IMPORTANT!
This unit must be operated in accordance with the technical specifications datasheet. This document is available on the corporate website of the manufacturer.
Danger from crushing due to the incorrect handling of attachments and connection parts.
Injuries to limbs may result.
To avoid muscle strain or injury, use proper lifting techniques and if required use a lifting aid.
When lifting up, putting down, and attaching the inverter, use the integrated grips.
When fitting any attachments, ensure that no limbs are located between the attachment and the inverter.
Do not hold onto the terminals when locking and unlocking.
IMPORTANT!
This unit must be operated in accordance with the technical specifications datasheet. This document is available on the corporate website of the manufacturer.
Danger from crushing due to the incorrect handling of attachments and connection parts.
Injuries to limbs may result.
To avoid muscle strain or injury, use proper lifting techniques and if required use a lifting aid.
When lifting up, putting down, and attaching the inverter, use the integrated grips.
When fitting any attachments, ensure that no limbs are located between the attachment and the inverter.
Do not hold onto the terminals when locking and unlocking.
IMPORTANT!
This unit must be operated in accordance with the technical specifications datasheet. This document is available on the corporate website of the manufacturer.
Danger from crushing due to the incorrect handling of attachments and connection parts.
Injuries to limbs may result.
To avoid muscle strain or injury, use proper lifting techniques and if required use a lifting aid.
When lifting up, putting down, and attaching the inverter, use the integrated grips.
When fitting any attachments, ensure that no limbs are located between the attachment and the inverter.
Do not hold onto the terminals when locking and unlocking.
Warnings are intended to warn people of possible injuries and to avoid personal injury and damage to the product. They relate to individual actions with and on the product.
Indicates an immediately dangerous situation.
Serious injury or death will result if the danger is not avoided.
Action step to escape the situation.
Indicates a potentially dangerous situation.
Serious injury or death may result if the danger is not avoided.
Action step to escape the situation.
Indicates a potentially dangerous situation.
Minor or moderate injury may result if the danger is not avoided.
Action step to escape the situation.
Indicates a situation that may result in property damage.
If the situation is not avoided, impaired work results, material damage to the product or other property are the possible consequences.
Action step to avoid the situation.
Safety instructions are designed to ensure safe product use. They are preventive and help to inform users about the fundamental risks involved when dealing with the product. They do not refer specifically to individual actions with and on the product.
All installations must comply with national and local electrical codes and standards.
In addition to the Operating Instructions, all applicable local regulations regarding accident prevention and environmental protection must also be followed.
All safety and danger notices on the device:Any safety devices that are not fully functional must be repaired by an authorized specialist before the device is switched on.
Never bypass or disable protection devices.
For the location of the safety and danger notices on the device, refer to the chapter headed "Warning notices on the device" in the Operating Instructions for your device.
Any equipment malfunctions which impair safety must be remedied before the device is turned on.
Operation or storage of the machine outside the stipulated area will be deemed as not in accordance with the intended purpose.
For exact information on permitted environmental conditions, please refer to the technical data.
During operation, due to the high electrical voltages and currents, local electromagnetic fields (EMF) are generated. Electromagnetic fields occur:
The applicable limit values for human exposure are observed when used in line with the intended use and a minimum distance of 20 cm is observed. If these limit values are complied with, according to current scientific knowledge, no negative health effects are to be expected.
Due to possible health risks, the following persons must consult their doctor before being near photovoltaic systems:
In certain cases, even though a device complies with the standard limit values for emissions, it may affect the application area for which it was designed (e.g., when there is equipment that is susceptible to interference at the same location or if the site where the device is installed is close to either radio or television receivers). If this is the case, the operator is obliged to take action to rectify the situation.
This system has backup power functions, which enable a replacement power supply to be established in the event of a failure of the public grid.
Where an automatic backup power supply is installed, a backup power warning notice (https://www.fronius.com/en/search-page, item number: 42,0409,0275) must be fitted on the electrical distributor.
Maintenance and installation work in the home network requires both disconnection on the utility side and deactivation of the replacement power mode by opening the integrated DC disconnector on the inverter.
The function of the residual current devices for the backup power supply must be checked at regular intervals (according to the manufacturer's instructions), but at least twice a year.
A description on how to perform the test operation can be found in the backup power checklist (https://www.fronius.com/en/search-page, item number: 42,0426,0365).
Depending on the insolation conditions and the battery state of charge, the backup power supply is automatically deactivated and activated. This can cause the backup power supply to unexpectedly return from standby mode. Therefore, installation work can only be performed on the home network when the backup power supply is deactivated.
Influencing factors on the total power in backup power mode:
Reactive power
Electrical loads with a power factor not equal to 1 also require reactive power in addition to effective power. The reactive power also loads the inverter. Therefore, to correctly calculate the actual total power, it is not the rated power of the load that is relevant, but the current caused by effective and reactive power.
Devices with a high reactive power are mainly electric motors such as:
High starting current
Electrical loads that need to accelerate a large mass usually require a high starting current. This can be up to 10 times higher than the nominal current. The maximum current of the inverter is available for the starting current. Loads with starting currents that are too high therefore cannot be started/operated, even though the nominal output of the inverter suggests that they can. When dimensioning the backup power circuit, the connected load power and any starting current must also be taken into account.
Devices with high starting currents are, for example:
IMPORTANT!
Very high starting currents can cause short-term distortion or a drop in output voltage. The simultaneous operation of electronic devices in the same backup power supply system should be avoided.
IMPORTANT!
The inverter may only be operated within the limits of its technical capabilities. Operation outside of its technical capabilities can cause the inverter to shut down.
Connection of a point in the device, system, or installation to ground to protect against electric shock in the event of a fault. When installing an inverter from safety class 1 (see Technical data), a ground conductor connection is required.
When connecting the ground conductor, ensure that it is secured to prevent unintentional disconnection. All of the points listed in the chapter headed Connecting the inverter to the public grid (AC side) on page (→) must be observed. When using cable glands, ensure that the ground conductor is last to be subjected to a load in the event of a failure of the cable gland. The respective national standards and regulations and requirements for minimum cross-section must be observed when connecting the ground conductor.
Limited rapid shutdown function in backup power mode (PV Point and Essential Backup)
If PV Point or Essential Backup is configured, rapid shutdown cannot be triggered via the loss of grid connection. This can result in serious personal injury and damage to the PV system.
A WSD switch must be installed for all backup power modes (PV-Point and Essential Backup) (see Installing the WSD (wired shutdown)). The rapid shutdown is then triggered via WSD.
When an RSD occurs, an entry appears in the Event Log menu: RsdTriggeredByLossOfAc (interruption by AC breaker) or RsdTriggeredBySwitch (interruption by WSD circuit)
In case a module-level shutdown equipment within the PV array is used in combination with the inverter, this labeling has to be used acording to NEC (Section 690.12), CSA C22.1 (Section 64-218):
In case a string-level shutdown equipment at the PV array is used in combination with the inverter, this labeling has to be used acording to NEC (Section 690.12), CSA C22.1 (Section 64-218):
Warning - The installer is responsible for the correct labeling of the PV system. The rapid shutdown requirement of the inverter is not affected by the FRT (fault ride through) capability, so the inverter is „Grid support interactive compatible“.
Warning - This photovoltaic rapid shutdown equipment (PVRSE) does not perform all of the functions of a complete photovoltaic rapid shutdown system (PVRSS). This PVRSE must be installed with other equipment to from a complete PVRSS that meets the requirements of NEC (NFPA 70) section 690.12 for controlled conductors outside the array. Other equipment installed in or on this PV system may adversly affect the operation of the PVRSS. It is the responsibility of the installer to ensure that the completed PV system meets the rapid shutdown functional requirements. This equipment must be installed according to the manufacturer´s installation instructions.
Self-test
A self-test of the RSD function can be performed manually or automatically. The automatic self-test relates only to the discharge circuit of the RSD function. All other RSD circuit components are produced so as to be fail-safe.
Sequence of automatic self-test:
In each startup procedure—prior to connection to the public grid—when there is sufficient DC voltage (40 V) the discharge circuit is activated for 10 ms and the feedback pin is checked prior to and during charging.
Sequence of manual self-test:
A manual self-test can be triggered by an interruption in the grid connection (e.g., AC breaker) or by the WSD trigger device (see also WSD (wired shutdown) on page (→)).
The discharge must be measured and checked using a multimeter.
Limited rapid shutdown function in backup power mode (PV Point and Essential Backup)
If PV Point or Essential Backup is configured, rapid shutdown cannot be triggered via the loss of grid connection. This can result in serious personal injury and damage to the PV system.
A WSD switch must be installed for all backup power modes (PV-Point and Essential Backup) (see Installing the WSD (wired shutdown)). The rapid shutdown is then triggered via WSD.
When an RSD occurs, an entry appears in the Event Log menu: RsdTriggeredByLossOfAc (interruption by AC breaker) or RsdTriggeredBySwitch (interruption by WSD circuit)
In case a module-level shutdown equipment within the PV array is used in combination with the inverter, this labeling has to be used acording to NEC (Section 690.12), CSA C22.1 (Section 64-218):
In case a string-level shutdown equipment at the PV array is used in combination with the inverter, this labeling has to be used acording to NEC (Section 690.12), CSA C22.1 (Section 64-218):
Warning - The installer is responsible for the correct labeling of the PV system. The rapid shutdown requirement of the inverter is not affected by the FRT (fault ride through) capability, so the inverter is „Grid support interactive compatible“.
Warning - This photovoltaic rapid shutdown equipment (PVRSE) does not perform all of the functions of a complete photovoltaic rapid shutdown system (PVRSS). This PVRSE must be installed with other equipment to from a complete PVRSS that meets the requirements of NEC (NFPA 70) section 690.12 for controlled conductors outside the array. Other equipment installed in or on this PV system may adversly affect the operation of the PVRSS. It is the responsibility of the installer to ensure that the completed PV system meets the rapid shutdown functional requirements. This equipment must be installed according to the manufacturer´s installation instructions.
Self-test
A self-test of the RSD function can be performed manually or automatically. The automatic self-test relates only to the discharge circuit of the RSD function. All other RSD circuit components are produced so as to be fail-safe.
Sequence of automatic self-test:
In each startup procedure—prior to connection to the public grid—when there is sufficient DC voltage (40 V) the discharge circuit is activated for 10 ms and the feedback pin is checked prior to and during charging.
Sequence of manual self-test:
A manual self-test can be triggered by an interruption in the grid connection (e.g., AC breaker) or by the WSD trigger device (see also WSD (wired shutdown) on page (→)).
The discharge must be measured and checked using a multimeter.
The inverter is equipped with a Power Line Communication (PLC) transmitter on the DC side. Its function is to ensure rapid shutdown in accordance with National Electric Code NEC 2023 Art. 690.12 and Canadian Electrical Code CSA C22.1:24 Art. 64-218. The PLC is implemented according to the specification “Communication Signal for Rapid Shutdown – SunSpec Interoperability Specification” (depending on national grid setup). Please visit www.sunspec.org for details.
To ensure compliance with all applicable regulations in your country and to ensure optimal reception among all recipients, please follow the recommendations below:Depending on the installation, an additional external AC and/or DC disconnect may be required if the inverter is installed in a location not easily accessible to utility or first responders. Contact your local authorities for additional information.
The wired shutdown (WSD) interrupts the inverter's grid power feed if the trigger device (switch, e.g., Emergency Stop or fire alarm contact) has been activated.
If the installation location requires inverter shutdown when the building fire alarm system is activated, the Wired Shut Down connection on the inverter can be used and connected to the building fire alarm system.
If an inverter (secondary device) fails, it is bypassed and the other inverters continue operating. If a second inverter (secondary device) or the inverter (primary device) fails, the operation of the entire WSD chain is interrupted.
For installation, see Installing the WSD (wired shutdown) on page (→).
If the installation location requires inverter shutdown when the building fire alarm system is activated, the Wired Shut Down connection on the inverter can be used and connected to the building fire alarm system.
The inverter is equipped with an RCMU (RCMU = residual current monitoring unit) according to UL1741 CRD 3rd Edition (Non-Isolated EPS Interactive PV Inverters).
It monitors residual currents from the PV module up to the AC output and disconnects the inverter from the grid when an improper residual current is detected. If five faults are detected within a period of 24 hours, grid power feed operation can also be permanently interrupted until a manual reconnection has been performed.
In the case of PV systems with ungrounded PV source circuits, the inverter checks the resistance between the positive or negative pole of the PV system and the ground potential before feeding energy into the grid. In the event of a short circuit between the DC+ or DC- cable and ground (e.g. due to inadequately insulated DC cables or damaged solar modules), the inverter is prevented from feeding energy into the grid.
An AFCI (arc fault circuit interrupter) protects against arc faults in accordance with National Electric Code NEC 2023 Art. 690.11 and Canadian Electrical Code CSA C22.1:24 Art. 64-216 and, in the narrower sense, is a protection device in the event of contact errors. The AFCI evaluates faults that occur in the current and voltage flow on the DC side using an electronic circuit and shuts down the circuit if a contact error is detected. This significantly reduces potential overheating and fire risk at poor contact points.
Danger from faulty or incorrect DC installation.
This may result in a risk of damage and, as a consequence, risk of fire in the PV system due to prohibited thermal loads that occur during an arc.
Check the plug connections to ensure that they are correct.
Repair faulty insulation correctly.
Perform connection work in line with the instructions.
IMPORTANT!
Fronius will not bear any costs for production downtimes, installation costs, etc., which may arise due to a detected electric arc and its consequences. Fronius accepts no liability for damage which may occur despite the integrated Arc Fault Circuit Interrupter/interruption (e.g., due to a parallel arc).
IMPORTANT!
Active PV module electronics (e.g., power optimizers) can impair the function of the Arc Fault Circuit Interrupter. Fronius cannot guarantee the correct function of the Arc Fault Circuit Interrupter in combination with active PV module electronics.
Reconnection behavior
Grid power feed operation is interrupted for at least 5 minutes after an arc has been detected. Depending on the configuration, grid power feed operation is then automatically resumed. If several arcs are detected within a period of 24 hours, grid power feed operation can also be permanently interrupted until a manual reconnection has been performed.
If one of the following safety devices is triggered, the inverter switches to the standby state:
In the standby state, the inverter no longer feeds in and is disconnected from the grid by the opening of the AC relay.
The inverter is equipped with an integrated surge protection device according to UL1741 3rd Edition, CSA-C22.2 No.107.1-16 on the DC (Category II) and AC (Category IV) side. The surge protection device protects the system against damage caused by overvoltage.
If the integrated surge protection devices become damaged due to prolonged overvoltage exposure, the damage may not be covered under the terms of warranty. See warranty terms for more information.
Warning notices and safety symbols are located on the inverter. These warning notices and safety symbols must not be removed or painted over. They warn against incorrect operation, as this may result in serious injury and property damage.
Symbols on the rating plate: | |
Devices marked with the CSA certification mark satisfy the requirements of the relevant product standards for Canada and the USA. | |
This equipment has been tested and found to comply with the limits for a Class B digital device, pursuant to part 15 of the FCC rules. | |
This device complies with Industry Canada licence-exempt RSS standard(s) and part 15 of the FCC Rules. Operation is subject to the following two conditions:
Safety symbols: | |
Danger of serious injury and property damage due to incorrect operation | |
Do not use the functions described here until you have fully read and understood the following documents:
| |
Dangerous electrical voltage | |
Allow the capacitors of the inverter to discharge (2 minutes). | |
Warning notice text:
WARNING!
An electric shock can be fatal. Before opening the device, ensure that the input and output sides are de-energized.
Warning notices and safety symbols are located on the inverter. These warning notices and safety symbols must not be removed or painted over. They warn against incorrect operation, as this may result in serious injury and property damage.
Symbols on the rating plate: | |
Devices marked with the CSA certification mark satisfy the requirements of the relevant product standards for Canada and the USA. | |
This equipment has been tested and found to comply with the limits for a Class B digital device, pursuant to part 15 of the FCC rules. | |
This device complies with Industry Canada licence-exempt RSS standard(s) and part 15 of the FCC Rules. Operation is subject to the following two conditions:
Safety symbols: | |
Danger of serious injury and property damage due to incorrect operation | |
Do not use the functions described here until you have fully read and understood the following documents:
| |
Dangerous electrical voltage | |
Allow the capacitors of the inverter to discharge (2 minutes). | |
Warning notice text:
WARNING!
An electric shock can be fatal. Before opening the device, ensure that the input and output sides are de-energized.
The conventions regarding how information is presented in the document, which are set out below, have been defined in order to increase the readability and comprehensibility of the document.
Application notes
IMPORTANT! Indicates application notes and other useful information. It does not indicate a harmful or dangerous situation.
Software
Software functions and elements of a graphical user interface (e.g., buttons, menu items) are highlighted in the text with this mark up.
Example: Click Save.
Instructions for action
The servicing information contained in these Operating Instructions is intended only for the use of qualified personnel as defined by the NFPA 70. An electric shock can be fatal. Do not carry out any actions other than those described in the documentation.
All cables and leads must be secured, undamaged, insulated, and adequately dimensioned. Loose connections, scorched, damaged, or under-dimensioned cables and leads must be repaired immediately by qualified personnel.
Maintenance and repair work must only be carried out by an authorized specialist.
It is impossible to guarantee that externally (aka, third-party) procured parts are designed and manufactured to meet the demands made on them, or that they satisfy safety requirements. Use only original spare parts (also applies to standard parts).
Do not carry out any alterations, installations, or modifications to the device without first obtaining the manufacturer's permission.
Components that are not in perfect condition must be changed immediately.
Data security for network and Internet connection
Unsecured networks and a lack of safeguards can result in data loss and unauthorized access. Observe the following points for safe operation:
Operate inverters and system components on a private, secure network. A WiFi network is considered secure if security standard WPA 2 is satisfied as a minimum.
Keep the network devices (e.g., WiFi routers) up to date with the latest technology.
Keep the software and/or firmware updated.
Use a wired network to ensure a stable data connection.
For security reasons, do not make inverters and system components accessible from the Internet via port forwarding or Port Address Translation (PAT).
Use the solutions provided by Fronius for monitoring and remote configuration.
The optional communication protocol Modbus TCP/IP1) is an unsecured interface. Only use Modbus TCP/IP if no other secured data communication protocol (MQTT2)) is possible (e.g., compatibility with older Smart Meters).
1) TCP/IP - Transmission Control Protocol/Internet Protocol
2) MQTT - Message Queuing Telemetry Protocol
When you connect your device (and any associated devices) to the internet, the following device and operating data (device ID/identifier, device IP address, device time, configuration settings, hardware and software information, device status log files, serial number) is sent automatically to
Fronius International GmbH, Froniusstraße 1, 4643 Pettenbach, Austria, telephone +43(0) 7242241-0, email: contact@fronius.com (controller)
and stored.
The processing of this device and operating data is carried out for the purpose of ensuring the operational safety of the device (time synchronization, provision of updates). This processing is therefore necessary for the functionality of the device and thus for the fulfillment of the contract (Art. 6 (1) (b) GDPR).
If you do not wish to have such data processed, you must manually disable the device's internet connection.
In addition, the device and operating data is also processed for the purpose of providing services as part of a supplementary digital service for your device (such as solar.web or similar) as soon as you have registered your device with such a digital service (identification). This data is processed to provide the requested digital services and is therefore necessary for the fulfillment of the contract (Art. 6 (1) (b) GDPR).
Furthermore, this data processing is also carried out for maintenance and support purposes and for handling customer concerns as well as in warranty and guarantee cases (only in individual cases and given connection between device and internet). In this context, the device and operating data may also be passed on to our cooperation partners (third-party providers and suppliers). The processing of this data is necessary for maintenance and support purposes or for processing warranty and guarantee cases and thus for the fulfillment of the contract (Art. 6 (1) (b) GDPR).
Device and operating data are also processed for analysis and diagnostic purposes in order to gain insights into the functionality of the devices and improve them accordingly. This data processing is based on our legitimate interest (Art. 6 (1) (f) GDPR).
We store this data for as long as it is necessary to fulfill the existing contract with you. Any storage beyond this is carried out for legal reasons or if we have a legitimate interest in doing so. For more information on data processing for the solar.web-digital service, as well as our general privacy policy and your rights as a data subject, please visit https://www.fronius.com.
Fronius International GmbH retains the copyrights of these operating instructions.
Text, illustrations, and other media correspond to the technical state of the art at the time of publication. Fronius reserves the right to make changes. If you have any suggestions for improvement or have found a mistake in this document, we would be most grateful for your comments.
This product is intended for use and sale outside the Province of Québec. It does not meet the French language documentation and labeling requirements of Québec's Charter of the French Language. Accordingly, Fronius International GmbH does not offer this product for sale to, or for delivery to, any address within the Province of Québec.
By placing an order, the customer represents and warrants that they are not purchasing the product for use or resale within Québec. Fronius International GmbH disclaims all liability and warranty obligations for any products operated in Québec in violation of these restrictions.
The inverter transforms the direct current generated by the PV modules into alternating current. This alternating current is fed into the public grid and synchronized with the mains voltage in use. Moreover, the solar energy can also be stored in a connected battery for later use.
The inverter is intended for use in grid-connected photovoltaic systems. The inverter has backup power functions and switches to backup power mode if it has been wired accordingly*.
The inverter automatically monitors the public grid. Whenever conditions in the electric grid are inconsistent with standard conditions (e.g., grid switch-off, interruption), the inverter will immediately stop producing power and interrupt the supply of power into the grid.
The grid is monitored by monitoring the voltage, frequency, and islanding conditions.
After installation and commissioning, the inverter's operation is fully automatic; the inverter draws the maximum possible power from the solar modules.
Depending on the operating point, this power is used in the home, stored in a battery*, or fed into the grid.
As soon as the energy provided by the solar modules is no longer sufficient, the power from the battery is fed into the home network. Depending on the setting, power may also be obtained from the public grid in order to charge the battery*.
When its temperature gets too high, the inverter automatically reduces the output or charging power, or switches off completely, in order to protect itself.
Reasons for the temperature being too high include a high ambient temperature or insufficient heat dissipation (for example, inadequate heat dissipation when installed in switch cabinets).
| * | Depending on the device variant, suitable battery, corresponding cabling, settings, and local standards and regulations. |
The inverter transforms the direct current generated by the PV modules into alternating current. This alternating current is fed into the public grid and synchronized with the mains voltage in use. Moreover, the solar energy can also be stored in a connected battery for later use.
The inverter is intended for use in grid-connected photovoltaic systems. The inverter has backup power functions and switches to backup power mode if it has been wired accordingly*.
The inverter automatically monitors the public grid. Whenever conditions in the electric grid are inconsistent with standard conditions (e.g., grid switch-off, interruption), the inverter will immediately stop producing power and interrupt the supply of power into the grid.
The grid is monitored by monitoring the voltage, frequency, and islanding conditions.
After installation and commissioning, the inverter's operation is fully automatic; the inverter draws the maximum possible power from the solar modules.
Depending on the operating point, this power is used in the home, stored in a battery*, or fed into the grid.
As soon as the energy provided by the solar modules is no longer sufficient, the power from the battery is fed into the home network. Depending on the setting, power may also be obtained from the public grid in order to charge the battery*.
When its temperature gets too high, the inverter automatically reduces the output or charging power, or switches off completely, in order to protect itself.
Reasons for the temperature being too high include a high ambient temperature or insufficient heat dissipation (for example, inadequate heat dissipation when installed in switch cabinets).
| * | Depending on the device variant, suitable battery, corresponding cabling, settings, and local standards and regulations. |
Function | Primo GEN24 | Primo GEN24 Plus |
|---|---|---|
Backup power variant - PV Point (OP) | ||
Battery connection* | Available as an option** | |
Backup power variant - Essential Backup | Available as an option** |
| * | For suitable batteries, see chapter Suitable batteries. |
| ** | The functions are optionally available via Fronius UP (see chapter Fronius UP). |
| (1) | Mounting bracket (illustration) |
| (2) | Inverter |
| (3) | Housing cover |
| (4) | Quick Start Guide |
With Fronius UP*, optionally available functions can be added to the inverter by the authorized specialist company (see chapter Function overview).
| * | The availability of Fronius UP is country-specific. Click here for further information on availability. |
The inverter is designed to convert direct current from PV modules into alternating current and feed this power into the public grid. A backup power mode* is possible if the wiring is set up accordingly.
Intended use also means:Follow all grid operator regulations regarding energy fed into the grid and connection methods.
The inverter is a grid-connected inverter with backup power function and is not a stand-alone inverter. The following restrictions in backup power mode must therefore be observed:| * | Depending on the device variant, suitable battery, corresponding cabling, settings, and local standards and regulations. |
Ambient air is drawn in at the front of the device by the fan and blown out at the sides. The even heat dissipation allows several inverters to be installed next to each other.
Risk due to insufficient cooling of the inverter.
This may result in a loss of power in the inverter.
Do not block the fan (e.g., with objects that protrude through the touch guard).
Do not cover the ventilation slots, even partially.
Make sure that the ambient air can always flow through the inverter's ventilation slots unimpeded.
System owners and installers can easily monitor and analyze the PV system using Fronius Solar.web or Fronius Solar.web Premium. With the appropriate configuration, the inverter transmits data such as power, yield, load, and energy balance to Fronius Solar.web. More detailed information can be found at Solar.web - Monitoring & analysis.
Configuration is carried out via the Setup wizard, see chapter Installation with the app or Installation with the browser.
Requirements for configuration:| * | These specifications do not provide an absolute guarantee of flawless operation. High error rates in the transmission, fluctuating receptions or misfires can have an adverse effect on data transfer. Fronius recommends on-site testing to ensure that the connections meet the minimum requirements. |
The inverter can be found via the Multicast DNS (mDNS) protocol. We recommend searching for the inverter using the assigned host name.
The following data can be called up via mDNS:PV module | ||
Fronius GEN24 inverter | ||
Additional inverter in the system | ||
Battery | ||
Primary meter | ||
Secondary meter | ||
Loads in the system | ||
Additional loads and producers in the system | ||
PV Point | ||
Essential Backup | ||
Grid | ||
PV module | ||
Fronius GEN24 inverter | ||
Additional inverter in the system | ||
Battery | ||
Primary meter | ||
Secondary meter | ||
Loads in the system | ||
Additional loads and producers in the system | ||
PV Point | ||
Essential Backup | ||
Grid | ||
IMPORTANT!
For backup power mode, a Backup Frequency Offset can be set for loads in the backup power circuit (see Inverter).
In the hybrid photovoltaic system, batteries must only be connected to one inverter with battery support. Batteries cannot be split between multiple inverters with battery support. However, depending on the battery manufacturer, several batteries can be combined on one inverter.
| (1) | PV module – inverter – load/grid/battery |
| (2) | Battery – inverter – load/grid* |
| (3) | Grid – inverter – load/battery* |
* Charging the battery from the public grid depends on the settings and local standards and regulations.
Battery systems distinguish between different operating states. In each case, the relevant current operating state is displayed on the user interface of the inverter or in Fronius Solar.web.
Operating state | Description |
|---|---|
Normal operation | The energy is stored or drawn, as required. |
Min. state of charge (SoC) reached | The battery has reached the minimum SoC specified by the manufacturer or the set minimum SoC. The battery cannot be discharged further. |
Energy saving mode (standby) | The system has been put into energy-saving mode. Energy saving mode is automatically ended as soon as sufficient surplus power is available again. |
Start | The battery system starts from energy-saving mode (standby). |
Forced re-charging | The inverter recharges the battery, in order to maintain the SoC specified by the manufacturer or the set minimum SoC (protection against deep discharge). |
Calibration charging | The battery system is charged to the SoC of 100% and then discharged to the SoC of 0%. After 1 hour of waiting time at SoC 0%, the calibration charge is stopped and the battery switches to normal operation. |
Service mode | The battery system is charged or discharged to the SoC of 30% and the SoC of 30% is maintained until the end of the service mode. |
Deactivated | The battery is not active. It has either been deactivated, switched off, or the communication between the battery and the inverter has been interrupted. |
Energy saving mode (standby mode) is used to reduce the self-consumption of the system. Both the inverter and the battery automatically switch to energy saving mode under certain conditions.
The inverter switches to energy saving mode if the battery is flat and no PV power is available. Only the inverter's communication with the Fronius Smart Meter and Fronius Solar.web is maintained.
Energy saving mode (standby mode) is used to reduce the self-consumption of the system. Both the inverter and the battery automatically switch to energy saving mode under certain conditions.
The inverter switches to energy saving mode if the battery is flat and no PV power is available. Only the inverter's communication with the Fronius Smart Meter and Fronius Solar.web is maintained.
If all the switch-off conditions are met, the battery switches into energy saving mode within ten minutes. This time delay ensures that the inverter can at least be restarted.
| The battery state of charge is less than or equal to the input minimum state of charge. | |
| The current charging or discharging power of the battery is less than 100 W. | |
| Less than 50 W is available for charging the battery. The power of feeding into the public grid is at least 50 W less than the power currently required in the home network. |
The inverter automatically switches into energy saving mode, following the battery.
If the inverter does not operate for 12 minutes (e.g., fault), or there is an interruption in the electrical connection between the inverter and the battery and there is no backup power mode, the battery switches to energy-saving mode in any case. This reduces self discharge of the battery.
| Energy saving mode is shown on the user interface of the inverter and in Solar.web by an "i" beside the battery symbol in the system overview. |
Fronius explicitly points out that the third-party batteries are not Fronius products. Fronius is not the manufacturer, distributor, or retailer of these batteries. Fronius accepts no liability and offers no service or guarantees for these batteries.
Install third-party batteries (part of a ESS (energy storage system)) according to applicable local and national codes.
Read this document and the Installation Instructions before installing and commissioning the external battery. The documentation is either enclosed with the external battery or can be obtained from the battery manufacturer or their service partners
All documents associated with the inverter can be found at the following address:
https://www.fronius.com/en/solar-energy/installers-partners/service-support/tech-support
Fronius explicitly points out that the third-party batteries are not Fronius products. Fronius is not the manufacturer, distributor, or retailer of these batteries. Fronius accepts no liability and offers no service or guarantees for these batteries.
Install third-party batteries (part of a ESS (energy storage system)) according to applicable local and national codes.
Read this document and the Installation Instructions before installing and commissioning the external battery. The documentation is either enclosed with the external battery or can be obtained from the battery manufacturer or their service partners
All documents associated with the inverter can be found at the following address:
https://www.fronius.com/en/solar-energy/installers-partners/service-support/tech-support
If the DC voltage exceeds 403 V, the battery can no longer be charged or discharged. The voltage of 403 V is rarely exceeded during normal operation of the inverter.
When the output power of the inverter is reduced, the operating point shifts towards higher DC voltages. The following conditions during normal operation can lead to the DC voltage of 403 V being exceeded:RENON Xtreme HV1.0 | 9.6 | 14.4 | 19.2 |
|---|---|---|---|
Number of battery modules | 2 | 3 | 4 |
Fronius Primo GEN24 / GEN24 SC * | |||
Fronius Primo GEN24 Plus / GEN24 Plus SC | |||
Battery parallel operation** |
| * | Battery support optionally available. |
| ** | Max. 3 batteries with the same capacity can be combined. |
Pylontech Force H3 | 9.9 | 14.9 |
|---|---|---|
Number of battery modules | 2 | 3 |
Fronius Primo GEN24 / GEN24 SC * | ||
Fronius Primo GEN24 Plus / GEN24 Plus SC | ||
Battery parallel operation** |
| * | Battery support optionally available. |
| ** | Max. 3 batteries with the same capacity can be combined. |
| (1) | 2 x 5-pin DC push-in terminal |
| (2) | Push-in WSD (wired shutdown) terminal |
| (3) | Push-in terminals in the data communication area (Modbus, digital inputs and outputs) |
| (4) | 3-pin push-in terminal for PV Point (OP) |
| (5) | 4-pin AC push-in terminal |
| (6) | 6-pin ground electrode terminal |
| (7) | Connection area divider |
| (8) | AC conduit connection (Ø ½ - 1 inch / 13 - 25 mm) |
| (9) | Ground spike conduit connection (Ø 5/8 inch / 16 mm) |
| (10) | DatCom conduit connection (Ø ½ - ¾ inch / 13 - 19 mm) |
| (11) | Data communication area conduit connection |
| (12) | Drain valve |
| (13) | DC conduit connection (Ø ½ - 1 inch / 13 - 25 mm) |
| (1) | 2 x 5-pin DC push-in terminal |
| (2) | Push-in WSD (wired shutdown) terminal |
| (3) | Push-in terminals in the data communication area (Modbus, digital inputs and outputs) |
| (4) | 3-pin push-in terminal for PV Point (OP) |
| (5) | 4-pin AC push-in terminal |
| (6) | 6-pin ground electrode terminal |
| (7) | Connection area divider |
| (8) | AC conduit connection (Ø ½ - 1 inch / 13 - 25 mm) |
| (9) | Ground spike conduit connection (Ø 5/8 inch / 16 mm) |
| (10) | DatCom conduit connection (Ø ½ - ¾ inch / 13 - 19 mm) |
| (11) | Data communication area conduit connection |
| (12) | Drain valve |
| (13) | DC conduit connection (Ø ½ - 1 inch / 13 - 25 mm) |
The connection area divider separates the high-voltage conductors (DC and AC) from the signal lines. To make it easier to reach the connection area, the divider can be removed for the connection work, and must be re-inserted.
| (1) | Integrated cable duct |
| (2) | Recesses for removing the connection area divider |
| (3) | Snap tabs for locking/unlocking |
| (4) | Defined breaking point for the DatCom connection |
The integrated cable duct (1) allows for the lines to be laid from one area of the inverter to the other. As a result, multiple inverters can be easily installed next to each other.
The ground electrode terminal provides the option of grounding additional components, such as:
The DC disconnector has 3 switch settings:
| (1) | Locked/off (turned to the left) |
| (2) | Off |
| (3) | On |
IMPORTANT!
In switch settings (1) and (3), the inverter can be secured to prevent it from being switched on/off using a standard padlock. The national guidelines must be complied with in this respect.
| Indicates the inverter operating status. |
BAT switch | Position 1: Setting for connecting compatible batteries (factory setting) |
WSD (wired shutdown) switch | Defines the inverter as the WSD primary device or WSD secondary device. |
Modbus 0 (MB0) switch | Switches the terminating resistor for Modbus 0 (MB0) on/off. |
Modbus 1 (MB1) switch | Switches the terminating resistor for Modbus 1 (MB1) on/off. |
| For operating the inverter. See chapter Button functions and LED status indicator on page (→). |
| Indicates the inverter connection status. |
Battery connection (Modbus RJ45) | Modbus connection for connecting a compatible battery. IMPORTANT!
|
LAN 1 | Ethernet connection for data communication (for example WiFi router, home network) or, for commissioning with a laptop (see chapter Installation with the browser on page (→)). |
LAN 2 | Reserved for future functions. |
I/O terminal | Push-in terminal for digital inputs/outputs. See chapter Permitted cables for the data communication connection on page (→). |
WSD terminal | Push-in terminal for the WSD installation. See chapter WSD (wired shutdown) on page (→). |
Modbus terminal | Push-in terminal for the installation of Modbus 0, Modbus 1, 12 V, and GND (ground). |
The status of the inverter is shown via the operating status LED. In the event of faults, carry out the individual steps in the Fronius Solar.start app. | |
The optical sensor is actuated by touching with a finger. | |
The status of the connection is shown via the communication LED. To establish the connection, carry out the individual steps in the Fronius Solar.start app. |
Sensor functions | ||
|---|---|---|
1x | ||
2x | ||
3 seconds | ||
LED status indicator | ||
|---|---|---|
The inverter is operating correctly. | ||
The inverter is performing the grid checks required by the applicable standards for feed-in mode. | ||
The inverter is in standby, is not operational (e.g. no feed-in at night) or is not configured. | ||
The inverter indicates a non-critical status. | ||
The inverter indicates a critical status and there is no grid power feed process. | ||
The inverter indicates a backup power overload. | ||
The network connection is being established via WPS. | ||
The network connection is being established via WLAN AP. | ||
The network connection is not configured. | ||
The inverter is operating correctly, a network fault is indicated. | ||
The network connection is active. | ||
The inverter is performing an update. | ||
There is a service message. | ||
The V+/ GND pin provides the possibility of feeding in a voltage in the range of 12.5 to 24 V (+ max. 20%) using an external power supply unit. Outputs IO 0 - 5 can then be operated using the external voltage that has been fed in. A maximum of 1 A may be drawn per output, whereby a total of max. 3 A is permitted. The fuse protection must take place externally.
Danger from polarity reversal at the terminals due to improper connection of external power supply units.
This may result in severe damage to the inverter.
Check the polarity of the external power supply unit with a suitable measuring device before connecting it.
Connect the cables to the V+/GND outputs while ensuring the correct polarity.
IMPORTANT!
If the total output (6 W) is exceeded, the inverter switches off the entire external power supply.
| (1) | Current limitation |
There is no energy available from the PV modules or from the public grid. If backup power operation or battery operation are not possible (e.g., deep discharge protection of the battery), the inverter and battery switch off.
There is no energy available from the PV modules or from the public grid. If backup power operation or battery operation are not possible (e.g., deep discharge protection of the battery), the inverter and battery switch off.
Status codes about the inactive state of the battery are displayed on the user interface of the inverter. A notification via e-mail can be activated in Fronius Solar.web.
As soon as energy is available again, the inverter starts operation automatically; however, the battery must be started manually. The switch-on sequence must be observed for this, see chapter Suitable batteries on page (→).
The inverter requires energy from the battery to start backup power operation. This is done manually on the battery; further information on the power supply for restarting the inverter via the battery can be found in the battery manufacturer's Operating Instructions.
With the default settings, the inverter can provide 120V at the PV Point. A corresponding configuration must be set up during commissioning.
At the selected output voltage, a maximum of 13 A AC continuous current is available. The maximum continuous output is 1560 W.
Example:
120 V *13 A = 1560 W
In backup power mode, some electrical appliances cannot function properly as start-up currents are too high (e.g., fridges and freezers). In backup power mode, we recommend switching off non-essential loads. Overload capacity of 35% is possible for a duration of 5 seconds, depending on the current power of the PV module.
There is a brief interruption when switching from grid-connected mode to backup power mode. As a result, the backup power function cannot be used as an uninterruptible power supply, for computers, for example.
If no energy from the PV modules is available in backup power mode, backup power mode ends automatically. Backup power mode restarts again automatically once sufficient energy can once again be provided by the PV modules.
In the event of excessive loads, backup power mode is stopped and the "Backup power overload" status code is displayed on the inverter's LED status indicator. The maximum power in backup power mode specified in the technical data must be observed.
With the default settings, the inverter can provide 120V at the PV Point. A corresponding configuration must be set up during commissioning.
At the selected output voltage, a maximum of 13 A AC continuous current is available. The maximum continuous output is 1560 W.
Example:
120 V *13 A = 1560 W
In backup power mode, some electrical appliances cannot function properly as start-up currents are too high (e.g., fridges and freezers). In backup power mode, we recommend switching off non-essential loads. Overload capacity of 35% is possible for a duration of 5 seconds, depending on the current power of the PV module.
There is a brief interruption when switching from grid-connected mode to backup power mode. As a result, the backup power function cannot be used as an uninterruptible power supply, for computers, for example.
If no energy from the PV modules is available in backup power mode, backup power mode ends automatically. Backup power mode restarts again automatically once sufficient energy can once again be provided by the PV modules.
In the event of excessive loads, backup power mode is stopped and the "Backup power overload" status code is displayed on the inverter's LED status indicator. The maximum power in backup power mode specified in the technical data must be observed.
With the default settings, the inverter can provide 120V at the PV Point. A corresponding configuration must be set up during commissioning.
At the selected output voltage, a maximum of 13 A AC continuous current is available. The maximum continuous output is 1560 W.
Example:
120 V *13 A = 1560 W
In backup power mode, some electrical appliances cannot function properly as start-up currents are too high (e.g., fridges and freezers). In backup power mode, we recommend switching off non-essential loads. Overload capacity of 35% is possible for a duration of 5 seconds, depending on the current power of the PV module.
There is a brief interruption when switching from grid-connected mode to backup power mode. As a result, the backup power function cannot be used as an uninterruptible power supply, for computers, for example.
If no energy from the PV modules is available in backup power mode, backup power mode ends automatically. Backup power mode restarts again automatically once sufficient energy can once again be provided by the PV modules.
In the event of excessive loads, backup power mode is stopped and the "Backup power overload" status code is displayed on the inverter's LED status indicator. The maximum power in backup power mode specified in the technical data must be observed.
Limited rapid shutdown function in backup power mode (PV Point and Essential Backup)
If PV Point or Essential Backup is configured, rapid shutdown cannot be triggered via the loss of grid connection. This can result in serious personal injury and damage to the PV system.
A WSD switch must be installed for all backup power modes (PV-Point and Essentail Backup) (see Installing the WSD (wired shutdown)). The rapid shutdown is then triggered via WSD.
With the PV Point, in the event of a failure of the public grid, electrical devices can be connected to the Opportunity Power (OP) terminal and supplied with a maximum power of 1.56 kW, if enough power is available in the PV modules. In grid-connected operation, the OP terminal is not supplied with voltage, therefore the connected loads will not be supplied with power in this operating mode.
IMPORTANT!
A grid switchover with relay is not possible.
Limited rapid shutdown function in backup power mode (PV Point and Essential Backup)
If PV Point or Essential Backup is configured, rapid shutdown cannot be triggered via the loss of grid connection. This can result in serious personal injury and damage to the PV system.
A WSD switch must be installed for all backup power modes (PV-Point and Essentail Backup) (see Installing the WSD (wired shutdown)). The rapid shutdown is then triggered via WSD.
With the PV Point, in the event of a failure of the public grid, electrical devices can be connected to the Opportunity Power (OP) terminal and supplied with a maximum power of 1.56 kW, if enough power is available in the PV modules.
IMPORTANT!
A grid switchover with relay is not possible.
IMPORTANT!
If several backup power variants are available, please note that only one backup power variant may be installed and configured.
IMPORTANT!
If several backup power variants are available, please note that only one backup power variant may be installed and configured.
Captive screws (1) are used on the housing for fitting or removing the connection area cover. To fit the connection area cover, rotate the screws by half a turn (180°) into the quick-fastener spring (2).
Close the quick-fastener system (3) using a screwdriver (TX20) and a torque of 0.5-5 Nm.
Danger when using a drill driver.
This may result in the destruction of the quick-fastener system due to overtorque.
Use a screwdriver (TX20).
Do not turn the screws more than 180°.
Captive screws (1) are used on the housing for fitting or removing the connection area cover. To fit the connection area cover, rotate the screws by half a turn (180°) into the quick-fastener spring (2).
Close the quick-fastener system (3) using a screwdriver (TX20) and a torque of 0.5-5 Nm.
Danger when using a drill driver.
This may result in the destruction of the quick-fastener system due to overtorque.
Use a screwdriver (TX20).
Do not turn the screws more than 180°.
Captive screws (1) are used on the housing for fitting or removing the connection area cover. To fit the connection area cover, rotate the screws by half a turn (180°) into the quick-fastener spring (2).
Close the quick-fastener system (3) using a screwdriver (TX20) and a torque of 0.5-5 Nm.
Danger when using a drill driver.
This may result in the destruction of the quick-fastener system due to overtorque.
Use a screwdriver (TX20).
Do not turn the screws more than 180°.
Risk from unsuitable choice of location for the inverter.
Failure or restricted operation of the inverter may result.
Adhere to the instructions relating to the location, according to this chapter
Adhere to national provisions and guidelines when installing the inverter.
Please note the following criteria when choosing a location for the inverter:
| Only install on a solid, non-flammable surface. | |
| Max. ambient temperatures: | |
| Relative humidity: | |
| When installing the inverter in a switch cabinet or similar closed environment, it is necessary to make sure that the hot air that develops will be dissipated by forced-air ventilation. | |
When installing the inverter on the outer walls of cattle sheds, it is important to maintain a minimum clearance of 6.5 ft between all sides of the inverter and the ventilation and building openings. | ||
The following substrates are permissible for installation:
| ||
| The inverter is suitable for indoor installation. | |
| The inverter is suitable for outdoor installation. When properly installed, the inverter has a Type 4X protection class, is not susceptible to spraying water on any side and can also be operated in moist environments. | |
| In order to keep inverter heating as low as possible, do not expose the inverter to direct sunlight. The inverter should be installed in a protected location, e.g., near the PV modules or under an overhanging roof. | |
| ||
IMPORTANT! The inverter must not be installed or operated at more than 13,123 ft / 4001 m above sea level. | ||
| Do not install the inverter:
| |
| During certain operating phases the inverter may produce a slight noise. For this reason it should not be installed in an occupied living area. | |
| Do not install the inverter in:
| |
| The inverter is essentially designed to be dustproof (Type 4X). In areas of high dust accumulation, dust deposits may collect on the cooling surfaces, and thus impair the thermal performance. Regular cleaning is required in this case; see the chapter headed Operation in dusty environments on page (→). We therefore recommend not installing the inverter in areas and environments with high dust accumulation. | |
| Do not install the inverter in:
| |
Risk from unsuitable choice of location for the inverter.
Failure or restricted operation of the inverter may result.
Adhere to the instructions relating to the location, according to this chapter
Adhere to national provisions and guidelines when installing the inverter.
Please note the following criteria when choosing a location for the inverter:
| Only install on a solid, non-flammable surface. | |
| Max. ambient temperatures: | |
| Relative humidity: | |
| When installing the inverter in a switch cabinet or similar closed environment, it is necessary to make sure that the hot air that develops will be dissipated by forced-air ventilation. | |
When installing the inverter on the outer walls of cattle sheds, it is important to maintain a minimum clearance of 6.5 ft between all sides of the inverter and the ventilation and building openings. | ||
The following substrates are permissible for installation:
| ||
| The inverter is suitable for indoor installation. | |
| The inverter is suitable for outdoor installation. When properly installed, the inverter has a Type 4X protection class, is not susceptible to spraying water on any side and can also be operated in moist environments. | |
| In order to keep inverter heating as low as possible, do not expose the inverter to direct sunlight. The inverter should be installed in a protected location, e.g., near the PV modules or under an overhanging roof. | |
| ||
IMPORTANT! The inverter must not be installed or operated at more than 13,123 ft / 4001 m above sea level. | ||
| Do not install the inverter:
| |
| During certain operating phases the inverter may produce a slight noise. For this reason it should not be installed in an occupied living area. | |
| Do not install the inverter in:
| |
| The inverter is essentially designed to be dustproof (Type 4X). In areas of high dust accumulation, dust deposits may collect on the cooling surfaces, and thus impair the thermal performance. Regular cleaning is required in this case; see the chapter headed Operation in dusty environments on page (→). We therefore recommend not installing the inverter in areas and environments with high dust accumulation. | |
| Do not install the inverter in:
| |
The inverter is suitable for vertical installation on a vertical wall or column. | ||
The inverter is suitable for installation on a sloping surface (min. slope of underside 10°). | ||
Do not install the inverter on a sloping surface with the connections upwards. | ||
Do not install the inverter in a sloping position on a vertical wall or column. | ||
Do not install the inverter in a horizontal position on a vertical wall or column. | ||
Do not install the inverter with the connections upwards on a vertical wall or column. | ||
Do not install the inverter overhanging with the connections upwards. | ||
Do not install the inverter overhanging with the connections downwards. | ||
Do not install the inverter on the ceiling. | ||
IMPORTANT! The knockouts must be drilled out using a step drill bit only. The maximum conduit sizes are ½ - 1 inch / 13 - 25 mm.
IMPORTANT! Void warranty if the conduit holes are drilled improperly.
Condensation within the conduits can damage the inverter or components of the photovoltaic systems.
To avoid undesirable air circulation and condensation in the conduits:
Attach appropriate conduits to all knockouts that have been drilled open.
When installing outdoors, only use waterproof conduit fittings and conduits.
Seal the conduits in accordance with the pictures above on both sides.
Conduit fittings and conduits are not part of the scope of supply for the inverter.
IMPORTANT! The knockouts must be drilled out using a step drill bit only. The maximum conduit sizes are ½ - 1 inch / 13 - 25 mm.
IMPORTANT! Void warranty if the conduit holes are drilled improperly.
Condensation within the conduits can damage the inverter or components of the photovoltaic systems.
To avoid undesirable air circulation and condensation in the conduits:
Attach appropriate conduits to all knockouts that have been drilled open.
When installing outdoors, only use waterproof conduit fittings and conduits.
Seal the conduits in accordance with the pictures above on both sides.
Conduit fittings and conduits are not part of the scope of supply for the inverter.
Use the corresponding fixing materials depending on the subsurface and observe the screw dimension recommendations for the mounting bracket.
The installer is responsible for selecting the right type of fixing.
Use the corresponding fixing materials depending on the subsurface and observe the screw dimension recommendations for the mounting bracket.
The installer is responsible for selecting the right type of fixing.
The mounting bracket (illustration) can also be used as a guide.
The pre-drilled holes on the mounting bracket are intended for screws with a thread diameter of 6-8 mm (0.24-0.32 inches). The distance from the left to the right pre-drilled hole is 406 mm (16 inches).
Unevenness on the mounting surface (e.g. coarse-textured plaster) is largely compensated by the mounting bracket.
When attaching the mounting bracket to the wall or to a column, make sure that the mounting bracket is not deformed.
A deformed mounting bracket may make it difficult to clip/swivel the inverter into position.
IMPORTANT!
When installing the mounting bracket, make sure that it is installed with the arrow pointing upwards.
IMPORTANT!
The mounting bracket must be affixed at a minimum of four points.
Lift the inverter by the integrated side handles.
Clip the inverter into the mounting bracket from above. The connections must point downwards.
Press the lower area of the inverter into the snap-in tabs on the mounting bracket until the inverter engages on both sides with an audible click.
Single-core | Multi-stranded | Fine-stranded | Fine-stranded with ferrule and collar | Fine-stranded with ferrule without collar |
|---|---|---|---|---|
Single-core | Multi-stranded | Fine-stranded | Fine-stranded with ferrule and collar | Fine-stranded with ferrule without collar |
|---|---|---|---|---|
Grid connections with push-in terminal * | |||||
|---|---|---|---|---|---|
Select a sufficiently large cable cross-section based on the actual device output. | |||||
Number of pins | |||||
4 | AWG 14–8 / 2.5 - 10 mm² | AWG 14–8 / 2.5 - 10 mm² | AWG 14–8 / 2.5 - 10 mm² | AWG 14–10 / 2.5 - 6 mm² | AWG 14–10 / 2.5 - 6 mm² |
Grid connections for backup power with push-in terminal * | |||||
|---|---|---|---|---|---|
Select a sufficiently large cable cross-section based on the actual device output. | |||||
Number of pins | |||||
3 | AWG 16–8 / 1.5 - 10 mm² | AWG 16–8 / 1.5 - 10 mm² | AWG 16–8 / 1.5 - 10 mm² | AWG 16–10 / 1.5 - 6 mm² | AWG 16–10 / 1.5 - 6 mm² |
PV connections with push-in terminal | |||||
|---|---|---|---|---|---|
Select a sufficiently large cable cross-section based on the actual device output. | |||||
Number of pins | |||||
2 x 5 | AWG 12–8 / 4 - 10 mm² | AWG 12–8 / 4 - 10 mm² | AWG 12–8 / 4 - 10 mm² | AWG 14–10 / 2.5 - 6 mm² | AWG 14–10 / 2.5 - 6 mm² |
Ground electrode terminal (6-pin) | |||||
|---|---|---|---|---|---|
Select a sufficiently large cable cross-section based on the actual device output. | |||||
Number of pins | |||||
3 | AWG 14–6 / 2.5 - 16 mm² | AWG 14–6 / 2.5 - 16 mm² | AWG 14–6 / 2.5 - 16 mm² | AWG 14–6 / 2.5 - 16 mm² | AWG 14–6 / 2.5 - 16 mm² |
3 | AWG 14–8 / 2.5 - 10 mm² | AWG 14–8 / 2.5 - 10 mm² | AWG 14–8 / 2.5 - 10 mm² | AWG 14–8 / 2.5 - 10 mm² | AWG 14–8 / 2.5 - 10 mm² |
| * | According to product standards UL1741 3rd Edition, Table 20.1 and CSA-C22.2 No.107.1-16 |
Connect round copper conductors to the terminals of the inverter as described below.
IMPORTANT!
If several single conductors are connected to an input of the terminal, connect the single conductors with a corresponding ferrule.
WSD connections | ||||||
|---|---|---|---|---|---|---|
Distance | Stripping length | Cable recommendation | ||||
100 m 109 yd | 10 mm | 0.14 - 1.5 mm2 | 0.14 - 1.5 mm2 | 0.14 - 1 mm2 | 0.14 - 1.5 mm2 | Min. CAT 5 UTP (unshielded twisted pair) |
Modbus connections | ||||||
|---|---|---|---|---|---|---|
Distance | Stripping length | Cable recommendation | ||||
300 m 328 yd | 10 mm | 0.14 - 1.5 mm2 | 0.14 - 1.5 mm2 | 0.14 - 1 mm2 | 0.14 - 1.5 mm2 | Min. CAT 5 STP (shielded twisted pair) |
IO connections | ||||||
|---|---|---|---|---|---|---|
Distance | Stripping length | Cable recommendation | ||||
30 m | 10 mm | 0.14 - 1.5 mm2 | 0.14 - 1.5 mm2 | 0.14 - 1 mm2 | 0.14 - 1.5 mm2 | Single conductors possible |
LAN connections |
|---|
Fronius recommends using at least CAT 5 STP (shielded twisted pair) cables and a maximum distance of 100 m (109 yd). |
Cable diameter for connection to the push-in terminal: 0.27 inches
IMPORTANT
For double-insulated cables with a cable diameter above 0.27 inches, the outer layer of insulation must be removed for the connection to the push-in terminal.
The national regulations of the grid operator or other factors may require a ground fault protection of equipment (GFPE) in the AC connection lead.
For this situation, a GFPE is generally adequate. Nevertheless, false alarms can be triggered for the GFPE in individual cases and depending on local conditions. For this reason, in accordance with national legislation, Fronius recommends that a GFPE with a tripping current of at least 100 mA suitable for frequency converters be used.
IMPORTANT! The inverter can be fused with max. an automatic circuit breaker 65 A.
Inverter | Phases | Maximum fuse rating | Recommended fuse rating ( 208V / 220V / 240 V) |
|---|---|---|---|
Primo GEN24 3.8 208-240 | 1 | 65 A | 25 A / 25 A / 20 A |
Primo GEN24 5.0 208-240 | 1 | 65 A | 30 A / 30 A / 30 A |
Primo GEN24 6.0 208-240 | 1 | 65 A | 35 A / 35 A / 35 A |
Danger from incorrect operation and work that is not carried out properly.
This can result in severe personal injury and damage to property.
Read the Installation Instructions and Operating Instructions before installing and commissioning the equipment.
Only qualified personnel are authorized to commission the inverter and only within the scope of the respective technical regulations.
Danger from grid voltage and DC voltage from PV modules that are exposed to light.
An electric shock can be fatal.
Prior to any connection work, ensure that the inverter is de-energized on the AC side and the DC side.
Only qualified personnel may connect this equipment to the public grid
Danger from damaged and/or contaminated terminals.
This can result in severe personal injury and damage to property.
Prior to connection work, check the terminals for damage and contamination.
Remove any contamination while the equipment is de-energized.
Have defective terminals replaced by an authorized technician.
Danger from incorrect operation and work that is not carried out properly.
This can result in severe personal injury and damage to property.
Read the Installation Instructions and Operating Instructions before installing and commissioning the equipment.
Only qualified personnel are authorized to commission the inverter and only within the scope of the respective technical regulations.
Danger from grid voltage and DC voltage from PV modules that are exposed to light.
An electric shock can be fatal.
Prior to any connection work, ensure that the inverter is de-energized on the AC side and the DC side.
Only qualified personnel may connect this equipment to the public grid
Danger from damaged and/or contaminated terminals.
This can result in severe personal injury and damage to property.
Prior to connection work, check the terminals for damage and contamination.
Remove any contamination while the equipment is de-energized.
Have defective terminals replaced by an authorized technician.
In grid configurations with neutral conductors, the neutral conductor must be connected in order to operate the inverter.
It is not possible to operate the inverter in ungrounded grids, e.g., IT grids (insulated grids without ground conductor). The grid power feed operation of the inverter can be adversely affected by an insufficiently dimensioned neutral conductor.
Make sure that the grid's neutral conductor is grounded.
Ensure the neutral conductor and live conductor are the same size.
IMPORTANT! The ground conductor/grounding of the AC cable must be laid so that it is disconnected last in the event of a failure.
Turn off the automatic circuit breaker. Set the DC disconnector to the "Off" switch position.
Loosen the five screws of the connection area cover by rotating them 180° to the left using a screwdriver (TX20).
Remove the connection area cover from the device.
Press the latch on the back of the terminal and remove the AC terminal.
Guide the mains cable from below through the cable gland on the right side.
IMPORTANT!
The ground conductor must be dimensioned longer and laid with a movement loop so that it is last loaded in the event of a failure of the cable gland.
Select the cable cross-section in accordance with chapter Permitted cables for the electrical connection on page (→).
Strip the insulation of the single conductors by 0.47 inches.
Lift to open the terminal's operating lever and insert the stripped single conductor into the slot provided as far as it will go.
Then close the terminal's operating lever until it engages.
Only one conductor may be connected to each pin.
The AC cables can be connected to the AC terminals without ferrules.
| L1 | Phase conductor |
| Nsens | Neutral conductor* |
| L2 | Phase conductor |
* Valid for grid configurations with neutral conductors.
Fasten the grounding cable to the ground electrode terminal using a screwdriver (TX20) and a torque of 1.475 ft lbs / 2 Nm.
Insert the AC terminal into the AC slot until it engages.
To enable suitable PV modules to be chosen and to use the inverter as efficiently as possible, it is important to bear the following points in mind:
IMPORTANT! Before connecting up the PV modules, check that the voltage for the PV modules specified by the manufacturer corresponds to the actual measured voltage.
IMPORTANT!
Solar module strings must not be grounded.
To enable suitable PV modules to be chosen and to use the inverter as efficiently as possible, it is important to bear the following points in mind:
IMPORTANT! Before connecting up the PV modules, check that the voltage for the PV modules specified by the manufacturer corresponds to the actual measured voltage.
IMPORTANT!
Solar module strings must not be grounded.
Danger from incorrect operation and work that is not carried out properly.
This can result in severe personal injury and damage to property.
The commissioning, maintenance, and service work in the inverter's power stage set may only be carried out by Fronius-trained service personnel in accordance with the technical specifications.
Read the installation instructions and operating instructions before installing and commissioning the equipment.
Danger from mains voltage and DC voltage from PV modules that are exposed to light.
This can result in severe personal injury and damage to property.
All connection, maintenance, and service work should only be carried out when the AC and DC sides have been disconnected from the inverter and are de-energized.
Only an authorized electrical engineer is permitted to connect this equipment to the public grid.
Danger of an electric shock due to improperly connected terminals/PV plug connectors.
An electric shock can be fatal.
When connecting, ensure that each pole of a string is routed via the same PV input, e.g.:
+ pole string 1 to the input PV 1.1+ and - pole string 1 to the input PV 1.1-
Danger from damaged and/or contaminated terminals.
This can result in severe personal injury and damage to property.
Prior to connection work, check the terminals for damage and contamination.
Remove any contamination while the equipment is de-energized.
Have defective terminals replaced by an authorized specialist company.
Two independent PV inputs (PV 1 and PV 2) are available. These inputs can be connected to a different number of modules.
When starting for the first time, set up the PV Generator in accordance with the respective configuration (can also be carried out at a later date in the Device Configuration > Components menu area).
IMPORTANT!
The installation must be carried out in accordance with the nationally applicable standards and directives. If the Arc Fault Circuit Interrupter integrated in the inverter is used for the arc detection requirement according to IEC 63027, the solar module strings must not be combined in front of the inverter.
Module array settings:
PV 1: ON
PV 2: OFF
IMPORTANT!
The maximum current load of a single terminal is 22 A.
Module array settings:
PV 1: ON
PV 2: ON
IMPORTANT!
It is not allowed to connect PV1 and PV2 in parallel, as otherwise currents of over 22A per terminal connection could flow.
Disconnect connections from the solar module strings (+/-).
Guide the DC cables through the electrical installation tube.
IMPORTANT!
Guide the cables through the electrical installation tube before stripping them in order to avoid twisting/bending single wires.
Danger from loose and/or incorrectly clamped single conductors in the terminal.
This can result in serious injury and damage to property.
Only connect one single conductor at each slot provided in the terminal.
Check that the single conductors are secure in the terminal.
Make sure that the single conductor has been fully inserted into the terminal and that no single wires are protruding out of the terminal.
Select the cable cross-section in accordance with the instructions in Permitted cables for the electrical connection from page (→).
Strip the insulation of the single conductors by 0.47 inches.
Lift to open the terminal's operating lever and insert the stripped single conductor into the slot provided, in each case as far as it will go. Then close the operating lever until it engages.
Connect the solar module strings (+/-).
Use a suitable measuring instrument to check the voltage and polarity of the DC cabling. Remove both DC terminals from the slots.
Danger due to polarity reversal at the terminals.
This may result in severe damage to the inverter.
Use a suitable measuring instrument to check the polarity of the DC cabling.
Use a suitable measuring instrument to check the voltage (max. 600 VDC)
Insert the DC terminals into the respective slot until they engage.
Danger due to incorrect operation and incorrectly performed work.
This can result in serious injury and damage to property.
Only a technical specialist is permitted to perform commissioning, maintenance, and service activities for inverters and batteries, and only within the scope of the technical regulations.
Read the installation instructions and operating instructions from the respective manufacturer before installing and commissioning the equipment.
Danger from mains voltage and DC voltage from the PV module that are exposed to light, as well as batteries.
This can result in serious injury and damage to property.
All connection, maintenance, and service work should only be carried out when the AC and DC sides have been disconnected from the inverter and battery, and are de-energized.
Only a technical specialist is permitted to connect this equipment to the public grid.
Danger from damaged and/or contaminated terminals.
This can result in serious injury and damage to property.
Prior to connection work, check the terminals for damage and contamination.
Remove any contamination while the equipment is de-energized.
Have defective terminals repaired by a technical specialist.
Danger due to incorrect operation and incorrectly performed work.
This can result in serious injury and damage to property.
Only a technical specialist is permitted to perform commissioning, maintenance, and service activities for inverters and batteries, and only within the scope of the technical regulations.
Read the installation instructions and operating instructions from the respective manufacturer before installing and commissioning the equipment.
Danger from mains voltage and DC voltage from the PV module that are exposed to light, as well as batteries.
This can result in serious injury and damage to property.
All connection, maintenance, and service work should only be carried out when the AC and DC sides have been disconnected from the inverter and battery, and are de-energized.
Only a technical specialist is permitted to connect this equipment to the public grid.
Danger from damaged and/or contaminated terminals.
This can result in serious injury and damage to property.
Prior to connection work, check the terminals for damage and contamination.
Remove any contamination while the equipment is de-energized.
Have defective terminals repaired by a technical specialist.
Danger due to operation of the battery above the permissible altitude as specified by the manufacturer.
Operating the battery above the permissible altitude can result in restricted operation, failure of the operation, and unsafe states of the battery.
Adhere to the manufacturer's instructions regarding the permissible altitude.
Operate the battery only at the altitude specified by the manufacturer.
IMPORTANT!
Prior to installing a battery, ensure that the battery is switched off. The max. DC cable length for the installation of external batteries must be taken into account according to the manufacturer's specifications, see chapter Suitable batteries on page (→).
Manually push the battery cables through the DC bushings.
* The battery ground conductor must be connected to the ground electrode terminal of the inverter,
IMPORTANT!
Before stripping the insulation, push the cables through the DC bushings to prevent individual wires being bent or broken.
Remove the DC push-in terminals from the slots.
Danger due to individual conductors in the terminal that are loose and/or improperly connected.
This can result in serious injury and damage to property.
Only connect one single conductor in the slot provided for each terminal.
Check that the single conductor is held securely in the terminal.
Ensure that all of the single conductor is within the terminal and that no individual wire strands are sticking out of the terminal.
Select the cable cross-section in accordance with the instructions in Permitted cables for the electrical connection from page (→).
Strip the insulation of the single conductors by 0.47 inches.
Lift to open the terminal's operating lever and insert the stripped single conductor into the slot provided, in each case as far as it will go. Then close the operating lever until it engages.
Danger due to overvoltage when using other slots on the terminal.
This may result in damage to the battery and/or the PV modules due to discharge.
Only use the slots labeled "BAT" for connecting the battery.
Danger due to polarity reversal at the terminals.
Serious damage to the PV system may result.
Use a suitable measuring instrument to check the polarity of the DC cabling when the battery is switched on.
The maximum voltage for the battery input must not be exceeded (see Technical data on page (→)).
Insert the DC terminals into the respective slot until they engage.
IMPORTANT! Information for the battery-side connection can be found in the installation instructions from the relevant manufacturer.
Danger from incorrect installation, commissioning, operation or incorrect use.
This can result in severe personal injury and damage to property.
Single 120 / 220 / 240 volt supply. Do not connect multi-wire branch circuits!
Only trained and qualified personnel are authorized to install and commission the system, and only within the scope of the technical regulations.
The Installation Instructions and Operating Instructions must be read carefully prior to use.
If anything is unclear, contact your vendor immediately.
Danger from damaged and/or contaminated terminals.
This can result in severe personal injury and damage to property.
Prior to connection work, check the terminals for damage and contamination.
Remove any contamination while the equipment is de-energized.
Have defective terminals replaced by an authorized technician.
Limited rapid shutdown function in backup power mode (PV Point and Essential Backup)
If PV Point or Essential Backup is configured, rapid shutdown cannot be triggered via the loss of grid connection. This can result in serious personal injury and damage to the PV system.
A WSD switch must be installed for all backup power modes (PV-Point and Essential Backup) (see Installing the WSD (wired shutdown)). The rapid shutdown is then triggered via WSD.
Power supply via the PV point is dependent on the available PV power
If the PV modules are not supplying enough power, interruptions may occur.
Do not connect any loads that require an interruption-free supply.
IMPORTANT!
The valid national laws, standards, and provisions, as well as the specifications of the relevant grid operator are to be taken into account and applied.
It is highly recommended that the specific installation be agreed with the grid operator and explicitly approved by this operator. This obligation applies to system constructors in particular (e.g., installers).
Danger from incorrect installation, commissioning, operation or incorrect use.
This can result in severe personal injury and damage to property.
Single 120 / 220 / 240 volt supply. Do not connect multi-wire branch circuits!
Only trained and qualified personnel are authorized to install and commission the system, and only within the scope of the technical regulations.
The Installation Instructions and Operating Instructions must be read carefully prior to use.
If anything is unclear, contact your vendor immediately.
Danger from damaged and/or contaminated terminals.
This can result in severe personal injury and damage to property.
Prior to connection work, check the terminals for damage and contamination.
Remove any contamination while the equipment is de-energized.
Have defective terminals replaced by an authorized technician.
Limited rapid shutdown function in backup power mode (PV Point and Essential Backup)
If PV Point or Essential Backup is configured, rapid shutdown cannot be triggered via the loss of grid connection. This can result in serious personal injury and damage to the PV system.
A WSD switch must be installed for all backup power modes (PV-Point and Essential Backup) (see Installing the WSD (wired shutdown)). The rapid shutdown is then triggered via WSD.
Power supply via the PV point is dependent on the available PV power
If the PV modules are not supplying enough power, interruptions may occur.
Do not connect any loads that require an interruption-free supply.
IMPORTANT!
The valid national laws, standards, and provisions, as well as the specifications of the relevant grid operator are to be taken into account and applied.
It is highly recommended that the specific installation be agreed with the grid operator and explicitly approved by this operator. This obligation applies to system constructors in particular (e.g., installers).
All loads that are to be supplied via the OP terminal must be protected by means of a ground fault circuit interrupter.
In order to ensure the ground fault circuit interrupter operates properly, a connection must be established between the neutral conductor N' (OP) and equipment grounding (GND).
Wiring proposal recommended by Fronius, see page (→).
Turn off the automatic circuit breaker. Set the DC disconnector to the "Off" switch position.
Loosen the five screws of the connection area cover by rotating them 180° to the left using a screwdriver (TX20).
Remove the connection area cover from the device.
Danger from faulty or incorrect bores.
This may lead to injuries to the eyes and hands as a result of flying debris and sharp edges, as well as damage to the inverter.
When drilling, wear suitable protective goggles.
Only use a step drill when drilling.
Ensure that nothing on the inside of the device is damaged (e.g., the connection block).
Adapt the diameter of the bore to match the corresponding connection.
Deburr the bores using a suitable tool.
Remove the drilling residues from the inverter.
Drill out the knockout with a step drill.
Guide the mains cable through the conduit from below.
Remove the OP terminal.
Danger from loose and/or incorrectly clamped single conductors in the terminal.
This can result in serious injury and damage to property.
Only connect one single conductor at each slot provided in the terminal.
Check that the single conductors are secure in the terminal.
Make sure that the single conductor has been fully inserted into the terminal and that no single wires are protruding out of the terminal.
Strip the insulation of the single conductors by 0.47 inches / 12 mm.
The cable cross-section must be between AWG 16 and AWG 8.
Lift to open the terminal's operating lever and insert the stripped single conductor into the slot provided, all the way up to the stop. Then close the operating lever until it engages.
Lift to open the terminal's operating lever and insert the stripped single conductor into the slot provided, in each case as far as it will go. Then close the operating lever until it engages.
| L1´ | Phase conductor |
| N´ | Neutral conductor |
| N´ | Ground conductor |
The ground conductor must have a cross-section of AWG 14-8.
Fasten the ground conductor and PEN conductor to the ground electrode terminal using a screwdriver (TX20) and a torque of 1.47 ft-lbs / 2 Nm.
Insert the OP terminal into the OP slot until it engages.
A battery charge of min. 30% is recommended for test mode.
A description of how to run the test mode can be found in the checklist – Backup power (https://www.fronius.com/de/download-center?searchword=42,0426,0365).
Inputs M0 and M1 can be selected for this purpose. A maximum of 4 Modbus participants can be connected to the Modbus terminal on inputs M0 and M1.
IMPORTANT! Only one primary meter and one battery can be connected per inverter. Due to the high data transfer of the battery, the battery occupies 2 participants. If the "Inverter control via Modbus" function is activated in the "Communication” → "Modbus" menu, no Modbus participants are possible. It is not possible to send and receive data at the same time.
Example 1:
Input | Battery | Quantity | Quantity |
|---|---|---|---|
Modbus 0 | 0 | 4 | |
0 | 2 | ||
0 | 1 | ||
Modbus 1 | 1 | 3 |
Example 2:
Input | Battery | Quantity | Quantity |
|---|---|---|---|
Modbus 0 | 1 | 3 | |
Modbus 1 | 0 | 4 | |
0 | 2 | ||
0 | 1 |
Inputs M0 and M1 can be selected for this purpose. A maximum of 4 Modbus participants can be connected to the Modbus terminal on inputs M0 and M1.
IMPORTANT! Only one primary meter and one battery can be connected per inverter. Due to the high data transfer of the battery, the battery occupies 2 participants. If the "Inverter control via Modbus" function is activated in the "Communication” → "Modbus" menu, no Modbus participants are possible. It is not possible to send and receive data at the same time.
Example 1:
Input | Battery | Quantity | Quantity |
|---|---|---|---|
Modbus 0 | 0 | 4 | |
0 | 2 | ||
0 | 1 | ||
Modbus 1 | 1 | 3 |
Example 2:
Input | Battery | Quantity | Quantity |
|---|---|---|---|
Modbus 0 | 1 | 3 | |
Modbus 1 | 0 | 4 | |
0 | 2 | ||
0 | 1 |
Drill out the knockout with a step drill.
Strip 10 mm/ 0.39 inch from the single conductors and mount the ferrules if necessary.
IMPORTANT!
Connect the individual conductors to an appropriate ferrule if several individual conductors are connected to one input of the push-in terminals.
Insert the cable into the respective slot and check the cable is securely retained.
IMPORTANT! Use a twisted cable pair for corresponding data cables.
Twist the cable shield and insert into the "Shield" slot.
IMPORTANT! Improperly fitted shielding can cause data communication problems.
For the wiring proposal recommended by Fronius, see page (→).
It may be possible for the system to function without terminating resistors. However, owing to interference, the use of terminating resistors according to the following overview is recommended for trouble-free operation.
For permissible cables and max. distances for the data communication area, refer to the chapter headed Permitted cables for the data communication connection on page (→).
IMPORTANT!Terminating resistors that are not positioned as illustrated can result in interference in the data communication.
Limited rapid shutdown function in backup power mode (PV Point and Essential Backup)
If PV Point or Essential Backup is configured, rapid shutdown cannot be triggered via the loss of grid connection. This can result in serious personal injury and damage to the photovoltaic system.
A WSD switch must be installed for all backup power modes (PV-Point and Essential Backup) (see Installing the WSD (wired shutdown)). The rapid shutdown is then triggered via WSD.
IMPORTANT! The push-in WSD terminal in the inverter's connection area comes with a bypass as standard. The bypass must be removed when installing a trigger device or a WSD chain.
Installing a Rapid Shutdown Initiator Switch
If a rotary switch for initiating the Rapid Shutdown is needed (for example as an emergency stop for backup systems), install the Fronius Rapid Shutdown Initiator Switch (42,0440,0338) as described below:
Connect signal wires (AWG 12).
Mount the switch in the enclosure.
Connect signal wires with the push-in WSD terminal.
WSD Chain
The WSD switch of the first inverter with connected trigger device in the WSD chain must be in position 1 (primary device). The WSD switch of all other inverters should be in position 0 (secondary device).
Maximum distance between two devices: 109 yd/100 m
Maximum number of devices: 28
* Floating contact of the trigger device (for example, central grid and system protection). If several floating contacts are used in a WSD chain, these must be connected in series.
The housing cover is fitted with a lock for safety reasons, which allows the housing cover on the inverter to be pivoted only when the DC disconnector is switched off.
Only clip and pivot the housing cover onto the inverter when the DC disconnector is switched off.
Do not use excessive force to clip in and pivot the housing cover.
Place the cover on the connection area. Tighten the five screws by rotating them 180° to the right in the indicated order using a screwdriver (TX20).
Clip the housing cover into the inverter from above.
Press on the lower part of the housing cover and tighten the 2 screws by rotating them 180° to the right using a screwdriver (TX20).
Turn the DC disconnector to the "On" switch position. Switch on the automatic circuit breaker. For systems with a battery, observe the switch-on sequence as per chapter Suitable batteries on page (→).
IMPORTANT! Open WLAN Access Point with the optical sensor, see chapter Button functions and LED status indicator on page (→)
The housing cover is fitted with a lock for safety reasons, which allows the housing cover on the inverter to be pivoted only when the DC disconnector is switched off.
Only clip and pivot the housing cover onto the inverter when the DC disconnector is switched off.
Do not use excessive force to clip in and pivot the housing cover.
Place the cover on the connection area. Tighten the five screws by rotating them 180° to the right in the indicated order using a screwdriver (TX20).
Clip the housing cover into the inverter from above.
Press on the lower part of the housing cover and tighten the 2 screws by rotating them 180° to the right using a screwdriver (TX20).
Turn the DC disconnector to the "On" switch position. Switch on the automatic circuit breaker. For systems with a battery, observe the switch-on sequence as per chapter Suitable batteries on page (→).
IMPORTANT! Open WLAN Access Point with the optical sensor, see chapter Button functions and LED status indicator on page (→)
When starting the inverter for the first time, various setup settings must be configured.
If the setup is canceled before completion, the input data is not saved and the start screen with the installation wizard is shown once again. The data is saved in the event of an interruption, e.g., a power failure. Commissioning is continued at the point at which the interruption occurred after the power supply is restored. If the setup was interrupted, the inverter feeds energy into the grid at maximum 500 W and the operating status LED flashes yellow.
The country setup can only be set when starting the inverter for the first time. If the country setup needs to be changed at a later date, contact your installer/technical support.
The Fronius Solar.start app is required for installation. Depending on the mobile device used to perform the installation, the app is available on the relevant platform.
The network wizard and product setup can be performed independently. A network connection is required for the Fronius Solar.web installation wizard.
The network wizard and product setup can be performed independently. A network connection is required for the Fronius Solar.web installation wizard.
WiFi:
Ethernet:
IMPORTANT! Wait for the capacitors of the inverter to discharge (2 minutes). The DC disconnector interrupts the power supply to the photovoltaic and battery connections.
IMPORTANT! Wait for the capacitors of the inverter to discharge (2 minutes). The DC disconnector interrupts the power supply to the photovoltaic and battery connections.
IMPORTANT!
Depending on the authorization of the user, settings can be made in the individual menu areas.
IMPORTANT!
Depending on the authorization of the user, settings can be made in the individual menu areas.
IMPORTANT!
Depending on the authorization of the user, settings can be made in the individual menu areas.
Select "Add component+" to add all available components to the system.
PV Generator
Activate the MPP tracker and enter the connected PV power in the associated field. For combined solar module strings, "PV 1 + PV 2 connected in parallel" must be activated.
Battery
If the SoC mode is set to "Automatic", the values "Minimum SoC" and "Maximum SoC" are preset according to the technical specifications of the battery manufacturer.
If the SoC mode is set to "Manual", the values "Minimum SoC" and "Maximum SoC" may be changed after consultation with the battery manufacturer within the scope of their technical specifications. In the event of a power outage requiring backup power, the set values are not taken into account.
Charging of the battery from other external producers is enabled/disabled using the "Allow battery charging from additional producers in home network" setting.
Charging of the battery from the public grid is enabled/disabled using the "Allow battery charging from public grid" setting.
The normative or feed-in tariff rules must be taken into account with this setting. The setting does not affect the charging of the battery by other producers within the home. It merely relates to the process of drawing charging energy from the public grid. Regardless of this setting, any charging from the public grid that is required for service reasons (e.g., necessary re-charging to protect against deep discharge) is still performed.
IMPORTANT!
Fronius accepts no liability for damage to third-party batteries.
Primary meter
To ensure smooth operation in conjunction with other energy producers and in Essential Backup backup power mode, it is important to install the Fronius Smart Meter at the feed-in point. The inverter and other producers must be connected to the public grid via the Fronius Smart Meter.
This setting also affects the behavior of the inverter at night. If the function is deactivated, the inverter switches to Standby mode as soon as there is no more PV power available, provided that no energy management command is sent to the battery (e.g., minimum state of charge reached). The message "Power low" is displayed. The inverter restarts as soon as an energy management command is sent or sufficient PV power is available.
If the function is activated, the inverter remains permanently connected to the grid so that energy can be drawn from other producers at any time.
After connecting the meter, the position must be configured. A different Modbus address needs to be set for each Smart Meter.
The watt value on the generator meter is the sum of all generator meters. The watt value on the consumption meter is the value of all secondary meters.
Select "Add component+" to add all available components to the system.
PV Generator
Activate the MPP tracker and enter the connected PV power in the associated field. For combined solar module strings, "PV 1 + PV 2 connected in parallel" must be activated.
Battery
If the SoC mode is set to "Automatic", the values "Minimum SoC" and "Maximum SoC" are preset according to the technical specifications of the battery manufacturer.
If the SoC mode is set to "Manual", the values "Minimum SoC" and "Maximum SoC" may be changed after consultation with the battery manufacturer within the scope of their technical specifications. In the event of a power outage requiring backup power, the set values are not taken into account.
Charging of the battery from other external producers is enabled/disabled using the "Allow battery charging from additional producers in home network" setting.
Charging of the battery from the public grid is enabled/disabled using the "Allow battery charging from public grid" setting.
The normative or feed-in tariff rules must be taken into account with this setting. The setting does not affect the charging of the battery by other producers within the home. It merely relates to the process of drawing charging energy from the public grid. Regardless of this setting, any charging from the public grid that is required for service reasons (e.g., necessary re-charging to protect against deep discharge) is still performed.
IMPORTANT!
Fronius accepts no liability for damage to third-party batteries.
Primary meter
To ensure smooth operation in conjunction with other energy producers and in Essential Backup backup power mode, it is important to install the Fronius Smart Meter at the feed-in point. The inverter and other producers must be connected to the public grid via the Fronius Smart Meter.
This setting also affects the behavior of the inverter at night. If the function is deactivated, the inverter switches to Standby mode as soon as there is no more PV power available, provided that no energy management command is sent to the battery (e.g., minimum state of charge reached). The message "Power low" is displayed. The inverter restarts as soon as an energy management command is sent or sufficient PV power is available.
If the function is activated, the inverter remains permanently connected to the grid so that energy can be drawn from other producers at any time.
After connecting the meter, the position must be configured. A different Modbus address needs to be set for each Smart Meter.
The watt value on the generator meter is the sum of all generator meters. The watt value on the consumption meter is the value of all secondary meters.
Backup power
Off, PV Point, or Essential Backup can be selected for backup power mode.
Essential Backup backup power mode can only be activated once the required I/O assignments have been configured for backup power. In addition, a meter must be mounted and configured at the feed-in point for Essential Backup backup power mode.
IMPORTANT!
When configuring PV Point backup power mode, the information in chapter Safety on page (→) must be observed.
Backup power nominal voltage
When backup power mode is activated, the nominal voltage of the public grid must be selected.
State of charge warning limit
A warning is output when the residual capacity of the battery specified here is reached in backup power mode.
Reserve capacity
The set value results in a residual capacity (depending on the capacity of the battery) that is reserved for backup power. The battery is not discharged below the residual capacity in grid-connected operation. In backup power mode, the manually set value Minimum SoC is not taken into account. If there is a power outage, the battery is always discharged down to the automatically preset minimum SoC in accordance with the technical specifications of the battery manufacturer.
Load management
Up to 4 pins can be selected for load management here. Additional load management settings are available in the Load management menu item.
Default: Pin 1
Enforce Standby
When the function is activated, the feed-in mode of the inverter is interrupted. This enables a powerless shutdown of the inverter and protects its components. When the inverter is restarted, the standby function is automatically deactivated.
Fan test
IMPORTANT!
To view and change settings in this menu item, select the user Technician, and enter and confirm the password for the user Technician. Settings may only be made by trained and qualified personnel.
This function can be used to check whether the fans of the inverter are working correctly based on acoustics, for example after replacing a fan.
The test takes around 30 seconds per fan. The inverter then switches back to normal operation. The test can be stopped manually using the Stop fan test function.
PV 1 and PV 2
Parameter | Value range | Description |
|---|---|---|
Mode | Off | The MPP tracker is deactivated. |
Auto | The inverter uses the voltage at which the max. possible output of the MPP tracker is possible. | |
Fixed | The MPP tracker uses the voltage defined in UDC fixed. | |
UDC fixed | 80 ‑ 530 V | The inverter uses the fixed voltage that is used on the MPP tracker. |
Dynamic Peak Manager
| Off | Function is deactivated. |
On | The entire solar module string is checked for optimization potential and determines the best possible voltage for the supply of energy from the inverter into the grid. | |
On (MLSD) | The function is optimized for systems with Module Level Shutdown devices (MLSD) and not suitable for PV optimizers. |
Ripple control signal
Ripple control signals are signals that are sent by the energy company in order to switch controllable loads on and off. Depending on the installation situation, ripple control signals can be dampened or amplified by the inverter. This can be counteracted if necessary by applying the following settings.
Parameter | Value range | Description |
|---|---|---|
Reduction of influence | Off | Function is deactivated. |
On | Function is activated. | |
Frequency of the ripple control signal | 100 ‑ 3000 Hz | The frequency specified by the energy company must be entered here. |
Grid inductance | 0.00001 ‑ 0.005 H | The value measured at the infeed point must be entered here. |
Measure against RCD false triggers
(when using a 30 mA residual current circuit breaker)
A residual current circuit breaker for the AC connecting cable may be required depending on national regulations, the grid operator, and other conditions.
A type A residual current circuit breaker is generally sufficient in this case. Nevertheless, false alarms can be triggered for the type A residual current circuit breaker in individual cases and depending on local conditions. For this reason, Fronius recommends using a residual current circuit breaker suitable for frequency inverters with a release current of least 100 mA, taking into account national provisions.
Parameter | Value range | Description |
|---|---|---|
Leakage current factor to reduce RCMU/RCD false trips | 0 ‑ 0,25 | Reducing the setting value reduces the leakage current and raises the intermediate circuit voltage, which slightly reduces the efficiency.
|
Switch-Off before 30mA RCD Trip | Off | The function for reducing false tripping of the residual current circuit breaker is deactivated. |
On | The function for reducing false tripping of the residual current circuit breaker is activated. | |
Rated residual non-operating current threshold | 0,015 ‑ 0,3 | The value of residual non-operating current, assigned to the residual current circuit breaker by the manufacturer, at which the residual current circuit breaker does not operate under specified conditions. |
Insulation warning
Parameter | Value range | Description |
|---|---|---|
Insulation warning | Off | The insulation warning is deactivated. |
On | The insulation warning is activated. | |
Insulation measurement mode
| Exact | Insulation monitoring takes place with the highest degree of accuracy and the measured insulation resistance is displayed on the user interface of the inverter. |
Fast | Insulation monitoring takes place with a lesser degree of accuracy, whereby the time to take the insulation measurement is shortened and the insulation value is not displayed on the user interface of the inverter. | |
Threshold for the insulation warning | 100000 ‑ | If the value drops below the threshold, status code 1083 is displayed on the user interface of the inverter. |
Backup power
Parameter | Value range | Description |
|---|---|---|
Backup power nominal voltage | 120 ‑ 240 V | The nominal phase voltage that is output in backup power mode. |
Backup power undervoltage protection limit value U< [pu] | 0 ‑ 2 % V | This set value represents the limit value for shutting down backup power mode. |
Backup Frequency Offset | -5 - +5 Hz | The setting value can be used to reduce or increase the nominal backup power frequency (see Technical data) by the offset value. The default value is +3 Hz. Connected loads detect that backup power mode is active based on the change in frequency and react accordingly (e.g., by activating energy saving mode) |
Backup power undervoltage protection time U< | 0.04 ‑ 20 s | Trip time for falling below the backup power undervoltage protection limit value. |
Backup power surge protection limit value U> [pu] | 0 ‑ 2 % V | This set value represents the limit value for shutting down backup power mode. |
Backup power surge protection time U> | 0.04 ‑ 20 s | Trip time for exceeding the backup power surge protection limit value. |
Backup power restart delay | 0 ‑ 600 s | Waiting time for restarting backup power mode following a shutdown. |
Backup power restart attempts | 1 ‑ 10 | The max. number of automated restart attempts. Once the max. number of automated restart attempts has been reached, service message 1177 must be manually acknowledged. |
Backup power short circuit switch-off time | 0.001 ‑ 60 s | If a short circuit occurs during backup power mode, backup power mode is interrupted within the set time. |
"Self-Consumption Optimization"
Set the operating mode to "Manual" or "Automatic". The inverter always regulates to the set "Target Value at Feed-In Point". In the "Automatic" operating mode (factory setting), an adjustment is made to 0 W at the feed-in point (maximum self-consumption).
"Target Value at Feed-In Point"
If "Manual" has been selected under Self-Consumption Optimization, the "Operating Mode" ("Consumption"/"Feed-In") and the "Target Value at Feed-In Point" can be set.
IMPORTANT!
"Self-Consumption Optimization" has lower priority than "Battery Management".
External producers (only possible with active battery)
If further decentralized producers are installed in the house, and these are incorporated into the self-consumption control of the Fronius Hybrid inverter, the setting "Allow battery charging from additional producers in home network" must be activated in the menu area "Device Configuration" → "Components" (see Components on page (→)
.This means that energy can be drawn from the home network and fed into the battery via the Fronius inverter (battery support required). You can restrict how much power is consumed by the Fronius inverter by specifying the maximum AC power (AC max.). A maximum power consumption of the AC rated power of the Fronius inverter is possible.
"Battery Management"
Using the time-dependent battery control, it is possible to prevent or restrict charging/discharging of the battery and to specify a defined charging power.
IMPORTANT!
The defined rules for battery control have the second lowest priority after Self-Consumption Optimization. Depending on the configuration, the rules may not be satisfied due to other settings.
The timing for when the rule applies is set in the "Time" input fields and by selecting the relevant "Weekdays".
It is not possible to define a time window over midnight (0:00 am).
Example: To set a control from 10 pm to 6 am, two inputs are required: "10 pm-11:59 pm" and "0:00 am-06 am".
"Self-Consumption Optimization"
Set the operating mode to "Manual" or "Automatic". The inverter always regulates to the set "Target Value at Feed-In Point". In the "Automatic" operating mode (factory setting), an adjustment is made to 0 W at the feed-in point (maximum self-consumption).
"Target Value at Feed-In Point"
If "Manual" has been selected under Self-Consumption Optimization, the "Operating Mode" ("Consumption"/"Feed-In") and the "Target Value at Feed-In Point" can be set.
IMPORTANT!
"Self-Consumption Optimization" has lower priority than "Battery Management".
External producers (only possible with active battery)
If further decentralized producers are installed in the house, and these are incorporated into the self-consumption control of the Fronius Hybrid inverter, the setting "Allow battery charging from additional producers in home network" must be activated in the menu area "Device Configuration" → "Components" (see Components on page (→)
.This means that energy can be drawn from the home network and fed into the battery via the Fronius inverter (battery support required). You can restrict how much power is consumed by the Fronius inverter by specifying the maximum AC power (AC max.). A maximum power consumption of the AC rated power of the Fronius inverter is possible.
"Battery Management"
Using the time-dependent battery control, it is possible to prevent or restrict charging/discharging of the battery and to specify a defined charging power.
IMPORTANT!
The defined rules for battery control have the second lowest priority after Self-Consumption Optimization. Depending on the configuration, the rules may not be satisfied due to other settings.
The timing for when the rule applies is set in the "Time" input fields and by selecting the relevant "Weekdays".
It is not possible to define a time window over midnight (0:00 am).
Example: To set a control from 10 pm to 6 am, two inputs are required: "10 pm-11:59 pm" and "0:00 am-06 am".
The following examples serve to explain the energy flows. Efficiency levels are not taken into account.
Battery system
PV system to inverter | 1000 W |
Power into the battery | 500 W |
Power output (AC) of the inverter | 500 W |
Set target value at feed-in point | 0 W |
Infeed into the public grid | 0 W |
Consumption in home | 500 W |
Battery system without photovoltaics, including second generator in the house
Power into the battery | 1500 W |
Power consumption (AC) of the inverter | 1500 W |
Second generator in home network | 2000 W |
Set target value at feed-in point | 0 W |
Infeed into the public grid | 0 W |
Consumption in home | 500 W |
Battery system including second generator in the house
PV system to inverter | 1000 W |
Power into the battery | 2500 W |
Power consumption (AC) of the inverter | 1500 W |
Second generator in home network | 2000 W |
Set target value at feed-in point | 0 W |
Infeed into the public grid | 0 W |
Consumption in home | 500 W |
A regulation always consists of a restriction or specification, and the time and days of the week when the regulation is active. The time of regulations with the same restriction (e.g., max. charging power) must not overlap.
Max. charging and discharging limits
One max. charging and one max. discharging power can be configured at the same time.
Specify charging range
It is possible to define a charging range using a min. and max. charging limit. In this case, it is not possible to discharge the battery.
Specify discharging range
It is possible to define a discharging range using a min. and max. discharging limit. In this case, it is not possible to charge the battery.
Specify a defined charge
It is possible to specify a defined charging power by setting the min. and max. charging power to the same value.
Specify a defined discharge
It is possible to specify a defined discharging power by setting the min. and max. discharging power to the same value.
Possible applications
The regulations in the Battery Management menu area enable optimal use of the energy generated. In some situations, the PV power cannot be used in full due to the time-dependent battery control.
Example | |
|---|---|
Fronius inverter (max. output power) | 6000 W |
Defined discharge of the battery | 6000 W |
PV power | 1000 W |
In this case, the inverter reduces the PV power to 0 W, since the output power of the inverter is max. 6000 W. The inverter is already being fully utilized through discharging the battery.
"Rules"
It is possible for up to four different load management rules to be defined. At the same threshold values, the rules are activated in succession. For deactivation, this is done in reverse; the I/O last switched on is the first to be switched off. In the case of different thresholds, the I/O with the lowest threshold is switched on first, followed by the second lowest, and so on.
IMPORTANT!
An I/O is activated/deactivated after 60 seconds.
All available updates for inverters and other Fronius devices are provided on the product pages and in the "Fronius Download Search" area at www.fronius.com .
The guided setup wizard can be accessed here.
All settings
Resets all configuration data, apart from the country setup. Changes to the country setup may only be made by authorized personnel.
All settings without network
Resets all configuration data, apart from the country setup and the network settings. Changes to the country setup may only be made by authorized personnel.
After the guided setup wizard is finished, a configuration report according to the standards of the Electric Power Research Institute (EPRI) can be created.This function can also be retrieved in the System menu. The report serves as essential documentation to verify that the appropriate settings in compliance with utility requirements have been applied.
The filename contains the serial number of the inverter and can be changed individually. Click the button to download the report either as a csv or a pdf file.
Current messagesAll current events of the linked system components are displayed here.
IMPORTANT!
Depending on the type of event, this must be confirmed via the "tick" button so that it can be further processed.
History
All events of the linked system components that are no longer present are displayed here.
All the information regarding the system and the current settings is displayed and provided for download in this menu area.
The power data and functional scope of the inverter are stored in the license file.
If the inverter, power stage set PC board, or data communication area is replaced, the license file must also be replaced.
IMPORTANT!
The support user exclusively enables Fronius Technical Support to configure settings on the inverter via a secure connection. Access is deactivated by clicking the Terminate Support User Session button.
IMPORTANT!
The remote access exclusively enables Fronius Technical Support to access the inverter via a secure connection. In this case, diagnostics data are transmitted, which are used for troubleshooting. The remote access can be activated only upon request by Fronius Support.
Server addresses for data transfer
If a firewall is used for outgoing connections, allow the below protocols, server addresses, and ports for successful data transfer, see:
https://www.fronius.com/~/downloads/Solar%20Energy/Firmware/SE_FW_Changelog_Firewall_Rules_EN.pdf
When using FRITZ!Box products, configure Internet access without any restrictions or limitations. Do not set the DHCP Lease Time (validity) to 0 (=infinite).
LAN:
After establishing the connection, check the connection status.
WiFi:
Activate the access point of the inverter. This is opened by touching the sensor > Communications LED flashes blue
After connecting, the status of the connection should be checked.
After establishing the connection, check the connection status.
Access point:
The inverter serves as the access point. A PC or mobile device connects directly to the inverter. Connecting to the Internet is not possible. Assign a Network Name (SSID) and Network Key (PSK) to establish a connection. Assign a Network Key (PSK) with at least 20 characters, consisting of upper and lower case letters, special characters, and numbers, to protect the device from unauthorized access.
It is possible to operate a connection via WiFi and via the access point at the same time.
Server addresses for data transfer
If a firewall is used for outgoing connections, allow the below protocols, server addresses, and ports for successful data transfer, see:
https://www.fronius.com/~/downloads/Solar%20Energy/Firmware/SE_FW_Changelog_Firewall_Rules_EN.pdf
When using FRITZ!Box products, configure Internet access without any restrictions or limitations. Do not set the DHCP Lease Time (validity) to 0 (=infinite).
LAN:
After establishing the connection, check the connection status.
WiFi:
Activate the access point of the inverter. This is opened by touching the sensor > Communications LED flashes blue
After connecting, the status of the connection should be checked.
After establishing the connection, check the connection status.
Access point:
The inverter serves as the access point. A PC or mobile device connects directly to the inverter. Connecting to the Internet is not possible. Assign a Network Name (SSID) and Network Key (PSK) to establish a connection. Assign a Network Key (PSK) with at least 20 characters, consisting of upper and lower case letters, special characters, and numbers, to protect the device from unauthorized access.
It is possible to operate a connection via WiFi and via the access point at the same time.
The inverter communicates with system components (e.g., Fronius Smart Meter) and other inverters via Modbus. The primary device (Modbus Client) sends control commands to the secondary device (Modbus Server). The control commands are executed by the secondary device.
RTU Server
The following input fields and functions are available for communication via Modbus RTU:
| Meter address offset |
| Inverter address |
| SunSpec Model Type |
| Interface |
| Baud Rate |
| Parity |
| Allow Control If this option is activated, the inverter is controlled via Modbus. Inverter control includes the following functions:
|
TCP Server
The following input fields and functions are available for communication via Modbus TCP:
| Meter address offset |
| SunSpec Model Type |
| Modbus port |
| Meter Address |
| Allow Control If this option is activated, the inverter is controlled via Modbus. Inverter control includes the following functions:
|
| Restrict Control |
The utility/energy supplier can influence the output power of the inverter with Cloud control. This requires the inverter to have an active Internet connection.
Parameter | Display | Description |
|---|---|---|
Cloud control | Off | Cloud control of the inverter is deactivated. |
On | Cloud control of the inverter is activated. |
Profile | Value range | Description |
|---|---|---|
Allow cloud control for regulatory purposes (Technician) | Deactivated/Activated | The function may be mandatory for proper operation of the system.* |
Allow cloud control for Virtual Power Plants (Customer) | Deactivated/Activated | If the Allow remote control for regulatory purposes (technician) function is activated (technician access required), the Allow remote control for virtual power plants function is automatically activated and cannot be deactivated.* |
* Cloud control
A virtual power plant is an interconnection of multiple generators. This virtual power plant can be controlled by means of the cloud control via the Internet. An active inverter Internet connection is a prerequisite for this. System data are transferred.
The Fronius Solar API is an IP-based, open JSON interface. If it is activated, IOT devices in the local network can access inverter information without authentication. For security reasons, the interface is deactivated ex works and must be activated if it is required for a third-party application (e.g., EV charger, Smart Home solutions, etc.).
For monitoring, Fronius recommends using Fronius Solar.web, which offers secure access to the inverter status and production information.
In the event of a firmware update to version 1.14.x, the setting is taken from the Fronius Solar API. In systems with a version below 1.14.x, the Solar API is activated; with higher versions, it is deactivated but can be switched on and off via the menu
Activating the Fronius Solar API
Activate the “Activate communication via Solar API” function in the menu area “Communication” → “Solar API” on the user interface of the inverter.
Danger from unauthorized fault analyses and repair work.
This can result in serious injury and damage to property.
Fault analyses and repair work on the PV system may only be carried out by installers/service technicians from authorized specialist companies in accordance with national standards and regulations.
Risk due to unauthorized access.
Incorrectly set parameters can have a negative effect on the public grid and/or the grid power feed operation of the inverter and result in the loss of standard conformity.
Parameters may only be adjusted by installers/service technicians from authorized specialist companies.
Do not give the access code to third parties and/or unauthorized persons.
Risk due to incorrectly set parameters.
Incorrectly set parameters can have a negative effect on the public grid and/or cause inverter malfunctions and failures and result in the loss of standard conformity.
Parameters may only be adjusted by installers/service technicians from authorized specialist companies.
Parameters may only be adjusted if this has been approved or requested by the utility.
Any parameter adjustments must be made in compliance with nationally applicable standards and/or directives as well as the specifications of the utility.
The Country Setup menu area is intended exclusively for installers/service technicians from authorized specialist companies. To apply for the access code required for this menu area, see chapter Requesting inverter codes in Solar.SOS.
The selected country setup for the country in question contains preset parameters in accordance with nationally applicable standards and requirements. Changes may need to be made to the selected country setup depending on local grid conditions and the specifications of the utility.
Danger from unauthorized fault analyses and repair work.
This can result in serious injury and damage to property.
Fault analyses and repair work on the PV system may only be carried out by installers/service technicians from authorized specialist companies in accordance with national standards and regulations.
Risk due to unauthorized access.
Incorrectly set parameters can have a negative effect on the public grid and/or the grid power feed operation of the inverter and result in the loss of standard conformity.
Parameters may only be adjusted by installers/service technicians from authorized specialist companies.
Do not give the access code to third parties and/or unauthorized persons.
Risk due to incorrectly set parameters.
Incorrectly set parameters can have a negative effect on the public grid and/or cause inverter malfunctions and failures and result in the loss of standard conformity.
Parameters may only be adjusted by installers/service technicians from authorized specialist companies.
Parameters may only be adjusted if this has been approved or requested by the utility.
Any parameter adjustments must be made in compliance with nationally applicable standards and/or directives as well as the specifications of the utility.
The Country Setup menu area is intended exclusively for installers/service technicians from authorized specialist companies. To apply for the access code required for this menu area, see chapter Requesting inverter codes in Solar.SOS.
The selected country setup for the country in question contains preset parameters in accordance with nationally applicable standards and requirements. Changes may need to be made to the selected country setup depending on local grid conditions and the specifications of the utility.
The Country Setup menu area is intended exclusively for installers/service technicians from authorized specialist companies. The inverter access code required for this menu area can be requested in the Fronius Solar.SOS portal.
Risk due to unauthorized access.
Incorrectly set parameters can have a negative effect on the public grid and/or the grid power feed operation of the inverter and result in the loss of standard conformity.
Parameters may only be adjusted by installers/service technicians from authorized specialist companies.
Do not give the access code to third parties and/or unauthorized persons.
Activating this function limits the output power of the inverter to the specified value in watts.
This system is equipped with a power control system (PCS) according to UL3141. All PCS controlled busbars or conductors shall be protected with suitably rated overcurrent devices appropriately sized for the busbar rating or conductor ampacity.
The Application Guide for the ESS modes is available at the following link:
https://www.fronius.com/~/downloads/Solar%20Energy/Whitepaper/SE_WP_Fronius_GEN24_Plus_ESS_Modes_EN.pdf
Energy companies or utilities may impose feed-in limits on inverters (e.g., a maximum of 70% of kWp or a maximum of 5 kW). The inverter limits the effective power at the grid connection point (installation location of the Fronius Smart Meter or primary meter) to the set value.
The inverter takes the household’s consumption into account before reducing output. An individual limit can be set.
In order to minimize yield losses due to the power of feeding in limitation, the power available from the module array can be:
If these possibilities have been exhausted, the power drawn from the module array is reduced to such an extent that the feed-in limit is not exceeded.
Installation options that include an inverter, Fronius Smart Meter, and system components are listed under Different operating modes.
Total DC system capacity
Input field for the total DC system capacity in Wp. Always enter this value if the Maximum grid feed-in power is specified in %.
Power Limitation disabled
The inverter converts all available photovoltaic power.
Power Limitation enabled
Limiting power feed-in with the following options:
Dynamic Power Limitation (Soft Limit)
If this value is exceeded, the inverter will reduce output to the set value. The value is adjusted within the timeframe required by national standards and regulations.
Max. Grid Feed-in Power
Input field for the maximum grid feed-in power in W or % (setting range: -10 to 100%).
If there is no meter in the system or the primary meter has failed, the inverter limits its output power to the set value.
Feed-in Limit Shut-off Function (PAV, E protection)
This function monitors compliance with the feed-in limit. If Dynamic feed-in limit (Soft Limit) is activated, the inverter controls the power of feeding in in such a way that this function is usually not activated. If the specified limit values and shutdown times are exceeded, this protective function disconnects the inverter from the grid.
The feed-in limitation shutdown function (PAV, E protection) is available only if a Smart Meter ingress protection configured with MQTT is installed at the feed-in point.
Feed-in Limitation Shutdown Function (Hard Limit Trip)
IMPORTANT! This feature is available only when Dynamic Power Limiting (Soft Limit) is enabled.
If this value is exceeded, the inverter switches off within max. 5 seconds. This value must be higher than the value set for Export Limit Control (Soft Limit).
If necessary, enable the Fail-safefunction, reduce inverter output to 0% when the connection to the Smart Meter is disconnected. When this function is enabled, the inverter activates standby mode. No power is being fed into the grid.
The use of WiFi for communication between the Fronius Smart Meter and the inverter is not recommended when the Fail-safefunction is activated. Even short-term disconnections can cause the inverter to shut down. This problem is particularly common with weak WiFi signal strengths, a slow or overloaded WiFi connection, and automatic channel selection of the router.
IMPORTANT! To view and change settings in this menu item, select the user Technician, and enter and confirm the password for the user Technician. Settings in this menu area may only be made by trained and qualified personnel.
The inverter can be used as a primary device to control dynamic feed-in limits for additional Fronius inverters (secondary devices) so that feed-in limits prescribed by energy companies or utilities can be centrally managed. This control refers to the Soft Limit feed-in limit (see Feed-in limit). The following requirements must be met:IMPORTANT! Only one primary meter is required for the primary device.
IMPORTANT! If an inverter with a battery is connected, it must be used as the primary device for dynamic feed-in limits.
Dynamic feed-in limitation is available with the following device combinations:
Primary device | Secondary devices |
|---|---|
Fronius Primo GEN24 | Fronius Primo GEN24, Fronius SnapINverter with Fronius Datamanager 2.0* |
Primary meter
The Fronius Smart Meter acts as the only primary meter and is connected directly to the primary device. The Smart Meter monitors the total output power of all inverters into the grid and passes this information to the primary device via Modbus.
Primary device
The primary device automatically scans the network for available secondary devices. A list of the inverters found is displayed. Click Refresh to perform the search again.

Secondary device
A secondary device takes over the export limitation of the primary device. No data are sent to the primary device for the export limitation. The following configurations must be set for the power control:
General
Settings relevant to the grid operator are defined as rules under this menu item. This relates to an effective power limit in % or watts and/or a power factor specification. To view and change settings, select the Technician user, and enter and confirm the password. Only technical specialists may make settings in this menu area.
Under Rules, expand a menu area (e.g., Rule 1). Configure the following settings:
Limitation
IMPORTANT!
A dynamic feed-in limit for several inverters can be configured under Feed-in limit. I/O power management rules are transferred from the inverter (primary device) to connected inverters in the system (secondary devices).
Select the following rules for power management:
IMPORTANT!
The rules for shutdown apply to this device and cannot be applied to other inverters in the system.
Input pattern (assignment of individual I/Os)
1 click = white, contact open
2 clicks = blue, contact closed
3 clicks = gray, not used
Power Factor (cos φ) (define value)
Impedance response
DNO Feedback
If the rule is activated, always configure the DNO Feedback output, e.g., for operating a signal device.
The Import and Export of defined rules can be carried out in the data format *.fpc. The rules and pin assignments in the following connection examples are not the only possible configurations. For pin assignment, take into account the available connections at the Data communication area and settings of the device configuration.
If there is an active rule for the control of the inverter, the device indicates this in the overview of the user interface under Device State.
Controlling Priorities
Used to set controlling priorities for I/O Power Management (DRM or ripple control receiver), the feed-in limit, and control via Modbus.
1 = highest priority, 3 = lowest priority
Local priorities of the I/O power management, the feed-in limit, and the Modbus interface are deactivated by cloud control commands (regulatory purposes and virtual power plants) – see Cloud control – and by backup power.
In terms of controlling priorities, the device differentiates between power control and inverter shutdown. Inverter shutdown always takes precedence over power control. An inverter shutdown command is always executed and does not need to be prioritized.
Power controlThe ripple control signal receiver and the I/O terminal of the inverter can be connected to one another as shown in the connection diagram.
For distances of over 11 yd between the inverter and the ripple control signal receiver, a CAT 5 cable is recommended as a minimum and the shielding must be connected on one side at the push-in terminal of the data communication area (SHIELD).
| (1) | Ripple control signal receiver with 4 relays for effective power limitation. |
| (2) | I/Os of the data communication area. |
The settings for 4-relay operation are saved.
The ripple control signal receiver and the I/O terminal of the inverter can be connected to one another as shown in the connection diagram.
For distances of over 11 yd between the inverter and the ripple control signal receiver, a CAT 5 cable is recommended as a minimum and the shielding must be connected on one side at the push-in terminal of the data communication area (SHIELD).
| (1) | Ripple control signal receiver with 3 relays for effective power limitation. |
| (2) | I/Os of the data communication area. |
The settings for 3-relay operation are saved.
The ripple control signal receiver and the I/O terminal of the inverter can be connected to one another as shown in the connection diagram.
For distances of over 11 yd between the inverter and the ripple control signal receiver, a CAT 5 cable is recommended as a minimum and the shielding must be connected on one side at the push-in terminal of the data communication area (SHIELD).
| (1) | Ripple control signal receiver with 2 relays for effective power limitation. |
| (2) | I/Os of the data communication area. |
The settings for 2-relay operation are saved.
The ripple control signal receiver and the I/O terminal of the inverter can be connected to one another as shown in the connection diagram.
For distances of over 10 m between the inverter and the ripple control signal receiver, a CAT 5 cable is recommended as a minimum and the shielding must be connected on one side at the push-in terminal of the data communication area (SHIELD).
| (1) | Ripple control signal receiver with 1 relay for effective power limitation. |
| (2) | I/Os of the data communication area. |
The settings for 1-relay operation are saved.
Danger due to electrical voltage on live parts of the photovoltaic system.
This can result in serious injury and damage to property.
Disconnect live parts of the photovoltaic system on all pins and on all sides.
Secure against re-activation in accordance with national regulations.
Allow the capacitors of the inverter to discharge (2 minutes).
Check that the inverter is de-energized with a suitable measuring device.
Danger due to work that has been carried out incorrectly.
This can result in serious injury and damage to property.
Installing and connecting an option must only be carried out by service personnel trained by Fronius and only within the scope of the respective technical regulations.
Follow the safety rules.
Danger due to damaged and/or contaminated terminals.
This can result in serious injury and damage to property.
Before making any connections, check the terminals for damage and contamination.
Remove contamination in the de-energized state.
Have defective terminals repaired by an authorized specialist.
Danger due to electrostatic discharge (ESD).
This may result in damage to electronic components.
Pay attention to the ESD marking on the product and/or on the packaging.
Take ESD protection measures (grounding, neutralizing, and shielding).
The continuous supply via the PV Point depends on the available PV power.
If the solar modules are not supplying enough power, interruptions may occur.
Do not connect any loads that require an uninterruptible supply.
IMPORTANT!
The valid national laws, standards, and provisions, as well as the specifications of the relevant grid operator are to be taken into account and applied.
It is highly recommended that the specific installation be agreed with the grid operator and explicitly approved by this operator. This obligation applies to system constructors in particular (e.g., installers).
Danger due to electrical voltage on live parts of the photovoltaic system.
This can result in serious injury and damage to property.
Disconnect live parts of the photovoltaic system on all pins and on all sides.
Secure against re-activation in accordance with national regulations.
Allow the capacitors of the inverter to discharge (2 minutes).
Check that the inverter is de-energized with a suitable measuring device.
Danger due to work that has been carried out incorrectly.
This can result in serious injury and damage to property.
Installing and connecting an option must only be carried out by service personnel trained by Fronius and only within the scope of the respective technical regulations.
Follow the safety rules.
Danger due to damaged and/or contaminated terminals.
This can result in serious injury and damage to property.
Before making any connections, check the terminals for damage and contamination.
Remove contamination in the de-energized state.
Have defective terminals repaired by an authorized specialist.
Danger due to electrostatic discharge (ESD).
This may result in damage to electronic components.
Pay attention to the ESD marking on the product and/or on the packaging.
Take ESD protection measures (grounding, neutralizing, and shielding).
The continuous supply via the PV Point depends on the available PV power.
If the solar modules are not supplying enough power, interruptions may occur.
Do not connect any loads that require an uninterruptible supply.
IMPORTANT!
The valid national laws, standards, and provisions, as well as the specifications of the relevant grid operator are to be taken into account and applied.
It is highly recommended that the specific installation be agreed with the grid operator and explicitly approved by this operator. This obligation applies to system constructors in particular (e.g., installers).
Danger due to electrical voltage on live parts of the photovoltaic system.
This can result in serious injury and damage to property.
Disconnect live parts of the photovoltaic system on all pins and on all sides.
Secure against re-activation in accordance with national regulations.
Allow the capacitors of the inverter to discharge (2 minutes).
Check that the inverter is de-energized with a suitable measuring device.
Danger due to work that has been carried out incorrectly.
This can result in serious injury and damage to property.
Installing and connecting an option must only be carried out by service personnel trained by Fronius and only within the scope of the respective technical regulations.
Follow the safety rules.
Danger due to damaged and/or contaminated terminals.
This can result in serious injury and damage to property.
Before making any connections, check the terminals for damage and contamination.
Remove contamination in the de-energized state.
Have defective terminals repaired by an authorized specialist.
Danger due to electrostatic discharge (ESD).
This may result in damage to electronic components.
Pay attention to the ESD marking on the product and/or on the packaging.
Take ESD protection measures (grounding, neutralizing, and shielding).
The continuous supply via the PV Point depends on the available PV power.
If the solar modules are not supplying enough power, interruptions may occur.
Do not connect any loads that require an uninterruptible supply.
IMPORTANT!
The valid national laws, standards, and provisions, as well as the specifications of the relevant grid operator are to be taken into account and applied.
It is highly recommended that the specific installation be agreed with the grid operator and explicitly approved by this operator. This obligation applies to system constructors in particular (e.g., installers).
The PV Point Comfort is available as an option and can be retrofitted to the inverter.
For technical data, see chapter Technical data on page (→).
Turn off the automatic circuit breaker. Set the DC disconnector to the "off" switch position.
Disconnect connections from the solar module strings (+/-). Switch off the battery connected to the inverter.
Wait for the capacitors of the inverter to discharge (2 minutes).
Danger due to insufficiently dimensioned ground conductor.
Damage to the inverter due to thermal overload can result.
The national standards and guidelines must be observed for dimensioning the ground conductor.
Loosen the 2 screws on the underside of the housing cover by rotating them 180° to the left using a screwdriver (TX20). Then lift the housing cover away from the inverter at the bottom and detach from above.
Loosen the 5 screws of the connection area cover by rotating them 180° to the left using a screwdriver (TX20).
Remove the connection area cover from the device.
Press the lock on the back of the terminal and remove the AC terminals.
Disconnect the single conductors from the AC terminal (only necessary if the installation already exists).
Loosen the ground conductor (PE) from the ground electrode terminal using a screwdriver (TX20).
Loosen the ground conductor (PE) from the conduit using a flathead screwdriver (1/8“).
Remove the mains cable from the inverter.
Insert the insulating film on the right side of the ground electrode terminal.
Insert the PC board into the inverter.
Fasten the PC board with the 4 screws (TX20) supplied and tighten to a torque of 10.6 in-lb / 1.2 Nm.
Strip the single conductors according to the specifications based on the power category of the inverter.
The cable cross-section must be selected according to the specifications for the respective power category of the inverter (see chapter Permitted cables for the electrical connection on page (→)).
Strip the insulation of the single conductors by 3/8 inch / 10 mm. Insert the stripped single conductor into the slot provided, all the way up to the stop.
Strip the single conductors (Primo 3.8 ‑ 6 kW = 1/2 inch / 12 mm, Primo 7.7 ‑ 10 kW = 3/4 inch / 19 mm). Lift to open the AC terminal's operating lever and insert the stripped single conductor into the slot provided, all the way up to the stop. Then close the operating lever until it engages.
IMPORTANT!
The PEN connection must be designed according to the national provisions.
Fasten the PEN conductor to the second input of the ground electrode terminal from the top using a screwdriver (TX20) and a torque of 16‑18 in-lb / 1.8‑2.0 Nm.
Strip the single conductors according to the specifications based on the power category of the inverter.
The cable cross-section must be selected according to the specifications for the respective power category of the inverter (see chapter Permitted cables for the electrical connection on page (→)).
IMPORTANT!
If necessary, an automatic circuit breaker of max. 16 A can also be used for protection. In backup power operation, a maximum of 13 A can be provided. The residual current circuit breaker and automatic circuit breaker must be designed according to the national provisions.
Connect the phase/neutral conductors to the terminals provided. Fasten the ground conductor to the third input of the ground electrode terminal from the top using a screwdriver (TX20) and a torque of 16‑18 in-lb / 1.8‑2.0 Nm.
IMPORTANT!
The ground conductor must be connected with a movement loop so that if the cable gland fails, the ground conductor is disconnected last.
Connect the stripped phase/neutral conductors to the terminals provided.
Insert the terminals into the respective slot until they engage.
Place the cover on the connection area. Tighten the five screws by rotating them 180° to the right in the indicated order using a screwdriver (TX20).
Clip the housing cover onto the inverter from above.
Press on the lower part of the housing cover and tighten the two screws by rotating them 180° to the right using a screwdriver (TX20).
Connect the solar module strings (+/-). Switch on the battery connected to the inverter.
Set the DC disconnector to the "on" switch position. Turn on the automatic circuit breaker.
Firmware version 1.25.2 or higher is required to commission the PV Point Comfort. Outdated firmware versions could lead to incompatibilities between the inverter and PV Point Comfort. In this case, the inverter firmware should be updated in accordance with the chapter headed Update on page (→).
A battery charge of min. 30% is recommended for test mode.
A description of how to run the test mode can be found in the checklist – Backup power (https://www.fronius.com/de/download-center?searchword=42,0426,0365).
The inverter is designed so that it does not require additional maintenance work. Nevertheless, a few points must be considered during operation to ensure that the inverter works perfectly.
The inverter is designed so that it does not require additional maintenance work. Nevertheless, a few points must be considered during operation to ensure that the inverter works perfectly.
The inverter is designed so that it does not require additional maintenance work. Nevertheless, a few points must be considered during operation to ensure that the inverter works perfectly.
Wipe the inverter, if necessary, with a damp cloth.
Do not use cleaning agents, scouring agents, solvents, or similar products to clean the inverter.
Maintenance and service work may only be carried out by a technical specialist.
The DC disconnector is used only to switch off power to the power stage set. When the DC disconnector is turned off, the connection area is still energized.
Danger from mains voltage and DC voltage from PV modules.
This can result in severe personal injury and damage to property.
The connection area must only be opened by an authorized electrician.
The separate power stage set area must only be opened by Fronius-trained service technicians.
Prior to any connection work, ensure that the inverter is de-energized on the AC side and the DC side.
Danger of residual voltage from capacitors.
This can result in severe personal injury and damage to property.
Allow the capacitors of the inverter to discharge (2 minutes).
If the inverter is operated in dusty environments, dirt may build up on the heat sink and fan.
This may result in a loss of power due to insufficient cooling of the inverter.
Make sure that the ambient air can always flow through the inverter's ventilation slots unimpeded.
Remove any build-ups of dirt from the heat sink and the fan.
Switch off power to the inverter and wait for the specified time until the capacitors have discharged and the fan has shut down.
Turn the DC disconnector to the "Off" switch setting.
Loosen the screws on the underside of the housing cover by rotating them 180° to the left using a screwdriver (TX20). Then lift the housing cover away from the inverter at the bottom and detach from above.
Remove any build-up of dirt on the heat sink and fan using compressed air, a cloth, or a brush.
Risk due to damage to the fan bearing in the event of incorrect cleaning.
Excessive speeds and the application of pressure to the fan bearing can cause damage.
Block the fan and clean with compressed air.
When using a cloth or brush, clean the fan without applying any pressure.
To start up the inverter again, follow the steps listed above in reverse order.
Used equipment and batteries must be returned to the distributor or an authorized local collection system. Do not dispose of batteries with domestic waste. Protect batteries from high temperatures, direct sunlight, moisture and corrosive environments.
Arrange for the safe collection and proper disposal of damaged, leaking or used batteries by a battery recycling company or the Fronius Service Partner.
In addition, it should be noted that batteries contain substances that, if disposed of improperly, can have a significant negative impact on the environment as well as on human health and the safety of persons, in particular due to the leakage of hazardous substances such as heavy metals or electrolytes, which can contaminate soil, water and air.
This ensures environmental protection and the sustainable use of natural resources.Packaging materialsDetailed warranty conditions specific to your country can be found at https://www.fronius.com/en/download-center?searchword=Warranty+conditions .
If there is a warranty for the relevant product, register the product at https://warranty.fronius.com/ and activate or extend the warranty.
Detailed warranty conditions specific to your country can be found at https://www.fronius.com/en/download-center?searchword=Warranty+conditions .
If there is a warranty for the relevant product, register the product at https://warranty.fronius.com/ and activate or extend the warranty.
Status codes are displayed on the user interface of the inverter in the System > Event Log menu area or in the user menu under Notifications and in Fronius Solar.web*.
| * | If configured accordingly, see chapter Fronius Solar.web on page (→). |
Status codes are displayed on the user interface of the inverter in the System > Event Log menu area or in the user menu under Notifications and in Fronius Solar.web*.
| * | If configured accordingly, see chapter Fronius Solar.web on page (→). |
| Cause: | A device that is connected in the WSD chain has interrupted the signal line (e.g., surge protection device) or the bypass installed ex works as standard has been removed and no trigger device has been installed. |
| Remedy: | If the SPD surge protection device has tripped, the inverter must be repaired by an authorized specialist. |
| OR: | Install the bypass installed ex works as standard or a trigger device. |
| OR: | Turn the WSD (wired shutdown) switch to position 1 (WSD primary device). |
WARNING!Danger from work that is not carried out properly. This can result in serious injury and damage to property. The installation and connection of an SPD surge protection device may only be carried out by Fronius-trained service personnel in accordance with the technical specifications. Observe safety rules. | |
| Cause: | An electric arc has been identified on the PV system, and the maximum number of automatic connections within 24 hours has been reached. |
| Remedy: | Keep the sensor pressed on the inverter for 3 seconds |
| OR: | On the user interface of the inverter, in the System > Event Log menu area, confirm the status 1173 - ArcContinuousFault. |
| OR: | On the user interface of the inverter, in the Notifications user menu, confirm the status 1173 - ArcContinuousFault. |
CAUTION!Danger from damaged components of the PV system Serious personal injury/damage to property may result. Before the status 1173 - ArcContinuousFault is confirmed, the entire photovoltaic system affected must be checked for any possible damage. Damaged components must be repaired by qualified specialists. | |
| Cause: | An electric arc has been identified on the PV system. |
| Remedy: | No action required. |
DC input data | ||
|---|---|---|
MPP voltage range | 200 – 480 V | |
Max. input voltage at 1 000 W/m²/14 °F in an open circuit | 600 V | |
Min. input voltage | 65 V | |
Start-up input voltage | 80 V | |
Nominal PV power | at 208 V | 3 940 W |
Max. PV array power | at 208 V | 5 700 W |
Nominal input voltage | at 208 V | 360 V |
Nominal input current | at 208 V | 10.9 A |
Max. input |
| |
Max. short circuit current for module array (ISC PV) |
| |
Max. total short circuit current for module array |
| |
Max. continuous utility backfeed current 1) | 0.0 A | |
AC output data | ||
|---|---|---|
Max. output power | at 208 V | 3 800 W |
Max. output power at +140 °F (60 °C) V min/V max | at 208 V | 2 400 W/1 500 W |
Nominal AC voltage | 208 V/220 V/240 V | |
Voltage trip limit accuracy | 1 % of nominal value | |
Max. continuous output current at Vnom | at 208 V | 18.3 A |
Output overcurrent protection | at 208 V | 25.0 A |
Phases | 1 | |
Max. output fault current per duration (peak/rms over duration) | at 208 V | 536 A/15.7 A over 151 ms |
Nominal output frequency | 60 Hz | |
Setting range for mains frequency | 45.0 – 66.0 Hz | |
Frequency trip limit accuracy | 0.05 Hz | |
Total harmonic distortion | < 3.5 % | |
Power factor (cos phi) | 0.8 – 1 ind./cap. 2) | |
Max. permitted mains impedance Zmax at PCC (mOhm)3) | None | |
General data | ||
|---|---|---|
Maximum efficiency | at 208 V | 97.4 % |
CEC efficiency | at 208 V | 96.5 % |
Night tare loss | at 208 V | 8.4 W |
Cooling | Controlled forced-air ventilation | |
Protection class | Type 4X | |
Dimensions H × W × D | 20.3 × 18.7 × 6.5 inches | |
Weight | 35.56 lbs. | |
Shipping dimensions H × W × D | 23.3 × 22.2 × 10.1 inches | |
Shipping weight | 41.23 lbs. | |
Inverter topology | non-isolated, no transformer | |
Permitted ambient temperature | -40 °F – +140 °F | |
Permissible humidity | 0 – 100 % | |
EMC emission class | B | |
DC/AC overvoltage (according to UL1741 3rd Edition, CSA-C22.2 No.107.1-16) | 2/4 | |
Pollution degree | 2 | |
Safety class (according to IEC 62103) | 1 | |
Protection devices | ||
|---|---|---|
DC isolation measurement | Error/shutdown at RISO < 500 kOhm | |
DC overload performance | Operating point shift, power limiter | |
DC disconnector | Integrated | |
DC reverse polarity protection | Integrated | |
Arc Fault Circuit Interrupter | AFCI type 1 integrated, according to UL1699B:2024 and F-I-AFPE-1-4-1 according to IEC63027:2023 | |
Rapid shutdown | Integrated PVRSE | RS2 equipment, in accordance with UL1741 and CSA C22.2 No.330 – 23 | |
RCMU | Integrated | |
Active anti-islanding method | Integrated | |
Behavior in the event of overheating | Power limiter, active cooling | |
Output data PV Point | ||
|---|---|---|
Nominal AC voltage PV Point | 1~NPE 120 V | |
Nominal output power PV Point | at 120 V | 1 560 W |
Max. continuous output current | at 120 V | 13.0 A |
Nominal output frequency | 63 Hz | |
Power factor | 0 – 1 ind./cap.2) | |
Switching time | < 17 s | |
Data communication | ||
|---|---|---|
WLAN SMA-RP connection | 802.11b/g/n (WPA, WPA2) | |
Ethernet (LAN) | RJ 45, 10/100 Mbit | |
Wired shutdown (WSD) | max. 28 devices/WSD chain | |
Modbus RTU SunSpec (2x) | RS485 2-wire | |
Battery Connection | Modbus O/RJ 45/12 V power supply | |
Voltage level of digital inputs | low: min. 0 V - max. 1.8 V | |
Input currents of digital inputs
| depending on the input voltage; | |
Total power for digital output | 6 W at 12 V | |
Power per digital output | 1 A at >12.5 V – 24 V | |
DC Input data battery 4) | ||
|---|---|---|
Min. voltage | 150 V | |
Max. voltage | 455 V | |
Max. current | 22 A | |
Max. input | 3 800 W | |
DC Inputs | 1 | |
Output data Essential Backup 5) | ||
|---|---|---|
Nominal output power Essential Backup | at 120 V | 3 800 W |
Max. continuous output current | at 120 V | 18.3 A |
Nominal output frequency | 63 Hz | |
Power factor | 0.8 – 1 ind./cap.2) | |
Switching time | < 17 s | |
DC input data | ||
|---|---|---|
MPP voltage range | 200 – 480 V | |
Max. input voltage at 1 000 W/m²/14 °F in an open circuit | 600 V | |
Min. input voltage | 65 V | |
Start-up input voltage | 80 V | |
Nominal PV power | at 208 V | 3 940 W |
Max. PV array power | at 208 V | 5 700 W |
Nominal input voltage | at 208 V | 360 V |
Nominal input current | at 208 V | 10.9 A |
Max. input |
| |
Max. short circuit current for module array (ISC PV) |
| |
Max. total short circuit current for module array |
| |
Max. continuous utility backfeed current 1) | 0.0 A | |
AC output data | ||
|---|---|---|
Max. output power | at 208 V | 3 800 W |
Max. output power at +140 °F (60 °C) V min/V max | at 208 V | 2 400 W/1 500 W |
Nominal AC voltage | 208 V/220 V/240 V | |
Voltage trip limit accuracy | 1 % of nominal value | |
Max. continuous output current at Vnom | at 208 V | 18.3 A |
Output overcurrent protection | at 208 V | 25.0 A |
Phases | 1 | |
Max. output fault current per duration (peak/rms over duration) | at 208 V | 536 A/15.7 A over 151 ms |
Nominal output frequency | 60 Hz | |
Setting range for mains frequency | 45.0 – 66.0 Hz | |
Frequency trip limit accuracy | 0.05 Hz | |
Total harmonic distortion | < 3.5 % | |
Power factor (cos phi) | 0.8 – 1 ind./cap. 2) | |
Max. permitted mains impedance Zmax at PCC (mOhm)3) | None | |
General data | ||
|---|---|---|
Maximum efficiency | at 208 V | 97.4 % |
CEC efficiency | at 208 V | 96.5 % |
Night tare loss | at 208 V | 8.4 W |
Cooling | Controlled forced-air ventilation | |
Protection class | Type 4X | |
Dimensions H × W × D | 20.3 × 18.7 × 6.5 inches | |
Weight | 35.56 lbs. | |
Shipping dimensions H × W × D | 23.3 × 22.2 × 10.1 inches | |
Shipping weight | 41.23 lbs. | |
Inverter topology | non-isolated, no transformer | |
Permitted ambient temperature | -40 °F – +140 °F | |
Permissible humidity | 0 – 100 % | |
EMC emission class | B | |
DC/AC overvoltage (according to UL1741 3rd Edition, CSA-C22.2 No.107.1-16) | 2/4 | |
Pollution degree | 2 | |
Safety class (according to IEC 62103) | 1 | |
Protection devices | ||
|---|---|---|
DC isolation measurement | Error/shutdown at RISO < 500 kOhm | |
DC overload performance | Operating point shift, power limiter | |
DC disconnector | Integrated | |
DC reverse polarity protection | Integrated | |
Arc Fault Circuit Interrupter | AFCI type 1 integrated, according to UL1699B:2024 and F-I-AFPE-1-4-1 according to IEC63027:2023 | |
Rapid shutdown | Integrated PVRSE | RS2 equipment, in accordance with UL1741 and CSA C22.2 No.330 – 23 | |
RCMU | Integrated | |
Active anti-islanding method | Integrated | |
Behavior in the event of overheating | Power limiter, active cooling | |
Output data PV Point | ||
|---|---|---|
Nominal AC voltage PV Point | 1~NPE 120 V | |
Nominal output power PV Point | at 120 V | 1 560 W |
Max. continuous output current | at 120 V | 13.0 A |
Nominal output frequency | 63 Hz | |
Power factor | 0 – 1 ind./cap.2) | |
Switching time | < 17 s | |
Data communication | ||
|---|---|---|
WLAN SMA-RP connection | 802.11b/g/n (WPA, WPA2) | |
Ethernet (LAN) | RJ 45, 10/100 Mbit | |
Wired shutdown (WSD) | max. 28 devices/WSD chain | |
Modbus RTU SunSpec (2x) | RS485 2-wire | |
Battery Connection | Modbus O/RJ 45/12 V power supply | |
Voltage level of digital inputs | low: min. 0 V - max. 1.8 V | |
Input currents of digital inputs
| depending on the input voltage; | |
Total power for digital output | 6 W at 12 V | |
Power per digital output | 1 A at >12.5 V – 24 V | |
DC Input data battery 4) | ||
|---|---|---|
Min. voltage | 150 V | |
Max. voltage | 455 V | |
Max. current | 22 A | |
Max. input | 3 800 W | |
DC Inputs | 1 | |
Output data Essential Backup 5) | ||
|---|---|---|
Nominal output power Essential Backup | at 120 V | 3 800 W |
Max. continuous output current | at 120 V | 18.3 A |
Nominal output frequency | 63 Hz | |
Power factor | 0.8 – 1 ind./cap.2) | |
Switching time | < 17 s | |
DC input data | ||
|---|---|---|
MPP voltage range | 230 – 480 V | |
Max. input voltage at 1 000 W/m²/14 °F in an open circuit | 600 V | |
Min. input voltage | 65 V | |
Start-up input voltage | 80 V | |
Nominal PV power | at 208 V | 5 150 W |
Nominal input voltage | at 208 V | 360 V |
Nominal input current | at 208 V | 14.3 A |
Max. PV array power | at 208 V | 7 500 W |
Max. input current |
| |
Max. short circuit current for module array (ISC PV) |
| |
Max. total short circuit current for module array |
| |
Max. continuous utility backfeed current 1) | 0.0 A | |
AC output data | ||
|---|---|---|
Max. output power | at 208 V | 5 000 W |
Max. output power at +140 °F (60 °C) V min/V max | at 208 V | 2 400 W/1 500 W |
Nominal AC voltage | 208 V/220 V/240 V | |
Voltage trip limit accuracy | 1 % of nominal value | |
Max. continuous output current at Vnom | at 208 V | 24.0 A |
Output overcurrent protection | at 208 V | 30.0 A |
Phases | 1 | |
Max. output fault current per duration (peak/rms over duration) | at 208 V | 536 A/15.7 A over 151 ms |
Nominal output frequency | 60 Hz | |
Setting range for mains frequency | 45.0 – 66.0 Hz | |
Frequency trip limit accuracy | 0.05 Hz | |
Total harmonic distortion | < 3.5 % | |
Power factor (cos phi) | 0.8 – 1 ind./cap. 2) | |
Max. permitted mains impedance Zmax at PCC (mOhm)3) | None | |
General data | ||
|---|---|---|
Maximum efficiency | at 208 V | 97.4 % |
CEC efficiency | at 208 V | 97 % |
Night tare loss | at 208 V | 8.2 W |
Cooling | Controlled forced-air ventilation | |
Protection class | Type 4X | |
Dimensions H × W × D | 20.3 × 18.7 × 6.5 inches | |
Weight | 35.56 lbs. | |
Shipping dimensions H × W× D | 23.3 × 22.2 × 10.1 inches | |
Shipping weight | 41.23 lbs. | |
Inverter topology | non-isolated, no transformer | |
Permitted ambient temperature | -40 °F – +140 °F | |
Permissible humidity | 0 – 100 % | |
EMC emission class | B | |
DC/AC overvoltage (according to UL1741 3rd Edition, CSA-C22.2 No.107.1-16) | 2/4 | |
Pollution degree | 2 | |
Safety class (according to IEC 62103) | 1 | |
Protection devices | ||
|---|---|---|
DC isolation measurement | Error/shutdown at RISO < 500 kOhm | |
DC overload performance | Operating point shift, power limiter | |
DC disconnector | Integrated | |
DC reverse polarity protection | Integrated | |
Arc Fault Circuit Interrupter | AFCI type 1 integrated, according to UL1699B:2024 and F-I-AFPE-1-4-1 according to IEC63027:2023 | |
Rapid shutdown | Integrated, in accordance with UL1741 and CSA C22.2 No.330 – 23 | |
RCMU | Integrated | |
Active anti-islanding method | Integrated | |
Behavior in the event of overheating | Power limiter, active cooling | |
Output data PV Point | ||
|---|---|---|
Nominal AC voltage PV Point | 1~NPE 120 V | |
Nominal output power PV Point | at 120 V | 1 560 W |
Max. continuous output current | at 120 V | 13.0 A |
Nominal output frequency | 63 Hz | |
Power factor | 0 – 1 ind./cap.2) | |
Switching time | < 17 s | |
Data communication | ||
|---|---|---|
WLAN SMA-RP connection | 802.11b/g/n (WPA, WPA2) | |
Ethernet (LAN) | RJ 45, 10/100 Mbit | |
Wired shutdown (WSD) | max. 28 devices/WSD chain | |
Modbus RTU SunSpec (2x) | RS485 2-wire | |
Battery Connection | Modbus O/RJ 45/12 V power supply | |
Voltage level of digital inputs | low: min. 0 V - max. 1.8 V | |
Input currents of digital inputs | depending on the input voltage; input resistance = 70 kOhm | |
Total power for digital output | 6 W at 12 V | |
Power per digital output | 1 A at >12.5 V – 24 V | |
DC input data battery 4) | ||
|---|---|---|
Min. voltage | 150 V | |
Max. voltage | 455 V | |
Max. current | 22 A | |
Max. input | 5 000 W | |
DC Inputs | 1 | |
Output data Essential Backup 5) | ||
|---|---|---|
Nominal output power Essential Backup | at 120 V | 5 000 W |
Max. continuous output current | at 120 V | 24.0 A |
Nominal output frequency | 63 Hz | |
Power factor | 0.8 – 1 ind./cap.2) | |
Switching time | < 17 s | |
DC input data | ||
|---|---|---|
MPP voltage range | 230 – 480 V | |
Max. input voltage at 1 000 W/m²/14 °F in an open circuit | 600 V | |
Min. input voltage | 65 V | |
Start-up input voltage | 80 V | |
Nominal PV power | at 208 V | 5 920 W |
Nominal input voltage | at 208 V | 360 V |
Max. PV array power | at 208 V | 8 000 W |
Nominal input current | at 208 V | 16.4 A |
Max. input current |
| |
Max. short circuit current for module array (ISC PV) |
| |
Max. total short circuit current for module array |
| |
Max. continuous utility backfeed current 1) | 0.0 A | |
AC output data | ||
|---|---|---|
Max. output power | at 208 V | 5 740 W |
Max. output power at +140 °F (60 °C) V min/V max | at 208 V | 2 400 W/1 500 W |
Nominal AC voltage | 208 V/220 V/240 V | |
Voltage trip limit accuracy | 1 % of nominal value | |
Max. continuous output current at Vnom | at 208 V | 27.6 A |
Output overcurrent protection | at 208 V | 35.0 A |
Phases | 1 | |
Max. output fault current per duration (peak/rms over duration) | at 208 V | 536 A/15.7 A over 151 ms |
Nominal output frequency | 60 Hz | |
Setting range for mains frequency | 45.0 – 66.0 Hz | |
Frequency trip limit accuracy | 0.05 Hz | |
Total harmonic distortion | < 3.5 % | |
Power factor (cos phi) | 0.8 – 1 ind./cap. 2) | |
Max. permitted mains impedance Zmax at PCC (mOhm)3) | None | |
General data | ||
|---|---|---|
Maximum efficiency | at 208 V | 97.4 % |
CEC efficiency | at 208 V | 97 % |
Night tare loss | at 208 V | 8.4 W |
Cooling | Controlled forced-air ventilation | |
Protection class | Type 4X | |
Dimensions H × W × D | 20.3 × 18.7 × 6.5 inches | |
Weight | 35.56 lbs. | |
Shipping dimensions H × W × D | 23.3 × 22.2 × 10.1 inches | |
Shipping weight | 41.23 lbs. | |
Inverter topology | non-isolated, no transformer | |
Permitted ambient temperature | -40 °F – +140 °F | |
Permissible humidity | 0 – 100 % | |
EMC emission class | B | |
DC/AC overvoltage (according to UL1741 3rd Edition, CSA-C22.2 No.107.1-16) | 2/4 | |
Pollution degree | 2 | |
Safety class (according to IEC 62103) | 1 | |
Protection devices | ||
|---|---|---|
DC isolation measurement | Error/shutdown at RISO < 500 kOhm | |
DC overload performance | Operating point shift, power limiter | |
DC disconnector | Integrated | |
DC reverse polarity protection | Integrated | |
Arc Fault Circuit Interrupter | AFCI type 1 integrated, according to UL1699B:2024 and F-I-AFPE-1-4-1 according to IEC63027:2023 | |
Rapid shutdown | Integrated, in accordance with UL1741 and CSA C22.2 No.330 – 23 | |
RCMU | Integrated | |
Active anti-islanding method | Integrated | |
Behavior in the event of overheating | Power limiter, active cooling | |
Output data PV Point | ||
|---|---|---|
Nominal AC voltage PV Point | 1~NPE 120 V | |
Nominal output power PV Point | at 120 V | 1 560 W |
Max. continuous output current | at 120 V | 13.0 A |
Nominal output frequency | 63 Hz | |
Power factor | 0 – 1 ind./cap.2) | |
Switching time | < 17 s | |
Data communication | ||
|---|---|---|
WLAN SMA-RP connection | 802.11b/g/n (WPA, WPA2) | |
Ethernet (LAN) | RJ 45, 10/100 Mbit | |
Wired shutdown (WSD) | max. 28 devices/WSD chain | |
Modbus RTU SunSpec (2x) | RS485 2-wire | |
Battery Connection | Modbus O/RJ 45/12 V power supply | |
Voltage level of digital inputs | low: min. 0 V - max. 1.8 V | |
Input currents of digital inputs
| depending on the input voltage; input resistance = 70 kOhm | |
Total power for digital output | 6 W at 12 V | |
Power per digital output | 1 A at >12.5 V – 24 V | |
DC Input data battery 4) | ||
|---|---|---|
Min. voltage | 150 V | |
Max. voltage | 455 V | |
Max. current | 22 A | |
Max. input | 6 000 W | |
DC Inputs | 1 | |
Output data Essential Backup 5) | ||
|---|---|---|
Nominal output power Essential Backup | at 120 V | 5 740 W |
Max. continuous output current | at 120 V | 27.6 A |
Nominal output frequency | 63 Hz | |
Power factor | 0.8 – 1 ind./cap.2) | |
Switching time | < 17 s | |
DC input data | ||
|---|---|---|
MPP voltage range | 190 - 480 V | |
Max. input voltage at 1000 W/m²/14 °F in an open circuit | 600 V | |
Min. input voltage | 65 V | |
Start-up input voltage | 80 V | |
Nominal PV power | at 208 V | 3 940 W |
Max. PV array power | at 208 V | 5 700 W |
Nominal input voltage | at 208 V | 365 V |
Nominal input current | at 208 V | 10.8 A |
Max. input |
| |
Max. short circuit current for module array (ISC PV) |
| |
Max. total short circuit current for module array |
| |
Max. continuous utility backfeed current 1) | 0.0 A | |
AC output data | ||
|---|---|---|
Max. output power | at 208 V | 3 800 W |
Max. output power at +140 °F (60 °C) V min / V max | at 208 V | 1 760 W/1 540 W |
Nominal AC voltage | 208 V/220 V/240 V | |
Voltage trip limit accuracy | 1% of nominal value | |
Max. continuous output current at Vnom | at 208 V | 18.3 A |
Output overcurrent protection | at 208 V | 25.0 A |
Phases | 1 | |
Max. output fault current per duration (peak / rms over duration) | at 208 V | 141 A/30.3 A over 11 ms |
Nominal output frequency | 60 Hz | |
Setting range for mains frequency | 45.0 - 66.0 Hz | |
Frequency trip limit accuracy | 0.05 Hz | |
Total harmonic distortion | < 3.5% | |
Power factor (cos phi) | 0.8 - 1 ind./cap. 2) | |
Max. permitted mains impedance Zmax at PCC (mOhm)3) | None | |
General data | ||
|---|---|---|
Maximum efficiency | at 208 V | 97.3 % |
CEC efficiency | at 208 V | 96.5 % |
Night tare loss | at 208 V | 7.7 W |
Cooling | Controlled forced-air ventilation | |
Protection class | Type 4X | |
Dimensions H × W × D | 20.3 × 18.7 × 6.5 inches | |
Weight | 32.96 lbs. | |
Shipping dimensions H × W × D | 23.3 × 22.2 × 10.1 inches | |
Shipping weight | 41.12 lbs. | |
Inverter topology | non-isolated, no transformer | |
Permitted ambient temperature | -40 °F - +140 °F | |
Permissible humidity | 0 - 100% | |
EMC emission class | B | |
DC/AC overvoltage (according to UL1741 3rd Edition, CSA-C22.2 No.107.1-16) | 2/4 | |
Pollution degree | 2 | |
Safety class (according to IEC 62103) | 1 | |
Protection devices | ||
|---|---|---|
DC isolation measurement | Error/shutdown at RISO < 500 kOhm | |
DC overload performance | Operating point shift, power limiter | |
DC disconnector | Integrated | |
DC reverse polarity protection | Integrated | |
Arc Fault Circuit Interrupter | AFCI type 1 integrated, according to UL1699B:2024 | |
Rapid shutdown | Integrated PVRSE | RS2 equipment, in accordance with UL1741 and CSA C22.2 No.330-23 | |
RCMU | Integrated | |
Active anti-islanding method | Integrated | |
Behavior in the event of overheating | Power limiter, active cooling | |
Output data PV Point | ||
|---|---|---|
Nominal AC voltage PV Point | 1~NPE 120 V | |
Nominal output power PV Point | at 120 V | 1 560 W |
Max. continuous output current | at 120 V | 13.0 A |
Nominal output frequency | 63 Hz | |
Power factor | 0 - 1 ind. / cap.2) | |
Switching time | <17 s. | |
Data communication | ||
|---|---|---|
WLAN SMA-RP connection | 802.11b/g/n (WPA, WPA2) | |
Ethernet (LAN) | RJ 45, 10/100 Mbit | |
Wired shutdown (WSD) | max. 28 devices/WSD chain | |
Modbus RTU SunSpec (2x) | RS485 2-wire | |
Battery Connection | Modbus O / RJ 45 / 12 V power supply | |
Voltage level of digital inputs | low: min. 0 V - max. 1.8 V | |
Input currents of digital inputs
| depending on the input voltage; | |
Total power for digital output | 6 W at 12 V | |
Power per digital output | 1 A at >12.5 V - 24 V | |
DC Input data battery 4) | ||
|---|---|---|
Min. voltage | 150 V | |
Max. voltage | 465 V | |
Max. current | 22 A | |
Max. input | 3 800 W | |
DC Inputs | 1 | |
Output data Essential Backup 5) | ||
|---|---|---|
Rated power Essential Backup | at 120 V | 3 800 W |
Max. continuous output current | at 120 V | 18.3 A |
Nominal output frequency | 63 Hz | |
Power factor | 0.8 - 1 ind. / cap.2) | |
Switching time | <17 s. | |
DC input data | ||
|---|---|---|
MPP voltage range | 190 - 480 V | |
Max. input voltage at 1000 W/m²/14 °F in an open circuit | 600 V | |
Min. input voltage | 65 V | |
Start-up input voltage | 80 V | |
Nominal PV power | at 208 V | 5 180 W |
Nominal input voltage | at 208 V | 365 V |
Nominal input current | at 208 V | 14.1 A |
Max. PV array power | at 208 V | 7 500 W |
Max. input current |
| |
Max. short circuit current for module array (ISC PV) |
| |
Max. total short circuit current for module array |
| |
Max. continuous utility backfeed current 1) | 0.0 A | |
AC output data | ||
|---|---|---|
Max. output power | at 208 V | 5 000 W |
Max. output power at +140 °F (60 °C) V min/V max | at 208 V | 1 760 W/1 540 W |
Nominal AC voltage | 208 V/220 V/240 V | |
Voltage trip limit accuracy | 1 % of nominal value | |
Max. continuous output current at Vnom | at 208 V | 24.0 A |
Output overcurrent protection | at 208 V | 30.0 A |
Phases | 1 | |
Max. output fault current per duration (peak/rms over duration) | at 208 V | 141 A/30.3 A over 11 ms |
Nominal output frequency | 60 Hz | |
Setting range for mains frequency | 45.0 - 66.0 Hz | |
Frequency trip limit accuracy | 0.05 Hz | |
Total harmonic distortion | < 3.5 % | |
Power factor (cos phi) | 0.8 - 1 ind./cap. 2) | |
Max. permitted mains impedance Zmax at PCC (mOhm)3) | None | |
General data | ||
|---|---|---|
Maximum efficiency | at 208 V | 97.3 % |
CEC efficiency | at 208 V | 96.5 % |
Night tare loss | at 208 V | 7.6 W |
Cooling | Controlled forced-air ventilation | |
Protection class | Type 4X | |
Dimensions H × W × D | 20.3 × 18.7 × 6.5 inches (516 × 474 × 165 mm) | |
Weight | 32.96 lbs. | |
Shipping dimensions H × W × D | 23.3 × 22.2 × 10.1 inches (593 × 564 × 257 mm) | |
Shipping weight | 41.12 lbs. | |
Inverter topology | non-isolated, no transformer | |
Permitted ambient temperature | -40 °F - +140 °F (-40 °C - +60 °C) | |
Permissible humidity | 0 – 100 % (incl. condensation) | |
EMC emission class | B | |
DC/AC overvoltage (according to UL1741 3rd Edition, CSA-C22.2 No.107.1-16) | 2/4 | |
Pollution degree | 2 | |
Safety class (according to IEC 62103) | 1 | |
Protection devices | ||
|---|---|---|
DC isolation measurement | Error/shutdown at RISO < 500 kOhm | |
DC overload performance | Operating point shift, power limiter | |
DC disconnector | Integrated | |
DC reverse polarity protection | Integrated | |
Arc Fault Circuit Interrupter | AFCI type 1 integrated, according to UL1699B:2024 | |
Rapid shutdown | Integrated, in accordance with UL1741 and CSA C22.2 No.330-23 | |
RCMU | Integrated | |
Active anti-islanding method | Integrated | |
Behavior in the event of overheating | Power limiter, active cooling | |
Output data PV Point | ||
|---|---|---|
Nominal AC voltage PV Point | 1~NPE 120 V | |
Nominal output power PV Point | at 120 V | 1 560 W |
Max. continuous output current | at 120 V | 13.0 A |
Nominal output frequency | 63 Hz | |
Power factor | 0 - 1 ind. / cap.2) | |
Switching time | <17 s. | |
Data communication | ||
|---|---|---|
WLAN SMA-RP connection | 802.11b/g/n (WPA, WPA2) | |
Ethernet (LAN) | RJ 45, 10/100 Mbit | |
Wired shutdown (WSD) | max. 28 devices/WSD chain | |
Modbus RTU SunSpec (2x) | RS485 2-wire | |
Battery Connection | Modbus O / RJ 45/12 V power supply | |
Voltage level of digital inputs | low: min. 0 V - max. 1.8 V | |
Input currents of digital inputs
| depending on the input voltage; input resistance = 70 kOhm | |
Total power for digital output (internal supply) | 6 W at 12 V | |
Power per digital output | 1 A at >12.5 V - 24 V | |
DC input data battery 4) | ||
|---|---|---|
Min. voltage | 150 V | |
Max. voltage | 465 V | |
Max. current | 22 A | |
Max. input | 5 000 W | |
DC Inputs | 1 | |
Output data Essential Backup 5) | ||
|---|---|---|
Nominal output power Essential Backup | at 120 V | 5 000 W |
Max. continuous output current | at 120 V | 24.0 A |
Nominal output frequency | 63 Hz | |
Power factor | 0.8 - 1 ind. / cap.2) | |
Switching time | <17 s | |
DC input data | ||
|---|---|---|
MPP voltage range | 190 - 480 V | |
Max. input voltage at 1000 W/m²/14 °F in an open circuit | 600 V | |
Min. input voltage | 65 V | |
Start-up input voltage | 80 V | |
Nominal PV power | at 208 V | 5 950 W |
Nominal input voltage | at 208 V | 365 V |
Max. PV array power | at 208 V | 8 000 W |
Nominal input current | at 208 V | 16.2 A |
Max. input current |
| |
Max. short circuit current for module array (ISC PV) |
| |
Max. total short circuit current for module array |
| |
Max. continuous utility backfeed current 1) | 0.0 A | |
AC output data | ||
|---|---|---|
Max. output power | at 208 V | 5 740 W |
Max. output power at +140 °F (60 °C) V min / V max | at 208 V | 1 760 W/1 540 W |
Nominal AC voltage | 208 V/220 V/240 V | |
Voltage trip limit accuracy | 1 % of nominal value | |
Max. continuous output current at Vnom | at 208 V | 27.6 A |
Output overcurrent protection | at 208 V | 35.0 A |
Phases | 1 | |
Max. output fault current per duration (peak / rms over duration) | at 208 V | 141 A/30.3 A over 11 ms |
Nominal output frequency | 60 Hz | |
Setting range for mains frequency | 45.0 - 66.0 Hz | |
Frequency trip limit accuracy | 0.05 Hz | |
Total harmonic distortion | < 3.5 % | |
Power factor (cos phi) | 0.8 - 1 ind./cap. 2) | |
Max. permitted mains impedance Zmax at PCC (mOhm)3) | None | |
General data | ||
|---|---|---|
Maximum efficiency | at 208 V | 97.3 % |
CEC efficiency | at 208 V | 96.5 % |
Night tare loss | at 208 V | 7.5 W |
Cooling | Controlled forced-air ventilation | |
Protection class | Type 4X | |
Dimensions H × W × D | 20.3 × 18.7 × 6.5 inches | |
Weight | 32.96 lbs. | |
Shipping dimensions H × W × D | 23.3 × 22.2 × 10.1 inches | |
Shipping weight | 41.12 lbs. | |
Inverter topology | non-isolated, no transformer | |
Permitted ambient temperature | -40 °F - +140 °F | |
Permissible humidity | 0 - 100 % | |
EMC emission class | B | |
DC/AC overvoltage (according to UL1741 3rd Edition, CSA-C22.2 No.107.1-16) | 2/4 | |
Pollution degree | 2 | |
Safety class (according to IEC 62103) | 1 | |
Protection devices | ||
|---|---|---|
DC isolation measurement | Error/shutdown at RISO < 500 kOhm | |
DC overload performance | Operating point shift, power limiter | |
DC disconnector | Integrated | |
DC reverse polarity protection | Integrated | |
Arc Fault Circuit Interrupter | AFCI type 1 integrated, according to UL1699B:2024 | |
Rapid shutdown | Integrated, in accordance with UL1741 and CSA C22.2 No.330-23 | |
RCMU | Integrated | |
Active anti-islanding method | Integrated | |
Behavior in the event of overheating | Power limiter, active cooling | |
Output data PV Point | ||
|---|---|---|
Nominal AC voltage PV Point | 1~NPE 120 V | |
Nominal output power PV Point | at 120 V | 1560 W |
Max. continuous output current | at 120 V | 13.0 A |
Nominal output frequency | 63 Hz | |
Power factor | 0 - 1 ind. / cap.2) | |
Switching time | <17 s | |
Data communication | ||
|---|---|---|
WLAN SMA-RP connection | 802.11b/g/n (WPA, WPA2) | |
Ethernet (LAN) | RJ 45, 10/100 Mbit | |
Wired shutdown (WSD) | max. 28 devices/WSD chain | |
Modbus RTU SunSpec (2x) | RS485 2-wire | |
Battery Connection | Modbus O / RJ 45 / 12 V power supply | |
Voltage level of digital inputs | low: min. 0 V - max. 1.8 V | |
Input currents of digital inputs
| depending on the input voltage; | |
Total power for digital output | 6 W at 12 V | |
Power per digital output | 1 A at >12.5 V - 24 V | |
DC Input data battery 4) | ||
|---|---|---|
Min. voltage | 150 V | |
Max. voltage | 465 V | |
Max. current | 22 A | |
Max. input | 6 000 W | |
DC Inputs | 1 | |
Output data Essential Backup 5) | ||
|---|---|---|
Nominal output power Essential Backup | at 120 V | 5 740 W |
Max. continuous output current | at 120 V | 27.6 A |
Nominal output frequency | 63 Hz | |
Power factor | 0.8 - 1 ind. / cap.2) | |
Switching time | <17 s | |
Frequency range | 2412 - 2462 MHz |
Channels / power used | Channel: 1-11 b,g,n HT20 |
Modulation | 802.11b: DSSS (1Mbps DBPSK, 2Mbps DQPSK, 5.5/11Mbps CCK) |
| 1) | The maximum current from the inverter to the PV module if an error occurs in the inverter. Guaranteed by the electrical design of the inverter. |
| 2) | Depending on the country setup or device-specific settings (ind. = inductive; cap. = capacitive). |
| 3) | Assured by the electrical design of the inverter. |
| 4) | The inverter can be upgraded to a GEN24 Plus Hybrid device in the future through the UP.storage software upgrade. This upgrade activates battery functionality, enabling the possibility of a Essential Backup power solution. However, external grid switching devices are required for this functionality. The technical specifications for battery operation and Essential Backup operation are detailed below. |
| 5) | For Essential Backup, additional external components are required for grid separation. |
General data | |
|---|---|
Product name | Benedict LS32 E 7905 |
Rated insulation voltage | 1000 VDC |
Rated impulse withstand voltage | 8 kV |
Suitability for insulation | Yes, DC only |
Utilization category and/or PV utilization category | according to IEC/EN 60947-3 utilization category DC-PV2 |
Rated short-time withstand current (Icw) | Rated short-time withstand current (Icw): 1000 A |
Rated short-circuit capacity (Icm) | Rated short-circuit capacity (Icm): 1000 A |
Rated operating current and rated breaking capacity | ||||
|---|---|---|---|---|
Rated operating voltage (Ue) | Rated operating current (Ie) | I(make) / I(break) | Rated operating current (Ie) | I(make) / I(break) |
≤ 500 VDC | 14 A | 56 A | 36 A | 144 A |
600 VDC | 8 A | 32 A | 30 A | 120 A |
Number of pins | 1 | 1 | 2 | 2 |
General data | |
|---|---|
Product name | Benedict LSA32 E 8229 |
Rated insulation voltage | 1000 VDC |
Rated impulse withstand voltage | 6 kV |
Suitability for insulation | Yes, DC only |
Utilization category and/or PV utilization category | according to IEC/EN 60947-3 utilization category DC-PV2 |
Rated short-time withstand current (Icw) | Rated short-time withstand current (Icw): 1000 A |
Rated short-circuit capacity (Icm) | Rated short-circuit capacity (Icm): 1000 A |
Rated operating current and rated breaking capacity | ||||
|---|---|---|---|---|
Rated operating voltage (Ue) | Rated operating current (Ie) | I(make) / I(break) | Rated operating current (Ie) | I(make) / I(break) |
300 VDC | 27 A | 108 A | 47 A | 188 A |
400 VDC | 20 A | 80 A | 45 A | 180 A |
500 VDC | 14 A | 56 A | 38 A | 152 A |
600 VDC | 11.5 A | 46 A | 33 A | 132 A |
700 VDC | 7.5 A | 30 A | 28 A | 112 A |
800 VDC | 5.75 A | 23 A | 23 A | 92 A |
900 VDC | 4.75 A | 19 A | 20 A | 80 A |
1 000 VDC | 4 A | 16 A | 13 A | 52 A |
Number of pins | 1 | 1 | 2 | 2 |