en
      Operating instructionsFronius Smart Meter TS 65A-3
    • General information
      • Safety information
        • Safety instructions and important information
        • Environmental conditions
      • General
        • How information is presented in the document
        • Target group
        • Data security
        • Privacy policy
        • Copyright
      • Fronius Smart Meter TS 65A-3
        • Device description
        • Information on the device
        • Intended use
        • Scope of supply
        • Positioning
    • Installation
      • Installation
        • Checklist for installation
        • Installation
        • Protective circuit
        • Cabling
        • Fitting the protective cover for the terminals
        • Connecting the data communication cable to the inverter
        • Terminating resistors - explanation of symbols
        • Connecting the terminating resistor
        • Mounting the connection cover
        • Multi meter system - Explanation of symbols
        • Modbus participant - Fronius SnapINverter
        • Multi-meter system - Fronius SnapINverter
        • Modbus participant - Fronius GEN24
        • Multi meter system - Fronius GEN24 inverter
        • Menu - Measured variables
        • Configuration menu - structure and parameters
        • Setting the address on the Fronius Smart Meter TS
        • Error messages
    • Commissioning
      • Fronius SnapINverter
        • General
        • Connect to Fronius Datamanager 2.0
        • Configuring the Fronius Smart Meter TS as the primary meter
        • Configuring the Fronius Smart Meter TS as a secondary meter
      • Fronius GEN24 inverter
        • General
        • Installation with the browser
    • Technical data
      • Technical data
      • Warranty
    • 023-17062026
    download
    Cabling
    Start-up
    Technical data
    ContactImprintTerms of usePrivacy statementCookie policy
    General information
    link_horizontalLink copied
    Safety information
    Warnings are intended to warn people of possible injuries and to avoid personal injury and damage to the product. They relate to individual actions with and on the product.
    DANGER!
    Indicates an immediately dangerous situation.
    Serious injury or death will result if the danger is not avoided.
    Action step to escape the situation.
    WARNING!
    Serious injury or death may result if the danger is not avoided.
    CAUTION!
    Minor or moderate injury may result if the danger is not avoided.
    NOTE!
    Indicates a situation that may result in property damage.
    If the situation is not avoided, impaired work results, material damage to the product or other property are the possible consequences.
    Action step to avoid the situation.
    Safety instructions are designed to ensure safe product use. They are preventive and help to inform users about the fundamental risks involved when dealing with the product. They do not refer specifically to individual actions with and on the product.
    1. General information
    Safety information
    DANGER!
    WARNING!
    CAUTION!
    NOTE!
    2. Safety information
    DANGER!
    WARNING!
    CAUTION!
    NOTE!
    WARNING!
    Incorrect operation or misuse
    IMPORTANT!
    In addition to the operating instructions, observe the following general and local rules:
    • Accident prevention
    • Fire protection
    • Environmental protection
    IMPORTANT!
    IMPORTANT!
    All safety and danger notices on the device:
    • Must be kept in a legible state
    • Must not be damaged/marked
    • Must not be removed
    • Must not be covered, have anything stuck on them, or painted over
    WARNING!
    Tampered-with and non-functioning protection devices
    WARNING!
    NOTE!
    The device may be damaged
    Operation or storage of the machine outside the stipulated area will be deemed as not in accordance with the intended purpose.
    For exact information on permitted environmental conditions, please refer to the technical data.
    General
    Application notes
    Software
    Example: Click Save.
    Instructions for action
    1Action steps are displayed with consecutive numbering.
    ✓This symbol indicates the result of the action step or the entire instruction.
    2. General
    Application notes
    Software
    2. General
    Target group
    This document provides detailed information and instructions to ensure that people can use the machine safely and efficiently.
    The information is intended for the following groups of people:
    • Technical specialists: People with appropriate qualifications and fundamental knowledge of electronics and mechanics. The activities of a technical specialist include installation, operation, maintenance, and service work.
    • User: People that use the machine in daily operation and want to understand its basic functions.
    Regardless of any qualifications, only perform the activities listed in this document.
    The definition of professional qualifications and their applicability are subject to national law.
    2. General
    Data security
    • Backing up any changes made to the factory settings
    • Saving and storing personal settings
    NOTE!
    2. General
    Privacy policy
    When you connect your device (and any associated devices) to the internet, the following device and operating data (device ID/identifier, device IP address, device time, configuration settings, hardware and software information, device status log files, serial number) is sent automatically to
    Fronius International GmbH, Froniusstraße 1, 4643 Pettenbach, Austria, telephone +43(0) 7242241-0, email: contact@fronius.com (controller)
    and stored.
    The processing of this device and operating data is carried out for the purpose of ensuring the operational safety of the device (time synchronization, provision of updates). This processing is therefore necessary for the functionality of the device and thus for the fulfillment of the contract (Art. 6 (1) (b) GDPR).
    If you do not wish to have such data processed, you must manually disable the device's internet connection.
    In addition, the device and operating data is also processed for the purpose of providing services as part of a supplementary digital service for your device (such as solar.web or similar) as soon as you have registered your device with such a digital service (identification). This data is processed to provide the requested digital services and is therefore necessary for the fulfillment of the contract (Art. 6 (1) (b) GDPR).
    Furthermore, this data processing is also carried out for maintenance and support purposes and for handling customer concerns as well as in warranty and guarantee cases (only in individual cases and given connection between device and internet). In this context, the device and operating data may also be passed on to our cooperation partners (third-party providers and suppliers). The processing of this data is necessary for maintenance and support purposes or for processing warranty and guarantee cases and thus for the fulfillment of the contract (Art. 6 (1) (b) GDPR).
    Device and operating data are also processed for analysis and diagnostic purposes in order to gain insights into the functionality of the devices and improve them accordingly. This data processing is based on our legitimate interest (Art. 6 (1) (f) GDPR).
    We store this data for as long as it is necessary to fulfill the existing contract with you. Any storage beyond this is carried out for legal reasons or if we have a legitimate interest in doing so. For more information on data processing for the solar.web-digital service, as well as our general privacy policy and your rights as a data subject, please visit https://www.fronius.com.
    2. General
    Copyright
    Device description
    The Fronius Smart Meter is a bidirectional electricity meter for optimizing self-consumption and recording a household's load characteristic curve. Together with a Fronius inverter or Fronius Datamanager 2.0 and a Fronius data interface, the Fronius Smart Meter allows you to view your own power consumption. The meter measures the energy flow to the loads or to the public grid and forwards the information to the Fronius inverter or Fronius Datamanager 2.0 via the Modbus RTU/RS485 interface.
    CAUTION!
    Danger due to non-compliance with the safety instructions
    Risk of injury and damage to the device as a result.
    Follow all safety instructions.
    Switch off the power supply before establishing the mains connection.
    2. Fronius Smart Meter TS 65A-3
    Device description
    CAUTION!
    Technical data, labels, and safety symbols are located on the Fronius Smart Meter TS. This information must be kept in a legible condition and must not be removed, covered, painted over, or concealed by stickers or labels. It warns against incorrect operation, which may result in serious injury and property damage.
    Markings:
    The equipment complies with all the requisite and relevant standards and directives that form part of the relevant EU directive, and therefore is permitted to display the CE mark.
    Insulated (protective class II)
    RCM (Regulatory Compliance Mark)
    All relevant regulatory requirements in Australia and New Zealand are complied with in terms of safety and electromagnetic compatibility, as well as special requirements for radio equipment.
    To comply with European Directive 2012/19/EU on Waste Electrical and Electronic Equipment and its implementation as national law, electrical equipment that has reached the end of its life must be collected separately and returned to an approved recycling facility. Any device that you no longer require must be returned to your distributor, or you must locate the approved collection and recycling facilities in your area. Ignoring this European Directive may have potentially adverse effects on the environment and your health.
    RoHS (Restriction of Hazardous Substances)
    The restricted use of certain hazardous substances in electrical and electronic equipment has been complied with in accordance with the EU Directive 2011/65/EU.
    Safety symbols:
    Risk of serious injury and property damage due to incorrect operation.
    Dangerous electrical voltage.
    Intended use
    The Fronius Smart Meter TS is a fixed piece of equipment for public grids of TN/TT systems and records the self-consumption or individual loads in the system. The Fronius Smart Meter TS is required for systems with an installed battery storage system and/or a Fronius Ohmpilot for communication between the individual components. The Smart Meter must be installed indoors on a DIN rail with corresponding back-up fuses, which are selected to suit the cable cross-sections of the copper conductors and the maximum current of the meter. The Fronius Smart Meter TS must only be operated in accordance with the specifications in the enclosed documentation and in accordance with local laws, regulations, provisions, standards, and within the limits of technical possibilities. Any use of the product other than as described under intended use shall be deemed to be not in accordance with intended use. The available documentation forms part of the product and must be read, observed, and kept in good condition. It must also be accessible at all times at the place of installation. The available documents do not replace regional, state, provincial, federal, or national laws, or regulations or standards that apply to the installation, electrical safety, and use of the product. Fronius International GmbH assumes no responsibility for compliance with or non-compliance with these laws or regulations in connection with the installation of the product.
    Interventions in the Fronius Smart Meter TS, e.g., modifications and alterations, are not permitted. Unauthorized interventions will void the warranty and warranty claims and, as a rule, void the user's authority to operate the equipment.
    Reasonably foreseeable misuse:
    The Fronius Smart Meter TS is not suitable for the power supply of life-sustaining medical devices or for billing costs to subtenants.
    Scope of supply
    (1)
    2x protective cover
    (2)
    (3)
    2x seal wire
    (4)
    2x connection cover
    (5)
    Quick Start Guide
    Positioning
    The Smart Meter can be installed in the following positions in the system:
    Positioning at the feed-in point
    Installation of the Fronius Smart Meter IP at the feed-in point
    Positioning at the consumption point
    Installation of the Fronius Smart Meter IP at the consumption point
    Installation
    Installation
    For installation information, see the following chapters:
    1Switch off the power supply before establishing a grid connection.
    2Mount the Fronius Smart Meter TS (see "Installation" on page (→)).
    3Connect automatic circuit breakers or automatic circuit breakers and disconnectors (see"Protective circuit" on page (→)).
    4Connect the mains cable to the Fronius Smart Meter TS (see "Cabling" on page (→)).
    5Fit the protective cover for the terminals (see "Fitting the protective cover for the terminals" on page (→)).
    6Connect the data communication connections of the Fronius Smart Meter TS to the Fronius system monitoring using a suitable cable (see "Connecting the data communication cable to the inverter" on page (→)).
    7If necessary, set terminating resistors (see "Connecting the terminating resistor" on page (→)).
    8Tug on each wire and plug to make sure that they are securely connected to the terminal blocks.
    9Switch on the power supply to the Fronius Smart Meter TS.
    10Check the firmware version of the Fronius system monitoring. To ensure compatibility between the inverter and the Fronius Smart Meter TS, the software must always be kept up to date. The update can be started via the inverter web page or using Solar.web.
    11If several Fronius Smart Meter TS are installed in the system, set the address (see "Setting the address" under "Setting the address on the Fronius Smart Meter TS" on page (→)).
    12Configure and commission the meter (see Commissioning on page (→)).
    1. Installation
    Installation
    1. Installation
    2. Installation
    1. Installation
    2. Installation
    Installation
    The Fronius Smart Meter TS can be mounted on a 35 mm DIN rail. The housing comprises 3 modules according to DIN 43880.
    1. Installation
    2. Installation
    Protective circuit
    The Fronius Smart Meter TS is a hard-wired device and requires a disconnecting device (circuit breaker, switch or disconnector) and overcurrent protection (automatic circuit breaker).
    The Fronius Smart Meter TS consumes 10 - 30 mA, the nominal capacity of the disconnecting devices and the overcurrent protection is determined by the wire thickness, the mains voltage, and the required breaking capacity.
    • Disconnecting devices must be mounted within sight and as close as possible to the Fronius Smart Meter TS; they must also be easy to use.
    • The disconnecting devices must satisfy the requirements of IEC 60947-1 and IEC 60947-3, as well as all national and local regulations for electrical systems.
    • Use overcurrent protection rated for max. 65 A.
    • To monitor more than one mains voltage, use connected automatic circuit breakers.
    • The overcurrent protection must protect the grid terminals marked L1, L2, and L3. In rare cases, the neutral conductor has an overcurrent protection, which must interrupt both neutral and non-grounded cables concurrently.
    1. Installation
    2. Installation
    Cabling
    IMPORTANT!
    Always switch off the power supply before connecting the mains voltage inputs to the Fronius Smart Meter TS.
    Recommended thickness of the strands of mains voltage cables for the terminals of the measuring input and measuring output:
    • Wire: 1 - 16 mm²
    • Recommended torque: max. 2.8 Nm
    Recommended thickness of the strands for the connection terminals of the data communication:
    • Wire: min. 0.05 mm²
    • Recommended torque: max. 0.4 Nm
    Connect each power cable to the terminal board as shown in the diagrams below.
    2 phases, 3 conductors
    3 phases, 3 conductors
    3 phases, 4 conductors
    IMPORTANT!
    For this connection variant, select the value 3Pn in the configuration menu under System > P3. This prevents incorrect measurements.
    WARNING!
    Danger from mains voltage.
    Switch off the power supply before connecting the mains voltage inputs to the Fronius Smart Meter TS.
    1. Installation
    2. Installation
    Insert the protective covers into the guides and press firmly.
    WARNING!
    Danger due to electrical voltage from missing or improperly fitted protective covers.
    An electric shock can be fatal and/or cause serious damage to property.
    Fit the protective covers immediately after installing the live cables.
    Fit the protective covers properly and check that they are secure.
    1. Installation
    2. Installation
    Connect the data communication connections of the Fronius Smart Meter TS to the Modbus interface of the Fronius inverter using a network cable (type CAT5 or higher).
    Several Smart Meters can be installed in the system, see chapter Multi-meter system - Fronius SnapINverter on page (→).
     To avoid interference, the terminating resistor must be used (see chapter Connecting the terminating resistor on page (→)).
    IMPORTANT!
    Further information for successful commissioning.
    Observe the following information on connecting the data communication cable to the inverter.
    • Use network cables of type CAT5 or higher.
    • The maximum cable length between the Fronius inverter and Fronius Smart Meter is 300 meters.
    • Use a mutual twisted cable pair for corresponding data lines (D+/D-, M0+/M0-).
    • On Fronius GEN24 inverters, the M0 and M1 inputs can be selected for this purpose.
    • If the data lines are close to the mains cabling, use wires or cables that are designed for 300 to 600 V (never less than the operating voltage).
    • Use double-insulated or sheathed data lines when they are close to bare conductors.
    • Use shielded twisted pair cables to avoid faults.
    • Two wires can be installed in each terminal; the wires are twisted first, inserted into the terminal, and tightened.
      Note: A loose wire can disable an entire area of the network.
    • The data communication connections of the Fronius Smart Meter TS are electrically isolated from hazardous voltages.
    1. Installation
    2. Installation
    Inverter in the system
    e.g., Fronius Symo
    Meter - Fronius Smart Meter TS
    Terminating resistor R 120 Ohm is set with a wire jumper between M- and T.
    Modbus RTU, third-party device
    e.g., Fronius Ohmpilot, battery, etc.
    R 120 Ohm
    1. Installation
    2. Installation
    The terminating resistor is integrated in the Fronius Smart Meter TS and is manufactured with a bridge between the M and T connections (T = termination).
    1. Installation
    2. Installation
    Due to interference, it is recommended that terminating resistors are used as illustrated below to ensure proper functioning.
    * The terminating resistor is integrated in the Fronius Smart Meter TS and is manufactured with a bridge between the M and T connections (T = termination).
    1. Installation
    2. Installation
    Insert the connection covers into the guides and press firmly.
    IMPORTANT!
    When fitting the connection covers, ensure that the cables are not kinked, pinched, crushed, or otherwise damaged.
    1. Installation
    2. Installation
    Grid
    supplies the loads in the system if insufficient power is being generated by the PV modules or supplied by the battery.
    e.g., Fronius Primo, Fronius Symo, etc.
    Fronius Smart Meter
    measures the metering data relevant for the billing of electricity quantities (grid consumption and grid feed-in). Based on the relevant billing data the electricity retailer will invoice for the energy sourced from the grid and the purchaser of the surplus energy will reimburse the energy fed into the grid.
    Primary meter
    records the load curve of the system and makes the measured data available for energy profiling in Fronius Solar.web. The primary meter controls the dynamic power of feeding in.
    Secondary meter
    records the load curve of individual generators and loads in the consumption branch and makes the measured data available for energy profiling in Fronius Solar.web.
    Loads in the system
    e.g., washing machine, lights, television, etc.
    Additional loads in the system
    e.g., heat pump
    Additional producers in the system
    e.g., wind power plant
    R 120 Ohm
    1. Installation
    2. Installation
    A maximum of 4 Modbus stations can be connected to the Modbus connection terminal.
    IMPORTANT!
    Only one primary meter, one battery and one Ohmpilot can be connected per inverter. Due to the high data transfer of the battery, the battery occupies 2 subscribers.
    Example:
    Input
    Battery
    Fronius
    Ohmpilot
    Number
    of primary meters
    Number
    of secondary meters
    Modbus
    0
    1. Installation
    2. Installation
    If several Fronius Smart Meter TS are installed, a separate address must be set for each (see Setting the address on the Fronius Smart Meter TS on page (→)). The primary meter is always assigned address 1. All the other meters are numbered consecutively with the address range from 2 to 14. Different Fronius Smart Meter power categories can be used in combination.
    IMPORTANT!
    Max. Use 3 secondary meters in the system. To avoid interference, it is recommended to install the terminating resistors according to chapter Connecting the terminating resistor on page (→).
    Location of the primary meter in the consumption branch. *Terminating resistor R 120 Ohm
    Location of the primary meter at the feed-in point. *Terminating resistor R 120 Ohm
    The following must be observed in a multi-meter system:
    • Only assign each Modbus address once.
    • Terminating resistors must be positioned individually for each channel.
    1. Installation
    2. Installation
    The inputs M0 and M1 can be freely selected. A maximum of 4 Modbus participants can be connected to the Modbus terminal on the inputs M0 and M1.
    IMPORTANT!
    Example 1:
    Input
    Battery
    Fronius
    Ohmpilot
    Number
    of primary meters
    Number
    of secondary meters
    Modbus 0
    (M0)
    0
    0
    0
    Modbus 1
    (M1)
    Example 2:
    Input
    Battery
    Fronius
    Ohmpilot
    Number
    of primary meters
    Number
    of secondary meters
    Modbus 0
    (M0)
    Modbus 1
    (M1)
    0
    0
    0
    1. Installation
    2. Installation
    If several Fronius Smart Meter TS are installed, a separate address must be set for each one (see Setting the address on the Fronius Smart Meter TS on page (→)). The primary meter always receives the address 1. All other meters are numbered consecutively in the address range from 2 to 14. Different Fronius Smart Meter power categories can be used together.
    IMPORTANT!
    Use no more than 7 secondary meters in the system. To avoid interference, it is recommended to install the terminating resistors according to the chapter Connecting the terminating resistor on page (→).
    3 secondary meters with connected generators and loads, primary meter in the consumption branch, third-party device Modbus RTU connected to the inverter
    Position of the primary meter in the consumption branch. *Terminating resistor R 120 Ohm
    3 secondary meters with connected generators and loads, primary meter at the feed-in point, third-party device Modbus RTU connected to the inverter.
    Position of the primary meter at the feed-in point. *Terminating resistor R 120 Ohm
    The following must be observed in a multi meter system:
    • Connect the primary meter and the battery to different channels (recommended).
    • Distribute the remaining Modbus participants evenly.
    • Each Modbus address is assigned only once.
    • Place the terminating resistors individually for each channel.
    1. Installation
    2. Installation
    Screen
    Description
    00
    1. Total active energy drawn*
    2. Total efficiency
    01
    1. Total active energy supplied**
    2. Total efficiency
    02
    2. Average conductor voltage in the system
    03
    2. Average phase voltage in the system
    04
    2. Power factor (L = inductive, C = capacitive)
    05
    2. Frequency
    06
    2. Total reactive power
    07
    1. Total reactive energy supplied**
    08
    1. Total active energy drawn**
    2. Total apparent power
    09
    2. Maximum demanded power (P = Peak demand) that has been reached since the last reset.
    3. Average demanded power (dMd = demand), calculated for the set interval. The value remains unchanged for the entire interval. It is "0" in the first interval after the start.
    10
    • Not used
    11
    • Not used
    12
    1. Active energy drawn*
    13
    1. Apparent power
    14
    1. Reactive energy drawn
    15
    1. Power factor (L = inductive, C = capacitive)
    16
    1. Phase voltage
    17
    1. Conductor voltage
    18
    1. Current
    19
    1. Effective power
    Displayed when easy connection mode is activated (measurement = A). This value indicates the total energy without considering the direction.
    Factory setting - displayed when drawn and delivered energy are measured separately (measurement = b).
    1. Installation
    2. Installation
    Screen
    Code
    Description
    Values
    PASS***
    P1
    Enter the current password
    2633*
    nPASS
    P2
    Password change **
    Four digits (0000-9999)
    SYStEM
    P3
    Type of system
    3Pn*: three-phase system, 4-core
    3P: three-phase system, 3-core
    2P: two-phase system, 3-core
    MEASurE
    P6
    Measurement mode **
    A: easy connection, measures all energy without taking the direction into account.
    B*: measures imported and exported energy separately.
    InStALL
    P7
    Connection check
    On: activated
    Off*: deactivated
    P int
    P8
    Average power calculation interval (minutes)
    1* - 30
    MOdE
    P9
    Display mode **
    Full*: full display
    Easy: reduced display. The values that are not displayed are still transmitted via the serial interface.
    tArIFF
    P10
    Tariff management **
    On: activated
    Off*: deactivated
    HoME
    P11
    Screen showing measured variables displayed at startup and after 120 seconds of inactivity **
    For full display (Mode = Full): 0 - 20*
    AddrESS***
    P14
    Modbus address
    1* - 247
    bAUd
    P15
    Baud rate (kBit/s) **
    9.6* / 19.2 / 38.4 / 57.6 / 115.2
    PArITY
    P16
    Parity **
    Even/No*
    STOP bit
    P16-2
    Only if parity = No. Stop bit. **
    1* / 2
    rESET
    P17
    Activation of the reset function for energy tariffs, maximum requested power, and part values of active and reactive energy (the latter are only transmitted via the serial interface) **
    No*: reset function deactivated.
    Yes: reset function activated.
    End
    P18
    Returns to the measured variables start screen
    None
    Factory settings
    The settings can be protected by changing the default password (password cannot be reset).
    Settings that need to be configured.
    1. Installation
    2. Installation
    Symbol
    Name
    Event
    Function
    Up
    1 x
    Scroll one screen forward, increase the value by 1
    Down
    1 x
    Scroll one screen back, decrease the value by 1
    Enter
    2 seconds
    Call up settings, confirm value
    1Press and hold "Enter" for 2 seconds.
    2Use "Up" or "Down" to access the P1 screen.
    3Set password "2633" with "Up" and "Down" and confirm each individual value with "Enter".
    4Note down the password.
    IMPORTANT!
    The password cannot be reset.
    1Use "Up" or "Down" to access the P14 screen.
    2Press and hold "Enter" for 2 seconds.
    3Set the address with "Up" and "Down" and confirm each individual value with "Enter".
    4Press "Up" to access screen P18 and press and hold "Enter" for 2 seconds to exit the settings.
    1. Installation
    2. Installation
    Error messages
    If the measured signal exceeds the permissible limit values of the meter, a corresponding message or symbol appears on the display:
    • EEE flashes: the measured signal value is outside the limit values.
    • EEE on: the measurement depends on a value that is outside the limit values.
    •   Direction of rotation of the power supply is incorrect
    •   Current direction of a phase (here phase 1) is incorrect
    Note: Active and reactive energy measurements are displayed but do not change.
    Commissioning
    General
    IMPORTANT! Settings under the "Meter" menu item are only to be made by trained and qualified personnel!
    The service password must be entered in order to access the "Meter" menu item.
    Three-phase or single-phase Fronius Smart Meter TS can be used. In both cases, the selection is made under the "Fronius Smart Meter" item. The Fronius Datamanager automatically identifies the meter type.
    A primary meter and several secondary meters can be selected. The primary meter needs to be configured first before a secondary meter can be selected.
    1. Commissioning
    General
    1. Commissioning
    2. Fronius SnapINverter
    General
    1. Commissioning
    Access Point:
    Activate the WiFi access point of the inverter:
    1.
    Navigate to settings (Setup).
    2.
    Navigate to WiFi Access Point.
    ✓Network and password are displayed.
    3.
    Activate WiFi access point with the Enter    key.
    1Select the Setup menu on the inverter display.
    2Navigate to WiFi Access Point.
    ✓Network (SS) and password (PW) are displayed.
    3Activate the WiFi Access Point with the Enter    key.
    Establish the connection from the inverter's WiFi access point to the PC:
    1Establish the connection to the inverter in the network settings (the inverter is displayed with the name "Fronius_240.XXXXXX").
    2Enter and confirm the password from the inverter display.
    3In the browser's address bar, enter the IP address http://192.168.250.181 and confirm.
    ✓The Fronius Datamanager 2.0 start page is displayed.
    LAN:
    1Connect the Fronius Datamanager and computer with a LAN cable.
    2Place the Fronius Datamanager 2.0 IP switch in the "A" position.
    3In the browser's address bar, enter the IP address http://169.254.0.180 and confirm.
    1. Commissioning
    1Go to the Fronius Datamanager website.
    - Open the web browser.
    - In the address bar of the browser, enter the IP address (IP address for WLAN: 192.168.250.181, IP address for LAN: 169.254.0.180) or the host and domain name of the Fronius Datamanager and confirm.
    - The Fronius Datamanager website will be displayed.
    2Click the "Settings" button.
    3Log in to the login area with the "service" user and the service password.
    4Open the "Meter" menu area.
    5Select the primary meter from the drop-down list.
    6Click the "Settings" button.
    7In the pop-up window, set the position of the meter (feed-in point or consumption point). For more information on the position of the Fronius Smart Meter TS, see Positioning on page (→).
    8Click the "Ok" button when the OK status is displayed. If the Timeout status is displayed, try again.
    9Click the    button to save the settings.
    The Fronius Smart Meter TS is configured as a primary meter.
    The "Current general view" menu area displays the power of the PV modules, self-consumption, the energy fed into the grid, and the battery charge (if available).
    1. Commissioning
    5Select the secondary meter from the drop-down list.
    6Click the "Add" button.
    7Enter the name of the secondary meter in the "Name" input field.
    8Enter the previously assigned address in the "Modbus address" input field.
    9Add meter description.
    10Click the    button to save the settings.
    The Fronius Smart Meter TS is configured as a secondary meter.
    1. Commissioning
    General
    IMPORTANT! Settings under the "Device configuration" menu item are only to be made by trained and qualified personnel!
    The service password must be entered in order to access the "Device configuration" menu item.
    Three-phase or single-phase Fronius Smart Meter TS can be used. In both cases, the selection is made under the "Components" menu area. The meter type is determined automatically.
    1. Commissioning
    2. Fronius GEN24 inverter
    General
    1. Commissioning
    WiFi:
    1Open the access point by touching the sensor    .
    ✓Communication LED flashes blue.
    2Establish the connection to the inverter in the network settings (the inverter is displayed with the name "FRONIUS_" and the serial number of the device).
    3Enter the password from the rating plate and confirm.
    IMPORTANT!
    To enter the password, first select the Connect using a security key instead link in order to establish the connection with the password.
    4Enter the IP address 192.168.250.181 in the address bar of the browser and confirm. The installation wizard opens.
    5Follow the installation wizard and complete the installation in the individual areas.
    6Add the system components in Fronius Solar.web and commission the PV system.
    Ethernet:
    1Establish a connection to the inverter (LAN1) using a network cable (min. CAT5 STP).
    2Open the access point by touching the sensor once    .
    3Enter the IP address 169.254.0.180 in the address bar of the browser and confirm. The installation wizard opens.
    4Follow the installation wizard and complete the installation in the individual areas.
    5Add the system components in Fronius Solar.web and commission the PV system.
    1. Commissioning
    1Access the inverter website.
    - In the address bar of the browser, enter the IP address (IP address for WLAN: 192.168.250.181, IP address for LAN: 169.254.0.180) or the host and domain name of the inverter and confirm.
    - The inverter website is displayed.
    2Click the "Device configuration" button.
    3Log in to the login area with the "Technician" user and the technician password.
    4Access the "Components“ menu area.
    5Click the "Add component" button.
    6In the "Position" drop-down list, set the position of the meter (feed-in point or consumption point). For more information on the position of the Fronius Smart Meter TS, see Positioning on page (→).
    7Click the "Add" button.
    8Click the "Save" button to save the settings.
    1. Commissioning
    6In the "Position" drop-down list, select the meter type (producer/load meter).
    7Enter the previously assigned address in the "Modbus address" input field.
    8Enter the name of the meter in the "Name" input field.
    9In the "Category" drop-down list, select the category (producer or load).
    10Click the "Add" button.
    11Click the "Save" button to save the settings.
    Technical data
    Technical data
    Modbus transmission speed: 9600 baud
    Parity bit:none
    Software version:
    • Fronius Datamanager 2.0 (from version 3.16.1 onwards)
    • Fronius Symo Hybrid (from version 1.16.1 onwards)
    Measuring input
    Nominal voltage
    Operating range
    208 - 400 V
    166.4 - 480 V
    Power consumption in the voltage path (max. voltage)
    ≤ 10 VA
    Nominal frequency
    Tolerance
    50 - 60 Hz
    45 - 65 Hz
    Nominal current, lb
    5 A
    Maximum current, Imax
    65 A
    Starting current
    20 mA
    Short-time overload
    (EN IEC 62053-21, EN IEC 62053-23)
    30 lmax / 0.001 s
    Self-consumption - current path (max. current)
    ≤ 1 W
    Power factor
    Operating range
    active cosφ 0.5 ind - 0.8 cap,
    reactive sinφ 0.5 ind - 0.5 cap
    Current total harmonic distortion
    In acc. with EN 50470
    Data output
    RS485 communication
    Electrically isolated from measuring input
    Standard
    RS485 - 3 conductors
    Transmission
    Serial, asynchronous
    Protocol
    Compatible with Modbus RTU
    Addresses
    1 - 255
    Number of bits
    8
    Stop bit
    Parity bit
    None - odd - even
    Baud rate
    300, 2400, 9600 bit/s
    Response time
    ≤ 200 ms
    Insulation (EN IEC 62052-11, EN IEC 62053-21)
    Installation category
    III
    Pollution degree
    Insulation voltage
    4 kVAC RMS (1min)
    Electromagnetic compatibility
    Emission test
    In acc. with EN IEC 62052-11, EN 50470-3
    Immunity test
    Operating conditions
    Reference temperature
    25 °C (±5 °C)
    Operating range
    -25 bis +55 °C
    Temperature limit for storage and transport
    -30 to +80 °C
    Mechanical environment
    Electromechanical environment
    M2
    E2
    Housing
    Housing
    Sealable housing/terminal cover
    Connection
    Screw connection
    Mounting
    Can be snapped onto 35 mm DIN rail
    Housing material
    Noryl, self-extinguishing
    Degree of protection (EN 60529)
    IP51 housing, IP20 connections
    Weight
    240 grams
    Communication LED signals
    red, flashing
    Pulse light according to EN50470-3, EN62052-11, 1000 pulse/kWh (min. frequency 90 ms)
    orange, lights up permanently
    Negative total efficiency
    This check is only carried out if Configuration menu - structure and parameters measurement mode "B" is active. In this case, the device measures drawn and delivered energy.
    Terminals
    Measuring input
    Wire
    min. 1 mm² / max. 16 mm²
    Recommended torque
    max. 2.8 Nm
    Data output
    Wire
    min 0.05 mm²
    Recommended torque
    max. 0.4 Nm
    1. Technical data
    Technical data
    Parity bit:none
    Software version:
    Measuring input
    Nominal voltage
    Operating range
    208 - 400 V
    166.4 - 480 V
    ≤ 10 VA
    Nominal frequency
    Tolerance
    50 - 60 Hz
    45 - 65 Hz
    Nominal current, lb
    5 A
    65 A
    Starting current
    20 mA
    Short-time overload
    30 lmax / 0.001 s
    ≤ 1 W
    Power factor
    Operating range
    Data output
    RS485 communication
    Standard
    Transmission
    Protocol
    Addresses
    1 - 255
    Number of bits
    8
    Stop bit
    Parity bit
    None - odd - even
    Baud rate
    Response time
    ≤ 200 ms
    III
    Pollution degree
    Insulation voltage
    4 kVAC RMS (1min)
    Emission test
    Immunity test
    25 °C (±5 °C)
    Operating range
    -25 bis +55 °C
    -30 to +80 °C
    M2
    E2
    Housing
    Housing
    Connection
    Screw connection
    Mounting
    Housing material
    Weight
    240 grams
    red, flashing
    Terminals
    Measuring input
    Wire
    Recommended torque
    max. 2.8 Nm
    Data output
    Wire
    min 0.05 mm²
    Recommended torque
    max. 0.4 Nm
    1. Technical data
    Warranty
    Detailed warranty conditions specific to your country can be found at https://www.fronius.com/en/download-center?searchword=Warranty+conditions .
    If there is a warranty for the relevant product, register the product at https://warranty.fronius.com/ and activate or extend the warranty.
