Manual
en-US
    • Fronius Argeno - Advanced Settings
    • Version: 001-08052025
    • Reactive power control
      • Operating power range depending on mains voltage
      • Dynamics and accuracy
      • Reactive power functions
      • Parameters for reactive power control
    • Effective power control
      • Dynamics/accuracy
      • Methods for effective power regulation
      • P set value
      • P limit
      • Voltage-dependent power reduction P(U)
      • P(f)
      • Parameters for P(f)
    • Dynamic grid support
      • Dynamic grid support (fault ride through)
      • Dynamic grid support by way of interference immunity
      • Dynamic grid support via fast feed-in of residual current
      • Parameters for FRT
    • Other grid-supporting functions in the case of effective power
      • Permanent power gradients
      • Parameters for permanent power limitation
      • Soft start up / power ramp-up limiting
      • Power gradient normal operation
    • Enhanced island detection
      • Island detection methods
    • Q on Demand
      • Q on Demand
    User information Fronius Argeno - Advanced Settings
    Quick links
    Q on Demand
    ContactImprintTerms and ConditionsData privacy statement
    link-horizontalLink copied
    Reactive power can be used in electrical energy supply networks to bolster the level of voltage. As such, feed-in inverters can contribute to static voltage stability. Reactive power brings about a voltage drop at the inductive and capacitive components of the equipment which can either bolster or reduce the level of voltage depending on what is indicated. If the generating system draws inductive reactive power while effective power is being fed in, part of the voltage swing caused by the effective power feed can be compensated for by drawing reactive power.
    The reactive power mode and the respective control process are specified by the utility. If no control process has been specified, the system should be operated with a fixed reactive power specification of 0%.
    1. Reactive power control
    The device can be operated within the respective fixed voltage range stated. The maximum apparent power in the event of undervoltage depends on the mains voltage due to the maximum continuous current, as shown in the table below.
    The following figures show the reactive power operating range as a function of the effective power and the apparent power operating range as a function of the mains voltage for various devices.
    Maximum continuous apparent power as a function of the mains voltage:
    Maximum apparent power [p.u.]
    Argeno 125 voltage with UN 380 V
    1.0
    ≥ 397
    0.95
    377
    0.90
    357
    0.85
    337
    P-Q operating range
    Apparent power subject to mains voltage
    For all of the control methods, the specified set value at the inverter's connection terminals is adjusted using a stationary deviation of the reactive power of maximum 2% SN. This maximum deviation always relates to the value specified for the reactive power. If the cos j power factor is specified in the control method, the deviation relates to the reactive power value resulting from the current power level.
    The transient response of the control methods is determined by a PT-1 filter. The settling time is 5 tau, which corresponds to achieving approx. 99% of the final value of a PT-1 filter. Depending on the control method selected, there are also other parameters that determine dynamic behavior.
    The following functions for controlling reactive power are implemented:
    • cos constant j
    • Q constant
    • cos j (P)
    • Q(P) 10 nodes
    • Q(U) 10 nodes
    Reactive power is prioritized by default for all methods but can be disabled. The priority can be selected when using the Q constant and Q(U) mode. The maximum possible effective power that can be fed in is reduced in line with the P-Q operating range when the maximum useful power is reached.
    Model
    Parameter
    Scale factor
    R/RW
    Range
    Description
    126.
    ModEna
    ModEna
    RW
    0 / 1
    The reactive power process selected in the device can only be enabled/disabled indirectly via SunSpec.
    cos constantj
    In cos j constant mode, the specified power factor is set permanently by the inverter. The reactive power level is set in line with Q = P * tan j as a function of the power so the specified power factor is continually maintained. If the setting value changes, the new value is adopted by way of a filter in a muted manner. The settling time can be parameterized and is 1 second (corresponds to 5 tau, while the ideal time according to SunSpec is 3 tau) with the transient response of a PT-1 filter with a time constant of tau = 200 ms. The specified power factor can be configured on the display or via communication using the RS485 protocol and MODBUS/SunSpec.
    If the applicable grid code calls for the j to respond to the set value with a defined gradient or a defined settling time that is shorter than the configured tau = 200 ms, this gradient or settling time must be implemented in the system controls
    Model
    Parameter
    Scale factor
    R/RW
    Range
    Description
    123.
    OutPFSet
    cos-phi constant
    OutPFSet_SF
    RW
    1-0.3 [°]
    Set power factor to a specific value
    123.
    OutPFSet_RmpTms
    Power gradient increase & Power gradient decrease
    R
    1-65,524 [% Slim / min]
    Specifies the dynamic behavior on changing the cos j power factor. The power factor is changed with the specified gradient.
    Note: The gradient is overlaid with the settling time.
    123.
    OutPFSet_WinTms
    Settling time
    VArPCt_SF
    RW
    1,000-120,000 [ms]
    Set the settling time in the event of an abrupt change in the reactive power set value (e.g., caused by a voltage jump).
    123.
    OutPFSet_RvrtTms
    Timeout
    RW
    0-1,000 [s]
    Specifies the time after which the inverter reverts to the previously valid reactive power process if it does not receive a new power factor specification.
    If the timeout is set to 0 seconds, the sent power factor specification is permanently maintained, even in the event of a communication failure.
    Note: If the device is restarted, the timeout is reset to the configured fallback time.
    Q constant
    In Q constant mode, the specified reactive power value is set permanently by the inverter. If the specification is changed, the new value is adopted by way of a filter in a muted manner. The settling time and gradient limit can be configured via the web interface. The settling time is 1 second and follows the transient response of a PT-1 filter with a time constant of tau = 200 ms. The specified reactive power can be configured on the display or via communication using the RS485 protocol and MODBUS/SunSpec.
    If the applicable grid code calls for the reactive power to be adjusted to the set value with a defined gradient or a defined settling time that is shorter than the configured tau = 200 ms, this gradient or settling time must be implemented in the system controls.
    Model
    Parameter
    Scale factor
    R/RW
    Range
    Description
    123.
    VArWMaxPct
    Q constant
    VArPCt_SF
    RW
    0-100 [%Pmax]
    The reactive power set value can be set as a function of the configured maximum effective power.
    123.
    VArPct_RvrtTms
    Timeout
    RW
    0-1,000 [s]
    Specifies the time after which the inverter reverts to the previously valid reactive power process if it does not receive a new reactive power specification.
    If the timeout is set to 0 seconds, the sent reactive power specification is permanently maintained, even in the event of a communication failure.
    Note: If the device is restarted, the timeout is reset to the default value.
    123.
    VArPct_RmpTms
    Output gradient limitation increase & Output gradient limitation decrease
    R
    Specifies the dynamic behavior on changing the reactive power value power factor. The reactive power is changed with the specified gradient.
    123.
    VArPct_RmpTms
    Settling time
    RW
    1,000-120,000 [ms]
    Specifies the dynamic behavior on changing the effective power set value. The effective power is changed according to a PT-1 characteristic with a settling time of 5 tau.
    NOTE: The settling time is overlaid with the increasing and decreasing gradient.
    cos j (P)
    In the cos j (P) operating mode, the cos j set value and the reactive power set value derived from this are calculated continuously as a function of the actual power level. This function ensures that grid support is provided by the reactive power when a significant voltage boost is anticipated due to a high feed-in level. A characteristic is specified which can be used to configure up to 10 nodes, i.e., value pairs for effective power and j. The effective power is entered as a percentage in relation to the maximum apparent power Slim. Other parameters can be used to limit functionality and to limit activation to certain voltage ranges.
    cos j (P) standard characteristic with three nodes
    Q(U) 10 nodes
    In Q(U) mode, the reactive power set value is calculated continuously as a function of the mains voltage. This function ensures that grid support is provided by the reactive power as soon as the voltage actually deviates from the target voltage. In this case, a characteristic is specified which can be used to configure up to 10 nodes consisting of value pairs for voltage and reactive power. Other parameters allow you to limit functionality and to limit activation to certain power levels as well as to parameterize the transient response.
    The displacement voltage of the neutral point is used to calculate the reactive power set value for three-phase devices.
    Q(U) standard characteristic with five nodes
    Q(P) 10 nodes
    In Q(U) mode, the reactive power set value is calculated continuously as a function of the effective power. In this mode, a characteristic is specified which can be used to configure up to 10 nodes consisting of value pairs for power and reactive power. The function allows you to parameterize the transient response. The displacement power of the neutral point is used to calculate the reactive power set value for three-phase devices.
    Q(P) standard characteristic with five nodes
    Display
    Setting
    Description
    Mode
    cos-phi constant | Q constant | Cos-phi(P/ Plim) | Q(U) | Q(P)
    Select active process for reactive power control and define the parameters in the respective process.
    Cos-phi constant
    Cos-phi constant
    0.3-1
    Specified power factor
    overexcited | underexcited
    Reactive power mode: Underexcited corresponds to an inductive load, overexcited to a capacitive load.
    Power gradient increase & decrease
    1-65,534
    [% Slim/min]
    Maximum change in the reactive power %Slim/min when switching to overexcited mode.
    Settling time
    1,000-120,000
    [ms]
    Specifies the dynamic behavior on changing the cos j set value. In the event of a change in the reactive power, cos j is changed according to a PT-1 characteristic with a settling time of 5 tau.
    Q constant
    Q constant
    0-100 [% Slim]
    Set as a percentage of the maximum reactive power.
    Output gradient limitation increase & decrease
    1-65,534
    [% Slim/min]
    In addition to configuring the dynamic behavior using the settling time corresponding to a first-order filter, the reactive power setting can be determined by a maximum gradient, i.e., the maximum change in the reactive power per time period.
    increase | decrease
    Maximum change in the reactive power %Slim/min in the event of switching to overexcited mode.
    Settling time
    1,000-120,000
    [ms]
    Specifies the dynamic behavior on changing the Q set value. In the event of a change in the reactive power or with lock-in or lock-out, Q is changed according to a PT-1 characteristic with a settling time of 5 tau.
    Cos-phi(P)
    Lock-In voltage
    10-126.6 [% Unom]
    The control is activated above this voltage.
    Lock-Out voltage
    10-126.6 [% Unom]
    The control is deactivated below this voltage.
    1-65,534 [% Slim/min]
    Settling time
    1,000-120,000 [ms]
    Specifies the dynamic behavior on changing the cos j set value. In the event of a change in the effective power or with lock-in or lock-out, cos j is changed according to a PT-1 characteristic with a settling time of 5 tau.
    Number of nodes
    2-10
    Specify the number of nodes for the j / (p/pn) characteristic.
    1. node ... 10. node
    0 V-max. voltage continuous operation
    Power of the node as a percentage of the maximum power.
    For the first node, the power must be 0%, for the last node the power must be 100%. The power values of the nodes must increase continuously.
    1-0.3
    Reactive power of the node as a percentage of the maximum power.
    Q(P) 10 nodes
    The rate of change of the output is limited by the configured value in the event of an increase in the output power.
    The rate of change of the output is limited to the configured value in the event of a decrease in the output power.
    Settling time
    200-60,000 [ms]
    Sets the dynamic behavior on changing the Q set value. In the event of a change in the effective power, the Q set value is changed according to a PT-1 characteristic with a settling time of 5 tau.
    Number of nodes
    2-10
    Specify the number of nodes for the Q(P) characteristic.
    1-0.3
    Q(U) 10 nodes
    Lock-In power
    0-100 [% Slim]
    Effective power threshold above which the function is activated.
    Lock-Out power
    0-100 [% Sn]
    Effective power threshold below which the function is activated.
    Lock-In time
    0-60,000 [ms]
    Length of time for which the effective power must remain below the lock-in power before control is deactivated.
    Lock-Out time
    0-60,000 [ms]
    Length of time for which the effective power must remain below the lock-out power before control is deactivated.
    Dead time
    0-10,000 [ms]
    If the voltage switches from a characteristic section with Q=0 to a characteristic section with Q ¹ 0 during active control, the reactive power setting is delayed by the set dead time. Once the dead time has expired, the control circuit is no longer subject to a delay and the set settling time determines the transient response.
    1-65,534
    [% Slim/min]
    increase | decrease
    Settling time
    1,000-120,000 [ms]
    Settling time in the event of an abrupt change in the reactive power set value (e.g., caused by a voltage jump). The transient response corresponds to a first-order filter (PT-1) with a settling time = 5 tau.
    Min. cos-phi Q1 - min. cos-phi Q4
    0-1
    In the event of a significant voltage deviation, the maximum reactive power range can be limited by a minimum cos j in order to prevent excessive feed-in of reactive power and, as a result, a significant reduction in the maximum effective power that can be fed in
    Q1
    Minimum j in overexcited operating mode (feed-in).
    Q4
    Minimum j in underexcited operating mode (feed-in).
    Q2
    Minimum j in overexcited operating mode (charging).
    Q3
    Minimum j in underexcited operating mode (charging).
    Voltage dead band
    0-5 [% Uref]
    Q(U) offset (temporary)
    U offset
    Q offset
    -100-100 [% Slim]
    -100-100 [% Slim]
    Q minimum
    0-100 [% Slim]
    underexcited | overexcited
    Set reactive power Q to a minimum value.
    Select the type of phase shift.
    Q maximum
    0-100 [% Slim]
    Set reactive power Q to a maximum value.
    Underexcited corresponds to inductive load, overexcited to a capacitive load.
    US, UD: Autonomous adjustment Vref
    The autonomous adjustment of the reference voltage enables a dynamic reactive power function. The reference voltage of the Q(U) characteristic is thus dynamically adjusted to the mains voltage via a PT-1 filter.
    US, UD: Time constant Vref adjustment
    300-5,000 [s]
    The time constant defines the control speed by which the reference voltage of the Q(U) characteristic is adjusted to the mains voltage.
    Priority mode
    Q-Priority | P-Priority
    P priority can be selected as an alternative to the default Q priority setting. With P priority, the reactive power adjustment range is limited subject to the apparent power limitation of the inverter and the active (effective) power that is currently available and being fed in.
    Active curve
    1-4 / Curve 1 TMP / Curve 2 / Curve 3 / Curve 4
    Up to four characteristics can be configured independently and one of them can be activated for regulation each time.
    Number of nodes
    2-10
    Specify the number of nodes for the Q(U) characteristic.
    Power | Voltage | Excitation
    0-100 [% Slim]
    0-125 [% Slim]
    Voltage of the node in volts.
    The voltage values of the nodes must increase continuously. At voltages below the first node and voltages above the last node, the reactive power value of the first or last node is used.
    Dynamics/accuracy
    In all of the control methods described below the specified set value at the inverter's terminals is adjusted using a stationary deviation of the effective power of maximum 2% SN.
    The transient response of the control methods is determined by a PT-1 filter. The settling time is 5 tau, which corresponds to achieving approx. 99% of the final value with a PT-1 filter. Depending on the control method selected, there are also other parameters that specify dynamic behavior.
    1. Effective power control
    Dynamics/accuracy
    Methods for regulating the effective power of feed-in inverters may be necessary for local management of load flows, for voltage stability in the distribution network, and for ensuring the stability of the interconnected grid.
    The device makes use of the following functions in order to regulate the effective power. These functions are described below:
    • P set value (MPPT (communication))
    • P limit (communication)
    • P(U) (characteristic)
    • P(f) (characteristic)
    P set value
    On all inverters, the function "P set value" is integrated in the MPP tracking of the inverter. The P set value is continually recalculated based on the MPP tracking algorithm.
    Model 704 (DER AC controls) thus also corresponds to the current market specifications.
    P limit
    The "P limit" function is available for limiting the maximum power of feeding in. If necessary, this can be used to reduce the maximum possible feed-in of an inverter, e.g., for managing bottlenecks for the operator of the distribution grid.
    P limit is only available via the MODBUS/SunSpec inverter model 123 Immediate Controls and via RS485 communication.
    When a set value is received for P limit, the output power of the inverter is limited to the specified power value. If the limit value is changed, the new value is adopted by way of a filter and a gradient limit. The actual power may be below the specified limit value because the available power (PV) and the set power value (storage) may be below the specified limit value. Depending on the inverter series, the settling time and gradient limit may be adjustable.
    Model
    Parameter
    Scale factor
    R/RW
    Range
    Description
    123
    WMaxLimPct
    Power limitation
    WMaxLimPct_SF
    RW
    0-100 [%]
    Set power limitation to a specific percentage value.
    123
    WMaxLimPct_RvrtTms
    Timeout
    RW
    0-1,000 [s]
    Specifies the time after which the inverter increases the power limitation if it does not receive a new one.
    If the timeout is set to 0 seconds, the power limitation that is sent is permanently maintained, even in the event of a communication failure.
    123
    WMaxLimPct_RmpTms
    RW
    Specifies the dynamic behavior on changing the effective power set value. The effective power is changed with the specified gradient.
    If the applicable grid connection guidelines call for the effective power to be adjusted to the set value with a defined gradient or a defined settling time, the device can be configured in such a way that this gradient is adhered to. The gradient can also be implemented on the system controller. This second solution is to be used for all other inverters.
    If the voltage increases too sharply in the upstream distribution network and not enough reactive power can be absorbed, it may be necessary to reduce the effective power. In this case, P(U) control is available for making optimum use of the grid.
    P(U) control reduces the effective power that is fed in as a function of the mains voltage using a prescribed characteristic as a basis. P(U) control is implemented as an absolute power limit. The actual power of the inverter may vary freely below this limit due to a possible fluctuation in the available power or the set value, but at no time increases above the absolute power limit.
    Configuration examples:
    • Without hysteresis: The function is activated as soon as the voltage exceeds the value of data point 1 (dp1). The power limit follows a straight line between dp1 and dp2. The function is deactivated as soon as the voltage falls below dp1.
      Characteristic example without hysteresis
    • With hysteresis: The function is activated as soon as the voltage exceeds the value of data point 2 (dp2). In this case, the power limit remains at 100% if the voltage exceeds dp1. The power limit follows a straight line between dp2 and dp3. Because of the activated hysteresis, the power limit is not increased when the voltage drops. The function is deactivated as soon as the voltage drops below dp1.
      Characteristic example with hysteresis and a deactivation threshold below the activation threshold
    Display
    Setting
    Description
    Operation mode
    Off | On
    Enable the control process.
    Off: Deactivates dynamic grid support using dynamic reactive current. Dynamic grid support remains active on account of interference immunity.
    Reference power
    Actual power | Nominal power
    Specifies the power reference for the characteristic. In this case, 100% corresponds to the rated power or the actual power at the time the function was activated, the time when the voltage passes the configured node.
    Evaluated voltage
    Maximum phase voltage | Positive phase sequence voltage
    Select the voltage to be rated.
    Specifies which voltage is evaluated in a three-phase system.
    Hysteresis mode
    Off | On
    Off: In non-hysteresis mode, the effective power is increased immediately if the voltage drops.
    On: In hysteresis mode, the power is not increased if the voltage drops.
    Deactivation gradient
    0-65,534 [% / min]
    If the available power is above the actual output at the time of deactivation, the power increase back to the maximum power is limited. The limitation is implemented by an absolute power limitation that increases with a continuous gradient up to the maximum power. The actual power of the inverter may vary freely below this limit due to a possible fluctuation in the available power or the set value, but at no time increases above the absolute power limit.
    Deactivation time
    0-60,000,000 [ms]
    Only evaluated when hysteresis mode is enabled: Monitoring time during which the voltage must remain below the lowest configured node before the function is disabled.
    1-65,534 [% / min]
    Specifies the dynamic response on changing the effective power for power increase. If the voltage changes, the effective power is changed with the specified gradient.
    Specifies the dynamic response on changing the effective power for power decrease. If the voltage changes, the effective power is changed with the specified gradient.
    Settling time
    1,000-120,000 [ms]
    Specifies the dynamic behavior on changing the effective power set value. In the event of a change in the voltage, the effective power is changed according to a PT-1 characteristic with a settling time of 5 tau.
    Active curve
    1-5
    Select active curve.
    Up to five characteristics can be configured independently and one of them can be enabled for regulation each time.
    Number of nodes
    2-5
    Up to five nodes can be configured. The power value of the first and last value pair is also used as the maximum or minimum effective power value, which is valid beyond the limits of the characteristic.
    Power
    0.0-100.0 [% Pref]
    Voltage
    80.0-126.0
    [% Unom]
    P(f)
    Adjusting the effective power P(f) in the event of overfrequency
    Feed-in inverters must assist with frequency stability in the interconnected grid. If the grid frequency leaves the normal tolerance range (e.g., ±200 MHz), the grid is in a critical state. In the event of overfrequency, there is a generation surplus; in the event of underfrequency, there is a generation deficit. Photovoltaic systems must adapt their power of feeding in relative to the frequency deviation. In the event of overfrequency, the power adjustment is determined by a maximum feed-in limit. The actual power of the inverter may vary freely below this limit due to a possible fluctuation in the available power or the set value, but at no time increases above the absolute power limit.
    Equation 1
    Equation 2
    Equation 1 defines the maximum limit with DP as per equation 2, PM the actual power at the time of activation, and Pref the reference power. Pref is defined as PM, the actual power at the time of activation. f is the actual frequency and f1 is the specified activation threshold.
    Equation 3
    Equation 4
    In some standards, the power adjustment is specified by a drop (s) instead of a gradient (g), as shown in equation 3. The drop s can be transformed into a gradient g in accordance with equation 4.
    The frequency f remains above the activation threshold f1 during an overfrequency event. Consequently, the expression (f1 – f) is negative and DP corresponds to a reduction in the power of feeding in.
    The measurement accuracy of the frequency is greater than 10 MHz.
    The specific mode of operation of the function is specified by the utility, the relevant standards, or the grid connection guidelines. The option to configure the function makes it possible to satisfy a wide variety of standards and guidelines. Certain configuration options are not available in some country settings because the relevant standards or grid connection guidelines prohibit adjustments.
    Adjusting the effective power P(f) in the event of underfrequency
    Some grid connection rules also require that the effective power P(f) be adjusted in the event of underfrequency. Because photovoltaic systems are typically operated in the maximum power point, a power reserve is not available to increase the power in the event of underfrequency.
    However, if the system is curtailed based on the market regulations, the effective power can be increased up to the available power. Because the inverter is unable to distinguish set values for the P constant between the utility's obligatory bottleneck management and market regulations, this must be implemented as part of the site-specific infrastructure for controlling the system.
    Example behavior with hysteresis
    Example behavior without hysteresis
    Parameters for P(f)
    Display
    Setting
    Description
    Operation mode
    Off | Mode 1 | Mode 2 | Mode 3
    Activate or deactivate function.
    Mode 1: Hysteresis active – Limit.
    Mode 2: Hysteresis inactive – Limit.
    In mode 1 and 2, the power is adjusted above or below the characteristic (depending on overfrequency or underfrequency) using a Pset command. Plim can also limit the power if there is an active P(f) characteristic.
    Mode 3: Hysteresis inactive – Set.
    In mode 3, the pre-fault power is saved and the power matches this characteristic.
    Dynamic gradient mode
    On | Off
    Enable dynamic gradient.
    "Gradient at under/overfrequency (feed-in)" is not displayed.
    Maximum dynamic gradient frequency
    50.22-70.5 [Hz]
    Dynamic gradient maximum frequency:
    If dynamic gradient mode is enabled, the gradient is calculated in order to guarantee a linear power adjustment and reach the maximum charging power if the frequency rises to the configured maximum frequency.
    Dynamic gradient minimum frequency:
    If dynamic gradient mode is enabled, the gradient is calculated in order to guarantee a linear power adjustment and reach the maximum power of feeding in if the frequency drops to the configured minimum frequency.
    Minimum dynamic gradient frequency
    45-50 [Hz]
    Activation threshold at underfrequency
    40-50 [Hz]
    Activation threshold (f1) underfrequency:
    Determines the frequency threshold for activating the function in case of underfrequency events. The effective power adjustment is activated if the frequency falls below the configured value and mode 1 or 2 is activated. In mode 2, the function is deactivated if the frequency rises above the configured value.
    Activation threshold (f1) overfrequency:
    Determines the frequency threshold for activating the function in case of overfrequency events. The effective power adjustment is activated if the frequency rises above the configured value and mode 1 or 2 is activated. In mode 2, the function is deactivated if the frequency falls below the configured value.
    Activation threshold at overfrequency
    50-60 [Hz]
    Deact. range lower limit
    40-50 [Hz]
    Only evaluated in mode 1.
    The function is deactivated if the frequency returns to the deactivation range and remains in this range for the duration the deactivation time.
    Deact. range upper limit
    50-60 [Hz]
    Deactivation time
    0-6,000,000 [ms]
    The function is deactivated if the frequency returns to the range between the minimum and maximum deactivation threshold and remains in this range for the duration of the deactivation time.
    Deact. lim. time after fault
    0-1,000 [s]
    Only evaluated in mode 2 and 3.
    The change in the effective power is limited to the configured gradient for the specified time after a fault.
    Deact. grad. incr. & decr. after fault
    0-65,534 [% / min]
    Specifies the dynamic response on changing the effective power for power increase and decrease. Any change in the effective power is limited to the configured value for the set period of time.
    Intentional delay
    0-5,000 [ms]
    Activation of the function based on the activation threshold is delayed by the configured time.
    This function is regarded as critical for the stability of the transmission grid and is therefore prohibited by several national grid connection regulations.
    This function is stipulated as a requirement by some national grid connection directives in order to prevent any negative impact on island detection. However, P(f) has no negative impact on the enhanced island detection.
    Settling time
    200-2,000 [ms]
    Specifies the dynamic behavior on changing the effective power limit. In the event of a change in the frequency, the effective power is changed according to a PT-1 characteristic with a settling time of 5 tau.
    0-65,534 [% / min]
    Specifies the dynamic response on changing the effective power for power increase and decrease. If the voltage changes, the effective power is changed with the specified gradient.
    0-65,534
    [%Smax/min]
    If the available power is above the actual output at the time of deactivation, the power increase back to the maximum power is limited. The limitation is implemented by an absolute power limitation that increases with a continuous gradient up to the maximum power. The actual power of the inverter may vary freely below this limit due to a possible fluctuation in the available power or the set power value, but at no time increases above the absolute power limit.
    The capacity of a generating system to remain immune to voltage dips and voltage spikes in the supply system is a key element in establishing a reliable energy supply. Interference immunity ensures that brief disruptions do not result in a loss of relevant generation capacity in a larger area of an interconnected grid. Grid support via fast feed-in of residual current also limits the spatial extent of the incident.
    The device offers this characteristic with its dynamic grid support by way of interference immunity. The ability to remain on the grid is the relevant factor. The protection settings also determine the device's ability to remain on the grid or not. Protection settings prevail over the capacity of interference immunity.
    1. Dynamic grid support
    Interference immunity against undervoltage
    Voltage dips above the limit curve (see figure below) can be overcome without the need for shutdown from the grid. The power of feeding in is constantly maintained within the limits of the maximum continuous current of the inverter.
    If a reduction in power occurs, the power is brought back up to the pre-fault level within 100 ms of the voltage returning.
    The inverter can overcome voltage fluctuations provided that the voltage level does not stay above the continuous operating voltage range for more than 100 s and does not rise above the short-term maximum operating voltage range (up to 100 s). The specific values for each inverter can be found here.
    The interface protection integrated in the inverter (voltage, frequency, anti-islanding) can be configured in a range that permits the above behavior. If, however, the setting of the interface protection limits the voltage/time characteristic, the interface protection triggers and interrupts the run-through as configured.
    Interference immunity characteristic in relation to the nominal voltage p(u)
    When dynamic grid support via fast feed-in of residual current is activated, residual current is fed-in in addition to the interference immunity properties against dips and spikes described above.
    The inverter adapts its current feed-in as soon as a dip or spike event occurs in order to bolster the mains voltage. The support takes place in the event of voltage dip with overexcited reactive current (corresponds to a capacitive load), and in the event of a voltage spike with underexcited reactive current (corresponds to an inductive load). In the reactive current priority mode, the active current is reduced to the extent necessary to comply with the limits of the maximum continuous current of the inverter.
    A dip or spike is detected if either the normal operating voltage range setting is exceeded by at least one phase-phase or phase-neutral voltage, or if a jump in the positive or negative sequence component of the voltage greater than the deadband setting occurs. The magnitude of the voltage jump of the positive and negative phase-sequence system equates to the difference between the pre-fault voltage and the actual voltage based on the reference voltage. The pre-fault voltage is calculated as the mean value over 50 periods.
    Formula 1
    The reactive current is adapted using a response time of < 20 ms and a settling time of < 60 ms after the event has occurred. Responses to changes in the voltage during the event or to the voltage recovery at the end of the event take place with the same dynamic.
    The formula for calculating the dynamic reactive current that is fed in for the positive and negative phase-sequence system is as follows:
    Formula 2, depending on the nominal current IN of the inverter
    DFor the positive and negative phase-sequence system, u equates to the difference between the pre-fault voltage and the current voltage in relation to the reference voltage. The pre-fault voltage is calculated as a 1-min mean value.
    Formula 3
    On account of the definition of a voltage jump in pre-norm EN50549-2 and in VDE-AR-N 4120 and VDE-AR-N 4110, it is typically the case that another voltage jump is detected when the event is at an end, when the fault is rectified, and when the voltage returns to a fault-free state. The result of this is that in an active operating mode, the dynamic grid support via a fast feed-in of residual current remains active even after the event has passed, and that reactive current is fed in according to formulas (2) and (3). Dynamic grid support using fast feed-in of residual current is then deactivated after a configured minimum support time, usually 5 s.
    The inverter stops feeding in current if the zero current threshold is exceeded. If the inverter is feeding in reactive power before the fault, the reactive power is reset to the value before the fault Q with the settling time configured in the activated reactive power control mode after the fault.
    Formula 4
    Parameters for FRT
    Display
    Setting
    Description
    FRT (Fault Ride Through)
    The device supports dynamic grid stabilization (fault ride through).
    Operation mode
    On | Off
    Setting: Manual
    All parameters can be configured independently.
    Setting: Predefined zero current
    Dynamic grid support active on account of interference immunity and zero current feed-in. During a voltage event, the current in the inverter is reduced to zero.
    All parameters are pre-configured, only the activation threshold for zero current has to be configured.
    Settings
    Manual | Predefined zero current
    Priority – limitation
    Reactive current | Active current priority
    Priority: Reactive current priority
    Dynamic grid support active on account of interference immunity and fast feed-in of residual current. The inverter feeds in additional reactive current according to formulas (2) and (4).
    Priority: Active current priority
    Dynamic grid support active on account of interference immunity and fast feed-in of residual current with active current priority. The inverter feeds in as much effective power as available. If, as a result of this, the maximum continuous current is not achieved, the inverter supplies additional reactive current according to formulas (2) or (4) up to the continuous current limitation.
    Zero current undervoltage threshold
    0-184 V
    If one or more phase-phase or phase-neutral conductor voltages exceed the configured threshold, the inverter switches to zero current mode. The total current is regulated to virtually zero.
    Zero current overvoltage threshold
    253-340 V
    0-80 [% Unom]
    108-129 [% Unom]
    Reference voltage
    80-110 [% Unom]
    Nominal value of the phase-neutral conductor voltage used as a reference voltage for formulas (1) and (3). Adjustable in the range from level 1 undervoltage protection to level 1 overvoltage (surge) protection.
    Constant k negative sequence dip and swell
    k 0-10
    Amplification factor for the negative phase-sequence system used in the calculation of the reactive current using formulas (2) and (4). Can be configured independently for drops and spikes.
    Constant k positive sequence dip and swell
    k 0-10
    Dead band
    2-120 [% Uref]
    Dynamic grid support through fast feed-in of residual current is activated in the case of voltage events with a voltage change greater than the dead band.
    Reference voltage
    80-110.0 [% Unom]
    Dynamic grid support via fast feed-in of residual current is activated in the case of voltage events with at least one phase-phase or phase-neutral conductor voltage outside the configured normal operating voltage range. Dynamic grid support via fast feed-in of residual current is deactivated when the voltage returns to the reference operating voltage range.
    Minimum operating voltage activation
    45-125.0 [% Unom]
    Maximum operating voltage activation
    45-125.0 [% Unom]
    Minimum operating voltage deactivation
    0-max [V]
    Dynamic grid support via fast feed-in of residual current is deactivated if the voltage is within the configured deactivation range. This parameter is only available for the country-specific settings VDE 4105, CH 4105, and UD.
    Maximum operating voltage deactivation
    0-max [V]
    Dynamic reactive current only
    Off | On
    Standard: The reactive current according to formulas (2) and (4) is fed in as additional reactive current. This means that the sum of the pre-fault and additional reactive current is fed in.
    Dynamic only: The reactive current according to formulas (2) and (4) is fed in as absolute reactive current. This means that regardless of the reactive current before the voltage event, only the reactive current according to formulas (2) and (4) is fed in during the voltage event.
    Dead band mode
    Mode 1 | Mode 2
    Mode 1: When calculating the reactive current, the value of the dead band is not subtracted from the amount of voltage change. As such, formula (2) applies to overvoltage and undervoltage events.
    Mode 2: When calculating the reactive current, the value of the dead band is subtracted from the amount of voltage change. As such, formula (4) applies to overvoltage and undervoltage events:
    104-248 [V]
    Dynamic grid support via fast feed-in of residual current is activated in the case of voltage events with at least one phase-phase or phase-neutral conductor voltage outside the configured normal operating voltage range. Dynamic grid support via fast feed-in of residual current is deactivated when the voltage returns to the normal operating voltage range.
    104-288 [V]
    Reactive current limitation
    0-100 [% Imax]
    The reactive power component of the fast feed-in of residual current is limited to permit a defined proportion of the active current component.
    Minimum support time
    1,000-15,000 [ms]
    If activated due to a voltage jump in accordance with formula (1) and the configured dead band, the dynamic grid support via fast feed-in of residual current is deactivated after the minimum support time elapses.
    Deactivation delay
    0 [ms] / 0-500 [ms] IL_LV / UD / 500 [ms] IL-MV
    Deactivates dynamic current support after the desired delay as soon as the voltage enters the normal operating range again. This parameter is only available for the country-specific settings IL_LV, IL-MV, and UD.
    The maximum effective and apparent power to be installed for a generation system is agreed between the utility and system operator. The device capacity of a system can be set to the exact agreed value using the Slim and Plim settings. To ensure that the load on the devices in a system is uniform, we recommend distributing the power reduction evenly across all devices.
    Some grid connection rules require that the agreed reactive power be supplied from every operating point of the system without a reduction in the actual effective power. Given that the inverter has the full P-Q operating range, a reduction in the effective power is, however, required during operation at maximum effective power because an apparent power reserve is not available.
    By adjusting Plim, the maximum effective power can be limited in order to establish an apparent power reserve and ensure that the agreed reactive power can be delivered from every effective power operating point.
    The diagram below shows the appropriate P-Q operating range with a required example effective power of 48% of the maximum apparent power of the system or 43% of the maximum effective power of the system.
    P-Q operating range with limited effective power for PV inverters
    The power limitation parameters can be adjusted using SunSpec model DID123. During this process, you should also check whether the internal and/or external power limitation is active.
    Internal power limitation
    Parameters for external power limitation
    Parameters for power limitation
    Status = active
    Status = active
    Parameters in SunSpec Model 123:
    Maximum apparent power Slim= 100,000 VA
    "WMaxLimPct" = 50% Plim (approx. 40,000 W)
    "WMaxLimPct_RvrtTms" = 60 s
    "WMaxLimPct_RmpTms" = 2 s
    "WMaxLim_Ena" = 1
    Maximum active power Plim= 80% (approx. 80,000 W)
    AC fallback active power Pfb = 75% Plim (approx. 60,000 W)
    PT1 settling time = 1 s
    If the ramp time "WMaxLimPct_RvrtTms" in the SunSpec model is specified as 0 s, the internal output gradient is used. Otherwise, the set value will be used.
    Irrespective of the communication protocol used, the settling time "WMaxLim_Ena" is used to transfer the new power value. Otherwise, the internally configured value is used. The additional ramp time "WMaxLimPct_RmpTms" specifies the jump time from one power value to the new power value.
    The following formulas are used to calculate the gradient Slim/min:
    Power gradient according to sample parameters and calculation
    The following formulas are used to calculate the Q filter parameter and cos j gradient:
    Formula for calculating the Q filter parameter
    Formula for calculating the cos j gradient (internal power gradient)
    1. Other grid-supporting functions in the case of effective power
    Status = active
    Status = active
    "WMaxLim_Ena" = 1
    Display
    Setting
    Description
    Power limitation
    Check activation
    Activate or deactivate the power limitation.
    Maximum apparent power (Slim)
    1,000-Smax [VA]
    The apparent power is limited globally to the configured value in VA. Once Slim has been configured, all of the active and reactive power control values will use Slim as 100% instead of Smax.
    Maximum active power (Plim)
    1-100 [% Slim]
    The effective power is limited globally to the configured value in % Slim.
    A soft start up function is available to prevent the grid from being negatively impacted by a sudden increase in feed-in power from the inverters.
    When the inverter is activated or switched on, the increase in power is limited by the set gradient.
    It is possible to configure:
    • Whether the soft start-up should occur every time the device is switched on
    • Whether the soft start-up should occur only upon initial start-up each day
    • Whether the soft start-up should occur only when starting up after the device has been switched off by the grid protection
    Primarily because there is a risk that many systems could increase their power levels simultaneously after they have been switched off by the grid protection, a soft start-up is usually only required for start-up after a device has been switched off by the grid protection.
    The soft start up is implemented by an absolute power limitation that increases with a continuous gradient up to the maximum power. The actual power of the inverter may vary freely below this limit due to a possible fluctuation in the available power or the set value, but at no time increases above the absolute power limit.
    In the case of very large systems, it may be necessary to limit the maximum change in power during normal operation. The grid power feed-in is increased or decreased according to the configured gradients when the specified set value (for increasing and decreasing power) is changed and when the solar irradiation (for increasing power) is changed. The change in power cannot be limited if solar irradiation is reduced.
    The function is not active if there are changes in power that are defined by a different grid support function, such as power recovery after fault ride through, P(f), P(U).
    Due to decentralized generation, there is the possibility that a deactivated part of the grid will remain live in an unintended island due to a local balance between load and generation in this part of the grid. The detection of unintended island formation is an important function of decentralized generating units and plays a role in preventing damage to equipment as well as ensuring the safety of personnel.
    Depending on the structure and operation of the distribution grid, there are a number of dangers:
    • In case of maintenance work in a distribution grid, persons may be endangered if the deactivated part of the grid remains live as an island. This is especially the case if not all safety rules are followed.
    • If fast reclosure is used in a distribution grid and the deactivated part of the grid remains live as an island, reclosure will likely occur with a phase shift, which could damage rotating machinery in the grid.
    • In the event of a fault in a medium-voltage grid, the faulty part of the grid is disconnected. If the fault has a significant resistance, the deactivated part of a medium-voltage grid remains live as an island. Depending on the type of fault, but explicitly in the case of a fault in the transformer, dangerous medium voltage might be present in exposed areas, even on low-voltage appliances.
    In the case of the last example in particular, the generating units need to be disconnected very quickly to cause the forming island to collapse. At the same time, any island formation detection method may cause false tripping. The industry is therefore working continually to develop methods that are fast and reliable and can also be depended on to prevent false tripping.
    1. Enhanced island detection
    Enhanced island detection uses a reliable island detection strategy based on the characteristic differences between an interconnected grid and an islanded grid, thus ensuring rapid and reliable detection and prevention of false tripping.
    An interconnected grid is dominated by rotating machinery, so the frequency is proportional to the effective power balance and the voltage is proportional to the reactive power balance. By contrast, an islanded grid behaves like an oscillating circuit, so the frequency is proportional to the reactive power balance and the voltage is proportional to the effective power balance. The active enhanced anti-islanding method detects this difference by monitoring the behavior of the grid. The enhanced anti-islanding method monitors the natural fluctuation in the grid frequency and injects a minimal reactive power that is proportional to the rate of change of the frequency. In the moment an island is formed, the connected grid closes a positive feedback loop which allows the inverter to detect the change in the situation and to disconnect. If an island forms, the inverter disconnects within several 100 ms, and well below 1,000 ms.
    • The number of inverters connected in parallel does not affect the reliability of this function.
    • This method also guarantees that effects on the distribution grid are minimized.
    • The function has not been found to have any effects on harmonic content, flicker, and grid stability during normal operation.
    This detection method is combined with a two-stage passive rate of change of frequency (ROCOF) observation. If the ROCOF of the grid exceeds the configured shutdown threshold (stage 1) for the configured shutdown time, the device switches to zero current mode. If the ROCOF of the grid exceeds the configured shutdown threshold (stage 2) for the shutdown disconnection time, the device switches off. In case of an island, this will shut down the island instantaneously. If the grid stabilizes, which might be the case if the ROCOF event was due to a brief disturbance in the grid, the inverter will resume normal operation. If stage 1 is active, the device has switched to zero current mode and will recommence feed-in after a few 100 ms. If stage 2 is active, the device has switched off and the configured reconnection conditions apply.
    Q on Demand
    Q on Demand
    DANGER!
    If night shutdown is disabled ("Q on Demand" mode), there may still be a high level of DC voltage on both the string collector and the device, despite the string collector being switched off.
    Severe injury and death may result.
    The device must also be disconnected from the power supply on the AC side when carrying out maintenance.
    We recommend that a danger notice to this effect be affixed to the string collector.
    The "Q on Demand" function can also provide a reactive power Q outside of grid power feed operation to stabilize the grid (e.g., at night).
    Important prerequisites:
    • The "Night Shutdown" function has been disabled in the menu
    • Device is connected on the AC side
    • Device has been in grid power feed operation.
    The specifications that the inverter receives from the utility through the system controller via Ethernet or RS485 take first priority. The parameters for Q constant and Q(U) stored in the inverter take second priority.
    If the AC supply is disconnected during "Q on Demand" operation outside of grid power feed operation, the "Q on Demand" function can only be used again following proper grid power feed operation (if there is an adequate DC supply). The existing "Night Shutdown" that has been deactivated also remains active.
    The following figures show normal operation in the P-Q operating range during the day (grid power feed operation) (1) and "Q on Demand" operation at night (2).
    Only reactive power is produced at night. A small amount of effective power will inevitably be required for the internal power supply in order to keep the pre-configured reactive power functions in "Q on Demand" mode (see item 2 in the negative P range).
    (1) Normal operation: Effective power and reactive power supply at different voltages.
    (2) "Q on Demand" operation: Reactive power supply with nominal grid voltage outside grid power feed operation.
    1. Q on Demand
    Q on Demand
    DANGER!