Fronius LogoFronius Mobile Logo
en
      Operating instructionsFronius Reserva 6.3 - 15.8 kWh
    • General information
      • Safety information
        • Explanation of warnings and safety instructions
        • Safety instructions and important information
        • Battery hazard
        • Recommended measures in case of emergencies and hazards
        • EMC measures
        • Electromagnetic fields
        • Protective earthing (PE), functional grounding
      • General
        • Information on the device
        • How information is presented in the document
        • Target group
        • Data security
        • Privacy policy
        • Copyright
      • Fronius Reserva
        • Device concept
        • Function overview
        • Scope of supply
        • Storage
        • Intended use
        • Foreseeable misuse
        • Fronius Solar.web
      • Different operating modes
        • Operating modes – Explanation of symbols
        • Operating mode – Solar energy
        • Operating mode – Self-consumption optimization
        • Operating mode – Backup power
        • Operating mode – Cost-optimized battery charging from the public grid
        • Energy flow direction of the inverter
        • Operating states (only for battery systems)
      • Operating controls and connections
        • Connection area
        • LED status indicators
    • Installation
      • General
        • System component compatibility
      • Choosing the Location
        • Selecting the battery location
      • Installation
        • Selecting the mounting material
        • Wall installation
        • Structure of the battery
      • Prerequisites for connecting
        • Various cable types
        • Permitted cables for the electrical connection
        • Maximum DC cable lengths
        • Permitted cables for the data communication connection
      • Electrical connection
        • Safety
        • Switching off the power to the photovoltaic system
        • Connecting the ground conductor (PE)
        • Connecting the DC cables
        • Connecting the DC cables for battery parallel operation
      • Connecting the data communication cables
        • PIN assignment
        • Connecting the data communication cable to the inverter
        • Connecting the data communication cables for battery parallel operation
        • Terminating resistors
      • Final tasks
        • Mounting covers on the battery
      • Adding/replacing the Reserva module of the battery system
        • Safety
        • Requirements for expanding the battery system
        • Setting the State of Charge (SoC) with Service Mode
        • Switching off the power to the photovoltaic system and battery
        • Removing the covers on the battery
        • Disconnecting and dismantling the Reserva BMS
        • Installing new Reserva module
        • Installing the Reserva BMS
        • Connecting the Reserva BMS
    • Commissioning
      • Switching on the photovoltaic system
      • Manual system start
        • Requirements
        • Notification of system shutdown
        • Manual battery start (dark start) after a system shutdown
        • Starting backup power mode after a system shutdown
      • Settings – User interface of the inverter
        • General
        • Commissioning with the app
        • Commissioning with the browser
        • Adding a battery in the user interface of the inverter
        • Firmware update
      • Switching the battery off and on
        • Switching off the battery
        • Switching on the battery
    • Appendix
      • Service, maintenance and disposal
        • Cleaning
        • Maintenance
        • Forced re-charging
        • Disposal
      • Warranty provisions
        • Warranty
      • Technical data
        • Fronius Reserva 6.3
        • Fronius Reserva 9.5
        • Fronius Reserva 12.6
        • Fronius Reserva 15.8
        • Explanation of footnotes
    • Dimensions
      • Fronius Reserva
    • 013-17072026
    download
    Installation
    Commissioning
    Technical data
    ContactImprintTerms of usePrivacy statementCookie policy
    © 2026 Fronius International GmbH
    General information
    link_horizontalLink copied
    Safety information
    Warnings are intended to warn people of possible injuries and to avoid personal injury and damage to the product. They relate to individual actions with and on the product.
    DANGER!
    Indicates an immediately dangerous situation.
    Serious injury or death will result if the danger is not avoided.
    Action step to escape the situation.
    WARNING!
    Indicates a potentially dangerous situation.
    Serious injury or death may result if the danger is not avoided.
    CAUTION!
    Minor or moderate injury may result if the danger is not avoided.
    NOTE!
    Indicates a situation that may result in property damage.
    If the situation is not avoided, impaired work results, material damage to the product or other property are the possible consequences.
    Action step to avoid the situation.
    Safety instructions are designed to ensure safe product use. They are preventive and help to inform users about the fundamental risks involved when dealing with the product. They do not refer specifically to individual actions with and on the product.
    1. General information
    Safety information
    DANGER!
    WARNING!
    CAUTION!
    NOTE!
    2. Safety information
    DANGER!
    WARNING!
    CAUTION!
    NOTE!
    The device has been manufactured in line with the state of the art and according to recognized safety standards.
    WARNING!
    Incorrect operation or misuse
    Serious to fatal injuries to the operator or third parties as well as damage to the device and other property of the operator may result.
    All persons involved in the commissioning, maintenance, and servicing of the device must be appropriately qualified and have knowledge of working with electrical installations.
    Read these operating instructions in full and follow them carefully and precisely.
    The operating instructions must always be kept to hand wherever the device is being used.
    IMPORTANT!
    In addition to the operating instructions, observe the following general and local rules:
    • Accident prevention
    • Fire protection
    • Environmental protection
    IMPORTANT!
    Labels, warning notices, and safety symbols are located on the device. A description can be found in these operating instructions.
    IMPORTANT!
    All safety and danger notices on the device:
    • Must be kept in a legible state
    • Must not be damaged/marked
    • Must not be removed
    • Must not be covered, have anything stuck on them, or painted over
    WARNING!
    Tampered-with and non-functioning protection devices
    Serious to fatal injuries as well as damage to the device and other property of the operator may result.
    Never bypass or disable protection devices.
    Any protection devices that are not fully functional must be repaired by an authorized specialist before the device is switched on.
    WARNING!
    Loose, damaged, or under-dimensioned cables
    An electric shock can be fatal.
    Use undamaged, insulated, and adequately dimensioned cables.
    Fasten the cables according to the specifications in the operating instructions.
    Loose, damaged, or under-dimensioned cables must be repaired or replaced immediately by an authorized specialist.
    NOTE!
    Installations or modifications to the device
    The device may be damaged
    Do not carry out any alterations, installations, or modifications to the device without first obtaining the manufacturer's permission.
    Damaged components must be replaced.
    Only use original spare parts.
    Battery hazard
    Electrolyte leakage
    • Do not expose the battery to strong shocks/vibrations.
    • Do not deform or pierce the battery.
    • Do not open or damage the battery.
    • Creation of an explosive atmosphere.
    Fire
    • Short circuits at voltage-carrying parts of the battery, e.g., connection terminals.
    • Do not expose the battery to direct sunlight.
    • Keep the battery away from fire sources as well as flammable, explosive, and chemical materials.
    • Do not place the battery into a fire.
    Electric shock
    • Contact with live parts such as connection terminals.
    • Do not touch the battery with wet hands.
    • Keep the battery out of reach of children and animals.
    • A battery may pose a risk of electric shock and burns due to a high short circuit current.
    • Risk of electric shock from batteries that are submerged in water.
    Damage
    • Do not immerse the battery in water.
    • Risk of mechanical deformation due to load from foreign bodies.
    • Do not step on or apply a load to the battery.
    Electrolyte leakage
    • Initiate rescue measures, alert and instruct emergency services.
    • Contact with skin: Wash thoroughly with soap and water.
    • Contact with eyes: Rinse eyes under clear running water for 15 minutes.
    • Contact with respiratory tract: Leave the contaminated area immediately and ensure a supply of fresh air.
    • If swallowed, do not induce vomiting. Vomiting can cause severe burns in the mouth, esophagus, and gastrointestinal tract.
    • Immediately seek medical assistance after first aid measures have been taken.
    • Only remove/dispose of leaked electrolyte with suitable protective equipment in accordance with the applicable specifications and guidelines.
    • Supply the danger area with sufficient fresh air.
    Fire
    Battery can ignite if heated above 150 °C. The following measures must be taken if this occurs:
    • If the battery catches fire during operation, switch off the DC disconnector of the battery, unless there is a direct danger.
    • Use a fire extinguisher in accordance with the applicable national regulations.
    Extreme natural events
    In the event of extreme natural events (e.g.,
    flooding, hurricane, forest fire, etc.), take the following measures:
    • Switch off the battery's DC disconnector if this does not pose a danger to life or limb.
    Electric shock
    • Disconnect the PV system and battery from the power supply, provided there is no immediate danger.
    • Do not touch the battery if it is wet or submerged in water. Leave the danger zone immediately, alert the emergency services if there is water damage to the battery and contact customer service or the distributor for technical assistance.
    • Installing the battery and establishing the cable connections must be carried out by qualified specialists.
    Damage
    • Damaged batteries are dangerous and must be handled with extreme caution. They must not be used and may pose a danger to people and/or property. If the battery is damaged, immediately switch off the battery's DC disconnector, contact the distributor to arrange repair or return.
    EMC measures
    In certain cases, even though a device complies with the standard limit values for emissions, it may affect the application area for which it was designed (e.g., when there is equipment that is susceptible to interference at the same location or if the site where the device is installed is close to either radio or television receivers). If this is the case, the operator is obliged to take action to rectify the situation.
    During operation, due to the high electrical voltages and currents, local electromagnetic fields (EMF) are generated. These occur in the immediate vicinity of the inverter and the Fronius system components. Electromagnetic fields are also present in the area of the PV modules and their supply lines.
    As long as the intended use and a minimum distance of 20 cm are observed, all limit values for human exposure are observed.
    If the limit values are complied with, according to current scientific knowledge, no negative health effects from EMF exposure are to be expected. For persons with prostheses1) or active physical aids2), there is a possible health risk in the vicinity of photovoltaic system components. To avoid possible health risks, consult with the responsible doctor.
    1) e.g., implants or metal parts
    2) e.g., pacemaker, insulin pump, hearing aid, etc.
    The connection of a defined point in the device, system, or installation to earth serves either to protect against electric shock in the event of a fault (protective earthing) or to ensure a defined electrical potential for operation (functional grounding).
    When installing a battery system, a ground conductor connection is required depending on the safety class (see Technical data).
    When connecting the ground conductor, ensure that it is secured against unintentional disconnection. All of the points listed in the chapter headed Connecting the ground conductor (PE) on page (→) must be observed. When using cable glands, make sure the ground conductor will be the last conductor subjected to mechanical stress in the event of a cable gland failure. The respective national standards and regulations and requirements for minimum cross-section must be observed when connecting the ground conductor.
    General
     Technical data, markings, warnings, and safety symbols are applied to the battery. This information must be kept in a legible condition and must not be removed, covered, painted over, or concealed by stickers or labels. The information and symbols warn against incorrect operation, which may result in serious injury and property damage.
    Rating plate
    Explanation of symbols – Rating plate
    RCM marking – tested according to the requirements of Australia and New Zealand.
    Warning: Electric voltage
    CE label – confirms compliance with applicable EU directives and regulations.
    Recyclable – the product is recyclable or made from recycled materials.
    WEEE marking – waste electrical and electronic equipment must be collected separately and recycled in an environmentally sound manner in accordance with the European Directive and national law.
    Separate collection – Battery Regulation 2023/1542/EU – batteries must be collected separately in accordance with the EU regulation and handed over to waste management for environmentally sound disposal or recycling.
    Battery code
    Description
    IFpP
    Type of battery (e.g., lithium iron phosphate)
    14/140/180
    Battery dimensions [mm]
    (32S)nS
    Number of cells in series (32 cells in series)
    Warning notice
    Explanation of symbols – Warning notice
    General Warning Sign
    Warning: Heavy load
    Do not reverse polarities
    Warning: Hazards due to the charging of batteries
    No open flame; fire, open source of ignition, and smoking prohibited
    Warning: Explosive substances
    Keep out of reach of children and animals
    Follow the operating instructions
    2. General
    Rating plate
    Battery code
    Description
    IFpP
    14/140/180
    (32S)nS
    Warning notice
    Warning: Heavy load
    2. General
    The conventions regarding how information is presented in the document, which are set out below, have been defined in order to increase the readability and comprehensibility of the document.
    Application notes
    IMPORTANT! Indicates application notes and other useful information. It does not indicate a harmful or dangerous situation.
    Software
    Software functions and elements of a graphical user interface (e.g., buttons, menu items) are highlighted in the text with this mark up.
    Example: Click Save.
    Instructions for action
    1Action steps are displayed with consecutive numbering.
    ✓This symbol indicates the result of the action step or the entire instruction.
    2. General
    Target group
    This document provides detailed information and instructions to ensure that people can use the machine safely and efficiently.
    The information is intended for the following groups of people:
    • Technical specialists: People with appropriate qualifications and fundamental knowledge of electronics and mechanics. The activities of a technical specialist include installation, operation, maintenance, and service work.
    • User: People that use the machine in daily operation and want to understand its basic functions.
    Regardless of any qualifications, only perform the activities listed in this document.
    The definition of professional qualifications and their applicability are subject to national law.
    2. General
    Data security
    With regard to data security, the user is responsible for:
    • Backing up any changes made to the factory settings
    • Saving and storing personal settings
    NOTE!
    Data security for network and Internet connection
    Unsecured networks and a lack of safeguards can result in data loss and unauthorized access. Observe the following points for safe operation:
    Operate inverters and system components on a private, secure network. A WiFi network is considered secure if security standard WPA 2 is satisfied as a minimum.
    Keep the network devices (e.g., WiFi routers) up to date with the latest technology.
    Keep the software and/or firmware updated.
    Use a wired network to ensure a stable data connection.
    For security reasons, do not make inverters and system components accessible from the Internet via port forwarding or Port Address Translation (PAT).
    Use the solutions provided by Fronius for monitoring and remote configuration.
    The optional communication protocol Modbus TCP/IP1) is an unsecured interface. Only use Modbus TCP/IP if no other secured data communication protocol (MQTT2)) is possible (e.g., compatibility with older Smart Meters).
    1) TCP/IP - Transmission Control Protocol/Internet Protocol
    2) MQTT - Message Queuing Telemetry Protocol
    2. General
    Privacy policy
    When you connect your device (and any associated devices) to the internet, the following device and operating data (device ID/identifier, device IP address, device time, configuration settings, hardware and software information, device status log files, serial number) is sent automatically to
    Fronius International GmbH, Froniusstraße 1, 4643 Pettenbach, Austria, telephone +43(0) 7242241-0, email: contact@fronius.com (controller)
    and stored.
    The processing of this device and operating data is carried out for the purpose of ensuring the operational safety of the device (time synchronization, provision of updates). This processing is therefore necessary for the functionality of the device and thus for the fulfillment of the contract (Art. 6 (1) (b) GDPR).
    If you do not wish to have such data processed, you must manually disable the device's internet connection.
    In addition, the device and operating data is also processed for the purpose of providing services as part of a supplementary digital service for your device (such as solar.web or similar) as soon as you have registered your device with such a digital service (identification). This data is processed to provide the requested digital services and is therefore necessary for the fulfillment of the contract (Art. 6 (1) (b) GDPR).
    Furthermore, this data processing is also carried out for maintenance and support purposes and for handling customer concerns as well as in warranty and guarantee cases (only in individual cases and given connection between device and internet). In this context, the device and operating data may also be passed on to our cooperation partners (third-party providers and suppliers). The processing of this data is necessary for maintenance and support purposes or for processing warranty and guarantee cases and thus for the fulfillment of the contract (Art. 6 (1) (b) GDPR).
    Device and operating data are also processed for analysis and diagnostic purposes in order to gain insights into the functionality of the devices and improve them accordingly. This data processing is based on our legitimate interest (Art. 6 (1) (f) GDPR).
    We store this data for as long as it is necessary to fulfill the existing contract with you. Any storage beyond this is carried out for legal reasons or if we have a legitimate interest in doing so. For more information on data processing for the solar.web-digital service, as well as our general privacy policy and your rights as a data subject, please visit https://www.fronius.com.
    2. General
    Copyright
    Fronius International GmbH retains the copyrights of these operating instructions.
    Text, illustrations, and other media correspond to the technical state of the art at the time of publication. Fronius reserves the right to make changes. If you have any suggestions for improvement or have found a mistake in this document, we would be most grateful for your comments.
    Fronius Reserva
    Device concept
    (1)
    Battery management system (BMS)
    (2)
    Battery module
    (3)
    Cover
    (4)
    Base plate
    The Fronius Reserva battery is a stackable battery system. Up to a maximum of 4 battery systems can be operated in parallel operation. Lithium iron phosphate (LFP) batteries are known for their high thermal and chemical stability. The multi-level safety design and intelligent safety monitoring systems ensure safe operation throughout the total life cycle of the batteries.
    The Fronius Reserva can be used as a backup power supply when used in combination with a Fronius inverter with backup power capability and backup power changeover with the appropriate configuration.
    2. Fronius Reserva
    Device concept
    (1)
    (2)
    Battery module
    (3)
    Cover
    (4)
    Base plate
    2. Fronius Reserva
    Function overview
    Function
    Description
    SoC calculation
    The current state of charge (SoC) is calculated and displayed on the LED status indicator. To ensure that the SoC calculation for the battery system is accurate, an SoC calibration is carried out every 2 months or 50 charging cycles.
    Safety
    The battery monitors and protects itself against defective operating behavior:
    • Overvoltage and undervoltage
    • Overcurrent
    • Excessively high or low temperatures
    • Cell and hardware errors
    Dark start
    The battery supplies energy for the manual system start (dark start) and the inverter automatically starts backup power mode.
    Update
    The battery firmware is updated via the user interface of the inverter.
    Capacity
    2 ‑ 5 Reserva modules per battery system and max. 4 battery systems with the same capacity in parallel operation.
    Monitoring
    Operating data and status indicators are transmitted to the inverter for monitoring via the RS485 interface.
    2. Fronius Reserva
    Scope of supply
    Reserva module
    No.
    Designation
    Quantity
    (1)
    Battery module
    1
    (2)
    Cover
    2
    (3)
    L-shaped mounting bracket
    2
    (4)
    M6x12 TX 30 screw
    4
    (5)
    M6 washer
    2
    (6)
    Quick Start Guide
    1
    Reserva BMS
    No.
    Designation
    Quantity
    (1)
    Cover (top)
    1
    (2)
    1
    (3)
    Cover (left)
    1
    (4)
    Cover (right)
    1
    (5)
    Quick Start Guide
    1
    (6)
    Drilling template
    1
    (7)
    RJ45 plug
    2
    (8)
    RJ45 screw connection (battery parallel operation)
    2
    (9)
    LP-16-C/RJ45 plug (battery to inverter)
    1
    (10)
    Stäubli MC4-Evo stor 6 mm2 (+/-)
    2
    (11)*
    Stäubli MC4-Evo stor 10 mm2 (+/-)
    2
    (12)
    M6x12 TX 30 screw
    3
    (13)
    Covers for the base plate
    2
    (14)
    Base plate
    1
    Only included in the scope of supply for Australia and New Zealand.
    2. Fronius Reserva
    Storage
    Max. storage period
    Temperature range
    Relative humidity
    SoC*
    7 days
    -30 to -20 °C
    45 to 60 °C
    5% ‑ 95%
    30%
    12 months
    -20 to 45 °C
    5% ‑ 95%
    30%
    * SoC at the time of storage.
    The following storage conditions must be observed for batteries that are not used for more than 7 days:
    • Store according to the instructions on the packaging and do not turn upside down.
    • Store in a place that is protected from direct sunlight and rain.
    • Keep at least 2 meters away from heat sources (e.g., radiators).
    • Avoid contact with corrosive and organic substances (including gas).
    • Defective batteries must be stored separately from intact batteries (e.g., through physical separation or different fire protection zones).
    • The storage area should be dry, clean, and well ventilated.
    For batteries that are not used for more than 12 months, the following measure is necessary:
    • Batteries must be recharged by the manufacturer. For this purpose, the batteries must be sent to the manufacturer.
    2. Fronius Reserva
    Intended use
    The Fronius Reserva battery is intended for storing electrical energy from photovoltaic systems. It is used to store surplus energy and release it again if necessary in order to optimize the energy supply and maximize the self-consumption of solar energy. The battery is designed for use in private households and for small to medium-sized commercial applications.
    The Fronius Reserva can be used for backup power supply in combination with an backup power-capable Fronius inverter and backup power switching devices.
    2. Fronius Reserva
    Foreseeable misuse
    The following circumstances are considered to be reasonably foreseeable misuse:
    • Any use that is not the intended use or goes beyond the intended use.
    • The use of incompatible chargers.
    • Improper handling, such as dropping or exposing to strong vibrations.
    • Backup power mode without suitable changeover devices.
    • Modification or manipulation of the battery system that is not expressly recommended by Fronius.
    • The supply of loads that require an uninterruptible power supply (e.g., IT networks, life-sustaining medical devices).
    • Parallel operation with battery systems of different capacities.
    2. Fronius Reserva
    Fronius Solar.web
    System owners and installers can easily monitor and analyze the PV system using Fronius Solar.web or Fronius Solar.web Premium. With the appropriate configuration, the inverter transmits system component data such as power, yield, load, and energy balance to Fronius Solar.web. More detailed information can be found at Solar.web - Monitoring & analysis.
    PV module
    generates direct current
    Fronius hybrid inverter
    converts direct current into alternating current and charges the battery (battery charging requires battery support).
    Battery
    is coupled to the inverter on the direct current side and stores electrical energy.
    Primary meter
    records the load curve of the system and makes the measured data available for energy profiling in Fronius Solar.web. The primary meter also controls the dynamic power of feeding in.
    Loads in the system
    are the loads connected in the system.
    Grid
    supplies the loads in the system if insufficient power is being generated by the PV modules or supplied by the battery.
    2. Different operating modes
    PV module
    Battery
    Primary meter
    Loads in the system
    Grid
    (1)
    The solar energy generated supplies the loads in the house, the battery is charged with solar energy and the surplus energy production is fed into the public grid.
    (1)
    There is no solar energy available from the PV modules.
    (2)
    The loads in the house are supplied with energy from the battery.
    (3)
    The loads in the house are supplied with energy from the public grid if the energy from the battery is insufficient.
    IMPORTANT!
    Appropriate installation and configuration is a prerequisite for the backup power operating mode.
    (1)
    The loads in the house are supplied with solar energy from the PV modules.
    (2)
    The loads in the house are supplied with energy from the battery if the solar energy from the PV modules is insufficient.
    (3)
    There is no energy available from the public grid.
    Requirements
    • Flexible electricity tariff
    • The “Energy Cost Assistant” function in Fronius Solar.web must be activated.
    • The restrictions of the grid operator must be taken into account.
    (1)
    (2)
    The battery is charged using energy from the public grid at a low electricity price.
    (3)
    (1)
    PV module – inverter – load/grid/battery
    (2)
    Battery – inverter – load/grid*
    (3)
    Grid – inverter – load/battery*
    * Charging the battery from the public grid depends on the settings and local standards and regulations.
    Battery systems distinguish between different operating states. In each case, the relevant current operating state is displayed on the user interface of the inverter or in Fronius Solar.web.
    Operating state
    Description
    Normal operation
    The energy is stored or drawn, as required.
    Min. state of charge (SoC) reached
    The battery has reached the minimum SoC specified by the manufacturer or the set minimum SoC. The battery cannot be discharged further.
    Energy saving mode (standby)
    The system has been put into energy-saving mode. Energy saving mode is automatically ended as soon as sufficient surplus power is available again.
    Start
    The battery system starts from energy-saving mode (standby).
    Forced re-charging
    The inverter recharges the battery, in order to maintain the SoC specified by the manufacturer or the set minimum SoC (protection against deep discharge).
    Calibration charging
    The battery system is charged to the SoC of 100% and then discharged to the SoC of 0%. After 1 hour of waiting time at SoC 0%, the calibration charge is stopped and the battery switches to normal operation.
    Service mode
    The battery system is charged or discharged to the SoC of 30% and the SoC of 30% is maintained until the end of the service mode.
    Deactivated
    The battery is not active. It has either been deactivated, switched off, or the communication between the battery and the inverter has been interrupted.
    Connection area
    No.
    Name
    Description
    (1)
    HVB connector
    High-voltage battery (HVB) and data communication connector
    (2)
    SERVICE
    12 V external activation signal connection
    (3)
    DC1-
    Negative pole for DC connection to inverter or battery in parallel operation
    (4)
    DC2-
    (5)
    DC1+
    Positive pole for DC connection to inverter or battery in parallel operation
    (6)
    DC2+
    (7)
    PE ground conductor connection
    (8)
    INVERTER
    Data communication connection to the inverter
    (9)
    OUT
    Data communication output between batteries in parallel operation
    (10)
    IN
    Data communication input between batteries in parallel operation
    (11)
    USB
    For external data exchange (e.g., firmware update)
    2. Operating controls and connections
    Connection area
    No.
    Name
    Description
    (1)
    HVB connector
    (2)
    SERVICE
    (3)
    DC1-
    (4)
    DC2-
    (5)
    DC1+
    (6)
    DC2+
    (7)
    (8)
    INVERTER
    (9)
    OUT
    (10)
    IN
    (11)
    USB
    Operating controls
    No.
    Name
    Description
    (1)
    Displays the status of the battery
    (2)
    Start button/dark start
    • Press once to start the battery
    • Press and hold for 5 seconds for manual battery start (dark start) after system shutdown
    (3)
    DC Disconnector
    Interrupts the current flow between the battery and the inverter
    Status
    Description
    LED status
    LED
    1
    LED
    2
    LED
    3
    LED
    4
    LED
    5
    Starting procedure
    The number of the battery systems is checked and started
    Start
    Primary battery
    Secondary battery 1
    Secondary battery 2
    Secondary battery 3
    Checking the application mode
    Successful parallel or single application mode verification
    5 x
    is displayed
    Establishing a connection for parallel operation
    is displayed
    Charging (SoC)
    0% - 25.0%
    25.1% - 50.0%
    50.1% - 75.0%
    75.1% - 99.9%
    100%
    Discharging / no load
    100% - 75.1%
    75.0% - 50.1%
    50.0% - 25.1%
    25.0% - 0%
    Error
    There is an error; please contact the technical specialist.
    Flashes green 1/s
    Flashes green 2/s
    Lights up green
    Lights up red
    The LED status varies depending on the error.
    Installation
    General
    All installed components in the PV system must be compatible with each other and have the necessary configuration options. The installed components must not restrict or negatively affect the functioning of the PV system.
    NOTE!
    Risk due to components in the PV system that are not and/or only partially compatible.
    Incompatible components can restrict and/or negatively affect the operation and/or functioning of the PV system.
    Only install components recommended by the manufacturer in the PV system.
    Before installation, check the compatibility of components that have not been expressly recommended with the manufacturer.
    1. Installation
    General
    NOTE!
    1. Installation
    2. General
    NOTE!
    1. Installation
    IMPORTANT! The installation location must be chosen such that all operating controls are easily accessible and simple to operate. The battery must not be covered or installed in enclosures.
    Maximum ambient temperature: -20 °C to +55 °C
    Relative humidity: 5 to 95%
    The battery must not be installed or operated at more than 2000 m above sea level.
    The battery is suitable for indoor installation.
    The battery is suitable for installation in protected outdoor areas (e.g., under an overhanging roof).
    The battery is not suitable for unprotected installation outdoors.
    In order to prevent the battery from heating up as much as possible, do not expose the battery to direct sunlight.
    The battery is not fully waterproof and must not be immersed in water.
    Do not install the battery:
    • Where it may be exposed to ammonia, corrosive gases, acids, or salts (e.g., vent openings for livestock stables, chemical plants, tanneries).
    Do not install the battery in:
    • Areas where there is an increased risk of accidents from farm animals (e.g., horses, cattle, sheep, pigs)
    • Stables or adjoining areas
    • Storage areas for hay, straw, chaff, animal feed, and fertilizers
    • Greenhouses
    • Storage or processing areas for fruit, vegetables, or viticulture products
    • Areas used in the preparation of grain, green fodder, or animal feeds
    Do not install the battery close to sources of fire or near to flammable, explosive or chemical materials. Ensure a minimum distance of 2 meters from heat sources (max. 60 °C).
    1. Installation
    2. Choosing the Location
    • Greenhouses
    1. Installation
    Installation
    Use appropriate mounting materials depending on the surface and pay attention to the recommendation for the screw dimensions for the L-shaped mounting bracket. A technical specialist is responsible for selecting appropriate mounting material.
    1. Installation
    2. Installation
    1. Installation
    2. Installation
    Wall installation
    A minimum distance of 300 mm is recommended on the left and right side of the battery.
    For detailed information on the dimensions of the battery, see chapter Dimensions on page(→).
    IMPORTANT!
    The battery system must be mounted on a sufficiently load-bearing and non-flammable surface ( e.g., brick or concrete wall). Make sure there are sufficient fastening points, as described below. These depend on the number of Reserva modules used.
    1
    Align the drilling template horizontally on the wall and stick it on.
    2
    Drill holes at the required fastening points.
    3
    Carefully loosen the drilling template from the wall.
    1. Installation
    2. Installation
    WARNING!
    Danger of electric shock due to live HVB connectors.
    This can result in serious injury and damage to property.
    Use the integrated handles for lifting and lowering.
    Wear personal protective equipment.
    Remove conductive objects such as watches, bracelets, and rings.
    WARNING!
    Danger due to soiled battery connections.
    Protect the battery connections from dirt.
    Check the battery connections for soiling.
    Always use personal protective equipment (insulated gloves, safety goggles, protective clothing) when cleaning soiled battery connections and remove soiling with a lint-free cloth without the use of cleaning agents.
    CAUTION!
    Danger due to improper battery transportation or installation.
    This can result in injuries.
    Lifting and lowering should be performed by at least 2 people.
    Use the integrated carrying handles.
    When lowering the battery, make sure that limbs do not come between the battery and the fixtures.
    Make sure that there are sufficient fastening points to prevent the battery from tipping over.
    1
    Position the base plate parallel to the wall at a distance of 50 ‑ 70 mm and align it horizontally by turning the adjusting feet with a socket wrench (width across flats 13).
    2
    Place the Reserva module parallel to the base plate.
    3
    Fasten the 2 connecting tabs using the screws supplied (TX30) and to a torque of 5 Nm.
    4
    Fasten the L‑shaped mounting brackets using the supplied screws (TX30), washers and to a torque of 5 Nm. Insert the bolt anchors into the wall and fasten with a socket wrench (width across flats 13).
    5
    Place the Reserva BMS parallel to the previous Reserva module.
    6
    7
    1. Installation
    Various cable types
    Solid
    Multi-stranded
    Fine-stranded
    Single-core cable type
    Multi-stranded cable type
    Fine-stranded cable type
    1. Installation
    2. Prerequisites for connecting
    Various cable types
    Solid
    Multi-stranded
    Fine-stranded
    1. Installation
    IMPORTANT! The cables used must comply with the requirements of EN 50618 or IEC 62930. Cables that do not comply with EN 50618 or IEC 62930 have a lower current carrying capacity and the technical specialist is responsible for ensuring appropriate cable dimensions and cable lengths.
    Round copper conductors can be connected to the terminals as described below:
    DC connections
    Manufacturer
    Ø insulation layer
    Stripping length
    Stäubli MC4 EVO STOR
    6 mm2
    4.7-6.4 mm
    7 mm
    6 mm2
    6 mm2
    10 mm2
    6.4-8.5 mm
    7 mm
    10 mm2
    10 mm2
    PE ground conductor connection (ring cable lug)
    Material
    Ø bore
    Torque
    Copper with tin coating
    6 mm
    5 Nm
    10 mm2
    10 mm2
    10 mm2
    1. Installation
    IMPORTANT! The max. cable length between the inverter and the battery is 30 m; the max. cable length between the battery systems is 10 m. The cable lengths between the battery systems should be as short as possible to avoid a voltage drop.
    Restrictions
    The capacity of the battery system affects the max. cable length (see tables below). If the max. cable length is exceeded without inline fuses, inline fuses (InlineFuse 50A MC4-Evo stor) must be used to avoid possible damage to the PV system. The specified cable lengths apply to cables in accordance with EN 50618 or IEC 62930.
    Number of
    battery systems
    Number of
    Reserva modules
    Max. cable length
    6 mm2
    With inline
    fuses
    1
    2-5
    30 m
    30 m
    2
    2
    14 m
    40 m
    3
    22 m
    4
    29 m
    5
    37 m
    3
    2
    7 m
    50 m
    3
    11 m
    4
    15 m
    5
    19 m
    4
    2
    4 m
    60 m
    3
    7 m
    4
    9 m
    5
    12 m
    Number of
    battery systems
    Number of
    Reserva modules
    Max. cable length
    10 mm2
    With inline
    fuses
    1
    2-5
    30 m
    30 m
    2
    2
    30 m
    40 m
    3
    40 m
    4
    40 m
    5
    40 m
    3
    2
    15 m
    50 m
    3
    24 m
    4
    32 m
    5
    41 m
    4
    2
    9 m
    60 m
    3
    14 m
    4
    19 m
    5
    24 m
    Cable length (DC+/DC-) between the inverter and the last connected battery system.
    1. Installation
    RJ45 connection
    Cable recommendation
    Max. cable length
    Min. CAT 5 STP (shielded twisted pair)
    30 m
    0.14 - 1.5 mm2
    0.14 - 1.5 mm2
    1. Installation
    Safety
    WARNING!
    Danger due to incorrect operation and incorrectly performed work.
    Only a technical specialist is permitted to perform commissioning, maintenance, and service activities for inverters and batteries, and only within the scope of the technical regulations.
    Read the installation instructions and operating instructions from the respective manufacturer before installing and commissioning the equipment.
    WARNING!
    Danger from mains voltage and DC voltage from the PV module that are exposed to light, as well as batteries.
    All connection, maintenance, and service work should only be carried out when the AC and DC sides have been disconnected from the inverter and battery, and are de-energized.
    Only a technical specialist is permitted to connect this equipment to the public grid.
    WARNING!
    Danger from damaged and/or contaminated terminals.
    Prior to connection work, check the terminals for damage and contamination.
    Remove any contamination while the equipment is de-energized.
    Have defective terminals repaired by a technical specialist.
    1. Installation
    2. Electrical connection
    Safety
    WARNING!
    WARNING!
    WARNING!
    1. Installation
    IMPORTANT! Allow the capacitors of the inverter to discharge.
    1
    Turn off the automatic circuit breaker. Set the switch position of the inverter's DC disconnector to "Off".
    1. Installation
    IMPORTANT! The battery modules are connected to one another in the battery system via a common ground connection. This ensures equipotential bonding of the battery system. An additional ground connection to the individual battery modules is neither necessary nor permitted.
    IMPORTANT! The battery ground conductor (PE) must be connected externally (e.g., switch cabinet). The technical specialist is responsible for selecting the ring cable lug and the screw lock.
    1
    Fasten the ground conductor (PE) to the ground conductor connection using the screws supplied (TX30) and to a torque of 5 Nm.
    1. Installation
    WARNING!
    Danger due to loose and/or incorrectly clamped single conductors.
    Check that the single conductors are secure in the crimp contact.
    Make sure that the single conductor has been fully inserted into the crimp contact and that no single strands are protruding out of it.
    IMPORTANT!
    The maximum cable length between the inverter and the battery is 30 m.
    1
    Remove the caps.
    2
    Select the cable cross-section in accordance with the instructions in Permitted cables for the electrical connection on page (→). Strip the insulation of the single conductors by 7 mm (0.27 inch).
    3
    Attach the crimp contact to the individual conductors using a suitable crimping tool.
    4
    Push the crimp contact into the MC4 plug with an audible click.
    5
    Tighten the cable glands with a torque of 2.5 Nm ‑ 3 Nm.
    6
    Push the MC4 plug (+/-) into the respective slot until it clicks into place.
    1. Installation
    WARNING!
    IMPORTANT!
    The max. cable lengths between the inverter and the battery and between the battery systems must be observed according to chapter (→) on page Maximum DC cable lengths. The cable lengths between the battery systems should be as short as possible to avoid a voltage drop.
    1
    Remove the caps.
    2
    3
    4
    5
    6
    IMPORTANT!
    When using inline fuses (InlineFuse 50A MC4-EVO stor), only install them in a DC cable (DC+ or DC-). Do not mix the fuses in both cables, otherwise the inline fuses will not work.
    1. Installation
    PIN assignment
    Observe the following points when connecting the data communication cable.
    • Use network cables of type CAT5 STP or higher.
    • Use a twisted cable pair for corresponding data cables.
    • Use double insulated or sheathed data cables when they are near to bare conductors.
    • Use shielded twisted pair cables to avoid interference.
    Connection overview of the data communication lines between the Fronius inverter and the Fronius Reserva.
    1. Installation
    2. Connecting the data communication cables
    PIN assignment
    1. Installation
    IMPORTANT!
    IMPORTANT!
    In case of improper connection, it is not possible to guarantee the strain-relief device and protection class IP65 for the data communication connection. The maximum possible width of the RJ45 plug is 12 mm. Only RJ45 plugs without locking and anti-kink protection are compatible with the LP-16-C/RJ45 plug.
    1
    First, guide the data cables through the union nut and then through the cable gland. Insert the plug insert until there is an audible click. Fasten the union nut to the cable gland.
    2
    Connect the data cable to the "INVERTER" data communication connection until there is an audible click.
    1. Installation
    IMPORTANT!
    The maximum cable length between the inverter and the battery is 30 m and the maximum cable length between the battery systems is 10 m.
    IMPORTANT!
    In case of improper connection, it is not possible to guarantee the strain-relief device and protection class IP65 for the data communication connection. The maximum possible width of the RJ45 plug is 12 mm. Only RJ45 plugs without locking and anti-kink protection are compatible with the cable gland.
    Overview
    The terminating resistors are installed at the factory. For parallel battery operation, the terminating resistors must be installed as shown below.
    1
    First, guide the data cable through the union nut, then through the seal and then through the cable gland. Fasten the union nut to the cable gland.
    2
    Remove the closure caps of the data communication connections "IN" (data input) or "OUT" (data output) by rotating them 90° to the left.
    3
    Connect the data cable to the "IN" (data input) or "OUT" (data output) data communication connection and rotate 90° to the right.
    1. Installation
    Installation without terminating resistors can lead to interference in the operation of the PV system. To ensure smooth operation, install the terminating resistors according to the following overview.
    For permissible cables and max. distances for the data communication area, see chapter Permitted cables for the data communication connection on page (→).
    1. Installation
    Final tasks
    1
    Place the cover (top) on the Reserva BMS and slide it to the right until the cover clicks into place.
    2
    Push in the side covers from above, starting with the base plate, until the covers engage.
    3
    Push in the side covers of the Reserva BMS from above until the covers engage. Feed the cables through the side cutout in the cover.
    1. Installation
    2. Final tasks
    1
    2
    3
    1. Installation
    Safety
    WARNING!
    This can result in severe personal injury and damage to property.
    CAUTION!
    Use the integrated carrying handles for lifting the battery and setting it down.
    1. Installation
    2. Adding/replacing the Reserva module of the battery system
    Safety
    WARNING!
    CAUTION!
    1. Installation
    The following points must be observed when expanding the battery system in order to be able to use the full capacity:
    • The state of charge (SoC) must be 30% (activate Service Mode, see chapter Setting the State of Charge (SoC) with Service Mode on page(→)).
    • Carry out expansion within the first 2 years from starting for the first time.
    • Charging/discharging cycle count <300
    NOTE!
    Restriction on expansions of the battery system after 2 years.
    It is possible to expand the battery system after 2 years, however with the restriction that the added battery module is operated with the lowest state of health (SoH) in the battery system.
    Example – Expansion outside of manufacturer’s recommendation
    SoH new Reserva module
    100%
    SoH installed Reserva modules
    96%
    SoH entire battery system
    96%
    1. Installation
      To activate Service Mode, a connection to the user interface of the inverter is required, see chapter Commissioning with the app on page (→) or Commissioning with the browser on page (→).
    1Open the user interface of the inverter.
    2Log in to the login section with user Customer or Technician and the relevant password.
    3Open the Energy Management > Battery Management > Service Mode menu area.
    4Activate Service Mode.
    5Click the Save button to save the settings.
    ✓The service mode is activated and the battery is charged/discharged to 30% SoC.
    1. Installation
    1
    IMPORTANT! Before starting work on the battery, all LEDs on the LED status indicator must be unlit.
    2
    Set the switch position of the battery's DC disconnector to "Off".
    1. Installation
    1
    Push the left and right covers on the Reserva BMS up and lift them off.
    2
    Starting at the top Reserva module, push the left and right covers up and lift them off.
    3
    Slide the top cover on the Reserva BMS to the left and lift off.
    1. Installation
    1
    Loosen the MC4 plugs (+/-) using a suitable tool.
    2
    Press the locking mechanism on the plug of the "INVERTER" data cable and remove the plug.
    For batteries in parallel operation, also disconnect the "IN" and "OUT" data cables.
    3
    Loosen the ground conductor using a screwdriver (TX30).
    4
    Loosen the L‑shaped mounting brackets.
    5
    Undo the 2 connecting tabs.
    6
    Lift the Reserva BMS installed in parallel off the last Reserva module.
    1. Installation
    1
    Position the new Reserva module in parallel.
    2
    3
    IMPORTANT!
    Ensure there are sufficient fastening points, see chapter Wall installation on page(→).
    Fasten the L-shaped mounting brackets using the supplied screws (TX30), washers and to a torque of 5 Nm. Insert the bolt anchors into the wall and fasten with a socket wrench (width across flats 13).
    1. Installation
    1
    2
    3
    1. Installation
    1
    2
    3
    1. Installation
    1
    2
    3
    Commissioning
    1
    Turn the DC disconnector of the battery to the "On" switch setting.
    2
    Close the cover of the DC disconnector until there is an audible click and secure it against unauthorized opening with the screws. Press the start button once to start the battery.
    3
    Turn on the automatic circuit breaker. Turn the DC disconnector of the inverter to the "On" switch setting.
    1. Commissioning
    1
    2
    3
    1. Commissioning
    2. Switching on the photovoltaic system
    1
    2
    3
    1. Commissioning
    Manual system start
    Requirements
    There is no energy available from the PV modules or from the public grid. If backup power operation or battery operation are not possible (e.g., deep discharge protection of the battery), the inverter and battery switch off.
    1. Commissioning
    2. Manual system start
    Requirements
    1. Commissioning
    Status codes about the inactive state of the battery are displayed on the user interface of the inverter. A notification via e-mail can be activated in Fronius Solar.web.
    1. Commissioning
    As soon as energy is available again, the inverter and the battery will start operation automatically. If the battery has switched off to protect against deep discharge for example, the battery must be started manually (dark start), see chapter Switching on the photovoltaic system on page (→).
    1. Commissioning
    The inverter requires a supply of energy from the battery to start backup power mode. This is done manually on the battery as described below.
    1
    2
    Close the cover of the DC disconnector until there is an audible click and secure it against unauthorized opening with the screws. Press and hold the start button for 5 seconds to start the battery.
    1. Commissioning
    General
    IMPORTANT! Settings in the Device Configuration menu item may only be entered by staff trained to do so!
    To access the Device Configuration menu item, you must log in with user “Technician” and the technician password.
    1. Commissioning
    2. Settings – User interface of the inverter
    General
    1. Commissioning
    The Fronius Solar.start app is required for commissioning. Depending on the mobile device used to perform the installation, the app is available on the relevant platform.
    1Download and install the Fronius Solar.start app.
    2Open the access point on the inverter by touching the sensor    .
    ✓Communication LED flashes blue.
    3Open the Fronius Solar.start app and scan the QR code on the rating plate of the inverter using a smartphone or tablet to connect to the inverter.
    4Add the battery as in chapter Adding a battery in the user interface of the inverter on page (→).
    The network wizard and product setup can be performed independently. A network connection is required for the Fronius Solar.web installation wizard.
    1. Commissioning
    WiFi:
    1Open the access point on the inverter by touching the sensor    .
    ✓Communications LED flashes blue.
    2Establish the connection to the inverter in the network settings (the inverter is displayed with the name “FRONIUS_” and the serial number of the device).
    3Enter the password from the inverter’s rating plate and confirm.
    IMPORTANT!
    To enter the password in Windows 10, first select the Connect using a security key instead link to be able to establish the connection with the password.
    4Enter the IP address 192.168.250.181 in the address bar of the browser and confirm to connect to the inverter.
    5Add the battery as in chapter Adding a battery in the user interface of the inverter on page (→).
    Ethernet:
    1Establish a connection to the inverter (LAN1) using a network cable (min. CAT5 STP).
    3Enter the IP address 169.254.0.180 in the address bar of the browser and confirm to connect to the inverter.
    1. Commissioning
    2In the Login menu area or in the User > User Login menu area, log in with username and password.
    3Go to the Device Configuration > Components menu area.
    4Click on the Add components+ button.
    5Select the Fronius battery battery in the Type drop-down list.
    6Click on the Add button.
    7Click the Save button to save the settings.
    ✓The battery has been added to the PV system.
    1. Commissioning
    Firmware update
    Obsolete firmware/software versions may lead to incompatibilities between the inverter and the battery. In this case, the following steps are to be performed:
    2Log in with user name and password in the Log in menu field or in the User > User login menu field.
    3Call up the System > Update menu field.
    4Drag the firmware file into the drop file here field, or select via Select file.
    ✓The update is carried out.
    All available updates are provided on the product page and in the "Fronius Download Search" area at www.fronius.com .
    1. Commissioning
    1
    1. Commissioning
    2. Switching the battery off and on
    1
    1. Commissioning
    1
    2
    Appendix
    Cleaning
    Wipe the device, if necessary, with a damp cloth.
    Do not use cleaning agents, scouring agents, solvents, or similar products to clean the device.
    1. Appendix
    Cleaning
    1. Appendix
    2. Service, maintenance and disposal
    Cleaning
    1. Appendix
    Maintenance
    The device is maintenance-free. Service work may only be carried out by qualified technical personnel.
    1. Appendix
    Forced re-charging
    Forced re-charging to protect against deep discharge takes place automatically using solar energy or energy from the grid if the battery's state of charge (SoC) falls below the minimum level and the requirements are met.
    NOTE!
    Danger of deep discharge of battery modules.
    This can result in irreparable damage to the battery modules.
    If the battery falls below the minimum state of charge (SoC), it must be recharged within 7 days to protect against deep discharge.
    Requirements for forced re-charging of the battery system
    • Set the switch position of the battery's DC disconnector to "On".
    • Grid-connected operation of the inverter.
    Start forced re-charging if the battery has switched off automatically to protect against deep discharge, see chapter Switching on the photovoltaic system on page (→).
    1. Appendix
    Disposal
    In accordance with the EU Directive and national law, the following products must be disposed of separately and recycled:
    • Waste electrical and electronic equipment
    • Used batteries (portable batteries, industrial batteries)
    Used equipment and batteries must be returned to the distributor or an authorized local collection system. Do not dispose of batteries with domestic waste. Protect batteries from high temperatures, direct sunlight, moisture and corrosive environments.
    Arrange for the safe collection and proper disposal of damaged, leaking or used batteries by a battery recycling company or the Fronius Service Partner.
    In addition, it should be noted that batteries contain substances that, if disposed of improperly, can have a significant negative impact on the environment as well as on human health and the safety of persons, in particular due to the leakage of hazardous substances such as heavy metals or electrolytes, which can contaminate soil, water and air.
    This ensures environmental protection and the sustainable use of natural resources.
    Packaging materials
    • Collect separately
    • Observe local regulations
    • Compress the cardboard box to reduce volume
    1. Appendix
    Warranty provisions
    Warranty
    Detailed warranty conditions specific to your country can be found at https://www.fronius.com/en/download-center?searchword=Warranty+conditions .
    If there is a warranty for the relevant product, register the product at https://warranty.fronius.com/ and activate or extend the warranty.
    1. Appendix
    2. Warranty provisions
    Warranty
    1. Appendix
    Technical data
    Fronius Reserva 6.3
    General data
    Usable capacity 1)
    30.85 Ah
    Max. charging current
    - 20 °C to -10 °C
    - 10 °C to 5 °C
    5 °C to 15 °C
    15 °C to 45 °C
    45 °C to 50 °C
    50 °C to 55 °C
    2.5 A
    8.0 A
    16.0 A
    32.0 A
    21.5 A
    8.0 A
    Max. discharge current
    -20 °C to 0 °C
    0 °C to 45 °C
    45 °C to 50 °C
    50 °C to 55 °C
    16.0 A
    32.0 A
    21.5 A
    8.0 A
    Max. charge/discharge currents (25 °C, 5 s)
    37.76 A
    Charging/discharging cycles (SoH ≥ 60%)
    6000 cycles
    Permitted ambient temperature
    -20 °C to 55 °C
    Optimum operating temperature
    15 °C to 30 °C
    Permissible humidity
    5% to 95%
    Cooling
    Convection cooling
    Altitude
    ≤ 2000 m
    Discharge rate Reserva module (25 °C)
    ≤ 1.5%/month
    Number of battery modules
    2
    Max. battery systems in parallel operation
    4
    Data communication between inverter and battery
    RS485
    Certifications
    IEC 62619:2022
    CE
    VDE-AR-E 2510-50:2017-05
    EN 62477-1:2012+A11+A1+A12
    IEC 62040-1:2017+A1+A2
    EMC standard
    EN IEC 61000-6-1:2019
    EN IEC 61000-6-3:2021
    UN Transportation Testing standard
    UN 38.3
    Certifications for environmental protection
    ROHS
    REACH
    Protection rating (when installed)
    IP65
    Corrosivity category
    C4
    Protective class
    1
    Overvoltage category
    2
    Dimensions incl. covers
    H × W × D
    890 x 772 x 176 mm
    Weight
    86.5 kg
    Electrical data
    Number of modules
    2
    Nominal energy
    6.68 kWh
    Usable energy
    6.31 kWh
    Rated voltage
    204.8 V
    Output voltage range
    179.2 ~ 230.4 V
    Operating AC voltage range
    185.6 ~ 227.2 V
    Charging/discharging capacity
    5.94 kW
    Peak value of charging/discharging power (25 °C, 5 s)
    8.45 kW
    Expected short circuit current
    1.70 kA
    1. Appendix
    2. Technical data
    Fronius Reserva 6.3
    General data
    Usable capacity 1)
    30.85 Ah
    - 20 °C to -10 °C
    - 10 °C to 5 °C
    5 °C to 15 °C
    15 °C to 45 °C
    45 °C to 50 °C
    50 °C to 55 °C
    2.5 A
    8.0 A
    16.0 A
    32.0 A
    21.5 A
    8.0 A
    -20 °C to 0 °C
    0 °C to 45 °C
    45 °C to 50 °C
    50 °C to 55 °C
    16.0 A
    32.0 A
    21.5 A
    8.0 A
    37.76 A
    6000 cycles
    -20 °C to 55 °C
    15 °C to 30 °C
    5% to 95%
    Cooling
    Convection cooling
    Altitude
    ≤ 2000 m
    ≤ 1.5%/month
    2
    4
    RS485
    Certifications
    IEC 62619:2022
    CE
    EMC standard
    UN 38.3
    ROHS
    REACH
    IP65
    C4
    Protective class
    1
    2
    H × W × D
    890 x 772 x 176 mm
    Weight
    86.5 kg
    Electrical data
    Number of modules
    2
    Nominal energy
    6.68 kWh
    Usable energy
    6.31 kWh
    Rated voltage
    204.8 V
    179.2 ~ 230.4 V
    185.6 ~ 227.2 V
    5.94 kW
    8.45 kW
    1.70 kA
    1. Appendix
    2. Technical data
    Fronius Reserva 9.5
    General data
    Usable capacity 1)
    30.85 Ah
    - 20 °C to -10 °C
    - 10 °C to 5 °C
    5 °C to 15 °C
    15 °C to 45 °C
    45 °C to 50 °C
    50 °C to 55 °C
    2.5 A
    8.0 A
    16.0 A
    32.0 A
    21.5 A
    8.0 A
    -20 °C to 0 °C
    0 °C to 45 °C
    45 °C to 50 °C
    50 °C to 55 °C
    16.0 A
    32.0 A
    21.5 A
    8.0 A
    37.76 A
    6000 cycles
    -20 °C to 55 °C
    15 °C to 30 °C
    5% to 95%
    Cooling
    Convection cooling
    Altitude
    ≤ 2000 m
    ≤ 1.5%/month
    3
    4
    RS485
    Certifications
    IEC 62619:2022
    CE
    EMC standard
    UN 38.3
    ROHS
    REACH
    IP65
    C4
    Protective class
    1
    2
    H × W × D
    1140 x 772 x 176 mm
    Weight
    120 kg
    Electrical data
    Number of modules
    3
    Nominal energy
    10.03 kWh
    Usable energy
    9.47 kWh
    Rated voltage
    307.2 V
    268.8 ~ 345.6 V
    278.4 ~ 340.8 V
    8.91 kW
    12.68 kW
    1.90 kA
    1. Appendix
    2. Technical data
    General data
    Usable capacity 1)
    30.85 Ah
    - 20 °C to -10 °C
    - 10 °C to 5 °C
    5 °C to 15 °C
    15 °C to 45 °C
    45 °C to 50 °C
    50 °C to 55 °C
    2.5 A
    8.0 A
    16.0 A
    32.0 A
    21.5 A
    8.0 A
    -20 °C to 0 °C
    0 °C to 45 °C
    45 °C to 50 °C
    50 °C to 55 °C
    16.0 A
    32.0 A
    21.5 A
    8.0 A
    37.76 A
    6000 cycles
    -20 °C to 55 °C
    15 °C to 30 °C
    5% to 95%
    Cooling
    Convection cooling
    Altitude
    ≤ 2000 m
    ≤ 1.5%/month
    4
    4
    RS485
    Certifications
    IEC 62619:2022
    CE
    EMC standard
    UN 38.3
    ROHS
    REACH
    IP65
    C4
    Protective class
    1
    2
    H × W × D
    1390 x 772 x 176 mm
    Weight
    153.5 kg
    Electrical data
    Number of modules
    4
    Nominal energy
    13.37 kWh
    Usable energy
    12.63 kWh
    Rated voltage
    409.6 V
    358.4 ~ 460.8 V
    371.2 ~ 454.4 V
    11.88 kW
    16.91 kW
    2.10 kA
    1. Appendix
    2. Technical data
    General data
    Usable capacity 1)
    30.85 Ah
    - 20 °C to -10 °C
    - 10 °C to 5 °C
    5 °C to 15 °C
    15 °C to 45 °C
    45 °C to 50 °C
    50 °C to 55 °C
    2.5 A
    8.0 A
    16.0 A
    32.0 A
    21.5 A
    8.0 A
    -20 °C to 0 °C
    0 °C to 45 °C
    45 °C to 50 °C
    50 °C to 55 °C
    16.0 A
    32.0 A
    21.5 A
    8.0 A
    37.76 A
    6000 cycles
    -20 °C to 55 °C
    15 °C to 30 °C
    5% to 95%
    Cooling
    Convection cooling
    Altitude
    ≤ 2000 m
    ≤ 1.5%/month
    5
    4
    RS485
    Certifications
    IEC 62619:2022
    CE
    EMC standard
    UN 38.3
    ROHS
    REACH
    IP65
    C4
    Protective class
    1
    2
    H × W × D
    1640 x 772 x 176 mm
    Weight
    187 kg
    Electrical data
    Number of modules
    5
    Nominal energy
    16.71 kWh
    Usable energy
    15.79 kWh
    Rated voltage
    512 V
    448 ~ 576 V
    464 ~ 568 V
    14.85 kW
    21.14 kW
    2.24 kA
    1. Appendix
    2. Technical data
    1)
    100% depth of discharge (DoD), 0.2 C charging and discharging rate at 25 °C.
    Dimensions
    Fronius Reserva
    1. Dimensions
    Fronius Reserva