Fronius LogoFronius Mobile Logo
en
      Operating instructionsFronius Smart Meter WR
    • General information
      • Safety information
        • Explanation of warnings and safety instructions
        • Safety instructions and important information
        • General
        • Environmental conditions
      • General
        • Information on the device
        • How information is presented in the document
        • Target group
        • Data security
        • Privacy policy
        • Copyright
        • FCC / RSS Compliance
        • Territorial Limitations
        • Disposal
      • Fronius Smart Meter WR
        • Device description
        • Positioning
        • Displays and connections
    • Installation
      • Installation Checklist
      • Mounting
      • Circuit Protection
      • Line Wiring
      • Connect Current Transformers
      • Power control systems (USA, Canada, Mexico)
      • CT Wiring
      • Connecting data communication cables to inverters
      • Set the address of the Fronius Smart Meter
      • Terminating resistors - explanation of symbols
      • Terminating Resistors
      • Set Baud Rate
      • Multi meter system - Explanation of symbols
      • Modbus participant - Fronius SnapINverter
      • Multi meter system – Fronius SnapINverter
      • Modbus participant - Fronius GEN24
      • Multi meter system - Fronius GEN24 inverter
    • Commissioning
      • Fronius SnapINverter
        • General
        • Connect to Fronius Datamanager 2.0
        • Configure Fronius Smart Meter as primary meter
        • Configure Fronius Smart Meter as a secondary meter
      • Fronius GEN24 inverter
        • General
        • Installation with the browser
        • Configure Fronius Smart Meter as primary meter
        • Configure Fronius Smart Meter as a secondary meter
    • Operation
      • Power Status LEDs
      • Modbus Communication LEDs
    • Technical data
      • Accuracy
      • Measurement
      • Models and Electrical
      • Certifications
      • Environmental
      • Warranty
    • 012-02062026

    Fronius Smart Meter WR

    download
    Installation Checklist
    Operation
    Technical Data
    ContactImprintTerms of usePrivacy statementCookie policy
    © 2026 Fronius International GmbH
    © 2026 Fronius International GmbH
    ContactImprintTerms of usePrivacy statementCookie policy

    General information

    link_horizontalLink copied

    Safety information

    Explanation of warnings and safety instructions

    Warnings are intended to warn people of possible injuries and to avoid personal injury and damage to the product. They relate to individual actions with and on the product.

    DANGER!

    Indicates an immediately dangerous situation.

    Serious injury or death will result if the danger is not avoided.

    Action step to escape the situation.

    WARNING!

    Indicates a potentially dangerous situation.

    Serious injury or death may result if the danger is not avoided.

    Action step to escape the situation.

    CAUTION!

    Indicates a potentially dangerous situation.

    Minor or moderate injury may result if the danger is not avoided.

    Action step to escape the situation.

    NOTE!

    Indicates a situation that may result in property damage.

    If the situation is not avoided, impaired work results, material damage to the product or other property are the possible consequences.

    Action step to avoid the situation.

    Safety instructions are designed to ensure safe product use. They are preventive and help to inform users about the fundamental risks involved when dealing with the product. They do not refer specifically to individual actions with and on the product.

    1. General information

    Safety information

    link_horizontalLink copied

    Explanation of warnings and safety instructions

    Warnings are intended to warn people of possible injuries and to avoid personal injury and damage to the product. They relate to individual actions with and on the product.

    DANGER!

    Indicates an immediately dangerous situation.

    Serious injury or death will result if the danger is not avoided.

    Action step to escape the situation.

    WARNING!

    Indicates a potentially dangerous situation.

    Serious injury or death may result if the danger is not avoided.

    Action step to escape the situation.

    CAUTION!

    Indicates a potentially dangerous situation.

    Minor or moderate injury may result if the danger is not avoided.

    Action step to escape the situation.

    NOTE!

    Indicates a situation that may result in property damage.

    If the situation is not avoided, impaired work results, material damage to the product or other property are the possible consequences.

    Action step to avoid the situation.

    Safety instructions are designed to ensure safe product use. They are preventive and help to inform users about the fundamental risks involved when dealing with the product. They do not refer specifically to individual actions with and on the product.

    1. General information
    2. Safety information

    Explanation of warnings and safety instructions

    link_horizontalLink copied

    Warnings are intended to warn people of possible injuries and to avoid personal injury and damage to the product. They relate to individual actions with and on the product.

    DANGER!

    Indicates an immediately dangerous situation.

    Serious injury or death will result if the danger is not avoided.

    Action step to escape the situation.

    WARNING!

    Indicates a potentially dangerous situation.

    Serious injury or death may result if the danger is not avoided.

    Action step to escape the situation.

    CAUTION!

    Indicates a potentially dangerous situation.

    Minor or moderate injury may result if the danger is not avoided.

    Action step to escape the situation.

    NOTE!

    Indicates a situation that may result in property damage.

    If the situation is not avoided, impaired work results, material damage to the product or other property are the possible consequences.

    Action step to avoid the situation.

    Safety instructions are designed to ensure safe product use. They are preventive and help to inform users about the fundamental risks involved when dealing with the product. They do not refer specifically to individual actions with and on the product.

    1. General information
    2. Safety information

    Safety instructions and important information

    link_horizontalLink copied

    The device has been manufactured in line with the state of the art and according to recognized safety standards.

    WARNING!

    Incorrect operation or misuse

    Serious to fatal injuries to the operator or third parties as well as damage to the device and other property of the operator may result.

    All persons involved in the commissioning, maintenance, and servicing of the device must be appropriately qualified and have knowledge of working with electrical installations.

    Read these operating instructions in full and follow them carefully and precisely.

    The operating instructions must always be kept to hand wherever the device is being used.

    IMPORTANT!
    In addition to the operating instructions, observe the following general and local rules:
    • Accident prevention
    • Fire protection
    • Environmental protection

    IMPORTANT!
    Labels, warning notices, and safety symbols are located on the device. A description can be found in these operating instructions.

    IMPORTANT!
    All safety and danger notices on the device:
    • Must be kept in a legible state
    • Must not be damaged/marked
    • Must not be removed
    • Must not be covered, have anything stuck on them, or painted over

    WARNING!

    Tampered-with and non-functioning protection devices

    Serious to fatal injuries as well as damage to the device and other property of the operator may result.

    Never bypass or disable protection devices.

    Any protection devices that are not fully functional must be repaired by an authorized specialist before the device is switched on.

    WARNING!

    Loose, damaged, or under-dimensioned cables

    An electric shock can be fatal.

    Use undamaged, insulated, and adequately dimensioned cables.

    Fasten the cables according to the specifications in the operating instructions.

    Loose, damaged, or under-dimensioned cables must be repaired or replaced immediately by an authorized specialist.

    NOTE!

    Installations or modifications to the device

    The device may be damaged

    Do not carry out any alterations, installations, or modifications to the device without first obtaining the manufacturer's permission.

    Damaged components must be replaced.

    Only use original spare parts.

    1. General information
    2. Safety information

    General

    link_horizontalLink copied
    The device has been manufactured using state-of-the-art technology and according to recognized safety standards. If used incorrectly or misused, however, it can cause
    • serious or fatal injury to the operator or a third party,
    • and damage to the device and other material assets belonging to the operating company.
    All persons involved in start-up operation, maintenance and servicing of the device must
    • be suitably qualified,
    • have knowledge of and experience in dealing with electrical installations and
    • have fully read and precisely followed these Operating Instructions.

    The Operating Instructions must always be kept on hand wherever the device is being used. In addition to the Operating Instructions, all applicable local rules and regulations regarding accident prevention and environmental protection must also be followed.

    All safety and danger notices on the device
    • must be kept in a legible state
    • must not be damaged/marked
    • must not be removed
    • must not be covered, pasted, or painted over.

    The terminals can reach high temperatures.

    Only operate the device when all protection devices are fully functional. If the protection devices are not fully functional, there is a risk of
    • serious or fatal injury to the operator or a third party,
    • and damage to the device and other material assets belonging to the operating company.

    Any safety devices that are not functioning properly must be repaired by an authorized specialist before the device is switched on.

    Never bypass or disable protection devices.

    For the location of the safety and danger notices on the device, refer to the section headed “General” in the Operating Instructions for the device.

    Any equipment malfunctions which might impair safety must be remedied immediately before the device is turned on.

    Your personal safety is at stake!

    1. General information
    2. Safety information

    Environmental conditions

    link_horizontalLink copied

    Operation or storage of the machine outside the stipulated area will be deemed as not in accordance with the intended purpose.

    For exact information on permitted environmental conditions, please refer to the technical data.

    1. General information

    General

    link_horizontalLink copied

    Information on the device

    Safety symbols:

    To avoid electric shocks:
    • Do not dismantle or modify the device
    • Do not allow any water to enter the device
    • Do not allow any foreign substances or material to enter the device
    • Do not touch any connections directly

    RCM Symbol - The product complies with the Australian laws.

    1. General information
    2. General

    Information on the device

    link_horizontalLink copied

    Safety symbols:

    To avoid electric shocks:
    • Do not dismantle or modify the device
    • Do not allow any water to enter the device
    • Do not allow any foreign substances or material to enter the device
    • Do not touch any connections directly

    RCM Symbol - The product complies with the Australian laws.

    1. General information
    2. General

    How information is presented in the document

    link_horizontalLink copied

    The conventions regarding how information is presented in the document, which are set out below, have been defined in order to increase the readability and comprehensibility of the document.

    Application notes

    IMPORTANT! Indicates application notes and other useful information. It does not indicate a harmful or dangerous situation.

    Software

    Software functions and elements of a graphical user interface (e.g., buttons, menu items) are highlighted in the text with this mark up.

    Example: Click Save.

    Instructions for action

    1Action steps are displayed with consecutive numbering.
    ✓This symbol indicates the result of the action step or the entire instruction.
    1. General information
    2. General

    Target group

    link_horizontalLink copied

    This document provides detailed information and instructions to ensure that people can use the machine safely and efficiently.

    The information is intended for the following groups of people:
    • Technical specialists: People with appropriate qualifications and fundamental knowledge of electronics and mechanics. The activities of a technical specialist include installation, operation, maintenance, and service work.
    • User: People that use the machine in daily operation and want to understand its basic functions.

    Regardless of any qualifications, only perform the activities listed in this document.

    The definition of professional qualifications and their applicability are subject to national law.

    1. General information
    2. General

    Data security

    link_horizontalLink copied
    With regard to data security, the user is responsible for:
    • Backing up any changes made to the factory settings
    • Saving and storing personal settings

    NOTE!

    Data security for network and Internet connection

    Unsecured networks and a lack of safeguards can result in data loss and unauthorized access. Observe the following points for safe operation:

    Operate inverters and system components on a private, secure network. A WiFi network is considered secure if security standard WPA 2 is satisfied as a minimum.

    Keep the network devices (e.g., WiFi routers) up to date with the latest technology.

    Keep the software and/or firmware updated.

    Use a wired network to ensure a stable data connection.

    For security reasons, do not make inverters and system components accessible from the Internet via port forwarding or Port Address Translation (PAT).

    Use the solutions provided by Fronius for monitoring and remote configuration.

    The optional communication protocol Modbus TCP/IP1) is an unsecured interface. Only use Modbus TCP/IP if no other secured data communication protocol (MQTT2)) is possible (e.g., compatibility with older Smart Meters).

    1) TCP/IP - Transmission Control Protocol/Internet Protocol
    2) MQTT - Message Queuing Telemetry Protocol

    1. General information
    2. General

    Privacy policy

    link_horizontalLink copied

    When you connect your device (and any associated devices) to the internet, the following device and operating data (device ID/identifier, device IP address, device time, configuration settings, hardware and software information, device status log files, serial number) is sent automatically to

    Fronius International GmbH, Froniusstraße 1, 4643 Pettenbach, Austria, telephone +43(0) 7242241-0, email: contact@fronius.com (controller)

    and stored.

    The processing of this device and operating data is carried out for the purpose of ensuring the operational safety of the device (time synchronization, provision of updates). This processing is therefore necessary for the functionality of the device and thus for the fulfillment of the contract (Art. 6 (1) (b) GDPR).

    If you do not wish to have such data processed, you must manually disable the device's internet connection.

    In addition, the device and operating data is also processed for the purpose of providing services as part of a supplementary digital service for your device (such as solar.web or similar) as soon as you have registered your device with such a digital service (identification). This data is processed to provide the requested digital services and is therefore necessary for the fulfillment of the contract (Art. 6 (1) (b) GDPR).

    Furthermore, this data processing is also carried out for maintenance and support purposes and for handling customer concerns as well as in warranty and guarantee cases (only in individual cases and given connection between device and internet). In this context, the device and operating data may also be passed on to our cooperation partners (third-party providers and suppliers). The processing of this data is necessary for maintenance and support purposes or for processing warranty and guarantee cases and thus for the fulfillment of the contract (Art. 6 (1) (b) GDPR).

    Device and operating data are also processed for analysis and diagnostic purposes in order to gain insights into the functionality of the devices and improve them accordingly. This data processing is based on our legitimate interest (Art. 6 (1) (f) GDPR).

    We store this data for as long as it is necessary to fulfill the existing contract with you. Any storage beyond this is carried out for legal reasons or if we have a legitimate interest in doing so. For more information on data processing for the solar.web-digital service, as well as our general privacy policy and your rights as a data subject, please visit https://www.fronius.com.

    1. General information
    2. General

    Copyright

    link_horizontalLink copied

    Fronius International GmbH retains the copyrights of these operating instructions.

    Text, illustrations, and other media correspond to the technical state of the art at the time of publication. Fronius reserves the right to make changes. If you have any suggestions for improvement or have found a mistake in this document, we would be most grateful for your comments.

    1. General information
    2. General

    FCC / RSS Compliance

    link_horizontalLink copied

    FCC
    This device corresponds to the limit values for a digital device of class B in accordance with Part 15 of the FCC regulations. The limit values should provide adequate protection against harmful interference in homes. This device creates and uses high frequency energy and can interfere with radio communications when not used in accordance with the instructions. However, there is no guarantee against interference occurring in a particular installation.
    If this device interferes with radio or television reception when turning the device on and off, it is recommended that the user solve this with one or more of the following measures:

    • adjust or reposition the receiving antenna
    • increase the distance between the affected device and the receiver
    • connect the device to another circuit, which does not include the receiver
    • for further support, please contact the retailer or an experienced radio/TV technician.

    Industry Canada RSS
    The device corresponds to the license-free Industry Canada RSS standards. Operation is subject to the following conditions:
    (1) The device may not cause harmful interference
    (2) The device must accept any interference received, including interference that may cause undesired operation.

    1. General information
    2. General

    Territorial Limitations

    link_horizontalLink copied

    This product is intended for use and sale outside the Province of Québec. It does not meet the French language documentation and labeling requirements of Québec's Charter of the French Language. Accordingly, Fronius International GmbH does not offer this product for sale to, or for delivery to, any address within the Province of Québec.

    By placing an order, the customer represents and warrants that they are not purchasing the product for use or resale within Québec. Fronius International GmbH disclaims all liability and warranty obligations for any products operated in Québec in violation of these restrictions.

    1. General information
    2. General

    Disposal

    link_horizontalLink copied
    In accordance with the EU Directive and national law, the following products must be disposed of separately and recycled:
    • Waste electrical and electronic equipment
    • Used batteries (portable batteries, industrial batteries)

    Used equipment and batteries must be returned to the distributor or an authorized local collection system. Do not dispose of batteries with domestic waste. Protect batteries from high temperatures, direct sunlight, moisture and corrosive environments.

    Arrange for the safe collection and proper disposal of damaged, leaking or used batteries by a battery recycling company or the Fronius Service Partner.

    In addition, it should be noted that batteries contain substances that, if disposed of improperly, can have a significant negative impact on the environment as well as on human health and the safety of persons, in particular due to the leakage of hazardous substances such as heavy metals or electrolytes, which can contaminate soil, water and air.

    This ensures environmental protection and the sustainable use of natural resources.

    Packaging materials
    • Collect separately
    • Observe local regulations
    • Compress the cardboard box to reduce volume
    1. General information

    Fronius Smart Meter WR

    link_horizontalLink copied

    Device description

    The Fronius Smart Meter is a bidirectional electricity meter for optimizing self-consumption and recording a household's load characteristic curve. Together with a Fronius inverter or Fronius Datamanager 2.0 and a Fronius data interface, the Fronius Smart Meter allows you to view your own power consumption. The meter measures the energy flow to the loads or to the public grid and forwards the information to the Fronius inverter or Fronius Datamanager 2.0 via the Modbus RTU/RS485 interface.

    CAUTION!

    Danger due to non-compliance with the safety instructions

    Risk of injury and damage to the device as a result.

    Follow all safety instructions.

    Switch off the power supply before establishing the mains connection.

    1. General information
    2. Fronius Smart Meter WR

    Device description

    link_horizontalLink copied

    The Fronius Smart Meter is a bidirectional electricity meter for optimizing self-consumption and recording a household's load characteristic curve. Together with a Fronius inverter or Fronius Datamanager 2.0 and a Fronius data interface, the Fronius Smart Meter allows you to view your own power consumption. The meter measures the energy flow to the loads or to the public grid and forwards the information to the Fronius inverter or Fronius Datamanager 2.0 via the Modbus RTU/RS485 interface.

    CAUTION!

    Danger due to non-compliance with the safety instructions

    Risk of injury and damage to the device as a result.

    Follow all safety instructions.

    Switch off the power supply before establishing the mains connection.

    1. General information
    2. Fronius Smart Meter WR

    Positioning

    link_horizontalLink copied

    The Fronius Smart Meter can be installed at two possible locations in the system, at the feed-in point and at the consumption point.

    Positioning at the feed-in point
    The positioning of the Fronius Smart Meter at the feed-in point.

    Positioning at the consumption point
    The positioning of the Fronius Smart Meter at the consumption point.

    1. General information
    2. Fronius Smart Meter WR

    Displays and connections

    link_horizontalLink copied
    (1)
    Product name
    (2)
    Nominal voltage, operating frequencies, measurement category
    (3)
    AC connection area
    (4)
    Note single-phase grids
    (5)
    Power status LED
    • green, flashing: Import of energy from public grid
    • red, flashing: Export of energy to the public grid
    • For further display options, see Power Status LEDs
    (6)
    DIP-switch:
    • set modbus adress, see Set the address of the Fronius Smart Meter
    • set terminating resistor, see Terminating Resistors
    • set Baud Rate, see Set Baud Rate
    (7)
    CT connection area
    (8)
    Data communication LED
    (9)
    Data communication connection area

    Installation

    link_horizontalLink copied

    Installation Checklist

    See the sections referenced below for installation details.
    1Turn off power before making line voltage connections.
    2Mount the Fronius Smart Meter (see Mounting on page (→)).
    3Connect circuit breakers or fuses and disconnects (see Circuit Protection on page (→)).
    4Connect the line voltage wires to the meter‘s terminal block (see Line Wiring on page (→)).
    5Mount the Current Transformers (CTs) around the line conductors. Make sure the CTs face the correct direction. An arrow might indicate either the load or the source (public grid) (see Connect Current Transformers on page (→)).
    6Connect the twisted white and black wires from the CTs to the terminal block on the meter, matching the wire colors to the white and black dots on the meter label (see CT Wiring on page (→)).
    7Check that the CT phases match the line voltage phases (see Connect Current Transformers on page (→)).
    8Record the CT rated current for each meter, because it will be required during setup.
    9Connect the output terminals of the Fronius Smart Meter to the monitoring equipment (see Connecting data communication cables to inverters on page (→)).
    10If necessary set terminating resistors (see Terminating Resistors on page (→)).
    11Check that all the wires and plugs are securely installed in the terminal blocks by tugging on each wire.
    12Turn on the power to the Smart Meter.
    13Verify that the LEDs indicate correct operation. If there is a consumption of power and all generated power sources are turned off, then the LEDs from the used phases should flash green (see Power Status LEDs on page (→)).
    14Check your Fronius System monitoring software. In order to ensure compatibility between the inverter and the Smart Meter, software must always be kept up-to-date. The update can be started via the inverter website or via Solar.web.
    15Set CT-Ratio and Grid Type on the web interface of the Fronius Datamanager in Settings - Meter - Settings (see Commissioning on page (→)).
    1. Installation

    Installation Checklist

    link_horizontalLink copied
    See the sections referenced below for installation details.
    1Turn off power before making line voltage connections.
    2Mount the Fronius Smart Meter (see Mounting on page (→)).
    3Connect circuit breakers or fuses and disconnects (see Circuit Protection on page (→)).
    4Connect the line voltage wires to the meter‘s terminal block (see Line Wiring on page (→)).
    5Mount the Current Transformers (CTs) around the line conductors. Make sure the CTs face the correct direction. An arrow might indicate either the load or the source (public grid) (see Connect Current Transformers on page (→)).
    6Connect the twisted white and black wires from the CTs to the terminal block on the meter, matching the wire colors to the white and black dots on the meter label (see CT Wiring on page (→)).
    7Check that the CT phases match the line voltage phases (see Connect Current Transformers on page (→)).
    8Record the CT rated current for each meter, because it will be required during setup.
    9Connect the output terminals of the Fronius Smart Meter to the monitoring equipment (see Connecting data communication cables to inverters on page (→)).
    10If necessary set terminating resistors (see Terminating Resistors on page (→)).
    11Check that all the wires and plugs are securely installed in the terminal blocks by tugging on each wire.
    12Turn on the power to the Smart Meter.
    13Verify that the LEDs indicate correct operation. If there is a consumption of power and all generated power sources are turned off, then the LEDs from the used phases should flash green (see Power Status LEDs on page (→)).
    14Check your Fronius System monitoring software. In order to ensure compatibility between the inverter and the Smart Meter, software must always be kept up-to-date. The update can be started via the inverter website or via Solar.web.
    15Set CT-Ratio and Grid Type on the web interface of the Fronius Datamanager in Settings - Meter - Settings (see Commissioning on page (→)).
    1. Installation

    Mounting

    link_horizontalLink copied

    The Fronius Smart meter has two mounting holes spaced 5.4 in. (137 mm) apart (center-to-center). These mounting holes are normally obscured by the detachable screw terminals. Remove the screw terminals to mark the hole positions and mount the meter.

    Self-tapping sheet metal screws are included. Do not over-tighten the screws, as long-term stress on the case can cause cracking.

    1. Installation

    Circuit Protection

    link_horizontalLink copied

    The Fronius Smart Meter is considered “permanently connected equipment“ and requires a disconnect means (circuit breaker, switch or disconnect) and overcurrent protection (fuse or circuit breaker).

    The Fronius Smart Meter only draws 10-30 mA, so the rating of any switches, disconnects, fuses and / or circuit breakers is determined by the wire gauge, the mains voltage and the current interrupting rating required.

    • The switch, disconnect or circuit breaker must be within sight and as close as practicable to the Fronius Smart Meter and must be easy to operate.
    • Use circuit breakers or fuses rated for 20 amps or less.
    • Use ganged circuit breakers when monitoring more than one line voltage.
    • The circuit breakers or fuses must protect the mains terminals labeled L1, L2 and L3. In the rare cases where neutral has overcurrent protection, the overcurrent protection device must interrupt both neutral and ungrounded conductors simultaneously.
    • The circuit protection / disconnect system must meet IEC 60947-1 and IEC 60947-3, as well as all national and local electrical codes.
    1. Installation

    Line Wiring

    link_horizontalLink copied
    • Always turn off power before connecting the line voltage inputs to the Fronius Smart Meter.
    • For the line voltage wires, 16 to 12 AWG stranded wire, type THHN, MTW or THWN, 600 V are recommended.
    • Do not place more than one wire per screw terminal; use separate wire nuts or terminal blocks if needed.
    • Verify that the line voltages match the line-to-line and line-to-neutral values printed in the white box on the front label.

    Connect each conductor to the appropriate phase; also connect ground and neutral (if applicable). The neutral connection “N“ is not required on delta models but we recommend connecting it to ground if neutral is not present.

    The screw terminal can handle wire up to 12 AWG. Connect each voltage line to the green terminal block as shown in the following figures. After the voltage lines have been connected, make sure both terminal blocks are fully seated in the Fronius Smart Meter.

    When power is first applied, check that the LEDs behave normally. If you see LEDs flashing red-green-red-green, the voltage is too high for this model, so disconnect the power switch immediately!

    Single-Phase Three-Wire (Mid-Point Neutral) / Two-Phase Australia

    Single-Phase Two-Wire without Neutral

    Single-Phase Two-Wire with Neutral

    Three-Phase Four-Wire Wye

    Three-Phase Three-Wire Delta without Neutral

    Three-Phase Four-Wire Stinger

    Three-Phase Two-Wire Corner Grounded Delta

    1. Installation

    Connect Current Transformers

    link_horizontalLink copied

    The current transformer must generate 333.33 millivolts AC at rated current. See the current transformer data sheets for CT ratings (Fronius CT, 41,0010,0104 / 41,0010,0105 / 41,0010,0232).

    • Do not use ratio or current output such as 1 amp or 5 amp output models!
    • See the CT data sheets for the maximum input current ratings.
    • Be careful to match the CTs with the voltage phases. Make sure the CT L1 is measuring the current on the same phase being monitored by the L1 voltage input and the same for phases L2 and L3. Use the supplied colored labels or colored tape to identify the CT leads.
    • To minimize current measurement noise, avoid extending the CT wires, especially in noisy environments. If it is necessary to extend the wires, use twisted pair cable 22 to 14 AWG, rated for 300 V or 600 V (not less than the service voltage) and shielded if possible
    • Make sure the CTs face the correct direction. An arrow might indicate either the load or the source (public grid)
    • If you see strange readings on unused phases, jumper the unused CT inputs: for each unused CT, connect a short cable from the terminal marked with a white dot to the terminal marked with a black dot.

    Install the CTs around the conductor to be measured and connect the CT leads to the Fronius Smart Meter. Always turn off power before disconnecting any live conductors. Put the line conductors through the CTs as shown in the previous section.

    CTs are directional. If they are mounted backwards or with their white and black wires swapped the measured power will be negative. The status LEDs indicate negative measured power by flashing red.

    Split-core CTs can be opened for installation around the conductor. A nylon cable tie may be secured around the CT to prevent inadvertent opening.

    1. Installation

    Power control systems (USA, Canada, Mexico)

    link_horizontalLink copied

    The device can be used for power control systems in accordance with the UL 3141 standard. The additionally required current transformers must comply with the specifications of the UL 2808 standard.

    NOTE!

    Power Control Systems

    Power Control Systems according to UL 3141 are only available for installations in the USA, Canada and Mexico.

    1. Installation

    CT Wiring

    link_horizontalLink copied

    The current transformers connect to the six position black screw terminal block. Connect the white and black CT wires to the Fronius Smart Meter terminals marked CT L1, CT L2 and CT L3. Excess length may be trimmed from the wires if desired. Connect each CT with the white wire aligned with the white dot on the label and the black wire aligned with the black dot. Note the order in which the phases are connected, as the line voltage phases must match the current phases for accurate power measurement.

    1. Installation

    Connecting data communication cables to inverters

    link_horizontalLink copied

    Fronius SnapINveter:
    Connect the data communication ports of the Fronius Smart Meter to the Fronius system monitoring in the inverter. Several Smart Meters can be installed in the system, see chapter Multi meter system – Fronius SnapINverter on page (→)

    1Connect D- to D-.
    2Connect D+ to D+.
    3Connect - to -.

    Fronius GEN24 inverter:
    Connect the data communication ports of the Fronius Smart Meter to the Modbus interface of the Fronius GEN24 inverter. Several Smart Meters can be installed in the system, see chapter Multi meter system - Fronius GEN24 inverter on page (→)

    1Connect D- to M1-.
    2Connect D+ to M1+.
    3Connect - to GND.
    IMPORTANT! Further information on successful start-up.
    Observe the following information on connecting the data communication line to the inverter.
    • Use a CAT5 type cable or higher.
    • For data lines belonging together (D+, D- and M1+, M1-) use a twisted pair of cables.
    • If the output cables are close to the mains wiring, use wires or cables rated at 300 V to 600 V (never less than the operating voltage).
    • Use double insulated or sheathed output cables when near bare conductors.
    • Use shielded twisted pair cables to avoid interference.
    • The outputs of the Fronius Smart Meter are galvanically isolated from dangerous voltages.
    1. Installation

    Set the address of the Fronius Smart Meter

    link_horizontalLink copied

    The Fronius Smart Meter must be connected to the Fronius Datamanager. If only one Fronius Smart Meter is installed, the Modbus Address is 1.

    DIP Switch

    1

    2

    3

    4

    5

    6

    7

    8

    Up (1) value

    1

    2

    4

    8

    16

    32

    R 120 Ohm

    Baud Rate

    Examples

    Modbus Adress 1

    DIP Switch

    1

    2

    3

    4

    5

    6

    Position

    1

    0

    0

    0

    0

    0

    Modbus Adress 2

    DIP Switch

    1

    2

    3

    4

    5

    6

    Position

    0

    1

    0

    0

    0

    0

    Modbus Adress 3 (value 1 + 2 = 3)

    DIP Switch

    1

    2

    3

    4

    5

    6

    Position

    1

    1

    0

    0

    0

    0

    Modbus Adress 4

    DIP Switch

    1

    2

    3

    4

    5

    6

    Position

    0

    0

    1

    0

    0

    0

    Modbus Adress 7 (value 1 + 2 + 4 = 7)

    DIP Switch

    1

    2

    3

    4

    5

    6

    Position

    1

    1

    1

    0

    0

    0

    Modbus Adress 20 (value 4 + 16 = 20)

    DIP Switch

    1

    2

    3

    4

    5

    6

    Position

    0

    0

    1

    0

    1

    0

    1. Installation

    Terminating resistors - explanation of symbols

    link_horizontalLink copied

    Inverter in the system
    e.g. Fronius Primo GEN24 208-240

    Meter - Fronius Smart Meter WR
    Terminating resistor is integrated in the meter.

    Fronius or third-party device, connection via Modbus RTU
    e.g. Fronius Ohmpilot, battery, etc.

    Termination resistance
    R 120 Ohm

    1. Installation

    Terminating Resistors

    link_horizontalLink copied

    The system might work without terminating resistors. Due to interferences, the use of terminating resistors according to the following schemes are recommended.

    Activate the Fronius Smart Meter terminating resistor (R 120 Ohm) by switching pin 7 to ON (1).

    1. Installation

    Set Baud Rate

    link_horizontalLink copied

    Select the baud rate by setting DIP switch position 8 (see below). The change will take effect immediately.

    Baud Rate

    DIP Switch 8

    9600 (default)

    0 (OFF)

    38400

    1 (ON)

    1. Installation

    Multi meter system - Explanation of symbols

    link_horizontalLink copied

    Grid
    Supplies the loads in the system if insufficient power is being generated by the PV modules or supplied by the battery.

    Inverter in the system
    e.g. Fronius Primo, Fronius Symo, etc.

    Utility meter
    Measures the metering data relevant for the billing of electricity quantities (primarily the kilowatt hours of grid purchases and grid power feed). On the basis of the data relevant for billing, the electricity retailer invoices a grid purchase and the purchaser of the surplus pays for the grid power feed.

    Primary meter
    Records the load curve of the system and makes the measured data available for energy profiling in Fronius Solar.web. The primary meter also regulates the dynamic feed-in control.

    Secondary meter
    Records the load curve of individual loads and producers (e.g. washing machine, lights, television, heat pump, etc.) in the consumption branch and makes the measured data available for energy profiling in Fronius Solar.web.

    Modbus RTU, Third-party device
    e.g. Fronius Ohmpilot, battery, etc.

    Loads in the system
    e.g. washing machine, lamps, TV, etc.

    Additional loads in the system
    e.g. heat pump

    Additional producers in the system
    e.g. wind power plant

    Terminating resistor
    R 120 Ohm

    1. Installation

    Modbus participant - Fronius SnapINverter

    link_horizontalLink copied

    A maximum of 4 Modbus stations can be connected to the Modbus connection terminal.

    IMPORTANT!
    Only one primary meter, one battery and one Ohmpilot can be connected per inverter. Due to the high data transfer of the battery, the battery occupies 2 subscribers.

    Example:

    Input

    Battery

    Fronius
    Ohmpilot

    Number
    of primary meters

    Number
    of secondary meters

    Modbus

    1

    0

    1

    1

    1

    2

    1

    3

    1. Installation

    Multi meter system – Fronius SnapINverter

    link_horizontalLink copied

    If several Fronius Smart Meters are installed, set a separate address for each Smart Meter. The primary meter always receives the address 1. Number all other meters consecutively in the address range from 2 to 14. Different Fronius Smart Meter power categories can be used together.

    IMPORTANT! Use a maximum of three secondary meters in a system. To avoid interference, install the terminating resistors as described in chapter Terminating Resistors.

    3 secondary meters with connected generators and loads, primary meter in the consumption branch
    Position of the primary meter in the consumption branch. *Terminating resistor R 120 Ohm
    3 secondary meters with connected generators and loads, primary meter at the feed-in point
    Position of the primary meter at the feed-in point. *Terminating resistor R 120 Ohm
    Observe the following in a multi meter system:
    • Each Modbus address is assigned only once.
    • Place the terminating resistors individually for each channel.
    1. Installation

    Modbus participant - Fronius GEN24

    link_horizontalLink copied

    The inputs M0 and M1 can be freely selected. A maximum of 4 Modbus participants can be connected to the Modbus terminal on the inputs M0 and M1.

    IMPORTANT!
    Only one primary meter, one battery and one Ohmpilot can be connected per inverter. Due to the high data transfer of the battery, the battery occupies 2 subscribers.

    Example 1:

    Input

    Battery

    Fronius
    Ohmpilot

    Number
    of primary meters

    Number
    of secondary meters

    Modbus 0
    (M0)

    0

    4

    0

    2

    0

    1

    Modbus 1
    (M1)

    1

    3

    Example 2:

    Input

    Battery

    Fronius
    Ohmpilot

    Number
    of primary meters

    Number
    of secondary meters

    Modbus 0
    (M0)

    1

    3

    Modbus 1
    (M1)

    0

    4

    0

    2

    0

    1

    1. Installation

    Multi meter system - Fronius GEN24 inverter

    link_horizontalLink copied

    If several Fronius Smart Meters are installed, a separate address must be set for each one (see Set the address of the Fronius Smart Meter on page (→)). The primary meter always receives the address 1. All other meters are numbered consecutively in the address range from 2 to 14. Different Fronius Smart Meter power categories can be used together.

    IMPORTANT!
    Use no more than Use 7 secondary meters in the system. To avoid interference, it is recommended to install the terminating resistors according to the chapter Terminating Resistors on page (→).

    Position of the primary meter in the consumption branch. *Termination resistance R 120 Ohm
    Position of the primary meter at the feed-in point. *Termination resistance R 120 Ohm
    The following must be observed in a multi meter system:
    • Connect the primary meter and the battery to different channels (recommended).
    • Distribute the remaining Modbus participants evenly.
    • Each Modbus address is assigned only once.
    • Place the terminating resistors individually for each channel.

    Commissioning

    link_horizontalLink copied

    Fronius SnapINverter

    General

    IMPORTANT! Settings in the "Meter" menu item may only be entered by staff trained to do so!

    The service password must be entered for the "Meter" menu item.

    Three-phase or one-phase Fronius Smart Meters may be used. In both cases, selection is made via the "Fronius Smart Meter" item. The Fronius Datamanager automatically detects the meter type.

    One primary meter and several secondary meters can be selected. The primary meter must be configured before a secondary meter can be chosen.

    1. Commissioning

    Fronius SnapINverter

    link_horizontalLink copied

    General

    IMPORTANT! Settings in the "Meter" menu item may only be entered by staff trained to do so!

    The service password must be entered for the "Meter" menu item.

    Three-phase or one-phase Fronius Smart Meters may be used. In both cases, selection is made via the "Fronius Smart Meter" item. The Fronius Datamanager automatically detects the meter type.

    One primary meter and several secondary meters can be selected. The primary meter must be configured before a secondary meter can be chosen.

    1. Commissioning
    2. Fronius SnapINverter

    General

    link_horizontalLink copied

    IMPORTANT! Settings in the "Meter" menu item may only be entered by staff trained to do so!

    The service password must be entered for the "Meter" menu item.

    Three-phase or one-phase Fronius Smart Meters may be used. In both cases, selection is made via the "Fronius Smart Meter" item. The Fronius Datamanager automatically detects the meter type.

    One primary meter and several secondary meters can be selected. The primary meter must be configured before a secondary meter can be chosen.

    1. Commissioning
    2. Fronius SnapINverter

    Connect to Fronius Datamanager 2.0

    link_horizontalLink copied

    Access Point:

    Activate the WiFi access point of the inverter:
    Ihr Browser kann diesen Film leider nicht anzeigen.
    1.
    Navigate to settings (Setup).
    2.
    Navigate to WiFi Access Point.
    ✓Network and password are displayed.
    3.
    Activate WiFi access point with the Enter    key.
    1Select the Setup menu on the inverter display.
    2Navigate to WiFi Access Point.
    ✓Network (SS) and password (PW) are displayed.
    3Activate the WiFi Access Point with the Enter    key.
    Establish the connection from the inverter's WiFi access point to the PC:
    1Establish the connection to the inverter in the network settings (the inverter is displayed with the name "Fronius_240.XXXXXX").
    2Enter and confirm the password from the inverter display.
    3In the browser's address bar, enter the IP address http://192.168.250.181 and confirm.
    ✓The Fronius Datamanager 2.0 start page is displayed.

    LAN:

    1Connect the Fronius Datamanager and computer with a LAN cable.
    2Place the Fronius Datamanager 2.0 IP switch in the "A" position.
    3In the browser's address bar, enter the IP address http://169.254.0.180 and confirm.
    1. Commissioning
    2. Fronius SnapINverter

    Configure Fronius Smart Meter as primary meter

    link_horizontalLink copied
    1Call up the Fronius Datamanager 2.0 website.
    - Open web browser.
    - In the browser's address bar, enter the IP address (IP address for WLAN: 192.168.250.181, IP address for LAN: 169.254.0.180) or enter and confirm the host and domain name of the Fronius Datamanager 2.0.
    - The Fronius Datamanager 2.0 website appears.
    2Click on the Settings button.
    3Log in to the login area with user Service and the service password.
    4Call up the Meter menu area.
    5Select the primary meter from the drop-down list.
    6Click on the Settings button.
    7Set the meter position of the meter (feed-in point or consumption point) in the pop-up window. For more information on the position of the Fronius Smart Meter, see Positioning on page (→).
    8Set the converter ratio and the network type.
    9Click the OK button when the status OK is displayed. If the timeout status is displayed, repeat the operation.
    10Click on the button    to save the settings.

    The Fronius Smart Meter is configured as a primary meter.

    In the menu area Current Total View, the power of the PV modules, the self-consumption, the grid power feed and battery charging (if available) are displayed.

    1. Commissioning
    2. Fronius SnapINverter

    Configure Fronius Smart Meter as a secondary meter

    link_horizontalLink copied
    1Call up the Fronius Datamanager 2.0 website.
    - Open web browser.
    - In the browser's address bar, enter the IP address (IP address for WLAN: 192.168.250.181, IP address for LAN: 169.254.0.180) or enter and confirm the host and domain name of the Fronius Datamanager 2.0.
    - The Fronius Datamanager 2.0 website appears.
    2Click on the Settings button.
    3Log in to the login area with user Service and the service password.
    4Call up the Meter menu area.
    5Select the secondary meter from the drop-down list.
    6Click on the Add button.
    7Enter the name of the secondary meter in the Name input field.
    8Enter the previously assigned address in the Modbus address input field.
    9Set the converter ratio and the network type.
    10Complete the description of the meter.
    11Click on the button    to save the settings.

    The Fronius Smart Meter is configured as a secondary meter.

    1. Commissioning

    Fronius GEN24 inverter

    link_horizontalLink copied

    General

    IMPORTANT! Settings in the "Device configuration" menu item may only be entered by staff trained to do so!

    The service password must be entered for the "Device configuration" menu item.

    Three-phase or one-phase Fronius Smart Meters may be used. In both cases, selection is made via the "Components" menu area. The meter type is determined automatically.

    One primary meter and several secondary meters can be selected. The primary meter must be configured before a secondary meter can be chosen.

    1. Commissioning
    2. Fronius GEN24 inverter

    General

    link_horizontalLink copied

    IMPORTANT! Settings in the "Device configuration" menu item may only be entered by staff trained to do so!

    The service password must be entered for the "Device configuration" menu item.

    Three-phase or one-phase Fronius Smart Meters may be used. In both cases, selection is made via the "Components" menu area. The meter type is determined automatically.

    One primary meter and several secondary meters can be selected. The primary meter must be configured before a secondary meter can be chosen.

    1. Commissioning
    2. Fronius GEN24 inverter

    Installation with the browser

    link_horizontalLink copied

    The network wizard and product setup can be performed independently. A network connection is required for the Fronius Solar.web installation wizard.

    WiFi:

    1Open the access point by touching the sensor    .
    ✓Communication LED flashes blue.
    2Establish the connection to the inverter in the network settings (the inverter is displayed with the name "FRONIUS_" and the serial number of the device).
    3Enter the password from the rating plate and confirm.
    IMPORTANT!
    To enter the password, first select the Connect using a security key instead link in order to establish the connection with the password.
    4Enter the IP address 192.168.250.181 in the address bar of the browser and confirm. The installation wizard opens.
    5Follow the installation wizard and complete the installation in the individual areas.
    6Add the system components in Fronius Solar.web and commission the PV system.

    Ethernet:

    1Establish a connection to the inverter (LAN1) using a network cable (min. CAT5 STP).
    2Open the access point by touching the sensor once    .
    ✓Communication LED flashes blue.
    3Enter the IP address 169.254.0.180 in the address bar of the browser and confirm. The installation wizard opens.
    4Follow the installation wizard and complete the installation in the individual areas.
    5Add the system components in Fronius Solar.web and commission the PV system.
    1. Commissioning
    2. Fronius GEN24 inverter

    Configure Fronius Smart Meter as primary meter

    link_horizontalLink copied
    1Call up the website of the inverter.
    - Open web browser.
    - In the browser's address bar, enter the IP address (IP address for WLAN: 192.168.250.181, IP address for LAN: 169.254.0.180) or enter and confirm the host and domain name of the inverter.
    - The website of the inverter is displayed.
    2Click on the Device configuration button.
    3Log in to the login area with user Technician and the technician password.
    4Call up the Components menu area.
    5Click on the Add components button.
    6Set the position of the meter (feed-in point or consumption point) in the Position drop-down list. For more information on the position of the Fronius Smart Meter, see Positioning on page (→).
    7Set the converter ratio and the network type.
    8Click on the Add button.
    9Click the Save button to save the settings.

    The Fronius Smart Meter is configured as a primary meter.

    1. Commissioning
    2. Fronius GEN24 inverter

    Configure Fronius Smart Meter as a secondary meter

    link_horizontalLink copied
    1Call up the website of the inverter.
    - Open web browser.
    - In the browser's address bar, enter the IP address (IP address for WLAN: 192.168.250.181, IP address for LAN: 169.254.0.180) or enter and confirm the host and domain name of the inverter.
    - The website of the inverter is displayed.
    2Click on the Device configuration button.
    3Log in to the login area with user Technician and the technician password.
    4Call up the Components menu area.
    5Click on the Add components button.
    6Select the meter type (generator meter/load meter) in the Position drop-down list.
    7Enter the previously assigned address in the Modbus address input field.
    8Enter the name of the meter in the Name input field.
    9Set the converter ratio and the network type.
    10Select the category (generator or load) in the Category drop-down list.
    11Click on the Add button.
    12Click the Save button to save the settings.

    The Fronius Smart Meter is configured as a secondary meter.

    Operation

    link_horizontalLink copied

    Power Status LEDs

    The three status LEDs on the front of the Fronius Smart Meter can help indicate correct measurements and operation. The “L1”, “L2”, and “L3” on the diagrams indicate the three phases:

    Normal Startup
    The Fronius Smart Meter displays the following startup sequence whenever power is first applied.

    Consuming Power
    Any phase with the LEDs flashing green is indicating normal positive power (Import of energy from public grid).
    If the inverter or any other power source is not producing power and some minimal power is being used, the LEDs should be flashing green. This is normal, when the inverter is in its 5 minute startup cycle.

    No Power
    Any phase with a solid green LED indicates no power, but line voltage is present.

    No Voltage
    Any phase LED that is off indicates no voltage on that phase.

    Generating Power
    Red flashing indicates negative power for that phase. This is a normal behavior if more power is produced (by the inverter or any other power source) than consumed (Export of energy to the public grid). If no power is produced at all, this might indicate either reversed CT's, swapped CT wires or CT's are not matched with the correct line voltage phase.

    Overvoltage Warning
    The following indicates that the line voltage is too high for this model. Disconnect power immediately! Check the line voltages and the meter ratings (in the white box on the label).

    Meter Not Operating
    If none of the LEDs are illuminated, check that the correct line voltages are applied to the meter. If the voltages are correct, call customer service for assistance.

    Error
    If the meter experiences an internal error, all LEDs will light up red for 3 or more seconds. If you see this happen repeatedly, call customer service for assistance.

    1. Operation

    Power Status LEDs

    link_horizontalLink copied

    The three status LEDs on the front of the Fronius Smart Meter can help indicate correct measurements and operation. The “L1”, “L2”, and “L3” on the diagrams indicate the three phases:

    Normal Startup
    The Fronius Smart Meter displays the following startup sequence whenever power is first applied.

    Consuming Power
    Any phase with the LEDs flashing green is indicating normal positive power (Import of energy from public grid).
    If the inverter or any other power source is not producing power and some minimal power is being used, the LEDs should be flashing green. This is normal, when the inverter is in its 5 minute startup cycle.

    No Power
    Any phase with a solid green LED indicates no power, but line voltage is present.

    No Voltage
    Any phase LED that is off indicates no voltage on that phase.

    Generating Power
    Red flashing indicates negative power for that phase. This is a normal behavior if more power is produced (by the inverter or any other power source) than consumed (Export of energy to the public grid). If no power is produced at all, this might indicate either reversed CT's, swapped CT wires or CT's are not matched with the correct line voltage phase.

    Overvoltage Warning
    The following indicates that the line voltage is too high for this model. Disconnect power immediately! Check the line voltages and the meter ratings (in the white box on the label).

    Meter Not Operating
    If none of the LEDs are illuminated, check that the correct line voltages are applied to the meter. If the voltages are correct, call customer service for assistance.

    Error
    If the meter experiences an internal error, all LEDs will light up red for 3 or more seconds. If you see this happen repeatedly, call customer service for assistance.

    1. Operation

    Modbus Communication LEDs

    link_horizontalLink copied

    Near the upper left corner, there is a diagnostic Com (communication) LED that can indicate the following:

    A short green flash indicates a valid packet addressed to this device.

    Short yellow flashes or rapid flashing indicate valid packets addressed to different devices.

    A one-second red flash indicates an invalid packet: bad baud rate, bad CRC, noise, bad parity, etc.

    Rapid red/yellow flashing indicates a possible address conflict (two devices with the same DIP switch address).

    Solid red indicates the address is set to zero: an invalid choice.

    Technical data

    link_horizontalLink copied

    Accuracy

    Normal Operation
    Line voltage: 90 - 347 Vac (Line to Neutral), 120 - 600 Vac (Line to Line)
    Power factor: 1.0
    Frequency: 45 - 65 Hz
    Ambient Temperature: 23° C ± 5° C
    CT Current: 5% - 100% of rated current
    Accuracy: ± 0.5% of reading

    1. Technical data

    Accuracy

    link_horizontalLink copied

    Normal Operation
    Line voltage: 90 - 347 Vac (Line to Neutral), 120 - 600 Vac (Line to Line)
    Power factor: 1.0
    Frequency: 45 - 65 Hz
    Ambient Temperature: 23° C ± 5° C
    CT Current: 5% - 100% of rated current
    Accuracy: ± 0.5% of reading

    1. Technical data

    Measurement

    link_horizontalLink copied

    Update Rate: 0.1 second. Internally, all measurements are performed at this rate.
    Startup Time: ~1.0 second. The Fronius Smart Meter starts communicating this long after AC voltage is applied. Energy measurement starts 50-100 milliseconds after AC is applied.
    Default CT Phase Angle Correction: 0.0 degrees.

    1. Technical data

    Models and Electrical

    link_horizontalLink copied

    Meter Service Type

    Nominal Vac
    Line-to-Neutral

    Nominal Vac
    Line-to-Line

    Phases

    Wires

    WR

    90-347

    120-600

    1 - 3

    2 - 4

    The Fronius Smart Meter has an optional neutral connection that may be used for measuring wye circuits. In the absence of neutral, voltages are measured with respect to ground. The Fronius Smart Meter uses the phase L1 (øA) and phase L2 (øB) connections for power.

    Over-Voltage Limit: 125% of nominal Vac. Extended over-voltage operation can damage the Fronius Smart Meter and void the warranty.
    Over-Current Limit: 120% of rated current. Exceeding 120% of rated current will not harm the Fronius Smart Meter but the current and power will not be measured accurately.
    Maximum Surge: 4 kV according to EN 61000-4-5

    Power Consumption:

    Operating Frequencies: 50 / 60 Hz
    Measurement Category: CAT III
    Measurement category III is for measurements performed in the building installation. Examples are measurements on distribution boards, circuit breakers, wiring, including cables, bus bars, junction boxes, switches, socket outlets in the fixed installation, and equipment for industrial use and some other equipment, for example, stationary motors with permanent connection to the fixed installation.

    The line voltage measurement terminals on the meter are rated for the following CAT III voltages (these ratings appear on the front label):

    Meter Service Type

    CAT III Voltage Rating

    WR

    600

    Current Transformer Inputs:
    Nominal Input Voltage (At CT Rated Current): 0.33333 Vac RMS
    Absolute Maximum Input Voltage: 5.0 Vac RMS
    Input Impedance at 50/60 Hz: 23 k Ohm

    1. Technical data

    Certifications

    link_horizontalLink copied
    EMC
    • EN55011:2007, CISPR 11:2009- Class B
    • FCC Part 15 - Class B
    • EN 61326-1:2012, includes:
      • Harmonics: IEC 61000-3-2
      • Flicker: IEC 61000-3-3
      • Electrostatic Discharge: IEC 61000-4-2
      • Radiated RF Immunity: IEC 61000-4-3
      • Electrical Fast Transient / Burst: IEC 61000-4-4
      • Surge Immunity: IEC 61000-4-5
      • Conducted RF Immunity: IEC 61000-4-6
      • Power Frequency H-Field: IEC 61000-4-8
      • Voltage Dips, Interrupts: IEC 61000-4-11
    Safety
    • UL 61010-1
    • CAN/CSA-C22.2 No. 61010-1-12
    • IEC 61010-2
    1. Technical data

    Environmental

    link_horizontalLink copied

    Operating Temperature: -40° C to +80° C (-40° F to 176° F)
    Altitude: Up to 3000 m (9842 ft)
    Operating Humidity: non-condensing, 5 to 90% relative humidity (RH) up to 40°C, decreasing linearly to 50% RH at 55°C
    Pollution:
    POLLUTION DEGREE 2 - Normally only non-conductive pollution; occasionally, a temporary conductivity caused by condensation must be expected.
    Indoor Use: Suitable for indoor use
    Outdoor Use: Suitable for outdoor use if mounted inside an electrical enclosure (Hammond Mfg., Type EJ Series) rated NEMA 3R or 4 (IP 66).

    1. Technical data

    Warranty

    link_horizontalLink copied

    Detailed warranty conditions specific to your country can be found at https://www.fronius.com/en/download-center?searchword=Warranty+conditions .

    If there is a warranty for the relevant product, register the product at https://warranty.fronius.com/ and activate or extend the warranty.