4 kV 1.2/60 µs |
Test voltage | 2.75 kV RMS. 50 Hz/1 min |
Test voltage | 4 kV RMS. 50 Hz/1 min |
Electromagnetic compatibility | |
Test in acc. with EN IEC 62052-11 |
Operating conditions | |
Reference temperature | 25 °C (± 5 °C) |
Operating range | -25 to +65 °C |
Temperature limit for storage and transport | -30 to +80 °C |
Max. power loss (for thermal dimensioning of the switch cabinet) | ≤ 2.8 W |
Housing | |
Housing | 3 modules according to DIN 43880 |
Sealable housing/terminal cover |
Connection | Screw connection |
Mounting | Can be snapped onto 35 mm DIN rail |
Housing material | Noryl, self-extinguishing |
Degree of protection (EN 60529) | IP54 housing, IP20 connections |
Weight | 240 grams |
Terminals | |
Measuring input | |
Wire | min. 1 mm² / max. 4 mm² |
Recommended torque | max. 0.6 Nm |
Data output and auxiliary power supply | |
Wire | min 0.05 mm² / max. 2.5 mm² |
Recommended torque | max. 0.4 Nm |
Parity bit:none
Measuring input | |
Energy | |
| Resolution |
Average power | |
Output | |
Stop bit | 1 |
Housing | |
Terminals | |
Measuring input | |
Detailed, country-specific warranty terms are available on the internet:
www.fronius.com/solar/warranty
To obtain the full warranty period for your newly installed Fronius inverter or storage system, please register at: www.solarweb.com.