Fronius Verto 15 – 20 kW / 25 kW 400
download
Warnings are intended to warn people of possible injuries and to avoid personal injury and damage to the product. They relate to individual actions with and on the product.
Indicates an immediately dangerous situation.
Serious injury or death will result if the danger is not avoided.
Action step to escape the situation.
Serious injury or death may result if the danger is not avoided.
Minor or moderate injury may result if the danger is not avoided.
Indicates a situation that may result in property damage.
If the situation is not avoided, impaired work results, material damage to the product or other property are the possible consequences.
Action step to avoid the situation.
Safety instructions are designed to ensure safe product use. They are preventive and help to inform users about the fundamental risks involved when dealing with the product. They do not refer specifically to individual actions with and on the product.
Incorrect operation or misuse
IMPORTANT!
Tampered-with and non-functioning protection devices
The device may be damaged
Operation or storage of the machine outside the stipulated area will be deemed as not in accordance with the intended purpose.
For exact information on permitted environmental conditions, please refer to the technical data.
The sound pressure level of the inverter is indicated in the Technical data.
The cooling of the device takes place via an electronic temperature control system at the lowest possible noise level and depends on the power used, ambient temperature, and the soiling level of the device, etc.
It is not possible to provide a workplace-related emission value for this device, because the actual sound pressure level is heavily influenced by the installation situation, the power quality, the surrounding walls, and the properties of the room in general.
Connection of a point in the device, system, or installation to ground to protect against electric shock in the event of a fault. When installing an inverter from safety class 1 (see Technical data), a ground conductor connection is required.
When connecting the ground conductor, ensure that it is secured to prevent unintentional disconnection. All of the points listed in the chapter headed Connecting the inverter to the public grid (AC side) on page (→) must be observed. When using cable glands, ensure that the ground conductor is last to be subjected to a load in the event of a failure of the cable gland. The respective national standards and regulations and requirements for minimum cross-section must be observed when connecting the ground conductor.
Attention: The installation of this equipment must comply with current technical standards for photovoltaic electrical installation (NBR 16690) and fire risk management in photovoltaic systems (IEC TR 63226)”.
Attention: It is expressly recommended to use rapid shutdown methods, systems or devices on the dc circuit that guarantee safety in firefighting situations".
However, as rapid shutdown devices may increase the number of DC connectors, which may increase the risk of fire (as stated in IEC TR 63226, §6.4), Fronius recommends using the methods listed below (with reference to sections of IEC TR 63226) to support firefighters in emergency situations:The above measures are provided as possible options for firefighter protection in the IEC TR 63226, as well as in other national fire safety regulations (such as VDE-AR-E 2100-712 in Germany, and OVE R11-1 in Austria) and guidelines from 3rd party organizations (TÜV Rheinland, Fraunhofer ISE, German Solar Industry Association - BSW).
The inverter offers the option to use the integrated AC relays as section switches in conjunction with a central grid and system protection unit (in accordance with VDE-AR-N 4105:2018:11 § 6.4.1). For this purpose, integrate the central trigger device (switch) into the WSD chain as described in chapter (→) on page WSD (wired shutdown).
Grid and system protection for systems with multiple invertersThe inverter offers the option to use the integrated AC relays as section switches in conjunction with a central grid and system protection unit (in accordance with VDE-AR-N 4105:2018:11 § 6.4.1). For this purpose, integrate the central trigger device (switch) into the WSD chain as described in chapter (→) on page WSD (wired shutdown).
Grid and system protection for systems with multiple invertersThe wired shutdown (WSD) interrupts the inverter's grid power feed if the trigger device (switch, e.g., Emergency Stop or fire alarm contact) has been activated.
If an inverter (slave) fails, it is bypassed and the other inverters continue operating. If a second inverter (slave) or the inverter (master) fails, the operation of the entire WSD chain is interrupted.
For installation, see Installing the WSD (wired shutdown) on page (→).
The inverter is equipped with an RCMU (RCMU = residual current monitoring unit) according to IEC 62109-2 and IEC63112.
It monitors residual currents from the PV module up to the AC output and disconnects the inverter from the grid when an improper residual current is detected.
In the case of photovoltaic systems with ungrounded PV modules, the inverter checks the resistance between the positive or negative pole of the photovoltaic system and the ground potential before starting grid power feed operation. In the event of a short circuit between the DC+ or DC- cable and ground (e.g., due to inadequately insulated DC cables or defective PV modules), feeding into the public grid is prevented.
An AFCI (Arc Fault Circuit Interrupter) protects against arc faults and is a protective device in the event of contact errors. The Arc Fault Circuit Interrupter monitors faults that occur in the current and voltage flow on the DC side and shuts down the circuit with an electronic circuit if a contact error is detected. The function prevents overheating at poor contact points and fires. When delivered, the Arc Guard function is disabled
In the Technical data chapter, check whether the Arc Fault Circuit Interrupter is available for the device in question.
Arc faults due to faulty or incorrect DC installation
Risk of fire as well as serious injuries and damage to the inverter and PV system.
Connection work must be carried out in accordance with the technical specifications.
Check the plug connections to ensure that they are in proper condition.
Professionally repair faulty insulation.
IMPORTANT! Despite the integrated Arc Fault Circuit Interrupter and arc interruption, damage to the device as well as to other system components may occur (e.g., due to a parallel arc).
IMPORTANT! Active PV module electronics (e.g., power optimizers) can impair the function of the Arc Fault Circuit Interrupter. We cannot guarantee that the Arc Fault Circuit Interrupter will work correctly in combination with active PV module electronics.
Reconnection behavior
The inverter interrupts grid power feed operation and stops PV power generation after an arc has been detected. The configuration in the Country Setup > Safety > DC Arc Fault Protection menu item determines whether or not the inverter automatically resumes PV power generation and grid power feed operation. If more arcs have been detected within 24 hours than are set in Automatic Reconnects, a manual reconnection needs to be performed.
In the safe state, the inverter infeed is deactivated and is disconnected from the grid by the AC relay opening. The inverter switches to the safe state when the following events occur:
Technical data, warning notices, labels, and safety symbols are located on and in the inverter. This information must be kept in a legible condition and must not be removed, covered, pasted over, or painted over. They warn against incorrect operation, which may result in serious injury and property damage.
Symbols on the rating plate: | |
CE label – confirms compliance with applicable EU directives and regulations. | |
WEEE marking – waste electrical and electronic equipment must be collected separately and recycled in an environmentally sound manner in accordance with the European Directive and national law. | |
Safety symbols: | |
Integrated switch disconnector on the input side of the inverter with switch-on, switch-off, and isolating function according to IEC 60947-3 and AS 60947.3. The values required by the applicable standard for Ithe solar +60°C are given. | |
General warning sign | |
Observe instructions
Warning of hot surface | |
Warning of electrical voltage | |
Allow the capacitors of the inverter to discharge (2 minutes). | |
Warning notice text:
WARNING!
An electric shock can be fatal. Before opening the device, ensure that the input and output sides are de-energized and disconnected.
Safety symbols: | |
WARNING!
Application notes
Software
Example: Click Save.
Instructions for action
This document provides detailed information and instructions to ensure that people can use the machine safely and efficiently.
The information is intended for the following groups of people:Regardless of any qualifications, only perform the activities listed in this document.
The definition of professional qualifications and their applicability are subject to national law.
When you connect your device (and any associated devices) to the internet, the following device and operating data (device ID/identifier, device IP address, device time, configuration settings, hardware and software information, device status log files, serial number) is sent automatically to
Fronius International GmbH, Froniusstraße 1, 4643 Pettenbach, Austria, telephone +43(0) 7242241-0, email: contact@fronius.com (controller)
and stored.
The processing of this device and operating data is carried out for the purpose of ensuring the operational safety of the device (time synchronization, provision of updates). This processing is therefore necessary for the functionality of the device and thus for the fulfillment of the contract (Art. 6 (1) (b) GDPR).
If you do not wish to have such data processed, you must manually disable the device's internet connection.
In addition, the device and operating data is also processed for the purpose of providing services as part of a supplementary digital service for your device (such as solar.web or similar) as soon as you have registered your device with such a digital service (identification). This data is processed to provide the requested digital services and is therefore necessary for the fulfillment of the contract (Art. 6 (1) (b) GDPR).
Furthermore, this data processing is also carried out for maintenance and support purposes and for handling customer concerns as well as in warranty and guarantee cases (only in individual cases and given connection between device and internet). In this context, the device and operating data may also be passed on to our cooperation partners (third-party providers and suppliers). The processing of this data is necessary for maintenance and support purposes or for processing warranty and guarantee cases and thus for the fulfillment of the contract (Art. 6 (1) (b) GDPR).
Device and operating data are also processed for analysis and diagnostic purposes in order to gain insights into the functionality of the devices and improve them accordingly. This data processing is based on our legitimate interest (Art. 6 (1) (f) GDPR).
We store this data for as long as it is necessary to fulfill the existing contract with you. Any storage beyond this is carried out for legal reasons or if we have a legitimate interest in doing so. For more information on data processing for the solar.web-digital service, as well as our general privacy policy and your rights as a data subject, please visit https://www.fronius.com.
The inverter transforms the direct current generated by the solar modules into alternating current. This alternating current is fed into the public grid and synchronized with the mains voltage in use.
The inverter is intended for use in grid-connected photovoltaic systems.
The inverter automatically monitors the public grid. Whenever conditions in the electric grid are inconsistent with standard conditions (for example, grid switch-off, interruption), the inverter will immediately stop producing power and interrupt the supply of power into the grid.
The grid is monitored by monitoring the voltage, frequency, and islanding conditions.
After installation and commissioning, the inverter's operation is fully automatic; the inverter draws the maximum possible power from the PV modules.
Depending on the operating point, this power is used in the home or fed into the grid.
When its temperature gets too high, the inverter automatically reduces the output power or switches off completely, in order to protect itself.
Reasons for the temperature being too high include a high ambient temperature or insufficient heat dissipation (for example, inadequate heat dissipation when installed in switch cabinets).
| (1) | Mounting bracket (is mounted on the inverter on delivery) |
| (2) | Inverter |
| (3) | Housing cover |
| (4) | Quick Start Guide |
Ambient air is drawn in at the top and bottom of the device by the fan and blown out at the sides. The even heat dissipation allows several inverters to be installed next to each another.
Risk due to insufficient cooling of the inverter.
This may result in a loss of power in the inverter.
Do not block the fan (e.g., with objects that protrude through the touch guard).
Do not cover the ventilation slots, even partially.
Make sure that the ambient air can always flow through the inverter's ventilation slots unimpeded.
System owners and installers can easily monitor and analyze the PV system using Fronius Solar.web or Fronius Solar.web Premium. With the appropriate configuration, the inverter transmits data such as power, yield, load, and energy balance to Fronius Solar.web. More detailed information can be found at Solar.web - Monitoring & analysis.
Configuration is carried out via the Setup wizard, see chapter Installation with the app or Installation with the browser.
Requirements for configuration:| * | These specifications do not provide an absolute guarantee of flawless operation. High error rates in the transmission, fluctuating receptions or misfires can have an adverse effect on data transfer. Fronius recommends on-site testing to ensure that the connections meet the minimum requirements. |
The inverter can be found via the Multicast DNS (mDNS) protocol. We recommend searching for the inverter using the assigned host name.
The following data can be called up via mDNS:The inverter is designed to convert direct current from PV modules into alternating current and feed this power into the public grid.
Intended use also means:Follow all grid operator regulations regarding energy fed into the grid and connection methods.
The inverter is designed exclusively to be connected and used with PV modules.
Use with other DC generators (e.g., wind generators) is not permitted.
When configuring the photovoltaic system, make sure that all photovoltaic system components are operating exclusively within their permitted operating range.
All measures recommended by the PV module manufacturer for maintaining the PV module properties must be followed.
| The surge protection device (SPD) protects against temporary overvoltages and diverts surge currents (e.g., lightning strike). Based on an overall lightning protection concept, the SPD contributes to the protection of the photovoltaic system components. | |
| If the surge protection device is triggered, the color of the indicator changes from green to red (mechanical display). A triggered SPD must be replaced with a fully functional SPD immediately by an authorized specialist company in order to maintain the full protective function of the device. | |
| It is possible to enable the option of digitally displaying the triggering of an SPD. If you wish to set this function, refer to the PDF "SPD Triggering / Temporary SPD Triggering" in the Service & Support area at www.fronius.com |
IMPORTANT!
After setting the function described above, the inverter also responds if the 2-pole signal cable of the surge protection device is damaged or is subject to an interruption.
Note: Replacing a device does not automatically result in replacement of the existing SPDs.
IMPORTANT!
| (1) | Push-in WSD (wired shutdown) terminal |
| (2) | Push-in terminals in the data communication area (Modbus) |
| (3) | Push-in terminals in the data communication area (digital inputs and outputs) |
| (4) | 5-pin AC terminal |
| (5) | Cable bushing/cable gland AC |
| (6) | AC SPD (surge protection device) |
| (7) | Optional cable bushing |
| (8) | Grounding clamping bolts |
| (9) | Cable bushing/cable gland in the data communication area |
| (10) | DIN rail (mounting option for third-party components) |
| (11) | DC connections MC4 |
| (12) | DC SPD (surge protection device) |
If further grounding options are required, suitable terminals can be fitted to the DIN rail.
There is space for the installation of third-party components in the connection area. Components up to a maximum width of 12 cm (6 transport units) can be mounted on the DIN rail. The components must have a temperature resistance of -40 °C to +70 °C.
The DC disconnector has 2 switch settings: 1 (On) / 0 (Off).
Protection against unintentional switching on:
When the switch is in the 0 (Off) position, a conventional padlock can be used to secure the inverter against being switched on. The national guidelines must be complied with in this respect.
| Indicates the inverter operating status. |
WSD (wired shutdown) switch | Defines the inverter as the WSD master or WSD slave. |
Modbus 0 (MB0) switch | Switches the terminating resistor for Modbus 0 (MB0) on/off. |
Modbus 1 (MB1) switch | Switches the terminating resistor for Modbus 1 (MB1) on/off. |
| For operating the inverter. See chapter Button functions and LED status indicator on page (→). |
| Indicates the inverter connection status. |
LAN 1 | Ethernet connection for data communication (e.g., WiFi router, home network or, for commissioning with a laptop, see chapter Installation with the browser on page (→)). |
LAN 2 | Reserved for future functions. To avoid malfunctions, only use LAN 1. |
I/O terminal | Push-in terminal for digital inputs/outputs. See chapter Permitted cables for the data communication connection on page (→). |
WSD terminal | Push-in terminal for the WSD installation. See chapter WSD (wired shutdown) on page (→). |
Modbus terminal | Push-in terminal for the installation of Modbus 0, Modbus 1, 12 V, and GND (ground). |
The operating status LED displays the status of the inverter. In case of faults, follow the individual steps in the Fronius Solar.web live app. | |
The optical sensor is actuated by touching it with a finger. | |
The communications LED displays the connection status. To establish a connection, follow the individual steps in the Fronius Solar.web live app. |
Sensor functions | ||
| 1x | |
| 2x | |
3 seconds | ||
LED status indicator | ||
| The inverter is operating correctly. | |
| The inverter is starting. | |
| The inverter is on standby, is not operating (e.g., no energy fed into the grid at night), or is not configured. | |
| The inverter displays a non-critical status. | |
| The inverter displays a critical status and no energy is fed into the grid. | |
| The network connection is being established via WPS. | |
| The network connection is being established via WLAN AP. | |
| The network connection is not configured. | |
| A network error is displayed, the inverter is operating correctly. | |
| The inverter is performing an update. | |
There is a service message. | ||
The V+/ GND pin provides the possibility of feeding in a voltage in the range of 12.5 to 24 V (+ max. 20%) using an external power supply unit. Outputs IO 0 - 5 can then be operated using the external voltage that has been fed in. A maximum of 1 A may be drawn per output, whereby a total of max. 3 A is permitted. The fuse protection must take place externally.
Danger from polarity reversal at the terminals due to improper connection of external power supply units.
This may result in severe damage to the inverter.
Check the polarity of the external power supply unit with a suitable measuring device before connecting it.
Connect the cables to the V+/GND outputs while ensuring the correct polarity.
IMPORTANT!
If the total output (6 W) is exceeded, the inverter switches off the entire external power supply.
| (1) | Current limitation |
Captive screws (1) are used on the housing for fitting or removing the connection area cover. To fit the connection area cover, rotate the screws by half a turn (180°) into the quick-fastener spring (2).
Close the quick-fastener system (3) using a screwdriver (TX20) and a torque of 0.5-5 Nm.
Danger when using a drill driver.
This may result in the destruction of the quick-fastener system due to overtorque.
Use a screwdriver (TX20).
Do not turn the screws more than 180°.
All installed components in the PV system must be compatible with each other and have the necessary configuration options. The installed components must not restrict or negatively affect the functioning of the PV system.
Risk due to components in the PV system that are not and/or only partially compatible.
Incompatible components can restrict and/or negatively affect the operation and/or functioning of the PV system.
Only install components recommended by the manufacturer in the PV system.
Before installation, check the compatibility of components that have not been expressly recommended with the manufacturer.
Please observe the following criteria when choosing a location for the inverter:
Only install on a solid, non-flammable surface. |
When installing the inverter in a switch cabinet or similar closed environment, ensure adequate heat dissipation by forced-air ventilation. |
When installing the inverter on the outer walls of cattle sheds, it is important to maintain a minimum clearance of 2 m between all sides of the inverter and the ventilation and building openings. |
The following substrates are allowed:
The inverter is suitable for indoor installation. | ||
The inverter is suitable for outdoor installation. | ||
Do not expose the inverter to direct sunlight in order to keep inverter heating as low as possible. | ||
The inverter should be installed in a protected location, e.g., near the PV modules or under an overhanging roof. | ||
The inverter must not be installed or operated at more than 4 000 m above sea level. The voltage UDCmax must not exceed the following values:
Do not install the inverter:
During certain operating phases the inverter may produce a slight noise. For this reason it should not be installed in an occupied living area. | ||
Do not install the inverter in:
The inverter is designed to be dust-proof (IP 66). In areas of high dust accumulation, dust deposits may collect on the cooling surfaces, and thus impair the thermal performance. In this case, cleaning is required regularly. We therefore recommend not installing the inverter in areas and environments with high dust accumulation. | ||
IMPORTANT!
Refer to the manufacturer's documents for specifications regarding the suitable location of third-party batteries.
The inverter is suitable for vertical installation on a vertical wall or column. Do not install the inverter:
The inverter is suitable for a horizontal installation position or for installation on a sloping surface. Do not install the inverter:
Use the corresponding fixing materials depending on the subsurface and observe the screw dimension recommendations for the mounting bracket.
The installer is responsible for selecting the right type of fixing.
The mounting bracket (illustration) can also be used as a guide.
The pre-drilled holes on the mounting bracket are intended for screws with a thread diameter of 6-8 mm (0.24-0.32 inches).
Unevenness on the installation surface (for example, coarse-grained plaster) is largely counterbalanced by the mounting bracket.
The mounting bracket must be fixed to the four outer tabs (marked in green). The four inner tabs (marked in orange) can be used in addition if required.
When attaching the mounting bracket to the wall or to a column, make sure that the mounting bracket is not deformed.
A deformed mounting bracket may make it difficult to clip/swivel the inverter into position.
IMPORTANT!
When installing the mounting bracket, make sure that it is installed with the arrow pointing upwards.
There are integrated grips on the side of the inverter which facilitate lifting/attaching.
Clip the inverter into the mounting bracket from above. The connections must point downwards.
Push the lower part of the inverter into the snap-in tabs of the mounting bracket until the inverter audibly clicks into place on both sides.
Check that the inverter is correctly positioned on both sides.
Aluminum cables can also be connected to the AC connections.
When using aluminum cables:
Follow all national and international guidelines regarding the connection of aluminum cables.
Grease aluminum wires with appropriate grease to protect them from oxidation.
Follow the instructions of the cable manufacturer.
Solid | Fine-stranded | Fine-stranded with ferrule and collar | Fine-stranded with ferrule without collar | Sectoral |
Round copper or aluminum conductors with a cross-section of 4 to 35 mm2 can be connected to the terminals of the inverter as described below.
The torques according to the following table must be observed:
Cross-section | Copper | Aluminum | ||
35 mm2 | 10 Nm | 10 Nm | 14 Nm | 14 Nm |
25 mm2 | 8 Nm | 8 Nm | 12 Nm | 10 Nm |
16 mm2 | 10 Nm | |||
10 mm2 | 6 Nm | 6 Nm | ||
6 mm2 | ||||
4 mm2 | ||||
The grounding must be established with a 6 mm² copper or 16 mm2 aluminum cable as a minimum requirement.
Round copper conductors with a cross section of 4-10 mm² can be connected to the MC4 plugs of the inverter.
Select a sufficiently large cable cross-section based on the actual device output and the installation situation! Observe the data sheet for the plug!
Connect round copper conductors to the terminals of the inverter as described below.
IMPORTANT!
If several single conductors are connected to an input of the terminal, connect the single conductors with a corresponding ferrule.
WSD connections | ||||||
Distance | Stripping length | Cable recommendation | ||||
100 m 109 yd | 10 mm | 0.14 - 1.5 mm2 | 0.14 - 1.5 mm2 | 0.14 - 1 mm2 | 0.14 - 1.5 mm2 | Min. CAT 5 UTP (unshielded twisted pair) |
Modbus connections | ||||||
300 m 328 yd | 10 mm | 0.14 - 1.5 mm2 | 0.14 - 1.5 mm2 | 0.14 - 1 mm2 | 0.14 - 1.5 mm2 | Min. CAT 5 STP (shielded twisted pair) |
IO connections | ||||||
30 m | 10 mm | 0.14 - 1.5 mm2 | 0.14 - 1.5 mm2 | 0.14 - 1 mm2 | 0.14 - 1.5 mm2 | Single conductors possible |
LAN connections |
Fronius recommends using at least CAT 5 STP (shielded twisted pair) cables and a maximum distance of 100 m (109 yd). |
For a standard M32 cable gland with a large reducer (green):
Cable diameter from 12-14 mm
For a standard M32 cable gland with a small reducer (red):
Cable diameter from 17-19 mm
For a standard M32 cable gland without a reducer:
Cable diameter from 20.5-24.5 mm
For an M50 cable gland:
Cable diameter from ≤35 mm
A residual current circuit breaker for the AC connecting cable may be required depending on national regulations, the grid operator, and other conditions.
A type A residual current circuit breaker is generally sufficient in this case. Nevertheless, false alarms can be triggered for the type A residual current circuit breaker in individual cases and depending on local conditions. For this reason, Fronius recommends using a residual current circuit breaker suitable for frequency inverters with a release current of at least 100 mA, taking into account national provisions.
Verto | AC power | Recommended fuse protection | Max. fuse protection |
15.0 | 15 kW | 32 A | 63 A |
17.5 | 17,5 kW | 40 A | 63 A |
20.0 | 20 kW | 40 A | 63 A |
24.0 | 24 kW | 50 A | 63 A |
25.0 400 | 25 kW | 50 A | 63 A |
Read the Installation Instructions and Operating Instructions before installing and commissioning the equipment.
Only qualified personnel are authorized to commission the inverter and only within the scope of the respective technical regulations.
Danger from grid voltage and DC voltage from PV modules that are exposed to light.
Prior to any connection work, ensure that the inverter is de-energized on the AC side and the DC side.
Only an authorized electrical engineer is permitted to connect this equipment to the public grid.
Danger from damaged and/or contaminated terminals.
Prior to connection work, check the terminals for damage and contamination.
Remove any contamination while the equipment is de-energized.
Have defective terminals replaced by an authorized specialist.
It is not possible to operate the inverter in ungrounded networks, e.g., IT networks (isolated networks without ground conductor).
In certain system configurations, it is not necessary to connect the neutral conductor. In this system configuration, the neutral conductor status parameter must be set to Not connected on the web interface of the inverter in the Device configuration > Inverter > AC grid menu.
Switch off the external automatic circuit breakers (AC and battery).
Make sure that the DC disconnector (see DC disconnector) is set to the "Off" switch position.
Loosen the 6 screws on the connection area cover by rotating them 180° to the left using a screwdriver (TX20).
Remove the connection area cover from the device.
Strip the insulation of the single conductors by 16 mm.
Select the cable cross-section in accordance with the instructions in Permitted cables for the electrical grid connection from page (→).
IMPORTANT!
Only one conductor may be connected to each pin. With a twin ferrule, two conductors can be connected to one pin.
4 Connection with neutral conductor | 4 Connection without neutral conductor | |
For more information about the cable gland, see chapter Cable diameter of the AC cable on page (→). | ||
5 Connection with neutral conductor | 5 Connection without neutral conductor | |||||||||||
IMPORTANT! Observe torques – see Permitted cables for the electrical grid connection on page (→). | ||||||||||||
IMPORTANT! | ||||||||||||
Fasten the union nut of the cable gland with a torque of 4 Nm.
IMPORTANT!
The PEN conductor must have ends that are permanently marked blue, according to the national regulations.
Dimension the ground conductor longer and lay it with a movement loop so that it is last loaded in the event of a failure of the cable gland.
To enable suitable PV modules to be chosen and to use the inverter as efficiently as possible, it is important to bear the following points in mind:
IMPORTANT!
Before connecting up the PV modules, check that the voltage for the PV modules specified by the manufacturer corresponds to the actual measured voltage.
IMPORTANT!
The PV modules connected to the inverter must comply with the IEC 61730 Class A standard.
IMPORTANT!
Solar module strings must not be grounded.
IMPORTANT!
IMPORTANT!
IMPORTANT!
The commissioning, maintenance, and service work in the inverter's power stage set may only be carried out by Fronius-trained service personnel in accordance with the technical specifications.
Read the installation instructions and operating instructions before installing and commissioning the equipment.
Danger from mains voltage and DC voltage from PV modules that are exposed to light.
All connection, maintenance, and service work should only be carried out when the AC and DC sides have been disconnected from the inverter and are de-energized.
Danger of an electric shock due to improperly connected terminals/PV plug connectors.
When connecting, ensure that each pole of a string is routed via the same PV input, e.g.:
+ pole string 1 to the input PV 1.1+ and - pole string 1 to the input PV 1.1-
Have defective terminals replaced by an authorized specialist company.
Several independent PV inputs are available. These inputs can be connected to a number of different modules.
When starting for the first time, set up the PV Generator in accordance with the respective configuration (can also be carried out at a later date in the System configuration menu field under menu item Components).
Use a suitable measuring instrument to check the voltage and polarity of the DC cabling.
Danger due to polarity reversal at the terminals.
Use a suitable measuring instrument to check the polarity of the DC cabling.
Use a suitable measuring instrument to check the voltage (max. 1 000 VDC)
Risk of damage due to incompatible plug connectors.
Incompatible plug connectors can cause thermal damage and may cause a fire.
Only use the original plug connectors (MC4) from Stäubli (formerly Multi-Contact).
Connect PV cables from the solar modules to the MC4 plugs according to the label
Unused MC4 plugs on the inverter must be closed by the cover caps supplied with the inverter.
The Modbus inputs M0 and M1 can be freely selected. A maximum of four Modbus participants can be connected to the Modbus terminal on the Modbus inputs M0 and M1.
IMPORTANT! Only one primary meter, one battery storage system, and one Ohmpilot/Ohmpilot Eco can be connected per inverter. Secondary meters can only be configured if a primary meter is defined in the system.
Due to the high volume of data transferred, some system components require more than one participant on the Modbus input:
System component | Required participants |
Primary meter/secondary meter | 1 |
Ohmpilot | 1 |
Ohmpilot Eco | 2 |
Battery storage | 2 |
Possible combination of system components per Modbus input M0/M1
| Required Modbus participants | ||
Number of different system components | per battery storage system | per heating solution | available Modbus inputs* |
3 meters | 0 | 0 | 1 |
1 battery storage system | 2 | 0 | 2 |
1 Ohmpilot | 0 | 1 | 3 |
1 Ohmpilot Eco | 0 | 2 | 2 |
1 battery storage system + 1 Ohmpilot | 2 | 1 | 1 |
1 battery storage system + 1 Ohmpilot Eco | 2 | 2 | 0 |
If the Inverter Control via Modbus function is enabled in the Communication > Modbus menu area, no Modbus participants can be connected. The inverter can either be controlled via Modbus or query system components via Modbus. If both are necessary, use both Modbus inputs.
Ohmpilot | 1 |
Ohmpilot Eco | 2 |
IMPORTANT!
Ingress protection rating IP 66 cannot be ensured if blanking plugs are missing or incorrectly inserted.
Remove the union nut on the cable gland and press the sealing ring with the blanking plugs out from the inside of the device.
Open up the sealing ring at the location where the blanking plugs are to be removed.
* Remove the blanking plugs with a sideways motion.
First, guide the data cables through the union nut of the cable gland and then through the housing opening.
Insert the sealing ring between the union nut and the housing opening. Press the data cables into the seal's cable guide. Then press in the seal until it reaches the underside of the cable gland.
Using a cable tie, attach the data cables to the protective cover of the DC surge protection device (SPD). Fasten the union nut of the cable gland with a torque of min. 2.5 - max. 4 Nm.
IMPORTANT!
The push-in WSD terminal in the inverter's connection area is delivered with a bypass ex works as standard. The bypass must be removed when installing a trigger device or a WSD chain.
The WSD switch of the first inverter with connected trigger device in the WSD chain must be in position 1 (master). The WSD switch of all other inverters should be in position 0 (secondary device).
Max. distance between 2 devices: 100 m
Max. Number of devices: 28
* Floating contact of the trigger device (e.g., central grid and system protection). If several floating contacts are used in a WSD chain, these must be connected in series.
Place the cover on the connection area. Tighten six screws by rotating them 180° to the right using a screwdriver (TX20).
Clip the housing cover into the inverter from above.
Press on the lower part of the housing cover and tighten the 2 screws by rotating them 180° to the right using a screwdriver (TX20).
Turn the DC disconnector (see DC disconnector) to the "On" switch setting. Switch on the external automatic circuit breakers (AC and battery).
When starting the inverter for the first time, various setup settings must be configured.
If the setup is canceled before completion, the input data is not saved and the start screen with the installation wizard is shown once again. The data is saved in the event of an interruption, e.g., a power failure. Commissioning is continued at the point at which the interruption occurred after the power supply is restored. If the setup was interrupted, the inverter feeds energy into the grid at maximum 500 W and the operating status LED flashes yellow.
The country setup can only be set when starting the inverter for the first time. If the country setup needs to be changed at a later date, contact your installer/technical support.
The Fronius Solar.start app is required for installation. Depending on the mobile device used to perform the installation, the app is available on the relevant platform.
WiFi:
Ethernet:
In the case of electrical devices with a high housing protection class, there is a risk of explosion in the event of a fault. Possible causes are defective components that release gases, improperly installed or commissioned devices, or the penetration of gas via lines (conduits).
This may result in serious personal injury and damage to property.
Turn off the automatic circuit breaker
If possible, switch off the DC line in front of the inverter (additional external DC disconnector)
Turn the DC disconnector to the "OFF" switch setting
IMPORTANT!
Wait for the capacitors of the inverter to discharge!
IMPORTANT!
Depending on the authorization of the user, settings can be made in the individual menu areas.
IMPORTANT!
IMPORTANT!
All available components of the system can be added via Add component+.
PV Generator
Activate the MPP tracker and enter the connected PV output in the relevant field.
Primary meter
For problem-free operation with further energy producers, it is important to install the Fronius Smart Meter at the feed-in point. The inverter and further producers must be connected to the public grid via the Fronius Smart Meter.
This setting also has an effect on the behavior of the inverter during the night. If the function is deactivated, the inverter switches to standby mode as soon as there is no more PV power available. The inverter starts again as soon as sufficient PV power is available.
If the function is activated, the inverter remains permanently connected to the grid in order to draw energy from other producers at any time.
After connecting the meter, the position must be configured.
For communication via MQTT, the inverter and Smart Meter must be in the same sub-network.
The following parameters must also be defined for the Smart Meter:
The Watt value for the production meter is the sum of all production meters. The Watt value for the secondary meter is the sum of all secondary meters.
Ohmpilot
All the Ohmpilots available in the system are displayed. Select the desired Ohmpilot and add to the system via “Add.”
PV Generator
Primary meter
Ohmpilot
Load Management
Select up to four pins for the load management. Further settings for the load management are available in the Load Management menu item.
Default: Pin 1
Australia - Demand Response Modes (DRM)
Activate the slider if DRM is required. Configure the pins for control via DRM as follows:
Mode | Description | Information | DRM Pin | I/O pin |
DRM0 | Inverter disconnects from the grid | DRM0 occurs in the event of an interruption or short circuit on the REF GEN or COM LOAD lines, or in the event of invalid combinations of DRM1 - DRM8. | REF GEN | IO4 |
DRM1 | Import Pnom ≤ 0% without disconnection from grid | currently not supported | DRM 1/5 | IN6 |
DRM2 | Import Pnom ≤ 50% | currently not supported | DRM 2/6 | IN7 |
DRM3 | Import Pnom ≤ 75% & | currently not supported | DRM 3/7 | IN8 |
DRM4 | Import Pnom ≤ 100% | currently not supported | DRM 4/8 | IN9 |
DRM5 | Export Pnom ≤ 0% without disconnection from grid | currently not supported | DRM 1/5 | IN6 |
DRM6 | Export Pnom ≤ 50% | currently not supported | DRM 2/6 | IN7 |
DRM7 | Export Pnom ≤ 75% & | currently not supported | DRM 3/7 | IN8 |
DRM8 | Export Pnom ≤ 100% | currently not supported | DRM 4/8 | IN9 |
The percentage specifications always relate to the rated device power. | ||||
IMPORTANT! If the Australia - Demand Response Modes (DRM) function is activated and no DRM control is connected, the inverter switches to standby mode.
Force standby
When this function is activated, the supply of energy from the inverter into the grid is interrupted. This makes it possible to shut down the inverter without power and protect its components. The standby function is automatically deactivated when the inverter is restarted.
Fan test
IMPORTANT!
For settings in this menu item, select the Technician user, enter the password for the Technician user, and confirm. Settings may only be made by trained and qualified personnel!
This function can be used to check whether the fans of the inverter are working correctly based on acoustics, for example after replacing a fan.
AC network
Parameter | Value range | Description |
Neutral conductor status | Not connected | The neutral conductor is not required in the system configuration and is therefore not connected. |
Connected | The neutral conductor is connected. |
PV 1 to PV 4
Mode | Off | The MPP tracker is deactivated. |
Auto | The inverter uses the voltage at which the max. possible output of the MPP tracker is possible. | |
Fixed | The MPP tracker uses the voltage defined in UDC fixed. | |
UDC fixed | 150‑870 V | The inverter uses the fixed voltage that is used on the MPP tracker. |
Dynamic Peak Manager | Off | Function is deactivated. |
On | The entire solar module string is checked for optimization potential and determines the best possible voltage for the supply of energy from the inverter into the grid. |
Ripple control signal
Ripple control signals are signals that are sent by the energy company in order to switch controllable loads on and off. Depending on the installation situation, ripple control signals can be dampened or amplified by the inverter. This can be counteracted if necessary by applying the following settings.
Reduction of influence | Off | Function is deactivated. |
On | Function is activated. | |
Frequency of the ripple control signal | 100‑3,000 Hz | The frequency specified by the energy company must be entered here. |
Grid inductance | 0.00001‑0.005 H | The value measured at the infeed point must be entered here. |
Measures to prevent FI/RCMU false alarms
(when using a 30 mA residual current circuit breaker)
A type A residual current circuit breaker is generally sufficient in this case. Nevertheless, false alarms can be triggered for the type A residual current circuit breaker in individual cases and depending on local conditions. For this reason, Fronius recommends using a residual current circuit breaker suitable for frequency inverters with a release current of least 100 mA, taking into account national provisions.
Leakage current factor to reduce RCMU/FI false tripping | 0‑0.25 | By reducing the setting value, the leakage current is reduced and the intermediate circuit voltage is increased, which slightly lowers the efficiency.
Shutdown before 30 mA FI triggers | Off | The function for reducing false tripping of the residual current circuit breaker is deactivated. |
On | The function for reducing false tripping of the residual current circuit breaker is activated. | |
Rated non-tripping fault current limit value | 0.015‑0.3 | Value of the non-tripping residual current specified by the manufacturer for the residual current circuit breaker at which the residual current circuit breaker does not switch off under specified conditions. |
Insulation warning
Insulation warning | Off | The insulation warning is deactivated. |
On | The insulation warning is activated. | |
Insulation measurement mode
| Exact | Insulation monitoring takes place with the highest degree of accuracy and the measured insulation resistance is displayed on the user interface of the inverter. |
Fast | Insulation monitoring takes place with a lesser degree of accuracy, whereby the time to take the insulation measurement is shortened and the insulation value is not displayed on the user interface of the inverter. | |
Threshold for the insulation warning | 100 | If the value drops below the threshold, status code 1083 is displayed on the user interface of the inverter. |
All available updates for inverters and other Fronius devices are provided on the product pages and in the "Fronius Download Search" area at www.fronius.com .
The guided setup wizard can be accessed here.
All settings
Resets all configuration data, apart from the country setup. Changes to the country setup may only be made by authorized personnel.
All settings without network
Resets all configuration data, apart from the country setup and the network settings. Changes to the country setup may only be made by authorized personnel.
Current messagesAll current events of the linked system components are displayed here.
IMPORTANT!
Depending on the type of event, this must be confirmed via the "tick" button so that it can be further processed.
History
All events of the linked system components that are no longer present are displayed here.
All the information regarding the system and the current settings is displayed and provided for download in this menu area.
The power data and functional scope of the inverter are stored in the license file.
If the inverter, power stage set PC board, or data communication area is replaced, the license file must also be replaced.
IMPORTANT!
The support user exclusively enables Fronius Technical Support to configure settings on the inverter via a secure connection. Access is deactivated by clicking the Terminate Support User Session button.
IMPORTANT!
The remote access exclusively enables Fronius Technical Support to access the inverter via a secure connection. In this case, diagnostics data are transmitted, which are used for troubleshooting. The remote access can be activated only upon request by Fronius Support.
Server addresses for data transfer
If a firewall is used for outgoing connections, allow the below protocols, server addresses, and ports for successful data transfer, see:
When using FRITZ!Box products, configure Internet access without any restrictions or limitations. Do not set the DHCP Lease Time (validity) to 0 (=infinite).
LAN:
After establishing the connection, check the connection status.
WiFi:
Activate the access point of the inverter. This is opened by touching the sensor > Communications LED flashes blue
After connecting, the status of the connection should be checked.
Access point:
The inverter serves as the access point. A PC or mobile device connects directly to the inverter. Connecting to the Internet is not possible. Assign a Network Name (SSID) and Network Key (PSK) to establish a connection. Assign a Network Key (PSK) with at least 20 characters, consisting of upper and lower case letters, special characters, and numbers, to protect the device from unauthorized access.
It is possible to operate a connection via WiFi and via the access point at the same time.
LAN:
WiFi:
Access point:
The inverter communicates with system components (e.g., Fronius Smart Meter) and other inverters via Modbus. The primary device (Modbus Client) sends control commands to the secondary device (Modbus Server). The control commands are executed by the secondary device.
RTU Server
The following input fields and functions are available for communication via Modbus RTU:
| Meter address offset |
| Inverter address |
| SunSpec Model Type |
| Interface |
| Baud Rate |
| Parity |
| Allow Control If this option is activated, the inverter is controlled via Modbus. Inverter control includes the following functions:
TCP Server
The following input fields and functions are available for communication via Modbus TCP:
| Modbus port |
| Meter Address |
| Restrict Control |
The utility/energy supplier can influence the output power of the inverter with Cloud control. This requires the inverter to have an active Internet connection.
Parameter | Display | Description |
Cloud control | Off | Cloud control of the inverter is deactivated. |
On | Cloud control of the inverter is activated. |
Profile | Value range | Description |
Allow cloud control for regulatory purposes (Technician) | Deactivated/Activated | The function may be mandatory for proper operation of the system.* |
Allow cloud control for Virtual Power Plants (Customer) | Deactivated/Activated | If the Allow remote control for regulatory purposes (technician) function is activated (technician access required), the Allow remote control for virtual power plants function is automatically activated and cannot be deactivated.* |
* Cloud control
A virtual power plant is an interconnection of multiple generators. This virtual power plant can be controlled by means of the cloud control via the Internet. An active inverter Internet connection is a prerequisite for this. System data are transferred.
The Solar API is an IP-based, open JSON interface. If enabled, IOT devices in the local network may access inverter information without authentication. For security reasons, the interface is disabled in the factory. Activate the interface manually if it is required for a third-party application (e.g., EV charger, smart home solutions, etc.). If there is a Fronius Wattpilot in the network, the inverter automatically activates the Solar API.
Fronius recommends using Fronius Solar.web for monitoring and analyzing the inverter and connected system components.
In the event of a firmware update to version 1.14.x, the Solar API setting is applied. In systems with a version below 1.14.x, the Solar API is activated; with higher versions, it is deactivated but can be switched on and off via the menu.
Manually activating the Fronius Solar API
On the user interface of the inverter in the Communication > Solar API menu area, activate the function Activate communication via Solar API.
In this menu, you can agree to the technically necessary data processing or reject it.
In addition, the transfer of analysis data and remote configuration via Fronius Solar.web can be enabled or disabled.
Danger from unauthorized fault analyses and repair work.
Fault analyses and repair work on the PV system may only be carried out by installers/service technicians from authorized specialist companies in accordance with national standards and regulations.
Risk due to unauthorized access.
Incorrectly set parameters can have a negative effect on the public grid and/or the grid power feed operation of the inverter and result in the loss of standard conformity.
Parameters may only be adjusted by installers/service technicians from authorized specialist companies.
Do not give the access code to third parties and/or unauthorized persons.
Risk due to incorrectly set parameters.
Incorrectly set parameters can have a negative effect on the public grid and/or cause inverter malfunctions and failures and result in the loss of standard conformity.
Parameters may only be adjusted if this has been approved or requested by the utility.
Any parameter adjustments must be made in compliance with nationally applicable standards and/or directives as well as the specifications of the utility.
The Country Setup menu area is intended exclusively for installers/service technicians from authorized specialist companies. To apply for the access code required for this menu area, see chapter Requesting inverter codes in Solar.SOS.
The selected country setup for the country in question contains preset parameters in accordance with nationally applicable standards and requirements. Changes may need to be made to the selected country setup depending on local grid conditions and the specifications of the utility.
The Country Setup menu area is intended exclusively for installers/service technicians from authorized specialist companies. The inverter access code required for this menu area can be requested in the Fronius Solar.SOS portal.
Activating this function limits the output power of the inverter to the specified value in watts.
Energy companies or grid operators can prescribe import limitations for inverters. The amperage is limited to the set value.
Energy companies or grid operators can prescribe feed-in limits for inverters (e.g., max. 70% of the kWp or max. 5 kW). The inverter limits the active power at the grid connection point (installation location of the Fronius Smart Meter or primary meter) to the set value.
The inverter takes account of self-consumption in the household before the power is reduced. An individual limit can be set.
In order to minimize the yield losses due to the power of feeding in limitation, the power available from the module array can be:
If these possibilities have been exhausted, the power drawn from the module array is reduced to such an extent that the feed-in limit is not exceeded.
Installation variants with an inverter, Fronius Smart Meter, and system components are listed under Components.
Total DC power of the system
The input field for the total DC power of the entire system in Wp. Always enter this value if the Maximum grid feed-in power is specified in %.
Power Control deactivated
The inverter converts all available PV energy.
Power Control activated
Feeding in limited with the following selection options:
IMPORTANT! Implement the settings for Limit per phase if national standards and regulations require a limitation of the single-phase power. Set the value for the permissible power of feeding in for each phase.
IMPORTANT! Power Control settings are automatically applied for the dynamic feed-in limit of I/O power management. Total Power Limit is the default configuration.
Dynamic feed-in limit (Soft Limit)
If this value is exceeded, the inverter readjusts down to the set value.
Export Limit Protection (PAV,E protection)
This function monitors compliance with the feed-in limit. If Dynamic feed-in limit (Soft Limit) is activated, the inverter controls the power of feeding in in such a way that this function is usually not activated. If the specified limit values and the switch-off times are exceeded, this protection function disconnects the inverter from the grid.
The Maximum grid feed-in power (PAV,E) in the case of an asymmetric feed-in (Limit per phase – asymmetric generation or Limit per phase – weakest phase) can be combined with the export limit protection (PAV,E protection) function. The Maximum grid feed-in power is calculated as follows: Maximum grid feed-in power per phase (PAV,E) x 3.
The export limit protection (PAV,E protection) function is only possible if a Smart Meter IP configured with MQTT is installed at the feed-in point.
Export Limit Protection (Hard Limit Trip)
IMPORTANT! This function is only available if Dynamic feed-in limit (Soft Limit) is activated.
Input field for the Maximum grid feed-in power in W or % (setting range: ‑10 % to 100 %).
If there is no meter in the system or if the primary meter has failed, the inverter limits its output power to the set value.
If this value is exceeded, the inverter switches off within max. 5 s. This value must be higher than the value set for Dynamic feed-in limit (Soft Limit).
If required, enable the fail-safe function Reduce inverter power to 0% if meter connection has been lost. When this function is enabled, the inverter activates standby mode. No feed-in takes place.
The use of WiFi for communication between the Fronius Smart Meter and the inverter is not recommended with the fail-safe function activated at the same time. Even short-term disconnections can cause the inverter to shut down. This problem arises with weak WiFi signal strengths, a slow or overloaded WiFi connection, and automatic channel selection of the router.
"Total Power Limit"
(feed-in limit 0 kW)
Explanation
No power (0 kW) may be fed into the public grid at the grid feed-in point. The load requirement in the home network (12 kW) is supplied by the power generated by the inverter.
"Limit per phase – asymmetric generation"
(feed-in limit 0 kW per phase) – asymmetric
Explanation
The load requirement in the home network per phase is determined and supplied.
(feed-in limit 1 kW per phase) – asymmetric
Explanation
The load requirement in the home network per phase is determined and supplied. In addition, the excess production (1 kW per phase) is fed into the public grid in accordance with the maximum permitted feed-in limit.
"Limit per phase – weakest phase"
(feed-in limit 0 kW per phase) – symmetrical
Explanation
The weakest phase in the load requirement in the home network is determined (phase 1 = 2 kW). The result of the weakest phase (2 kW) is applied to all phases. Phase 1 (2 kW) can be supplied. Phase 2 (4 kW) and phase 3 (6 kW) cannot be supplied, power from the public grid is required (phase 2 = 2 kW, phase 3 = 4 kW).
(feed-in limit 1 kW per phase) – symmetrical
Explanation
The weakest phase in the load requirement in the home network is determined (phase 1 = 2 kW) and the max. permitted feed-in limit (1 kW) is added. The result of the weakest phase (2 kW) is applied to all phases. Phase 1 (2 kW) can be supplied. Phase 2 (4 kW) and phase 3 (6 kW) cannot be supplied, power from the public grid is required (phase 2 = 1 kW, phase 3 = 3 kW).
IMPORTANT! To view and change settings in this menu item, select the Technician user. Enter and confirm the password for the Technician user. Settings in this menu area may only be made by technical specialists.
The inverter can be used as a primary device to control dynamic feed-in limits for additional Fronius inverters (secondary devices) so that feed-in limits prescribed by energy companies or utilities can be centrally managed. This control refers to the Soft Limit feed-in limit, see Feed-in limit. To do so, the following requirements must be met:
IMPORTANT! Only one primary meter is required for the primary device.
IMPORTANT! If an inverter with a battery is connected, use this inverter as the primary device for Multiple Inverter Control.
External grid and system protection
Regional standards and guidelines may require the installation of external grid and system protection for systems >30 kVA (see Central grid and system protection).
Multiple Inverter Control is available for the following device combinations:
Primary devices | Secondary devices |
GEN24, Verto, Tauro |
Primary meter
One Fronius Smart Meter acts as the only primary meter and is connected directly to the primary device. This Smart Meter measures the total output power of all inverters into the grid and passes this information to the primary device.
Primary device
Configure the feed-in limit on the user interface of the inverter:
To perform the search again, press the Refresh button.
If Use Modbus TCP is enabled, it is also possible to select Fronius SnapINverters with Datamanager 2.0 and Fronius Argeno with Use Inverter.
For more information on configuring the Fronius Argeno or Fronius Datamanager 2.0 as a secondary device, refer to the respective operating instructions.
Secondary device
Each secondary device takes over the settings for the feed-in limit from the primary device. A secondary device does not transmit any data for the feed-in limit to the primary device. To do so, the following requirements must be met:
Set the following configurations for the feed-in limit on the secondary device:
Only carry out work steps 2 and 3 if Use Modbus TCP is enabled on the primary device.
General
Settings relevant to the grid operator are defined as rules under this menu item. This relates to an effective power limit in % or watts and/or a power factor specification. To view and change settings, select the Technician user, and enter and confirm the password. Only technical specialists may make settings in this menu area.
Under Rules, expand a menu area (e.g., Rule 1). Configure the following settings:
Limitation
IMPORTANT!
A dynamic feed-in limit for several inverters can be configured under Feed-in limit. I/O power management rules are transferred from the inverter (primary device) to connected inverters in the system (secondary devices).
Select the following rules for power management:
IMPORTANT!
The rules for shutdown apply to this device and cannot be applied to other inverters in the system.
Input pattern (assignment of individual I/Os)
1 click = white, contact open
2 clicks = blue, contact closed
3 clicks = gray, not used
Power Factor (cos φ) (define value)
Impedance response
DNO Feedback
If the rule is activated, always configure the DNO Feedback output, e.g., for operating a signal device.
The Import and Export of defined rules can be carried out in the data format *.fpc. The rules and pin assignments in the following connection examples are not the only possible configurations. For pin assignment, take into account the available connections at the Data communication area and settings of the device configuration.
If there is an active rule for the control of the inverter, the device indicates this in the overview of the user interface under Device State.
Controlling Priorities
Used to set controlling priorities for I/O Power Management (DRM or ripple control receiver), the feed-in limit, and control via Modbus.
1 = highest priority, 3 = lowest priority
Local priorities of the I/O power management, the feed-in limit, and the Modbus interface are deactivated by cloud control commands (regulatory purposes and virtual power plants) – see Cloud control – and by backup power.
In terms of controlling priorities, the device differentiates between power control and inverter shutdown. Inverter shutdown always takes precedence over power control. An inverter shutdown command is always executed and does not need to be prioritized.
Power controlConnect the ripple control signal receiver and the I/O terminals of the inverter to one another as shown in the connection diagram.
For distances greater than 10 m between the inverter and the ripple control signal receiver, use a shielded data communication cable (CAT 5 or higher) with twisted cable pairs. Connect the shielding on one side to the terminal of the data communication area (SHIELD).
| (1) | Ripple control signal receiver with 4 relays for effective power limitation. |
| (2) | I/O connection terminals of the data communication area. |
| (1) | Ripple control signal receiver with 3 relays for effective power limitation. |
| (1) | Ripple control signal receiver with 2 relays for effective power limitation. |
| (1) | Ripple control signal receiver with 1 relay for effective power limitation. |
Description
The Autotest makes it possible to check the Italian protection function, required by the applicable standard for monitoring the voltage and frequency limit values of the inverter during commissioning. In normal operation, the inverter constantly checks the real-time actual value of the voltage and frequency of the grid.
Once the Autotest has started, different individual tests are carried out automatically, in succession. Depending on the grid conditions, the duration of the test is approximately 15 minutes.
IMPORTANT!
In Italy, the inverter may only be commissioned following a successfully completed Autotest (CEI 0-21). If an Autotest is not passed, grid power feed operation may not take place. Once the Autotest is started, it must be completed successfully. The Autotest cannot be started during backup power mode.
Umax | Test for checking the maximum voltage in the phase conductors |
Umin | Test for checking the minimum voltage in the phase conductors |
fmax | Test for checking the maximum mains frequency |
fmin | Test for checking the minimum mains frequency |
fmax alt | Test for checking an alternative maximum mains frequency |
fmin alt | Test for checking an alternative minimum mains frequency |
U outer min | Test for checking the minimum outer voltages |
U longT. | Test for checking the 10 min. voltage average |
Note on the Autotest
The limit values are set in the Safety and Grid Regulations > Country Setup> Grid Support Functions menu area.
The Country Setup menu area is intended exclusively for installers/service technicians from authorized specialist companies. The inverter access code required for this menu area can be requested in the Fronius Solar.SOS portal (see chapter Requesting inverter codes in Solar.SOS on page (→)).
The grid operator may request the connection of one or more inverters to a ripple control receiver in order to limit the active power and/or the power factor of the photovoltaic system.
On the user interface of each inverter connected to the ripple control receiver, set the same parameters for I/O power management.
The inverter is designed so that it does not require additional maintenance work. Nevertheless, a few points must be considered during operation to ensure that the inverter works perfectly.
Maintenance and service work may only be carried out by a technical specialist.
Wipe the inverter, if necessary, with a damp cloth.
Do not use cleaning agents, scouring agents, solvents, or similar products to clean the inverter.
If the inverter is operated in dusty environments, dirt may build up on the heat sink and fan.
This may result in a loss of power due to insufficient cooling of the inverter.
Remove any build-ups of dirt from the heat sink and the fan.
Switch off power to the inverter and wait for the capacitors to discharge (2 minutes) and the fan to shut down.
Turn the DC disconnector to the "off" switch setting.
Remove any build-up of dirt on the heat sink and fan using compressed air, a cloth, or a brush.
Risk due to damage to the fan bearing in the event of incorrect cleaning.
Excessive speeds and the application of pressure to the fan bearing can cause damage.
Block the fan and clean with compressed air.
When using a cloth or brush, clean the fan without applying any pressure.
To start up the inverter again, follow the steps listed above in reverse order.
Danger from mains voltage and DC voltage from PV modules.
The connection area must only be opened by an authorized electrician.
The separate power stage set area must only be opened by Fronius-trained service technicians.
Prior to any connection work, disconnect the inverter on the AC side and the DC side.
Danger due to residual voltage from capacitors.
Allow the capacitors of the inverter to discharge (2 minutes).
Used equipment and batteries must be returned to the distributor or an authorized local collection system. Do not dispose of batteries with domestic waste. Protect batteries from high temperatures, direct sunlight, moisture and corrosive environments.
Arrange for the safe collection and proper disposal of damaged, leaking or used batteries by a battery recycling company or the Fronius Service Partner.
In addition, it should be noted that batteries contain substances that, if disposed of improperly, can have a significant negative impact on the environment as well as on human health and the safety of persons, in particular due to the leakage of hazardous substances such as heavy metals or electrolytes, which can contaminate soil, water and air.
This ensures environmental protection and the sustainable use of natural resources.Packaging materialsDetailed warranty conditions specific to your country can be found at https://www.fronius.com/en/download-center?searchword=Warranty+conditions .
If there is a warranty for the relevant product, register the product at https://warranty.fronius.com/ and activate or extend the warranty.
Status codes are displayed on the user interface of the inverter in the System > Event Log menu area or in the user menu under Notifications and in Fronius Solar.web*.
| * | If configured accordingly, see chapter Fronius Solar.web on page (→). |
| Cause: | A device that is connected in the WSD chain has interrupted the signal line (e.g., surge protection device) or the bypass installed ex works as standard has been removed and no trigger device has been installed. |
| Remedy: | If the SPD surge protection device has tripped, the inverter must be repaired by an authorized specialist. |
| OR: | Install the bypass installed ex works as standard or a trigger device. |
| OR: | Turn the WSD (wired shutdown) switch to position 1 (WSD primary device). |
WARNINGDanger from work that is not carried out properly. This can result in serious injury and damage to property. The installation and connection of an SPD surge protection device may only be carried out by Fronius-trained service personnel in accordance with the technical specifications. Observe safety rules. | |
Input data | |
Maximum input voltage | 1000 VDC |
Start-up input voltage | 150 VDC |
MPP voltage range | 210–870 VDC |
Number of MPP controllers | 3 |
Maximum total input current (IDC max) | 75 A |
Max. total short circuit current 8) | 100 A |
Maximum total array power (PPV max) | 22.5 kWp |
DC overvoltage category | 2 |
Max. inverter backfeed current to the array 3) | 50 A4) |
Max. capacity of the PV generator against earth | 5400 nF |
Limit value of the insulation resistance test between module array and ground (on delivery) 7) | 100 kΩ |
Adjustable range of the insulation resistance test between module array and ground 6) | 10–10,000 kΩ |
Limit value and trip time of sudden residual current monitoring (on delivery) | 30 / 300 mA / ms |
Limit value and trip time of continuous residual current monitoring (on delivery) | 300 / 300 mA / ms |
Adjustable range of continuous residual current monitoring 6) | 30–300 mA |
Cyclical repetition of insulation resistance test (on delivery) | 24 h |
Adjustable range for cyclical repetition of insulation resistance test | - |
Output data | |
Grid voltage range | 176–528 VAC |
Rated grid voltage | 220 | 230 VAC 1) |
Rated power | 15 kW |
Rated apparent power | 15 kVA |
Rated frequency | 50 / 60 Hz 1) |
Maximum output current/phase | 38.5 A |
Power factor (cos phi) | 0-1 ind./cap.2) |
Grid connection | 3~ (N)PE 380 / 220 VAC |
Earthing systems | TT (allowed if UN_PE < 30 V) |
Maximum output power | 15 kW |
Rated output current/phase | 22.7 / 21.7 / 19.7 / 18.1 A |
Total harmonic distortion | < 3% |
AC overvoltage category | 3 |
Current (inrush) 5) | 24.72 A peak / |
Max. output fault current/duration | 33.8 A / 11.8 ms |
General data | |
Night-time power loss = standby consumption | 12 W |
European Efficiency (210 / 620 / 870 VDC) | 97.08% / 98.19% / 97.54% |
Maximum efficiency | 98.53% |
Protective class | 1 |
EMC emission class | B |
Pollution degree | 3 |
Permitted ambient temperature | -40 °C to +60 °C |
Permitted storage temperature | -40 °C to +70 °C |
Relative humidity | 0–100% |
Sound pressure level | 56.5 dB(A) (ref. 20 µPA) |
Ingress protection rating | IP66 |
Dimensions (height × width × depth) | 730 × 540 × 278 mm |
Weight | 35.2 kg |
Weight with packaging | 41.8 kg |
Inverter topology | Non-insulated, transformerless |
Input data | |
Output data | |
General data | |
Weight | 35.2 kg |
Input data | |
MPP voltage range | 245–870 VDC |
Maximum total array power (PPV max) | 26.25 kWp |
Output data | |
Rated power | 17.5 kW |
Rated apparent power | 17.5 kVA |
Maximum output power | 17.5 kW |
Rated output current/phase | 26.5 / 25.4 / 23 / 21.1 A |
General data | |
European Efficiency (245 / 620 / 870 VDC) | 97.28% / 98.29% / 97.72% |
Maximum efficiency | 98.55% |
Weight | 35.2 kg |
Input data | |
MPP voltage range | 275–870 VDC |
Maximum total array power (PPV max) | 30 kWp |
Output data | |
Rated power | 20 kW |
Rated apparent power | 20 kVA |
Maximum output power | 20 kW |
Rated output current/phase | 30.3 / 29 / 26.2 / 24.1 A |
General data | |
European Efficiency (275 / 620 / 870 VDC) | 97.41% / 98.33% / 97.80% |
Maximum efficiency | 98.56% |
Weight | 35.2 kg |
Input data | |
MPP voltage range | 355–870 VDC |
Maximum total array power (PPV max) | 36 kWp |
Output data | |
Rated power | 24 kW |
Rated apparent power | 24 kVA |
Maximum output power | 24 kW |
Rated output current/phase | 36.4 / 34.8 / 31.5 / 28.9 A |
General data | |
European Efficiency (335 / 620 / 870 VDC) | 97.62% / 98.35% / 97.93% |
Maximum efficiency | 98.54% |
Weight | 35.2 kg |
Input data | |
MPP voltage range | 350–870 VDC |
Maximum total array power (PPV max) | 37.5 kWp |
Output data | |
Rated grid voltage | 230 VAC 1) |
Rated power | 25 kW |
Rated apparent power | 25 kVA |
Rated frequency | 50/60 Hz 1) |
Grid connection | 3~ (N)PE 400 / 230 VAC |
Maximum output power | 25 kW |
Rated output current/phase | 36.1 / 32.8 / 30.1 A |
General data | |
European Efficiency (350 / 620 / 870 VDC) | 97.67% / 98.35% / 97.98% |
Weight | 35.2 kg |
DC disconnector | Integrated |
Cooling principle | Controlled forced-air ventilation |
RCMU 9) | Integrated |
RCMU classification | The software class of the safety platform(s) is defined as a class B control function (single-channel with periodic self-test) in accordance with IEC 60730 Annex H. |
DC isolation measurement 9) | integrated 2) |
Overload performance | Operating point shift |
Active anti-islanding method | Frequency point shift method |
AFCI | optional |
AFPE (AFCI) classification (according to IEC 63027) 9) | F-I-AFPE-2-4/2-2 |
Frequency range | 2412 - 2462 MHz |
Channels / power used | Channel: 1-11 b,g,n HT20 |
Modulation | 802.11b: DSSS (1Mbps DBPSK, 2Mbps DQPSK, 5.5/11Mbps CCK) |
WiFi SMA-RP connection | 802.11b/g/n (WPA, WPA2) |
Ethernet (LAN) | RJ 45, 10/100 Mbit |
Wired shutdown (WSD) | Max. 28 devices/WSD chain |
Modbus RTU SunSpec (2x) | RS485 2-wire |
Battery connection (only for Verto Plus devices) | Modbus O / RJ 45 / 12 V power supply |
Voltage level of digital inputs | Low: min. 0 V-max. 1.8 V |
Input currents of digital inputs | depending on the input voltage; |
Total power for digital output (with internal supply) | 6 W at 12 V |
Power per digital output | 1 A at >12.5 V - 24 V |
Datalogger/web server | Integrated |
General data | |
Continuous operating current (Icpv) | < 0.1 mA |
Rated discharge current (In) | 20 kA |
Protection level (Up) | 3.6 kV |
Short circuit strength PV (Iscpv) | 15 kA |
Disconnector | |
Thermal disconnector | Integrated |
External fuse | None |
Mechanical properties | |
Disconnection indicator | Mechanical indicator (red) |
Remote communication of the connection interruption | Output on the changeover contact |
Housing material | Thermoplastic UL-94-V0 |
Test standards | IEC 61643-31 / EN 61643-31 |
| 1) | The values stated are defaults; the inverter is configured specifically to suit the requirements of the relevant country. |
| 2) | Depending on the country setup or device-specific settings (ind. = inductive; cap. = capacitive). |
| 3) | Maximum current from a defective PV module to all other PV modules. From the inverter itself to the PV side of the inverter, it is 0 A. |
| 4) | Guaranteed by the electrical configuration of the inverter. |
| 5) | Current peak when switching on the inverter. |
| 6) | Specified values are standard values; depending on the requirement and PV power, these values must be adjusted accordingly. |
| 7) | Specified value is a max. value; exceeding the max. value may negatively affect the function. |
| 8) | ISC PV = ICP PV ≥ ISC max = I SC (STC) x 1.25 according to e.g., IEC 60364-7-712, NEC 2020, AS/NZS 5033:2021 |
| 9) | Software class B (single channel with periodic self-test) control function according to IEC60730-1 Annex H. |
General data | |
Product name | Benedict LSA32 E 8237 |
Rated insulation voltage | 1000 VDC |
Rated impulse withstand voltage | 8 kV |
Suitability for insulation | Yes, DC only |
Utilization category and/or PV utilization category | according to IEC/EN 60947-3 utilization category DC-PV2 |
Rated short-time withstand current (Icw) | Rated short-time withstand current (Icw): 1000 A |
Rated short-circuit capacity (Icm) | Rated short-circuit capacity (Icm): 1000 A |
Rated operating current and rated breaking capacity | ||||
Rated operating voltage (Ue) | Rated operating current (Ie) | I(make) / I(break) | Rated operating current (Ie) | I(make) / I(break) |
≤ 500 VDC | 14 A | 56 A | 28 A | 112 A |
600 VDC | 11.5 A | 46 A | 28 A | 112 A |
700 VDC | 7.5 A | 30 A | 28 A | 112 A |
800 VDC | 5.75 A | 23 A | 23 A | 92 A |
900 VDC | 4.75 A | 19 A | 20 A | 80 A |
1000 VDC | 4 A | 16 A | 13 A | 52 A |
Number of pins | 1 | 1 | 2 | 2 |