Incorrect operation or misuse
IMPORTANT!
IMPORTANT!
All safety and danger notices on the device:Tampered-with and non-functioning protection devices
The device may be damaged
Technical data, labels, and safety symbols are located on the Fronius Smart Meter IP 5kA-3. This information must be kept in a legible condition and must not be removed, covered, pasted over, or painted over. The notices and symbols warn against incorrect operation, which may result in serious injury and property damage.
Symbols on the rating plate: | ||
| CE label – confirms compliance with applicable EU directives and regulations. The product has been tested by a specific notified body. | |
| WEEE marking – waste electrical and electronic equipment must be collected separately and recycled in an environmentally sound manner in accordance with the European Directive and national law. | |
| UKCA marking – confirms compliance with applicable UK directives and regulations. | |
| RCM marking – tested according to the requirements of Australia and New Zealand. | |
Application notes
Software
Example: Click Save.
Instructions for action
This document provides detailed information and instructions to ensure that all users can use the device safely and efficiently.
The Fronius Smart Meter IP 5kA-3 is a bidirectional electricity meter which optimizes self-consumption and records a household's load curve. The Fronius Smart Meter IP 5kA-3 provides an overview of a user's own power consumption in conjunction with a Fronius inverter or Fronius Datamanager 2.0 and a Fronius data interface.
The meter measures the energy flow to the loads or to the public grid and forwards the information via the Modbus RTU/RS485- or TCP interface (LAN/WLAN) to the Fronius inverter or the Fronius Datamanager 2.0.
The Fronius Smart Meter IP 5kA-3 is a fixed piece of equipment for public grids of TN/TT systems and may only be used to measure loads and self-consumption.
The Fronius Smart Meter IP 5kA-3 is required for systems with a battery storage system and/or a Fronius Ohmpilot installed for communication between the individual components.
The installation is carried out on an indoor DIN rail with corresponding back-up fuses, which are adapted to the cable cross-sections of the copper conductors and to the maximum current of the meter. The Fronius Smart Meter IP 5kA-3 must only be operated in accordance with the specifications in the enclosed documentation and in accordance with local laws, regulations, provisions, standards, and within the limits of technical possibilities. Any use of the product other than as described in the intended use shall be deemed to be not in accordance with the intended purpose.
The available documentation forms part of the product and must be read, observed, and kept in good condition. It must also be accessible at all times at the place of installation. Fronius International GmbH assumes no responsibility for compliance with or non-compliance with these laws or regulations in connection with the installation of the product.
| (1) | Fronius Smart Meter IP 5kA-3 |
| (2) | Quick Start Guide |
The Smart Meter can be installed in the following positions in the system:
Positioning at the feed-in point
Positioning at the consumption point
The Fronius Smart Meter IP 5kA-3 has accuracy class 1 when measuring active energy (EN IEC 62053-21) in the voltage ranges 208-480 VLL and 100-240 VLN. For further details see Technical data.
The Fronius Smart Meter IP 5kA-3 can be used with Modbus RTU/TCP data cabling in backup power mode. In the case of Modbus TCP data cabling, it should be noted that reconnection to the public grid requires more time because the data network (e.g., network router/switch) is restarted. Fronius recommends a data connection via Modbus RTU.
| (1) | Voltage transformer connection area |
| (2) | LAN port |
| (3) | DIP switch
| (4) | Modbus RTU connection area |
| (5) | LED indicators |
| (6) | WLAN access point and reset function button
| (7) | QR code to start the Setup wizard |
| (8) | AC connection area |
| (2) | LAN port |
| (3) | DIP switch
The LED status indicators show the operating status and data connection of the Fronius Smart Meter IP 5kA-3.
| (3) | Link 1 LED Steady green: Data connection established with the network |
| (4) | Link 2 LED Lights up red: No data connection Flashing red: Open WLAN access point |
| (5) | WLAN LED Flashing green: WLAN connection is being established Lights up green: WLAN connection is active |
Please note the following criteria when choosing a location for the Smart Meter:
Only install on a solid, non-flammable surface.
When installing the Smart Meter in a switch cabinet or similar enclosure, make sure that it is of the appropriate safety class and that the hot air that develops will be dissipated by forced-air ventilation.
The Smart Meter is suitable for indoor installation. | ||
The Smart Meter must not be installed or used at altitudes above 2,000 m. | ||
The Fronius Smart Meter IP 5kA-3 can be mounted on a 35 mm DIN rail.
The Fronius Smart Meter IP 5kA-3 is a hard-wired device and requires a disconnecting device (automatic circuit breaker).
The Fronius Smart Meter IP 5kA-3 consumes 30 mA, the nominal capacity of the disconnecting devices and the overcurrent protection is determined by the conductor cross-sections, the mains voltage, and the required breaking capacity.
Disconnecting device for the mains terminals
The automatic circuit breaker must protect the mains terminals marked L1, L2, and L3. In rare cases, the neutral conductor has a disconnecting device, which must interrupt both neutral and non-earthed cables concurrently.
Danger from live mains voltage inputs
Switch off the power supply before connecting the mains voltage inputs.
Each live conductor must be connected to the AC terminals as shown in the figures below.
It is recommended to use Fronius CT current transformers (item numbers 41,0010,0104 / 41,0010,0105 / 41,0010,0232). In order to ensure problem-free operation of the Fronius Smart Meter IP 5kA-3 and accurate measurement results, all connected current transformers must meet these requirements:
Danger of electric shock due to unintentional opening of folding current transformers
This can result in severe injury and damage to property.
Switch off the power when working on the current transformers.
Attach plastic cable ties to the current transformer to prevent unintentional opening.
Observe direction information when installing the current transformers
Negative power values occur when the current transformers are connected incorrectly.
Observe the data sheet and the marking on the current transformer (arrow indicates the direction to the load or to the public grid)
Check the correct position of the black and white cable.
Danger from mains voltage
Switch off the power supply before disconnecting live conductors.
Cable length of the current transformers
Cables that are too long can have a negative effect on the measuring accuracy.
If a cable extension is necessary, use a shielded 0.34 to 1.5 mm2 (AWG 22-16) CAT 5 STP (Shielded Twisted Pair) cable rated for 300 V or 600 V (higher than the operating voltage).
Unusual measured values on unused phases
If unusual measured values occur on unused phases, bypass the unused current transformer inputs.
To do so, for each unused current transformer, connect the terminal marked with a white dot to the terminal marked with a black dot using a short cable.
IMPORTANT!
Ensure sufficient WLAN signal strength at the installation site. If the signal strength is low, a WLAN booster must be installed, for example.
The use of a static IP address is recommended.
Connect the data communication connections of the Fronius Smart Meter IP to the Modbus interface of the Fronius inverter using a CAT 5 STP (Shielded Twisted Pair) or higher data cable.
The Fronius Smart Meter IP can also be connected to the network (LAN / WLAN). This allows software updates to be carried out.
Standard Modbus address & TCP port:To avoid interference, the terminating resistor must be used (see chapter Setting the Modbus RTU terminating resistor on page (→)).
If a battery is installed in the system, the BIAS switch must be set (see chapter Setting the Modbus RTU BIAS on page (→)).
Further settings are necessary on the user interface of the inverter and the Fronius Smart Meter IP (see Advanced settings).
IMPORTANT!
A loose wire can disable an entire area of the network. The data communication connections of the Fronius Smart Meter IP are electrically isolated from hazardous voltages.
Inverter in the system | |
Meter - Fronius Smart Meter IP | |
Fronius or third-party device, connection via Modbus TRU | |
Terminating resistor |
The terminating resistor is integrated in the Fronius Smart Meter IP and is set by a switch.
For information on whether the terminating resistor must be set or not, see chapter Terminating resistors on page (→).
Due to interference, it is recommended that terminating resistors are used as illustrated below to ensure proper functioning.
If the Smart Meter is connected to the same Modbus interface (MB0 or MB1) as the battery, the BIAS switch must be set to ON.
It is recommended to activate the Automatic Updates function during commissioning. The Fronius Smart Meter IP checks for available updates daily and automatically installs them between midnight and 6 am. A precise time can be set.
If this function is not activated, software updates can also be searched for and started manually on the user interface of the device.
The software of the Fronius Smart Meter IP is compatible with the following software versions of connected Fronius components:
IMPORTANT! Settings under the "Meter" menu item are only to be made by trained and qualified personnel!
The service password must be entered in order to access the "Meter" menu item.
The meter is selected in the Fronius Smart Meter menu item. The Fronius Datamanager 2.0 automatically identifies the meter type.
A primary meter and several secondary meters can be selected. The primary meter needs to be configured first before a secondary meter can be selected.
The Fronius Smart Meter IP can be connected with Modbus TCP or Modbus RTU.
Access Point:
LAN:
The Fronius Smart Meter IP is configured as the primary meter.
The Current general view menu area displays the power of the PV modules, self-consumption, the energy fed into the grid, and the battery charge (if available).
The Fronius Smart Meter IP is configured as a secondary meter.
Modbus RTU: A maximum of 4 Modbus stations can be connected to the Modbus terminal.
Modbus TCP: Fronius recommends using a maximum of 7 secondary meters in the system.
IMPORTANT!
Only one primary meter, one battery, and one Ohmpilot can be connected per inverter. Due to the high data transfer of the battery, the battery occupies two participants.
Example:
Input | Battery | Fronius | Number | Number |
Modbus | 1 | 0 | ||
1 | 1 | |||
1 | 2 | |||
1 | 3 |
Grid | |
Utility meter | |
Primary meter | |
Secondary meter | |
Modbus RTU, Third-party device | |
Loads in the system | |
Additional loads in the system | |
Additional producers in the system | |
If several Fronius Smart Meters are installed, a separate address must be set for each one. The primary meter always receives the address 1. All other meters are numbered consecutively in the address range from 2 to 14. Different Fronius Smart Meter power categories can be used together.
IMPORTANT!
Use no more than 3 secondary meters in the system. To avoid interference, it is recommended to install the terminating resistors according to the chapter Terminating resistors.
IMPORTANT! Settings under the Device configuration menu item are only to be made by trained and qualified personnel!
The technician password must be entered in order to access the Device configuration menu item.
The Fronius Smart Meter IP can be operated in single-, two-, and three-phase mode. In all cases, the selection is made under the Components menu area. The meter type is determined automatically.
WLAN:
Ethernet:
Modbus RTU: The inputs M0 and M1 can be selected for this purpose. A maximum of 4 Modbus participants each can be connected to the Modbus terminal at inputs M0 and M1.
Modbus TCP: A maximum of 7 secondary meters can be used in the system.
IMPORTANT!
Only one primary meter, one battery, and one Ohmpilot can be connected per inverter. Due to the high data transfer of the battery, the battery occupies 2 participants.
Example 1:
Modbus 0 | 0 | 4 | ||
0 | 2 | |||
0 | 1 | |||
Modbus 1 | 1 | 3 |
Example 2:
Modbus 0 | 1 | 3 | ||
Modbus 1 | 0 | 4 | ||
0 | 2 | |||
0 | 1 |
Grid | |
Utility meter | |
Primary meter | |
Secondary meter | |
IMPORTANT!
Use no more than 7 secondary meters in the system. Data connection via RTU and TCP is possible. To avoid interference, it is recommended to install the terminating resistors according to the chapter Setting the Modbus RTU terminating resistor.
| Measurement data and connections | |
| Language | |
| Change password Password guidelines
If the password has been forgotten, the Smart Meter must be reset (see chapter Restoring the factory settings on page (→). | |
| Advanced settings | |
| Info | |
| Logout |
| Language | |
| Info | |
| Logout |
| Language | |
| Info | |
| Logout |
Network The WLAN or LAN connection can be configured here. The use of a static IP address is recommended. | |
Meter values Here all values can be set to 0 or meter values can be corrected manually. The input current of the current transformers can be changed, see Changing the input current of the current transformers on page (→). | |
Software update Software update settings can be made here. It is possible to configure an automatic update. | |
Data interfaces Several data interfaces can be used simultaneously. Detailed views - Entering the login data is required.
Single-phase/multiphase The connection type of the Fronius Smart Meter IP can be selected here. | |
Restart device Click on Restart device to restart the Fronius Smart Meter IP. |
Press and hold the WLAN access point and reset button for 20 seconds to reset the Fronius Smart Meter IP 5kA-3 to factory settings.
Maintenance and service work may only be carried out by a trained technician.
Clean the Fronius Smart Meter as required with a damp cloth.
Do not use cleaning agents, abrasives solvents, or similar to clean the Smart Meter.
Packaging materialsDetailed warranty conditions specific to your country can be found at www.fronius.com/solar/garantie .
To secure the full warranty period for the newly installed Fronius product, it is necessary to register at www.solarweb.com .
Measurement input | |
Nominal voltage (3-phase) incl. tolerance | 208 - 480 V |
Nominal voltage (1-phase) incl. tolerance | 100 - 240 V |
Self-consumption | 30 mA |
Rated frequency | 50 - 60 Hz |
Maximum current, Imax | 5000 A |
Short-time overload | 3x Imax / 20 s |
Self-consumption (max. current) | max. 5 W |
Current distortion factor | according to EN IEC 62053-21 |
Power factor | active cosφ 0.5 ind - 0.8 cap, |
Current transformer (kCT) | 1 - 5000 Only use Rogowski coils with integrators. Failure to use integrators will result in erroneous measurement results. |
Energy | |
Active energy accuracy | Class 1 |
Reactive energy accuracy | Class 2 |
Response time after switching on | < 5 s |
Output | |
RS485 communication | |
Standard | RS485 - 3 conductors |
Transfer | serial, asynchronous |
Protocol | Modbus RTU |
Addresses | 1 - 255 |
Bit count | 8 |
Stop bit | 1 |
Parity bit | none - even - odd |
Baud rate (Modbus transmission speed) | 9600 bit/s |
Response time | ≤ 200 ms |
WiFi | |
Frequency range | 2412 - 2472 MHz |
Channels used | Channel: 1-13 b,g,n HT20 |
Power | <18 dBm |
Modulation | 802.11b: DSSS (1Mbps DBPSK, 2Mbps DQPSK, 5.5/11Mbps CCK) |
Insulation (EN IEC 62052-11, EN IEC 62053-21) | |
Installation category | II |
Pollution degree | PD2 |
Insulation voltage | 4 kV RMS |
Surge withstand capability | 4 kV 1.2/60 µs |
Test voltage | 2.5 kV RMS. 50 Hz/1 min |
Test voltage | 4 kV RMS. 50 Hz/1 min |
Electromagnetic compatibility | |
Test standard | Test according to EN IEC 62052-11 |
Environmental conditions | |
Reference temperature | 25 °C (± 5 °C) |
Operating range | -25 to +55 °C |
Limit temperature for storage and transport | -30 to +80 °C |
Max. humidity | 93% |
Max. power loss (for thermal dimensioning of the switch cabinet) | ≤ 6 W |
Overvoltage category | III |
Housing | |
Housing | 3 modules according to DIN 43880 |
Connection | Spring-type terminals |
Mounting | 35 mm DIN rail |
Housing material | PA-765 UL |
Protection class (EN 60529) | IP20 housing, IP30 connections |
Weight | 132 grams |
Terminals | |
Voltage input | |
Wire | min. 1.5 mm² / max. 4 mm² |
Data output and current transformer input | |
Wire | min. 0.25 mm² / max. 2.5 mm² |
Energy | |
Output | |
Bit count | 8 |
Stop bit | 1 |
WiFi | |
Power | <18 dBm |
Housing | |
Terminals | |
Voltage input | |