Indicates a situation where damage could occur.
If you see any of the symbols depicted in the "Safety rules" chapter, special care is required.
Danger from crushing due to the incorrect handling of attachments and connection parts.
Injuries to limbs may result.
When lifting up, putting down and attaching the inverter, use the integrated grips.
When fitting attachments, ensure that no limbs are located between the attachment and the inverter.
Do not hold onto the individual poles on the terminals when locking and unlocking.
In addition to the Operating Instructions, all applicable local rules and regulations regarding accident prevention and environmental protection must also be followed.
All safety and danger notices on the device:Any safety devices that are not fully functional must be repaired by an authorized specialist before the device is switched on.
For the location of the safety and danger notices on the device, refer to the chapter headed "Warning notices on the device" in the Operating Instructions for your device.
Faults that could compromise safety must be remedied before switching on the device.
The servicing information contained in these operating instructions is intended only for the use of qualified service engineers. An electric shock can be fatal. Do not carry out any actions other than those described in the documentation. This also applies to qualified personnel.
All cables and leads must be secured, undamaged, insulated and adequately dimensioned. Loose connections, scorched, damaged or inadequately dimensioned cables and leads must be immediately repaired by authorised personnel.
Maintenance and repair work must only be carried out by an authorised specialist.
It is impossible to guarantee that bought-in parts are designed and manufactured to meet the demands made on them, or that they satisfy safety requirements. Use only original spare parts (also applies to standard parts).
Components that are not in perfect condition must be changed immediately.
The sound power level of the inverter is specified in the Technical data.
The device is cooled as quietly as possible with the aid of an electronic temperature control system; this depends on the amount of converted power, the ambient temperature, the level of soiling of the device, etc.
It is not possible to provide a workplace-related emission value for this device because the actual sound pressure level is heavily influenced by the installation situation, the grid quality, the surrounding walls and the properties of the room in general.
In certain cases, even though a device complies with the standard limit values for emissions, it may affect the application area for which it was designed (e.g., when there is equipment that is susceptible to interference at the same location, or if the site where the device is installed is close to either radio or television receivers). If this is the case, then the operator is obliged to take action to rectify the situation.
This system has backup power functions, which enable a replacement power supply to be established in the event of a failure of the public grid.
Where an automatic backup power supply is installed, a backup power warning notice (https://www.fronius.com/en/search-page, item number: 42,0409,0275) must be fitted on the electrical distributor.
Maintenance and installation work in the home network requires both disconnection on the utility side and deactivation of the replacement power mode by opening the integrated DC disconnector on the inverter.
The function of the residual current devices for the backup power supply must be checked at regular intervals (according to the manufacturer's instructions), but at least twice a year.
A description on how to perform the test operation can be found in the backup power checklist (https://www.fronius.com/en/search-page, item number: 42,0426,0365).
Depending on the insolation conditions and the battery state of charge, the backup power supply is automatically deactivated and activated. This can cause the backup power supply to unexpectedly return from standby mode. Therefore, installation work can only be performed on the home network when the backup power supply is deactivated.
Influencing factors on the total power in backup power mode:
Reactive power
Electrical loads with a power factor not equal to 1 also require reactive power in addition to effective power. The reactive power also loads the inverter. Therefore, to correctly calculate the actual total power, it is not the rated power of the load that is relevant, but the current caused by effective and reactive power.
Devices with a high reactive power are mainly electric motors such as:
High starting current
Electrical loads that need to accelerate a large mass usually require a high starting current. This can be up to 10 times higher than the nominal current. The maximum current of the inverter is available for the starting current. Loads with too high starting currents therefore cannot be started/operated, even though the nominal power of the inverter suggests that they can. When dimensioning the backup power circuit, the connected load power and any starting current must also be taken into account.
Devices with high starting currents are, for example:
IMPORTANT!
Very high starting currents can cause short-term distortion or a drop in output voltage. The simultaneous operation of electronic devices in the same backup power supply system should be avoided.
Load imbalance
When dimensioning three-phase backup power networks, the total output power and the power output per phase of the inverter must be taken into account.
IMPORTANT!
The inverter may only be operated within the limits of its technical capabilities. Operation outside of its technical capabilities can cause the inverter to shut down.
Connection of a point in the device, system or installation to earth to protect against electric shock in the event of a fault. When installing a safety class 1 inverter (see Technical data), the ground conductor connection is required.
When connecting the ground conductor, ensure that it is secured against accidental disconnection. All the points listed in Connecting the inverter to the public grid (AC side) on page (→) must be observed. When using cable glands, ensure that the ground conductor will be strained last in the event of failure of the cable gland. When connecting the ground conductor, the minimum cross-section requirements specified by the respective national standards and guidelines must be observed.
The inverter transforms the direct current generated by the solar modules into alternating current. This alternating current is fed into the public grid and synchronized with the grid voltage in use. Moreover, the solar energy can also be stored in a connected battery for later use.
The inverter is intended for use in grid-connected photovoltaic systems. The inverter has backup power functions and switches to backup power mode if it has been wired accordingly*.
The inverter automatically monitors the public grid. Whenever conditions in the electric grid are inconsistent with standard conditions (for example, grid switch-off, interruption), the inverter will immediately stop producing power and interrupt the supply of power into the grid.
The grid is monitored by monitoring the voltage, frequency and islanding conditions.
After installation and commissioning, the inverter's operation is fully automatic; the inverter draws the maximum possible power from the PV modules.
Depending on the operating point, this power is used in the home, stored in a battery* or fed into the grid.
As soon as the energy provided by the PV modules is no longer sufficient, the power from the battery is fed into the home. Depending on the setting, power may also be obtained from the public grid in order to charge the battery*.
When its temperature gets too high, the inverter automatically reduces the output or charging power, or switches off completely, in order to protect itself.
Reasons for the temperature being too high include a high ambient temperature or insufficient heat dissipation (for example, inadequate heat dissipation when installed in switch cabinets).
* | Depending on the device variant, suitable battery, appropriate wiring, settings and local standards and guidelines. |
Function | Symo GEN24 SC | Symo GEN24 Plus SC |
Backup power variant - PV Point (OP) | ||
Battery connection* | Available as an option** | |
Backup power variant - Full Backup | Available as an option** |
* | For suitable batteries, see chapter Suitable batteries. |
** | The functions are optionally available via Fronius UP (see chapter Fronius UP). |
With Fronius UP*, the inverter can be expanded by the authorised specialist to include optionally available functions (see chapter Function overview).
* | The availability of Fronius UP varies from country to country. For more information on Fronius UP and availability, see Installation guide: Fronius GEN24 & GEN24 Plus. |
(1) | Housing cover |
(2) | Inverter |
(3) | Mounting bracket (illustration) |
(4) | Quick Start guide |
(5) | 2x ferrite ring with holder |
The manufacturer is not responsible for any damage resulting from improper use.
All warranty claims are considered void in such cases.
When designing the photovoltaic system, ensure that all components of the photovoltaic system are operated exclusively within their permissible operating range.
Take into account the grid operator's regulations for energy fed into the grid and connection methods.
* | Depending on the device variant, suitable battery, appropriate wiring, settings, and local standards and guidelines. |
Ambient air is drawn in by the fan on the front side and blown out at the device sides. The even heat dissipation allows several inverters to be installed next to each other.
Risk due to insufficient cooling of the inverter.
This may result in a loss of power in the inverter.
Do not block the fan (for example, with objects that protrude through the touch guard).
Do not cover the ventilation slots, even partially.
Make sure that the ambient air can always flow through the inverter's ventilation slots unimpeded.
With Fronius Solar.web or Fronius Solar.web Premium, the PV system can be easily monitored and analysed by the system owner and installer. If configured accordingly, the inverter transmits data such as power, yields, load, and energy balance to Fronius Solar.web. For more information see Solar.web - monitoring & analysis.
Configuration is carried out via the setup wizard, see chapter Installation with the app on page (→) or Installation using the web browser on page (→).
Prerequisites for configuration:* | The information given does not constitute an absolute guarantee of faultless function. High error rates in the transmission, reception fluctuations or transmission drop-outs can have a negative effect on the data transfer. Fronius recommends testing the Internet connection on site according to the minimum requirements. |
The inverter can be found via the Multicast DNS protocol (mDNS). It is recommended to search for the inverter by the assigned host name.
The following data can be retrieved via mDNS:PV module | ||
Fronius GEN24 inverter | ||
Additional inverter in the system | ||
Battery | ||
Fronius Ohmpilot | ||
Primary meter | ||
Secondary meter | ||
Loads in the system | ||
Additional loads and producers in the system | ||
PV Point | ||
Full Backup | ||
Grid |
PV module | ||
Battery | ||
Primary meter | ||
PV Point | ||
Full Backup | ||
Grid |
In order to be able to obtain the highest rate of self-consumption with your PV system, a battery can be used to store excess energy. The battery is coupled to the inverter on the direct current side. Multiple current conversion is therefore not required, and the efficiency is increased.
IMPORTANT!
In backup power mode, an increased nominal frequency is used in order to prevent undesired parallel operation with other power generators.
IMPORTANT!
In the fully equipped hybrid PV system with a Fronius Ohmpilot, the Ohmpilot cannot be operated in the event of a power failure for regulatory reasons. It is therefore sensible to install the Ohmpilot outside of the backup power branch.
In the hybrid photovoltaic system, batteries must only be connected to one inverter with battery support. Batteries cannot be split between multiple inverters with battery support. However, depending on the battery manufacturer, several batteries can be combined on one inverter.
In the case of hybrid inverters, there are four different energy flow directions:
(1) | PV module – inverter – load/grid |
(2) | PV module – inverter – battery* |
(3) | Battery – inverter – load/grid* |
(4) | Grid – inverter – battery* |
* depending on the settings and local standards and regulations.
Battery systems distinguish different operating states. In this case, the relevant current operating state is displayed on the user interface of the inverter or in Solar.web.
Operating state | Description |
Normal operation | Energy is stored or drawn, as required. |
Min. state of charge (SOC) achieved | Battery has reached the minimum SOC set or specified by the manufacturer. The battery cannot be discharged any further. |
Energy saving mode (standby) | The system has been put into energy saving mode. Energy saving mode is automatically ended as soon as sufficient excess energy is available again. |
Start | The storage system starts from energy saving mode (standby). |
Forced re-charging | The inverter re-charges the battery, in order to maintain the set minimum SOC (state of charge) or the SOC specified by the manufacturer (protection against deep discharge). |
Deactivated | The battery is not active. It has either been deactivated/switched off, or an error means that no communication with the battery is possible. |
Energy saving mode (standby mode) is used to reduce the self-consumption of the system. Both the inverter and the battery automatically switch to energy saving mode under certain conditions.
The inverter switches to energy saving mode if the battery is flat and no PV power is available. Only the inverter's communication with the Fronius Smart Meter and Fronius Solar.web is maintained.
If all the switch-off conditions are met, the battery switches into energy saving mode within ten minutes. This time delay ensures that the inverter can at least be restarted.
| The battery state of charge is less than or equal to the input minimum state of charge. | |
| The current charging or discharging power of the battery is less than 100 W. | |
| Less than 50 W is available for charging the battery. The power of feeding into the public grid is at least 50 W less than the power currently required in the home network. |
The inverter automatically switches into energy saving mode, following the battery.
If the inverter does not operate for 12 minutes (e.g. fault), or there is an interruption in the electrical connection between the inverter and the battery and there is no backup power mode, the battery switches to energy-saving mode in any case. This reduces self discharge of the battery.
Energy saving mode is shown on the user interface of the inverter and in Solar.web by an "i" beside the battery symbol in the system overview.
Fronius explicitly points out that the third-party batteries are not Fronius products. Fronius is not the manufacturer, distributor or retailer of these batteries. Fronius accepts no liability and offers no service or guarantees for these batteries.
Read this document and the Installation Instructions before installing and commissioning the external battery. The documentation is either enclosed with the external battery or can be obtained from the battery manufacturer or their service partners
All documents associated with the inverter can be found at the following address:
BYD Battery-Box Premium HVS | 5.1 | 7.7 | 10.2 | 12.8 |
Number of battery modules | 2 | 3 | 4 | 5 |
Fronius Symo GEN24 SC* | ||||
Fronius Symo GEN24 Plus SC | ||||
Battery parallel operation** |
BYD Battery-Box Premium HVM | 8.3 | 11.0 | 13.8 | 16.6 | 19.3 | 22.1 |
Number of battery modules | 3 | 4 | 5 | 6 | 7 | 8 |
Fronius Symo GEN24 SC* | ||||||
Fronius Symo GEN24 Plus SC | ||||||
* | Battery support optionally available. |
** | Max. 3 batteries with the same capacity can be combined. Max. 2 batteries can be combined with BYD Battery-Box Premium HVM 22.1. |
Switch on the battery.
Set the DC disconnector to the "On" switch position. Switch on the automatic circuit breaker.
LG FLEX | 8.6 | 12.9 | 17.2 |
Pull off the cover to the right.
Pull off the cover of the DC disconnector to the front. Set the DC disconnector to the "On" switch position.
To refit the battery, follow the steps listed above in reverse order.
There is no energy available from the PV modules or from the public grid. If backup power operation or battery operation are not possible (e.g. deep discharge protection of the battery), the inverter and battery switch off.
Status codes about the inactive state of the battery are displayed on the user interface of the inverter or sent via Solar.web by means of SMS or e-mail (only if notification via Solar.web is configured accordingly).
As soon as energy is available again, the inverter starts operation automatically; however the battery must be started manually. The switch-on sequence must be observed for this, see chapter Suitable batteries on page (→).
The inverter requires energy from the battery to start backup power operation. This is done manually on the battery; further information on the power supply for restarting the inverter via the battery can be found in the battery manufacturer's Operating Instructions.
The inverter offers the option to use the integrated AC relays as coupling switches in conjunction with a central grid and system protection unit (in accordance with VDE-AR-N 4105:2018:11 §6.4.1). For this purpose, the central trigger device (switch) must be integrated into the WSD chain as described in the chapter "WSD (Wired Shut Down)".
The wired shutdown (WSD) interrupts the inverter feeding energy into the grid if the trigger device (switch, e.g. emergency stop or fire alarm switch) has been activated.
If an inverter (secondary device) fails, it is bypassed and the other inverters continue operating. If a second inverter (secondary device) or the inverter (primary device) fails, the operation of the entire WSD chain is interrupted.
For installation, see Installing the WSD (wired shutdown) on page (→).
The inverter is equipped with a universal current-sensitive residual current monitoring unit (RCMU = Residual Current Monitoring Unit) in accordance with IEC 62109-2 and IEC63112.
This device monitors residual currents from the PV module to the AC output of the inverter and disconnects the inverter from the grid in the event of unauthorised residual current.
In the case of PV systems with ungrounded solar modules, the inverter checks the resistance between the positive or negative pole of the PV system and the ground potential before feeding energy into the grid. In the event of a short circuit between DC+ or DC- cable and ground (e.g. due to inadequately insulated DC cables or damaged solar modules), an infeed into the grid is prevented.
AFCI (Arc Fault Circuit Interrupter) protects against arcing faults and in the narrower sense is a protection device against contact faults. The AFCI evaluates any DC-side faults that occur in the current and voltage curve with an electronic circuit and switches off the circuit when a contact fault is detected. This prevents overheating on poor contacts and ideally possible fires.
Danger due to incorrect or unprofessional DC installation.
The result is risk of damage and in turn, risk of fire to the PV system due to inadmissible thermal loads that arise with an arc.
Check plug connections are in good condition.
Repair incorrect insulation as appropriate.
Complete connections as per the specifications.
IMPORTANT!
Fronius will not accept any costs associated with production downtimes, installer costs, etc., that may arise as the result of a detected arc and its consequences. Fronius accepts no liability for damage that can occur despite the presence of the integrated Arc Fault Circuit Interrupter/extinguishing system ( e.g. caused by a parallel arc).
IMPORTANT!
Active PV module electronics (e.g., power optimiser) can impair the function of the Arc Fault Circuit Interrupter. Fronius does not guarantee that the Arc Fault Circuit Interrupter will work correctly in combination with active PV module electronics.
Reconnection behaviour
After detection of an arc, feeding energy into the grid is interrupted for at least 5 minutes. Depending on the configuration, feeding energy into the grid is then automatically resumed. If several arcs are detected within a period of 24 hours, feeding energy into the grid can also be permanently interrupted until a manual reconnection has taken place."
If one of the following safety devices is triggered, the inverter switches to a safe state:
In the safe state, the inverter no longer feeds energy in and is disconnected from the grid by opening the AC relays.
(1) | 2 x 4-pin DC push-in terminal |
(2) | Push-in WSD (wired shutdown) terminal |
(3) | Push-in terminals in the data communication area (Modbus, digital inputs and outputs) |
(4) | 3-pin push-in terminal for PV Point (OP) |
(5) | 5-pin AC push-in terminal |
(6) | Cable bushing/cable gland AC |
(7) | 6-pin ground electrode terminal |
(8) | Cable bushing/cable gland in the data communication area |
(9) | Connection area divider |
(10) | 10x DC cable bushings |
(11) | Optional cable bushing (M16) |
(12) | Optional cable bushing (M16 - M20) |
(13) | Optional cable bushing (M16 - M32) |
(14) | Optional cable bushing (M16 - M25) |
The connection area divider separates the high-voltage conductors (DC and AC) from the signal lines. To make it easier to reach the connection area, the divider can be removed for the connection work, and must be re-inserted.
(1) | Integrated cable duct |
(2) | Recesses for removing the connection area divider |
(3) | Snap tabs for locking/unlocking |
(4) | Defined breaking point for the Datcom connection |
The integrated cable duct (1) allows for the lines to be laid from one area of the inverter to the other. As a result, multiple inverters can be easily installed next to each other.
The ground electrode terminal allows additional components to be earthed, such as:
The DC disconnector has 3 switch settings:
(1) | Locked/off (turned to the left) |
(2) | Off |
(3) | On |
IMPORTANT!
In switch settings (1) and (3), a conventional padlock can be used to secure the inverter against being switched on/off. The national guidelines must be complied with in this respect.
| Indicates the inverter operating status. |
WSD (wired shutdown) switch | Defines the inverter as a WSD primary device or WSD secondary device. |
Modbus 0 (MB0) switch | Switches the terminating resistor for Modbus 0 (MB0) on/off. |
Modbus 1 (MB1) switch | Switches the terminating resistor for Modbus 1 (MB1) on/off. |
| To operate the inverter. See chapter Button functions and LED status indicator on page (→). |
| Indicates the inverter connection status. |
LAN 1 | Ethernet connection for data communication (e.g. WLAN router, home network or for commissioning with a laptop see chapter Installation using the web browser on page (→)). |
LAN 2 | Reserved for future functions. Only use LAN 1 to avoid malfunctions. |
I/Os terminal | Push-in terminal for digital inputs/outputs. See chapter Permissible cables for the data communication connection on page (→). |
WSD terminal | Push-in terminal for the WSD installation. See chapter "WSD (wired shutdown)" on page (→). |
Modbus terminal | Push-in terminal for the installation of Modbus 0, Modbus 1, 12 V and GND (ground). |
The status of the inverter is shown via the operating status LED. In the event of faults, carry out the individual steps in the Fronius Solar.start app. | |
The optical sensor is actuated by touching with a finger. | |
The status of the connection is shown via the communication LED. To establish the connection, carry out the individual steps in the Fronius Solar.start app. |
Sensor functions | ||
1x | ||
2x | ||
3 seconds |
LED status indicator | ||
The inverter is operating correctly. | ||
The inverter is performing the grid checks required by the applicable standards for feed-in mode. | ||
The inverter is in standby, is not operational (e.g. no feed-in at night) or is not configured. | ||
The inverter indicates a non-critical status. | ||
The inverter indicates a critical status and there is no grid power feed process. | ||
The inverter indicates a backup power overload. | ||
The network connection is being established via WPS. | ||
The network connection is being established via WLAN AP. | ||
The network connection is not configured. | ||
The inverter is operating correctly, a network fault is indicated. | ||
The network connection is active. | ||
The inverter is performing an update. | ||
There is a service message. |
On the V+/GND pin, it is possible to feed in a voltage of around 12.5–24 V (+ max. 20%) with an external power supply. The outputs IO 0–5 can then be operated with the external voltage. A maximum of 1 A can be drawn per output, with a maximum of 3 A allowed in total. The fuse protection must be located externally.
Risk of polarity reversal at the terminals due to improper connection of external power supplies.
This may result in severe damage to the inverter.
Check the polarity of the external power supply with a suitable measuring device before connecting it.
Connect the cables to the V+/GND outputs with the correct polarity.
IMPORTANT!
If the total output (6 W) is exceeded, the inverter switches off the entire external power supply.
(1) | Power limitation |
IMPORTANT!
If several backup power variants are available, please note that only one backup power variant may be installed and configured.
The inverter can provide 220 ‑ 240 V at the PV Point/PV Point Comfort. A corresponding configuration must be set up during commissioning.
At 220 ‑ 240 V output voltage, max. 13 A AC continuous current is available.
Example:
220 V *13 A = 2860 W
230 V *13 A = max. 3 kW
In backup power mode, some electrical appliances cannot function properly as starting currents are too high (for example, fridges and freezers). It is recommended to switch off non-essential loads during backup power mode. Overload capacity of 35 % is possible for a duration of 5 seconds, depending on the capacity of the PV modules and/or the battery at that moment in time.
There is a brief interruption when switching from grid-connected mode to backup power mode. For this reason, the backup power function cannot be used as an uninterruptible power supply, for example for computers.
If no energy from the battery or the PV modules is available in backup power mode, backup power mode ends automatically. If sufficient energy becomes available from the PV modules once again, backup power mode starts again automatically.
In the event of excessive consumption, backup power mode is stopped and the "backup power overload" status code is displayed on the inverter's LED status indicator (see Button functions and LED status indicator on page (→)). The maximum power in backup power mode according to the technical data must be observed.
IMPORTANT!
Example:
IMPORTANT!
Example:
With the PV Point, in the event of a failure of the public grid, 1‑phase electrical devices can be connected to the Opportunity Power (OP) terminal and supplied with a maximum power of 3 kW, if enough power is available from the PV modules or an optional battery. In grid-connected operation, the OP terminal is not supplied with voltage, therefore the connected loads will not be continuously supplied with power.
IMPORTANT!
A relay-based network switching setup is not possible.
Installation Instructions, see Connecting backup power - PV Point (OP) on page (→).
IMPORTANT!
IMPORTANT!
IMPORTANT!
A quick-lock system (3) is used to mount the connection area cover and front cover. The system is opened and closed with a half-rotation (180°) of the captive screw (1) into the quick-lock spring (2).
The system is independent of torque.
Danger when using a drill driver.
This may result in the destruction of the quick-lock system due to overtorque.
Use a screwdriver (TX20).
Do not turn the screws more than 180°.
Technical data, warning notices and safety symbols are affixed to the inverter. These warning notices and safety symbols must not be removed or painted over. They warn against incorrect operation which can lead to serious injury and damage.
A 4-digit number (coded production date) is printed on the rating plate at the very bottom, from which the production date can be calculated.
If you subtract the value 11 from the first two digits, you get the production year. The last two digits stand for the calendar week in which the device was produced.
Example:
Value on rating plate = 3206
32 - 11 = 21 → Production year 2021
06 = Calendar week 06
Symbols on the rating plate: | |
CE mark – confirms compliance with applicable EU directives and regulations. | |
UKCA mark – confirms compliance with applicable UK directives and regulations. | |
WEEE mark – waste electrical and electronic equipment must be collected separately and recycled in an environmentally sound manner in accordance with the European Directive and national law. | |
RCM mark – tested in accordance with the requirements of Australia and New Zealand. | |
ICASA mark – tested in accordance with the requirements of the Independent Communications Authority of South Africa. | |
CMIM mark – tested in accordance with IMANOR requirements for import regulations and compliance with Moroccan standards. |
Safety symbols: | |
Risk of serious injury and damage due to incorrect operation. | |
Dangerous electrical voltage. | |
Allow the capacitors of the inverter to discharge (2 minutes). |
Warning notice text:
WARNING!
An electric shock can be fatal. Before opening the device, it must be disconnected and de-energised at the input and output.
All installed components in the photovoltaic system must be compatible and have the necessary configuration options. The installed components must not restrict or negatively influence the functioning of the photovoltaic system.
Risk due to components in the photovoltaic system that are not compatible and/or have limited compatibility.
Incompatible components may limit and/or negatively affect the operation and/or functioning of the photovoltaic system.
Only install components recommended by the manufacturer in the photovoltaic system.
Before installation, check the compatibility of components not expressly recommended with the manufacturer.
Please note the following criteria when choosing a location for the inverter:
| Only install on a solid, non-flammable surface. | |
| Max. ambient temperatures: | |
| Relative humidity: | |
| If the inverter is installed in a switch cabinet or similar enclosed space, ensure sufficient heat dissipation with forced-air ventilation. | |
When installing the inverter on the outer walls of cattle sheds, it is important to maintain a minimum clearance of 2 m between the inverter and the ventilation and building openings on all sides. | ||
The following substrates are permissible for installation:
The inverter is suitable for indoor installation. | ||
The inverter is suitable for outdoor installation. | ||
In order to minimise the heating up of the inverter, do not expose it to direct insolation. | ||
The inverter should be installed in a protected location, for example, below the PV modules or under an overhanging roof. | ||
The inverter must not be installed or used at altitudes above 4000 m. | ||
Do not install the inverter in:
During certain operating phases the inverter may produce a slight noise. For this reason it should not be installed in an occupied living area. | ||
The inverter is designed to be dustproof (IP 66). In areas of high dust accumulation, dust deposits may collect on the cooling surfaces, and thus impair the thermal performance. Regular cleaning is required in this case, see chapter Operation in dusty environments on page (→). We therefore recommend not installing the device in areas and environments with high dust accumulation. | ||
IMPORTANT!
Refer to the manufacturer's documents for the suitable location for third-party batteries.
The inverter is suitable for vertical installation on a vertical wall or column. | ||
The inverter is suitable for a horizontal installation position. | ||
The inverter is suitable for installation on a sloping surface. | ||
Do not install the inverter on a sloping surface with its connection sockets at the top. | ||
Do not install the inverter at an angle on a vertical wall or column. | ||
Do not install the inverter horizontally on a vertical wall or pillar. | ||
Do not install the inverter on a vertical wall or pillar with its connection sockets facing upwards. | ||
Do not install the inverter overhanging with the connection sockets at the top. | ||
Do not install the inverter overhanging with the connection sockets at the bottom. | ||
Do not install the inverter on the ceiling. |
Use the corresponding fixing materials depending on the subsurface and observe the screw dimension recommendations for the mounting bracket.
The installer is responsible for selecting the correct type of fixing.
The mounting bracket (illustration) is also used as the gauge.
The pre-drilled holes on the mounting bracket are intended for screws with a thread diameter of 6 - 8 mm (0.24 - 0.32 inches).
Unevenness on the installation surface (for example, coarse-grained plaster) is largely counterbalanced by the mounting bracket.
When fitting the mounting bracket to the wall or column, ensure that the mounting bracket does not become deformed.
A deformed mounting bracket may make it difficult to clip/swivel the inverter into position.
IMPORTANT!
When installing the mounting bracket, make sure that it is installed with the arrow pointing upwards.
When installing the inverter on a mast or beam, Fronius recommends using the "Pole clamp" (order no. SZ 2584.000) mounting kit from Rittal GmbH.
The "Pole clamp" kit covers the following dimensions:
IMPORTANT!
The mounting bracket must be affixed at a minimum of four points.
There are integrated grips on the side of the inverter which facilitate lifting/attaching.
Clip the inverter into the mounting bracket from above. The connections must point downwards.
Push the lower part of the inverter into the snap-in tabs of the mounting bracket until the inverter audibly clicks into place on both sides.
Check that the inverter is correctly positioned on both sides.
Single-core | Multi-stranded | Fine-stranded | Fine-stranded with ferrule and collar | Fine-stranded with ferrule without collar |
Round copper conductors can be connected to the terminals of the inverter as described below.
Grid connections with push-in terminal* | |||||
Number of pins | |||||
5 | 2.5-10 mm2 | 2.5-10 mm2 | 2.5-10 mm2 | 2.5-6 mm2 | 2.5-6 mm2 |
Grid connections backup power with push-in terminal* | |||||
3 | 1.5-10 mm2 | 1.5-10 mm2 | 1.5-10 mm2 | 1.5-6 mm2 | 1.5-6 mm2 |
PV/BAT connections with push-in terminal** | |||||
2 x 4 | 4-10 mm2 | 4-10 mm2 | 4-10 mm2 | 4-6 mm2 | 4-6 mm2 |
Ground electrode terminal | |||||
2 | 2.5-16 mm2 | 2.5-16 mm2 | 2.5-16 mm2 | 2.5-16 mm2 | 2.5-16 mm2 |
4 | 2.5-10 mm2 | 2.5-10 mm2 | 2.5-10 mm2 | 2.5-10 mm2 | 2.5-10 mm2 |
* | According to product standard IEC 62109, the ground conductor must correspond to the phase cross-section for phase cross-sections ≤16 mm², while for phase cross-sections >16 mm², it must be at least 16 mm². For a conductor cross-section of 1.5 mm2, the maximum permissible cable length is 100 m. |
** | The cable cross-section must be dimensioned in accordance with the installation situation and the specifications of the battery manufacturer. |
IMPORTANT!
Connect the individual conductors to an appropriate ferrule if several individual conductors are connected to one input of the push-in terminals.
WSD connections with push-in terminal | ||||||
Distance | Stripping length | Cable recommendation | ||||
100 m 109 yd | 10 mm | 0.14-1.5 mm2 | 0.14-1.5 mm2 | 0.14-1 mm2 | 0.14-1.5 mm2 | min. CAT 5 UTP (unshielded twisted pair) |
Modbus connections with push-in terminal | ||||||
300 m 328 yd | 10 mm | 0.14-1.5 mm2 | 0.14-1.5 mm2 | 0.14-1 mm2 | 0.14-1.5 mm2 | min. CAT 5 STP (shielded twisted pair) |
IO connections with push-in terminal | ||||||
30 m | 10 mm | 0.14-1.5 mm2 | 0.14-1.5 mm2 | 0.14-1 mm2 | 0.14-1.5 mm2 | Single conductor possible |
LAN connections |
Fronius recommends at least CAT 5 STP (shielded twisted pair) cables and a maximum distance of 100 m (109 yd). |
For a standard M32 cable gland with a reducer:
7-15 mm
For a standard M32 cable gland without a reducer:
11-21 mmWith cable diameters greater than 21 mm, the M32 cable gland must be replaced by an M32 cable gland with a larger clamping area – item number: 42,0407,0780 – strain-relief device M32 x 1.5 KB 18-25.
Cable diameter for the strain-relief device: max. 9 mm.
.Cable diameter for the connection to the push-in terminal: max. 6 mm
IMPORTANT!
For double-insulated cables with a cable diameter over 6 mm, the external insulation layer must be removed to connect to the push-in terminal.
The national regulations of the grid operator or other factors may require a residual current circuit breaker in the AC connection lead.
For this situation, a type A residual current circuit breaker is generally adequate. Nevertheless, false alarms can be triggered for the type A residual current circuit breaker in individual cases and depending on local conditions. For this reason, in accordance with national legislation, Fronius recommends that a residual current circuit breaker with a tripping current of at least 100 mA suitable for frequency converters be used.
IMPORTANT!
As a maximum, the inverter can be used with an automatic circuit breaker 32 A.
Inverter | Phases | AC output | Maximum fuse rating | Recommended fuse rating |
Fronius Symo GEN24 12.0 SC | 3 | 12000 W | 32 A | 32 A |
Read the Installation and Operating Instructions before installing and commissioning the equipment.
Only qualified personnel are authorised to commission your inverter and only within the scope of the respective technical regulations.
Danger due to grid voltage and DC voltage from solar modules that are exposed to light.
Prior to any connection work, disconnect the inverter on the AC side and the DC side.
Only an authorised electrical engineer is permitted to connect this equipment to the public grid.
Danger due to damaged and/or contaminated terminals.
Before making any connections, check the terminals for damage and contamination.
Remove contamination in the de-energized state.
Have defective terminals repaired by an authorised specialist.
The neutral conductor must be connected in order to operate the inverter.
It is not possible to operate the inverter in unearthed grids, such as IT grids (insulated grids without ground conductor).
Make sure that the grid's neutral conductor is earthed.
Turn off the automatic circuit breaker. Set the DC disconnector to the "Off" switch position.
Loosen the 5 screws of the connection area cover by rotating them 180° to the left using a screwdriver (TX20).
Remove the connection area cover from the device.
Press the lock on the back of the terminal and remove the AC terminal.
Route the mains cable from below through the cable gland on the right side and the ferrite core.
IMPORTANT!
The ground conductor should not be routed through the ferrite core, it should be dimensioned longer and laid in a loop to allow for movement so that it is strained last in the event of failure of the cable gland.
For more information on the cable gland, see Cable diameter of the AC cable on page(→).
Strip the insulation of the single conductors by 12 mm. Select the cable cross section in accordance with the instructions in Permissible cables for the electrical connection on page (→).
Lift to open the terminal's operating lever and insert the stripped single conductor into the slot provided as far as it will go. Then close the operating lever until it engages.
IMPORTANT!
Only one conductor may be connected to each pin. The AC cables can be connected to the AC terminal without ferrules.
L1 | Phase conductor |
L2 | Phase conductor |
L3 | Phase conductor |
N | Neutral conductor |
PE | Ground conductor |
Insert the AC terminal into the AC slot until it engages. Fasten the union nut of the cable gland with a torque of 6 ‑ 7 Nm.
To enable suitable PV modules to be chosen and to use the inverter as efficiently as possible, it is important to bear the following points in mind:
IMPORTANT!
Before connecting up the PV modules, check that the voltage for the PV modules specified by the manufacturer corresponds to the actual measured voltage.
IMPORTANT!
The PV modules connected to the inverter must comply with the IEC 61730 Class A standard.
IMPORTANT!
Solar module strings must not be earthed.
IMPORTANT!
IMPORTANT!
IMPORTANT!
Commissioning as well as maintenance and service work in the power module of the inverter must only be carried out by service personnel trained by Fronius and only within the scope of the respective technical regulations.
Ensure that the AC and DC side of the inverter are de-energised before carrying out any connection, maintenance or service tasks.
2 independent PV inputs (PV 1 and PV 2) are available. These can be connected to a different number of modules.
When using for the first time, set up the module array according to the respective configuration (also possible later in the “System configuration” menu under the “Components” menu item).
IMPORTANT!
The installation must be carried out in accordance with the nationally applicable standards and directives. If the Arc Fault Circuit Interrupter integrated in the inverter is used for the requirement according to IEC 63027 for arc detection, the solar module strings must not be combined upstream of the inverter.
Module array settings:
PV 1: ON
PV 2: OFF
PV 1: ON
PV 2: OFF
PV 1: ON
PV 2: OFF
PV 1 + PV 2 (connected in parallel): ON
IMPORTANT!
The maximum current load of a single terminal is 28 A. PV‑connection strings with a total current of more than 28 A must be split between both PV inputs upstream of the terminals (ISC max ≤ 60 A). The plug connection for splitting the total current must be sufficiently dimensioned, suitable and correctly installed. Splitting the current by bridging from PV 1 to PV 2 at the terminal is not permitted.
PV 1: ON
PV 2: ON
Push the DC cables through the DC bushings by hand.
IMPORTANT!
Before stripping the insulation, push the cables through the DC bushings to prevent individual wires being bent or broken.
Select the cable cross section in accordance with the instructions in Permissible cables for the electrical connection from page (→).
Strip the insulation of the individual conductors by 12 mm. Lift to open the terminal's operating lever and insert the stripped single conductor into the slot provided, in each case as far as it will go. Then close the operating lever until it engages.
Danger due to individual conductors in the terminal that are loose and/or improperly connected.
Only connect one single conductor in the slot provided for each terminal.
Check that the single conductor is held securely in the terminal.
Ensure that all of the single conductor is within the terminal and that no individual wires are sticking out of the terminal.
Use a suitable measuring instrument to check the voltage and polarity of the DC cabling. Remove both DC terminals from the slots.
Danger due to polarity reversal at the terminals.
Use a suitable measuring instrument to check the polarity of the DC cabling.
Use a suitable measuring instrument to check the voltage (max. 1 000 VDC)
Insert the DC terminals into the respective slot until they engage. Fasten the screws of the strain-relief device to the housing using a screwdriver (TX20) and tighten to a torque of 1.3-1.5 Nm.
Risk due to overtorque at the strain-relief device.
This may result in damage to the strain-relief device.
Do not use a drill driver.
Commissioning as well as maintenance and service work on the inverter and battery must only be carried out by service personnel trained by the respective inverter or battery manufacturer and only within the scope of the respective technical regulations.
Read the Installation and Operating Instructions provided by the respective manufacturer before installing and commissioning the equipment.
Danger due to grid voltage and DC voltage from solar modules that are exposed to light and from batteries.
Ensure that the AC and DC side of the inverter and the battery are de-energised before carrying out any connection, maintenance or service tasks.
Danger due to operation of the battery above the permissible altitude as specified by the manufacturer.
Operating the battery above the permissible altitude can result in restricted operation, failure of the operation, and unsafe states of the battery.
Adhere to the manufacturer's instructions regarding the permissible altitude.
Operate the battery only at the altitude specified by the manufacturer.
IMPORTANT!
Prior to installing a battery, ensure that the battery is switched off. The max. DC cable length for the installation of external batteries must be taken into account according to the manufacturer's specifications, see Suitable batteries on page (→).
Manually push the battery cables through the DC bushings.
* The battery ground conductor must be connected externally (e.g. switch cabinet). When connecting an LG FLEX battery, the battery ground conductor can be connected in the inverter (see Connecting the LG FLEX ground conductor on page (→). Observe the minimum cross section of the ground conductor to the battery.
IMPORTANT!
Ensure that all of the single conductor is within the terminal and that no individual wire strands are sticking out of the terminal.
Risk due to overvoltage when using other slots on the terminal.
This may result in damage to the battery and/or the PV modules due to discharge.
Only use the slots marked BAT for connecting the battery.
Serious substantive damage to the PV system may result.
Use a suitable measuring instrument to check the polarity of the DC cabling when the battery is switched on.
The maximum voltage for the battery input must not be exceeded (see Technical data on page (→)).
Fasten the screws of the cable guide to the housing using a screwdriver (TX20) and tighten to a torque of 1.3-1.5 Nm.
IMPORTANT!
Information for connection on the battery side can be found in the Installation Instructions from the relevant manufacturer.
Route the battery ground conductor into the integrated cable duct of the connection area divider and into the AC connection area.
Fasten the battery ground conductor to the second input of the ground electrode terminal from the top using a screwdriver (TX20) and a torque of 1.8 – 2 Nm.
IMPORTANT!
Installing and connecting an option must only be carried out by service personnel trained by Fronius and only within the scope of the respective technical regulations.
Follow the safety rules.
During the switch from grid-connected operation to backup power mode, momentary interruptions will occur. The PV Point output requires PV power from the solar modules or a battery to power the connected loads.
Connected loads will not be supplied with power during the switchover.
Do not connect any loads that require an uninterruptible supply ( e.g. IT networks, life-sustaining medical devices).
IMPORTANT!
The valid national laws, standards and provisions, as well as the specifications of the relevant grid operator are to be taken into account and applied.
It is highly recommended that the specific installation be agreed with the grid operator and explicitly approved by this operator. This obligation applies to system constructors in particular (e.g. installers).
IMPORTANT!
All loads that have to be supplied via the OP terminal must be protected by means of a residual current circuit breaker.
In order to ensure the residual current circuit breaker operates properly, a connection must be established between the neutral conductor N´ (OP) and earth.
For the Circuit Diagram recommended by Fronius, see Circuit Diagram - PV Point (OP) on page (→).
Switch off the automatic circuit breaker and DC disconnector. Turn the DC disconnector to the "Off" switch position.
Danger from faulty or incorrect bores.
This may lead to injuries to the eyes and hands as a result of flying debris and sharp edges, as well as damage to the inverter.
When drilling, wear suitable protective goggles.
Only ever use a step drill when drilling.
Ensure that nothing is damaged inside the device (for example connection block).
Adapt the diameter of the bore to match the corresponding connection.
Deburr the bores using a suitable tool.
Remove the drilling residues from the inverter.
Drill out the optional cable guide with a step drill.
Insert the cable gland into the bore and secure to the torque specified by the manufacturer.
Guide the mains cable through the cable gland from below.
Pull off the OP terminal.
The cable cross section must be between 1.5 mm2 and 10 mm2. Lift to open the terminal's operating lever and insert the stripped single conductor into the slot provided, all the way up to the stop. Then close the operating lever until it engages.
L1´ | Phase conductor |
N´ | Neutral conductor |
N´ | PEN conductor |
IMPORTANT!
The PEN conductor must be produced with ends that are permanently marked blue, according to the national provisions, and have a cross section of 10 mm².
Fasten the ground conductor and PEN conductor to the ground electrode terminal using a screwdriver (TX20) and tighten to a torque of 1.8-2 Nm.
Insert the OP terminal into the OP slot until it engages. Tighten the union nut of the cable gland to the torque specified by the manufacturer.
After the initial installation and configuration of the backup power operation, it is recommended to test the backup power operation. For test mode, a battery charge of min. 30 % is recommended.
A description on how to run test mode can be found in the backup power checklist (https://www.fronius.com/en/search-page, item number: 42,0426,0365).
Danger from incorrect installation, commissioning, operation or incorrect use.
This can result in severe personal injury/damage to property.
Only trained and qualified personnel are authorised to install and commission the system, and only within the scope of the technical regulations.
The Installation and Operating Instructions must be read carefully prior to use.
If anything is unclear, contact your vendor immediately.
IMPORTANT!
It is highly recommended to coordinate the concrete examples implemented and in particular the specific installation with the grid operator to obtain their explicit approval. This obligation applies to system constructors in particular (e.g. installers).
The examples suggested here show a backup power supply with or without an external protection relay (external grid and system protection unit). Whether an external protection relay must be used or not is the decision of the respective grid operator.
IMPORTANT!
An uninterruptible power supply (UPS) may only be used to supply individual loads (e.g. computers). Feeding into the power supply of the house network is not permitted. The Installation and Operating Instructions must be read carefully prior to use. If anything is unclear, contact your vendor immediately.
The examples given in this document (in particular cabling variants and Circuit Diagrams) are suggestions only. These examples have been carefully developed and tested. They can therefore be used as a basis for real-life installation. Anyone following or using these examples does so at their own risk.
IMPORTANT!
IMPORTANT!
IMPORTANT!
The cabling variant required by the grid operator must be clarified with the grid operator.
Cabling of backup power circuit and non-backup power circuits
If not all the loads in the home need to be supplied in a backup power situation, the circuits need to be divided into backup power circuits and non-backup power circuits. The total load of the backup power circuits must not exceed the rated power of the inverter.
The backup power circuits and non-backup power circuits must be fused separately according to the required safety measures (residual current circuit breaker, automatic circuit breaker, etc.).
In backup power mode, only the backup power circuits are 3-pin disconnected from the grid by contactor K1. The rest of the home network is not supplied with power in this case.
The emergency power circuits and non-emergency power circuits must be fused separately according to the required safety measures (residual current circuit breaker, automatic circuit breaker, etc.).
In backup power mode, only the backup power circuits are all-pin disconnected from the grid by contactor K1; a ground connection is only established for these circuits. The rest of the home network is not supplied with power in this case.
Cabling for backup power circuit and non-backup power circuits
IMPORTANT!
Fronius Smart Meter US-480 must be used for these circuit variants.
In backup power mode, only the backup power circuits are disconnected from the grid by contactors K1 and K2; an earth connection is only established for these circuits. The rest of the home network is not supplied with power in this case.
IMPORTANT!
The Circuit Diagrams to be used are to be applied depending on the country standard and implementation regulations of the grid operator.
If not all the loads in the home need to be supplied in a backup power situation, the circuits need to be divided into backup power circuits and non-backup power circuits. The total load of the backup power circuit must not exceed the rated power of the inverter.
In backup power mode, only the backup power circuits and inverter are disconnected from the grid by the changeover switch Q1. With all-pin separation, an additional earth connection is established. In this case, the loads in the non-backup circuit are not supplied by the inverter.
The inputs M0 and M1 can be selected for this purpose. A maximum of 4 Modbus participants can be connected to the Modbus terminal on inputs M0 and M1.
IMPORTANT!
Only one primary meter, one battery and one Ohmpilot can be connected per inverter. Due to the high data transfer of the battery, the battery occupies 2 participants. If the "Inverter control via Modbus" function is activated in the "Communication” → "Modbus" menu, no Modbus participants are possible. It is not possible to send and receive data at the same time.
Example 1:
Input | Battery | Fronius | Quantity | Quantity |
Modbus 0 (M0) | 0 | 4 | ||
0 | 2 | |||
0 | 1 | |||
Modbus 1 (M1) | 1 | 3 |
Example 2:
Modbus 0 (M0) | 1 | 3 | ||
Modbus 1 (M1) | 0 | 4 | ||
0 | 2 | |||
0 | 1 |
IMPORTANT!
Example 1:
0 | 2 | |||
0 | 1 | |||
Example 2:
0 | 2 | |||
0 | 1 |
IMPORTANT!
Should the blanking plugs be missing or improperly fitted, then safety class IP66 cannot be guaranteed.
Undo the cable gland union nut and push out the sealing ring and the blanking plug from the inside of the device.
Open up the sealing ring at the location where the blanking plug is to be removed.
* Liberate the blanking plug by moving it sideways.
Guide the data cables first through the cable gland union nut and then through the housing opening.
Insert the sealing ring between the union nut and the housing opening. Press the data cables into the seal's cable guide. Then press in the seal until it reaches the underside of the cable gland.
Tighten the union nut for the cable gland to a torque of min. 2.5 to max. 4 Nm.
Strip 10 mm from the single conductors and mount the ferrules if necessary.
IMPORTANT!
Insert the cable into the respective slot and check the cable is securely retained.
IMPORTANT!
Use only twisted pairs for connecting "Data +/-" and "Enable +/-", see Permissible cables for the data communication connection on page (→).
Twist the cable shield and insert into the "SHIELD" slot.
IMPORTANT!
Improperly fitted shielding can cause data communication problems.
For the wiring proposal recommended by Fronius, see page (→).
It may be possible for the system to function without terminating resistors. However, owing to interference, the use of terminating resistors according to the following overview is recommended for trouble-free functioning.
For permissible cable and max. distances for the data communication range see chapter Permissible cables for the data communication connection on page (→).
IMPORTANT!
Terminating resistors that are not positioned as illustrated can result in interference in the data communication.
IMPORTANT!
The push-in WSD terminal in the inverter's connection area is delivered with a bypass ex works as standard. The bypass must be removed when installing a trigger device or a WSD chain.
The WSD switch of the first inverter with connected trigger device in the WSD chain must be in position 1 (primary device). The WSD switch of all other inverters should be in the 0 (secondary device) position.
Max. distance between 2 devices: 100 m
Max. number of devices: 28
* Floating contact of the trigger device (e.g. central grid and system protection). If several floating contacts are used in a WSD chain, they must be connected in series.
The housing cover is fitted with a lock for safety reasons, which allows the housing cover on the inverter to be pivoted only when the DC disconnector is switched off.
Only clip and pivot the housing cover onto the inverter when the DC disconnector is switched off.
Do not use excessive force to clip in and pivot the housing cover.
Place the cover on the connection area. Tighten the five screws by rotating them 180° to the right in the indicated order using a screwdriver (TX20).
Clip the housing cover onto the inverter from above.
Press on the lower part of the housing cover and tighten the two screws 180° to the right using a Torx screwdriver (TX20).
Turn the DC disconnector to the "On" switch position. Switch on the automatic circuit breaker. For systems with a battery, observe the switch-on sequence as per chapter Suitable batteries on page (→).
IMPORTANT! Open WLAN Access Point with the optical sensor, see chapter Button functions and LED status indicator on page (→)
When starting the inverter for the first time, various setup settings must be configured.
If the setup process is cancelled before the process is complete, any data that has been input up to this point is lost and the start screen with the installation wizard is shown again. If the process is interrupted, such as in the event of a power outage, the data is saved. Commissioning may be continued from the point at which the process was interrupted once the power supply has been restored. If the setup was interrupted, the inverter feeds energy into the grid at maximum 500 W and the operating status LED flashes yellow.
The country setup can only be set when starting the inverter for the first time. If the country setup needs to be changed at a later date, please contact your installer / Technical Support team.
The "Fronius Solar.start" app is required for this installation method. Depending on the end device with which the installation will be carried out, download the app for the respective platform.
The network wizard and the product setup can be carried out independently of each other. A network connection is required for the Solar.web installation wizard.
WLAN:
The network wizard and the product setup can be carried out independently of each other. A network connection is required for the Fronius Solar.web installation wizard.
Ethernet:
To start up the inverter again, follow the steps listed above in reverse order.
IMPORTANT!
Depending on the user's authorization, settings can be executed in the individual menus.
IMPORTANT!
IMPORTANT!
Select "Add component+" to add all available components to the system.
PV generator
Activate the MPP tracker and enter the connected PV power in the associated field. For combined solar module strings, "PV 1 + PV 2 connected in parallel" must be activated.
Battery
If the SoC mode is set to "Automatic", the values "Minimum SoC" and "Maximum SoC" are preset according to the technical specifications of the battery manufacturer.
If the SoC mode is set to "Manual", the values "Minimum SoC" and "Maximum SoC" may be changed after consultation with the battery manufacturer within the scope of their technical specifications. In the event of a power outage requiring backup power, the set values are not taken into account.
Using the "Allow battery charging from additional producers in home network" setting, charging of the battery from other external producers is enabled/disabled.
Using the "Allow battery charging from public grid" setting, charging of the battery from the public grid is enabled/disabled.
The normative or feed-in tariff rules must be taken into account with this setting. The setting does not affect the charging of the battery by other producers within the home. It merely relates to the process of drawing charging energy from the public grid. Regardless of this setting, any charging from the public grid that is required for service reasons (e.g. necessary re-charging to protect against deep discharge) is still performed.
IMPORTANT!
Fronius accepts no liability for damage to third-party batteries.
Primary meter
To ensure smooth operation in conjunction with other energy producers and in Full Backup backup power mode, it is important to install the Fronius Smart Meter at the feed-in point. The inverter and other producers must be connected to the public grid via the Fronius Smart Meter.
This setting also affects the behaviour of the inverter at night. If the function is deactivated, the inverter switches to Standby mode as soon as there is no more PV power available, provided that no energy management command is sent to the battery (e.g. minimum state of charge reached). The message "Power low" is displayed. The inverter restarts as soon as an energy management command is sent or sufficient PV power is available.
If the function is activated, the inverter remains permanently connected to the grid so that energy can be drawn from other producers at any time.
After connecting the meter, the position must be configured. A different Modbus address needs to be set for each Smart Meter.
The Watt value on the generator meter is the sum of all generator meters. The Watt value on the consumption meter is the value of all secondary meters.
Ohmpilot
All Ohmpilots available in the system are displayed. Select the desired Ohmpilot and add it to the system via "Add".
PV generator
Battery
IMPORTANT!
Primary meter
Ohmpilot
Backup power
"Off", "PV Point" or "Full Backup" can be selected for backup power mode.
”Full Backup” backup power mode can only be activated once the required I/O assignments have been configured for backup power. In addition, a meter must be mounted and configured at the feed-in point for “Full Backup” backup power mode.
IMPORTANT!
When configuring "PV Point" backup power mode, the information in chapter Safety on page (→) must be observed.
When configuring "Full Backup" backup power mode, the information in chapter Safety on page (→) must be observed.
Backup power nominal voltage
When backup power mode is activated, the nominal voltage of the public grid must be selected.
State of charge warning limit
A warning is output when the residual capacity of the battery specified here is reached in backup power mode.
Reserve capacity
The set value results in a residual capacity (depending on the capacity of the battery) that is reserved for backup power. The battery is not discharged below the residual capacity in grid-connected operation. In backup power mode, the manually set value "Minimum SoC" is not taken into account. If there is a power outage, the battery is always discharged down to the automatically preset minimum SoC in accordance with the technical specifications of the battery manufacturer.
Load management
Up to 4 pins can be selected for load management here. Additional load management settings are available in the "Load management" menu item.
Default: Pin 1
The pins for control via DRM can be set here:
Mode | Description | Information | DRM pin | I/O pin |
DRM0 | Inverter disconnects itself from the grid | DRM0 occurs if there is an interruption or short circuit on the REF GEN or COM LOAD leads, or if the combinations DRM1 - DRM8 are invalid. | REF GEN | IO4 |
DRM1 | Import Pnom ≤ 0% without disconnection from the grid | currently not supported | DRM 1/5 | IN6 |
DRM2 | Import Pnom ≤ 50% | currently not supported | DRM 2/6 | IN7 |
DRM3 | Import Pnom ≤ 75% & | currently not supported | DRM 3/7 | IN8 |
DRM4 | Import Pnom ≤ 100% | currently not supported | DRM 4/8 | IN9 |
DRM5 | Export Pnom ≤ 0% without disconnection from the grid | currently not supported | DRM 1/5 | IN6 |
DRM6 | Export Pnom ≤ 50% | currently not supported | DRM 2/6 | IN7 |
DRM7 | Export Pnom ≤ 75% & | currently not supported | DRM 3/7 | IN8 |
DRM8 | Export Pnom ≤ 100% | currently not supported | DRM 4/8 | IN9 |
The percentages always refer to the nominal device output. |
IMPORTANT!
If the Demand Response Mode (DRM) function is enabled and no DRM control is connected, the inverter switches to Standby mode.
Here you can enter a value for the apparent power input and the apparent power output for the Australia country setup.
"Enforce Standby"
When the function is activated, the feed-in mode of the inverter is interrupted. This enables a powerless shutdown of the inverter and protects its components. When the inverter is restarted, the standby function is automatically deactivated.
"PV 1" and "PV 2"
Parameter | Value range | Description |
"Mode" | Off | The MPP tracker is deactivated. |
Auto | The inverter uses the voltage at which the max. possible power of the MPP tracker is possible. | |
Fix | The MPP tracker uses the voltage defined in the "UDC fix". | |
"UDC fix" | 80 ‑ 530 V | The inverter uses the fixed preset voltage used at the MPP tracker. |
"Dynamic Peak Manager" | Off | The function is deactivated. |
On | The entire solar module string is checked for optimisation potential and determines the best possible voltage for feed-in mode. |
"Ripple Control"
Ripple control signals are signals sent out by the energy company to switch controllable loads on and off. Depending on the installation situation, ripple control signals may be attenuated or amplified by the inverter. The settings below can be used to counteract this if necessary.
"Reduction of Influence" | Off | The function is deactivated. |
On | The function is activated. | |
"Frequency of Ripple Control Signal" | 100 ‑ 3000 Hz | The frequency specified by the energy company must be entered here. |
"Grid Inductance" | 0.00001 ‑ 0.005 H | The value measured at the feed-in point must be entered here. |
"Measures against RCD/RCMU false triggers"
(when using a 30 mA residual current circuit breaker)
For this situation, a type A residual-current circuit breaker is generally adequate. Nevertheless, false alarms can be triggered for the type A residual-current circuit breaker in individual cases and depending on local conditions. For this reason, in accordance with national legislation, Fronius recommends that a residual-current circuit breaker with a tripping current of at least 100 mA suitable for frequency converters be used.
"Switch-Off before 30mA RCD Trip" | 0 | No measures to prevent false tripping. |
1 | The inverter switches off at 15 mA before the residual-current circuit breaker trips. | |
"Leakage current factor to reduce RCMU/RCD false trips" (only for Symo GEN24) | 0 ‑ 0.25 | Reducing the setting value reduces the leakage current and raises the intermediate circuit voltage, which slightly reduces the efficiency. Setting value 0.16 enables optimum efficiency. |
"Iso Warning"
"Iso Warning" | Off | The isolation warning is deactivated. |
On | The isolation warning is activated. | |
"Iso Alternative Mode"
| Accurate | Isolation monitoring is performed with the highest accuracy and the measured insulation resistance is displayed on the user interface of the inverter. |
Fast | Isolation monitoring is performed with lower accuracy, which shortens the duration of the isolation measurement, and the isolation value is not displayed on the user interface of the inverter. | |
"Isolation Warning Threshold" | 100,000 ‑ | If this threshold is undershot, status code 1083 is displayed on the user interface of the inverter. |
"Backup Power"
"Backup Nominal Voltage" | 220 ‑ 240 V | Is the nominal phase voltage output in backup power mode. |
"Backup Undervoltage Protection Limit U< [pu]" | 0 ‑ 2 %V | The setting value is used to set the limit value for switching off backup power mode, |
"Backup Undervoltage Protection Time U<" | 0.04 ‑ 20 s | Triggering time for falling below the backup power undervoltage protection limit value. |
"Backup Overvoltage Protection Limit U> [pu]" | 0 ‑ 2 %V | The setting value is used to set the limit value for switching off backup power mode, |
"Backup Overvoltage Protection Time U>" | 0.04 ‑ 20 s | Triggering time for exceeding the backup power overvoltage protection limit value. |
"Backup Restart Delay" | 0 ‑ 600 s | Is the waiting time for resumption of backup power mode after a shutdown. |
"Backup Restart Attempts" | 1 ‑ 10 | Is the max. number of automatic restart attempts. When the max. number of automatic restart attempts is reached, the service message 1177 must be acknowledged manually. |
"Backup External Frequency Check"
| Off | The function is deactivated |
On | For backup power mode (Full Backup) in Italy, the external frequency check must be activated. Before ending backup power mode, the grid frequency is checked. When the grid frequency is in the allowed limit range, the loads are connected to the public grid. | |
"Backup Short Circuit Trip Time" | 0.001 ‑ 60 s | If a short circuit occurs in backup power mode, this mode is interrupted within the set time. |
New rules for charging batteries will apply in Germany from 1 January 2024. The maximum charging power from public grids is 4.2 kW when controlled in accordance with Section 14a of the EnWG (Law on the Fuel and Electricity Industries).
The inverter must establish a connection to Solar.web for documentation purposes and be permanently connected to the internet in order to be able to prove the implementation of the external control commands.
The charging power is limited to a value below this by default. Make sure not to use more than the allowed 4.2 kW charging power.
"Self-Consumption Optimization"
Set the operating mode to "Manual" or "Automatic". The inverter always regulates to the set "Target Value at Feed-In Point". In the "Automatic" operating mode (factory setting), an adjustment is made to 0 W at the feed-in point (maximum self-consumption).
If "Manual" has been selected under Self-Consumption Optimization, the "Operating Mode" ("Consumption"/"Feed-In") and the "Target Value at Feed-In Point" can be set.
IMPORTANT!
"Self-Consumption Optimization" has lower priority than "Battery Management".
External producers (only possible with active battery)
If further decentralised producers are installed in the house, and these are incorporated into the self-consumption control of the Fronius Hybrid inverter, the setting "Allow battery charging from additional producers in home network" must be activated in the menu area "Device Configuration" → "Components" (see Components on page (→)
.This means that energy can be drawn from the home network and fed into the battery via the Fronius inverter (battery support required). You can restrict how much power is consumed by the Fronius inverter by specifying the maximum AC power (AC max.). A maximum power consumption of the AC rated power of the Fronius inverter is possible.
Using the time-dependent battery control, it is possible to prevent or restrict charging/discharging of the battery and to specify a defined charging power.
IMPORTANT!
The defined rules for battery control have the second lowest priority after Self-Consumption Optimization. Depending on the configuration, the rules may not be satisfied due to other settings.
The timing for when the rule applies is set in the "Time" input fields and by selecting the relevant "Weekdays".
It is not possible to define a time window over midnight (00:00).
Example: To set a control from 22:00 to 06:00, two inputs are required: "22:00 - 23:59" and "00:00 - 06:00".
The examples below serve to explain the energy flows. Efficiency levels are not taken into account.
Example: Battery system | |
PV system available power | 1000 W |
Power into the battery | 500 W |
Power output (AC) of the inverter | 500 W |
Target value set at feed-in point | 0 W |
Infeed into the public grid | 0 W |
Consumption in home | 500 W |
Example: Battery system without photovoltaics, including second producer in the house | |
Power into the battery | 1500 W |
Power consumption (AC) of the inverter | 1500 W |
Second producer in home network | 2000 W |
Example: Battery system including second producer in the house | |
Power into the battery | 2500 W |
Example: Battery system including second producer in the house (with AC max. limitation) | |
Power into the battery | 2000 W |
Power consumption AC max. limited to | 1000 W |
Power consumption (AC) of the inverter | 1000 W |
Infeed into the public grid | 500 W |
A rule always consists of a restriction or parameter and the time control "Time" and "Weekdays" while the rule is active. Rules with the same restriction (e.g. max. charging power) must not overlap in time.
Max. charging and discharging limits
The max. charging/max. discharging power can be configured at the same time.
Specifying the charging range
It is possible to define a charging range with a min. and max. charging limit. In this case, it is not possible for the battery to discharge.
Specifying the discharging range
It is possible to define a discharging range with a min. and max. discharging limit. In this case, it is not possible for the battery to charge.
Specifying a defined charging power
A defined charging power can be specified by setting the min. and max. charging power to the same value.
Specifying a defined discharging power
A defined discharging power can be specified by setting the min. and max. discharging power to the same value.
Possible applications
The rules in the "Battery Management" menu area enable optimum use of the energy generated. Situations may arise, however, in which PV power cannot be used in full due to the time-dependent battery control.
Example | |
Fronius inverter (max. output power) | 6000 W |
Defined battery discharging | 6000 W |
PV power | 1000 W |
In this case, the inverter would have to reduce the PV power to 0 W, since the output power of the inverter is max. 6000 W and this is already being used to capacity by the battery discharging.
Since it doesn't make sense to waste PV power, the power limit is automatically adjusted in Battery Management such that no PV power is wasted. In the example above, this means that the battery is discharged only at 5000 W, so that the 1000 W PV power can be used.
"Priorities"
If additional components (e.g. battery, Fronius Ohmpilot) are present in the system, the priorities can be set here. Devices having higher priority are actuated first, and subsequently, if there is still excess energy available, the other devices.
IMPORTANT!
If there is a Fronius Wattpilot in the photovoltaic system, it is seen as a load. The priority for the load management of the Wattpilot must be configured in the Fronius Solar.Wattpilot app.
"Rules"
It is possible for up to four different load management rules to be defined. At the same threshold values, the rules are activated in succession. For deactivation, this is done in reverse; the I/O last switched on is the first to be switched off. In the case of different thresholds, the I/O with the lowest threshold is switched on first, followed by the second lowest, and so on.
I/Os controlled by the produced power are always prioritised over a battery and Fronius Ohmpilot. That is to say that an I/O can switch on and result in the battery no longer being charged or the Fronius Ohmpilot no longer being activated.
IMPORTANT!
An I/O is activated/deactivated only after 60 seconds.
All available updates are made available on the product page and in the "Download search" area under www.fronius.com .
The update will start.
The guided setup wizard can be accessed here.
All settings
All configuration data is reset with the exception of the country setup. Changes to the country setup may only be carried out by authorized personnel.
All settings with no network
All configuration data is reset with the exception of the country setup and the network settings. Changes to the country setup may only be carried out by authorized personnel.
Current Messages
All current events of the connected system components are shown here.
IMPORTANT!
Depending on the type of event, these must be confirmed via the "tick" button in order to be processed further.
History
All events of the connected system components that no longer exist are shown here.
This menu displays all system information and the current settings.
The PDF is created and displayed.
The licence file contains the performance data and the scope of functions of the inverter. When replacing the inverter, power stage set or data communication area, the licence file must also be replaced.
The licence activation starts.
The support user is enabled.
IMPORTANT!
The support user only allows Fronius Technical Support to implement settings on the inverter via a secure connection. The button "Terminate Support User Session" deactivates the access.
The sdp.cry file is saved in the downloads.
Remote maintenance access for the Fronius Support team is enabled.
IMPORTANT!
Remote maintenance access gives Fronius Technical Support exclusive access to the inverter via a secure connection. Diagnostic data is transmitted here that can be used for troubleshooting purposes. Only enable remote maintenance access following a request from the Fronius Support team.
When using FRITZ!Box products, the Internet access must be configured to be unlimited and unrestricted. The DHCP Lease Time (validity) must not be set to 0 (=infinite).
LAN:
After connecting, the status of the connection should be checked (see "Internet Services" on page (→)).
WLAN:
The access point of the inverter must be active. It is opened by touching the sensor → communication LED flashes blue.
Access point:
The inverter serves as an access point. A PC or smart device connects directly to the inverter. It is not possible to connect to the internet. The "Network name (SSID)" and "Network key (PSK)" can be assigned in this menu.
It is possible to operate a connection via WLAN and via access point simultaneously.
LAN:
WLAN:
Access point:
Modbus RTU interface 0 / 1
If one of the two Modbus RTU interfaces is set to Slave, the following input fields are available:
| Baud rate |
| Parity |
| SunSpec Model Type |
| Meter address |
| Meter address |
Slave as Modbus TCP
This setting is necessary to enable inverter control via Modbus. If the function Slave as Modbus TCP is activated, the following input fields are available:
| Modbus port |
| Meter address |
| Inverter address |
| Inverter control via Modbus If this option is activated, the inverter is controlled via Modbus. Inverter control includes the following functions:
| Restrict Control |
Remote control and Profiles
The grid operator/energy supplier can influence the output power of the inverter by means of remote control. The prerequisite for this is for the inverter to have an active internet connection.
Remote control | Off | Remote control of the inverter is deactivated. |
On | Remote control of the inverter is activated. | |
Allow remote control for regulatory purposes (Technician) | Deactivated/Activated | The function Allow remote control for regulatory purposes may be mandatory for proper operation of the system. *) |
Allow remote control for Virtual Power Plants (Customer) | Deactivated/Activated | If the Allow remote control for regulatory purposes function is enabled (technician access required), the Allow remote control for Virtual Power Plants function is automatically enabled and cannot be disabled. *) |
*) Cloud Control
A virtual power plant is an interconnection of several power plant operators to form a network. This network can be controlled via the cloud over the internet. The inverter must have an active internet connection for this. System data is transmitted.
The Fronius Solar API is an IP-based, open JSON interface. When enabled, IOT devices on the local network can access inverter information without authentication. For security reasons, the interface is deactivated at the factory and must be activated if it is required for a third-party application (e.g. EV charger, smart home solutions, etc.) or the Fronius Wattpilot.
For monitoring, Fronius recommends using Fronius Solar.web, which provides secure access to inverter status and production information.
When performing a firmware update to version 1.14.x, the setting of the Fronius Solar API is adopted. The Solar API is activated for systems with a version below 1.14.x. Above this version it is deactivated but can be switched on and off in the menu.
Activate the Fronius Solar API
Enable the "Activate communication via Solar API" function on the user interface of the inverter in the "Communication" → "Solar API" menu.
This menu displays information about the connections and the current connection status. In case of problems with the connection, a short error description is shown.
Danger due to unauthorised error analyses and repair work.
Fault analyses and repair work on the photovoltaic system may only be carried out by installers/service technicians from authorised specialist companies in accordance with national standards and guidelines.
Risk due to unauthorised access.
Incorrectly set parameters can negatively influence the public grid and/or the inverter feeding energy into the grid, and lead to a loss of conformity with the standard.
The parameters may only be adjusted by installers/service technicians from authorised specialist companies.
Do not give the access code to third parties and/or unauthorised persons.
Risk due to incorrectly set parameters.
Incorrectly set parameters can negatively influence the public grid and/or cause faults and failures on the inverter, and lead to the loss of conformity with the standard.
The parameters may only be adjusted if the energy provider permits or requires this.
Only adjust the parameters taking into account the nationally applicable standards and/or directives and the specifications of the energy provider.
The "Country Setup" menu area is intended exclusively for installers/service technicians from authorised specialist companies. To request the access code required for this menu area, see chapter Requesting inverter codes in Solar.SOS.
The selected country setup for the respective country contains preset parameters according to the nationally applicable standards and requirements. Depending on local grid conditions and the specifications of the energy provider, adjustments to the selected country setup may be necessary.
The "Country Setup" menu area is intended exclusively for installers/service technicians from authorised specialist companies. The inverter access code required for this menu area can be requested in the Fronius Solar.SOS portal.
Energy companies or grid operators may stipulate export limitations for an inverter (e.g. max. 70% of kWp or max. 5 kW).
The export limitation takes account of self-consumption by the household before the power of an inverter is reduced:
With the inverter, any PV power that is not allowed to be fed into the public grid is used to charge the battery instead and/or used by the Fronius Ohmpilot so that it does not go to waste. The export limitation is only active if the power of feeding in is higher than the set power reduction.
"Power limitation" deactivated
The inverter converts the entire available PV power and feeds it into the public grid.
"Power limitation" activated
Feed-in is limited with the following selection options:
Example: "Limit per Phase" (setting value: 2,000 W | ||||
| Phase 1 | Phase 2 | Phase 3 | Total |
Max. possible production [Wp] | 2,000 | 2,000 | 2,000 | 6,000 |
Set value | 1,000 | 3,000 | ||
Load demand in the household network [W] | 2,000 | 3,000 | 5,000 | 10,000 |
Load coverage in the household network via PV system [W] | 1,000 | 3,000 | ||
Purchase from the public grid [W] | 1,000 | 2,000 | 4,000 | 7,000 |
"Total DC power of the Entire System"
Input field for the total DC system power in Wp.
If there are multiple Fronius inverters, this value is used when the "Maximum Grid Feed-In Power" is specified in %.
Input field for the "Maximum Grid Feed-In Power" in W or % (setting range: -10 to 100%).
If there is no meter in the system, the inverter limits the power of feeding in to the set value. Activate the function "Reduce inverter power to 0% if meter connection has been lost." for control in the event of a Fail-Safe.
Example: Export Limitation | |
PV system to Fronius inverter | 5,000 W |
Loads in the house | 1,000 W |
Maximum grid feed-in power | 60% = 3,000 W |
Case 1: The battery can be charged | |
Power at grid feed-in point | 0 W |
Power at inverter output | 1,000 W |
Power into the battery | 4,000 W |
Case 2: The battery cannot be charged | |
Power at grid feed-in point | 3,000 W |
Power at inverter output | 4,000 W |
Power into the battery | 0 W |
In this example, no more than 3,000 W may be fed into the public grid at the grid feed-in point. However, any loads that are located between the inverter and the grid feed-in point can be supplied by additional power from the inverter. |
"Soft Limit"
If this value is exceeded, the inverter will regulate down to the set value within the time required by national standards and regulations.
"Hard Limit Trip"
If this value is exceeded, the inverter switches off within max. 5 seconds. This value must be higher than the value set for "Soft Limit".
Example 1: Fronius SnapINverter ≤ Fronius Symo GEN24 SC
Only one primary meter is required for the Fronius Symo GEN24 SC inverter.
The power values shown are an example. Inverter configurations with power values other than those shown in the example are possible, taking into account the criteria for this example.
IMPORTANT!
Zero feed-in is not possible when using two inverters.
Example 2a: Fronius SnapINverter > Fronius Symo GEN24 SC
Two primary meters are required for the inverters.
IMPORTANT!
With two primary meters at the feed-in point without a secondary meter, Fronius SnapINverter and Fronius Symo GEN24 SC inverters cannot be displayed as a combined PV system in Solar.web. Two individual PV systems must be created in Solar.web.
Example 2b: Fronius SnapINverter > Fronius Symo GEN24 SC
Two primary meters and one secondary meter are required for the inverters.
IMPORTANT!
In order to be able to record all PV system data in Solar.web in full, only the Fronius Symo GEN24 SC inverter may be created in this PV system. The Fronius SnapINverter data is transmitted from the secondary meter to the Fronius Symo GEN24 SC inverter and thus displayed in Solar.web.
We recommend that you set up the Fronius SnapINverter as a separate additional PV system in Solar.web for servicing and maintenance work (e.g. status codes, online updates, etc.).
General
In this menu item, settings relevant for a distribution network operator (DNO) are made. An effective power limitation in % and/or a power factor limitation can be set.
IMPORTANT!
Select the "Technician" user for settings in this menu item, enter and the password for the "Technician" user and confirm. Settings in this menu area must only be made by trained and qualified personnel.
"Input pattern" (assignment of individual I/Os)
1 click = white (contact open)
2 clicks = blue (contact closed)
3 clicks = grey (not used)
"Power factor (cos φ)"
"ind" = inductive
"cap" = capacitive
"DNO feedback"
When the rule is enabled, output "DNO feedback" (pin 1 recommended) must be configured (e.g. for operating a signalling device).
For "Import" or "Export", the data format *.fpc is supported.
Control priorities
For setting the control priorities for the ripple control signal receiver, the export limitation and control via Modbus.
1 = highest priority, 3 = lowest priority
The ripple control signal receiver and the I/Os terminal of the inverter can be connected to one another in accordance with the connection diagram.
If the distance between the inverter and the ripple control signal receiver exceeds 10 m, at least a CAT 5 cable is recommended and the shield must be connected at one end to the push-in terminal of the data communication area (SHIELD).
(1) | Ripple control signal receiver with 4 relays, for effective power limiting. |
(2) | I/Os of the data communication area. |
The settings for 4-relay mode are stored.
(1) | Ripple control signal receiver with 3 relays, for effective power limiting. |
The settings for 3-relay mode are stored.
(1) | Ripple control signal receiver with 2 relays, for effective power limiting. |
The settings for 2-relay mode are stored.
(1) | Ripple control signal receiver with 1 relay, for effective power limiting. |
The settings for 1-relay mode are stored.
The grid operator may request the connection of one or more inverters to a ripple control receiver in order to limit the effective power and/or the power factor of the photovoltaic system.
The following Fronius inverters can be connected to a ripple control receiver via a distributor (coupling relay):
IMPORTANT!
The "4-relay mode" setting (see Connection diagram - 4 relay andI/O power management settings - 4 relays) must be enabled on the user interface of each inverter connected to the ripple control receiver.
Description
The "Autotest" can be used to check the protection function required by Italian standards for monitoring the voltage and frequency limit values of the inverter during commissioning. In normal operation, the inverter constantly checks the current voltage and frequency actual value of the grid.
After starting the autotest, various individual tests run automatically one after the other. Depending on network conditions, the duration of the test is about 15 minutes.
IMPORTANT!
The inverter may only be commissioned in Italy after an autotest has been successfully performed (CEI 0-21). If the autotest is not passed, feeding energy into the grid is not permitted. Once the autotest is started, it must be completed successfully. The autotest cannot be started during backup power operation.
U max | Test for checking the maximum voltage in phase conductors |
U min | Test for checking the minimum voltage in phase conductors |
f max | Test for checking the maximum grid frequency |
f min | Test for checking the minimum grid frequency |
f max alt | Test for checking an alternative maximum grid frequency |
f min alt | Test for checking an alternative minimum grid frequency |
U outer min | Test for checking the minimum external voltages |
U longT. | Test for checking the 10-minute mean voltage value |
Note on the autotest
The limit values are set in the "Grid Code" menu.
The access code for the "Grid Code" menu corresponds to the installer code (PROFI menu) and is only made available after a written request to Fronius. A corresponding application form is available from the national technical support.
A surge protective device (SPD) protects against temporary overvoltages and dissipates surge currents (e.g. lightning strike). Building on an overall lightning protection concept, the SPD helps to protect your PV system components.
For detailed information on the wiring diagram of the surge protective device, see chapter Surge protective device (SPD) on page (→).
If the surge protective device is triggered, the colour of the indicator changes from green to red (mechanical display) and the operation LED of the inverter lights up red (see chapter Button functions and LED status indicator on page (→)). The error code "1030 WSD Open" is displayed on the user interface of the inverter in the "System" → "Event Log" menu or in the user menu under "Notifications" as well as in Fronius Solar.web. In this case, the inverter must be repaired by an authorised specialist.
IMPORTANT!
The inverter also switches off if the 2-pin signal cable of the surge protective device is interrupted or damaged.
External surge protective device
To receive notification when external surge protective devices are triggered, it is recommended to connect the feedback contacts in series to the WSD input.
IMPORTANT!
IMPORTANT!
Danger due to electrical voltage on live parts of the photovoltaic system.
Disconnect live parts of the photovoltaic system on all pins and on all sides.
Secure against re-activation in accordance with national regulations.
Allow the capacitors of the inverter to discharge (2 minutes).
Check that the inverter is de-energised with a suitable measuring device.
The surge protective device (SPD) is an optional extra and can be retrofitted to the inverter.
For technical data, see chapter "Technical data" on page (→).
Disconnect connections from the solar module strings (+/-). Switch off the battery connected to the inverter.
Wait for the capacitors of the inverter to discharge (2 minutes).
Danger due to insufficiently dimensioned ground conductor.
Damage to the inverter due to thermal overload can result.
The national standards and guidelines must be observed for dimensioning the ground conductor.
Loosen the two screws on the underside of the housing cover by rotating them 180° to the left using a screwdriver (TX20). Then lift the housing cover away from the inverter at the bottom and detach from above.
Loosen the five screws of the connection area cover by rotating them 180° to the left using a screwdriver (TX20).
Remove the connection area divider by pressing the snap tabs.
Remove the DC push-in terminals from the slots and disconnect them from the cables (only necessary if the installation already exists).
Connect the supplied PV+/PV- cables to the respective connections.
IMPORTANT!
Note the labelling of the cables when connecting.
Connect the supplied cables to the respective connections on the PC board.
IMPORTANT!
The plugs must be connected onto the PC board as far as they will go.
Insert the PC board into the inverter and secure with the four screws (TX20) supplied at a torque of 1.0 ‑ 1.2 Nm.
IMPORTANT!
Depending on national standards and guidelines, a larger cross section of the ground conductor may be required.
Dimension the cable cross section of the ground conductor according to the national standards and guidelines and fit a ring cable lug (inner diameter: 4 mm, outer diameter: max. 10 mm) as well as a corresponding ferrule. Fasten the ground conductor to the PC board with a torque of 1.5 Nm.
Fasten the ground conductor to the first input from the bottom of the ground electrode terminal using a screwdriver (TX20) and a torque of 1.8 - 2 Nm.
IMPORTANT!
The use of other inputs can make it difficult to insert the connection area divider or damage the ground conductor.
Strip the insulation on the single conductors by 12 mm and secure to the corresponding slot of the terminal on the PC board with a torque of 1.2 - 1.5 Nm.
IMPORTANT!
The cable cross-section must be selected according to the specifications for the respective inverter power category (see chapter Permissible cables for the electrical connection on page (→)).
Push the DC push-in terminals into the corresponding slot until there is an audible click.
Re-insert the connection area divider.
* Lay the ground conductor in the integrated cable duct.
IMPORTANT!
Make sure when inserting the connection area divider that the ground conductor is not damaged (kinked, pinched, crushed, etc.).
Remove the factory installed bypass on the push-in WSD terminal.
Connect the signal cable to the push-in WSD terminal on the IN- and IN+ slots, observing the labelling.
Check whether the WSD switch is in position 1, adjust if necessary (factory setting: position 1).
Press on the lower part of the housing cover and tighten the two screws by rotating them 180° to the right using a screwdriver (TX20).
Connect the solar module strings (+/-). Switch on the battery connected to the inverter.
Set the DC disconnector to the "On" switch position. Switch on the automatic circuit breaker.
The DC Connector Kit GEN24 (item number: 4,240,046) enables the connection of PV connection strings with a total current above 28 A.
IMPORTANT!
If the Arc Fault Circuit Interrupter (AFCI) integrated in the inverter is used for the requirement according to IEC 63027 for arc detection, DC Connector Kit GEN24 must not be used. The installation must be carried out in accordance with the nationally applicable standards and directives.
IMPORTANT!
IMPORTANT!
IMPORTANT!
IMPORTANT!
The DC Connector Kit GEN24 is an optional extra and can be retrofitted to the inverter.
Danger due to insufficiently dimensioned DC cables.
When dimensioning the DC cables, adhere to the specifications in Permissible cables for the electrical connection on page (→).
Insert the DC Connector GEN24 into the inverter and secure with the two screws (TX20) supplied at a torque of 1.0 ‑ 1.2 Nm.
Manually push the DC cables through the DC bushings.
Press the lock on the back of the terminal and remove the DC terminals.
Strip the insulation of the single conductors by 18-20 mm.
Use a slotted screwdriver to push in the lock on the terminal. Insert the stripped single conductor into the slot provided, in each case as far as it will go. Then withdraw the slotted screwdriver from the lock.
This may result in severe damage to the inverter.
Check the voltage (max. 1000 VDC) and polarity of the DC cabling with a suitable measuring instrument.
Place the cover on the connection area. Tighten the 5 screws by rotating them 180° to the right in the indicated order using a screwdriver (TX20).
Press on the lower part of the housing cover and tighten the 2 screws by rotating them 180° to the right using a screwdriver (TX20).
The inverter is designed in such a way that no additional maintenance work builds up. Nevertheless, a few points must be considered during operation to ensure that the inverter works perfectly.
Maintenance and servicing may only be carried out by Fronius-trained service technicians.
Clean the inverter as required with a damp cloth.
Do not use cleaning agents, abrasives solvents or similar to clean the inverter.
The DC disconnector is used only to switch off power to the power stage set. When the DC disconnector is turned off, the connection area is still energized.
Danger from grid voltage and DC voltage from PV modules.
The connection area must only be opened by an authorised electrician.
The separate power stage set area must only be opened by Fronius-trained service technicians.
Prior to any connection work, disconnect the inverter on the AC side and the DC side.
Danger of residual voltage from capacitors.
If the inverter is operated in dusty environments, dirt may build up on the heat sink and fan.
This may result in a loss of power due to insufficient cooling of the inverter.
Make sure that the ambient air can always flow through the inverter's ventilation slots unimpeded.
Remove any build-up of dirt on the heat sink and the fan.
Switch off power to the inverter and wait for the specified time (2 minutes) until the capacitors have discharged and the fan has shut down.
Turn the DC disconnector to the "Off" position.
Loosen the screws on the underside of the housing cover by rotating them 180° to the left using a screwdriver (TX20). Then lift the housing cover away from the inverter at the bottom and detach from above.
Remove any build-up of dirt on the heat sink and fan using compressed air, or a cloth or brush.
Risk due to damage to the fan bearing from improper cleaning.
Excessive speed and pressure on the fan bearing can cause damage.
Block the fan and clean it with compressed air.
When using a cloth or brush, clean the fan without applying pressure to the fan.
Waste electrical and electronic equipment must be collected separately and recycled in an environmentally responsible manner in accordance with the EU Directive and national law. Used equipment must be returned to the distributor or through a local, authorised collection and disposal system. Proper disposal of the old device promotes sustainable recycling of material resources. Ignoring this may lead to potential health/environmental impacts.
Packaging materials
Collected separately. Check your municipality’s regulations. Reduce the volume of the box.
Detailed, country-specific warranty conditions are available at www.fronius.com/solar/warranty.
To obtain the full warranty period for your newly installed Fronius product, please register at www.solarweb.com.
Device name | Current converter | Item number |
Fronius Smart Meter 63A-3 | 43,0001,1473 | |
Fronius Smart Meter 50kA-3 | 43,0001,1478 | |
Fronius Smart Meter TS 65A-3 | 43,0001,0044 | |
Fronius Smart Meter TS 5kA-3 | 43,0001,0046 | |
Fronius Smart Meter WR | 43,0001,3591 |
K1 and K2 - AC installation contactor with auxiliary contact | |||
Number of pins | 3-pin or 4-pin | ||
Rated current | depends on house connection | ||
Coil voltage | 230 VAC | ||
Rated frequency | 50/60 Hz | ||
Coil fuse | 6 A | ||
Min. short circuit current | 3 kA (make contacts) | ||
Test standard | IEC 60947-4-1 | ||
Auxiliary contact | |||
Number of NC contacts | 1 | ||
Switching voltage | 12-230 V @ 50/60 Hz | ||
Min. nominal current | 1 A | ||
Min. short circuit current | 1 kA | ||
Examples of contactors and relays | ISKRA IK63-40 / Schrack BZ326461 |
K1 and K2 - DC installation contactor with auxiliary contact (Fault Ride Through) | |||
Coil voltage | 24 VDC | ||
Switching voltage | 24 VDC | ||
Examples of contactors and relays | Finder 22.64.0.024.4710 |
K3 - modular relay | |||
Number of changeover contacts | 2 | ||
Coil voltage | 12 VDC | ||
Examples of contactors and relays | Finder 22.23.9.012.4000 / Schrack relay RT424012 (bracket RT17017, relay base RT78725) |
K4 and K5 - installation contactor | |||
Number of NC contacts | 2 (25 A) | ||
Coil voltage | 230 V AC (2P) | ||
Examples of contactors and relays | ISKRA IKA225-02 |
Device name | Current transformer | Item number |
Q1 manual changeover switch | |||
Coil voltage | 230/400 VAC | ||
Example Hager | HIM306 + HZC312 / HIM406 + HZC312 | ||
Example Kraus&Naimer | KA63B.T903.VE2 + 2 * K0 H010/A11-VE KA40B.T904.VE2.F437 + 2 * K0 H010/A11-VE |
Status codes are displayed on the user interface of the inverter in the "System" → "Event Log" menu or in the user menu under "Notifications" or in Fronius Solar.web*.
* | with corresponding configuration, see chapter Fronius Solar.web on page (→). |
Cause: | A device connected in the WSD chain has interrupted the signal line (e.g. a surge protective device) or the bypass ex works has been removed and no trigger device has been installed. |
Remedy: | If the SPD surge protective device is triggered, the inverter must be repaired by an authorised specialist. |
OR: | Install the bypass ex works or a trigger device. |
OR: | Set the WSD (wired shutdown) switch to position 1 (WSD primary device). |
WARNING!Danger due to work that has been carried out incorrectly. This can result in serious injury and damage to property. Installing and connecting a surge protective device (SPD) must only be carried out by service personnel trained by Fronius and only within the scope of the respective technical regulations. Follow the safety rules. |
DC input data | |
MPP voltage range | 295 – 800 V |
Max. connected load (PPV max) |
Max. processable PV power |
Max. input voltage | 1000 V |
Feed-in start-up input voltage in grid operation 5) | 80 V |
Max. input current |
Max. short circuit current of module array (ISC PV) |
Max. total short circuit current of module array |
Max. inverter backfeed current to the array 3) |
Number of inputs - PV 1 | 2 |
Number of inputs - PV 2 | 1 |
Max. capacity of the module array to earth |
Insulation resistance test limit value between module array and earth (on delivery) 10) | 100 kΩ |
Adjustable range of insulation resistance test between module array and earth 9) | 10 – 10,000 kΩ |
Limit value and tripping time of the sudden residual current monitoring (on delivery) | 30 / 300 mA / ms |
Limit value and tripping time of the continuous residual current monitoring (on delivery) | 300 / 300 mA / ms |
Adjustable range of continuous residual current monitoring 9) | 30 – 300 mA |
Cyclic repetition of the insulation resistance test (on delivery) | 24 h |
Adjustable range for the cyclic repetition of the insulation resistance test | - |
DC input data, battery 8) | |
Max. voltage 11) | 531 V |
Min. voltage | 160 V |
Max. current | 22 A |
Max. output | 12,000 W |
DC inputs | 1 |
AC input/output data | |
Rated power (Pnom) | 12,000 W |
Max. output power | 12,000 W |
Rated apparent power | 12,000 VA |
Nominal grid voltage | 3 ~ NPE 220 V / 380 V |
Min. grid voltage | 154 V 1) |
Max. grid voltage | 280 V 1) |
Max. output current | 18.5 A |
Nominal output current (at 230 V) | 17.4 A |
Current (inrush) 6) | 9.9 A / 4 ms |
Nominal frequency | 50/60 Hz 1) |
Initial short circuit alternating current / phase IK | 18.5 A |
Nominal frequency for Full Backup | 53/63 Hz 1) |
Total harmonic distortion | < 3.5% |
Power factor cos phi 2) | 0 – 1 (adjustable) |
Max. permitted mains impedance Zmax on PCC 4) | None |
Maximum output fault current / duration | 80.7 A / 10 ms |
AC output data PV Point / PV Point Comfort | |
Max. output power | 4255 W (for 5 s) |
Rated power | 3000 W |
Nominal output current | 13 A |
Nominal grid voltage | 1 ~ NPE 220 V / 230 V / 240 V |
Nominal frequency | 53/63 Hz 1) |
Switching time | < 90 s |
Power factor cos phi 2) | 0 – 1 |
AC output data Full Backup 8) | |
Max. output power | 12,765 W (for 5 s) |
Max. output power (per phase) | 4255 W (for 5 s) |
Rated power | 12,000 W |
Rated power (per phase) 7) | 4133 W |
Nominal output current (per phase) | 16 A |
General data | |
Maximum efficiency | 98.3% |
European efficiency (Umpp nom) | 98.1% |
European efficiency (Umpp max) | 97.9% |
European efficiency (Umpp min) | 97.2% |
Self-consumption at night | ≤ 10 W |
Cooling | Controlled forced-air ventilation |
Protection class | IP 66 |
Dimensions H x W x D | 595 × 529 × 180 mm |
Weight | 22.8 kg |
Inverter topology | Non-insulated transformerless |
Permitted ambient temperature | -25 °C – +60 °C |
Permissible humidity | 0 – 100% (incl. condensation) |
EMC emission class | B |
DC/AC overvoltage category | 2 / 3 |
Pollution degree | 2 |
Sound pressure | 47 dB(A) |
Safety class (in accordance with IEC 62103) | 1 |
Protection devices | |
DC isolation measurement | Warning / shutdown at RISO < 100 kOhm |
Overload performance | Operating point shift, power limitation |
DC disconnector | Integrated |
RCMU | Integrated |
RCMU classification | The software class of the safety platform(s) is specified as a class B control function (single channel with periodic self-test) according to IEC 60730 Annex H. |
Active anti-islanding method | Frequency conversion method |
AFCI | Integrated |
AFPE (AFCI) classification (according to IEC 63027) 12) | = F-I-AFPE-1-3-1 |
Data communication | |
WLAN SMA-RP connection | 802.11b/g/n (WPA, WPA2) |
Ethernet (LAN) | RJ 45, 10/100 MBit |
Wired shutdown (WSD) | Max. 28 devices / WSD chain |
Modbus RTU SunSpec (2x) | RS485 2-wire |
Voltage level of digital inputs | Low: min. 0 V – max. 1.8 V |
Input currents of digital inputs | Depending on the input voltage; |
Total power for digital output (for internal supply) | 6 W at 12 V (USB not connected) |
Power per digital output | 1 A at >12.5 V – 24 V |
Datalogger/web server | Integrated |
DC input data | |
DC inputs | 1 |
General data | |
Weight | 22.8 kg |
RCMU | Integrated |
AFCI | Integrated |
WLAN | |
Frequency range | 2412–2462 MHz |
Channels / power used | Channel: 1–11 b,g,n HT20 |
Modulation | 802.11b: DSSS (1 Mbps DBPSK, 2 Mbps DQPSK, 5.5/11 Mbps CCK) |
General data | |
Continuous operating current (Icpv) | < 0.1 mA |
Rated discharge current (In) | 20 kA |
Lightning surge current (limp) | 6.25 kA |
Protection level (Up) | 4 kV |
Short-circuit strength PV (Iscpv) | 15 kA |
Disconnector | |
Thermal disconnector | Integrated |
External fuse | None |
Mechanical properties | |
Disconnection indicator | Mechanical indicator (red) |
Remote communication of the connection interruption | Output on the changeover contact |
Housing material | Thermoplastic UL-94-V0 |
Test standards | IEC 61643-31 / DIN EN 50539-11 |
1) | The values stated are defaults; the inverter is configured specifically to suit the requirements of the relevant country. |
2) | Depending on the country setup or device-specific settings (ind. = inductive; cap. = capacitive). |
3) | Maximum current from a defective PV module to all other PV modules. From the inverter itself to the PV side of the inverter, it is 0 A. |
4) | Guaranteed by the electrical configuration of the inverter. |
5) | For backup power mode (PV Point) without a battery, a minimum voltage of 150 V is required. |
6) | Current peak when switching on the inverter. |
7) | The sum of the rated power per phase must not exceed the rated power of the inverter. |
8) | Valid for Fronius inverter with battery support. |
9) | Specified values are standard values; depending on the requirement and PV power, these values must be adjusted accordingly. |
10) | Specified value is a max. value; exceeding the max. value may negatively affect the function. |
11) | The system solution with suitable disconnection device in the event of a fault for the voltage range up to max. 700 V is currently not available. |
12) | Software class B (single-channel with periodic self-test) per IEC 60730-1 Annex H. |
General data | |
Product name | Benedict LS32 E 7905 |
Rated insulation voltage | 1000 VDC |
Rated impulse withstand voltage | 8 kV |
Suitability for insulation | Yes, DC only |
Utilisation category and / or PV utilisation category | In accordance with IEC/EN 60947-3 utilisation category DC-PV2 |
Rated short-time withstand current (lcw) | Rated short-time withstand current (lcw): 1000 A |
Rated short-circuit making capacity (lcm) | Rated short-circuit making capacity (lcm): 1000 A |
Rated operating current and rated breaking capacity | ||||
Rated operating voltage (Ue) | Rated operating current (le) | I(make) / I(break) | Rated operating current (le) | I(make) / I(break) |
≤ 500 VDC | 14 A | 56 A | 36 A | 144 A |
600 VDC | 8 A | 32 A | 30 A | 120 A |
700 VDC | 3 A | 12 A | 26 A | 88 A |
800 VDC | 3 A | 12 A | 17 A | 68 A |
900 VDC | 2 A | 8 A | 12 A | 48 A |
1000 VDC | 2 A | 8 A | 6 A | 24 A |
Number of pins | 1 | 1 | 2 | 2 |