  • General information
    • General
      • Intended use
      • System components required
      • Integrating the Fronius Smart Meter
      • Description of the device
      • System design
    • Control elements and connections
      • Indications/controls on the device
      • Connection area
    • Selection of heater
      • 1-phase heater
      • 3-phase heater
      • Example for calculating the charging time
  • Installation and commissioning
    • Choice of location and installation position
      • Choosing location - general remarks
      • Installation position
    • Wall mounting
      • Safety
      • Selecting wall plugs and screws
      • Mounting the Ohmpilot on the wall
    • Installation
      • Stripping lengths
      • Electrical connection
    • 1-phase heating element up to 3 kW
      • Application example 1
    • 3-phase heating element 900 W up to 9 kW
      • Application example 2
    • 1-phase heating element up to 3 kW with heat pump control
      • Application example 3
      • Settings in the menu area
    • 1-phase heating element up to 3 kW and external source
      • Application example 4
    • Two heating elements - 3-phase and 1-phase
      • Application example 5
    • Two 3-phase heating elements up to 9 kW
      • Application example 6
    • 1-phase heating element up to 3 KW / 3-phase heating element and circulation pump
      • Application example 7
    • Establishing the data connection
      • Possible communication channels
      • Pairing the inverter to the Ohmpilot
      • Establishing a connection via Modbus RTU
      • Establishing a connection via LAN
      • Establishing a connection via WLAN
    • Boost Mode
      • Boost Mode
    • User interface
      • Status display
    • Optional settings
      • Manual settings for HEATER 1
      • Activating Legionella prevention
      • Adapting the day curve
      • Temperature limitation
  • Appendix
    • Status Codes
      • Status codes
    • Technical data
      • Fronius Ohmpilot technical data
    • Tests/specifications
    • Warranty terms and conditions, and disposal
      • Fronius manufacturer's warranty
      • Disposal
      • Applicable standards and directives
Fronius Ohmpilot Operating Instructions
Controls and connections
User interface
Status codes
Technical data
User interface
Status codes
Technical data
Safety rules
DANGER!
Indicates immediate danger.
WARNING!
CAUTION!
NOTE!
  1. Safety rules
DANGER!
WARNING!
CAUTION!
NOTE!
  1. Safety rules
General
The device has been manufactured in line with the state of the art and according to recognised safety standards. In the event of incorrect operation or misuse, there is a risk of:
  • Serious or fatal injury to the operator or third parties
  • Damage to the device and other material assets belonging to the operating company
All personnel involved in commissioning, maintenance and servicing of the device must:
  • Be suitably qualified
  • Have knowledge of and experience in dealing with electrical installations
  • Read and follow these Operating Instructions carefully
In addition to the Operating Instructions, all applicable local rules and regulations regarding accident prevention and environmental protection must also be followed.
All safety and danger notices on the device:
  • Must be kept in a legible state
  • Must not be damaged
  • Must not be removed
  • Must not be covered, pasted or painted over
Only operate the device when all protection devices are fully functional. If the protection devices are not fully functional, there is a risk of:
Any safety devices that are not fully functional must be repaired by an authorized specialist before the device is switched on.
For the location of the safety and danger notices on the device, refer to the chapter headed "Warning notices on the device" in the Operating Instructions for your device.
Faults that could compromise safety must be remedied before switching on the device.
  1. Safety rules
  1. Safety rules
Qualified personnel
The servicing information contained in these operating instructions is intended only for the use of qualified service engineers. An electric shock can be fatal. Do not carry out any actions other than those described in the documentation. This also applies to qualified personnel.
All cables and leads must be secured, undamaged, insulated and adequately dimensioned. Loose connections, scorched, damaged or inadequately dimensioned cables and leads must be immediately repaired by authorised personnel.
Maintenance and repair work must only be carried out by an authorised specialist.
It is impossible to guarantee that bought-in parts are designed and manufactured to meet the demands made on them, or that they satisfy safety requirements. Use only original spare parts (also applies to standard parts).
Components that are not in perfect condition must be changed immediately.
  1. Safety rules
EMC measures
In certain cases, even though a device complies with the standard limit values for emissions, it may affect the application area for which it was designed (e.g., when there is equipment that is susceptible to interference at the same location, or if the site where the device is installed is close to either radio or television receivers). If this is the case, then the operator is obliged to take action to rectify the situation.
  1. Safety rules
Data security
  • saving and retaining personal settings
  1. Safety rules
Copyright
The text and illustrations are all technically correct at the time of printing. We reserve the right to make changes. The contents of the operating instructions shall not provide the basis for any claims whatsoever on the part of the purchaser. If you have any suggestions for improvement, or can point out any mistakes that you have found in the instructions, we will be most grateful for your comments.
General information
General
Intended use
The Fronius Ohmpilot is an addition to the Fronius product portfolio in the field of energy management. The device controls the heating of hot water using surplus energy from a photovoltaic system. Any other use is considered improper.
  1. General information
General
Intended use
  2. General
Intended use
  2. General
  • GEN24 inverter
    • Fronius Primo / Symo GEN24
  • Fronius SnapINverter
    • Fronius Symo / Galvo / Eco or Primo (from Fronius Datamanager 2.0 software version 3.8.1-x onwards) or Fronius Symo Hybrid (from Fronius Hybridmanager software version V1.8.1.x onwards)
  • Fronius Smart Meter
  • Fronius Ohmpilot
  • Resistive load (e.g. boiler with heating element)
  2. General
To operate the Ohmpilot, a Fronius Smart Meter is required to measure the surplus energy. On the user interface of the inverter, it is necessary to set whether the Fronius Smart Meter is installed at the feed-in point or in the consumption branch.
  2. General
The Ohmpilot uses pulse width modulation to regulate the surplus power from the photovoltaic system for one phase. With one phase, it is possible to control a heating element with a continuously variable output of up to 3 kW for example. The Ohmpilot has two additional outputs for switching further phases. This means that heating elements with an output of 300 W to 9 kW can be controlled.
For a heating element with 9 kW output, the surplus power of 0 - 3 kW is controlled in phase 1. If more power is available, the Ohmpilot switches to phase 2. Phase 1 can therefore be continuously adjusted between 3 and 6 kW. If the available power is > 6 kW, the Ohmpilot adds phase 3. Phase 1 is again continuously adjusted between 6 and 9 kW
Power range
Phase 1
Phase 2
Phase 3
0 - 3 kW
0 - 3 kW continuously variable
3 - 6 kW
3 kW fixed
6 - 9 kW
3 kW fixed
3 kW fixed
Other resistive loads such as infra-red heaters and towel dryers can also be controlled.
  2. General
System design
CAUTION!
Danger from connecting an electronic thermostat.
This would destroy the Ohmpilot or the connected load.
Use mechanical temperature switches.
CAUTION!
Danger due to connection of an incorrect load (e.g. fan heater).
This may result in destruction of the load.
Connect only purely resistive loads.
NOTE!
Phase control
The sum of all phases forms the basis for Ohmpilot control. The Ohmpilot is not suitable for phase-accurate billing.
NOTE!
Ohmpilot and Fronius Datamanager 2.0 / Fronius Hybridmanager
Only one Ohmpilot can be connected per Fronius Datamanager 2.0 / Fronius Hybridmanager.
NOTE!
Ohmpilot and dynamic power reduction
From software version 3.13.1-x of the Fronius Datamanager or 1.11.1-x of the Fronius Hybridmanager, the Ohmpilot can be used together with dynamic power reduction from 0-100%.
NOTE!
Use of other generation sources
Other generation sources can also be used in conjunction with the Fronius Datamanager Box 2.0, e.g. CHP, third-party inverters, etc. Generated power and consumption data cannot be acquired for other generation sources, so these figures cannot be displayed in Fronius Solar.web.
NOTE!
Backup power
Due to the high heat output, the Ohmpilot cannot be operated in backup power situations.
Install the Ohmpilot outside the backup power circuit.
NOTE!
Calcification of the connected heating element
Calcification can occur with hard water, especially if the minimum temperature is set above 60 °C. An annual inspection of the heating element is recommended.
Remove the heating element from the tank and remove the limescale;
do not scratch the surface of the heating element while doing so.
  2. General
Safety symbols and warnings are located on the left-hand side of the Ohmpilot. These warning notices and safety symbols must not be removed or painted over. They warn against incorrect operation, as this may result in serious injury and damage.
Safety symbols:
Danger of serious injury and damage due to incorrect operation
  • All the Operating Instructions for the system components, especially the safety rules
Dangerous electrical voltage
Before opening the machine, wait for the capacitors to discharge!
Hot surface
Text of the warning notices:
WARNING!
An electric shock can be fatal. Before opening the device, it must be disconnected at the input and output. Wait for the capacitors to discharge (15 seconds).
WARNING!
The device must not be covered and nothing may be hung over the device or cable.
Function key
1x WPS
2x ACCESS POINT
3x BOOST MODE
Press 1x
WPS (Wi-Fi Protected Setup) opens for 2 minutes or until successful pairing with the router. Pressing the WPS button on the router sends the WLAN password to the Ohmpilot.
Press 2x
WLAN access point is activated for 30 minutes so that settings can be implemented on the Ohmpilot via the Fronius Solar.web app.
Press 3x
Boost mode - dimmer level is activated at 100% for 4 hours, switching takes place through phases 2 and 3. This may result in electricity being sourced from the grid.
Press again
Ohmpilot is returned to the standard operating mode; boost mode, access point or WPS are deactivated.
Press for 7 seconds
Ohmpilot restarts
Heater indication
Unlit
No power supply to the Ohmpilot.
Flashing green (permanently)
The faster the flashing frequency, the greater the heat output. The LED flashes slowly at 0 W heat output and quickly at full output.
Flashing green (twice)
The heating element output is being measured. The Ohmpilot recognises whether a 1-phase or 3-phase heating element is connected.
Lights up green
Minimum temperature undershot or Legionella prevention system active (full heat output).
LAN / WLAN
connection indicator
Unlit
No connection
Flashing blue (once)
Flashing blue (twice)
WLAN access point open
Lights steady blue
Connection with network
Error indication
Unlit
No error
Flashing red (once)
No connection to the inverter
Flashing red (twice)
Temperature measurement faulty
Flashing red (three times)
Heating element faulty
Flashing red (four times)
Ohmpilot faulty
Flashing red (five times)
Minimum temperature not reached
A detailed description of the error is provided in Fronius Solar.web.
  2. Control elements and connections
Function key
1x WPS
2x ACCESS POINT
3x BOOST MODE
Press 1x
Press 2x
Press 3x
Press again
Press for 7 seconds
Ohmpilot restarts
Heater indication
Unlit
Lights up green
LAN / WLAN
Unlit
No connection
Lights steady blue
Error indication
Unlit
No error
Flashing red (once)
Ohmpilot faulty
Connection area
(1)
Green LED
(2)
Blue LED
(3)
Red LED
(4)
Function key
(5)
Ethernet RJ45
Cable at least CAT5, shielded
(6)
Modbus RTU (default address 40)
Spring balancer 0.2 - 1.5 mm2, cable length max. 1000 m, shielded and twisted
(7)
Temperature sensor terminal
Cable sensor PT 1000, spring balancer 0.2 - 1.5 mm2
(8)
Input - grid supply
1x 230 V or 3x 230 V, spring balancer 1.5 - 2.5 mm2
(9)
Output - L3 heating element
Spring balancer 1.5 - 2.5 mm2
(10)
Output - L2 heating element
(11)
Multifunctional relay output
Variable max. 13 A resistive load, spring balancer 1.5 - 2.5 mm2
WARNING!
Danger due to wires coming loose
Loose wires can come into contact with live parts and cause an electric shock.
When connecting signal cables, tie the individual wires together with a cable tie immediately before the terminal.
(12)
Output - heating element / dimming level L1
Continuously variable up to 3 kW
Selection of heater
1-phase heater
Controlled in a continuously variable manner from 0.3 to 3 kW
  • Resistive load (no electronic temperature limiters, fans, etc.)
  2. Selection of heater
1-phase heater
3-phase heater
Controlled in a continuously variable manner from 0.3 to 9 kW.
  • Equal load distribution on all 3 phases (e.g. 3 x 3 kW).
  • If a mechanical temperature switch is being used, it must switch all 3 phases simultaneously.
  • Purely resistive load (no electronic temperature limiters, fans, etc.)
  • Neutral conductor must be connected
A mechanical temperature switch simplifies commissioning and use. If no mechanical temperature switch is available, a temperature sensor can also be connected to the Ohmpilot. This limits the maximum temperature (see chapter "Temperature limitation" on page).
500 l boiler, heater is fitted at the very bottom of the boiler,
temperature spread 45 - 60 °C = 15 °C
4.5 kW heater
Possible stored energy = 500 l (storage tank capacity) x 1.16 Wh (energy requirement per litre) x 15 °C (temperature spread) = 8.7 kWh. If the heater at full power (4.5 kW), heating up takes approximately 2 hours.
For optimum utilisation of the surplus power and rapid reheating of the hot water, adjust the output of the heating system to the output of the photovoltaic system, e.g. 5 kWp system output => 4.5 kW heating
Please note the following criteria when choosing a location for the Ohmpilot:
Install only on a solid surface.
Max. ambient temperatures:
0 °C / +40 °C
Relative humidity:
0 - 99%
The airflow within the Ohmpilot is from the bottom to the top.
If the Ohmpilot is installed in an enclosed space, forced-air ventilation must be provided to ensure adequate heat dissipation.
NOTE!
Cable length
The maximum cable length from the output of the Ohmpilot to the load (heating element) must not exceed 5 m.
  1. Installation and commissioning
0 °C / +40 °C
Relative humidity:
0 - 99%
NOTE!
Cable length
  2. Choice of location and installation position
0 °C / +40 °C
Relative humidity:
0 - 99%
NOTE!
Cable length
Choice of location
The Ohmpilot is suitable for indoor installation. The housing satisfies protection class IP 54 and is protected against splashing water on all sides.
In order to minimise heating up of the Ohmpilot, do not expose it to direct sunlight. Install the Ohmpilot in a protected position. The Ohmpilot must only be installed and operated at an ambient temperature of 0-40 °C.
IMPORTANT! The Ohmpilot must not be installed or used at altitudes above 2000 m.
Do not install the Ohmpilot:
  • In areas where ammonia, corrosive vapours, acids or salts are present (e.g. fertiliser stores, ventilation openings from cattle sheds, chemical plants, tanneries, etc.)
Do not install the Ohmpilot in:
  • Places where there is an increased risk of damage from farm animals (horses, cattle, sheep, pigs, etc.)
  • Stables or adjoining areas
  • Storage areas for hay, straw, chaff, animal feed, fertilisers, etc.
Do not install the Ohmpilot in rooms or environments where there is a lot of dust. All Ohmpilot units are designed to be dust-tight. However, in areas with a heavy build-up of dust, the thermal efficiency may still be impaired by dust forming on the cooling surfaces. Regular cleaning is necessary in such situations.
  • Greenhouses
  • Storage or processing areas for fruit, vegetables or viticulture products
  • Areas used in the preparation of grain, green fodder or animal feeds
The Ohmpilot must be installed level, with the connections facing downwards, on a vertical wall. All inclined and horizontal installation positions are prohibited.
Wall mounting
Safety
WARNING!
Danger due to residual voltage from capacitors.
An electric shock can be fatal!
Before opening the device, wait for the capacitors to discharge (15 seconds).
WARNING!
Risk of burns from the heat sink when open.
This can result in personal injury.
Wear suitable protective equipment.
Allow heat sink to cool.
Do not touch the hot heat sink.
IMPORTANT! The IP 54 protection class only applies if the cover is firmly screwed to the back.
  2. Wall mounting
Safety
WARNING!
WARNING!
  2. Wall mounting
IMPORTANT! Different fixings may be required to fit the Ohmpilot, depending on the type of surface. The fixings are not included in the scope of supply. The installer is responsible for selecting the right type of fixing. The underlying surface must be load-bearing.
To install the Ohmpilot in masonry, Fronius recommends the use of steel screws with a diameter of 4 - 6 mm.
  2. Wall mounting
NOTE!
Risk of dirt and moisture on the connections or electronic components
This may result in damage to the Ohmpilot.
When drilling, ensure that terminals and electronic components in the connection area do not become dirty or wet.
Undo the 4 screws and remove the housing cover.
Mark drill holes, drill and insert wall plugs
3Attach the Ohmpilot to the wall with 4 screws
Installation
Stripping lengths
Stripping lengths of terminals for power stage set (L1, L2, etc.) and terminals for data communication area (D+, D-, PT1000)
  2. Installation
Stripping lengths
  2. Installation
IMPORTANT! Electrical connection work must be carried out by a specialist.
WARNING!
Danger from inadequate ground conductor connection.
This can result in severe personal injury or damage to property.
Install and connect the ground conductor connection in accordance with the national specifications
NOTE!
Overvoltage from the grid
Overvoltage can damage the device
Equip the Ohmpilot with a type B16 A automatic circuit breaker and a residual current circuit breaker.
NOTE!
Cable length
The maximum cable length from the output of the Ohmpilot to the load (heating element) must not exceed 5 metres due to electromagnetic compatibility.
NOTE!
Load connection
Only connect purely resistive loads.
When connecting a heating element, check the earthing of the boiler/buffer and the heating system.
Observe the maximum permissible flow and hot water temperature when setting the temperature on the heating element.
(1)
Temperature sensor PT1000
(2)
Hot water boiler
(3)
External source (e.g. gas-fired heating)
(4)
Heating element (max. 3 kW)
(5)
Ferrite rings (included in scope of delivery)
(6)
Output up to 3 kW variable, max. 13 A resistive load, spring-loaded terminal 1.5 - 2.5 mm²
(7)
Input - grid supply 1x 230V network, spring-loaded terminal 1.5 - 2.5 mm²
(8)
Residual-current circuit breaker
(9)
Automatic circuit breaker max. B16A
IMPORTANT! Plug & Play - no further settings are required for this application after successful connection to the inverter.
The Fronius Smart Meter records the current power at the feed-in point and transfers the data to the inverter. By controlling the Ohmpilot, the inverter adjusts any surplus energy that is available to zero. Specifically, this takes place by continuously adjusting the heating element connected to the Ohmpilot. Surplus energy is consumed using the heating element in a continuously variable manner.
If no temperature sensor is fitted, an external source (e.g. gas-fired heating) must be used to ensure the minimum temperature is met.
As an alternative, the Ohmpilot can ensure the minimum temperature. To do this, a temperature sensor must be connected so that the Ohmpilot can measure the temperature. This may result in electricity being sourced from the grid.
The maximum temperature must be set on the heating element thermostat. If the heating element does not have a thermostat, the Ohmpilot can also carry out this task as an alternative (see "Optional settings" section Optional settings on page (→)).
  2. 1-phase heating element up to 3 kW
(1)
(2)
Hot water boiler
(3)
(4)
(5)
(6)
(7)
(8)
(9)
(1)
(2)
Hot water boiler
(3)
(4)
Heating element (max. 9 kW)
(5)
(6)
(7)
(8)
(9)
Input - grid supply 3x 230V network, spring-loaded terminal 1.5 - 2.5 mm²
(10)
(11)
The Fronius Smart Meter records the current power at the feed-in point and transfers the data to the inverter. By controlling the Ohmpilot, the inverter adjusts any surplus energy that is available to zero. Specifically, this takes place by continuously adjusting the heating element connected to the Ohmpilot. This means that the surplus energy is consumed in a continuously variable manner by the heating element.
Depending on the surplus power, the individual phases are switched on or off and the remaining power is consumed at L1. As a result, the heating element output is divided by three.
IMPORTANT! A neutral conductor must be connected to the heating element!
  2. 3-phase heating element 900 W up to 9 kW
(1)
(2)
Hot water boiler
(3)
(4)
(5)
(6)
(7)
(8)
(9)
(10)
(11)
(1)
(2)
Hot water boiler
(3)
Heat pump with SG Ready control input
(4)
(5)
(6)
(7)
NOTE!
Relay contacts can oxidise.
The voltage must be at least 15 V and the current at least 2 mA, so that the relay contacts do not oxidise.
(8)
CAUTION!
Danger due to contact with live, stripped wires
A short circuit can be triggered and damage the device.
Carry out all connection work in accordance with the applicable electrotechnical guidelines and regulations.
Observe the maximum stripping length of 10 mm.
When connecting the phases, tie the individual wires together with a cable tie immediately before the terminal.
(9)
(10)
The Fronius Smart Meter records the current power at the feed-in point and transfers the data to the inverter. By controlling the Ohmpilot, the inverter adjusts any surplus energy that is available to zero. Specifically, this takes place by continuously adjusting the heating element connected to the Ohmpilot and by targeted switching on of the heat pump.
For activation, the heat pump must have a control input (SG Ready or approval from grid operator). The heat pump can be switched from normal operation to boost mode by activating input 2 of the heat pump with the relay. The heat pump can also be switched from grid operator-blocked operation to normal operation by activating input 1 of the heat pump with the relay. Information on the compatibility of the heat pump with this control unit can be found in the operating instructions for the respective device.
Relatively small surpluses are consumed by the heating element in a continuously variable manner. The heat pump should be activated above a certain surplus output due to the higher efficiency. The average COP (coefficient of performance) for water heating up to 53 °C is 2.5. This means that 1 kW of electrical energy is converted into 2.5 kW of thermal energy.
The optimum switching times depend on the following factors:
  • Heat pump COP. The higher the temperature to which the hot water is heated, the lower the COP.
  • The electrical heat pump output.
  • Feed-in tariff and the costs for purchasing energy.
  • Reduction of the heat pump's start-up cycles = increase in service life of the heat pump.
  • Thermal losses from the heat pump and the pipes.
If no temperature sensor is fitted, the heat pump must ensure the minimum temperature is met. As an alternative, the Ohmpilot can also ensure the minimum temperature by activating the heat pump. This may result in electricity being sourced from the grid. The maximum temperature must be set on the heating element thermostat and on the heat pump. If the heating element does not have a thermostat, the Ohmpilot can also carry out this task as an alternative (see "Optional settings" section Optional settings on page (→)).
This function can also be combined with a 3-phase heating element.
  2. 1-phase heating element up to 3 kW with heat pump control
(1)
(2)
Hot water boiler
(3)
(4)
(5)
(6)
(7)
NOTE!
(8)
CAUTION!
(9)
(10)
General settings, symbolic representation
1Open the Ohmpilot user interface (see section Establishing the data connection).
2Under HEATER 2, select "SG Ready heat pump" for Consumer.
3Select "Feed-in" under Starting threshold and enter the desired output in watts at which the heat pump is to be switched on.
4Under Switch-off threshold, select "Consume" or "Feed-in" and enter the desired output in watts at which the heat pump is to be switched off.
Example 1: If you have selected "Consume" under the switch-off threshold and a power of 500 W has been entered, the heat pump will be switched off as soon as the power being drawn from the grid exceeds 500 W.
Example 2: If you have selected "Feed-in" under the switch-off threshold and entered a power of 500 W, the heat pump will be switched off as soon as the power being fed in is less than 500 W.
NOTE!
The heat pump must be connected to the same utility meter.
Between the switch-on and switch-off thresholds, the self-consumption of the heat pump must also be taken into consideration. For example, if the heat pump consumes 3000 Watts of electricity and a hysteresis of 500 Watts must be taken into account, the switch-on threshold can be set to a feed-in of 3000 Watts and the switch-off threshold to a consumption of 500 Watts.
(1)
(2)
Hot water boiler
(3)
NOTE!
(4)
(5)
(6)
Output up to 3 kW variable, max. 13 A resistive load, spring-loaded terminal 1.5 - 2.5 mm2
(7)
(8)
Input - grid supply 1x 230V network, spring-loaded terminal 1.5 - 2.5 mm2
WARNING!
Short circuit
If live, stripped wires touch each other, a short circuit will occur.
(9)
(10)
The temperature is measured by the Ohmpilot. If the temperature falls below the minimum, then an external source (e.g. gas-fired heating) will be activated until the minimum temperature is reached again, so that the Ohmpilot only uses surplus energy and does not draw any energy from the grid.
The heating element is used for the Legionella prevention program.
  2. 1-phase heating element up to 3 kW and external source
(1)
(2)
Hot water boiler
(3)
NOTE!
(4)
(5)
(6)
(7)
(8)
WARNING!
Short circuit
(9)
(10)
2Enable the "Temperature sensor present" field
3Enable the "Adapt day curve" field
4Set the settings under "Time from", "Time to" and "Minimum temperature" as required
For more information, see section Adapting the day curve
5Under HEATER 2, select "Activate external source" for Consumer
(1)
(2)
(3)
Hot water boiler
(4)
(5)
Heating element 1 (max. 3 kW)
(6)
Buffer
(7)
Heating element 2 (max. 9 kW)
(8)
(9)
(10)
(11)
(12)
Input - grid supply 3x 230V network, spring-loaded terminal 1.5 - 2.5 mm2
(13)
(14)
Many heating systems consist of a boiler and a buffer, whereby the central heating supplies the buffer, and a control system feeds the hot water boiler via a pump. As with thermal photovoltaic systems, the Ohmpilot is also capable of heating the hot water boiler first and then the buffer, so that the maximum amount of photovoltaic surplus energy can be stored.
The Fronius Smart Meter records the current power at the feed-in point and transfers the data to the inverter. By controlling the Ohmpilot, the inverter adjusts any surplus energy that is available to zero. This takes place by continuously adjusting the heating element connected to the Ohmpilot.
For this application, two heating elements are installed, with preference being given to activation of the first heating element (5). Only once the maximum temperature in the boiler (3) has been reached is the second heating element activated in a continuously variable manner, so that the remaining energy can, for example, be stored in a buffer.
If no temperature sensor is connected to the Ohmpilot, after 30 minutes the Ohmpilot attempts to output energy via the first heating element once again. If a temperature sensor is present, the system switches back to the first heating element from a temperature difference of 8 °C (to the temperature measured before switching over).
This switching can also be used for layering in a boiler/buffer, so that the maximum temperature is reached in the top part of the boiler using minimal energy and the remaining energy is stored in the lower part of the boiler. By using layering in a storage tank, it is also possible to store significantly more energy, as a minimum temperature is normally maintained in the top part of the boiler. This means that the temperature difference and thus the amount of energy is rather small. In the lower part of the boiler, a high temperature difference of 50 °C, for example, can be used.
Both the first and the second heating element can be 1-phase or 3-phase. For two 3-phase heating elements, see Application example 6. If no temperature sensor is fitted, an external source (e.g. gas-fired heating) must be used to ensure the minimum temperature is met.
As an alternative, the Ohmpilot can also ensure the minimum temperature. This may result in electricity being sourced from the grid. The maximum temperature must be set on the heating element thermostat. If heating element 1 (5) does not have a thermostat, the Ohmpilot can also carry out this task as an alternative (see chapter Optional settings on page (→)). However, heating element 2 (7) must have a thermostat.
NOTE!
Both heating elements can never be heated at the same time!
  2. Two heating elements - 3-phase and 1-phase
(1)
(2)
(3)
Hot water boiler
(4)
(5)
(6)
Buffer
(7)
(8)
(9)
(10)
(11)
(12)
(13)
(14)
NOTE!
2Under HEATER 1, select "Manual" and "Single-phase or Three-phase".
3Under HEATER 2, select "Single-phase or Three-phase" and enter the output of the load.
(1)
(2)
(3)
Hot water boiler
(4)
(5)
Heating element 1 (max. 9 kW)
(6)
Buffer
(7)
(8)
Contactor switching
(9)
(10)
(11)
(12)
(13)
Input - grid supply 3x 230V network, spring-loaded terminal 1.5 - 2.5 mm2.
(14)
(15)
For this application, two heating elements are installed, with preference being given to activation of the first heating element (5). Only once the maximum temperature in the boiler (3) has been reached is the second heating element (7) activated in a continuously variable manner, so that the remaining energy can, for example, be stored in a buffer.
This switching can also be used for layering in a boiler/buffer, so that the maximum temperature is reached in the top part of the boiler using minimal energy and the remaining energy is stored in the lower part of the boiler. By using layering in a storage tank, it is also possible to store significantly more energy, as a minimum temperature is normally maintained in the top part of the boiler. This means that the temperature difference and therefore the amount of energy is rather small. In the lower part of the boiler, a high temperature difference of 50 °C, for example, can be used.
Switching must be realised by an external contactor. If no temperature sensor is fitted, an external source (e.g. gas-fired heating) must be used to ensure the minimum temperature is met.
NOTE!
  2. Two 3-phase heating elements up to 9 kW
(1)
(2)
(3)
Hot water boiler
(4)
(5)
(6)
Buffer
(7)
(8)
Contactor switching
(9)
(10)
(11)
(12)
(13)
(14)
(15)
NOTE!
2Under HEATER 2, select "Three-phase" and enter the output of the load.
(1)
(2)
(3)
Hot water boiler
(4)
Heating element
NOTE!
1-phase and 3-phase heating element
This function can be implemented with a 1-phase and 3-phase heating element.
(5)
Circulating pump auxiliary relay
NOTE!
Circulating pump run-on time
At the end of the heating operation, the circulating pump is active for 60 seconds.
(6)
(7)
NOTE!
(8)
CAUTION!
(9)
(10)
The Ohmpilot can also control a circulating pump in a heating system in parallel to a heating element via the floating contact of the device control. This is possible with all circulating pumps that have an auxiliary relay.
The designation of the floating contact on the Ohmpilot is NC W NO. When the contact is activated, the switching rocker (W) switches from the "normally open" (NO) position to "normally closed" (NC).
In heating mode, this contact is activated and the circulating pump runs as "HEATER 2" in parallel to the heating element, which is operated via the "HEATER 1" output.
To prevent the auxiliary relay of the circulating pump from switching on and off continuously in case of low or fluctuating PV power, the Ohmpilot is equipped with a delay. This has a positive effect on the wear and service life of the relay and the pump.
  2. 1-phase heating element up to 3 KW / 3-phase heating element and circulation pump
(1)
(2)
(3)
Hot water boiler
(4)
Heating element
NOTE!
(5)
NOTE!
(6)
(7)
NOTE!
(8)
CAUTION!
(9)
(10)
2Under HEATER 1, select "Automatic".
3Under HEATER 2, select "Circulating pump"
NOTE!
If the "Circulating pump" option is selected, no other heater can be controlled by the Ohmpilot. The HEATER 1 output controls the heating element which, in combination with the circulating pump, heats a hot water tank.
The data connection is required for communication between the inverter and the Ohmpilot. The inverter mainly sends default values to the Ohmpilot. For some applications, it is necessary to make settings via the Ohmpilot user interface.
There are 3 possible communication channels:
  • Modbus RTU (via RS 485)
  • LAN (Ethernet)
  • WLAN
NOTE!
In order to communicate with the Ohmpilot, software version 3.8.1-x onwards must be installed on the SnapINverter series inverter (Fronius Datamanager 2.0).
  2. Establishing the data connection
  • LAN (Ethernet)
  • WLAN
NOTE!
Each inverter with a Fronius Smart Meter automatically connects to the Ohmpilot. If there are several inverters with Fronius Smart Meter in the network, the Ohmpilot must be paired manually on the user interface of the inverter to be paired under "Device Configuration".
Information on how to access the user interface of the inverter can be found in the operating instructions for the respective device.
Ohmpilot connections
Fronius Smart Meter connections
Fronius SnapINverter / GEN24 connections
D+
Rx / M+
D+ / M1+
D-
Tx / M-
D- / M1-
GND
GND
WARNING!
Danger if cables are mixed up
If data cables and live mains cables are mixed up, this can result in personal injury and damage to property.
Use data cables that are clearly distinguishable from the mains cables.
Mark cables (e.g. by labelling)
NOTE!
Defective cabling is signalled by the red LED indicator flashing once.
1Connect the data communication cable in parallel to the Ohmpilot and system components.
2Activate the terminating resistor on the first and last device of the Modbus cable. Activate the resistor on the Ohmpilot with DIP switch number 5.
3Set the Modbus address using DIP switches 1-3.
Default address: 40 (for future applications, the Modbus address can be changed using the DIP switches on the Ohmpilot.)
DIP switch settings
Switch
Setting
DIP 1-3
Modbus address BCD
DIP 4
Reserve
DIP 5
Terminating resistor (120 Ohm)
Establish a WLAN connection to implement further settings:
1Press the button on the Ohmpilot 2x.
The blue LED flashes twice. The WLAN access point is activated for 30 minutes.
2Activate the "Ohmpilot" WLAN network on the mobile device or PC.
3In the browser, enter the address http://192.168.250.181 or http://ohmpilotW.local.
4Continue configuration on the user interface.
As standard, the Ohmpilot obtains its IP address automatically from the DHCP server, meaning that no settings are generally necessary.
The inverter automatically searches for the Ohmpilot, and the search process may take up to 5 minutes. If the red LED is not lit and the green LED is flashing, the Ohmpilot is working correctly.
A static IP address can be assigned to the Ohmpilot via the user interface.
Set Up Network, symbolic representation
1In the web browser, open the address http://ohmpilotL.local.Alternatively, the IP address assigned by the DHCP server can also be read out. Almost every router displays its connected devices (clients) on its user interface. Apps such as Fing can help you find the automatically assigned IP address. Alternatively, the Ohmpilot can also be searched on the network using the Fronius Solar.start App.
NOTE!
Accessing the Ohmpilot via the network.
In networks with a DNS suffix, the Ohmpilot can be accessed at http://ohmpilotL.<DNS-Suffix>, e.g. http://ohmpilotL.fronius.com
To set the IP address manually, the "Static" option must be selected. Then enter the desired IP address.
The Ohmpilot can then be reached at http://ohmpilotL.local or at the fixed IP address assigned.
There are two options for connecting the Ohmpilot to an existing WLAN network:
Connecting via WPS (WiFi Protected Setup)
1Press the button on the Ohmpilot 1x.
The blue LED flashes (once) as long as WPS is active.
2Press the WPS button on the router within 2 minutes.
If the blue LED on the Ohmpilot lights up permanently, the connection to the network was successful.
The inverter automatically searches for the Ohmpilot, and the search process can take up to 5 minutes. If the red LED is not lit and the green LED is flashing, the Ohmpilot is working correctly.
Set Up Navigation, symbolic representation
Connecting via access point and manual configuration of the WLAN settings
The blue LED flashes (twice) as long as the WLAN access point is active (30 minutes). Before the access point is opened, it searches for available WLAN networks.
2Activate the "Ohmpilot" WLAN network on your smart device or PC.
3In the browser, enter the address http://192.168.250.181 or http://ohmpilotW.local. Alternatively, the Ohmpilot can also be searched on the network using the Fronius Solar.start App.
4Select the desired network in the WLAN network tab.
NOTE!
Desired network not listed.
If the desired WLAN network is not listed, end access point mode by pressing the button again and repeat the process.
5Click on "Save & Connect", enter WLAN password.
NOTE!
WLAN network scan not possible.
When the access point is opened, it is not possible to scan the WLAN networks.
The Ohmpilot can then be reached at http://ohmpilotW.local or at the fixed IP address assigned. Alternatively, the Ohmpilot can also be searched on the network using the Fronius Solar.web App.
NOTE!
Device connections.
Only one device can connect to the Ohmpilot.
NOTE!
In networks with a DNS suffix, the Ohmpilot can be accessed at http:// ohmpilotW.<DNS-Suffix>, e.g. http://ohmpilotW.fronius.com
Boost Mode
Boost Mode
Boost Mode is used to supply the load at the "Heater 1" output with 100% of the available power for a short time. The dimming level is set to 100% over a maximum period of 4 hours; switching through phases L2 and L3 takes place. This may result in electricity being sourced from the grid.
Boost Mode can be activated and deactivated by pressing the function key on the Ohmpilot (see Indications/controls on the device ) or via the user interface.
  2. Boost Mode
Boost Mode
  2. Boost Mode
Boost Mode, symbolic representation
2Click on the Boost Mode button to activate the function.
3Click again to deactivate Boost Mode.
User interface
Status display
Status display, symbolic representation
Status
OK
Ohmpilot is operating in normal mode.
Minimum temperature
The minimum temperature has been undershot. Heater 1 heats up to 100%.
Legionella prevention program is active. Heater 1 heats up to 100%.
Boost
The Ohmpilot was manually set to Boost Mode. Heater 1 heats up to 100%.
Error
An error has been detected. Further information is displayed in Fronius Solar.web.
Temperature
Current measured temperature. A valid value is only displayed when a temperature sensor is connected.
Heat output
Current power being used by the Ohmpilot.
Heater 2
Heater 2 is active. Heater 2 may be a second heating element, a heat pump or an external source (e.g. gas-fired heating).
L2 heating element
Phase 2 of 3-phase heating element is active.
L3 heating element
Phase 3 of 3-phase heating element is active.
  2. User interface
Status display
Status
OK
Minimum temperature
Boost
Error
Temperature
Heat output
Heater 2
L2 heating element
L3 heating element
Optional settings
NOTE!
Application
The settings described here can be implemented for all the application examples shown above.
Setting the output of HEATER 1 manually:
1Under HEATER 1, select "Manual"
2Select "Single-phase" or "Three-phase" for Consumer
3Enter the output of the load
NOTE!
Automatic measurement of heating element 1
In the case of applications with a 1-phase and a 3-phase heating element, it is not possible for the Ohmpilot to measure heating element 1 automatically due to the cabling. In this case, the configuration must be carried out manually.
  2. Optional settings
NOTE!
Application
NOTE!
CAUTION!
Danger due to Legionella
Legionella bacteria can cause serious illnesses. Despite setting the "Legionella prevention" function, contamination of the water with Legionella bacteria cannot be fully ruled out.
Perform the Legionella prevention function regularly.
Ensure continuous circulation and extraction of hot water.
Check the hot water temperature regularly
NOTE!
If the boiler is operated at a temperature < 60 °C for a longer period of time and a hygienic storage tank is not used, measures must be taken to kill Legionella.
For private use, it is recommended to run the Legionella prevention function at least once a week (168 hours). The actual interval depends on the size of the storage tank and the set temperature.
A PT1000 temperature sensor is required for this function and can be sourced from Fronius under item number 43,0001,1188.
When the Legionella prevention system is activated, the hot water is heated to 60 °C at a set interval.
1Enable the "Temperature sensor present" field
2Enable the "Legionella prevention (h)" field
3Enter the desired Legionella prevention cycle
This function ensures that the user-specified temperature is not undershot. If there is insufficient surplus current, the external source (if activated) is controlled or power is drawn from the grid to ensure a minimum temperature.
Up to four time periods and minimum temperatures can be defined. For example, higher hot water temperatures are available in the evening. During the day, more potential for the surplus is then possible by selecting a lower minimum temperature.
Adapting the day curve:
2Enable the "Adapt day curve" field
3Under "Time from", enter the time from which the Ohmpilot should start to heat to the new minimum temperature.
4Under "Time to" enter the time until which the Ohmpilot should heat to the minimum temperature.
5Under "Minimum temperature", select the desired end temperature.
NOTE!
Undefined time ranges.
If no time ranges are defined, heating is not provided via the grid or external source during this time. Only surplus PV energy is used.
NOTE!
If time ranges overlap, the higher temperature is used, so that, for example, a basic temperature of 40 °C can be set for the whole day and is increased to 50 °C at certain times.
NOTE!
Primary heat source.
If heater 1 is the primary heat source, the day curve must be adapted to guarantee the desired minimum temperature. A PT1000 temperature sensor is required for this function and can be sourced from Fronius under item number 43,0001,1188. The temperature sensor must be installed above the heating element / external source to ensure a continuous supply of hot water.
Example
Time / desired temperature
Application case
3.00 - 5.00 am / 45 °C
So that hot water is available for showering at 6.00 am. After showering, the hot water is only heated with surplus energy.
4.00 - 6.00 pm / 45 °C
If there is not enough surplus energy, the hot water is reheated for showering. After showering, the heater is no longer reheated to minimise heat loss.
If heater 1 does not have a configurable thermostat, this function can be used to limit the temperature.
2Enable the "Temperature limitation" field
3Enter the maximum temperature (e.g.: 60 °C)
NOTE!
This function is only possible for heater 1.
If a second heating element is being used as heater 2, it must be equipped with a thermostat. A PT1000 temperature sensor is required for this function and can be sourced from Fronius under item number 43,0001,1188. The position of the temperature sensor should be just above the heating element, so that the incoming cold water is immediately heated again and thus the maximum amount of storage is used.
Appendix
Status Codes
Status codes
Sending errors
  • Errors are saved in Fronius Datamanager 2.0 and can be sent via Fronius Solar.web.
  • Possible error outputs:
Status codes
HE = Heating element TS = Temperature sensor I = Inverter ES = External source (e.g. gas-fired heating)
Code
Description
Cause
Remedy
906
Heating element 1 faulty - short circuit L1
The load on L1 is higher than 3 kW. Short circuit on L1.
Check heating element 1. Check wiring.
907
908
HE 1 - Overload on L2
HE 1 - Overload on L3
Current on L2 greater than 16 A
Current on L3 greater than 16 A
Check HE 1 and replace if necessary.
909
910
911
HE 1 faulty - L1 highly resistive
HE 1 faulty - L2 highly resistive
HE 1 faulty - L3 highly resistive
No current is flowing through L1/L2/L3. L1/L2/L3 of HE 1 faulty. Phase L1/L2/L3 interrupted.
Check L1/L2/L3. Check L1/L2/L3 connections.
912
HE 2 faulty - short circuit L1
Check HE 2. Check wiring.
913
914
HE 2 - Overload on L2
HE 2 - Overload on L3
Check HE2 and replace if necessary.
915
916
917
HE 2 faulty - L1 highly resistive
HE 2 faulty - L2 highly resistive
HE 2 faulty - L3 highly resistive
No current is flowing through L1/L2/L3. L1/L2/L3 of HE 2 faulty. Phase L1/L2/L3 interrupted.
918
919
Relay 2 (phase L2) defective
Relay 3 (phase L3) defective
Relay R2/R3 does not switch.
Replace Ohmpilot.
920
TS short circuit
TS input resistance less than 200 Ohm. No PT1000 TS connected. TS defective.
Check cable and connections on TS cable. Replace TS.
921
TS not connected or faulty
No TS connected (input resistance greater than 2000 Ohm). TS is activated (should be deactivated). TS cable defective. TS defective. No PT1000 TS connected.
Connect TS to device. Deactivate TS via the user interface (if sensor not needed). Check TS cable. Replace TS.
922
923
60 °C for Legionella prevention could not be achieved within 24 hours.
Minimum temperature could not be achieved within 5 hours
ES is switched off/faulty. (922 only). TS has not been fitted correctly. Heating system has not been dimensioned properly (hot water consumption too high, etc.) HE/TS defective.
Switch on ES (922 only). Fit TS above the HE (in the protective tube). Legionella prevention via the user interface. Replace HE/TS.
924
ES could not achieve minimum temperature within 5 hours.
ES switched off/faulty. ES not connected to Ohmpilot. TS incorrectly mounted. Heating system not dimensioned properly (hot water consumption too high, etc.). TS faulty.
Switch on ES. Connect ES to relay 1. Fit TS above the heater battery of the ES. Check minimum temperature setting. Replace TS.
925
Time not synchronised
Time not synchronised in the last 24 hours. Router has been switched off/reconfigured.
Check connection between Ohmpilot and inverter. Switch on router. Check network settings.
926
No connection to inverter
No connection between inverter and Ohmpilot. Inverter switched off. The Ohmpilot also needs a connection to the inverter at night. Router switched off/faulty/reconfigured. Night switch-off function enabled on the inverter. Poor WLAN connection between inverter or Ohmpilot and router.
Check connection. Switch on the inverter. Update the software. Switch the Ohmpilot and inverter off and on again. Deactivate the night switch-off function of the inverter. On the inverter display, set night mode to ON under "SETUP/Display Setting/Night Mode" menu. Switch on router. Reposition the WLAN antenna to a better location. Check network settings.
927
Ohmpilot overtemperature
Ambient temperature too high (> 40 °C). The output of the heating element is too high. Ventilation slots are covered.
Install Ohmpilot in a cooler location. Use a heating element with a permissible output. Uncover the ventilation slots.
928
Ohmpilot undertemperature
Ambient temperature too low (<0 °C).
Install Ohmpilot in a warmer location. Installation outdoors is not permitted.
Residual current circuit breaker triggered
Neutral conductor (N) and phase (L) reversed.
Connect N and L correctly.
Ohmpilot is not using any surplus
Thermostat on heating element has switched off. Safety thermostat (STC) on the heating element has triggered.
Wait until thermostat switches on again. Reset safety thermostat.
Ohmpilot is using only part of the surplus power
Heating element power is lower than surplus power.
Select a larger heating element where necessary
Power at the feed-in point is not always adjusted to 0
Load and generation fluctuations require a few seconds to settle down.
After switch-on, the green LED makes 2 long flashes
Thermostat on heating element has switched off. Heating element is not connected.
Briefly turn up the thermostat for the power measurement. Connect the heating element.
After a power failure, the Ohmpilot will no longer work
After a power failure, the Ohmpilot automatically assigns itself the following fixed IP address if it does not receive an IP address after 40 seconds: 169.254.0.180 (only valid if the Ohmpilot is connected to the router via WLAN).
Restart Ohmpilot so that the WLAN connection is re-established.
  1. Appendix
Status Codes
Status codes
Sending errors
Status codes
Code
Description
Cause
Remedy
906
907
908
909
910
911
912
913
914
915
916
917
918
919
Replace Ohmpilot.
920
TS short circuit
921
922
923
924
925
926
927
928
  1. Appendix
  2. Status Codes
Status codes
Sending errors
Status codes
Code
Description
Cause
Remedy
906
907
908
909
910
911
912
913
914
915
916
917
918
919
Replace Ohmpilot.
920
TS short circuit
921
922
923
924
925
926
927
928
  1. Appendix
Technical data
General data
Dimensions (height x width x depth)
350 mm x 280 mm x 110 mm
Weight
3.9 kg
Protection class
IP 54
Installation
Wall
Ambient temperature range
0 to 40 °C
Permissible humidity
0%-99% (non-condensing)
Cooling
Convection
Storage temperature
-40 to 70 °C
EMC emission class
B
Overvoltage category
Pollution degree
Input data
Frequency
50 Hz
Nominal voltage
230 V / 400 V
Max. input current
1 X 16 A / 3 x 16 A
Interfaces
Modbus RTU
RS 485, max. 1000 m, shielded and twisted
LAN
Ethernet at least CAT5, shielded
WLAN
Standard IEEE 802.11 b/g/n
Temperature sensor
PT1000 (max. 30 m)
Output data
Analogue output 1-phase/3-phase
Continuously variable 0 - 3 / 0 - 9 kW
Analogue nominal current per phase
13 A
Analogue output short-circuit current
16 A (max. 5 seconds)
Relay output max. current
L2 / L3 16 A (max. 5 seconds)
min. 15 V / 2 mA; max. 16 A (max. 5 seconds)
Efficiency during rated operation
at least 98%
Consumption during standby
typically 1.8 W
  1. Appendix
  2. Technical data
General data
Weight
3.9 kg
Protection class
IP 54
Installation
Wall
0 to 40 °C
Cooling
Convection
Storage temperature
-40 to 70 °C
EMC emission class
B
Pollution degree
Input data
Frequency
50 Hz
Nominal voltage
230 V / 400 V
Max. input current
1 X 16 A / 3 x 16 A
Interfaces
Modbus RTU
LAN
WLAN
Temperature sensor
PT1000 (max. 30 m)
Output data
13 A
at least 98%
typically 1.8 W
  1. Appendix
Tests/specifications per EN60730 Section 1 Table 7.2
6a
Construction
Electronic RS 2.5.5, independently mounted RS
19
Screwless terminals
2.10.6.1 type X mounting
24
Classification of the RS according to protection against electric shock, Section 6.8
Safety class I 6.8.3
29
Type of shutdown or open circuit for each circuit
Micro-interruption per 2.4.4.
30
PTI value of the insulation materials used for insulation
PTI 175 in accordance with 6.13.2
31a
Type of ground conductor connection
N in accordance with 7.4.3, grounding terminal in accordance with 9.1.1
39
Operating principle
Operating principle TYPE 1 in accordance with 2.6.1
40
Additional properties for operating principle
C in accordance with 6.4.3.3
51
Glow wire test temperatures (Sections 21.2.1, 21.2.2, 21.2.3 and 21.2.4)
Housing 550 °C, cable gland/strain-relief device 650 °C; category B in accordance with EN 60730-1:2000/A1:2004;
75
Rated surge voltage (Sections 2.1.12, 20.1)
In accordance with EN 61000-6-2:2005, EN 60730-1:2011, EN 301 489-1 (V1.9.2)
Wire to wire | Wire(s) to ground, signal and control lines: --- ± | 1 kV
DC mains inputs: ± 0.5 kV | ± 0.5 kV
AC mains inputs: ± 1 kV |± 2 kV
77
Temperature of the ball pressure test
In accordance with 21.2.1, 21.2.2, 21.2.3 and 21.2.4, case (housing):
Ball pressure test 1: 102°C
Cable bushing (cable gland):
Ball pressure test 2: 125 °C
80
Rated surge voltage for creepage distance or contact-gap
Signal and control lines: --- ± | 1 kV
  1. Appendix
  2. Tests/specifications
6a
Construction
19
Screwless terminals
24
29
30
31a
39
Operating principle
40
51
75
77
80
  1. Appendix
Detailed, country-specific warranty conditions are available on the internet
www.fronius.com/solar/garantie
  1. Appendix
  2. Warranty terms and conditions, and disposal
  1. Appendix
Disposal
Packaging materials
  • Collect separately
  • Observe locally valid regulations
  • Compress the cardboard box to reduce volume
  1. Appendix
CE mark
The devices conform to all the requisite and relevant standards and guidelines that form part of the relevant EU directive, and are therefore permitted to display the CE mark.